Just a heads-up Travis, It might go deeper than matching footprints- that is rarely a problem. A problem would be if the exhaust rate sizer used QR, 165F, at max 225 S.F., but you, being a 13 aficionado, installed QR, 200F, at 324 S.F.
In a ~16 ft ceiling the exhaust rate would fall about 20,000 CFM short... ballpark figures, of course. Brad On Apr 13, 2016 5:42 PM, "Roland Huggins" <[email protected]> wrote: > There is a section in the IBC that tries to address the fact that fire > alarm zones and sprinklers zones are different sizes and that the larger > sprinkler zone is NOT limited to the size of the fire alarm zone. See > section 907.6.4 > > Roland > > > Roland Huggins, PE - VP Engineering > American Fire Sprinkler Assn. --- Fire Sprinklers Saves Lives > Dallas, TX > http://www.firesprinkler.org <http://www.firesprinkler.org/> > > > > > On Apr 13, 2016, at 11:20 AM, Travis Mack, SET <[email protected]> > wrote: > > > > I have a reviewer stating that the fire sprinkler plan has to match the > evacuation plan and the smoke zones of the fire alarm plan. This is an I-2 > Occupancy. Has anyone ever come across this? After 3 weeks in plan > review, he kicked it back saying he can't review until we provide this > information. It is the first time I have ever heard of this. > > > > Travis Mack, SET > > MFP Design, LLC > > 2508 E Lodgepole Drive > > Gilbert, AZ 85298 > > 480-505-9271 > > fax: 866-430-6107 > > email:[email protected] > > > > http://www.mfpdesign.com > > https://www.facebook.com/pages/MFP-Design-LLC/92218417692 > > Send large files to us via: https://www.hightail.com/u/MFPDesign > > LinkedIn: https://www.linkedin.com/in/travismack > > > > > > _______________________________________________ > > Sprinklerforum mailing list > > [email protected] > > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org > _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org