Just a heads-up Travis,
It might go deeper than matching footprints- that is rarely a problem.
A problem would be if the exhaust rate sizer used QR, 165F, at max 225
S.F., but you, being a 13 aficionado, installed QR, 200F, at 324 S.F.

In a ~16 ft ceiling the exhaust rate would fall about 20,000 CFM short...

ballpark figures, of course.

Brad
On Apr 13, 2016 5:42 PM, "Roland Huggins" <[email protected]>
wrote:

> There is a section in the IBC that tries to address the fact that fire
> alarm zones and sprinklers zones are different sizes and that the larger
> sprinkler zone is NOT limited to the size of the fire alarm zone. See
> section 907.6.4
>
> Roland
>
>
> Roland Huggins, PE - VP Engineering
> American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives
> Dallas, TX
> http://www.firesprinkler.org <http://www.firesprinkler.org/>
>
>
>
> > On Apr 13, 2016, at 11:20 AM, Travis Mack, SET <[email protected]>
> wrote:
> >
> > I have a reviewer stating that the fire sprinkler plan has to match the
> evacuation plan and the smoke zones of the fire alarm plan. This is an I-2
> Occupancy.  Has anyone ever come across this?  After 3 weeks in plan
> review, he kicked it back saying he can't review until we provide this
> information. It is the first time I have ever heard of this.
> >
> > Travis Mack, SET
> > MFP Design, LLC
> > 2508 E Lodgepole Drive
> > Gilbert, AZ 85298
> > 480-505-9271
> > fax: 866-430-6107
> > email:[email protected]
> >
> > http://www.mfpdesign.com
> > https://www.facebook.com/pages/MFP-Design-LLC/92218417692
> > Send large files to us via: https://www.hightail.com/u/MFPDesign
> > LinkedIn: https://www.linkedin.com/in/travismack
> >
> >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> >
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to