One other thing to consider when looking at fire apparatus suction pressure is 
pressure losses in the LDH to the pump suction.  If you have to lay 250- 500 ft 
of hose from a hydrant with only 5-10 psi, what do you have at the pump suction 
at the apparatus?  You can't assume the hose will be in a perfect straight line.



Craig L. Prahl 
Fire Protection Group Lead
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29303
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]


-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of [email protected]
Sent: Monday, December 08, 2014 9:55 AM
To: [email protected]
Subject: RE: A Poll of the Experienced

Absolutely agree with you about the non-value of extrapolating the flow test 
beyond the observed flow. The part I'm not so sure I would agree with is 
requiring the 20 psi minimum at the onsite hydrants. The IFC commentary notes 
that the 20 psi is used because it is the recommended minimum pressure "for 
fire engine use by the water authorities in order to minimize the possibility 
of creating a negative pressure in the water main and the resulting damage to 
the water supply system." Many of the buildings we are involved in require 
4,000 gpm. They have private fire loops around the property with usually two 
connections (with BFP's)  to the city water system. Doing the hydraulics 
flowing 1,000 gpm @ 20 psi for the most demanding four hydrants usually 
requires a minimum pressure of around 45-50 psi at the city connections. I 
don't see how taking the pressure in the private fire loop below 20 would 
damage anything in the municipal system because the pressure would always be 
above 20 psi at the connection to the city mains. I don't know about the effect 
on the pumper truck but I think as long as they have water at any pressure they 
will continue pumping.
Ron F

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of [email protected]
Sent: Monday, December 08, 2014 6:52 AM
To: [email protected]
Subject: RE: A Poll of the Experienced

Ah, Fire Flow.  Now you will gets heads spinning.

First, let's start with the basics.  There are at least five methods used by 
various authorities to determine Fire Flow.  So if you are dealing with this, 
be sure Appendix B is the correct method used by the local/state fire 
authority.  Section 507 in the IFC states that Fire Flow is to be determined by 
an "Approved Method".  AHJ will provide or confirm that approved method.  
Appendix B is not part of the Code and is not always adopted through the legal 
adoption process, that's why you have to ask, you can't assume.

But let's say we're past that and Appendix B is the approved method.

The next step is you need to also verify that the local AHJ will permit the 
flow reduction rate based on sprinklers, do not assume that to be the case.  
I'm assuming that you might have a warehouse with a fairly high hazard level if 
you're using ESFR so in cases such as that or where chemicals or other high 
hazards are present I have had the AHJ deny the reduction.  So be sure, don't 
assume you can apply the reduction.

So you've gone down the chart and found your building requires 8000 gpm for 4 
hours.   The city supply or private fire service system needs to be able to 
provide that flow and duration to the fire loop serving the hydrants.   A 
minimum of 20 psi residual needs to be available at every hydrant on the loop.  
This is will be the suction pressure for pumper apparatus.   You can assume 
that in an event that would require 8000 gpm there will be multiple pumpers 
connected to multiple hydrants.  

The other issue when dealing with a municipal supply is make sure they can 
ACTUALLY supply the demand.  I've had too many single outlet flow tests and the 
testing agency extrapolated the curve to show they can meet the demand.  I 
reject those tests.  When conducting follow-up tests involving multiple 
hydrants, more often than not was it proven that the municipality could not 
actually flow that much water through their system.   Extrapolated tests are 
worthless.  You need real data.

So the 20 psi pressure needs to be at the hydrants.

Fire flow is the water needed to actually fight the fire through the use of 
manual hand hose lines.  This is totally separate and unrelated to sprinkler 
flow and hose stream allowance.

I was involved with a project for a warehouse where the fire fight lasted 13 
hours, needless to say they used a LOT of water.   

This is one topic where the majority of fire protection engineers and designers 
have not been educated.  It is a Code requirement, not an option as most think. 
  



Craig L. Prahl 
Fire Protection Group Lead
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29303
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]


-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of [email protected]
Sent: Friday, December 05, 2014 9:29 PM
To: [email protected]
Subject: Re: A Poll of the Experienced

I think I agree with you, but to be very specific, let's assume I'm designing a 
new building on a greenfield site which is served by a public water system. The 
building is type V construction, 600,000 square feet and fully protected with 
ESFR sprinklers. Table B105.2 indicated a fire flow rate of 8000 GPM, reduced 
to 4000 GPM for sprinkler credit, at minimum 20psi. My question is, WHERE is 
this 4000 GPM at 20 psi measured? At the city water main connection? Or at the 
fire pump discharge? 

Mark at Aero
602 820-7894

 
> 
> -------- Original message --------
> From: [email protected]
> Date:12/05/2014 8:12 PM (GMT-06:00)
> To: [email protected]
> Subject: A Poll of the Experienced
> 
> Over this weekend I'd like to ask the opinion of those forumites experienced 
> in the reading and understanding of the "International Fire  Code" on the 
> topic of "Fire Flow" described in Chapter 5, and further prescribed in 
> Appendix B. Is the available flow rate and residual pressure referenced, 
> intended to describe these values of the municipal or private water supply 
> available to the building site? Or, the minimum output of any fire pump 
> associated specifically with the automatic sprinkler system in the building?
> Any takers? Questions? Clarifications?
> Thanks for any answers.
> 
> Mark at Aero
> 602 820-7894
> 
> Sent from my iPhone
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to