Just tried that and the POT still does nothing. Now it just sits at 27.6v 
constantly.

-- 
Christopher Tyler 
MTCRE/MTCNA/MTCTCE/MTCWE 
Total Highspeed Internet Services 
417.851.1107

- Original Message -
From: George Skorup (Cyber Broadcasting) geo...@cbcast.com
To: af@afmug.com
Sent: Thursday, April 9, 2015 9:40:04 AM
Subject: Re: [AFMUG] Low Voltage Disconnect

22-23 volts I think is the bottom of the adjustment range on the TSP 
power supply. At least you know the remote cable is working because the 
BCM can shut down the power supply. Try disconnecting the remote cable 
and adjust the pot on the power supply up to 27.6 volts. Power off, then 
reconnect the remote cable and power back up.

It was quite a while ago, but I think that's the same problem I had on 
the BCM48. If the PS is turned all the way down, it sorta acts like a 
limiter, so the BCM can't say hey, I need all your volts!

On 4/9/2015 9:29 AM, Christopher Tyler wrote:
 Looks like I have a bad BCM maybe. I disconnected the battery and the temp 
 sensor and left the remote wire connected.
 I adjusted the pot on the BCM, and it does nothing at all.
 The remote wire is definitely connected correctly, if I turn off the BCM it 
 turns off the power supply, turn it back on, and after a few seconds it turns 
 the power supply back on.




Re: [AFMUG] Low Voltage Disconnect

2015-04-09 Thread George Skorup (Cyber Broadcasting)
Yep, sounds like there's something messed up with the remote voltage 
control. Hard to tell if it's the PS or the BCM, unless you have another 
set.


On 4/9/2015 11:12 AM, Christopher Tyler wrote:

When I cut off AC power it switches over to battery just fine.
It's just the power supply control that appears to be broken, everything else 
seems to work. I followed the instructions line for line when I got it and it 
didn't appear to work properly then either, so I think I just got a bad unit. 
Should still be under warranty so, I'll see about getting an RMA for it and 
thanks for the additional information, all very good information to keep in 
mind.





Re: [AFMUG] Low Voltage Disconnect

2015-04-09 Thread Christopher Tyler
Looks like I have a bad BCM maybe. I disconnected the battery and the temp 
sensor and left the remote wire connected.
I adjusted the pot on the BCM, and it does nothing at all.
The remote wire is definitely connected correctly, if I turn off the BCM it 
turns off the power supply, turn it back on, and after a few seconds it turns 
the power supply back on.

-- 
Christopher Tyler 
MTCRE/MTCNA/MTCTCE/MTCWE 
Total Highspeed Internet Services 
417.851.1107

- Original Message -
From: George Skorup (Cyber Broadcasting) geo...@cbcast.com
To: af@afmug.com
Sent: Wednesday, April 8, 2015 7:41:14 PM
Subject: Re: [AFMUG] Low Voltage Disconnect

If the temp comp probe isn't connected, it assumes 25C/77F, IIRC. I 
would definitely not run it without the temp probe unless this is in a 
NOC or controlled shelter type environment.

There's a jumper that controls the battery type in use. Gel for gel, SLA 
for VRLA, AGM, etc. That also does something with the LVD, but I don't 
remember what. The temp compensation also has an effect on the LVD. It's 
all microprocessor controlled.

With the remote cable connected and batteries + temp sensor 
disconnected, adjust the pot on the BCM (not the power supply) for your 
desired float voltage with a meter on the battery terminals. I usually 
set it to 27.6. Do not touch that potentiometer with the sensor, 
batteries or load connected.

Power everything off then connect the temp probe and batteries. Power it 
back up. Like Ken said, the BCM adjusts the TSP power supply output 
voltage. Check battery output voltage at the BCM, look at your shunt 
reading or clamp-on ammeter, etc. You should see 1 amp (that's the BCM 
current limit) if the batteries are 90% or so.

The LVD will cut off at 1.83 volt per cell for SLA. The BATT-OK contact 
will open slightly before the LVD kicks in as an early warning (awesome 
feature). So 22V for the BCM24 and 44V for the BCM48. That is very, very 
conservative if you ask me, especially for a UPS. The batteries are not 
being cycled daily like solar. AGMs can be taken down very deep in a 
typical UPS situation and not sustain any damage or loss of capacity. 
Again, this is not solar.

The Mean Well AD-155 LVD is much lower. Like 19.5V for the 155B, IIRC. 
Fine with me since I put those at smaller sites with smaller batteries, 
and they're cheap batteries, so if it ruins them, oh well, replace.

On 4/8/2015 5:54 PM, Ken Hohhof wrote:
 With the Traco setup, the BCM controls the power supply voltage to be 
 what is needed to charge the batteries.  The loads get that same 
 voltage, so the output will be 27 or 28 volts not 24.

 Is there a possibility the battery remote temperature probe is not 
 connected correctly or is bad?  I don't know what happens if that is 
 open.  Some chargers will assume 27*C if the probe is missing, I don't 
 know what Traco does.


 -Original Message- From: Bill Prince
 Sent: Wednesday, April 08, 2015 5:02 PM
 To: af@afmug.com
 Subject: Re: [AFMUG] Low Voltage Disconnect

 I've never used this setup, but with the chargers/controllers I've used,
 the output of the power supply has to be greater than 24V. In fact,
 doesn't the output of the power supply have to be at least 28 or 28.5
 volts? This would allow the battery controller to modulate the output to
 the batteries, whether it be bulk, absorption, or float?


 bp
 part15sbs{at}gmail{dot}com

 On 4/8/2015 1:27 PM, Christopher Tyler wrote:
 Attached is a picture of the setup as it is now.  24 supply and 24v 
 loads, everything feeds through the Meanwell regulator.

 I followed the instructions from Traco, but as you can see the 
 battery is currently at about 23v and that is what the Traco power 
 supply is outputting. The instructions say to turn the power supply 
 all the way down and to let the BCM control the output. It's all set 
 up, jumper is in position 1, the feedback cable is connected between 
 the PS and the BCM but the BCM doesn't appear to be telling the power 
 supply to do anything except turn on.

 Anyone with some experience with Traco care to tell me what I'm doing 
 wrong. It's worked like this since day one, the BCM doesn't appear to 
 be doing anything regardless of the battery voltage.





Re: [AFMUG] Low Voltage Disconnect

2015-04-09 Thread Christopher Tyler
Which I don't :P
Oh well. I have other chargers that I can use to bring the batteries up and 
keep them conditioned with. A really nice ICT unit in fact. :)

-- 
Christopher Tyler 
MTCRE/MTCNA/MTCTCE/MTCWE 
Total Highspeed Internet Services 
417.851.1107

- Original Message -
From: George Skorup (Cyber Broadcasting) geo...@cbcast.com
To: af@afmug.com
Sent: Thursday, April 9, 2015 2:37:08 PM
Subject: Re: [AFMUG] Low Voltage Disconnect

Yep, sounds like there's something messed up with the remote voltage 
control. Hard to tell if it's the PS or the BCM, unless you have another 
set.

On 4/9/2015 11:12 AM, Christopher Tyler wrote:
 When I cut off AC power it switches over to battery just fine.
 It's just the power supply control that appears to be broken, everything else 
 seems to work. I followed the instructions line for line when I got it and it 
 didn't appear to work properly then either, so I think I just got a bad unit. 
 Should still be under warranty so, I'll see about getting an RMA for it and 
 thanks for the additional information, all very good information to keep in 
 mind.




Re: [AFMUG] Low Voltage Disconnect

2015-04-09 Thread George Skorup (Cyber Broadcasting)
Did you reconnect the battery? It senses the battery, so it might not do 
anything if the battery isn't connected.


With the battery connected, do you see any current going into it?

Also, with the battery connected, disconnect the AC from the power 
supply. Do you hear the relay click in the BCM?


On 4/9/2015 9:58 AM, Christopher Tyler wrote:

Just tried that and the POT still does nothing. Now it just sits at 27.6v 
constantly.





Re: [AFMUG] Low Voltage Disconnect

2015-04-09 Thread George Skorup (Cyber Broadcasting)
22-23 volts I think is the bottom of the adjustment range on the TSP 
power supply. At least you know the remote cable is working because the 
BCM can shut down the power supply. Try disconnecting the remote cable 
and adjust the pot on the power supply up to 27.6 volts. Power off, then 
reconnect the remote cable and power back up.


It was quite a while ago, but I think that's the same problem I had on 
the BCM48. If the PS is turned all the way down, it sorta acts like a 
limiter, so the BCM can't say hey, I need all your volts!


On 4/9/2015 9:29 AM, Christopher Tyler wrote:

Looks like I have a bad BCM maybe. I disconnected the battery and the temp 
sensor and left the remote wire connected.
I adjusted the pot on the BCM, and it does nothing at all.
The remote wire is definitely connected correctly, if I turn off the BCM it 
turns off the power supply, turn it back on, and after a few seconds it turns 
the power supply back on.





Re: [AFMUG] Low Voltage Disconnect

2015-04-09 Thread Bill Prince
Sounds like you could set it at 27 volts until you get a replacement BCM 
in there.


bp
part15sbs{at}gmail{dot}com

On 4/9/2015 7:58 AM, Christopher Tyler wrote:

Just tried that and the POT still does nothing. Now it just sits at 27.6v 
constantly.





Re: [AFMUG] Low Voltage Disconnect

2015-04-09 Thread George Skorup (Cyber Broadcasting)
You can use the BCM without a Traco power supply, or in this case 
without the remote cable. Set your PS output voltage to your desired 
float voltage and it works like any other battery/UPS module. The only 
kicker is obviously the temp compensation doesn't work without the 
remote voltage control.


On 4/9/2015 3:00 PM, Christopher Tyler wrote:

Which I don't :P
Oh well. I have other chargers that I can use to bring the batteries up and 
keep them conditioned with. A really nice ICT unit in fact. :)






Re: [AFMUG] Low Voltage Disconnect

2015-04-09 Thread Christopher Tyler
When I cut off AC power it switches over to battery just fine.
It's just the power supply control that appears to be broken, everything else 
seems to work. I followed the instructions line for line when I got it and it 
didn't appear to work properly then either, so I think I just got a bad unit. 
Should still be under warranty so, I'll see about getting an RMA for it and 
thanks for the additional information, all very good information to keep in 
mind.

-- 
Christopher Tyler 
MTCRE/MTCNA/MTCTCE/MTCWE 
Total Highspeed Internet Services 
417.851.1107

- Original Message -
From: Ken Hohhof af...@kwisp.com
To: af@afmug.com
Sent: Thursday, April 9, 2015 10:25:53 AM
Subject: Re: [AFMUG] Low Voltage Disconnect

I'm going from memory, but I also thought they told you to adjust the pot 
all the way down to minimum voltage.  Whatever the instructions were, I 
followed them and it worked.


-Original Message- 
From: George Skorup (Cyber Broadcasting)
Sent: Thursday, April 09, 2015 10:05 AM
To: af@afmug.com
Subject: Re: [AFMUG] Low Voltage Disconnect

Did you reconnect the battery? It senses the battery, so it might not do
anything if the battery isn't connected.

With the battery connected, do you see any current going into it?

Also, with the battery connected, disconnect the AC from the power
supply. Do you hear the relay click in the BCM?

On 4/9/2015 9:58 AM, Christopher Tyler wrote:
 Just tried that and the POT still does nothing. Now it just sits at 27.6v 
 constantly.





Re: [AFMUG] Low Voltage Disconnect

2015-04-09 Thread George Skorup (Cyber Broadcasting)
Oops, hit send too soon. Reason I ask about the relay in the BCM is I've 
accidentally shorted the output before (long story) and the relay seemed 
to be stuck. I smacked it and power-cycled a couple times and it was 
fixed. Fuses, dummy! Facepalm.


On 4/9/2015 10:05 AM, George Skorup (Cyber Broadcasting) wrote:
Did you reconnect the battery? It senses the battery, so it might not 
do anything if the battery isn't connected.


With the battery connected, do you see any current going into it?

Also, with the battery connected, disconnect the AC from the power 
supply. Do you hear the relay click in the BCM?


On 4/9/2015 9:58 AM, Christopher Tyler wrote:
Just tried that and the POT still does nothing. Now it just sits at 
27.6v constantly.








Re: [AFMUG] Low Voltage Disconnect

2015-04-09 Thread Ken Hohhof
I'm going from memory, but I also thought they told you to adjust the pot 
all the way down to minimum voltage.  Whatever the instructions were, I 
followed them and it worked.



-Original Message- 
From: George Skorup (Cyber Broadcasting)

Sent: Thursday, April 09, 2015 10:05 AM
To: af@afmug.com
Subject: Re: [AFMUG] Low Voltage Disconnect

Did you reconnect the battery? It senses the battery, so it might not do
anything if the battery isn't connected.

With the battery connected, do you see any current going into it?

Also, with the battery connected, disconnect the AC from the power
supply. Do you hear the relay click in the BCM?

On 4/9/2015 9:58 AM, Christopher Tyler wrote:
Just tried that and the POT still does nothing. Now it just sits at 27.6v 
constantly.







[AFMUG] Low Voltage Disconnect

2015-04-08 Thread Christopher Tyler
Looking for recommendations on a 24v LVD to protect our batteries from being 
drained.
Anyone have one they recommend?

-- 
Christopher Tyler 
MTCRE/MTCNA/MTCTCE/MTCWE 
Total Highspeed Internet Services 
417.851.1107



Re: [AFMUG] Low Voltage Disconnect

2015-04-08 Thread Josh Luthman
First off I'd suggest getting enough batteries that you wouldn't need an
LVD.

Second, I'd rather see my batteries lose a bit of life and keep the site up
then have everything go down saving my batteries.

Tertiary/finally, what equipment do you have now?  My regulator cuts off at
19v and still provides 24v.  I figure the batteries are at 9.5v they're
already sper low.


Josh Luthman
Office: 937-552-2340
Direct: 937-552-2343
1100 Wayne St
Suite 1337
Troy, OH 45373

On Wed, Apr 8, 2015 at 2:44 PM, Christopher Tyler ch...@totalhighspeed.net
wrote:

 Looking for recommendations on a 24v LVD to protect our batteries from
 being drained.
 Anyone have one they recommend?

 --
 Christopher Tyler
 MTCRE/MTCNA/MTCTCE/MTCWE
 Total Highspeed Internet Services
 417.851.1107




Re: [AFMUG] Low Voltage Disconnect

2015-04-08 Thread Christopher Tyler
We are currently testing using two 12v 100Ah telecom batteries in series.
They are slightly expensive to replace, especially when we will have four (or 
more) at some sites, most will have two.

I'm using a Meanwell RSD-100B-24 regulator for the Tik RB-493G router right 
now. Looks like the cutout for the regulator is around 16v from what I can 
decipher from the datasheet.
My test radios (2 Canopy and 2 UBNT) are connected to the battery without 
regulation.

This setup will drain the batteries until they are pretty much dead and buried. 
I ran them over the weekend and I figured it would stop draining around 10v at 
worst, it didn't. They ended up around 6v in parallel or 3v per battery.  I 
figure I shaved off some capacity and lifetime of my test batteries with that, 
hopefully not too much.

-- 
Christopher Tyler 
MTCRE/MTCNA/MTCTCE/MTCWE 
Total Highspeed Internet Services 
417.851.1107

- Original Message -
From: Josh Luthman j...@imaginenetworksllc.com
To: af@afmug.com
Sent: Wednesday, April 8, 2015 1:49:05 PM
Subject: Re: [AFMUG] Low Voltage Disconnect

First off I'd suggest getting enough batteries that you wouldn't need an
LVD.

Second, I'd rather see my batteries lose a bit of life and keep the site up
then have everything go down saving my batteries.

Tertiary/finally, what equipment do you have now?  My regulator cuts off at
19v and still provides 24v.  I figure the batteries are at 9.5v they're
already sper low.


Josh Luthman
Office: 937-552-2340
Direct: 937-552-2343
1100 Wayne St
Suite 1337
Troy, OH 45373

On Wed, Apr 8, 2015 at 2:44 PM, Christopher Tyler ch...@totalhighspeed.net
wrote:

 Looking for recommendations on a 24v LVD to protect our batteries from
 being drained.
 Anyone have one they recommend?

 --
 Christopher Tyler
 MTCRE/MTCNA/MTCTCE/MTCWE
 Total Highspeed Internet Services
 417.851.1107




Re: [AFMUG] Low Voltage Disconnect

2015-04-08 Thread Josh Luthman
Correct:
continuous 16.8 ~ 31.2VDC
1 second 14.4 ~ 33.6VDC

If you already dropped them to 3v I think they'd be toast.

If you didn't have your charger you're not really testing the compatibility
with Ubnt.  I believe the cut off is something like 27.5v for the Airmax
stuff and your charge is around 27.3 (depending on battery).  To me, that
was too close for comfort and hence I use the regulator.

I don't know why you would expect them to stop at 10v.  At 20v both Canopy
and Ubnt would happily run.  The radios would continue to pull power from
the batteries forever.


Josh Luthman
Office: 937-552-2340
Direct: 937-552-2343
1100 Wayne St
Suite 1337
Troy, OH 45373

On Wed, Apr 8, 2015 at 3:23 PM, Christopher Tyler ch...@totalhighspeed.net
wrote:

 We are currently testing using two 12v 100Ah telecom batteries in series.
 They are slightly expensive to replace, especially when we will have four
 (or more) at some sites, most will have two.

 I'm using a Meanwell RSD-100B-24 regulator for the Tik RB-493G router
 right now. Looks like the cutout for the regulator is around 16v from what
 I can decipher from the datasheet.
 My test radios (2 Canopy and 2 UBNT) are connected to the battery without
 regulation.

 This setup will drain the batteries until they are pretty much dead and
 buried. I ran them over the weekend and I figured it would stop draining
 around 10v at worst, it didn't. They ended up around 6v in parallel or 3v
 per battery.  I figure I shaved off some capacity and lifetime of my test
 batteries with that, hopefully not too much.

 --
 Christopher Tyler
 MTCRE/MTCNA/MTCTCE/MTCWE
 Total Highspeed Internet Services
 417.851.1107

 - Original Message -
 From: Josh Luthman j...@imaginenetworksllc.com
 To: af@afmug.com
 Sent: Wednesday, April 8, 2015 1:49:05 PM
 Subject: Re: [AFMUG] Low Voltage Disconnect

 First off I'd suggest getting enough batteries that you wouldn't need an
 LVD.

 Second, I'd rather see my batteries lose a bit of life and keep the site up
 then have everything go down saving my batteries.

 Tertiary/finally, what equipment do you have now?  My regulator cuts off at
 19v and still provides 24v.  I figure the batteries are at 9.5v they're
 already sper low.


 Josh Luthman
 Office: 937-552-2340
 Direct: 937-552-2343
 1100 Wayne St
 Suite 1337
 Troy, OH 45373

 On Wed, Apr 8, 2015 at 2:44 PM, Christopher Tyler 
 ch...@totalhighspeed.net
 wrote:

  Looking for recommendations on a 24v LVD to protect our batteries from
  being drained.
  Anyone have one they recommend?
 
  --
  Christopher Tyler
  MTCRE/MTCNA/MTCTCE/MTCWE
  Total Highspeed Internet Services
  417.851.1107
 
 



Re: [AFMUG] Low Voltage Disconnect

2015-04-08 Thread Adam Moffett
LVD is a built in feature on the Meanwell AD-155 and the Traco TSP BCM.  
It's also a built in feature on solar controllers.


What are you using for a charger?



We are currently testing using two 12v 100Ah telecom batteries in series.
They are slightly expensive to replace, especially when we will have four (or 
more) at some sites, most will have two.

I'm using a Meanwell RSD-100B-24 regulator for the Tik RB-493G router right 
now. Looks like the cutout for the regulator is around 16v from what I can 
decipher from the datasheet.
My test radios (2 Canopy and 2 UBNT) are connected to the battery without 
regulation.

This setup will drain the batteries until they are pretty much dead and buried. 
I ran them over the weekend and I figured it would stop draining around 10v at 
worst, it didn't. They ended up around 6v in parallel or 3v per battery.  I 
figure I shaved off some capacity and lifetime of my test batteries with that, 
hopefully not too much.





Re: [AFMUG] Low Voltage Disconnect

2015-04-08 Thread Josh Luthman
AD-155

battery low: 10V 0.8V
19.5V(+1.5V,-1V )
39V 2V

So it would cut out at 18.5v - or 9.25v each battery; is that high enough
for this purpose?


Josh Luthman
Office: 937-552-2340
Direct: 937-552-2343
1100 Wayne St
Suite 1337
Troy, OH 45373

On Wed, Apr 8, 2015 at 3:29 PM, Adam Moffett dmmoff...@gmail.com wrote:

 LVD is a built in feature on the Meanwell AD-155 and the Traco TSP BCM.
 It's also a built in feature on solar controllers.

 What are you using for a charger?



  We are currently testing using two 12v 100Ah telecom batteries in series.
 They are slightly expensive to replace, especially when we will have four
 (or more) at some sites, most will have two.

 I'm using a Meanwell RSD-100B-24 regulator for the Tik RB-493G router
 right now. Looks like the cutout for the regulator is around 16v from what
 I can decipher from the datasheet.
 My test radios (2 Canopy and 2 UBNT) are connected to the battery without
 regulation.

 This setup will drain the batteries until they are pretty much dead and
 buried. I ran them over the weekend and I figured it would stop draining
 around 10v at worst, it didn't. They ended up around 6v in parallel or 3v
 per battery.  I figure I shaved off some capacity and lifetime of my test
 batteries with that, hopefully not too much.





Re: [AFMUG] Low Voltage Disconnect

2015-04-08 Thread Christopher Tyler
I used a Tripp-Lite APC750 that we have to charge the batteries. It's a 12v 
system though, so to keep it simple for the test I just rewired the batteries 
in series to get 24v and then plugged the batteries in to the circuit without 
anything in between (TrippLite was disconnected as well). Just raw DC power 
straight from the trough. :)

We do have a Traco TSP-BCM24A which I used to charged the batteries back up 
which I should have used (hindsight).

Oddly enough the batteries seem to be fine, they are holding steady at about 
24v, have not tested capacity yet though.

So note to self, use a charge controller next time, it has the LVD built in. 
Got it.

-- 
Christopher Tyler 
MTCRE/MTCNA/MTCTCE/MTCWE 
Total Highspeed Internet Services 
417.851.1107

- Original Message -
From: Adam Moffett dmmoff...@gmail.com
To: af@afmug.com
Sent: Wednesday, April 8, 2015 2:29:15 PM
Subject: Re: [AFMUG] Low Voltage Disconnect

LVD is a built in feature on the Meanwell AD-155 and the Traco TSP BCM.  
It's also a built in feature on solar controllers.

What are you using for a charger?


 We are currently testing using two 12v 100Ah telecom batteries in series.
 They are slightly expensive to replace, especially when we will have four (or 
 more) at some sites, most will have two.

 I'm using a Meanwell RSD-100B-24 regulator for the Tik RB-493G router right 
 now. Looks like the cutout for the regulator is around 16v from what I can 
 decipher from the datasheet.
 My test radios (2 Canopy and 2 UBNT) are connected to the battery without 
 regulation.

 This setup will drain the batteries until they are pretty much dead and 
 buried. I ran them over the weekend and I figured it would stop draining 
 around 10v at worst, it didn't. They ended up around 6v in parallel or 3v per 
 battery.  I figure I shaved off some capacity and lifetime of my test 
 batteries with that, hopefully not too much.




Re: [AFMUG] Low Voltage Disconnect

2015-04-08 Thread Adam Moffett

Better than 3v.


AD-155

battery low: 10V 0.8V
19.5V(+1.5V,-1V )
39V 2V

So it would cut out at 18.5v - or 9.25v each battery; is that high 
enough for this purpose?



Josh Luthman
Office: 937-552-2340 tel:937-552-2340
Direct: 937-552-2343 tel:937-552-2343
1100 Wayne St
Suite 1337
Troy, OH 45373

On Wed, Apr 8, 2015 at 3:29 PM, Adam Moffett dmmoff...@gmail.com 
mailto:dmmoff...@gmail.com wrote:


LVD is a built in feature on the Meanwell AD-155 and the Traco TSP
BCM.  It's also a built in feature on solar controllers.

What are you using for a charger?



We are currently testing using two 12v 100Ah telecom batteries
in series.
They are slightly expensive to replace, especially when we
will have four (or more) at some sites, most will have two.

I'm using a Meanwell RSD-100B-24 regulator for the Tik RB-493G
router right now. Looks like the cutout for the regulator is
around 16v from what I can decipher from the datasheet.
My test radios (2 Canopy and 2 UBNT) are connected to the
battery without regulation.

This setup will drain the batteries until they are pretty much
dead and buried. I ran them over the weekend and I figured it
would stop draining around 10v at worst, it didn't. They ended
up around 6v in parallel or 3v per battery.  I figure I shaved
off some capacity and lifetime of my test batteries with that,
hopefully not too much.







Re: [AFMUG] Low Voltage Disconnect

2015-04-08 Thread Christopher Tyler
Commercial power.

-- 
Christopher Tyler 
MTCRE/MTCNA/MTCTCE/MTCWE 
Total Highspeed Internet Services 
417.851.1107

- Original Message -
From: Ken Hohhof af...@kwisp.com
To: af@afmug.com
Sent: Wednesday, April 8, 2015 3:18:25 PM
Subject: Re: [AFMUG] Low Voltage Disconnect

Is this powered by solar or commercial power?
One approach is to use a charger that includes a LVD, like the Traco TSP-BCM 
(which controls a TSP series AC/DC power supply).
The LVD is fixed not adjustable.


-Original Message- 
From: Christopher Tyler
Sent: Wednesday, April 08, 2015 2:23 PM
To: af@afmug.com
Subject: Re: [AFMUG] Low Voltage Disconnect

We are currently testing using two 12v 100Ah telecom batteries in series.
They are slightly expensive to replace, especially when we will have four 
(or more) at some sites, most will have two.

I'm using a Meanwell RSD-100B-24 regulator for the Tik RB-493G router right 
now. Looks like the cutout for the regulator is around 16v from what I can 
decipher from the datasheet.
My test radios (2 Canopy and 2 UBNT) are connected to the battery without 
regulation.

This setup will drain the batteries until they are pretty much dead and 
buried. I ran them over the weekend and I figured it would stop draining 
around 10v at worst, it didn't. They ended up around 6v in parallel or 3v 
per battery.  I figure I shaved off some capacity and lifetime of my test 
batteries with that, hopefully not too much.

-- 
Christopher Tyler
MTCRE/MTCNA/MTCTCE/MTCWE
Total Highspeed Internet Services
417.851.1107

- Original Message -
From: Josh Luthman j...@imaginenetworksllc.com
To: af@afmug.com
Sent: Wednesday, April 8, 2015 1:49:05 PM
Subject: Re: [AFMUG] Low Voltage Disconnect

First off I'd suggest getting enough batteries that you wouldn't need an
LVD.

Second, I'd rather see my batteries lose a bit of life and keep the site up
then have everything go down saving my batteries.

Tertiary/finally, what equipment do you have now?  My regulator cuts off at
19v and still provides 24v.  I figure the batteries are at 9.5v they're
already sper low.


Josh Luthman
Office: 937-552-2340
Direct: 937-552-2343
1100 Wayne St
Suite 1337
Troy, OH 45373

On Wed, Apr 8, 2015 at 2:44 PM, Christopher Tyler ch...@totalhighspeed.net
wrote:

 Looking for recommendations on a 24v LVD to protect our batteries from
 being drained.
 Anyone have one they recommend?

 --
 Christopher Tyler
 MTCRE/MTCNA/MTCTCE/MTCWE
 Total Highspeed Internet Services
 417.851.1107

 




Re: [AFMUG] Low Voltage Disconnect

2015-04-08 Thread Josh Baird
I can't speak for the LVD (I'm sure someone can), but I don't see any fuses
on your DC distribution.  I may just be missing them, but if not, you may
want to consider adding some.  It would be a good practice to put DC
breakers/fuses in between your battery bank and charger as well.

On Wed, Apr 8, 2015 at 4:27 PM, Christopher Tyler ch...@totalhighspeed.net
wrote:

 Might help if there was a pic, eh?

 --
 Christopher Tyler
 MTCRE/MTCNA/MTCTCE/MTCWE
 Total Highspeed Internet Services
 417.851.1107

 - Original Message -
 From: Christopher Tyler ch...@totalhighspeed.net
 To: af@afmug.com
 Sent: Wednesday, April 8, 2015 3:27:15 PM
 Subject: Re: [AFMUG] Low Voltage Disconnect

 Attached is a picture of the setup as it is now.  24 supply and 24v loads,
 everything feeds through the Meanwell regulator.

 I followed the instructions from Traco, but as you can see the battery is
 currently at about 23v and that is what the Traco power supply is
 outputting. The instructions say to turn the power supply all the way down
 and to let the BCM control the output. It's all set up, jumper is in
 position 1, the feedback cable is connected between the PS and the BCM but
 the BCM doesn't appear to be telling the power supply to do anything except
 turn on.

 Anyone with some experience with Traco care to tell me what I'm doing
 wrong. It's worked like this since day one, the BCM doesn't appear to be
 doing anything regardless of the battery voltage.

 --
 Christopher Tyler
 MTCRE/MTCNA/MTCTCE/MTCWE
 Total Highspeed Internet Services
 417.851.1107

 - Original Message -
 From: Christopher Tyler ch...@totalhighspeed.net
 To: af@afmug.com
 Sent: Wednesday, April 8, 2015 3:19:35 PM
 Subject: Re: [AFMUG] Low Voltage Disconnect

 Commercial power.

 --
 Christopher Tyler
 MTCRE/MTCNA/MTCTCE/MTCWE
 Total Highspeed Internet Services
 417.851.1107

 - Original Message -
 From: Ken Hohhof af...@kwisp.com
 To: af@afmug.com
 Sent: Wednesday, April 8, 2015 3:18:25 PM
 Subject: Re: [AFMUG] Low Voltage Disconnect

 Is this powered by solar or commercial power?
 One approach is to use a charger that includes a LVD, like the Traco
 TSP-BCM
 (which controls a TSP series AC/DC power supply).
 The LVD is fixed not adjustable.


 -Original Message-
 From: Christopher Tyler
 Sent: Wednesday, April 08, 2015 2:23 PM
 To: af@afmug.com
 Subject: Re: [AFMUG] Low Voltage Disconnect

 We are currently testing using two 12v 100Ah telecom batteries in series.
 They are slightly expensive to replace, especially when we will have four
 (or more) at some sites, most will have two.

 I'm using a Meanwell RSD-100B-24 regulator for the Tik RB-493G router right
 now. Looks like the cutout for the regulator is around 16v from what I can
 decipher from the datasheet.
 My test radios (2 Canopy and 2 UBNT) are connected to the battery without
 regulation.

 This setup will drain the batteries until they are pretty much dead and
 buried. I ran them over the weekend and I figured it would stop draining
 around 10v at worst, it didn't. They ended up around 6v in parallel or 3v
 per battery.  I figure I shaved off some capacity and lifetime of my test
 batteries with that, hopefully not too much.

 --
 Christopher Tyler
 MTCRE/MTCNA/MTCTCE/MTCWE
 Total Highspeed Internet Services
 417.851.1107

 - Original Message -
 From: Josh Luthman j...@imaginenetworksllc.com
 To: af@afmug.com
 Sent: Wednesday, April 8, 2015 1:49:05 PM
 Subject: Re: [AFMUG] Low Voltage Disconnect

 First off I'd suggest getting enough batteries that you wouldn't need an
 LVD.

 Second, I'd rather see my batteries lose a bit of life and keep the site up
 then have everything go down saving my batteries.

 Tertiary/finally, what equipment do you have now?  My regulator cuts off at
 19v and still provides 24v.  I figure the batteries are at 9.5v they're
 already sper low.


 Josh Luthman
 Office: 937-552-2340
 Direct: 937-552-2343
 1100 Wayne St
 Suite 1337
 Troy, OH 45373

 On Wed, Apr 8, 2015 at 2:44 PM, Christopher Tyler 
 ch...@totalhighspeed.net
 wrote:

  Looking for recommendations on a 24v LVD to protect our batteries from
  being drained.
  Anyone have one they recommend?
 
  --
  Christopher Tyler
  MTCRE/MTCNA/MTCTCE/MTCWE
  Total Highspeed Internet Services
  417.851.1107
 
 





Re: [AFMUG] Low Voltage Disconnect

2015-04-08 Thread Randy Cosby
For some solar sites, we'll use a Morningstar Tristar MPPT 60 as the 
charger, then a Morningstar Tristar TS-60 (non-mppt) in LVD mode. Price 
isn't too bad and you can set the voltage points with dip switches.



On 4/8/2015 12:44 PM, Christopher Tyler wrote:

Looking for recommendations on a 24v LVD to protect our batteries from being 
drained.
Anyone have one they recommend?





Re: [AFMUG] Low Voltage Disconnect

2015-04-08 Thread Bill Prince
Our 24V solar sites go up to about 28.5 volts when they are in bulk 
charge mode, then drop to about 27.5 volts when in float. A typical 
partly cloudty day is shown below for one of our solar sites. The big 
dip in the afternoon was some big clouds rolling through.


So we feel obliged to protect UBNT equipment with a 36/72 V - 24 V 
converter, because I think going up to 28.5V might just let the smoke out.


bp
part15sbs{at}gmail{dot}com



On 4/8/2015 12:28 PM, Josh Luthman wrote:

Correct:
continuous 16.8 ~ 31.2VDC
1 second 14.4 ~ 33.6VDC

If you already dropped them to 3v I think they'd be toast.

If you didn't have your charger you're not really testing the 
compatibility with Ubnt.  I believe the cut off is something like 
27.5v for the Airmax stuff and your charge is around 27.3 (depending 
on battery).  To me, that was too close for comfort and hence I use 
the regulator.


I don't know why you would expect them to stop at 10v.  At 20v both 
Canopy and Ubnt would happily run.  The radios would continue to pull 
power from the batteries forever.



Josh Luthman
Office: 937-552-2340
Direct: 937-552-2343
1100 Wayne St
Suite 1337
Troy, OH 45373

On Wed, Apr 8, 2015 at 3:23 PM, Christopher Tyler 
ch...@totalhighspeed.net mailto:ch...@totalhighspeed.net wrote:


We are currently testing using two 12v 100Ah telecom batteries in
series.
They are slightly expensive to replace, especially when we will
have four (or more) at some sites, most will have two.

I'm using a Meanwell RSD-100B-24 regulator for the Tik RB-493G
router right now. Looks like the cutout for the regulator is
around 16v from what I can decipher from the datasheet.
My test radios (2 Canopy and 2 UBNT) are connected to the battery
without regulation.

This setup will drain the batteries until they are pretty much
dead and buried. I ran them over the weekend and I figured it
would stop draining around 10v at worst, it didn't. They ended up
around 6v in parallel or 3v per battery.  I figure I shaved off
some capacity and lifetime of my test batteries with that,
hopefully not too much.

--
Christopher Tyler
MTCRE/MTCNA/MTCTCE/MTCWE
Total Highspeed Internet Services
417.851.1107 tel:417.851.1107

- Original Message -
From: Josh Luthman j...@imaginenetworksllc.com
mailto:j...@imaginenetworksllc.com
To: af@afmug.com mailto:af@afmug.com
Sent: Wednesday, April 8, 2015 1:49:05 PM
Subject: Re: [AFMUG] Low Voltage Disconnect

First off I'd suggest getting enough batteries that you wouldn't
need an
LVD.

Second, I'd rather see my batteries lose a bit of life and keep
the site up
then have everything go down saving my batteries.

Tertiary/finally, what equipment do you have now?  My regulator
cuts off at
19v and still provides 24v.  I figure the batteries are at 9.5v
they're
already sper low.


Josh Luthman
Office: 937-552-2340
Direct: 937-552-2343
1100 Wayne St
Suite 1337
Troy, OH 45373

On Wed, Apr 8, 2015 at 2:44 PM, Christopher Tyler
ch...@totalhighspeed.net mailto:ch...@totalhighspeed.net
wrote:

 Looking for recommendations on a 24v LVD to protect our
batteries from
 being drained.
 Anyone have one they recommend?

 --
 Christopher Tyler
 MTCRE/MTCNA/MTCTCE/MTCWE
 Total Highspeed Internet Services
 417.851.1107 tel:417.851.1107








Re: [AFMUG] Low Voltage Disconnect

2015-04-08 Thread Christopher Tyler
Attached is a picture of the setup as it is now.  24 supply and 24v loads, 
everything feeds through the Meanwell regulator.

I followed the instructions from Traco, but as you can see the battery is 
currently at about 23v and that is what the Traco power supply is outputting. 
The instructions say to turn the power supply all the way down and to let the 
BCM control the output. It's all set up, jumper is in position 1, the feedback 
cable is connected between the PS and the BCM but the BCM doesn't appear to be 
telling the power supply to do anything except turn on.

Anyone with some experience with Traco care to tell me what I'm doing wrong. 
It's worked like this since day one, the BCM doesn't appear to be doing 
anything regardless of the battery voltage.

-- 
Christopher Tyler 
MTCRE/MTCNA/MTCTCE/MTCWE 
Total Highspeed Internet Services 
417.851.1107

- Original Message -
From: Christopher Tyler ch...@totalhighspeed.net
To: af@afmug.com
Sent: Wednesday, April 8, 2015 3:19:35 PM
Subject: Re: [AFMUG] Low Voltage Disconnect

Commercial power.

-- 
Christopher Tyler 
MTCRE/MTCNA/MTCTCE/MTCWE 
Total Highspeed Internet Services 
417.851.1107

- Original Message -
From: Ken Hohhof af...@kwisp.com
To: af@afmug.com
Sent: Wednesday, April 8, 2015 3:18:25 PM
Subject: Re: [AFMUG] Low Voltage Disconnect

Is this powered by solar or commercial power?
One approach is to use a charger that includes a LVD, like the Traco TSP-BCM 
(which controls a TSP series AC/DC power supply).
The LVD is fixed not adjustable.


-Original Message- 
From: Christopher Tyler
Sent: Wednesday, April 08, 2015 2:23 PM
To: af@afmug.com
Subject: Re: [AFMUG] Low Voltage Disconnect

We are currently testing using two 12v 100Ah telecom batteries in series.
They are slightly expensive to replace, especially when we will have four 
(or more) at some sites, most will have two.

I'm using a Meanwell RSD-100B-24 regulator for the Tik RB-493G router right 
now. Looks like the cutout for the regulator is around 16v from what I can 
decipher from the datasheet.
My test radios (2 Canopy and 2 UBNT) are connected to the battery without 
regulation.

This setup will drain the batteries until they are pretty much dead and 
buried. I ran them over the weekend and I figured it would stop draining 
around 10v at worst, it didn't. They ended up around 6v in parallel or 3v 
per battery.  I figure I shaved off some capacity and lifetime of my test 
batteries with that, hopefully not too much.

-- 
Christopher Tyler
MTCRE/MTCNA/MTCTCE/MTCWE
Total Highspeed Internet Services
417.851.1107

- Original Message -
From: Josh Luthman j...@imaginenetworksllc.com
To: af@afmug.com
Sent: Wednesday, April 8, 2015 1:49:05 PM
Subject: Re: [AFMUG] Low Voltage Disconnect

First off I'd suggest getting enough batteries that you wouldn't need an
LVD.

Second, I'd rather see my batteries lose a bit of life and keep the site up
then have everything go down saving my batteries.

Tertiary/finally, what equipment do you have now?  My regulator cuts off at
19v and still provides 24v.  I figure the batteries are at 9.5v they're
already sper low.


Josh Luthman
Office: 937-552-2340
Direct: 937-552-2343
1100 Wayne St
Suite 1337
Troy, OH 45373

On Wed, Apr 8, 2015 at 2:44 PM, Christopher Tyler ch...@totalhighspeed.net
wrote:

 Looking for recommendations on a 24v LVD to protect our batteries from
 being drained.
 Anyone have one they recommend?

 --
 Christopher Tyler
 MTCRE/MTCNA/MTCTCE/MTCWE
 Total Highspeed Internet Services
 417.851.1107

 




Re: [AFMUG] Low Voltage Disconnect

2015-04-08 Thread Ken Hohhof

Is this powered by solar or commercial power?
One approach is to use a charger that includes a LVD, like the Traco TSP-BCM 
(which controls a TSP series AC/DC power supply).

The LVD is fixed not adjustable.


-Original Message- 
From: Christopher Tyler

Sent: Wednesday, April 08, 2015 2:23 PM
To: af@afmug.com
Subject: Re: [AFMUG] Low Voltage Disconnect

We are currently testing using two 12v 100Ah telecom batteries in series.
They are slightly expensive to replace, especially when we will have four 
(or more) at some sites, most will have two.


I'm using a Meanwell RSD-100B-24 regulator for the Tik RB-493G router right 
now. Looks like the cutout for the regulator is around 16v from what I can 
decipher from the datasheet.
My test radios (2 Canopy and 2 UBNT) are connected to the battery without 
regulation.


This setup will drain the batteries until they are pretty much dead and 
buried. I ran them over the weekend and I figured it would stop draining 
around 10v at worst, it didn't. They ended up around 6v in parallel or 3v 
per battery.  I figure I shaved off some capacity and lifetime of my test 
batteries with that, hopefully not too much.


--
Christopher Tyler
MTCRE/MTCNA/MTCTCE/MTCWE
Total Highspeed Internet Services
417.851.1107

- Original Message -
From: Josh Luthman j...@imaginenetworksllc.com
To: af@afmug.com
Sent: Wednesday, April 8, 2015 1:49:05 PM
Subject: Re: [AFMUG] Low Voltage Disconnect

First off I'd suggest getting enough batteries that you wouldn't need an
LVD.

Second, I'd rather see my batteries lose a bit of life and keep the site up
then have everything go down saving my batteries.

Tertiary/finally, what equipment do you have now?  My regulator cuts off at
19v and still provides 24v.  I figure the batteries are at 9.5v they're
already sper low.


Josh Luthman
Office: 937-552-2340
Direct: 937-552-2343
1100 Wayne St
Suite 1337
Troy, OH 45373

On Wed, Apr 8, 2015 at 2:44 PM, Christopher Tyler ch...@totalhighspeed.net
wrote:


Looking for recommendations on a 24v LVD to protect our batteries from
being drained.
Anyone have one they recommend?

--
Christopher Tyler
MTCRE/MTCNA/MTCTCE/MTCWE
Total Highspeed Internet Services
417.851.1107







Re: [AFMUG] Low Voltage Disconnect

2015-04-08 Thread Ken Hohhof
Also there is a fuse in the Traco BCM, I assume you’ve checked that.

I have at least one of these and it works as you’d expect.  I think George has 
a bunch of them, maybe he’ll weigh in.


From: Josh Baird 
Sent: Wednesday, April 08, 2015 3:37 PM
To: af@afmug.com 
Subject: Re: [AFMUG] Low Voltage Disconnect

I can't speak for the LVD (I'm sure someone can), but I don't see any fuses on 
your DC distribution.  I may just be missing them, but if not, you may want to 
consider adding some.  It would be a good practice to put DC breakers/fuses in 
between your battery bank and charger as well.

On Wed, Apr 8, 2015 at 4:27 PM, Christopher Tyler ch...@totalhighspeed.net 
wrote:

  Might help if there was a pic, eh?

  --
  Christopher Tyler
  MTCRE/MTCNA/MTCTCE/MTCWE
  Total Highspeed Internet Services
  417.851.1107

  - Original Message -
  From: Christopher Tyler ch...@totalhighspeed.net
  To: af@afmug.com

  Sent: Wednesday, April 8, 2015 3:27:15 PM
  Subject: Re: [AFMUG] Low Voltage Disconnect

  Attached is a picture of the setup as it is now.  24 supply and 24v loads, 
everything feeds through the Meanwell regulator.

  I followed the instructions from Traco, but as you can see the battery is 
currently at about 23v and that is what the Traco power supply is outputting. 
The instructions say to turn the power supply all the way down and to let the 
BCM control the output. It's all set up, jumper is in position 1, the feedback 
cable is connected between the PS and the BCM but the BCM doesn't appear to be 
telling the power supply to do anything except turn on.

  Anyone with some experience with Traco care to tell me what I'm doing wrong. 
It's worked like this since day one, the BCM doesn't appear to be doing 
anything regardless of the battery voltage.

  --
  Christopher Tyler
  MTCRE/MTCNA/MTCTCE/MTCWE
  Total Highspeed Internet Services
  417.851.1107

  - Original Message -
  From: Christopher Tyler ch...@totalhighspeed.net
  To: af@afmug.com
  Sent: Wednesday, April 8, 2015 3:19:35 PM
  Subject: Re: [AFMUG] Low Voltage Disconnect

  Commercial power.

  --
  Christopher Tyler
  MTCRE/MTCNA/MTCTCE/MTCWE
  Total Highspeed Internet Services
  417.851.1107

  - Original Message -
  From: Ken Hohhof af...@kwisp.com
  To: af@afmug.com
  Sent: Wednesday, April 8, 2015 3:18:25 PM
  Subject: Re: [AFMUG] Low Voltage Disconnect

  Is this powered by solar or commercial power?
  One approach is to use a charger that includes a LVD, like the Traco TSP-BCM
  (which controls a TSP series AC/DC power supply).
  The LVD is fixed not adjustable.


  -Original Message-
  From: Christopher Tyler
  Sent: Wednesday, April 08, 2015 2:23 PM
  To: af@afmug.com
  Subject: Re: [AFMUG] Low Voltage Disconnect

  We are currently testing using two 12v 100Ah telecom batteries in series.
  They are slightly expensive to replace, especially when we will have four
  (or more) at some sites, most will have two.

  I'm using a Meanwell RSD-100B-24 regulator for the Tik RB-493G router right
  now. Looks like the cutout for the regulator is around 16v from what I can
  decipher from the datasheet.
  My test radios (2 Canopy and 2 UBNT) are connected to the battery without
  regulation.

  This setup will drain the batteries until they are pretty much dead and
  buried. I ran them over the weekend and I figured it would stop draining
  around 10v at worst, it didn't. They ended up around 6v in parallel or 3v
  per battery.  I figure I shaved off some capacity and lifetime of my test
  batteries with that, hopefully not too much.

  --
  Christopher Tyler
  MTCRE/MTCNA/MTCTCE/MTCWE
  Total Highspeed Internet Services
  417.851.1107

  - Original Message -
  From: Josh Luthman j...@imaginenetworksllc.com
  To: af@afmug.com
  Sent: Wednesday, April 8, 2015 1:49:05 PM
  Subject: Re: [AFMUG] Low Voltage Disconnect

  First off I'd suggest getting enough batteries that you wouldn't need an
  LVD.

  Second, I'd rather see my batteries lose a bit of life and keep the site up
  then have everything go down saving my batteries.

  Tertiary/finally, what equipment do you have now?  My regulator cuts off at
  19v and still provides 24v.  I figure the batteries are at 9.5v they're
  already sper low.


  Josh Luthman
  Office: 937-552-2340
  Direct: 937-552-2343
  1100 Wayne St
  Suite 1337
  Troy, OH 45373

  On Wed, Apr 8, 2015 at 2:44 PM, Christopher Tyler ch...@totalhighspeed.net
  wrote:

   Looking for recommendations on a 24v LVD to protect our batteries from
   being drained.
   Anyone have one they recommend?
  
   --
   Christopher Tyler
   MTCRE/MTCNA/MTCTCE/MTCWE
   Total Highspeed Internet Services
   417.851.1107
  
  





Re: [AFMUG] Low Voltage Disconnect

2015-04-08 Thread Chuck McCown
+1 

Screw LVD.  Do you want to risk losing connectivity when the LVD trips only to 
have power restored 10 minutes later?  If you power is that crappy that it will 
trip enough to significantly save your battery you do not have a large enough 
battery.  

If you are doing LVD to prevent the chance of a infrequent deep discharge, it 
is still a waste of money.  Again, more battery is the answer.  A deep 
discharge once a year is not going to markedly reduce battery life unless you 
draw them clear down and leave them discharged for an extended period of time.  

If you don’t want to put the money into a larger battery, put in telemetry that 
is monitored with a PRTG/MRTG type of tool that will send you and email when 
things are getting low.  Then you can run out with a generator or perhaps 
manually turn stuff off via telemetry until power comes back on.  

I used to be a believer in LVD but not any more.  Now, if there is any chance 
of  keeping things running, I want to keep things running.  



From: Josh Luthman 
Sent: Wednesday, April 08, 2015 12:49 PM
To: af@afmug.com 
Subject: Re: [AFMUG] Low Voltage Disconnect

First off I'd suggest getting enough batteries that you wouldn't need an LVD. 

Second, I'd rather see my batteries lose a bit of life and keep the site up 
then have everything go down saving my batteries.

Tertiary/finally, what equipment do you have now?  My regulator cuts off at 19v 
and still provides 24v.  I figure the batteries are at 9.5v they're already 
sper low.


Josh Luthman
Office: 937-552-2340
Direct: 937-552-2343
1100 Wayne St
Suite 1337
Troy, OH 45373

On Wed, Apr 8, 2015 at 2:44 PM, Christopher Tyler ch...@totalhighspeed.net 
wrote:

  Looking for recommendations on a 24v LVD to protect our batteries from being 
drained.
  Anyone have one they recommend?

  --
  Christopher Tyler
  MTCRE/MTCNA/MTCTCE/MTCWE
  Total Highspeed Internet Services
  417.851.1107




Re: [AFMUG] Low Voltage Disconnect

2015-04-08 Thread Chuck McCown
Depends on how long it went that low, the rate of discharge etc.  I don’t think 
a lead acid based chemistry will develop enough sulfide (sulfite?) with one or 
two deep discharges like that to matter unless they are left in that condition. 
 It takes deep discharge and time to allow those crystals to form.  

From: Josh Luthman 
Sent: Wednesday, April 08, 2015 6:41 PM
To: af@afmug.com 
Subject: Re: [AFMUG] Low Voltage Disconnect

If a 12v battery went down to 3v, is it toast?  Or if it's only happened once 
can you simply charge it and expect it to operate normally?


Josh Luthman
Office: 937-552-2340
Direct: 937-552-2343
1100 Wayne St
Suite 1337
Troy, OH 45373

On Wed, Apr 8, 2015 at 8:32 PM, Chuck McCown ch...@wbmfg.com wrote:

  +1 

  Screw LVD.  Do you want to risk losing connectivity when the LVD trips only 
to have power restored 10 minutes later?  If you power is that crappy that it 
will trip enough to significantly save your battery you do not have a large 
enough battery.  

  If you are doing LVD to prevent the chance of a infrequent deep discharge, it 
is still a waste of money.  Again, more battery is the answer.  A deep 
discharge once a year is not going to markedly reduce battery life unless you 
draw them clear down and leave them discharged for an extended period of time.  

  If you don’t want to put the money into a larger battery, put in telemetry 
that is monitored with a PRTG/MRTG type of tool that will send you and email 
when things are getting low.  Then you can run out with a generator or perhaps 
manually turn stuff off via telemetry until power comes back on.  

  I used to be a believer in LVD but not any more.  Now, if there is any chance 
of  keeping things running, I want to keep things running.  



  From: Josh Luthman 
  Sent: Wednesday, April 08, 2015 12:49 PM
  To: af@afmug.com 
  Subject: Re: [AFMUG] Low Voltage Disconnect

  First off I'd suggest getting enough batteries that you wouldn't need an LVD. 

  Second, I'd rather see my batteries lose a bit of life and keep the site up 
then have everything go down saving my batteries.

  Tertiary/finally, what equipment do you have now?  My regulator cuts off at 
19v and still provides 24v.  I figure the batteries are at 9.5v they're already 
sper low.


  Josh Luthman
  Office: 937-552-2340
  Direct: 937-552-2343
  1100 Wayne St
  Suite 1337
  Troy, OH 45373

  On Wed, Apr 8, 2015 at 2:44 PM, Christopher Tyler ch...@totalhighspeed.net 
wrote:

Looking for recommendations on a 24v LVD to protect our batteries from 
being drained.
Anyone have one they recommend?

--
Christopher Tyler
MTCRE/MTCNA/MTCTCE/MTCWE
Total Highspeed Internet Services
417.851.1107





Re: [AFMUG] Low Voltage Disconnect

2015-04-08 Thread Tim Reichhart
You can also use one of these: http://www.ebay.com/itm/390655816891 I am 
building my own battery back up using one of these for the setup.

 

Tim

 

From: Af [mailto:af-boun...@afmug.com] On Behalf Of Jaime Solorza
Sent: Wednesday, April 08, 2015 8:43 PM
To: Animal Farm
Subject: Re: [AFMUG] Low Voltage Disconnect

 

More battery. And I do like the Morning star idea. 

Jaime Solorza

On Apr 8, 2015 6:32 PM, Chuck McCown ch...@wbmfg.com wrote:

+1 

 

Screw LVD.  Do you want to risk losing connectivity when the LVD trips only to 
have power restored 10 minutes later?  If you power is that crappy that it will 
trip enough to significantly save your battery you do not have a large enough 
battery.  

 

If you are doing LVD to prevent the chance of a infrequent deep discharge, it 
is still a waste of money.  Again, more battery is the answer.  A deep 
discharge once a year is not going to markedly reduce battery life unless you 
draw them clear down and leave them discharged for an extended period of time.  

 

If you don’t want to put the money into a larger battery, put in telemetry that 
is monitored with a PRTG/MRTG type of tool that will send you and email when 
things are getting low.  Then you can run out with a generator or perhaps 
manually turn stuff off via telemetry until power comes back on.  

 

I used to be a believer in LVD but not any more.  Now, if there is any chance 
of  keeping things running, I want to keep things running.  

 

 

 

From: Josh Luthman mailto:j...@imaginenetworksllc.com  

Sent: Wednesday, April 08, 2015 12:49 PM

To: af@afmug.com 

Subject: Re: [AFMUG] Low Voltage Disconnect

 

First off I'd suggest getting enough batteries that you wouldn't need an LVD. 


Second, I'd rather see my batteries lose a bit of life and keep the site up 
then have everything go down saving my batteries.

 

Tertiary/finally, what equipment do you have now?  My regulator cuts off at 19v 
and still provides 24v.  I figure the batteries are at 9.5v they're already 
sper low.

 

 

Josh Luthman
Office: 937-552-2340
Direct: 937-552-2343
1100 Wayne St
Suite 1337
Troy, OH 45373

 

On Wed, Apr 8, 2015 at 2:44 PM, Christopher Tyler ch...@totalhighspeed.net 
wrote:

Looking for recommendations on a 24v LVD to protect our batteries from being 
drained.
Anyone have one they recommend?

--
Christopher Tyler
MTCRE/MTCNA/MTCTCE/MTCWE
Total Highspeed Internet Services
417.851.1107

 



Re: [AFMUG] Low Voltage Disconnect

2015-04-08 Thread Jaime Solorza
More battery. And I do like the Morning star idea.

Jaime Solorza
On Apr 8, 2015 6:32 PM, Chuck McCown ch...@wbmfg.com wrote:

   +1

 Screw LVD.  Do you want to risk losing connectivity when the LVD trips
 only to have power restored 10 minutes later?  If you power is that crappy
 that it will trip enough to significantly save your battery you do not have
 a large enough battery.

 If you are doing LVD to prevent the chance of a infrequent deep discharge,
 it is still a waste of money.  Again, more battery is the answer.  A deep
 discharge once a year is not going to markedly reduce battery life unless
 you draw them clear down and leave them discharged for an extended period
 of time.

 If you don’t want to put the money into a larger battery, put in telemetry
 that is monitored with a PRTG/MRTG type of tool that will send you and
 email when things are getting low.  Then you can run out with a generator
 or perhaps manually turn stuff off via telemetry until power comes back
 on.

 I used to be a believer in LVD but not any more.  Now, if there is any
 chance of  keeping things running, I want to keep things running.



  *From:* Josh Luthman j...@imaginenetworksllc.com
 *Sent:* Wednesday, April 08, 2015 12:49 PM
 *To:* af@afmug.com
 *Subject:* Re: [AFMUG] Low Voltage Disconnect

  First off I'd suggest getting enough batteries that you wouldn't need an
 LVD.

 Second, I'd rather see my batteries lose a bit of life and keep the site
 up then have everything go down saving my batteries.

 Tertiary/finally, what equipment do you have now?  My regulator cuts off
 at 19v and still provides 24v.  I figure the batteries are at 9.5v they're
 already sper low.


 Josh Luthman
 Office: 937-552-2340
 Direct: 937-552-2343
 1100 Wayne St
 Suite 1337
 Troy, OH 45373

 On Wed, Apr 8, 2015 at 2:44 PM, Christopher Tyler 
 ch...@totalhighspeed.net wrote:

 Looking for recommendations on a 24v LVD to protect our batteries from
 being drained.
 Anyone have one they recommend?

 --
 Christopher Tyler
 MTCRE/MTCNA/MTCTCE/MTCWE
 Total Highspeed Internet Services
 417.851.1107





Re: [AFMUG] Low Voltage Disconnect

2015-04-08 Thread Bill Prince
I should mention that this particular site is using a MidNite Solar The 
Kid solar controller. I got this controller because it had some neat 
features I hadn't seen anywhere else.


For one thing, it is 100% programmable. You can program the bulk 
voltage, the float voltage, the LVD voltage, everything. Plus, it will 
handle batteries as small as 12V all the way up to 48V, and everything 
in between. If you should decide that you want to have a 36V battery 
array, this can do it. It will also handle up to about 30 amps, 
regardless of voltage. This one has been in operation for about 6 
months, and so far I am happy with it. Our other sites are using some 
Morningstar controllers, and this one is much more consistent.


bp
part15sbs{at}gmail{dot}com

On 4/8/2015 1:14 PM, Bill Prince wrote:
Our 24V solar sites go up to about 28.5 volts when they are in bulk 
charge mode, then drop to about 27.5 volts when in float. A typical 
partly cloudty day is shown below for one of our solar sites. The 
big dip in the afternoon was some big clouds rolling through.


So we feel obliged to protect UBNT equipment with a 36/72 V - 24 V 
converter, because I think going up to 28.5V might just let the smoke out.

bp
part15sbs{at}gmail{dot}com



On 4/8/2015 12:28 PM, Josh Luthman wrote:

Correct:
continuous 16.8 ~ 31.2VDC
1 second 14.4 ~ 33.6VDC

If you already dropped them to 3v I think they'd be toast.

If you didn't have your charger you're not really testing the 
compatibility with Ubnt.  I believe the cut off is something like 
27.5v for the Airmax stuff and your charge is around 27.3 (depending 
on battery).  To me, that was too close for comfort and hence I use 
the regulator.


I don't know why you would expect them to stop at 10v. At 20v both 
Canopy and Ubnt would happily run.  The radios would continue to pull 
power from the batteries forever.



Josh Luthman
Office: 937-552-2340
Direct: 937-552-2343
1100 Wayne St
Suite 1337
Troy, OH 45373

On Wed, Apr 8, 2015 at 3:23 PM, Christopher Tyler 
ch...@totalhighspeed.net mailto:ch...@totalhighspeed.net wrote:


We are currently testing using two 12v 100Ah telecom batteries in
series.
They are slightly expensive to replace, especially when we will
have four (or more) at some sites, most will have two.

I'm using a Meanwell RSD-100B-24 regulator for the Tik RB-493G
router right now. Looks like the cutout for the regulator is
around 16v from what I can decipher from the datasheet.
My test radios (2 Canopy and 2 UBNT) are connected to the battery
without regulation.

This setup will drain the batteries until they are pretty much
dead and buried. I ran them over the weekend and I figured it
would stop draining around 10v at worst, it didn't. They ended up
around 6v in parallel or 3v per battery.  I figure I shaved off
some capacity and lifetime of my test batteries with that,
hopefully not too much.

--
Christopher Tyler
MTCRE/MTCNA/MTCTCE/MTCWE
Total Highspeed Internet Services
417.851.1107 tel:417.851.1107

- Original Message -
From: Josh Luthman j...@imaginenetworksllc.com
mailto:j...@imaginenetworksllc.com
To: af@afmug.com mailto:af@afmug.com
Sent: Wednesday, April 8, 2015 1:49:05 PM
Subject: Re: [AFMUG] Low Voltage Disconnect

First off I'd suggest getting enough batteries that you wouldn't
need an
LVD.

Second, I'd rather see my batteries lose a bit of life and keep
the site up
then have everything go down saving my batteries.

Tertiary/finally, what equipment do you have now?  My regulator
cuts off at
19v and still provides 24v.  I figure the batteries are at 9.5v
they're
already sper low.


Josh Luthman
Office: 937-552-2340
Direct: 937-552-2343
1100 Wayne St
Suite 1337
Troy, OH 45373

On Wed, Apr 8, 2015 at 2:44 PM, Christopher Tyler
ch...@totalhighspeed.net mailto:ch...@totalhighspeed.net
wrote:

 Looking for recommendations on a 24v LVD to protect our
batteries from
 being drained.
 Anyone have one they recommend?

 --
 Christopher Tyler
 MTCRE/MTCNA/MTCTCE/MTCWE
 Total Highspeed Internet Services
 417.851.1107 tel:417.851.1107










Re: [AFMUG] Low Voltage Disconnect

2015-04-08 Thread George Skorup (Cyber Broadcasting)
If the temp comp probe isn't connected, it assumes 25C/77F, IIRC. I 
would definitely not run it without the temp probe unless this is in a 
NOC or controlled shelter type environment.


There's a jumper that controls the battery type in use. Gel for gel, SLA 
for VRLA, AGM, etc. That also does something with the LVD, but I don't 
remember what. The temp compensation also has an effect on the LVD. It's 
all microprocessor controlled.


With the remote cable connected and batteries + temp sensor 
disconnected, adjust the pot on the BCM (not the power supply) for your 
desired float voltage with a meter on the battery terminals. I usually 
set it to 27.6. Do not touch that potentiometer with the sensor, 
batteries or load connected.


Power everything off then connect the temp probe and batteries. Power it 
back up. Like Ken said, the BCM adjusts the TSP power supply output 
voltage. Check battery output voltage at the BCM, look at your shunt 
reading or clamp-on ammeter, etc. You should see 1 amp (that's the BCM 
current limit) if the batteries are 90% or so.


The LVD will cut off at 1.83 volt per cell for SLA. The BATT-OK contact 
will open slightly before the LVD kicks in as an early warning (awesome 
feature). So 22V for the BCM24 and 44V for the BCM48. That is very, very 
conservative if you ask me, especially for a UPS. The batteries are not 
being cycled daily like solar. AGMs can be taken down very deep in a 
typical UPS situation and not sustain any damage or loss of capacity. 
Again, this is not solar.


The Mean Well AD-155 LVD is much lower. Like 19.5V for the 155B, IIRC. 
Fine with me since I put those at smaller sites with smaller batteries, 
and they're cheap batteries, so if it ruins them, oh well, replace.


On 4/8/2015 5:54 PM, Ken Hohhof wrote:
With the Traco setup, the BCM controls the power supply voltage to be 
what is needed to charge the batteries.  The loads get that same 
voltage, so the output will be 27 or 28 volts not 24.


Is there a possibility the battery remote temperature probe is not 
connected correctly or is bad?  I don't know what happens if that is 
open.  Some chargers will assume 27*C if the probe is missing, I don't 
know what Traco does.



-Original Message- From: Bill Prince
Sent: Wednesday, April 08, 2015 5:02 PM
To: af@afmug.com
Subject: Re: [AFMUG] Low Voltage Disconnect

I've never used this setup, but with the chargers/controllers I've used,
the output of the power supply has to be greater than 24V. In fact,
doesn't the output of the power supply have to be at least 28 or 28.5
volts? This would allow the battery controller to modulate the output to
the batteries, whether it be bulk, absorption, or float?


bp
part15sbs{at}gmail{dot}com

On 4/8/2015 1:27 PM, Christopher Tyler wrote:
Attached is a picture of the setup as it is now.  24 supply and 24v 
loads, everything feeds through the Meanwell regulator.


I followed the instructions from Traco, but as you can see the 
battery is currently at about 23v and that is what the Traco power 
supply is outputting. The instructions say to turn the power supply 
all the way down and to let the BCM control the output. It's all set 
up, jumper is in position 1, the feedback cable is connected between 
the PS and the BCM but the BCM doesn't appear to be telling the power 
supply to do anything except turn on.


Anyone with some experience with Traco care to tell me what I'm doing 
wrong. It's worked like this since day one, the BCM doesn't appear to 
be doing anything regardless of the battery voltage.









Re: [AFMUG] Low Voltage Disconnect

2015-04-08 Thread Josh Luthman
If a 12v battery went down to 3v, is it toast?  Or if it's only happened
once can you simply charge it and expect it to operate normally?


Josh Luthman
Office: 937-552-2340
Direct: 937-552-2343
1100 Wayne St
Suite 1337
Troy, OH 45373

On Wed, Apr 8, 2015 at 8:32 PM, Chuck McCown ch...@wbmfg.com wrote:

   +1

 Screw LVD.  Do you want to risk losing connectivity when the LVD trips
 only to have power restored 10 minutes later?  If you power is that crappy
 that it will trip enough to significantly save your battery you do not have
 a large enough battery.

 If you are doing LVD to prevent the chance of a infrequent deep discharge,
 it is still a waste of money.  Again, more battery is the answer.  A deep
 discharge once a year is not going to markedly reduce battery life unless
 you draw them clear down and leave them discharged for an extended period
 of time.

 If you don’t want to put the money into a larger battery, put in telemetry
 that is monitored with a PRTG/MRTG type of tool that will send you and
 email when things are getting low.  Then you can run out with a generator
 or perhaps manually turn stuff off via telemetry until power comes back
 on.

 I used to be a believer in LVD but not any more.  Now, if there is any
 chance of  keeping things running, I want to keep things running.



  *From:* Josh Luthman j...@imaginenetworksllc.com
 *Sent:* Wednesday, April 08, 2015 12:49 PM
 *To:* af@afmug.com
 *Subject:* Re: [AFMUG] Low Voltage Disconnect

  First off I'd suggest getting enough batteries that you wouldn't need an
 LVD.

 Second, I'd rather see my batteries lose a bit of life and keep the site
 up then have everything go down saving my batteries.

 Tertiary/finally, what equipment do you have now?  My regulator cuts off
 at 19v and still provides 24v.  I figure the batteries are at 9.5v they're
 already sper low.


 Josh Luthman
 Office: 937-552-2340
 Direct: 937-552-2343
 1100 Wayne St
 Suite 1337
 Troy, OH 45373

 On Wed, Apr 8, 2015 at 2:44 PM, Christopher Tyler 
 ch...@totalhighspeed.net wrote:

 Looking for recommendations on a 24v LVD to protect our batteries from
 being drained.
 Anyone have one they recommend?

 --
 Christopher Tyler
 MTCRE/MTCNA/MTCTCE/MTCWE
 Total Highspeed Internet Services
 417.851.1107





Re: [AFMUG] Low Voltage Disconnect

2015-04-08 Thread Josh Luthman
DEFINITELY between batteries.


Josh Luthman
Office: 937-552-2340
Direct: 937-552-2343
1100 Wayne St
Suite 1337
Troy, OH 45373

On Wed, Apr 8, 2015 at 4:37 PM, Josh Baird joshba...@gmail.com wrote:

 I can't speak for the LVD (I'm sure someone can), but I don't see any
 fuses on your DC distribution.  I may just be missing them, but if not, you
 may want to consider adding some.  It would be a good practice to put DC
 breakers/fuses in between your battery bank and charger as well.

 On Wed, Apr 8, 2015 at 4:27 PM, Christopher Tyler 
 ch...@totalhighspeed.net wrote:

 Might help if there was a pic, eh?

 --
 Christopher Tyler
 MTCRE/MTCNA/MTCTCE/MTCWE
 Total Highspeed Internet Services
 417.851.1107

 - Original Message -
 From: Christopher Tyler ch...@totalhighspeed.net
 To: af@afmug.com
 Sent: Wednesday, April 8, 2015 3:27:15 PM
 Subject: Re: [AFMUG] Low Voltage Disconnect

 Attached is a picture of the setup as it is now.  24 supply and 24v
 loads, everything feeds through the Meanwell regulator.

 I followed the instructions from Traco, but as you can see the battery is
 currently at about 23v and that is what the Traco power supply is
 outputting. The instructions say to turn the power supply all the way down
 and to let the BCM control the output. It's all set up, jumper is in
 position 1, the feedback cable is connected between the PS and the BCM but
 the BCM doesn't appear to be telling the power supply to do anything except
 turn on.

 Anyone with some experience with Traco care to tell me what I'm doing
 wrong. It's worked like this since day one, the BCM doesn't appear to be
 doing anything regardless of the battery voltage.

 --
 Christopher Tyler
 MTCRE/MTCNA/MTCTCE/MTCWE
 Total Highspeed Internet Services
 417.851.1107

 - Original Message -
 From: Christopher Tyler ch...@totalhighspeed.net
 To: af@afmug.com
 Sent: Wednesday, April 8, 2015 3:19:35 PM
 Subject: Re: [AFMUG] Low Voltage Disconnect

 Commercial power.

 --
 Christopher Tyler
 MTCRE/MTCNA/MTCTCE/MTCWE
 Total Highspeed Internet Services
 417.851.1107

 - Original Message -
 From: Ken Hohhof af...@kwisp.com
 To: af@afmug.com
 Sent: Wednesday, April 8, 2015 3:18:25 PM
 Subject: Re: [AFMUG] Low Voltage Disconnect

 Is this powered by solar or commercial power?
 One approach is to use a charger that includes a LVD, like the Traco
 TSP-BCM
 (which controls a TSP series AC/DC power supply).
 The LVD is fixed not adjustable.


 -Original Message-
 From: Christopher Tyler
 Sent: Wednesday, April 08, 2015 2:23 PM
 To: af@afmug.com
 Subject: Re: [AFMUG] Low Voltage Disconnect

 We are currently testing using two 12v 100Ah telecom batteries in series.
 They are slightly expensive to replace, especially when we will have four
 (or more) at some sites, most will have two.

 I'm using a Meanwell RSD-100B-24 regulator for the Tik RB-493G router
 right
 now. Looks like the cutout for the regulator is around 16v from what I can
 decipher from the datasheet.
 My test radios (2 Canopy and 2 UBNT) are connected to the battery without
 regulation.

 This setup will drain the batteries until they are pretty much dead and
 buried. I ran them over the weekend and I figured it would stop draining
 around 10v at worst, it didn't. They ended up around 6v in parallel or 3v
 per battery.  I figure I shaved off some capacity and lifetime of my test
 batteries with that, hopefully not too much.

 --
 Christopher Tyler
 MTCRE/MTCNA/MTCTCE/MTCWE
 Total Highspeed Internet Services
 417.851.1107

 - Original Message -
 From: Josh Luthman j...@imaginenetworksllc.com
 To: af@afmug.com
 Sent: Wednesday, April 8, 2015 1:49:05 PM
 Subject: Re: [AFMUG] Low Voltage Disconnect

 First off I'd suggest getting enough batteries that you wouldn't need an
 LVD.

 Second, I'd rather see my batteries lose a bit of life and keep the site
 up
 then have everything go down saving my batteries.

 Tertiary/finally, what equipment do you have now?  My regulator cuts off
 at
 19v and still provides 24v.  I figure the batteries are at 9.5v they're
 already sper low.


 Josh Luthman
 Office: 937-552-2340
 Direct: 937-552-2343
 1100 Wayne St
 Suite 1337
 Troy, OH 45373

 On Wed, Apr 8, 2015 at 2:44 PM, Christopher Tyler 
 ch...@totalhighspeed.net
 wrote:

  Looking for recommendations on a 24v LVD to protect our batteries from
  being drained.
  Anyone have one they recommend?
 
  --
  Christopher Tyler
  MTCRE/MTCNA/MTCTCE/MTCWE
  Total Highspeed Internet Services
  417.851.1107
 
 






Re: [AFMUG] Low Voltage Disconnect

2015-04-08 Thread Bill Prince
I've never used this setup, but with the chargers/controllers I've used, 
the output of the power supply has to be greater than 24V. In fact, 
doesn't the output of the power supply have to be at least 28 or 28.5 
volts? This would allow the battery controller to modulate the output to 
the batteries, whether it be bulk, absorption, or float?



bp
part15sbs{at}gmail{dot}com

On 4/8/2015 1:27 PM, Christopher Tyler wrote:

Attached is a picture of the setup as it is now.  24 supply and 24v loads, 
everything feeds through the Meanwell regulator.

I followed the instructions from Traco, but as you can see the battery is 
currently at about 23v and that is what the Traco power supply is outputting. 
The instructions say to turn the power supply all the way down and to let the 
BCM control the output. It's all set up, jumper is in position 1, the feedback 
cable is connected between the PS and the BCM but the BCM doesn't appear to be 
telling the power supply to do anything except turn on.

Anyone with some experience with Traco care to tell me what I'm doing wrong. 
It's worked like this since day one, the BCM doesn't appear to be doing 
anything regardless of the battery voltage.





Re: [AFMUG] Low Voltage Disconnect

2015-04-08 Thread Ken Hohhof
With the Traco setup, the BCM controls the power supply voltage to be what 
is needed to charge the batteries.  The loads get that same voltage, so the 
output will be 27 or 28 volts not 24.


Is there a possibility the battery remote temperature probe is not connected 
correctly or is bad?  I don't know what happens if that is open.  Some 
chargers will assume 27*C if the probe is missing, I don't know what Traco 
does.



-Original Message- 
From: Bill Prince

Sent: Wednesday, April 08, 2015 5:02 PM
To: af@afmug.com
Subject: Re: [AFMUG] Low Voltage Disconnect

I've never used this setup, but with the chargers/controllers I've used,
the output of the power supply has to be greater than 24V. In fact,
doesn't the output of the power supply have to be at least 28 or 28.5
volts? This would allow the battery controller to modulate the output to
the batteries, whether it be bulk, absorption, or float?


bp
part15sbs{at}gmail{dot}com

On 4/8/2015 1:27 PM, Christopher Tyler wrote:
Attached is a picture of the setup as it is now.  24 supply and 24v loads, 
everything feeds through the Meanwell regulator.


I followed the instructions from Traco, but as you can see the battery is 
currently at about 23v and that is what the Traco power supply is 
outputting. The instructions say to turn the power supply all the way down 
and to let the BCM control the output. It's all set up, jumper is in 
position 1, the feedback cable is connected between the PS and the BCM but 
the BCM doesn't appear to be telling the power supply to do anything 
except turn on.


Anyone with some experience with Traco care to tell me what I'm doing 
wrong. It's worked like this since day one, the BCM doesn't appear to be 
doing anything regardless of the battery voltage.