What Ron said. Some poor fitter out in Oct looking for low points and on a 
schedule....

Best.

> On Aug 15, 2019, at 12:55, Ron Greenman via Sprinklerforum 
> <sprinklerforum@lists.firesprinkler.org> wrote:
> 
> I didn't mean to suggest that you didn't need access to low points. You do, 
> and you need to put the sign on them or next to them, but you also need to 
> note where they are on the general info sign. Too many low points drain get 
> lost in the insulation. I think it was Bob that said inspections per 25 only 
> had to be made from the floor (or that's what he meant 🙊), but Scott makes 
> some good points about the difficulty that might be encountered for other 
> activities.
> 
> 
> Ron Greenman
> 
> rongreen...@gmail.com
> 
> 253.576.9700
> 
> The Universe is monstrously indifferent to the presence of man. -Werner 
> Herzog, screenwriter, film director, author, actor and opera director (1942-)
> 
> 
>> On Thu, Aug 15, 2019 at 12:41 PM David Williams via Sprinklerforum 
>> <sprinklerforum@lists.firesprinkler.org> wrote:
>> Nope I think 6/12 top surface 4/12 lower..
>> 
>>  
>> 
>> David T Williams – Lead MEP/FP Engineer
>> 
>>  
>> 
>> LHB, Inc. | PERFORMANCE DRIVEN DESIGN.
>> 
>>  
>> 
>> From: Travis Mack <tm...@mfpdesign.com> 
>> Sent: Thursday, August 15, 2019 2:40 PM
>> To: sprinklerforum@lists.firesprinkler.org
>> Cc: b...@firebyknight.com; David Williams <david.willi...@lhbcorp.com>
>> Subject: Re: Attic/Concealed space access to sprinkler heads
>> 
>>  
>> 
>> What is your attic slope? Is <2:12 then you need specially listed sprinklers 
>> for the areas <36” deep. 
>> 
>> Travis Mack, CFPS, CWBSP, RME-G, SET
>> 
>> 480-505-9271
>> 
>> MFP Design, LLC
>> 
>> www.mfpdesign,com
>> 
>> Send large files to MFP Design via:
>> 
>> https://www.hightail.com/u/MFPDesign
>> 
>>  
>> 
>> Sent from my iPhone
>> 
>> 
>> On Aug 15, 2019, at 12:02 PM, David Williams via Sprinklerforum 
>> <sprinklerforum@lists.firesprinkler.org> wrote:
>> 
>> Thanks.. I didn’t see it  either but I wanted to see if there were other 
>> opinions/options.
>> 
>>  
>> 
>> David T Williams – Lead MEP/FP Engineer
>> 
>>  
>> 
>> LHB, Inc. | PERFORMANCE DRIVEN DESIGN.
>> 
>>  
>> 
>> From: Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org> On 
>> Behalf Of Bob Knight via Sprinklerforum
>> Sent: Thursday, August 15, 2019 1:59 PM
>> To: sprinklerforum@lists.firesprinkler.org
>> Cc: Bob Knight <b...@firebyknight.com>
>> Subject: RE: Attic/Concealed space access to sprinkler heads
>> 
>>  
>> 
>> NFPA 25 does not require the inspection of sprinklers in concealed spaces, 
>> so that should not be an issue.
>> 
>>  
>> 
>>  
>> 
>> Thank you,
>> 
>>  
>> 
>> Bob Knight, CET III
>> 
>> Fire by Knight, LLC
>> 
>> 208-318-3057
>> 
>>  
>> 
>> From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] 
>> On Behalf Of David Williams via Sprinklerforum
>> Sent: Thursday, August 15, 2019 12:43 PM
>> To: sprinklerforum@lists.firesprinkler.org
>> Cc: David Williams
>> Subject: Attic/Concealed space access to sprinkler heads
>> 
>>  
>> 
>> I have a project intended to be fully sprinkled with a combustible attic 
>> that tapers from 2’ to 4 ‘ without being filled to within 2 inches of the 
>> deck with insulation. So I am planning on a dry pipe system with standard 
>> heads as the design of the attic does not allow the effective use of special 
>> application attic sprinklers.
>> 
>>  
>> 
>> The questions are: whether inspection access is required to be provided, is 
>> it prudent to do so at the heads, or can the locations just be noted on the 
>> gypsum mounted to the bottom chord of the open web trusses.
>> 
>>  
>> 
>> TIA
>> 
>>  
>> 
>> David T Williams, PE – Lead MEP/FP Engineer
>> 
>> 21 West Superior Street, Suite 500, Duluth, MN 55802
>> 
>> Direct 218.279.2436 | Cell 218.310.2446
>> 
>> LHBcorp.com
>> 
>>  
>> 
>> LHB, Inc. | PERFORMANCE DRIVEN DESIGN.
>> 
>>  
>> 
>> _______________________________________________
>> Sprinklerforum mailing list
>> Sprinklerforum@lists.firesprinkler.org
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>> 
>> _______________________________________________
>> Sprinklerforum mailing list
>> Sprinklerforum@lists.firesprinkler.org
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to