[Sprinklerforum] Re: WFD In Pump Suction Line

2022-08-06 Thread AKS-Gmail-IMAP
When there is a will, there is a way. The paddle-type water flow device can be installed in a small parallel byp[ass run of this suction line with an appropriate large hole strainer, supervised maintenance valves and all the trimmings. Engineer it so that it gets enough flow through this

[Sprinklerforum] Re: WFD In Pump Suction Line

2022-08-06 Thread Rick Matsuda
On Aug 5, 2022, at 2:06 PM, Kyle.Montgomery >>>> wrote: >>>> >>>>  >>>> Also not free, but what about utilizing a backflow preventer with a >>>> detector assembly? Not an additional one, just in lieu of the one that’s >&

[Sprinklerforum] Re: WFD In Pump Suction Line

2022-08-05 Thread Taylor Schumacher
Schumacher Sent: Friday, August 5, 2022 10:51 AM To: Discussion list on issues relating to automatic fire sprinklers Subject: [EXTERNAL] [Sprinklerforum] Re: WFD In Pump Suction Line Those are often the things that people who make suggestions don’t have to consider. Taylor Schumacher ET

[Sprinklerforum] Re: WFD In Pump Suction Line

2022-08-05 Thread Rick Matsuda
2 10:51 AM >> To: Discussion list on issues relating to automatic fire sprinklers >> >> Subject: [EXTERNAL] [Sprinklerforum] Re: WFD In Pump Suction Line >> >> Those are often the things that people who make suggestions don’t have to >> consider. >>

[Sprinklerforum] Re: WFD In Pump Suction Line

2022-08-05 Thread Taylor Schumacher
nklers mailto:sprinklerforum@lists.firesprinkler.org>> Subject: [Sprinklerforum] Re: WFD In Pump Suction Line Are you going to be able to get a change order from the owner to cover this suggestion from the plan reviewer? Matt From: Anthony Carrizosa mailto:anth...@archerconstruction.com>

[Sprinklerforum] Re: WFD In Pump Suction Line

2022-08-05 Thread Taylor Schumacher
Those are often the things that people who make suggestions don’t have to consider. Taylor Schumacher ET From: Matt Grise Sent: Friday, August 05, 2022 11:56 AM To: Discussion list on issues relating to automatic fire sprinklers Subject: [Sprinklerforum] Re: WFD In Pump Suction Line

[Sprinklerforum] Re: WFD In Pump Suction Line

2022-08-05 Thread Taylor Schumacher
this forum is! Taylor Schumacher ET From: Anthony Carrizosa Sent: Friday, August 05, 2022 11:54 AM To: Discussion list on issues relating to automatic fire sprinklers Subject: [Sprinklerforum] Re: WFD In Pump Suction Line Taylor Every time the jockey pump turns on it will ring the bell? Unless

[Sprinklerforum] Re: WFD In Pump Suction Line

2022-08-05 Thread Matt Grise
nklers mailto:sprinklerforum@lists.firesprinkler.org>> Subject: [Sprinklerforum] Re: WFD In Pump Suction Line Ding Ding Ding (pun intended) I think we have a winner. Taylor Schumacher ET From: Vincent J. Como mailto:vjc...@waynefire.com>> Sent: Friday, August 05, 2022 10:41 AM To: Discuss

[Sprinklerforum] Re: WFD In Pump Suction Line

2022-08-05 Thread Anthony Carrizosa
> Subject: [Sprinklerforum] Re: WFD In Pump Suction Line If pressure isn’t the issue…I vote water motor gong Thanks, [Proudly Saving Lives since 1978. Wayne Automatic Fire Sprinklers, Inc. Minutes Matter.]<https://linkprotect.cudasvc.com/url?a=https%3a%2f%2fwww.wayne

[Sprinklerforum] Re: WFD In Pump Suction Line

2022-08-05 Thread Taylor Schumacher
Ding Ding Ding (pun intended) I think we have a winner. Taylor Schumacher ET From: Vincent J. Como Sent: Friday, August 05, 2022 10:41 AM To: Discussion list on issues relating to automatic fire sprinklers Subject: [Sprinklerforum] Re: WFD In Pump Suction Line If pressure isn’t the issue

[Sprinklerforum] Re: WFD In Pump Suction Line

2022-08-05 Thread John Denhardt
My comments: The engineer of record or reviewer might be concerned with a supply pipe in a structure with no means of detecting a break or major leak. A waterflow switch could provide this piece of mind. However, I would be concerned about the water velocity limit of the wqte switch which

[Sprinklerforum] Re: WFD In Pump Suction Line

2022-08-05 Thread Vincent J. Como
lariedesign.com/signatures/wayne/images/icon-fb.png] <https://www.facebook.com/Wayne-Automatic-Fire-Sprinklers-Inc-122998935990/> From: Taylor Schumacher Sent: Friday, August 5, 2022 11:32 AM To: Discussion list on issues relating to automatic fire sprinklers Subject: [Sprinklerforum] Re: WFD I

[Sprinklerforum] Re: WFD In Pump Suction Line

2022-08-05 Thread Ken Wagoner
Taylor, prompted by Anthony Carrisoza, I looked in the 2019 Handbook edition of NFPA 20, and found this item in §4.16.9.2(2): * /Where the authority having jurisdiction requires positive pressure to be maintained onthe suction piping, *_a pressure sensing line_* for a low suction

[Sprinklerforum] Re: WFD In Pump Suction Line

2022-08-05 Thread David Williams
of licensure. From: Taylor Schumacher Sent: Friday, August 5, 2022 9:43 AM To: Discussion list on issues relating to automatic fire sprinklers Subject: [Sprinklerforum] Re: WFD In Pump Suction Line I thought about using the turbulence distances as a good practice. I have over 200 feet of pipe so

[Sprinklerforum] Re: WFD In Pump Suction Line

2022-08-05 Thread Taylor Schumacher
Subject: Re: [Sprinklerforum] WFD In Pump Suction Line Taylor, After reading your original post, and several of the responses, particularly that of Chris Dorn, I'm prompted to share my thoughts. * Is the AHJ looking for supervision of the appropriate suction pressure in that feed

[Sprinklerforum] Re: WFD In Pump Suction Line

2022-08-05 Thread Ken Wagoner
Taylor, After reading your original post, and several of the responses, particularly that of Chris Dorn, I'm prompted to share my thoughts. * Is the AHJ looking for supervision of the appropriate suction pressure in that feed to the fire pump?  I'm sure you understand this - however

[Sprinklerforum] Re: WFD In Pump Suction Line

2022-08-05 Thread Anthony Carrizosa
to automatic fire sprinklers Subject: [Sprinklerforum] Re: WFD In Pump Suction Line Independent reviewer representing the city. Taylor Schumacher ET From: Matt Grise mailto:m...@afpsprink.com>> Sent: Friday, August 05, 2022 9:50 AM To: Discussion list on issues relating to automati

[Sprinklerforum] Re: WFD In Pump Suction Line

2022-08-05 Thread Matt Grise
Does he have the authority to require flow switches in excess of code requirements? Matt From: Taylor Schumacher Sent: Friday, August 05, 2022 9:54 AM To: Discussion list on issues relating to automatic fire sprinklers Subject: [Sprinklerforum] Re: WFD In Pump Suction Line Independent

[Sprinklerforum] Re: WFD In Pump Suction Line

2022-08-05 Thread Anthony Carrizosa
Taylor I had a similar issue come up on a job I was working on and I showed the Engineer the specs on a flow switch, they only detect flow of 10GPM or more. So not really a leak detector. They only notify on a major flow of water which if you have more than 10GPM flowing in a garage people will

[Sprinklerforum] Re: WFD In Pump Suction Line

2022-08-05 Thread Travis.Mack
ts.firesprinkler.org>> Subject: [Sprinklerforum] Re: WFD In Pump Suction Line Just out of curiosity - who does this plan reviewer work for? Is it an owner's rep/engineer/insurance rep or a city code official? Matt From: Taylor Schumacher mailto:tay...@sfsprinkler.com>> Sent: Friday, August 05,

[Sprinklerforum] Re: WFD In Pump Suction Line

2022-08-05 Thread Taylor Schumacher
Independent reviewer representing the city. Taylor Schumacher ET From: Matt Grise Sent: Friday, August 05, 2022 9:50 AM To: Discussion list on issues relating to automatic fire sprinklers Subject: [Sprinklerforum] Re: WFD In Pump Suction Line Just out of curiosity - who does this plan

[Sprinklerforum] Re: WFD In Pump Suction Line

2022-08-05 Thread Taylor Schumacher
It doesn’t, I’ll look into those options. Thanks for that idea! Taylor Schumacher ET From: Chris Dorn Sent: Friday, August 05, 2022 8:52 AM To: Discussion list on issues relating to automatic fire sprinklers Subject: [Sprinklerforum] Re: WFD In Pump Suction Line Does the panel monitor low

[Sprinklerforum] Re: WFD In Pump Suction Line

2022-08-05 Thread Matt Grise
c fire sprinklers mailto:sprinklerforum@lists.firesprinkler.org>> Subject: [Sprinklerforum] Re: WFD In Pump Suction Line I get the concern also - but the request seems to be in direct contradiction to the code. And it introduces a paddle that could jam in the pipe or detach from the swi

[Sprinklerforum] Re: WFD In Pump Suction Line

2022-08-05 Thread Taylor Schumacher
requirement for that installation. For what it's worth, the pipe is traveling in a parking garage. Taylor Schumacher ET From: Matt Grise Sent: Friday, August 05, 2022 8:45 AM To: Discussion list on issues relating to automatic fire sprinklers Subject: [Sprinklerforum] Re: WFD In Pump Suction

[Sprinklerforum] Re: WFD In Pump Suction Line

2022-08-05 Thread Chris Dorn
: [Sprinklerforum] Re: WFD In Pump Suction Line I get the concern also - but the request seems to be in direct contradiction to the code. And it introduces a paddle that could jam in the pipe or detach from the switch and flow into the pump. Many plan reviewers are limited to enforcing codes

[Sprinklerforum] Re: WFD In Pump Suction Line

2022-08-05 Thread Chris Dorn
: [Sprinklerforum] Re: WFD In Pump Suction Line Sounds like a really bad idea. Would a pressure gauge give him what he is looking for? On Aug 5, 2022 at 9:36 AM, mailto:tay...@sfsprinkler.com>> wrote: Does anyone have any experience with a paddle-type water flow detector in the suctio

[Sprinklerforum] Re: WFD In Pump Suction Line

2022-08-05 Thread Matt Grise
I get the concern also - but the request seems to be in direct contradiction to the code. And it introduces a paddle that could jam in the pipe or detach from the switch and flow into the pump. Many plan reviewers are limited to enforcing codes, not enforcing their personal preferences. Can

[Sprinklerforum] Re: WFD In Pump Suction Line

2022-08-05 Thread Scott Futrell
I would suggest you might need to provide the size and length of pipe before the suction flange, the pump size, and the water flow test information for an appropriate answer. Scott Office: (763) 425-1001 x 2 Cell: (612) 759-5556 From: Taylor Schumacher Sent: Friday, August 5, 2022 8:35 AM

[Sprinklerforum] Re: WFD In Pump Suction Line

2022-08-05 Thread Fpdcdesign
Sounds like a really bad idea. Would a pressure gauge give him what he is looking for? > > On Aug 5, 2022 at 9:36 AM, (mailto:tay...@sfsprinkler.com)> wrote: > > > > > > Does anyone have any experience with a paddle-type water flow detector in the