RE: 13D UG flush

2022-03-03 Thread Steele, Andrew via Sprinklerforum
Yes, but... NFPA #24 (Underground Fire Mains), within the scope paragraph, excludes 13R and 13D systems. Andrew Steele -Original Message- From: Sprinklerforum On Behalf Of Matt Grise via Sprinklerforum Sent: Thursday, March 3, 2022 10:24 AM To: sprinklerforum@lists.firesprinkler.org

Re: Food trucks inside a building

2022-01-14 Thread Steele, Andrew via Sprinklerforum
Big concerns; frying and grilling "inside" will require type I hoods and suppression systems, and no propane cylinders inside structures. I don't foresee this being viable. Sincerely, Andrew Steele (Fire Inspector in Ohio) On Jan 13, 2022 10:08, Ed Kramer via Sprinklerforum wrote: I'm

Re: Distilled Spirits

2021-02-03 Thread Steele, Andrew via Sprinklerforum
Sorry, should have also said verify its flash and boiling points, then classify into the appropriate flammable liquid class. But also will need to know container type and storage configuration. On Feb 3, 2021 13:21, "Trillium Fire Sprinkler Design Inc. via Sprinklerforum" wrote: Can anyone

Re: Distilled Spirits

2021-02-03 Thread Steele, Andrew via Sprinklerforum
Look at the model IFC, it now has a distilled spirits section, which will likely be incorporated into state and local fire codes over the next code adoption cycles. On Feb 3, 2021 13:21, "Trillium Fire Sprinkler Design Inc. via Sprinklerforum" wrote: Can anyone direct me to design criteria

RE: Antifreeze Rp issue

2020-07-21 Thread Steele, Andrew via Sprinklerforum
Similar, I'm aware of an antifreeze system that twice split open the expansion tank(s). The first two expansion tanks were generic expansion tanks not listed for antifreeze service. The third (listed/approved) tank has been on for eight or ten years now, with no issues. Don't underestimate

RE: mattress storage

2020-06-04 Thread Steele, Andrew via Sprinklerforum
Also consider looking at the applicable fire code. If the ICC fire code, then this might be a high-piled combustible storage situation beginning at six feet (see high-piled storage definition in ICC Fire Code Chapter 2, and then Chapter 32). Pillows and mattress are in section 3203.6, further

RE: Curbs for Containment (from IFC and NFPA #30)

2020-04-09 Thread Steele, Andrew via Sprinklerforum
IFC Section 5004.2.2.3 (and also similar language in NFPA #30) Secondary containment for indoor storage areas shall be designed to contain a spill from the largest vessel plus the design flow volume of fire protection water calculated to discharge from the fire-extinguishing system over the

RE: Flammable liquid tanks in a garage

2020-02-26 Thread Steele, Andrew via Sprinklerforum
My thoughts - cooking oil is a class IIIB combustible liquid; the model building codes would limit to not more than 13,200 gallons before changing to an H use group. If the containers are metal, then no issue. If they are plastic (prohibited for class I flammables and class II and IIIA

RE: IBC "throughout"

2020-01-30 Thread Steele, Andrew via Sprinklerforum
Yes, the commentary for sections 903.1 and 903.3.1.1.1 of the IBC explains. I strongly recommend both the IIC Building and Fire Code commentary books - a lot of usefully information, along with the actual code language. Andrew Steele From: Sprinklerforum

RE: Vehicular Sallyport classification

2019-08-05 Thread Steele, Andrew
Not a location to skimp on protection. The vehicles (cruisers) are often run hard, and not without higher maintenance/fire risk. If there is a second floor above the salleyport, then I would certainly go with the engineers spec; that and the fact that cars are no longer “metal”, with metal

RE: fire hydrant

2019-05-20 Thread Steele, Andrew
Ask the AHJ. If explosives, then other NFPA standards, more specific, are likely to apply. If 40-ft stands, then it's possible to consider that the fire hydrant might be used for maintenance flushing/testing of the water service, and/or as a supply to a fire apparatus taking a position

RE: NFPA 22 help - For Fire Flow, check ICC Fire Code

2019-03-13 Thread Steele, Andrew
If you are looking for a guide for fire flow demands, not associated with any one fire sprinkler system, then look at ICC Fire Code section 507 "Fire Protection Water Supplies" and ICC Fire Code Appendix "B", Fire-Flow Requirements for Buildings. These will assist with total fire flow in

underground valves

2018-12-03 Thread Steele, Andrew
If the state or jurisdiction has adopted NFPA #24, then section 6.6 covers valves. * Sprinkler “riser” supply - See NFPA #24 Section 6.2.11 for valve requirements for each of the fire sprinkler system supplies. The typical valve is a PIV, but other arrangements are also permitted. *

RE: Improving the process

2018-09-28 Thread Steele, Andrew
I would suggest that the best way forward for universal application would be for AFSA (or anyone) to submit code change proposal for the ICC Building Code. The proposal would be to add a specific code requirement for the Owner Certificate. This would fit nicely into ICC Building Code section

Re: Sprinkler heads popping off randomly

2018-09-13 Thread Steele, Andrew
A couple of thoughts: - Any heat producing machinery, (shrink wrap station for example), skylight or steam pipe in proximity to a sprinkler LINE? - Is there a pressure relief device anywhere on the system? (My guess, you are slowly building up system pressure in excess of head test pressure,

RE: Hose Connections - Main Stair Landings vs. Intermediate Landings

2018-09-11 Thread Steele, Andrew
It sort of matters; think firefighters flaking out no less than 100-feet of hose (maybe more) in the stairwell before charging the hose line with standpipe water. This has to be laid neatly so it does tangle and kink on charging. Typically the FD will hook to the first outlet BELOW the level

RE: Building Heights Requiring Standpipes

2018-08-08 Thread Steele, Andrew
Good example diagrams are in the ICC Fire /Bldg Code Commentary books. On Aug 8, 2018 18:01, Jim Davidson wrote: Go to the Building Code for the definition of height above lowest level of FD Access, if ICC's IBC then call for a code interpretation and if needed ask for a written response. The

RE: High Rise and Non-High Rise Standpipes

2018-06-29 Thread Steele, Andrew
First thought, is it really ONE building, or three (or two, etc. based on firewalls). This is a question for the Architect and/or the Building Official, not the FM. The FM may not know, particularly if they were not involved in the structural review/permitting process. Or they may know, and

RE: 300 ft. rule for flow tests

2018-03-01 Thread Steele, Andrew
The American Water Works Association Manual of Water Supply Practices has a publication AWWA document M17 "Installation, Field Testing and Maintenance of Fire Hydrants". Chapter 6 is flow testing. It doesn't specify a minimum distance, at least in my 1989 third edition book. This is a

RE: threaded union fitting

2018-02-08 Thread Steele, Andrew
Accessible to view during the 200-lb hydrostatic acceptance testing (YES) (before sofit or wall or ceiling is installed to cover pipe), or accessible permanently (for us, not required). Andrew Steele Dayton OH Fire Dept. – Fire Marshal. From: Sprinklerforum

RE: Lithium Batteries

2017-07-18 Thread Steele, Andrew
See FM Global. Their data-sheets are now free and easy for anyone to access: http://newsroom.fmglobal.com/releases/fm-global-conducts-new-large-scale-fire-tests-on-warehoused-lithium-ion-batteries Andrew Steele Dayton FD From: Sprinklerforum

RE: Pre-action detection options

2017-06-12 Thread Steele, Andrew
Assuming that there is no open flame, reflected flame, or smoke associated with the high ceiling heat conditions, then a camera detection system, positioned in the building to be environmentally protected – but still with a clear view, might work. Fike Signifire is one. Curious as to your

RE: Seeking false water flow alarm suggestions

2016-10-12 Thread Steele, Andrew
as daytime usage increases. This is about a five to eight pound change, sometimes it's enough to cause systems with failed check valves and short flow detection cycles, to alarm. On Oct 12, 2016 8:38 AM, "Steele, Andrew" <andrew.ste...@daytonohio.gov> wrote: Check v

Re: Seeking false water flow alarm suggestions

2016-10-12 Thread Steele, Andrew
the check valve (soldered copper with no unions). I would have > no problem draining the system, opening up the check valve and repairing it, > if it is repairable. What do you suggest? > > > On 10/12/2016 5:38 AM, Steele, Andrew wrote: >> >> Check valve failure, so tha

RE: Seeking false water flow alarm suggestions

2016-10-12 Thread Steele, Andrew
Check valve failure, so that the sprinkler leg is no longer isolated? -Original Message- From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Barry Levine Sent: Wednesday, October 12, 2016 1:01 AM To: sprinklerforum@lists.firesprinkler.org

RE: Apparatus Bays

2016-08-22 Thread Steele, Andrew
Given a choice, OH-2. Interior “shielded” areas within and under the apparatus are significantly larger than regular passenger cars (i.e. bigger fires when they do happen). Risk of fire is also higher, most apparatus have multiple batteries, 110-volt plug in chargers, lots of add-on, non-OEM

RE: Visual Inspection of CPVC System

2016-07-13 Thread Steele, Andrew
Yes. We, as AHJ during system acceptance testing, are finding multiple heads with internal glue obstructions. The heads are (and continue to be on plastic jobs) installed prior to the drop being set into place, with glue subsequently "dripping" down into the head. Photo examples if you want

RE: Hose Valves for Stage (fire department use)

2016-05-09 Thread Steele, Andrew
-Original Message- From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Steele, Andrew Sent: Monday, May 09, 2016 6:09 AM To: 'sprinklerforum@lists.firesprinkler.org' Subject: RE: Hose Valves for Stage (fire department use) >From an operations point of vi

RE: Hose Valves for Stage (fire department use)

2016-05-09 Thread Steele, Andrew
>From an operations point of view, specific to my local fire department, it >would make sense to have the 2-1/2 outlet even when not required. The 1-1/2 outlet with racked hose would be for incipient fire use by the occupants, if they so choose. The 2-1/2 outlet would be used by the responding

RE: NFPA 13 2013 ed bathroom sprinklers

2016-05-03 Thread Steele, Andrew
I would suggest that the thinking for hotel/motel uses only was that temporary stay occupants wouldn't have opportunity to install significant amounts of combustible materials into a bathroom. However home/apartment occupants do. As a Fire Official, I've seen some pretty significant fires

RE: modular offices (trailers) within a building

2016-01-21 Thread Steele, Andrew
If the trailer is "permanently installed" and not moved around, then yes, sprinklers are required. No different than a constructed room with ceiling causing overhead obstruction. If not "permanent", then overhead density needs to be adequate for the trailer. 2013 edition of NFPA #13, see 4.1

RE: PRV on Standpipe Calcs

2015-09-01 Thread Steele, Andrew
What type of nozzles does the local fire department use, and what pressure would they want on the tip? Size and length of the hose line on their standpipe packs? A.Steele -Original Message- From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of

RE: Holding Cells

2015-07-09 Thread Steele, Andrew
This is a common problem, and in my opinion, the occurrences of damage won't go away even with a pre-action system - in fact, it probably would get worse. Furthermore, a pre-action system would only complicate things, increase install and service costs while decreasing the intended level of

RE: Attic Insulation

2015-07-07 Thread Steele, Andrew
Another consideration is wind. We (Dayton, Ohio) have seen several ordinary apt. buildings with wet pipe freeze/breaks at the second floor and third floor levels of three story buildings with full attics, where the pipe was installed in an INTERIOR wall between well heated apartments. Exterior

RE: co2, fm200

2015-05-27 Thread Steele, Andrew
My questions would be: 1) Is this system installed in place of sprinklers, if so, then YES to reserve cylinders. 2) If a fire develops, how much ordinary combustibles are present? Will the fire be not only controlled, but extinguished within 3 to 5 mins of agent release, or is a more deep

RE: Hot box or other types of exterior fire riser enclosures

2015-01-27 Thread Steele, Andrew
Open sided construction creates an exposure problem to firefighters who might need to access control valves, if/during a fully involved active fire. We had a warehouse fully involved (1987 Sherwin Williams), large areas of roof collapse, where the sprinkler mains needed to be shut down to

RE: 6 Story Hotel

2014-07-28 Thread Steele, Andrew
There are some other building code (and possibly even insurance risk assessment) issues that are likely to arise when using a NFPA #13R system; a 13R system IS NOT a fully protected building. For example, ICC Table 508 required separation of occupancies does not recognize 13R systems, so if

RE: Inspector's Test Valve Residual Pressure

2014-07-10 Thread Steele, Andrew
I would suggest running a quick calc showing the theoretical flow/pressure from the inspector's test and the residual pressure at the riser, and how that compares to the system demand. Or think of it this way, the inspectors test flow (via a single 1/2 outlet) should always be less than the

RE: Water Supply Evaluation

2014-06-26 Thread Steele, Andrew
This most likely is from the International Fire Code, Chapter 5, Fire Service Features, (G) Section 507 Fire Protection Water Supplies. Subsection 507.3 says fire flow requirements for building or portions of building and facilities shall be determined by an approved method. In Ohio, this has been

RE: Help Identify this pipe

2014-06-23 Thread Steele, Andrew
Suggestion - try the AHJ/Building Department (open records request) to see if and when originally installed, they permitted the installation, and what, if any, of the original plans and specifications they might still have in their files. Andrew Steele Strategic Programs and Safety Dayton Fire

Three Unexplained Sprinkler Head Activations

2013-03-21 Thread Steele, Andrew
Group, any thoughts or recommendations for unexplained sprinkler head activations? Situation - one story church, built in 1994. Sprinkler installed late spring summer in Dayton, Ohio. City static water pressure is 135-lbs. 200-lb hydro tests at system acceptance. There is a pressure relief

Re: Bedbugs

2013-02-28 Thread Steele, Andrew
We had a 17-story residential high-rise fumigated three or four years ago; the fumigant was toxic to humans, so building had to be sealed/guarded and we (municipal fire department) were apprised and cautioned not to enter without full SCBA, etc. To make this work, they had to temporarily