Dewayne,
Thanks, that's what I was thinking and hoping for was to treat it as
obstructed construction w/low sprinklers. I just wanted to be sure I wasn't
missing anything.
Any other opinions on this?
Bobby Gillett
Project Manager
[EMAIL PROTECTED]
(731) 424-0130 office
(731) 267-4853 cell
In past similair situations here, we have done the individual stores.
The AHJ's have had no problems since the walls are fire rated.
Bobby Gillett
Senior Project Manager
[EMAIL PROTECTED]
(731) 424-0130 office
(731) 267-4853 cell
On Nov 22, 2008, at 10:22 AM, Greg McGahan [EMAIL PROTECTED
,
Merry CHRISTmas to all
Bobby Gillett
Sr.Project Manager
Key Fire Protection, Inc.
bobby.gill...@keyfireprotection.com
(731) 424-0130 office
(731) 424-9285 fax
(731) 267-4853 cell
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun
, then pipe these from your most remote branch line(s).
The orfice would be equivalent to those in your most demanding area, the
pipe size is a min of 1.
Bobby Gillett
Sr.Project Manager
Key Fire Protection, Inc.
bobby.gill...@keyfireprotection.com
(731) 424-0130 office
(731) 424-9285 fax
(731) 267-4853
, and as the
handbook explains 7.3.2.7 it states this is not to provide a pass or fail
situation but to provide documented results to serve as a comparative basis
to identify possible system malfunctions or impairments.
Bobby Gillett
Sr.Project Manager
Key Fire Protection, Inc.
bobby.gill
. with a quick
opening device.
Bobby Gillett
Sr.Project Manager
Key Fire Protection, Inc.
bobby.gill...@keyfireprotection.com
(731) 424-0130 office
(731) 424-9285 fax
(731) 267-4853 cell
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org
for our
plastic piping and have never had it kicked back. Even the straps are
supplied with their own screws from both of the above manuf., this is part
of their listing. If you follow the listing on the pipe and then the strap,
I don't see where you are not in compliance.
Bobby Gillett
Sr.Project
One question, the 6 rod rule (9.3.5.3.8) for lateral would still apply, if
this is the case then you would only need longitudinal on your cross and
feed mains per 2007, correct?
Bobby Gillett
Sr.Project Manager
Key Fire Protection, Inc.
bobby.gill...@keyfireprotection.com
(731) 424-0130 office
To be clearer, the question is asked as if we were using the straps on the
cpvc as previously mentioned and not hanging it.
Bobby Gillett
Sr.Project Manager
Key Fire Protection, Inc.
bobby.gill...@keyfireprotection.com
(731) 424-0130 office
(731) 424-9285 fax
(731) 267-4853 cell
-Original
We are installing a 13R system. There is a pump room with (5) 400gallon
plastic tanks that will be piped together. Is there anything that gives
direction for the requirements for piping materials, valves, etc. between
the tanks and pump?
Thank You,
Bobby Gillett
Sr.Project Manager
Key
That is what I had planned and put a air relief or vacuum break on the fill
pipe. One thing we were debating was the use of plastic or steel, but we
decided to groove it and go steel.
Thanks,
Bobby Gillett
Sr.Project Manager
Key Fire Protection, Inc.
bobby.gill...@keyfireprotection.com
(731) 424
where to find direction for protecting the packaging of
explosives/ammunition.
Thank you in advance.
Bobby Gillett
Sr.Project Manager
Key Fire Protection, Inc.
bobby.gill...@keyfireprotection.com
(731) 424-0130 office
(731) 424-9285 fax
(731) 267-4853 cell
the spacing protects it now. There reason for tearing
down and rebuilding is to create an open floor plan for packaging, right now
there are concrete walls throughout and minimal space for packaging. At the
same time they are increasing eave height.
Bobby Gillett
Sr.Project Manager
Key Fire Protection
=The depth of the bottom chord member
C=The distance from the bottom of the top chord to the bottom of the bottom
chord
D=The outside diameter of the pipe
Length = (AxC)/(B+D)
Bobby Gillett
Sr.Project Manager
Key Fire Protection, Inc.
bobby.gill...@keyfireprotection.com
(731) 424-0130 office
(731) 424
The processing side conveys bricks of C-4 and drills holes in them to be
strung together. They are packaged in the new building.
Bobby Gillett
Sr.Project Manager
Key Fire Protection, Inc.
bobby.gill...@keyfireprotection.com
(731) 424-0130 office
(731) 424-9285 fax
(731) 267-4853 cell
A= 3'-10 B= 3 C= 20 D= 4
3.83/(3+4)x20
Bobby Gillett
Sr.Project Manager
Key Fire Protection, Inc.
bobby.gill...@keyfireprotection.com
(731) 424-0130 office
(731) 424-9285 fax
(731) 267-4853 cell
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum
, Army Tech
Bulletin 700-2. Extinguishing Media recommended: Wet System/Deluge System
recommended.
They are telling they want it wet, utilizing the original riser.
I'm going to try and get more specifications from them.
Bobby Gillett
Sr.Project Manager
Key Fire Protection, Inc.
bobby.gill
system is what is desired. If the need was to provide a
deluge or ultra high speed deluge, they take care of that themselves!!!
H...
Thank You again to all.
Bobby Gillett
Sr.Project Manager
Key Fire Protection, Inc.
bobby.gill...@keyfireprotection.com
(731) 424-0130 office
(731) 424-9285 fax
(731
I agree, everyone's first response, including mine, was C-4?!?!?! With the
hole jaw open and eyebrows raised thing going on.
Bobby Gillett
Sr.Project Manager
Key Fire Protection, Inc.
bobby.gill...@keyfireprotection.com
(731) 424-0130 office
(731) 424-9285 fax
(731) 267-4853 cell
-Original
, it wasn't as bad as it seems as long as you were prepared when
you bid it. The field training and installation went well.
Bobby Gillett
SR. Project Manager
Key Fire Protection, Inc.
(731) 424-0130 office (731) 424-9285 fax
(731) 267-4853 cell
bobby.gill...@keyfireprotection.com
-Original
Does anybody know where one can find any information (spec's, data sheets,
etc.) on Hodgman sprinklers?
Bobby Gillett
Sr. Project Manager
Key Fire Protection, Inc.
(731) 424-0130 office (731) 424-9285 fax
(731) 267-4853 cell
mailto:bobby.gill...@keyfireprotection.com
bobby.gill
Thanks to all for the help, I have Googled it as well. I have a call in to
Globe's Tech dept. to hopefully get an answer. We have a fire marshal
questioning an old vertical sidewall he came across. He doesn't believe.
Thanks, again.
Bobby Gillett
Sr. Project Manager
Key Fire Protection, Inc
That is exactly right. We even went as far as to pull out the sprinkler and
show him, where it could be seen goodstill not satisfied. What's a man
to do? We'll see what he says next.
Bobby Gillett
Sr. Project Manager
Key Fire Protection, Inc.
(731) 424-0130 office (731) 424-9285 fax
(731
contractor made him pose his question, and if we weren't there
would he have just left it alone?! Here nor there, we plan on showing him
cut sheets from another one, explaining this one isn't available anymore,
and go from there.
Thanks to all.
Bobby Gillett
Sr. Project Manager
Key Fire Protection, Inc
to the
electrician before hand, if it doesn't answer his questions he can reference
it while the pump rep is walking him through it.
Bobby Gillett
Sr. Project Manager
Key Fire Protection, Inc.
(731) 424-0130 office (731) 424-9285 fax
(731) 267-4853 cell
bobby.gill...@keyfireprotection.com
Understand, sorry I couldn't help further.
Bobby Gillett
Sr. Project Manager
Key Fire Protection, Inc.
(731) 424-0130 office (731) 424-9285 fax
(731) 267-4853 cell
bobby.gill...@keyfireprotection.com
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
control valve of the ACV. Does this scenario sound correct?
Thank You,
Bobby Gillett
Sr. Project Manager
Key Fire Protection, Inc.
(731) 424-0130 office (731) 424-9285 fax
(731) 267-4853 cell
mailto:bobby.gill...@keyfireprotection.com
bobby.gill...@keyfireprotection.com
?
Thank You,
Bobby Gillett
Sr. Project Manager
Key Fire Protection, Inc.
(731) 424-0130 office (731) 424-9285 fax
(731) 267-4853 cell
mailto:bobby.gill...@keyfireprotection.com
bobby.gill...@keyfireprotection.com
___
Sprinklerforum mailing
Great,
Thank You
Bobby Gillett
Sr. Project Manager
Key Fire Protection, Inc.
(731) 424-0130 office (731) 424-9285 fax
(731) 267-4853 cell
bobby.gill...@keyfireprotection.com
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun
Not right now. But if duplicates of the material info and specs aren't
possible then availability to info for future situations would be
sufficient.
I appreciate the help.
Bobby Gillett
Sr. Project Manager
Key Fire Protection, Inc.
(731) 424-0130 office (731) 424-9285 fax
(731) 267-4853 cell
allowing only the jockey to come on.
Any other comments are definitely welcome.
Thank You,
Bobby Gillett
Sr. Project Manager
Key Fire Protection, Inc.
(731) 424-0130 office (731) 424-9285 fax
(731) 267-4853 cell
bobby.gill...@keyfireprotection.com
-Original Message-
From
Great, thanks for the help. I'll look into this.
Bobby Gillett
Sr. Project Manager
Key Fire Protection, Inc.
(731) 424-0130 office (731) 424-9285 fax
(731) 267-4853 cell
bobby.gill...@keyfireprotection.com
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
FYI - In a similar situation with FM they say you should install all galv.
pipe on a dry system. I had to talk and talk to get the should allowed and
them to pass the black on the inside of the last one I did for one of their
clients.
Bobby Gillett
Sr. Project Manager
Key Fire Protection, Inc
in but they don't check out!
Bobby Gillett
Sr. Project Manager
Key Fire Protection, Inc.
(731) 424-0130 office (731) 424-9285 fax
(731) 267-4853 cell
bobby.gill...@keyfireprotection.com
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun
I agree. We argued for a long time (and lost), now wherever we travel we
always keep the same scenario, not to get bit there as well.
Bobby Gillett
Sr. Project Manager
Key Fire Protection, Inc.
(731) 424-0130 office (731) 424-9285 fax
(731) 267-4853 cell
bobby.gill...@keyfireprotection.com
Found it!
Bobby Gillett
Sr. Project Manager
Key Fire Protection, Inc.
(731) 424-0130 office (731) 424-9285 fax
(731) 267-4853 cell
bobby.gill...@keyfireprotection.com
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org
I understand that this spells out the areas sprinkler pipe can and can't go.
But where does it say you can or can't pass through the electrical room.
Bobby Gillett
Sr. Project Manager
Key Fire Protection, Inc.
(731) 424-0130 office (731) 424-9285 fax
(731) 267-4853 cell
bobby.gill
Is this in NFPA 70 2007 and if so where?
Bobby Gillett
Sr. Project Manager
Key Fire Protection, Inc.
(731) 424-0130 office (731) 424-9285 fax
(731) 267-4853 cell
bobby.gill...@keyfireprotection.com
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
What Thom said!!
Bobby Gillett
Sr. Project Manager
Key Fire Protection, Inc.
(731) 424-0130 office (731) 424-9285 fax
(731) 267-4853 cell
bobby.gill...@keyfireprotection.com
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun
into the
stairwell (also fed by cpvc from the corridor). The question being asked by
the fire marshall - What is the fire rating of the escutcheons?
Bobby Gillett
Sr. Project Manager
Key Fire Protection, Inc.
(731) 424-0130 office (731) 424-9285 fax
(731) 267-4853 cell
mailto:bobby.gill
But truly with the sprinkler being semi-recessed the pipe is not penetrating
the wall the sprinkler and escutcheon are. If the cpvc is considered
pentrating the wall, could you not transition to steel before the
penetration?
Bobby Gillett
Sr. Project Manager
Key Fire Protection, Inc.
(731) 424
My thoughts exactly Greg! Only way I know is to use a non recessed sprinkler
with a 2 piece deep plate and transition to steel.
Bobby Gillett
Sr. Project Manager
Key Fire Protection, Inc.
(731) 424-0130 office (731) 424-9285 fax
(731) 267-4853 cell
bobby.gill...@keyfireprotection.com
How do you propose fire rating the penetration when you have a HSW or
pendent in a ceiling? Especially concealed or semi recessed.
Bobby Gillett
Sr. Project Manager
Key Fire Protection, Inc.
(731) 424-0130 office (731) 424-9285 fax
(731) 267-4853 cell
bobby.gill...@keyfireprotection.com
wanting to know the fire
rating of the escutcheon.
Bobby Gillett
Sr. Project Manager
Key Fire Protection, Inc.
(731) 424-0130 office (731) 424-9285 fax
(731) 267-4853 cell
bobby.gill...@keyfireprotection.com
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
Thank You,
That makes total sense. I can't believe that fire caulking a sprinkler
w/concealed or recessed escutcheon would be expected, nor would it be
allowed.
Thank You to all who helped in this and those who still have comments to
come.
Bobby Gillett
Sr. Project Manager
Key Fire Protection
Well the rating of the escutcheon is back, we replied to the fire marshall
with the comments from the IBC. His response was - show me the rating on the
escutcheon or show me in the SBC, I'm not recognizing the IBC. Anybody have
it in the SBC?
Thank You,
Bobby Gillett
Sr. Project Manager
Thanks, Craig. He is using SBC '99. This project is in Northwest TN - local
city fire marshal.
Bobby Gillett
Sr. Project Manager
Key Fire Protection, Inc.
(731) 424-0130 office (731) 424-9285 fax
(731) 267-4853 cell
bobby.gill...@keyfireprotection.com
-Original Message-
From
Thanks to all.
Bobby Gillett
Sr. Project Manager
Key Fire Protection, Inc.
(731) 424-0130 office (731) 424-9285 fax
(731) 267-4853 cell
bobby.gill...@keyfireprotection.com
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun
Just to clarify, if it makes a difference, the sprinklers going to the two
rooms are staggered not being fed from a tee or cross.
Bobby Gillett
Sr. Project Manager
Key Fire Protection, Inc.
(731) 424-0130 office (731) 424-9285 fax
(731) 267-4853 cell
bobby.gill...@keyfireprotection.com
I thought Reliable had some new listings lately on them, might check theirs
as well.
Bobby Gillett
Sr. Project Manager
Key Fire Protection, Inc.
(731) 424-0130 office (731) 424-9285 fax
(731) 267-4853 cell
bobby.gill...@keyfireprotection.com
-Original Message-
From: sprinklerforum
Staggered (membrane). We have passed along the '99 SBC info that Craig
supplied earlier, and imagine that - he's satisfied. If that didn't work, I
was going to take the advice a friend on the west coast suggested.
Thanks to all.
Bobby Gillett
Sr. Project Manager
Key Fire Protection, Inc.
(731
No, but 9.3.5.4.1 Longitudinal sway bracing spaced at a maximum of 80ft on
center shall be provided for all feed and cross mains.
Are you putting Longitudinal on 1½ branch lines? Or am I mistaken?
Bobby Gillett
Sr. Project Manager
Key Fire Protection, Inc.
(731) 424-0130 office (731) 424-9285
I was mistaken, I'm with you now. You must have some long bracing to require
this (5'-0 o.c.)
Bobby Gillett
Sr. Project Manager
Key Fire Protection, Inc.
(731) 424-0130 office (731) 424-9285 fax
(731) 267-4853 cell
bobby.gill...@keyfireprotection.com
-Original Message-
From
Richard,
See NFPA 13 2007 8.16.2.3.3
Bobby Gillett
Sr. Project Manager
Key Fire Protection, Inc.
(731) 424-0130 office (731) 424-9285 fax
(731) 267-4853 cell
bobby.gill...@keyfireprotection.com
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
luck.
Bobby Gillett
Designer
[EMAIL PROTECTED]
(731)-424-0130
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Matthew Stone
Sent: Wednesday, June 13, 2007 12:08 PM
To: sprinklerforum@firesprinkler.org
Subject: Hanging branch lines from panel points
We
A test question leads me to ask the following;
Has anyone ever heard of a wax coated residential sprinkler? I would think
cost and appearance would limit everyone to poly. If there is any other
comments or reasoning please let me know.
Bobby Gillett
Designer
[EMAIL PROTECTED]
(731)-424
The polycoated also works well in this instance if color or appearance is an
issue. The original question came from a test question someone had on a
licensing ordeal. We had never heard of a wax coated res. And were just
curious to see what might be out there.
Bobby Gillett
Designer
[EMAIL
details are general for all trades but specific at the same time. Our
S-T is in TN and I believe most GC don't enforce the whole branhline hanger
due to factoring in common sense vs. type.
Bobby Gillett
Designer
[EMAIL PROTECTED]
(731)-424-0130
-Original Message-
From: [EMAIL PROTECTED]
[mailto
If the overhead system is wet then there would be no necessity for a dry in
the office. The office seems to be built inside the warehouse to a defined
height with nothing but a clg and insulation separating it from the
warehouse.
Bobby Gillett
Designer
[EMAIL PROTECTED]
(731)-424-0130
I agree, that is the typical around here for that type of scenario.
Bobby Gillett
Designer
[EMAIL PROTECTED]
(731)-424-0130
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Bob Knight
Sent: Monday, June 18, 2007 11:23 AM
To: sprinklerforum
We knew it going into it, it was still close. We just had a real tight
schedule, we had 1 more day before it was below freezing when we finished.
Bobby Gillett
Project Manager
[EMAIL PROTECTED]
(731)-424-0130
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf
We look at it, as you said, a Sprinkler Success story. They look at it as
minor, not enough to report on. If they only understood!!
Bobby Gillett
Project Manager
[EMAIL PROTECTED]
(731)-424-0130
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Jay Stough
Not if they stay parked there all night
Bobby Gillett
Project Manager
[EMAIL PROTECTED]
(731)-424-0130
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of George Church
Sent: Monday, July 09, 2007 3:33 PM
To: sprinklerforum@firesprinkler.org
Subject: RE
OH or LH - If there is a dry ex. coverage sprinkler for the hazard and roof
pitch that you can pipe around beams, etc. I would say - Yes.
Bobby Gillett
Project Manager
[EMAIL PROTECTED]
(731)-424-0130
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Greg
There was an earlier post about placing sprinklers under obstructions when
the overhead system is ESFR, are these required to be ESFR as well? I didn't
see any replies in the archives. How about it?
Bobby Gillett
Project Manager
[EMAIL PROTECTED]
(731)-424-0130
to be ½ or larger and capable of restoring normal
air pressure to the system within 30 min. I don't see any requirements in 13
for pipe type of this supply.
Bobby Gillett
Project Manager
[EMAIL PROTECTED]
(731)-424-0130
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf
I agree, but this is the only reference I see in 13 that they might be
addressing this with.
Bobby Gillett
Project Manager
[EMAIL PROTECTED]
(731)-424-0130
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Bill Minkel
Sent: Wednesday, July 25, 2007 1:55 PM
space them on a horizontal plane or with the slope. And do you space to each
hip ( 4 individual spaces) or space across the hip ( one floor space) ?
Bobby Gillett
Project Manager
[EMAIL PROTECTED]
(731)-424-0130
___
Sprinklerforum mailing list
and the As to the edge of the hip?
Bobby Gillett
Project Manager
[EMAIL PROTECTED]
(731)-424-0130
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Travis Mack
Sent: Friday, July 27, 2007 9:22 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Sprinkler layout under slope
and be 30 away. I believe this would act like an
obstruction and the one we added would not have an affect on the other
sprinkler spacing-correct?
Bobby Gillett
Project Manager
[EMAIL PROTECTED]
(731)-424-0130
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf
to opening distances will have to be field verified but I
believe they're closer than 30. The bad part is everyone (HVAC, Elect.,
Plumbing, etc.) had our sprinkler layout and all of these except 2 could
have been centered between lines/heads.
Bobby Gillett
Project Manager
[EMAIL PROTECTED]
(731)-424-0130
be treated in the way an obstruction is treated correct? If we could
respace and be sufficient in the spacing of the other heads that would be
the way out, but that is impossible it creates under/over spacing.
Bobby Gillett
Project Manager
[EMAIL PROTECTED]
(731)-424-0130
-Original Message
They are manual, for heat removal only. There is no A/C in the main part of
the building.
Bobby Gillett
Project Manager
[EMAIL PROTECTED]
(731)-424-0130
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
[EMAIL PROTECTED]
Sent: Wednesday, September 05, 2007
The only D1 at Reliable that I am familiar with is a D1 guard. How old is
this sidewall sprinkler and what type--Dry, QR, SR, etc.?
Bobby Gillett
Project Manager
[EMAIL PROTECTED]
(731)-424-0130
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Smith
Did you see the response from Sal Izzo @ Reliable Technical Services? If not
give him a call at 1.800.55.RASCO or 864.843.5227. I believe he has what you
need.
Bobby Gillett
Project Manager
[EMAIL PROTECTED]
(731)-424-0130
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL
It is probably a vertical SW that was one of the sheets Sal had.
Bobby Gillett
Project Manager
[EMAIL PROTECTED]
(731)-424-0130
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Smith, Steven
D. (CSFD)
Sent: Friday, September 14, 2007 9:23 AM
I've done a few + and even with much coordination, they usually require some
somewhere. We did one in 2002 that the insurance co. is now requiring them
to add some under conveyors. Thank goodness we did the original
design/installation where we have everything we need.
Bobby Gillett
Project
If I'm reading 8.6.5.1.2 correctly, it says if you are against the wall- the
soffit has to be 30 or under to be able to use this.
Anything over 30 that is against the wall would require additional
sprinklers. Or am I having another Monday today?
Bobby Gillett
Project Manager
[EMAIL PROTECTED
If I'm reading 8.6.5.1.2 correctly, it says if you are against the wall- the
soffit has to be 30 or under to be able to use this.
Anything over 30 that is against the wall would require additional
sprinklers. Or am I having another Monday today?
Bobby Gillett
Project Manager
[EMAIL PROTECTED
! That surpasses the less than or equal
to 30 described in 8.6.5.1.2
Bobby Gillett
Project Manager
[EMAIL PROTECTED]
(731)-424-0130
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Travis Mack
Sent: Wednesday, September 19, 2007 11:26 AM
To: sprinklerforum
off of one wall.
Bobby Gillett
Project Manager
[EMAIL PROTECTED]
(731)-424-0130
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Travis Mack
Sent: Wednesday, September 19, 2007 12:47 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Sprinklers in Soffit
NO you aren't missing anything--you are correct all the way. I was looking
at the wrong chart. When you replied last - I double checked where I was
looking (at the correct chart for the incorrect sprinkler).
MY BOWS AND APOLOGIES!!
Bobby Gillett
Project Manager
[EMAIL PROTECTED]
(731)-424-0130
Yep, me too!! By the way what is tomorrow? Oh yeah--MONDAY!!
Bobby Gillett
Project Manager
[EMAIL PROTECTED]
(731)-424-0130
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Travis Mack
Sent: Wednesday, September 19, 2007 2:06 PM
To: sprinklerforum
Sometimes the Owner's Certificate supplied in NFPA-13 4.3 can be of
assistance to you. You can then forward that info to the AHJ, and you'll
have it on file as well for those unclear surprises in storage at the last
minute.
Bobby Gillett
Project Manager
[EMAIL PROTECTED]
(731)-424-0130
are!!
Bobby Gillett
Project Manager
[EMAIL PROTECTED]
(731)-424-0130
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Matthew J.
Willis
Sent: Thursday, September 27, 2007 10:45 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Pipe clamps on Z purlins
Its
?
Bobby Gillett
Project Manager
[EMAIL PROTECTED]
(731)-424-0130
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED
Thanks,
That was the outcome that I had came up with, but didn't want to bump heads
with the AHJ until I had received some feed back from experience. Just in
case I was missing something and to see how some of you might have handled
this.
Again thanks to all!!
Bobby Gillett
Project Manager
this than I am to add
hydrants. The city hydrants meet this so we're ok on that.
Thanks for the artillery; I'm waiting on a call back from them. I'll let you
know how it goes.
Bobby Gillett
Project Manager
[EMAIL PROTECTED]
(731)-424-0130
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL
The project is using 2003 IBC and I don't see the chart or exception in
there. Is this new to 2006 IBC?
Bobby Gillett
Project Manager
[EMAIL PROTECTED]
(731)-424-0130
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Fletcher, Ron
Sent: Wednesday, October
the barrier as described in the previous paragraph. (See
Figure 2.4.5.3.5)
Bobby Gillett
Project Manager
[EMAIL PROTECTED]
(731)-424-0130
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Chris Cahill
Sent: Wednesday, October 03, 2007 11:32 AM
To: sprinklerforum
less demanding requirements for non-storage
applications and dwellings.
Bobby Gillett
Project Manager
[EMAIL PROTECTED]
(731)-424-0130
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Ray Schmid
Sent: Wednesday, October 03, 2007 1:13 PM
To: sprinklerforum
Are you saying the entire unit is above the deflector and nothing is below?
If this is the case then you don't worry about the obstruction rule, but if
the UH is lowered below the deflector -- then it becomes an obstruction.
Bobby Gillett
Project Manager
[EMAIL PROTECTED]
(731)-424-0130
I don't know all of the dimensions and distances in your particular case,
but try applying 8.12.5.2 - this is more for the U.H. than 8.12.5.1
Bobby Gillett
Project Manager
[EMAIL PROTECTED]
(731)-424-0130
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf
with you on your opinion and this is also mine and no one
else'setcetc.
Bobby Gillett
Project Manager
[EMAIL PROTECTED]
(731)-424-0130
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Matt Willis
Sent: Thursday, October 18, 2007 8:47 AM
only and another company's listing on the similair sprinkler is UL listed
for non-combustible obstructed construction.
On a second note my AFSA Fire Sprinkler School Book states that it is
obstructed construction although most AHJ's will consider it unobstructed.
Bobby Gillett
Project Manager
only and another company's listing on the similair sprinkler is UL listed
for non-combustible obstructed construction.
On a second note my AFSA Fire Sprinkler School Book states that it is
obstructed construction although most AHJ's will consider it unobstructed.
Bobby Gillett
Project Manager
. etc. This is something that needs to be cleared up for
all to see and we can get on the same page w/ each other and the AHJ's.
Bobby Gillett
Project Manager
[EMAIL PROTECTED]
(731)-424-0130
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of A.P.Silva
Sent
My pricing was about .81 cents higher than the Reliable--I don't know what
yours will be.
Do you agree with EC in this situation per NFPA then?
Bobby Gillett
Project Manager
[EMAIL PROTECTED]
(731)-424-0130
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf
I have a brass upright 286° Model HHX (I believe its an old GEM), can anyone
verify the orfice/k-factor? Tyco is closed this afternoon.
Thank you,
Bobby Gillett
Sr. Project Manager
Key Fire Protection, Inc.
(731) 424-0130 office (731) 424-9285 fax
(731) 267-4853 cell
http
Sorry, I should have also mentioned it is 3/4 thread and the deflector is
marked SSU-3 458A.
Bobby Gillett
Sr. Project Manager
Key Fire Protection, Inc.
(731) 424-0130 office (731) 424-9285 fax
(731) 267-4853 cell
www.keyfireprotection.com
-Original Message-
From: sprinklerforum-boun