You won't find it Matthew.
I am like one of those old style kites that lost its tail-- I'm way out
there dude. .. ... ....
On Apr 13, 2016 6:46 PM, "Matthew J Willis" <[email protected]> wrote:

> Ok, first thing in the am, I am re reading 13 on where any of this applies
> to a sprinkler drawing....
>
>
>
> Sent from my Verizon Wireless 4G LTE smartphone
>
>
> -------- Original message --------
> From: Brad Casterline <[email protected]>
> Date: 04/13/2016 5:44 PM (GMT-07:00)
> To: [email protected]
> Subject: Re: Fire Sprinkler Plan to Match Evacuation Plan??
>
> Just a heads-up Travis,
> It might go deeper than matching footprints- that is rarely a problem.
> A problem would be if the exhaust rate sizer used QR, 165F, at max 225
> S.F., but you, being a 13 aficionado, installed QR, 200F, at 324 S.F.
>
> In a ~16 ft ceiling the exhaust rate would fall about 20,000 CFM short...
>
> ballpark figures, of course.
>
> Brad
> On Apr 13, 2016 5:42 PM, "Roland Huggins" <[email protected]>
> wrote:
>
> > There is a section in the IBC that tries to address the fact that fire
> > alarm zones and sprinklers zones are different sizes and that the larger
> > sprinkler zone is NOT limited to the size of the fire alarm zone. See
> > section 907.6.4
> >
> > Roland
> >
> >
> > Roland Huggins, PE - VP Engineering
> > American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives
> > Dallas, TX
> > http://www.firesprinkler.org <http://www.firesprinkler.org/>
> >
> >
> >
> > > On Apr 13, 2016, at 11:20 AM, Travis Mack, SET <[email protected]>
> > wrote:
> > >
> > > I have a reviewer stating that the fire sprinkler plan has to match the
> > evacuation plan and the smoke zones of the fire alarm plan. This is an
> I-2
> > Occupancy.  Has anyone ever come across this?  After 3 weeks in plan
> > review, he kicked it back saying he can't review until we provide this
> > information. It is the first time I have ever heard of this.
> > >
> > > Travis Mack, SET
> > > MFP Design, LLC
> > > 2508 E Lodgepole Drive
> > > Gilbert, AZ 85298
> > > 480-505-9271
> > > fax: 866-430-6107
> > > email:[email protected]
> > >
> > > http://www.mfpdesign.com
> > > https://www.facebook.com/pages/MFP-Design-LLC/92218417692
> > > Send large files to us via: https://www.hightail.com/u/MFPDesign
> > > LinkedIn: https://www.linkedin.com/in/travismack
> > >
> > >
> > > _______________________________________________
> > > Sprinklerforum mailing list
> > > [email protected]
> > >
> >
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> >
> >
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> >
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to