When there is a will, there is a way. The paddle-type water flow device can be
installed in a small parallel byp[ass run of this suction line with an
appropriate large hole strainer, supervised maintenance valves and all the
trimmings. Engineer it so that it gets enough flow through this
On Aug 5, 2022, at 2:06 PM, Kyle.Montgomery
>>>> wrote:
>>>>
>>>>
>>>> Also not free, but what about utilizing a backflow preventer with a
>>>> detector assembly? Not an additional one, just in lieu of the one that’s
>&
Schumacher
Sent: Friday, August 5, 2022 10:51 AM
To: Discussion list on issues relating to automatic fire sprinklers
Subject: [EXTERNAL] [Sprinklerforum] Re: WFD In Pump Suction Line
Those are often the things that people who make suggestions don’t have to
consider.
Taylor Schumacher ET
2 10:51 AM
>> To: Discussion list on issues relating to automatic fire sprinklers
>>
>> Subject: [EXTERNAL] [Sprinklerforum] Re: WFD In Pump Suction Line
>>
>> Those are often the things that people who make suggestions don’t have to
>> consider.
>>
nklers
mailto:sprinklerforum@lists.firesprinkler.org>>
Subject: [Sprinklerforum] Re: WFD In Pump Suction Line
Are you going to be able to get a change order from the owner to cover this
suggestion from the plan reviewer?
Matt
From: Anthony Carrizosa
mailto:anth...@archerconstruction.com>
Those are often the things that people who make suggestions don’t have to
consider.
Taylor Schumacher ET
From: Matt Grise
Sent: Friday, August 05, 2022 11:56 AM
To: Discussion list on issues relating to automatic fire sprinklers
Subject: [Sprinklerforum] Re: WFD In Pump Suction Line
this forum is!
Taylor Schumacher ET
From: Anthony Carrizosa
Sent: Friday, August 05, 2022 11:54 AM
To: Discussion list on issues relating to automatic fire sprinklers
Subject: [Sprinklerforum] Re: WFD In Pump Suction Line
Taylor
Every time the jockey pump turns on it will ring the bell? Unless
nklers
mailto:sprinklerforum@lists.firesprinkler.org>>
Subject: [Sprinklerforum] Re: WFD In Pump Suction Line
Ding Ding Ding (pun intended) I think we have a winner.
Taylor Schumacher ET
From: Vincent J. Como mailto:vjc...@waynefire.com>>
Sent: Friday, August 05, 2022 10:41 AM
To: Discuss
>
Subject: [Sprinklerforum] Re: WFD In Pump Suction Line
If pressure isn’t the issue…I vote water motor gong
Thanks,
[Proudly Saving Lives since 1978. Wayne Automatic Fire Sprinklers, Inc. Minutes
Matter.]<https://linkprotect.cudasvc.com/url?a=https%3a%2f%2fwww.wayne
Ding Ding Ding (pun intended) I think we have a winner.
Taylor Schumacher ET
From: Vincent J. Como
Sent: Friday, August 05, 2022 10:41 AM
To: Discussion list on issues relating to automatic fire sprinklers
Subject: [Sprinklerforum] Re: WFD In Pump Suction Line
If pressure isn’t the issue
My comments:
The engineer of record or reviewer might be concerned with a supply pipe in
a structure with no means of detecting a break or major leak. A waterflow
switch could provide this piece of mind. However, I would be concerned
about the water velocity limit of the wqte switch which
lariedesign.com/signatures/wayne/images/icon-fb.png]
<https://www.facebook.com/Wayne-Automatic-Fire-Sprinklers-Inc-122998935990/>
From: Taylor Schumacher
Sent: Friday, August 5, 2022 11:32 AM
To: Discussion list on issues relating to automatic fire sprinklers
Subject: [Sprinklerforum] Re: WFD I
Taylor,
prompted by Anthony Carrisoza, I looked in the 2019 Handbook edition of
NFPA 20, and found this item in §4.16.9.2(2):
* /Where the authority having jurisdiction requires positive pressure
to be maintained onthe suction piping, *_a pressure sensing
line_* for a low suction
of licensure.
From: Taylor Schumacher
Sent: Friday, August 5, 2022 9:43 AM
To: Discussion list on issues relating to automatic fire sprinklers
Subject: [Sprinklerforum] Re: WFD In Pump Suction Line
I thought about using the turbulence distances as a good practice. I have over
200 feet of pipe so
Subject: Re: [Sprinklerforum] WFD In Pump Suction Line
Taylor,
After reading your original post, and several of the responses, particularly
that of Chris Dorn, I'm prompted to share my thoughts.
* Is the AHJ looking for supervision of the appropriate suction pressure in
that feed
Taylor,
After reading your original post, and several of the responses,
particularly that of Chris Dorn, I'm prompted to share my thoughts.
* Is the AHJ looking for supervision of the appropriate suction
pressure in that feed to the fire pump? I'm sure you understand
this - however
to automatic fire sprinklers
Subject: [Sprinklerforum] Re: WFD In Pump Suction Line
Independent reviewer representing the city.
Taylor Schumacher ET
From: Matt Grise mailto:m...@afpsprink.com>>
Sent: Friday, August 05, 2022 9:50 AM
To: Discussion list on issues relating to automati
Does he have the authority to require flow switches in excess of code
requirements?
Matt
From: Taylor Schumacher
Sent: Friday, August 05, 2022 9:54 AM
To: Discussion list on issues relating to automatic fire sprinklers
Subject: [Sprinklerforum] Re: WFD In Pump Suction Line
Independent
Taylor
I had a similar issue come up on a job I was working on and I showed the
Engineer the specs on a flow switch, they only detect flow of 10GPM or more. So
not really a leak detector. They only notify on a major flow of water which if
you have more than 10GPM flowing in a garage people will
ts.firesprinkler.org>>
Subject: [Sprinklerforum] Re: WFD In Pump Suction Line
Just out of curiosity - who does this plan reviewer work for? Is it an owner's
rep/engineer/insurance rep or a city code official?
Matt
From: Taylor Schumacher mailto:tay...@sfsprinkler.com>>
Sent: Friday, August 05,
Independent reviewer representing the city.
Taylor Schumacher ET
From: Matt Grise
Sent: Friday, August 05, 2022 9:50 AM
To: Discussion list on issues relating to automatic fire sprinklers
Subject: [Sprinklerforum] Re: WFD In Pump Suction Line
Just out of curiosity - who does this plan
It doesn’t, I’ll look into those options. Thanks for that idea!
Taylor Schumacher ET
From: Chris Dorn
Sent: Friday, August 05, 2022 8:52 AM
To: Discussion list on issues relating to automatic fire sprinklers
Subject: [Sprinklerforum] Re: WFD In Pump Suction Line
Does the panel monitor low
c fire sprinklers
mailto:sprinklerforum@lists.firesprinkler.org>>
Subject: [Sprinklerforum] Re: WFD In Pump Suction Line
I get the concern also - but the request seems to be in direct contradiction to
the code. And it introduces a paddle that could jam in the pipe or detach from
the swi
requirement for that installation.
For what it's worth, the pipe is traveling in a parking garage.
Taylor Schumacher ET
From: Matt Grise
Sent: Friday, August 05, 2022 8:45 AM
To: Discussion list on issues relating to automatic fire sprinklers
Subject: [Sprinklerforum] Re: WFD In Pump Suction
: [Sprinklerforum] Re: WFD In Pump Suction Line
I get the concern also - but the request seems to be in direct contradiction to
the code. And it introduces a paddle that could jam in the pipe or detach from
the switch and flow into the pump.
Many plan reviewers are limited to enforcing codes
: [Sprinklerforum] Re: WFD In Pump Suction Line
Sounds like a really bad idea. Would a pressure gauge give him what he is
looking for?
On Aug 5, 2022 at 9:36 AM, mailto:tay...@sfsprinkler.com>>
wrote:
Does anyone have any experience with a paddle-type water flow detector in the
suctio
I get the concern also - but the request seems to be in direct contradiction to
the code. And it introduces a paddle that could jam in the pipe or detach from
the switch and flow into the pump.
Many plan reviewers are limited to enforcing codes, not enforcing their
personal preferences. Can
I would suggest you might need to provide the size and length of pipe before
the suction flange, the pump size, and the water flow test information for an
appropriate answer.
Scott
Office: (763) 425-1001 x 2
Cell: (612) 759-5556
From: Taylor Schumacher
Sent: Friday, August 5, 2022 8:35 AM
Sounds like a really bad idea. Would a pressure gauge give him what he is
looking for?
>
> On Aug 5, 2022 at 9:36 AM, (mailto:tay...@sfsprinkler.com)> wrote:
>
>
>
>
>
> Does anyone have any experience with a paddle-type water flow detector in the