Re: [RE-wrenches] Sol-Ark 15K AC Output

2024-03-27 Thread Jason Szumlanski via RE-wrenches
; can really add up. > > > > With either interlock option, the inverter combining, the interlocked > bypass and output breakers all fit into one load center. > > > > I hope the time we spent on this discussion helps someone out there. > That’s why we do it. > >

Re: [RE-wrenches] Sol-Ark 15K AC Output

2024-03-27 Thread William Miller via RE-wrenches
Solar 17395 Oak Road, Atascadero, CA 93422 805-438-5600 www.millersolar.com CA Lic. 773985 *From:* Jason Szumlanski [mailto:ja...@floridasolardesigngroup.com] *Sent:* Wednesday, March 27, 2024 3:52 PM *To:* Kirk Herander *Cc:* William Miller; RE-wrenches *Subject:* Re: [RE-wrenches] Sol-Ark 15K

Re: [RE-wrenches] Sol-Ark 15K AC Output

2024-03-27 Thread Jason Szumlanski via RE-wrenches
ining, the interlocked >> bypass and output breakers all fit into one load center. >> >> >> >> I hope the time we spent on this discussion helps someone out there. >> That’s why we do it. >> >> >> >> Wm >> >> >> >> M

Re: [RE-wrenches] Sol-Ark 15K AC Output

2024-03-27 Thread Kirk Herander via RE-wrenches
eone out there. > That’s why we do it. > > > > Wm > > > > Miller Solar > > 17395 Oak Road, Atascadero, CA 93422 > > 805-438-5600 > > www.millersolar.com > > CA Lic. 773985 > > > > > > *From:* Kirk Herander [mai

Re: [RE-wrenches] Sol-Ark 15K AC Output

2024-03-27 Thread William Miller via RE-wrenches
*Subject:* Re: [RE-wrenches] Sol-Ark 15K AC Output www.interlockkit.com - they stock and custom make interlock bypasses including multiple breakers. Square D also makes a 400 A panel which excepts either bolt on or snap on QO breakers. *Kirk Herander / **kirkh@vermont.solar * *Owner

Re: [RE-wrenches] Sol-Ark 15K AC Output

2024-03-27 Thread Kirk Herander via RE-wrenches
, Atascadero, CA 93422 > > 805-438-5600 > > www.millersolar.com > > CA Lic. 773985 > > > > > > *From:* Jason Szumlanski [mailto:ja...@floridasolardesigngroup.com] > *Sent:* Wednesday, March 27, 2024 3:12 AM > *To:* will...@millersolar.com > *Cc:* RE-wrenches

Re: [RE-wrenches] Sol-Ark 15K AC Output

2024-03-27 Thread William Miller via RE-wrenches
*Subject:* Re: [RE-wrenches] Sol-Ark 15K AC Output William, Thanks for the information on grid peak shaving. That is what I thought could be done. The description is a misnomer of sorts (like a lot of things in Sol-Ark lingo). It's a bit hard to follow and not nearly well enough documented

Re: [RE-wrenches] Sol-Ark 15K AC Output

2024-03-27 Thread Jason Szumlanski via RE-wrenches
on how to provide bypass.  I tried to depict the > > > bypass interlock graphically.  The point is you cannot turn on the bypass > > > breaker without turning off the inverter output breakers.  See photos of > > > the actual hardware on the web page linked below.  I find

Re: [RE-wrenches] Sol-Ark 15K AC Output

2024-03-27 Thread Chris Sparadeo via RE-wrenches
elow. I find bypass >> very handy because if there is an inverter or battery failure the client >> can restore power immediately and I can respond at a more convenient time. >> >> >> >> >> >> >> >> >> >> Wm >> >&g

Re: [RE-wrenches] Sol-Ark 15K AC Output

2024-03-27 Thread Michael Morningstar via RE-wrenches
very handy because if there is an inverter or battery failure the client >> can restore power immediately and I can respond at a more convenient time. >> >> >> >> >> >> >> >> >> >> Wm >> >> >> >> Miller

Re: [RE-wrenches] Sol-Ark 15K AC Output

2024-03-26 Thread Jerry Shafer via RE-wrenches
Wrenches, Jason I have always either with outback and with solark have always connected each unit with a distribution panel with breakers regardless of what's in the inverter package. This same goes for the gen set connections with proper breakers so not to have to over size the wires. I have

Re: [RE-wrenches] Sol-Ark 15K AC Output

2024-03-26 Thread Jason Szumlanski via RE-wrenches
#4 wire as the output of each inverter is definitely not adequate, as each inverter can pass through 150A of generator power. In theory it would be spit across all four, but that doesn't matter. It's an open spigot, so at a minimum the output conductors would need to be 150A rated in my opinion.

Re: [RE-wrenches] Sol-Ark 15K AC Output

2024-03-26 Thread Jason Szumlanski via RE-wrenches
Hi Dave, XW inverters do a decent job of explaining generator support mode where small generators can be supplemented by inverter power to start up large loads. I believe several other brands can do this, and I believe Sol-Ark is one of them. But front line customer service wasn't really up to

Re: [RE-wrenches] Sol-Ark 15K AC Output

2024-03-26 Thread William Miller via RE-wrenches
Jason: I am wondering on the advisability of hardwiring the outputs of all four inverters together. If one inverter fails the other three can backfeed into it without any means to disconnect the failed inverter and without over-current protection. Have you considered landing the output of

Re: [RE-wrenches] Sol-Ark 15K AC Output

2024-03-26 Thread Dave Tedeyan via RE-wrenches
I may be wrong, but I was under the impression that most inverter/chargers are either being an inverter or a charger at any given time, but not both. So, once the inverter sees the AC voltage from the generator, then it will switch to being a charger and use the generator AC power to charge the

Re: [RE-wrenches] Sol-Ark 15k Conduit Entries

2023-08-05 Thread Max Balchowsky via RE-wrenches
i like using gutters, it keeps it clean you can just as easily put the gutter vertical on the side and use close nipples….. Max Balchowsky SEE Systems On Wed, Aug 2, 2023 at 8:04 AM Jason Szumlanski via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > I see a lot of pictures with

Re: [RE-wrenches] Sol-Ark 15k Conduit Entries

2023-08-04 Thread Michael Morningstar via RE-wrenches
I just checked out the Homegrid batteries. Just throwing this out there. If there is enough ceiling height you could hang them. That's typically how we deal with transformers in commercial and industrial settings. We usually build a permanent gantry out of square tubing, 1/2" rod and strut. Then

Re: [RE-wrenches] Sol-Ark 15k Conduit Entries

2023-08-04 Thread Dave Angelini Offgrid Solar via RE-wrenches
Very nice Install Michael! Was that the project on the xxCloud River we talked about? It looks like you have kept the gutter heat gain down to protect electronics. "the rule of thumb is that every 10°C increase in temperature reduces component life by half"

Re: [RE-wrenches] Sol-Ark 15k Conduit Entries

2023-08-04 Thread Jason Szumlanski via RE-wrenches
Michael, I think your work looks stellar, and I seriously doubt there would be any airflow issues. I plan to use strut to put the inverters out from the wall to deal with the working depth issue, which should also help with airflow. That was part of my thought process - even if the inverters

Re: [RE-wrenches] Sol-Ark 15k Conduit Entries

2023-08-04 Thread Michael Morningstar via RE-wrenches
We handle the 15Ks much like most vfds since both have cooling vents in the rear and knockouts or wiring compartments in the rear. What we do is set the units back so that the rear portion is hanging off of the rear of the gutter. The gutter in this case is held off of the wall for air flow. It

Re: [RE-wrenches] Sol-Ark 15k Conduit Entries

2023-08-04 Thread Jason Szumlanski via RE-wrenches
Thanks, Lou. I missed that 6" bottom spacing requirement in the manual. That could explain a lot of the installation pictures I have seen. On the flip side, we have seen some examples of installations in this thread without this 6-inch spacing, presumably without any adverse effects. Obviously,

Re: [RE-wrenches] Sol-Ark 15k Conduit Entries

2023-08-03 Thread Lou Russo via RE-wrenches
Hello All, Super impressive install, Michael. Almost worth a flight, and a site visit! Back to Jason's initial question If you are using the 15kW Outdoor Sol-Ark they vent from the top and bottom with a required 6" minimum spacing on both the top and bottom. A 12kW Outdoor with 8x8 gutter

Re: [RE-wrenches] Sol-Ark 15k Conduit Entries

2023-08-02 Thread Jerry Shafer via RE-wrenches
Jason In plenty of applications l will use couplers with chase nipples, height is one issue but installed working height is very important. I use a 8"x8"x X gutter and sometimes even off set that from the wall, l have had AHJ not want to see mixed cables LVDC and AC in the same conduit so pass

Re: [RE-wrenches] Sol-Ark 15k Conduit Entries

2023-08-02 Thread Maverick Brown via RE-wrenches
Jason The old Sol-Ark had the PV disconnect and the Wi-Fi adapter connection on the bottom and that needed about six or 8 inches of clearance. The current Sol-Ark has those items on the side of the unit so you don’t need such clearance on the bottom. I installed several Sol-Ark and I use the

Re: [RE-wrenches] Sol-Ark 15k

2022-05-10 Thread Jerry Shafer via RE-wrenches
Just so it is abundantly clear to all that wish to modify or cut open an inverter, SMA will not do any advanced replacements of any inverters that have been modified, Outback is not a problem as they are field serviceable, SolArk is a all in one unit and any modification to the cabinet will

Re: [RE-wrenches] Sol-Ark 15k

2022-05-09 Thread Jason Szumlanski via RE-wrenches
I think the idea here is that 690.9 allows the inverter output conductors to be sized based on the maximum ampacity and an OCPD is actually not required is the conductor ampacity is sufficient. So in an off-grid scenario, the wires could be as small as #4. In a grid interconnected situation where

Re: [RE-wrenches] Sol-Ark 15k

2022-05-09 Thread Jerry Shafer via RE-wrenches
Wrenches The new solark 15 has a 200 amp rated contactor this is so if you want to have whole home pass through you can but if you only have an inverter then use that as your starting point and if the genny is contributing then add that is, you do not need 2/0 for a single 15 k off grid but you

Re: [RE-wrenches] Sol-Ark 15k

2022-05-08 Thread Jeff Clearwater via RE-wrenches
I've been using two gutters with multiple 12KW Sol-Arks Installs - one 4x4" that I mount immediately under the AC KOs using forward biased offset nipples (it's front face is just abouut 1/2" in front of front plane of Sol-Arks)  and then a 6x6" set back and down and reached with 4" nipples

Re: [RE-wrenches] Sol-Ark 15k

2022-05-08 Thread Jerry Shafer via RE-wrenches
Be carefull about modifying inverters or any cabinets with long term warranties because modifying may result in sending your unit for repair and not getting exchange units in the event of a warranty issue. Outback is served in parts so that may not be an issue, solark is too soon to tell. Fronius

Re: [RE-wrenches] Sol-Ark 15k

2022-05-08 Thread Michael Morningstar via RE-wrenches
We cut out the bottom plate entirely with a die grinder/cut off wheel and then wrap the raw edge with vinyl "edge wrap" and set the inverters on top of 10 x 10 x whatever gutters. The layout and sizes of Sol-Arks knock-outs is screwy. Just need a bonding jumper between both enclosures. This is

Re: [RE-wrenches] Sol-Ark 15k

2022-05-08 Thread Jay via RE-wrenches
Hi Chris, Can’t you increase the size of the KO’s? Jay > On May 7, 2022, at 7:17 PM, Chris Sparadeo via RE-wrenches > wrote: > >  > Jason, > > I think I agree with your interpretation of the wiring diagram. My hesitation > is, with a 1-1/4” KO for AC inputs, only choice seems to be a >24”

Re: [RE-wrenches] Sol-Ark 15k

2022-05-07 Thread Chris Sparadeo via RE-wrenches
Jason, I think I agree with your interpretation of the wiring diagram. My hesitation is, with a 1-1/4” KO for AC inputs, only choice seems to be a >24” stub conduit for 2/0 conductores to a fused disconnect. Not a fun pipe to bend…and extra BOS seems like a less than ideal solution. Is this your

Re: [RE-wrenches] Sol-Ark 15k

2022-04-17 Thread Darryl Thayer via RE-wrenches
Yes and no, I think this is a tap, "a tap shall be permitted anywhere along a feeder" ' as long as it is less than a 10-foot rule or 25-foot rule ending in a listed OCPD with a rating sufficient to handle the maximum overcurrent'. Service equipment residential is rated for fault currents of up

Re: [RE-wrenches] Sol-Ark 15k

2022-04-17 Thread Jason Szumlanski via RE-wrenches
But this isn't a tap. It's a feeder conductor connected to an OCPD. I guess if you don't have a grid in or generator in or AC Coupled PV, you could just call it an inverter output circuit and it could be sized accordingly. But it would still need to be protected at it's source by an appropriately

Re: [RE-wrenches] Sol-Ark 15k

2022-04-17 Thread Darryl Thayer via RE-wrenches
The tap rule says you can reduce to 10% of the nominal size for 10 feet and protect at the downstream OCPD or 25% for 25 feet for solar with multiple sources see 705 On Sat, Apr 16, 2022 at 9:16 PM Jason Szumlanski via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > That's what I'm

Re: [RE-wrenches] Sol-Ark 15k

2022-04-16 Thread Jason Szumlanski via RE-wrenches
That's what I'm thinking. You would need to use a 200A conductor to a separate load out OCPD before downsizing the wire. I guess there are pros and cons, but it seems this is geared toward whole house backup for 200A services. I'm eager to get an opportunity to use it in that scenario. Jason

Re: [RE-wrenches] Sol-Ark 15k

2022-04-16 Thread Chris Sparadeo via RE-wrenches
Jason, Any additional OCPD downstream of the 200A load output breaker could allow for a smaller wire size to be used at these terminals. For example, load output conductors run to a 100A main breaker panel board. Obviously depending on circumstances, a #4 copper could fit the bill. What I’m not

Re: [RE-wrenches] Sol-Ark 15k

2022-04-16 Thread Darryl Thayer via RE-wrenches
Hello, The overcurrent device is to protect the conductors. you can put any size wire, but you must protect with the overcurrent device. REmember in solar equipment; you may have more than one supply source. The DC best example is solar modules connected in parallel, on On Fri, Apr 15,

Re: [RE-wrenches] Sol-Ark 15k

2022-04-15 Thread Jason Szumlanski via RE-wrenches
That's a different scenario, as a 100A genny would have a 100A OCPD. I understand that the inverter output rating is limited, but what section of code allows a 200A breaker to protect a #4 wire? On Fri, Apr 15, 2022 at 9:26 PM Jerry Shafer via RE-wrenches <

Re: [RE-wrenches] Sol-Ark 15k

2022-04-15 Thread Jerry Shafer via RE-wrenches
You must meet all expected source output potentials within the design and operating limits, as long as the distribution panel and connected wiring is rated for the max output of the protected source then you are good. A 200 ATS connected to a 10 kW genny does not require 2/0 as it will never meet

Re: [RE-wrenches] Sol-Ark 15k

2022-04-15 Thread Chris Sparadeo via RE-wrenches
Hi Jason, You bring up a valid point….in an off-grid scenario with the 15k do you size the conductors to the continuous capacity, surge capacity or the OCPD of the unit? -Chris On Fri, Apr 15, 2022 at 4:01 PM Jason Szumlanski via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > P.S.

Re: [RE-wrenches] Sol-Ark 15k

2022-04-15 Thread Jason Szumlanski via RE-wrenches
P.S. ICYMI, this inverter has a massive combined AC coupled and DC coupled capacity. They allow 15kWdc plus 19.2kWac!!! Impressive. On Fri, Apr 15, 2022 at 10:59 AM Jason Szumlanski < ja...@floridasolardesigngroup.com> wrote: > I'm not following the wiring diagrams for this new inverter. It