There is a section in the IBC that tries to address the fact that fire alarm 
zones and sprinklers zones are different sizes and that the larger sprinkler 
zone is NOT limited to the size of the fire alarm zone. See section 907.6.4

Roland


Roland Huggins, PE - VP Engineering
American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives
Dallas, TX
http://www.firesprinkler.org <http://www.firesprinkler.org/>



> On Apr 13, 2016, at 11:20 AM, Travis Mack, SET <[email protected]> wrote:
> 
> I have a reviewer stating that the fire sprinkler plan has to match the 
> evacuation plan and the smoke zones of the fire alarm plan. This is an I-2 
> Occupancy.  Has anyone ever come across this?  After 3 weeks in plan review, 
> he kicked it back saying he can't review until we provide this information. 
> It is the first time I have ever heard of this.
> 