NFPA 25 does not require the inspection of sprinklers in concealed spaces,
so that should not be an issue.

 

 

Thank you,

 

Bob Knight, CET III

Fire by Knight, LLC

208-318-3057

 

From: Sprinklerforum [mailto:[email protected]]
On Behalf Of David Williams via Sprinklerforum
Sent: Thursday, August 15, 2019 12:43 PM
To: [email protected]
Cc: David Williams
Subject: Attic/Concealed space access to sprinkler heads

 

I have a project intended to be fully sprinkled with a combustible attic
that tapers from 2' to 4 ' without being filled to within 2 inches of the
deck with insulation. So I am planning on a dry pipe system with standard
heads as the design of the attic does not allow the effective use of special
application attic sprinklers.

 

The questions are: whether inspection access is required to be provided, is
it prudent to do so at the heads, or can the locations just be noted on the
gypsum mounted to the bottom chord of the open web trusses.

 

TIA

 