Interesting story.Watch video.(Why would a chief make a comment on optional sprinklers?)

2008-10-25 Thread Stewart Kidd
I passed this item on to a few friends in the UK and one of them, a former senior fire safety officer with many years experience responded: Answer: simple - he likes going to fires. Stewart ___ Sprinklerforum mailing list

Re: Russian sub fire

2008-11-10 Thread Stewart Kidd
among other toxic gases S On 10 Nov 2008, at 14:28, Ergo wrote: Freon! If they used freon (R-12 ) it's no wonder that fatalities occured. When freon and flame combine the product is a deadly gas called phosgene. Ergo On Sun, Nov 9, 2008 at 9:45 AM, Stewart Kidd [EMAIL PROTECTED] wrote

Re: Russian sub fire

2008-11-09 Thread Stewart Kidd
According to the BBC the fire fighting gas was 'freon' Stewart On 9 Nov 2008, at 16:52, Todd Williams - FPDC wrote: It will be interesting to see how this plays out in the next few weeks. http://www.cnn.com./2008/WORLD/europe/11/09/russia.submarine/index.html Todd G. Williams, PE Fire

Re: Russian sub fire

2008-11-10 Thread Stewart Kidd
, wasn't phosgene used quite a bit during WWI? At 09:28 AM 11/10/2008, you wrote: Freon! If they used freon (R-12 ) it's no wonder that fatalities occured. When freon and flame combine the product is a deadly gas called phosgene. Ergo On Sun, Nov 9, 2008 at 9:45 AM, Stewart Kidd [EMAIL PROTECTED

Re: White papers and definition of roles

2008-11-10 Thread Stewart Kidd
All due respect to Craig and his comments but as a consultant can I propose that architects are much harder to deal with than PE's ? In the UK architects do a seven year university course. On this, in most cases, they spend less than one day on fire protection. Do I make my point ?

Re: Man made reservoir to be used for fire protection?

2008-11-21 Thread Stewart Kidd
not only the hydrant main but also sprinklers and a large deluge system Regards Stewart Stewart Kidd www.risk-consultant.com On 21 Nov 2008, at 13:37, [EMAIL PROTECTED] [EMAIL PROTECTED] wrote: Is there a specific reason for going with the pond instead of a tank? If it's aesthetics

Re: Coal conveying belts

2008-11-24 Thread Stewart Kidd
covered in NFPA 850. Stewart Stewart Kidd www.risk-consultant.com On 24 Nov 2008, at 14:17, [EMAIL PROTECTED] wrote: Ron, When you say tube style, I am assuming that is the same as pipe conveyors where the belt is open at loading and unloading ends, but is wrapped closed by idlers for travel

Re: Hot oil kettles - Large

2008-11-25 Thread Stewart Kidd
premises) but there is a serious risk of re- ignition once the gas concentration dissipates Regards Stewart Kidd www.risk-consultant.com On 25 Nov 2008, at 18:49, Fletcher, Ron wrote: Thanks Charles, we are looking at CO2. The kettles are 7.5 ft. x 20 ft. and they have covers latched

Re: Hot oil kettles - Large

2008-11-25 Thread Stewart Kidd
to remove carbon particles and any emulsification, probably be reused. Stewart On 25 Nov 2008, at 21:10, Fletcher, Ron wrote: Thanks Stewart. Have you ever compared the cost of mist to CO2? Ron -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Stewart Kidd

Re: another fire - this will be interesting

2008-12-31 Thread Stewart Kidd
Interesting story - I have recently had 'discussions' with a consultant who has undertaken a 'fire engineering study' for an education dept in England which concluded that sprinklers were not needed in a new school (despite a presumption issued by the Government Department responsible for

Re: another fire - this will be interesting

2008-12-31 Thread Stewart Kidd
Scot The Government department responsible for Education in England has issued a risk assessment tool which has to be used in planning all new schools. In the case of virtually all secondary schools and many larger primary tools the outcome from the risk assessment indicates that

Re: another fire - this will be interesting

2009-01-01 Thread Stewart Kidd
Todd is absolutely right - all UK fire law (until 2005) was written after major life loss fires. What odds will anyone give me that the Thai government will be considering new legislation for nightclubs right about now ? Stewart On 2 Jan 2009, at 00:00, Todd Williams wrote: Go back in

Re: Sprinkler system interconnection to domestic waste pipe

2009-01-09 Thread Stewart Kidd
In the power stations in Hong Kong we used to use 'tun dishes' to collect the test drain water in deluge systems - these were copper or galvanised iron hoppers around 40 inches by 16 inches by 24 inches deep and the bottom of the tun dish had a 4 inch diameter connection to its own little

MIC

2009-01-20 Thread Stewart Kidd
Colleagues I have received an enquiry from a UK company as follows: Has anyone heard of “anti MIC chemical coatings” for metal sprinkler systems? Can anyone help ? Thanks Stewart___ Sprinklerforum mailing list

Re: MIC

2009-01-20 Thread Stewart Kidd
-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Stewart Kidd Sent: Tuesday, January 20, 2009 2:00 PM To: sprinklerforum@firesprinkler.org Subject: MIC Colleagues I have received an enquiry from a UK company as follows: Has anyone heard of anti MIC

Re: Inergen vs Nitrogen vs Argon

2009-01-30 Thread Stewart Kidd
Reza Inergen and Argonite are proprietary gas mixtures which are direct competitors of carbon dioxide for total flooding systems. I guess there are people selling straight Argon mixtures but I have never been asked to review such a system. Argonite and carbon dioxide are not recommended

Re: Inergen vs Nitrogen vs Argon --- and HAV

2009-01-30 Thread Stewart Kidd
Hypoxic Air Inerting to give it is correct name is indeed prohibited in some jurisdictions and OSHA maintains its stance that any system which reduces oxygen levels to below 16% is unsafe for occupied spaces,. I have been involved in the design studies and installation of one such small

Re: Inergen vs Nitrogen vs Argon

2009-01-30 Thread Stewart Kidd
) and IG-01 (Argon) and IG-100 (Nitrogen), are these three prohibited to use for occupied spaces? Water mist Regards Stewart I eagerly would like to know your ideas about the above three scenarios. Thanks, Reza --- On Fri, 1/30/09, Stewart Kidd stewart-k...@ndirect.co.uk wrote: From

Re: antifreeze combustibility?

2009-04-21 Thread Stewart Kidd
Most anti freeze additives on the market appear to contain ethylene glycol which (when I last looked) is certainly combustible. Whether it is flammable depends on how you define 'flammable'. It has a fairly high flashpoint 110ºC so is not 'easy' to ignite with a match or a spark but it

Re: UAE, Saudi, Codes and standards and component certifications

2009-05-11 Thread Stewart Kidd
Craig There are no consistent regimes regarding equipment standards. In most of the Gulf States (UAE, Bahrain, Qatar) the local Civil Defence (= Fire Department) will accept LPCB, VdS and UL standards. FM listings are also generally acceptable. in addition, some of the UAE CD depts also

Re: Reasons to not sprinkler a pharmaceutical plant

2009-05-14 Thread Stewart Kidd
Franz The mention of the underground parking also rings bells ! Recent tests for the UK government suggest that the likelihood of fire spread from vehicle to vehicle is much greater than previouslyb thought and the fuel load of modern cars is rated at around 7Mw ! Stewart PS Currently

Re: Reasons to not sprinkler a pharmaceutical plant

2009-05-14 Thread Stewart Kidd
learn from the mistakes of others! glc -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Stewart Kidd Sent: Thursday, May 14, 2009 8:15 AM To: sprinklerforum@firesprinkler.org Subject: Re: Reasons

Fire Service College Fire: All 11 appliances lost

2009-05-16 Thread Stewart Kidd
Colleagues For once, I find myself a loss for words and I'm n sure whether to laugh or cry ! The FSC is government-owned and is the UK's principle fire training centre. The fire destroyed (I am told) all of the colleges fire trucks. Stewart

Re: Fire Service College Fire: All 11 appliances lost

2009-05-17 Thread Stewart Kidd
No - 1960's construction - some UK fire departments started fitting sprinklers to stations back in the mid 90's. There are very, very few sprinklered government buildings Stewart On 16 May 2009, at 23:58, scott mitchell wrote: Was it sprinklered?

Re: Fire Hydrant Sprinkler System Water Supply

2009-06-03 Thread Stewart Kidd
Reza For what it's worth, UK practice does not permit hydrants and hose reels/racks to be taken from sprinkler mains. However these are insurer requirements and as such are subject to negotiation. I had a problem many years ago on a coal fired power station (1600 MW) which had a massive

Re: Membrane dome in Sprinkler Age

2009-07-05 Thread Stewart Kidd
Frans Can't recall the article but there is a UK shopping centre (converted from a skating rink) which is sprinkler protected using free standing posts each with three or four arms containing sprinkler heads. I'll send you a picture off-line. Regards Stewart On 5 Jul 2009, at 01:19,

Re: Membrane dome in Sprinkler Age

2009-07-05 Thread Stewart Kidd
[mailto:sprinklerforum-boun...@firesprinkler.org ] On Behalf Of Stewart Kidd Sent: Sunday, July 05, 2009 11:58 AM To: sprinklerforum@firesprinkler.org Subject: Re: Membrane dome in Sprinkler Age Frans Can't recall the article but there is a UK shopping centre (converted from a skating rink

Re: Membrane dome in Sprinkler Age

2009-07-06 Thread Stewart Kidd
unnecessary. Regards Stewart On 6 Jul 2009, at 00:10, Thomas Watt wrote: Wow...no heat collection necessary eh? - Original Message - From: Stewart Kidd stewart-k...@ndirect.co.uk To: sprinklerforum@firesprinkler.org Sent: Sunday, July 05, 2009 6:30 AM Subject: Re: Membrane dome

Re: Membrane dome in Sprinkler Age

2009-07-06 Thread Stewart Kidd
of Red Bank, NJ -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Stewart Kidd Sent: Monday, July 06, 2009 8:54 AM To: sprinklerforum@firesprinkler.org Subject: Re: Membrane dome in Sprinkler Age Thomas

RE: Hollywoods version of LH Office Sprinkler Systems

2007-01-17 Thread Stewart Kidd
In the new Bond film (Casino Royale) the baddie sets off all the sprinklers in Miami airport by operating a pull box. Several people have complained but the studio's response was 'It's only a movie'. Regards Stewart Since we're running w/ this thread... Frequency w/ Dennis Quaid and Jim

RE: Saltwater Standpipe System for a Shipyard

2007-04-04 Thread Stewart Kidd
take the sort of pressures you would want for fire department use. I normally specify that there is a locked (but easily openable) gate valve upstream of the sea water pump and then backfill this section with fresh water. Stewart Kidd Loss Prevention Consultancy Ltd coastally-Original

Nursing Homes

2007-05-14 Thread Stewart Kidd
. Best regards to all Stewart Stewart Kidd (this time as) Secretary General, British Automatic Fire Sprinkler Association ___ Sprinklerforum mailing list Sprinklerforum@firesprinkler.org http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Re: Nursing Homes

2007-05-14 Thread Stewart Kidd
Roland Quite right old boy, slip of the keyboard. Thanks Stewart Me thinks (as some Brits say) that Brant would be contacted for FPC whereas you'll want to discuss this with Janet Knowles (AFSA). Roland On May 14, 2007, at 8:25 AM, Stewart Kidd wrote: Just read Ronny Coleman's piece

RE: Carbon Dioxide System Discharge Time

2007-08-23 Thread Stewart Kidd
question is: What's wrong with sprinklers or mist ? I specify these all the time for IT and comms rooms. Stewart Stewart Kidd Loss Prevention Consultancy Cambridge, England Reza, No I minute is OK. BUT be careful of over pressurization due to the high rate and high concentration. The intent

RE: Fire Pump Selection - REVISED

2007-09-04 Thread Stewart Kidd
or other of the international reinsurers who will certainly be looking for reliable fire water supplies - especially when local fire departments may be some distance away or less than effective in high risk premises. Kind regards Stewart Stewart Kidd Loss Prevention Consultancy Ltd http

..and now for the good news

2007-09-14 Thread Stewart Kidd
For once, representing the British Automatic Fire Sprinkler Association, I thought I would share two pieces of good news. 1. The Welsh Assembly (kind of like a state assembly) will later this year debate a Bill to require all new homes in Wales to be sprinklered. 2, Following strong lobbying,

Re: Museum Fire Protection

2007-10-02 Thread Stewart Kidd
Reza I work a great deal in the heritage/museum/gallery/kibrary area and would advise great caution in listening to salesmen. FM 200 is most certainly not the widest used system for museum and gallery protection - sprinklers and water mist are much more commonly used. You should note

Re: Museum Fire Protection

2007-10-02 Thread Stewart Kidd
You can download a summary of the report or order the complete work http://www.riksantikvaren.no/Norsk/Publikasjoner/Utgitt_i_samarbeid_med_andre/filestore/ManualContentsandExecutivesummaryonly.pdfhere Stewart Reza I work a great deal in the heritage/museum/gallery/kibrary area and would

RE: Proposal Form

2007-10-03 Thread Stewart Kidd
Try getting into the form via this link - it appears to be accesible without logging in as a committee member or as an NFPA member. http://submissions.nfpa.org/onlinesub/onsubmain.php Stewart http://www.nfpa.org/assets/files/PDF/CodesStandards/NFPAProposalForm.doc You might have to be a

Re: Museum Fire Protection

2007-10-06 Thread Stewart Kidd
Reza Geir is the world expert on air reduction systems - you can take anything he says on this to the bank. (He and I have spent the last five years working on an EU sponsored heritage protection project). If the oxy levels are reduced to 15 -16% or less combustion cannot take place but in

RE: sprinkler piping in unsprinklered areas

2007-10-10 Thread Stewart Kidd
Not much help but an observation: most UK insurers require an enhanced level of physical fire separation between sprinklered and unprinklered buildings. This is normally two hours but I have seen four hours being specified for a plastics factory. Stewart Isn't there an assumption made by

Re: Any trustworthy Chinese/Taiwanese UL listed sprinkler/valve manufactures?

2007-10-23 Thread Stewart Kidd
No good experience with any of the Chinese/Taiwanese components (but that doesn;t mean that all of them are garbage - there's a lot of stuff from the Far East circulating in the Arabian Gulf - some of it clear knock-offs of listed components. Hong Kong Fire Services Department maintains a

Re: [NDO NEWT] *** SPAM *** (UK scale)

2007-10-29 Thread Stewart Kidd
Nah -We went metric 35 years ago - common scales are 1:100, 1:200 Stewart Hello Everyone, Are plans drawn in the UK using 1/4 = 1' ? I had this question asked of me and, by-golly, I found myself scratching my head. Regards

Re: [NDO NEWT] *** SPAM *** (Re: [NDO NEWT] *** SPAM *** (UK scale))

2007-10-29 Thread Stewart Kidd
My old 1977 Land Rover needs Whitworth, AF and metric spanners/sockets SK And I've been holding on to my Whitworth spanners. On 10/29/07, Stewart Kidd [EMAIL PROTECTED] wrote: Nah -We went metric 35 years ago - common scales are 1:100, 1:200 Stewart Hello Everyone, Are plans drawn

RE: Wow

2007-11-21 Thread Stewart Kidd
Let's hope the 'medical centre' includes the provision of a psychiatric facility Stewart Well if that's the case, speaking as a designer I think dude's a genius. Keep those prices up fellahs ... Steve Leyton Protection Design Consulting -Original Message- From: [EMAIL

RE: Wow - Info

2007-11-24 Thread Stewart Kidd
I'm truly amazed - and grateful to John D for this reference - not to mention horrified. I can't believe in the litigious USofA that I know and love that no one has questioned the advertising claims for such systems. The most fundamental lesson in fire safety is that it is the smoke in

Re: oil filled electrical transformers - protection?

2007-12-05 Thread Stewart Kidd
I spent more than 10 years as a power company's FPE and have been involved in dozens of substation schemes. The determining factor on protection of a large power Tx is a complex matrix of: Type of fluid in the Tx and any coolers Volume of fluid Normal termperature of fluid Indoor/Outdoor

Substation Fires

2007-12-14 Thread Stewart Kidd
This demonstrates the chaos even a small substation fire can cause Regards Stewart Tower fires in Melbourne December 6, 2007 Thousands of workers were evacuated from two central Melbourne office towers after an explosion in an electrical substation in a car park caused a fire in one and cut

RE: high pressure water mist vs NFPA 13: 175:psig systems

2008-01-03 Thread Stewart Kidd
Craig There's plenty of data and experience out there if you look beyond the US. Not all mist systems need pumps - I have been responsible for a number where all that was needed was two cylinders of water and one of nitrogen. There is a draft EN (European Standard) 14972 for mist

Re: Great Forum Advice...

2008-01-16 Thread Stewart Kidd
consolation I know, but reflect that what this particular union is doing used to be illegal under English common law and was known as Barratry. I belive some US states retain the offence under codified law. Good luck to your contractor friend. Stewart Kidd Hi All, I would like to gather some

Re: Fire sprinkler question

2008-01-26 Thread Stewart Kidd
which was installed around 1930 which successfully extinguished a fire in February 2005. Stewart Kidd BAFSA, Ely, England Here is a question I was asked today: Where can I find a list that indicates the Estimated Design life for a fire suppression/sprinkler system? What say ye

Re: Another Save

2008-02-04 Thread Stewart Kidd
Presumably the premises are not as we on this side of the pond would understand a 'Gentleman's Club'? Presumably one of the young ladiesor one of the members overheated ? Regards Stewart Hello sprinklerforum, Near the bottom of the page

Re: Clearance from 440v

2008-02-18 Thread Stewart Kidd
George You won't go far wrong if you follow the table ( 1.9 I think in NFPA 15). This requires a minimum of 7 inches (178mm) for all voltages 13.8 kV Stewart Kidd Would anyone know how much clearance we need to leave between or steel feed main and an exposed crane rail with 440 volts

RE: SC sprinkler legislation

2008-04-04 Thread Stewart Kidd
Have recently been involved in insurance inspections of two very large plants in SC (including one near Spartanburg) I have been following this [articular debate. The VFD's in the area all seem to roll tankers regardless of the presence of hydrants on even quite small roads. Both my plants

Re: worried about Sprinklers leakage

2008-06-23 Thread Stewart Kidd
! Masalaama ! Stewart Stewart Kidd Loss Prevention Consultancy Ltd UK On 23 Jun 2008, at 13:44, Haji, Jaber M wrote: Newly constructed research and development lab facility is protected by a wet type sprinkler system, one of the lab scientist is worried about the accidental release

Re: South Carolina Legislature Overrides Governor Veto of Sprinkler Bill

2008-06-27 Thread Stewart Kidd
That's quite a majority ! Well done SC Stewart On 27 Jun 2008, at 12:09, John Drucker wrote: -Original Message- From: John Drucker [mailto:[EMAIL PROTECTED] Sent: Friday, June 27, 2008 7:09 AM To:NJFireSafety Subject: South Carolina Legislature Overrides Governor Veto of Sprinkler

Re: green dry chemical agent

2008-08-13 Thread Stewart Kidd
While NOVEC is certainly greener than FM200 (and of course, less corrosive and has a lower toxicity) the 'non-chemical' fire fighting gases (Argonite and Inergen) have fairly green credentials too. Nitrogen or Argon do not have any GWP - although the 8% CO2 in Inergen has obviously some

Re: Re[2]: FM-200 Decomposition Product _URGENT!!!

2008-08-13 Thread Stewart Kidd
Reza Not sure that the ill-effects are entirely due to the fire gases. The 1996 LPC Report 'Halon Alternatives' based on a series of well documented tests suggests that FM 200 generates high levels of hydrogen fluoride in the presence of fire - these were stated in respect of the test fires

Re: FM-200 enclosure volume (Exclude Cabinets volume?)

2008-09-03 Thread Stewart Kidd
Based on UK insurers protocols any FM200 protected space is unsafe for occupation at such concentration levels. Most companies follow similar procedures for CO2 systems and evacuate FM200 protected rooms before the gas is discharged. Stewart On 3 Sep 2008, at 19:05, Reza Esmaeili wrote:

Re: Coal Bunkers

2008-09-11 Thread Stewart Kidd
offline to: [EMAIL PROTECTED] Regards Stewart Stewart Kidd Loss Prevention Consultancy Cambridge, England On 11 Sep 2008, at 13:46, [EMAIL PROTECTED] [EMAIL PROTECTED] wrote: NFPA 85 has a lot of verbiage concerning coal bunkers. But there's not a lot if any fixed fire protection involved

Re: Expected life of painted steel fire main with brackish water in it

2009-07-27 Thread Stewart Kidd
water in Bahrain and none of it good. We filled all fire mains and tanks with 'sweet water' (desalinated water from flash distillers with some added minerals) and then had to flush any line that was used before refilling. Regards Stewart Stewart Kidd On 27 Jul 2009, at 11:06, Steve Kowkabany

Another UK Fire Service Fire

2009-07-31 Thread Stewart Kidd
Dear Colleagues Ooops...yet another fire in embarrassing circumstances! http://news.bbc.co.uk/1/hi/northern_ireland/8177701.stm Stewart ___ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical

UK Research into Sprinkler Attitudes

2009-08-06 Thread Stewart Kidd
Colleagues You may be interested in the very interesting recent research carried out by Kent Fire Rescue Service into changes in public attitudes to sprinklers: http://www.bafsa.org.uk/snews.php Regards Stewart ___ Sprinklerforum mailing list

Re: Another UK Fire Service Fire

2009-08-10 Thread Stewart Kidd
, Wings (fenders), torches, lifts I can add 'fire appliances' Kevin Mowle -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Stewart Kidd Sent: Friday, July 31, 2009 2:36 PM To: sprinklerforum

Re: Salt Water for Fire Sprinkler System

2009-08-20 Thread Stewart Kidd
Brian I had several systems in the Gulf where brackish water was used - I always speciified gunmetal pump casings and volutes and this seems to have been satisfactory. Stewart Kidd On 20 Aug 2009, at 14:13, Brian Harris wrote: Has anyone had any experience with a fire pump taking suction

Re: Salt Water for Fire Sprinkler System

2009-08-20 Thread Stewart Kidd
Thom In many part of the world the public water mains supply water which may be technically within WHO guidelines for potability is essentially brackish. In the Arabian Gulf this is produced by blending ground water with distilled/desalted water. People use this for general household

Re: Salt Water for Fire Sprinkler System

2009-08-20 Thread Stewart Kidd
McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926 f Stewart Kidd Sent: Thursday, August 20, 2009 10:31 AM To: sprinklerforum@firesprinkler.org Subject: Re: Salt Water for Fire Sprinkler System Incidentally

Re: European electricity grid

2009-08-26 Thread Stewart Kidd
There's a DC link from Sangatte in France to Sellinge in Kent. This allows the UK to utilise nuclear generated power but puts all the reactor risks in France's backyard. Stewart On 26 Aug 2009, at 20:13, Van pellicom Giedo wrote: And the last one, for the Belgium Electricity grid lovers

Re: European electricity grid

2009-08-26 Thread Stewart Kidd
The capacity is two circuits (each of two pairs of cables) offering a total of 2000 MW import export, each operating at 270 kV. Both UK and France use 50Hz but the DC link was chosen for better control and lower losses. The whole link is 73 km with the under sea section is 48 km. I did

Re: 3 from 1

2009-08-27 Thread Stewart Kidd
You'd be welcome ! Stewart PS Bring your voltage and frequency converters - our extra strength 240v 50 hz AC munches wimpy US 110v 60 Hz appliances ! On 27 Aug 2009, at 16:42, George Church wrote: EFSN conference? -Original Message- From: sprinklerforum-boun...@firesprinkler.org

Re: Fire Sprinker System Changes in Vis Lab

2009-09-04 Thread Stewart Kidd
Haji Missed the first post. While preaction systems are one way to appease the fears of the anti sprinkler lobby, I have major philosophical problems with the rationale of taking a simple, effective system with an incredibly high success rate and very low failure rate and then making it

Re: Fire Sprinker System Changes in Vis Lab

2009-09-04 Thread Stewart Kidd
Ron 'Haji' is an honorific representing Jaber Mohammed's status as a Moslem male who has made the 'Haj', (the pilgrimage to Mecca) - it's kind of optional but most people who use the word in their name appreciate their status being acknowledged. Jaber probably has two or three other

Re: Storage of idle wooden pallets and hi-ex foam

2009-11-23 Thread Stewart Kidd
Frans Hi ex foam can sometimes not work to suppress fires in complex structures due to back pressures. I had a failure in a basement and tunnel system some years ago. There have also been problems with foam systems in cable tunnels in power stations. I think the only areas where foam is

Re: Fire Protection Handbook

2009-12-17 Thread Stewart Kidd
I'm still using the 16th edition - wonder what the postage would be to the UK ? Stewart On 17 Dec 2009, at 20:09, Brian Harris wrote: For some reason the link got truncated, you need to combine both lines. Sorry. http://cgi.ebay.com/Fire-Protection-Handbook-Hardcover-2003_W0QQitemZ3412923

Re: Bio-diesel in pump drivers

2009-12-22 Thread Stewart Kidd
is a greater probability that the fuel will sit in the tank for a long time. There have reportedly been a couple of cases where fire pumps have failed to start due to clogged filters. Regards Stewart Stewart Kidd Secretary General British Automatic Fire Sprinkler Association Ltd Registered

Welsh Assembly Votes Unanimously to BNring in Sprinkler Law for Residential Properties

2010-01-27 Thread Stewart Kidd
Colleagues I thought I would share some joyful news with you all and record how one woman's persistence and determination can overcome civil service inertia and bureaucracy. We are not yet there but there is a light at the end of the tunnel and it ain't a candle ! Best wishes Stewart Kidd

Re: Car Park/Stacker....

2010-03-02 Thread Stewart Kidd
://www.bafsa.org.uk/publications/general-3rd-party-publications.php Cost quite a lot (for a small trade group !) so feel free Best wishes Stewart Stewart Kidd Secretary General British Automatic Fire Sprinkler Association Ltd Registered in England in 1974: No 01194637 as a company limited

Re: Car Park/Stacker....

2010-03-02 Thread Stewart Kidd
-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Stewart Kidd Sent: Tuesday, March 02, 2010 12:23 PM To: sprinklerforum@firesprinkler.org Subject: Re: Car Park/Stacker Colleagues Just seen this - am in Scotland where broadband refers to a belt

Re: Claymore

2010-03-03 Thread Stewart Kidd
Ron ahem !getting back to the forum: Historic Scotland, the government agency for looking after Scotland's built heritage are one of my consultancy customers. I do quite a lot of training, technical writing and consultancy on fire systems (some of you will remember the sprinkler

Re: Clean agent questions

2010-03-05 Thread Stewart Kidd
Can't comment on whether drives are sealed but when FM200 is discharged during a fire it produces a residue which is corrosive - let me know if you want a citation for this. Stewart Kidd On 5 Mar 2010, at 13:27, craig.pr...@ch2m.com craig.pr...@ch2m.com wrote: They do leave some residue

Re: Clean agent questions

2010-03-05 Thread Stewart Kidd
Geoff Inergen will not leave a residue as its component gases are all inert. It's only the chemical gases which can do this as when they discharge under some circumstances there is a breakdown of their constituents in the presence of heat and products of combstion. Stewart On 5 Mar 2010, at

Re: Clean agent questions

2010-03-05 Thread Stewart Kidd
-Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Stewart Kidd Sent: Friday, March 05, 2010 8:12 AM To: sprinklerforum@firesprinkler.org Subject: Re: Clean agent questions Can't comment on whether drives

Re: Clean agent questions

2010-03-05 Thread Stewart Kidd
...@firesprinkler.org] On Behalf Of Stewart Kidd Sent: Friday, March 05, 2010 8:12 AM To: sprinklerforum@firesprinkler.org Subject: Re: Clean agent questions Can't comment on whether drives are sealed but when FM200 is discharged during a fire it produces a residue which is corrosive - let me know

Re: CLEAN COMBUSTION RESEARCH CENTER

2010-06-13 Thread Stewart Kidd
Haji Mabrouk ! Whatever you do, avoid the FM 200 as the gas decomposes during firefighting to generate hydrogen fluoride which is highly corrosive. The HF will form a layer on all exposed surfaces and equipment and quickly attack most metals and materials like printed circuit boards. I have

Re: Another fine piece of journalism - NOT!

2010-08-23 Thread Stewart Kidd
responding fire truck had been carrying a wedge or sprinkler stopper ? Stewart Kidd Cambridge, England On 23 Aug 2010, at 14:07, George Church wrote: Careful- the $1,000 is the damage from the FIRE. Damage from the sprinkler is what was EXTENSIVE. They'd have been so much further ahead

Re: Another fine piece of journalism - NOT!

2010-08-23 Thread Stewart Kidd
that there are still people out there who should know better when commenting on the effects of a sprinkler operation. Wouldn't it have been nice if the first responding fire truck had been carrying a wedge or sprinkler stopper ? Stewart Kidd Cambridge, England On 23 Aug 2010, at 14:07, George Church wrote

Re: Court Strikes Down Pennsylvania Builders Association's Bid to Keep

2010-08-26 Thread Stewart Kidd
Nice to see common sense as well as jurisprudence triumphing - unlike the present position in the UK where the coalition Conservative/Liberal Democrat administration is proposing to repeal local regulations in several counties which permit the local fire authorities to require sprinklers in

Re: Cooling tower basin as water storage for fire pump

2010-12-29 Thread Stewart Kidd
Craig Extreme care is needed for use of cooling water in fire systems. I've had several problems with power stations in developing countries where this has initially seemed an attractive and cost-effective option. Not only are there serious potential problems with the chemicals used in the

Re: Electrical Rooms

2011-01-27 Thread Stewart Kidd
I'm with Craig - having spent 10 years managing fire protection for two electrical utility operations in my sordid youth, this is a subject dear to my heart. Despite trying for 25 years I've not been able to find any evidence of anyone having been injured or killed by the conductivity of water

Re: Electrical Rooms

2011-01-28 Thread Stewart Kidd
Systems L.L.C. 318-387-1134 Voice 318-816-1087 Mobile 318-387-1163 Facsimile m...@norredfire.com -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum- boun...@firesprinkler.org] On Behalf Of Stewart Kidd Sent: Thursday, January 27, 2011 4:59 PM

Sprinkler Law for Homes is Approved by Welsh Parliament

2011-02-16 Thread Stewart Kidd
to have such a law. More on: http://www.bbc.co.uk/news/uk-wales-12477983 Best wishes to all Stewart Stewart Kidd Secretary General British Automatic Fire Sprinkler Association Ltd Registered in England in 1974: No 01194637 as a company limited by guarantee Richmond House, Broad Street, Ely CB7

Re: System Area Size

2011-02-23 Thread Stewart Kidd
installations. This equals 59,000 square feet. Regards Stewart Stewart Kidd Secretary General British Automatic Fire Sprinkler Association Ltd Registered in England in 1974: No 01194637 as a company limited by guarantee Richmond House, Broad Street, Ely CB7 4AH Tel 01353 659187, Fax 01353 19

Re: System Area Size

2011-02-23 Thread Stewart Kidd
Thom Excellent point - in the UK at least, insurers are the AHJ on most industrial and warehouse occupancies as our building regs on large warehouses do not kick in until you get to 20,000m2 (ie 215,000 sq ft.) Stewart On 23 Feb 2011, at 15:50, Thom wrote: Actually I think this could make a

Re: Fertilizer Plant

2011-02-23 Thread Stewart Kidd
Coal dust is very explosive and so is the most common fertiliser, ammonium nitrate. NH4NO3 is commonly used in improvised explosive devices - often with diesel oil as a binder and enhancer. used to be known as Co-op Mixture in N Ireland. Stewart On 23 Feb 2011, at 22:12, Todd Williams wrote:

Re: Fertilizer Plant

2011-02-23 Thread Stewart Kidd
Coal is crushed in power stations by ball mills and is then blown into boilers by forced draft fans to be burnt like oil. I spent 10 years in power gen and used to be a member of NFPA 850 and I have never heard of non combustible coal. The coal which someone mentioned as being spontaneously

Re: Fertilizer Plant

2011-02-23 Thread Stewart Kidd
in this transmission or any of its attachments without separate authentication of its authenticity or approval. If you have received this in error I apologize please notify me so I can correct my records. Thank you for your cooperation. -Original Message- From: Stewart Kidd

Re: pump work, 2 die when tank collapses

2011-04-11 Thread Stewart Kidd
Todd We had one in the UK in March - not caused by freezing for sure. Tank was 22 years old - it's the first I had heard of although I am aware of a 5 million gall make up water tank in an eastern European power station which burst killing 38 people. The tank was only 8 years old. Stewart

Re: pump work, 2 die when tank collapses

2011-04-11 Thread Stewart Kidd
that this is in common use for any kind of incident which results in an escape. 'collapse' has its own subtext as does 'rupture'. Perhaps we need a euphemism that won't get the insurers and lawyers too excited ? Stewart On 11 Apr 2011, at 15:46, Stewart Kidd wrote: Todd We had one in the UK in March

Re: Watermist for 66kv Transformers

2011-04-12 Thread Stewart Kidd
Robert Assuming that the tx are outdoors then there is a real concern that the flux density needed to achieve extinction could be affected by air movement. While I'd like to think that mist would be entirely suitable for this purpose I have personal reservations - especially as one of the

Re: Watermist for 66kv Transformers

2011-04-12 Thread Stewart Kidd
Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Stewart Kidd Sent: Monday, April 11, 2011 11:59 PM To: sprinklerforum@firesprinkler.org Subject: Re: Watermist for 66kv Transformers Robert Assuming that the tx