HI All, I've got someone who might want a really big array for his house, something above the 30kW form for PGE. ( he wants 65kW) I'm looking for any information etc on larger interconnection tips, advice etc for dealing with PGE thanks in advance. jay peltz power j...@asis.com

Re: [RE-wrenches] California wrenches PGE

2015-01-16 Thread jay peltz
I am just asking about any advice for the paperwork process above 30kW with pge as I've never done one this large for a residence. Customer has a standard 400 amp 240v single phase connection. Thanks Jay Peltz power On Jan 16, 2015, at 5:25 PM, Jerry Shafer jerrysgarag...@gmail.com

Re: [RE-wrenches] 24V Zephyr Vent Fan from a Magnum MS4024PAE inverter

2015-01-07 Thread jay peltz
The router version magnum remote has a dry contact relay ME-RTR Jay Peltz power. On Jan 7, 2015, at 10:56 AM, Ray Walters r...@solarray.com wrote: The Magnums do not have relays available like the old SWs, but you can run a Zephyr directly from either a Outback FM controller

[RE-wrenches] wire sizing question

2015-01-02 Thread jay peltz
Happy new year all. I have a question on wire sizing for the following. 250 amp breaker, in a UL enclosure ( say midnite or outback etc) conduit from battery box to enclosure I'm wondering how folks size this for ampacity not voltage drop. thanks jay peltz power

[RE-wrenches] Outback control boards

2014-12-20 Thread jay peltz
Hi all I'm looking for control boards to converter 2 GVFX 3648 to VFX. If anyone has some or knows where to get them ( outback won't sell them to me) Please let me know off list Thanks Jay Peltz power___ List sponsored by Redwood Alliance List

Re: [RE-wrenches] Magnum System - Discharged Battery Bank

2014-12-19 Thread Jay Peltz
at one go? Jay Peltz power Sent from my iPhone On Dec 19, 2014, at 9:47 AM, jarmo.venalai...@schneider-electric.com wrote: Hi: This cell reversal ability of lead acid batteries gives good perspective on just how much you can mistreat them and beat them up and still have an expectation

Re: [RE-wrenches] Honda EM7000is Generator Two wire start Gizmo?

2014-12-17 Thread jay peltz
Hi dan Funny, was just at a place yesterday with one They used a GSCM mini. Works ok. Custom hookup. Jay Peltz power ( ps if you need a GSCM I've got one) On Dec 17, 2014, at 7:07 AM, d...@foxfire-energy.com wrote: Anyone have a solid recommendation for interfacing a Honda EM7000is

Re: [RE-wrenches] Magnum System - Discharged Battery Bank

2014-12-17 Thread Jay Peltz
All magnum auxiliaries are battery direct ( AGS,BMK) so they drain the battery. Jay Peltz power Sent from my iPhone On Dec 17, 2014, at 10:20 AM, Allan Sindelar al...@sindelarsolar.com wrote: Corey, In a somewhat similar situation years ago: a client had installed a generator/inverter

Re: [RE-wrenches] Magnum System - Discharged Battery Bank

2014-12-16 Thread jay peltz
How long has this system been operational? Jay Peltz power On Dec 16, 2014, at 6:27 PM, Corey Shalanski cshalan...@joule-energy.com wrote: Wrenches, I visited a customer today whose grid-tied battery backup system suffered some sort of catastrophic failure, and now I'm trying

Re: [RE-wrenches] Programmable Battery Charger

2014-12-15 Thread jay peltz
the AC and hence the DC for these lower voltage units. jay peltz power On Dec 15, 2014, at 5:38 PM, Kirk Herander wrote: This has been discussed on this list in years past. It is possible to use an outback charge controller as a battery charger. You need to put the 120 AC into a bridge

Re: [RE-wrenches] Programmable Battery Charger

2014-12-15 Thread jay peltz
HI Jerry, Just a standard bridge rectifier, with correct amp rating. AC to diode to CC, thats it. All regulation is via CC. jay On Dec 15, 2014, at 7:30 PM, Jerry Shafer wrote: Very interesting, what diodes did you use to rectify the AC, it sounds similar to the wind machine designs I

Re: [RE-wrenches] AC coupling SolarEdge

2014-12-10 Thread jay peltz
the whole array. Simple, easy reliable. And in the end you'd need to do this anyway even if you did some string disco's as you mention is a modest ( small) battery which means its easy to over cook it, and Im guessing its VRLA. jay peltz power On Dec 10, 2014, at 6:12 AM, Mac Lewis wrote: Hello

[RE-wrenches] UL 1703

2014-12-10 Thread jay peltz
HI All, After reading the info from bill and others, I guess I'm still unclear if we have to buy listed systems ( rack/modules) or components. And I don't know where to find a list of listed components/systems. Anybody know? thanks in advance, jay peltz power

Re: [RE-wrenches] AC coupling SolarEdge

2014-12-10 Thread jay peltz
Question Is the Hz shift/ power reduction included/required in all battery less inverters? Thanks Jay Peltz power___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address settings: http

Re: [RE-wrenches] common ground on fm80 aux output?

2014-12-05 Thread jay peltz
Hi ray. , There is the diversion solid state for SS relays. Jay Peltz power On Dec 5, 2014, at 3:08 PM, Ray Walters r...@solarray.com wrote: I don't believe the aux is PWM. It should be a straight 12 v 200 mA output as I recall. Its just enough to run a battery fan, or a 12 v relay

Re: [RE-wrenches] common ground on fm80 aux output?

2014-12-05 Thread jay peltz
no? Jay Peltz power On Dec 5, 2014, at 2:09 PM, Hugh Piggott h...@scoraigwind.co.uk wrote: Hi Hugh again Just to clarify the set up: The SSR controls the AC power from the inverter to the heating load. It switches partway through each half cycle and thus controls the power to the load

Re: [RE-wrenches] Aux Output on Outback Devices

2014-12-05 Thread jay peltz
the aux wires, and poof 1 dead inverter. Jay Peltz power On Dec 5, 2014, at 4:19 PM, William Miller will...@millersolar.com wrote: Friends: I suspect my employees may have fried a VFX3648 recently by shorting the Aux output leads. Does anyone know if the FX inverter Aux output

Re: [RE-wrenches] common ground on fm80 aux output?

2014-12-05 Thread jay peltz
Hi Roy, The fm-80 has two different diversion options. Diversion:relay And Diversion: solid state. ( which is PWM) Jay Peltz power On Dec 5, 2014, at 5:34 PM, Windsine Inc. winds...@gmail.com wrote: oh ok, now figured out what your doing. The aux output on the FM80 is not PWM

Re: [RE-wrenches] Aux Output on Outback Devices

2014-12-05 Thread jay peltz
Hi William Page 23 of the VFX manual states will reset if short circuited, no fusing is required. Jay Peltz power On Dec 5, 2014, at 5:01 PM, William Miller will...@millersolar.com wrote: Jay: I suspect shorting the Aux leads will kill an FX inverter. We traced the Aux PCB

Re: [RE-wrenches] Aux Output on Outback Devices

2014-12-05 Thread jay peltz
this is current, but they are all the same I just looked at the 2008 version from the previous website and its exactly the same, same page even. jay On Dec 5, 2014, at 7:14 PM, William Miller wrote: Jay: Is this true for an FX manufactured in 2003? What version manual is this from

Re: [RE-wrenches] Parallel Wire combining

2014-12-03 Thread jay peltz
numbers. The watts per foot is extremely low, so overheating of wires I don't believe an issue either. my 2 cents, jay peltz power On Dec 3, 2014, at 10:19 AM, Daniel Young wrote: Three things: 1. The skin effect would only apply in and AC situation, correct?. So we need to keep AC/DC separated

Re: [RE-wrenches] Mitsubishi Mini Split fighting with Outback VFX Off Grid

2014-12-01 Thread jay peltz
. And I'm going to agree with Mitsubishi, most likely the inverter. The OB/FX just isn't compatible with some machines. jay peltz power On Nov 30, 2014, at 4:29 PM, d...@foxfire-energy.com d...@foxfire-energy.com wrote: We're still not at the bottom of it. Seems Mitsubishi is doing their level

Re: [RE-wrenches] propane generator

2014-11-21 Thread jay peltz
Hi Mac Thanks Easy fix for the 120 only is to install small transformer to step up 240 to trick the avr. I'll check out the ecogen Thx Jay On Nov 21, 2014, at 5:41 AM, Mac Lewis maclew...@gmail.com wrote: Hi Jay, Although I like the Cummins units, we have a fairly weak Cummins

[RE-wrenches] propane generator

2014-11-20 Thread jay peltz
Hi All, I know this has been discussed before. I can't seem to find the threads about propane generators. I've got a client with a Kohler 8.5 that is having problems. Hes looking for good quality options other than the Kohler. thanks in advance, jay

Re: [RE-wrenches] Suspect MX 60

2014-11-19 Thread jay peltz
Hi drake. Other options are a bad temp sensor. And you can adjust end amps, on the mx-60 Go to. Misc Next Next Default is 0. Adjust as needed. Jay Peltz power On Nov 18, 2014, at 6:51 AM, Drake drake.chamber...@redwoodalliance.org wrote: Hello Wrenches, An MX 60

Re: [RE-wrenches] Suspect MX 60

2014-11-19 Thread jay peltz
HI Tump, I was just informed by OB that its $90 for a mate 1 firmware update. If its a older version with the AGS bug, then they will upgrade for free. 4.1.2 I believe. jay peltz power On Nov 19, 2014, at 9:30 AM, Tump wrote: To add; I am a firm believer that every few years I will send

Re: [RE-wrenches] Comp roof care

2014-11-10 Thread jay peltz
Google yellow spaghetti roof walkway Best stuff ever Jay Peltz power On Nov 9, 2014, at 9:27 PM, Jerry Shafer jerrysgarag...@gmail.com wrote: Like you said if the roof gets hot get off, we do use carpet strips but they are messy, i have been on a roof since i could walk (ya really

Re: [RE-wrenches] Aqueous Hybrid Ion batteries

2014-11-10 Thread jay peltz
Hi Marco, what sort of price are we talking about? thanks jay On Nov 10, 2014, at 4:31 PM, Marco Mangelsdorf wrote: This battery module—I have one sitting in my warehouse—is rated at 3,000 cycles @ 100 percent DOD. I don’t know of anything else that’s comparable on the market

Re: [RE-wrenches] J-Box Damage

2014-11-06 Thread jay peltz
Hi Corey, To me the question is did it happen before the uninstall or during the uninstall? Could be lightning as Jeff says. bad j boxes I'm leaning towards something really weird about how it was taken down. jay peltz power On Nov 4, 2014, at 1:38 PM, Corey Shalanski wrote: Wrenches

Re: [RE-wrenches] magnum question

2014-11-03 Thread jay peltz
showed the menus/ adjustments Mostly this what folks need IMHO. If they have a problem they'll call but sometimes getting them to understand where to go/ how to get there is difficult via phone. But a map included with each item ( RC/ARC only really) will really help out. Thanks jay peltz power

Re: [RE-wrenches] Passive Battery Venting

2014-10-30 Thread jay peltz
Hi drake, I think you need to charge him so you can actually calculate/design the max H2 for any condition and size the vent system for that. And lawyer = conduit Jay Peltz power. On Oct 29, 2014, at 5:19 PM, Drake drake.chamber...@redwoodalliance.org wrote: Hi Daniel, I

Re: [RE-wrenches] PV wire

2014-10-23 Thread jay peltz
HI Marco I think there has been a lot of bad/old information about PV vs double insulated wire. However now it only listed as PV wire. 690.35 D (3) jay peltz power On Oct 23, 2014, at 2:29 PM, Marco Mangelsdorf wrote: Yet again this “PV wire” thing rears its head. For our PV systems

[RE-wrenches] magnum question

2014-10-23 Thread jay peltz
HI All, Does anyone have a person at Magnum in engineering or higher up than tech support. I've got a problem with an inverter that tech support won't or can't help with. thanks jay peltz power ___ List sponsored by Redwood Alliance List Address

Re: [RE-wrenches] Grundfos SQFlex

2014-10-20 Thread jay peltz
Hi Ron Where did you read that the CU 200 is only good for 120vac. The manual I see shows 240vac 50/60hz? Jay Peltz power. On Oct 20, 2014, at 6:21 PM, Ron @ earthRight Solar solarea...@solareagle.com wrote: Hello water pumping Wrenches, I have a customer who has a Grundfos SQFlex

Re: [RE-wrenches] Thirsty batteries: Daily absorb cycles on top of grid powered float

2014-10-06 Thread jay peltz
Hi mick, The more current classic firmware has a VMX mode which is adjustable for absorb time based on how quickly it got there, plus you can set it to skip days etc. Also. The new wiz bang jr allows better return amp monitoring So if you are running old firmware, good time to upgrade. Jay

Re: [RE-wrenches] TL inverter with long DC Feeder

2014-10-06 Thread jay peltz
I do believe the outback and midnite combiners have a lock hole to prevent exactly your concern. unauthorized access. jay peltz power On Oct 6, 2014, at 11:40 AM, William Miller wrote: Wrenches: We are getting up to speed on using transformer-less inverters. I have advocated long

Re: [RE-wrenches] Fall Protection Recommendations?

2014-10-06 Thread jay peltz
I've always been a fan of Petzl stuff, super comfortable. Here is a quick link I found. http://www.patrollersupply.com/equipment/item_4446.asp jay peltz power On Oct 6, 2014, at 3:31 PM, David Brearley wrote: Hi Bill, Joey Krys not only sells a lot of fall protection equipment, but also

Re: [RE-wrenches] Microfractures in PV Modules

2014-10-04 Thread jay peltz
Hi Chris, Do you mean the AHJ? jay On Oct 4, 2014, at 8:20 AM, Christopher Warfel wrote: Recently a inspector raised the issue of microfractures in pv modules, and that the existence of such fractures would require replacement of the modules and a failing of the system inspection. I

Re: [RE-wrenches] Microfractures in PV Modules

2014-10-04 Thread jay peltz
from a shoulder pressing on a cell area ( carrying it like a sheet of plywood). If you are looking for someone who can do these field tests, contact me off site, jay peltz power On Oct 4, 2014, at 10:46 AM, Christopher Warfel wrote: No, this is a third party quality assurance inspector

Re: [RE-wrenches] 12VDC LED lighting for Edison E26 socket

2014-09-28 Thread jay peltz
HI Dan, I would suggest looking at Backwoods. I've used some of theirs and they are nice. jay peltz power On Sep 28, 2014, at 10:44 AM, Dan Fink wrote: Esteemed Wrenches; Anyone have any recommendations for 12 volt DC, 3 - 12 watt Edison E26-27 screw base (standard light bulb socket

[RE-wrenches] outback radian on 120v

2014-09-25 Thread jay peltz
HI All, I can't seem to find this. Anyone know if you can battery charge a Radian on 120v? 120/240 60hz version. thanks jay ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address

Re: [RE-wrenches] Watsun problem

2014-09-22 Thread jay peltz
Hi Jesse I've always found the tech support at Array tech to be really good I'd call them. Jay Peltz power On Sep 22, 2014, at 9:30 AM, Solar dahlso...@gmail.com wrote: Hello, I am having an issue with a Watsun dual axis tracker. It is a 24VDC model, run of a battery bank

Re: [RE-wrenches] wood gasification to grid

2014-09-21 Thread jay peltz
. But how do you deal with the MPPT working with the generator output? It wouldn't work like a PV output. I know from experience that trying to use standard batteryless inverters on motors ( such as hydros) doesn't always work. Some inverters ( brands) work, some don't jay peltz power

Re: [RE-wrenches] Sunny Island sending power to the generator??

2014-09-19 Thread Jay Peltz
it handles the generator vs other inverters, ( it has to) so I'm not sure I agree with the email from Schneider. Jay Peltz power Sent from my iPhone On Sep 19, 2014, at 6:11 AM, Tump t...@swnl.net wrote: I too must agree with Kevin, SMA SI is the kind! (although I have had a few fail) SMA

Re: [RE-wrenches] Enphase AC coupled through autotransformer

2014-09-19 Thread Jay Peltz
Hi drake I've done exactly this, VFX 3524 2 x enphase 190's Worked fine. I didn't like the 60 hz ripple so I removed it. Jay Peltz power Sent from my iPhone On Sep 18, 2014, at 4:46 PM, Drake drake.chamber...@redwoodalliance.org wrote: Hello Wrenches, Has anyone AC coupled

Re: [RE-wrenches] LiFePo4

2014-09-17 Thread jay peltz
HI Ray, We could still use them now and for legacy systems. I can only think it could be a big help in saving battery banks of all types. jay peltz power On Sep 17, 2014, at 6:32 AM, Ray Walters wrote: I think if we started over fresh with our lead acid battery system designs, we would find

Re: [RE-wrenches] Decking only flashed attachment?

2014-09-16 Thread jay peltz
HI Lars, you don't mention the type of roof cover, guessing comp shingle? have you looked at the DPW easy feet? A slight modification is to use flat flashing first, then anchor the easy feet through the flashing designed for exactly the roof you have jay peltz power On Sep 15, 2014, at 9:20

Re: [RE-wrenches] Poletop rack with easy tilt change...anybody got that?

2014-09-08 Thread jay peltz
Hi Mick, Ive been using General Specialites out of Idaho for the larger ones. http://generalspecialties.biz/ They have a geared winch option for the larger ones. Very solid design. jay peltz power On Sep 8, 2014, at 8:11 AM, Mick Abraham wrote: Hi, My client wants one of the larger top

[RE-wrenches] trace SW plus fan

2014-09-07 Thread jay peltz
the fan/s Done plenty of SW's though. Any help on this one? thanks jay peltz power ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address settings: http://lists.re-wrenches.org/options.cgi

Re: [RE-wrenches] Rapid shutdown questions

2014-08-31 Thread jay peltz
HI Dan, If you are doing 24v battery or below, you should be able to ignore the battery rapid shutdown part. IE under 30v jay peltz power On Aug 30, 2014, at 2:04 PM, Dan Fink wrote: Dave; I feel your pain as do many others. I feel like I've been Rick-rolled on the whole 690.12 thing

Re: [RE-wrenches] Assembly Protects Conductors?

2014-08-23 Thread jay peltz
others out there way way better on code than me, and so correct me please. IMHO, I think this 2nd 25% has been misinterpreted to mean conductor instead of breaker derating. jay peltz power On Aug 23, 2014, at 8:41 AM, Mark Frye wrote: Ray, I can't follow you all the way down that path

[RE-wrenches] wifi or like switched outlets

2014-08-21 Thread jay peltz
by wire. Thanks all, jay peltz power ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive

Re: [RE-wrenches] High specific gravity

2014-08-12 Thread jay peltz
HI Dan, I would respectfully disagree that hydrometers are always accurate. However both can be easily tested with distilled water, should be 1.0 Jay Peltz Power On Aug 12, 2014, at 7:40 PM, Dan Fink wrote: Brian; That was to be my next response to Mac after he checked the refractometer

[RE-wrenches] 3 phase battery inverters

2014-07-23 Thread Jay Peltz
Hi all I have a client who Might need 3 phase battery based inverters for 208/120 US 60 hz. I believe the choices are: SI, XW( with reprogramming) and outback FX line. This is not for motors, but running off of a 3 phase generator. Anything I've missed? Jay Peltz power PS thanks for all

Re: [RE-wrenches] 3 phase battery inverters

2014-07-23 Thread jay peltz
Hi Guys, Yes that could work, but then you wouldn't have genny backup, which isn't a good idea IMHO. I'm still researching if the client really needs 3 phase or not. thanks all, jay On Jul 23, 2014, at 4:21 PM, Chris Mason wrote: Are the loads three phase or just the generator

Re: [RE-wrenches] 2v metal cased cells

2014-07-12 Thread jay peltz
that individual steel cased cells will have greater surface area and cool faster than other batteries. But maybe others have different ideas? Jay On Jul 12, 2014, at 5:01 AM, Tump t...@swnl.net wrote: Why would you NOT use the Surrette batteries. Far easier to move, up to 2400 Has@20 hr rate

[RE-wrenches] 2v metal cased cells

2014-07-11 Thread jay peltz
Hi All, I'm wondering what options people are using for steel cased individual 2v industrial cells. thanks jay ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address settings

Re: [RE-wrenches] 2v metal cased cells

2014-07-11 Thread jay peltz
HI All, I'm sorry I was unclear on my question. I am looking for individual steel cased 2v industrial batteries, not 12v or 24v packs. thanks jay ps thanks chris. On Jul 11, 2014, at 4:13 PM, Ray Walters wrote: HUPs are 6 individual cells in a heavy steel case. The individual cells can

Re: [RE-wrenches] Combining Multiple Inverters

2014-06-27 Thread jay peltz
Hi guys, Sma installation manual us-5000-8000 inverters. section 6.5, page 42. Maximum over current protection 50 amps. Section 6.5.1, page 42 #6 wire max. Jay Peltz power On Jun 27, 2014, at 4:53 AM, richard.l.rat...@valley.net (Richard L Ratico) wrote: I may be playing

Re: [RE-wrenches] Combining Multiple Inverters

2014-06-26 Thread Jay Peltz
I have never seen an inverter that does not specify a OCPD size. Jay Peltz power. Sent from my iPhone On Jun 26, 2014, at 3:20 PM, Dave Click davecl...@fsec.ucf.edu wrote: Corey, The line of reasoning is faulty. It's 705.12(D)(1). Micro-inverters are the exception because

Re: [RE-wrenches] Timer for SQF pump

2014-06-22 Thread jay peltz
Yep non inductive. Try measuring the current ramp some time. jay peltz power On Jun 22, 2014, at 6:41 PM, Jerry Shafer wrote: There are self powered electronic 7 day timers and to be safe I would make the connection at the float low volts low current and designed to stop the pump On Jun

Re: [RE-wrenches] SolarJack Controller

2014-06-03 Thread jay peltz
Hi Mac Try Sunpumps. Jay Peltz power On Jun 3, 2014, at 5:55 AM, Mac Lewis maclew...@gmail.com wrote: Hello wrenches, Does any one recognize the controller in the attached photo? It is a SolarJack brand. The caretaker thinks its a pump controller but I'm not familiar

Re: [RE-wrenches] 2014 NEC AFCI

2014-05-28 Thread jay peltz
Hi Kirk I thought about that, but you'll still need it on for the 5 minute clock. If Nick is right and no voltage is acceptable on output side, then I don't see how even with relays etc to get it to work? Jay Peltz power On May 28, 2014, at 7:32 AM, Kirk Herander k...@vtsolar.com wrote

[RE-wrenches] China trade war

2014-05-28 Thread jay peltz
Can anyone point me to a web site or provide info on the latest round of tariffs with china? How bad is it going to be? I missed the AEE webinar Thanks in advance Jay Peltz power ___ List sponsored by Home Power magazine List Address: RE-wrenches

Re: [RE-wrenches] 2014 NEC

2014-05-27 Thread Jay Peltz
Hi nick Good to know, I was told this by bill brooks at a training a few months ago. Jay Sent from my iPhone On May 27, 2014, at 9:00 AM, Nick Soleil nsol...@enphaseenergy.com wrote: Hi Jay, It is not acceptable to wire the AFCI breaker with the utility power on the output

Re: [RE-wrenches] Fwd: Halliburton science says solar PV can drain the sun's energy!

2014-05-24 Thread jay peltz
Wow, I thought I've seen it all. Amazing. jay On May 24, 2014, at 4:20 PM, Drake wrote: http://nationalreport.net/solar-panels-drain-suns-energy-experts-say/ „Put into laymen‚s terms, the solar panels capture the sun‚s energy, but pull on the sun over time, forcing more energy

Re: [RE-wrenches] 2014 NEC

2014-05-20 Thread jay peltz
HI Will, You can do this. Take a standard breaker panel, install a Arc fault and run the wiring from the enphase like it is the grid: ie into the main lugs. Then this will go out through the breaker in the correct fashion, and onto the main panel. jay peltz power PS as to the code

[RE-wrenches] Sunfix racking

2014-05-16 Thread jay peltz
is, who really makes sunfix racking? thanks Jay Peltz power ___ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Change email address settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

Re: [RE-wrenches] Solarups by Trace

2014-05-12 Thread jay peltz
Photron is correct. jay peltz power On May 12, 2014, at 2:08 PM, Kirk wrote: I believe the control box was made by a company called Photron or Photon. They made lots of pv and inverter accessories. I may have a manual. None of their stuff was UL. Kirk Herander VSE On May 12, 2014

Re: [RE-wrenches] XW 6048 3 HP pump

2014-05-11 Thread jay peltz
Hi Mac, As no one has chimed in I will. Depending on what else you are using,battery size, SOC, pump condition etc, it may work. But my guess is that it'll be a stretch, thats a super huge hit, Whats the LRA? If it was my system, I'd be looking to replace the pump jay peltz power

Re: [RE-wrenches] Article 690, or The Haves Vs. Have Nots

2014-04-30 Thread jay peltz
Hi Jason, Always good to get a different view on how to do it. I've always found it easier and cheaper to pull the circuits off the roof to the AC combiner, so my overcurrent is in a different location Jay Peltz power On Apr 30, 2014, at 5:08 AM, Jason Szumlanski ja...@fafcosolar.com

Re: [RE-wrenches] Flexible stranded Connectors

2014-04-30 Thread jay peltz
with arctic ultra flex wire with ferrules) Jay Peltz power On Apr 29, 2014, at 10:48 PM, Ray Walters r...@solarray.com wrote: Hi All; In order to avoid any of my work showing up in someone's slideshow of horrors, I'm trying to find the correct way to wire 3 Sunny Islands with Cobra X flex

Re: [RE-wrenches] Article 690, or The Haves Vs. Have Nots

2014-04-30 Thread jay peltz
Yep they make them http://w3.usa.siemens.com/powerdistribution/us/en/product-portfolio/meter-load-center/Documents/SIE_BR_SOLAR.pdf Jay On Apr 30, 2014, at 6:56 AM, Jason Szumlanski ja...@fafcosolar.com wrote: Yeah, #10 wire is pretty cheap, especially when purchased in bulk

Re: [RE-wrenches] high efficiency modules in U.S.

2014-04-29 Thread jay peltz
Dan, Are they assembling or actually making cells as well? jay peltz power On Apr 28, 2014, at 8:52 PM, Exeltech wrote: There's also 1Soltech Dallas, Texas. Made in the USA. (Confirmed. I visited their plant on a field trip with a solar energy club not long ago and saw their production

Re: [RE-wrenches] Article 690, or The Haves Vs. Have Nots

2014-04-29 Thread jay peltz
Follow up to Bill's point. For Micros I've installed a disconnect on the roof, but never a breaker or fuse Why install a breaker? jay peltz power On Apr 29, 2014, at 9:43 AM, Bill Hoffer wrote: Dave I agree, in the case of microinverters, you already have a main PV System disconnect

Re: [RE-wrenches] Nano cleaning and sealing products.

2014-04-21 Thread jay peltz
HI James I can't speak to this product, but they use such things in the middle east to keep the dust off the windows on high rise buildings. jay peltz power On Apr 21, 2014, at 1:48 PM, James Rudolph wrote: Aloha Wrenches, Now that one in ten houses have a solar system here in Oahu

Re: [RE-wrenches] Uni-Solar, Kaneka.now Panasonic?

2014-03-14 Thread jay peltz
Hi Guys, I like to use what Photon is doing with real world production values. jay peltz power On Mar 14, 2014, at 9:50 AM, August Goers wrote: Hi Larry, It sounds like you are talking about the temperature coefficient or energy yield per kW-peak? Uni-Solar was great on paper but I'm

[RE-wrenches] Lithium ion

2014-02-26 Thread Jay Peltz
Does anyone know of a distributor of lithium ion for re systems And recommended brands Thanks Jay Jay @asis.com ___ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Change email address settings: http

[RE-wrenches] financial modeling

2014-02-21 Thread jay peltz
Hi all, In reading the article on SunEdison's new IPO, I was wondering if anyone has the break down on how they are generating a yield of $.74 watt? of course its too early to understand how they are going to up that to $1.94 watt jay peltz power

Re: [RE-wrenches] Trojan IND9-6V settings with Outback FX and Flexmax 60

2014-02-20 Thread jay peltz
are in their IND product literature. jay peltz power On Feb 19, 2014, at 2:28 PM, Larry Crutcher, Starlight Solar Power Systems wrote: Hi Chris, Moving from VRLA to flooded, the customer should know it takes about 20% more energy and longer charge time to get to 100% SoC. Trojan

Re: [RE-wrenches] controllers

2014-02-20 Thread jay peltz
Have you looked at the new controller from Midnite, the KID, 30 amp. jay On Feb 20, 2014, at 3:49 PM, RM You wrote: Anybody have any recommendations for a 45a MPPT controller other than Morningstar? I’ve had absolutely miserable tech support from Morningstar so I want to drop the line but I

Re: [RE-wrenches] Trojan IND9-6V settings with Outback FX and Flexmax 60

2014-02-20 Thread jay peltz
HI Larry, Yep totally confusing about their overview information, and they are working on it to get it more clear. The specific spec sheets are accurate though. jay On Feb 20, 2014, at 3:49 PM, Larry Crutcher, Starlight Solar Power Systems wrote: Hey Jay, What do you have

[RE-wrenches] schott info

2014-02-13 Thread jay peltz
HI All, Anybody have contact info for Schott modules warranty? Please contact me off list thanks, jay j...@asis.com ___ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Change email address settings: http

Re: [RE-wrenches] Sunny Island battery OCP

2014-02-11 Thread jay peltz
HI William, I agree with your choices below, but Im curious why you decided against the midnite Epanel for the SI? thanks jay peltz power On Feb 10, 2014, at 9:33 PM, will...@millersolar.com wrote: Friends: Thanks for all of the replies. Here is what I have learned so far 1

Re: [RE-wrenches] Outback Chargers

2014-02-11 Thread jay peltz
try to run the inverters such that you can test to see how they are each working. For the quad stack, try 2 at full tilt, then the other 2 and see if you can find something there, might take some rewiring to test all combos. For the tri stack, well you get the drift. jay peltz power On Feb 10

Re: [RE-wrenches] Charging a HUP

2014-02-09 Thread jay peltz
Hi guys, The HUP manual specifies minimum charge rate of 136 amps, max at 272, jay peltz power On Feb 9, 2014, at 1:38 AM, RE Ellison wrote: Sounds like there is a need for a bigger generator, my gut tells me there is almost enough (but not quite), with 12kw to almost max the chargers

Re: [RE-wrenches] Charging a HUP

2014-02-09 Thread jay peltz
Hi Bob, While I did see on this list earlier about batteries preferring to charge slowly, some manufactures feel very differently. In my experience the industrial type require a C10ish minimum charge rate, some higher even. The info was on the HUP website jay peltz power On Feb 9, 2014

Re: [RE-wrenches] generator stumpage

2014-02-07 Thread jay peltz
Hi Todd While I can't help on the genny side The radian has always had genny support and the new magnum RE version does as well Jay Peltz Power On Feb 6, 2014, at 8:15 PM, toddc...@finestplanet.com wrote: hey wrenches, im working on a design for an offgrid camp and am stumped at my

Re: [RE-wrenches] Static shock

2014-01-25 Thread jay peltz
HI All, Thanks for the insights and the confirmation. I've just never seen it before. jay peltz power On Jan 25, 2014, at 9:21 AM, Ray Walters wrote: I've heard that the entire array can build a surface static charge, though I don't recall getting zapped by the array. Seems

[RE-wrenches] Static shock

2014-01-24 Thread jay peltz
a rain forest and never moved. Thoughts? Thanks Jay Peltz power ___ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Change email address settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re

Re: [RE-wrenches] Very small PV systems for surveillance or other micro loads

2014-01-21 Thread jay peltz
HI Jason, My only thing to add is the smaller the system the more care I take in design. And on most of my systems I install a KwH meter. Makes it very easy to see what they really use a month etc. Good luck, jay peltz power On Jan 21, 2014, at 11:14 AM, Jason Szumlanski wrote: I'm well

Re: [RE-wrenches] Utility refuses to upgrade transformer to accommodate photovoltaic system

2014-01-16 Thread jay peltz
Hi Jason Out of curiosity how big is this PV system? Good luck and keep us informed. Jay Peltz power On Jan 16, 2014, at 12:45 PM, b...@midnitesolar.com b...@midnitesolar.com wrote: I wonder if anybody at the FSEC might have some good advice here ? Just a wild guess... boB

Re: [RE-wrenches] interchangeability of battery temp sensors

2014-01-15 Thread Jay Peltz
Hi Mac Outback and midnight are compatible but not with xantrex Jay Peltz power Sent from my iPhone On Jan 15, 2014, at 8:47 AM, Mac Lewis maclew...@gmail.com wrote: Hello wrenches, Does anyone know if the older xantrex bts/15 temp sensor is the interchangeable with the Outback RTS

Re: [RE-wrenches] Flickering LED lights on and Outback Dual 7248VFX system

2014-01-07 Thread jay peltz
the chargers off line, As to bulbs, I've been super happy with the Cree ones from Home Depot. $10 ish and beautiful light both warm and daylight. Jay Peltz power ___ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re

Re: [RE-wrenches] Flickering LED lights on and Outback Dual 7248 VFX system

2014-01-06 Thread Jay Peltz
Hi Kirpal Are the lights on dimmers? Jay Peltz power Sent from my iPhone On Jan 6, 2014, at 1:09 PM, Kirpal Khalsa solarwo...@gmail.com wrote: Hi All.have a puzzling problemcustomer has a fully LED lit house. All LED lights are flickering when the fridge compressor, tile saw

Re: [RE-wrenches] Flickering LED lights on and Outback Dual 7248 VFX system

2014-01-06 Thread Jay Peltz
Dimmers are super specific to light brand/type. You'll have to do the research For now swapping to regular switches should work Jay ___ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Change email address

Re: [RE-wrenches] Electric fence, metal buildings, lightning protection systems

2013-12-06 Thread jay peltz
Hi Erika, What seems to be the issue? And what equipment ( inverters ) are you using Jay Peltz power On Dec 6, 2013, at 5:57 AM, Erika Weliczko er...@repowersolutions.com wrote: Anyone had to contend with electric fence installation (AC controller) using a ground rod (not main

Re: [RE-wrenches] PV Wiring methods

2013-11-19 Thread jay peltz
Hi August, I can only assume that the inspectors are talking about say running a return leg which would have no pair back to the combiner/junction box? jay peltz power On Nov 19, 2013, at 9:38 AM, August Goers wrote: Hi All – On a related note, I’ve become good friends with some

Re: [RE-wrenches] PV Wiring methods

2013-11-14 Thread jay peltz
Hi Bill, I get mine from PV-cables Less expensive and no minimum order Cheers, jay peltz power On Nov 14, 2013, at 6:21 PM, Bill Hoffer wrote: Jason I just started using Nine Fasteners, Inc www.ninefasteners.com . 410 stainless wire management clips. Got turned on to them at SPI

Re: [RE-wrenches] To stack or not to stack? Off-grid 240V

2013-10-30 Thread jay peltz
generator. One option is to swap the motor for a 3 phase and then get a 240 single phase to 3 phase motor speed controller. This will allow a soft start, very cool stuff. let us know what you do, jay peltz power On Oct 29, 2013, at 7:47 PM, Hilton Dier III wrote: Hello Wrenches, I have an off