[Sprinklerforum] Re: NFPA 13R residential system - Exposed CPVC

2024-04-26 Thread Greg McGahan
Dapr, The Installation Guidelines of the CPVC will give you the criteria for installing CPVC exposed rather than 13R. Greg McGahan Genesis Fire Services, LLC. From: Dapr Jones Sent: Friday, April 26, 2024 10:57 AM To: Discussion list on issues relating

[Sprinklerforum] NFPA 13R residential system - Exposed CPVC

2024-04-26 Thread Dapr Jones
A multi-family fit up project will have existing to remain upper floor and new first floor apt. units. Currently the building is not sprinkled and will have a new sprinkler system. The contractor wants to run the new sprinkler pipe exposed using CPVC in the existing upper level units. NFPA 13R

[Sprinklerforum] Re: CPVC Exposed

2023-05-31 Thread Rick Matsuda
n.com > www.FergusonFire.com > > From: Brett Peters > Sent: Tuesday, May 30, 2023 2:01 PM > To: Discussion list on issues relating to automatic fire sprinklers > > Subject: [Sprinklerforum] Re: CPVC Exposed > > In these situations I always go back to the GC or build

[Sprinklerforum] Re: CPVC Exposed

2023-05-31 Thread matthew.willis1
.com/> From: Brett Peters Sent: Tuesday, May 30, 2023 2:01 PM To: Discussion list on issues relating to automatic fire sprinklers Subject: [Sprinklerforum] Re: CPVC Exposed In these situations I always go back to the GC or building owner, project was bid to code and there was no d

[Sprinklerforum] Re: CPVC Exposed

2023-05-30 Thread Rick Matsuda
To: Discussion list on issues relating to automatic fire sprinklers > > Subject: [Sprinklerforum] Re: CPVC Exposed > > You can hang me out to dry if you wish but I would agree with the AHJ about > the isolation valves at the bottom of the risers. > > The only purpose of

[Sprinklerforum] Re: CPVC Exposed

2023-05-30 Thread Travis Mack
lating to automatic fire sprinklers Subject: [Sprinklerforum] Re: CPVC Exposed You can hang me out to dry if you wish but I would agree with the AHJ about the isolation valves at the bottom of the risers. The only purpose of an isolation valve is to shutoff the riser for repairs so it needs a

[Sprinklerforum] Re: CPVC Exposed

2023-05-30 Thread Rick Matsuda
Can you wrap the exposed pipe with fireproofing or find a spray-on product that is compatible with CPVC? Rick Matsuda > On May 30, 2023, at 10:01 AM, Brett Peters wrote: > >  > In these situations I always go back to the GC or building owner, project was &

[Sprinklerforum] Re: CPVC Exposed

2023-05-30 Thread Fpdcdesign
If you are only talking about 1 or 2 closets, it would probably just be better to swap it out for a 1’ piece of 1” steel pipe with an elbow , transition to the CPVC in the neighboring room and walk away. > > On May 30, 2023 at 3:52 PM, mail

[Sprinklerforum] Re: CPVC Exposed

2023-05-30 Thread Mike Morey
fax 260.487.7991 email mmo...@shambaugh.com [cid:image001.png@01D99310.B44E2400] From: Brett Peters Sent: Tuesday, May 30, 2023 4:01 PM To: Discussion list on issues relating to automatic fire sprinklers Subject: [Sprinklerforum] Re: CPVC Exposed In these situations I always go back to th

[Sprinklerforum] Re: CPVC Exposed

2023-05-30 Thread Brett Peters
nt to push another issue with them, but: > > > > Is it permissible to install exposed CPVC in a mechanical closet of ±40 sq > ft? Light hazard, the piping can be installed exposed provided that > certain criteria are met with sprinklers, spacing, etc. The listings go on > to state

[Sprinklerforum] CPVC Exposed

2023-05-30 Thread Travis Mack
is the only one that sees how the standard is correctly interpreted. So, it is likely a mute point to push another issue with them, but: Is it permissible to install exposed CPVC in a mechanical closet of ±40 sq ft? Light hazard, the piping can be installed exposed provided that certain criteria

[Sprinklerforum] Re: [EXTERNAL] Re: Hydraulic Calculations for CPVC - Tees - Straight-through Flow

2022-12-12 Thread Kyle . Montgomery
Thank you guys. That answers it. From: J H Sent: Monday, December 12, 2022 9:02 AM To: Discussion list on issues relating to automatic fire sprinklers Subject: [EXTERNAL] [Sprinklerforum] Re: Hydraulic Calculations for CPVC - Tees - Straight-through Flow A little more clarification

[Sprinklerforum] Re: Hydraulic Calculations for CPVC - Tees - Straight-through Flow

2022-12-12 Thread J H
A little more clarification to Taylor's response: It's only req'd for a 13D system IF you're using the simplified calculation method using only the static pressure. 13D then points you to their charts for friction loss which includes CPVC tees on the run. If you're calculating a 13D system using

[Sprinklerforum] Re: Hydraulic Calculations for CPVC - Tees - Straight-through Flow

2022-12-12 Thread Taylor Schumacher
for CPVC - Tees - Straight-through Flow NFPA 13 clearly states that "fitting loss for straight-through flow in a tee or cross shall not be included". But some of the manufacturer's data for CPVC products specifically lists equivalent lengths for these fittings (tee on the ru

[Sprinklerforum] Hydraulic Calculations for CPVC - Tees - Straight-through Flow

2022-12-12 Thread Kyle . Montgomery
NFPA 13 clearly states that "fitting loss for straight-through flow in a tee or cross shall not be included". But some of the manufacturer's data for CPVC products specifically lists equivalent lengths for these fittings (tee on the run) as well as for couplings. So, are those

[Sprinklerforum] Re: [EXTERNAL] Re: Nitrogen and CPVC

2022-04-22 Thread Matt Grise
Ah… right! So is the goal to nitrogen purge when the system is drained? Matt From: Kyle.Montgomery Sent: Thursday, April 21, 2022 5:10 PM To: Matt Grise ; sprinklerforum@lists.firesprinkler.org Subject: RE: [EXTERNAL] [Sprinklerforum] Re: Nitrogen and CPVC It’s a WET system. So, no, I don’t

[Sprinklerforum] Re: Nitrogen and CPVC

2022-04-21 Thread Matt Grise
klerforum@lists.firesprinkler.org> Subject: [Sprinklerforum] Nitrogen and CPVC I am looking for thoughts on nitrogen corrosion for a wet system that has both CPVC and steel pipes. I read most manufacturers only allow air or nitrogen at no more than 15 PSI for pre-testing only. So I am wondering how nitrogen

[Sprinklerforum] Re: Nitrogen and CPVC

2022-04-21 Thread Steve Leyton
We know vaping in CA. But seriously folks... I wouldn't take my (or Cecil's, no offense) opinion for more than you're paying for it with regard to CPVC compatibility. Reach out to Lubrizol or Spears, highest level tech support you can connect with. Steve From: Sprinkler Academy - C Bilbo

[Sprinklerforum] Re: Nitrogen and CPVC

2022-04-21 Thread Sprinkler Academy - C Bilbo
Joe, Filling the system with nitrogen prior to filling with water would permit "sparging" of the N2 with the H2O. You could very well leave 14 psi of nitrogen on the CPVC system prior to filling with water. This would achieve an added protective for your metal piping. But, yo

[Sprinklerforum] Re: Nitrogen and CPVC

2022-04-21 Thread Joe Burtell
Good question. Sorry, thoughts on applying it to CPVC. Best regards, *Joe Burtell, SET, CFPS* [image: Burtell Fire_Small] Phone | Fax | Mobile| Text *406-204-4653 <++1-406-204-4653>* 116 N. 11th Street | Billings, MT 59101 Email: j...@burtellfire.com Web Site: http://www.burtellfi

[Sprinklerforum] Re: Nitrogen and CPVC

2022-04-21 Thread Steve Leyton
Are you seeking thoughts on applying it to CPVC or thoughts on the practice of Nitrogen inerting wet systems? Steve From: Joe Burtell Sent: Thursday, April 21, 2022 8:29 AM To: sprinklerforum@lists.firesprinkler.org Subject: [Sprinklerforum] Nitrogen and CPVC I am looking for thoughts

[Sprinklerforum] Nitrogen and CPVC

2022-04-21 Thread Joe Burtell
I am looking for thoughts on nitrogen corrosion for a wet system that has both CPVC and steel pipes. I read most manufacturers only allow air or nitrogen at no more than 15 PSI for pre-testing only. So I am wondering how nitrogen pressure can be used at all when you have a wet CPVC system? Best

RE: [External]RE: Exposed CPVC pipe and residential upright sprinklers

2022-01-21 Thread Kyle.Montgomery via Sprinklerforum
SHOULD or SHALL? Mwahahahaha... -Original Message- From: Sprinklerforum On Behalf Of Dewayne Martinez via Sprinklerforum Sent: Friday, January 21, 2022 2:17 PM To: sprinklerforum@lists.firesprinkler.org Cc: Dewayne Martinez Subject: [EXTERNAL] RE: [External]RE: Exposed CPVC pipe

RE: [External]RE: Exposed CPVC pipe and residential upright sprinklers

2022-01-21 Thread Dewayne Martinez via Sprinklerforum
@lists.firesprinkler.org Cc: Matt Grise Subject: [External]RE: Exposed CPVC pipe and residential upright sprinklers They are a newer product... maybe have not been added to the install guide yet? Have you called a manufacturer? Matt Grise Alliance Fire Protection 130 w 9th Ave North Kansas City, MO 913.526.7443

RE: Exposed CPVC pipe and residential upright sprinklers

2022-01-21 Thread Matt Grise via Sprinklerforum
Sprinklerforum Date: 1/21/22 12:34 PM (GMT-06:00) To: sprinklerforum@lists.firesprinkler.org Cc: Dewayne Martinez Subject: Exposed CPVC pipe and residential upright sprinklers I don't see an option for using residential upright sprinkler on exposed CPVC pipe in any of the manufactures installation

RE: [External]RE: Exposed CPVC pipe and residential upright sprinklers

2022-01-21 Thread Dewayne Martinez via Sprinklerforum
upright sprinklers with exposed CPVC. Thank you,   Dewayne Martinez Fire Protection Design Manager   TOTAL Mechanical Building Integrity W234 N2830 Paul Rd. Pewaukee, WI  53072 dmarti...@total-mechanical.com Ph:  262-522-7110 Cell: 414-406-5208 http://www.total-mechanical.com

RE: Exposed CPVC pipe and residential upright sprinklers

2022-01-21 Thread Cary Webber via Sprinklerforum
and one wouldn't use uprights? I don't know but am curious to see where this goes. Definitely a question for the CPVC manufacturers though. Cary Webber CFPS Director, Technical Services Reliable Automatic Sprinkler Co., Inc. 1470 Smith Grove Road, Liberty, SC  29657 Tel: 864-843-5161

Exposed CPVC pipe and residential upright sprinklers

2022-01-21 Thread Dewayne Martinez via Sprinklerforum
I don't see an option for using residential upright sprinkler on exposed CPVC pipe in any of the manufactures installation manuals. Am I missing something or is QR uprights my only option? Thank you, Dewayne Martinez Fire Protection Design Manager TOTAL Mechanical Building Integrity W234

RE: CPVC Fitting

2021-11-09 Thread Scott Futrell via Sprinklerforum
@lists.firesprinkler.org Cc: r...@westernslopefire.com Subject: RE: CPVC Fitting Look at spears data Flame guard fittings -Original Message- From: Sprinklerforum On Behalf Of Taylor Schumacher via Sprinklerforum Sent: Tuesday, November 09, 2021 2:06 PM To: sprinklerforum@lists.firesprinkler.org Cc

RE: CPVC Fitting

2021-11-09 Thread Mike Morey via Sprinklerforum
klerforum Sent: Tuesday, November 9, 2021 4:06 PM To: sprinklerforum@lists.firesprinkler.org Cc: Taylor Schumacher Subject: RE: CPVC Fitting BE ADVISED - This email originated outside EMCOR. Seems silly that a threaded female x threaded female fitting in CPVC would even exist? Taylor S

RE: CPVC Fitting

2021-11-09 Thread rix rixford via Sprinklerforum
Look at spears data Flame guard fittings -Original Message- From: Sprinklerforum On Behalf Of Taylor Schumacher via Sprinklerforum Sent: Tuesday, November 09, 2021 2:06 PM To: sprinklerforum@lists.firesprinkler.org Cc: Taylor Schumacher Subject: RE: CPVC Fitting Seems silly

RE: CPVC Fitting

2021-11-09 Thread Taylor Schumacher via Sprinklerforum
Seems silly that a threaded female x threaded female fitting in CPVC would even exist? Taylor Schumacher -Original Message- From: Sprinklerforum On Behalf Of Scott Futrell via Sprinklerforum Sent: Tuesday, November 09, 2021 2:18 PM To: sprinklerforum@lists.firesprinkler.org Cc

Re: CPVC Drops in Seismic Areas

2021-03-02 Thread BRUCE VERHEI via Sprinklerforum
in restrooms. No problem. It’s not only allowed. With the flexibility of CPVC it just should be a rare problem. The other? No clearance needed in rated GWB walls. Not a problem. Did we get all the broken GWB caused by metallic pipe bouncing around? Hahaha. Good one. Best. Bruce V. > On 03/02/2

Re: [EXTERNAL] Re: CPVC Drops in Seismic Areas

2021-03-02 Thread Michael.Spatafore via Sprinklerforum
DwICAg=wn3mZQLIuInh2ClcJ0_DIA=GIS2RCKGscVLbU61DuFzgH3FhC3Vepu3l9fL3Gu7k2M=kET3jiqTJ6JW_ld5XkRiekWZHQ2WimpLjdKEFra2uCw=NN_TTIhrWT1Cy0JBrjosYNByYYG0-bqvGZL9_wr9tTQ= >> > >> <#m_-3296756546440371397_DAB4FAD8-2DD7-40BB-A1B8-4E2AA1F9FDF2> >> >> On Tue, Mar 2, 2021 at 10:39 AM Kyle.Montgomery

Re: CPVC Drops in Seismic Areas

2021-03-02 Thread J H via Sprinklerforum
-email?utm_medium=email_source=link_campaign=sig-email_content=webmail_term=link> > <#m_-3296756546440371397_DAB4FAD8-2DD7-40BB-A1B8-4E2AA1F9FDF2> > > On Tue, Mar 2, 2021 at 10:39 AM Kyle.Montgomery via Sprinklerforum < > sprinklerforum@lists.firesprinkler.org> wrote: >

Re: CPVC Drops in Seismic Areas

2021-03-02 Thread J H via Sprinklerforum
inklerforum < sprinklerforum@lists.firesprinkler.org> wrote: > When installing a CPVC system in a seismic area (area where seismic > bracing is required) are there any special considerations needed for the > drops to sprinkler heads? In the past, with steel pipe systems we've ofte

CPVC Drops in Seismic Areas

2021-03-02 Thread Kyle.Montgomery via Sprinklerforum
When installing a CPVC system in a seismic area (area where seismic bracing is required) are there any special considerations needed for the drops to sprinkler heads? In the past, with steel pipe systems we've often utilized flexible sprinkler connections to avoid any concern about differential

Re: CPVC EQ Bracing - 2 hole straps and another question

2021-01-03 Thread cw bamford via Sprinklerforum
Ken W. did this article a couple years ago. Afocn/Anvil and Tolco/Eaton have some braces. https://sprinklerage.com/seismic-bracing-of-cpvc-pipe/ "ABOUT THE AUTHOR: Ken Wagoner, C.F.P.E., C.W.B.S.P, S.E.T. " Seismic Bracing of CPVC Pipe August 29, 2018 please note comments: IMPORT

Re: CPVC EQ Bracing - 2 hole straps and another question

2021-01-02 Thread John Denhardt via Sprinklerforum
Scott makes a great point. CPVC piping has to be free to move. Thanks, John John August Denhardt, PE *Vice President, Engineering and Technical Services* *American Fire Sprinkler Association* m: p: 301-343-1457 214-349-5965 ext 121 w: firesprinkler.org <https://www.facebook.

Re: CPVC EQ Bracing - 2 hole straps and another question

2020-12-31 Thread Jeff Normand via Sprinklerforum
straps used to secure CPVC acted as seismic > bracing? I don't know where I've heard that and couldn't find anything in > the standard. Is this correct? > > Also, if you have a 1"x8'-6" riser to a single horizontal sidewall > sprinkler would that technically be an 'armove

RE: CPVC EQ Bracing - 2 hole straps and another question

2020-12-30 Thread Scott Futrell via Sprinklerforum
Just remember to allow for thermal expansion and contraction. It can get very ugly if the CPVC is restrained and thermal expansion and contraction has not been appropriately allowed for. This applies when a building is warm in the summer during construction and then air conditioning is turned

RE: CPVC EQ Bracing - 2 hole straps and another question

2020-12-30 Thread Bob Knight via Sprinklerforum
Personally, I would provide the restraint and be done. As Travis said, apply the less than 6" criteria and you should be good with the CPVC hangers. 9.3.5.8.5 Four-way bracing shall not be required where risers penetrate intermediate floors in multistory buildings where the clearance

Re: CPVC EQ Bracing - 2 hole straps and another question

2020-12-30 Thread J H via Sprinklerforum
December 30, 2020 12:28 PM > To: sprinklerforum@lists.firesprinkler.org > Cc: Matthew J Willis > Subject: RE: CPVC EQ Bracing - 2 hole straps and another question > > To my knowledge, the 2 hole strap is listed as a hanger only. Not for > seismic. > > The second question is a

Re: CPVC EQ Bracing - 2 hole straps and another question

2020-12-30 Thread Travis Mack via Sprinklerforum
vorite ferguson.com features. Apple iOS devices or Android devices** From: Sprinklerforum on behalf of Matthew J Willis via Sprinklerforum Sent: Wednesday, December 30, 2020 12:27:54 PM To: sprinklerforum@lists.firesprinkler.org Cc: Matthew J Willis Subject: RE: CPVC EQ B

RE: CPVC EQ Bracing - 2 hole straps and another question

2020-12-30 Thread Bob Knight via Sprinklerforum
...@lists.firesprinkler.org] On Behalf Of Matthew J Willis via Sprinklerforum Sent: Wednesday, December 30, 2020 12:28 PM To: sprinklerforum@lists.firesprinkler.org Cc: Matthew J Willis Subject: RE: CPVC EQ Bracing - 2 hole straps and another question To my knowledge, the 2 hole strap is listed as a hanger only

RE: CPVC EQ Bracing - 2 hole straps and another question

2020-12-30 Thread Matthew J Willis via Sprinklerforum
H via Sprinklerforum Sent: Wednesday, December 30, 2020 12:13 PM To: sprinklerforum@lists.firesprinkler.org Cc: J H Subject: CPVC EQ Bracing - 2 hole straps and another question Hello, I thought that two hole straps used to secure CPVC acted as seismic bracing? I don't know where I've heard that a

CPVC EQ Bracing - 2 hole straps and another question

2020-12-30 Thread J H via Sprinklerforum
Hello, I thought that two hole straps used to secure CPVC acted as seismic bracing? I don't know where I've heard that and couldn't find anything in the standard. Is this correct? Also, if you have a 1"x8'-6" riser to a single horizontal sidewall sprinkler would that technically be a

RE: [EXTERNAL] RE: Hangers for CPVC Pipe going through TGI Joists

2020-09-30 Thread Kyle.Montgomery via Sprinklerforum
Some of you guys mentioned bushings or "other method to prevent chafing". Can we elaborate on that? I've seen bushings used where CPVC is run in a wall and passes through metal studs, but I don't think I've seem them installed in this scenario. Is that really a requirement

RE: Hangers for CPVC Pipe going through TGI Joists

2020-09-30 Thread Bob Knight via Sprinklerforum
forum Sent: Wednesday, September 30, 2020 6:39 AM To: Sprinkler Forum Cc: Mike Hairfield Subject: Hangers for CPVC Pipe going through TGI Joists The TGI Joists are spaced 16" apart, does NFPA-13 require hangers on the CPVC pipe since the TGI joists are supporting

RE: Re: Hangers for CPVC Pipe going through TGI Joists

2020-09-30 Thread Pritchard, John via Sprinklerforum
e: Hangers for CPVC Pipe going through TGI Joists Agree - the structure is the support. Restraints or chafing protectuion might be needed. Thanks, John John August Denhardt, PE *Vice President, Engineering and Technical Services* *American Fire Sprinkler Association* m: p: 301-343-1457 214-349-5965

Re: Hangers for CPVC Pipe going through TGI Joists

2020-09-30 Thread John Denhardt via Sprinklerforum
e to side movement expected. > > R/ > Matt > > -Original Message- > From: Sprinklerforum On > Behalf Of Mike Hairfield via Sprinklerforum > Sent: Wednesday, September 30, 2020 6:39 AM > To: Sprinkler Forum > Cc: Mike Hairfield > Subject: Hangers for CPVC Pipe goi

RE: Hangers for CPVC Pipe going through TGI Joists

2020-09-30 Thread Matthew J Willis via Sprinklerforum
To: Sprinkler Forum Cc: Mike Hairfield Subject: Hangers for CPVC Pipe going through TGI Joists The TGI Joists are spaced 16" apart, does NFPA-13 require hangers on the CPVC pipe since the TGI joists are supporting the pipe? Mike ___ Sprinkler

Hangers for CPVC Pipe going through TGI Joists

2020-09-30 Thread Mike Hairfield via Sprinklerforum
The TGI Joists are spaced 16" apart, does NFPA-13 require hangers on the CPVC pipe since the TGI joists are supporting the pipe? Mike ___ Sprinklerforum mailing list Sprinklerforum@lists.firesprinkler.org http://lists.firesprinkler.org/listinf

RESTRAINT of CPVC Branch Lines

2019-05-30 Thread Matthew J Willis
Any edition 10 and after..., We have a situation where we are using hangers less than 6" on our entire system. Yes, we comply with the other items. Since this omits Lateral bracing, I was looking into restraints. Are the spacing requirements for Restraints still in play? Or does the reduced

Re: Grooved Coupling for CPVC

2019-04-04 Thread Timothy Goins
My CPVC documentation states to user only flex couplings, not standard rigid. And I will give them one heart, and I will put a new spirit within you; and I will take the stony heart out of their flesh, and will give them an heart of flesh Eze 11:19 > On Apr 4, 2019, at 11:24 AM, Dale Wing

RE: Grooved Coupling for CPVC

2019-04-04 Thread Mike Stossel
e: 973-670-2627 m...@knssprinkler.com<mailto:m...@knssprinkler.com> From: Sprinklerforum On Behalf Of Mike Hairfield Sent: Thursday, April 4, 2019 12:11 PM To: Sprinklerforum Subject: Grooved Coupling for CPVC I have a local AHJ asking for a data sheet that states that a standard grooved

RE: Grooved Coupling for CPVC

2019-04-04 Thread Prahl, Craig/GVL
Blazemaster has a grooved CPVC adapter. Contact the Viking Rep and ask them what coupling is approved for that fitting. Victaulic also has a line of grooved CPVC fittings but these don't appear to be for Sprinkler systems. Craig Prahl | Jacobs | Group Lead - Fire Protection | 864.676.5252

RE: Grooved Coupling for CPVC

2019-04-04 Thread Dale Wingard
Try contacting your CPVC manufacturer and they should be able to provide you with a statement that the grooved adapter was made to be used with a standard coupling. Dale F. Wingard, SET Designer Commercial/Marine Division NICET IV #76284 Water-based Systems Hiller Systems A Division

RE: Grooved Coupling for CPVC

2019-04-04 Thread tstone52
Check out Rasco. Cover sheet indicates UL Listing. From: Sprinklerforum On Behalf Of Mike Hairfield Sent: Thursday, April 4, 2019 12:19 PM To: sprinklerforum@lists.firesprinkler.org Subject: Re: Grooved Coupling for CPVC Done that and I could not find anyone that has coupling

Re: Grooved Coupling for CPVC

2019-04-04 Thread Mike Hairfield
for CPVC Check with your supplier or down load their grooved literature. Regards, G. Tim Stone G. Tim Stone Consulting, LLC NICET Level III Engineering Technician Fire Protection Sprinkler Design and Consulting Services 117 Old Stage Rd. - Essex Jct., VT. 05452 CELL: (802) 373-0638

RE: Grooved Coupling for CPVC

2019-04-04 Thread tstone52
TEL: (802) 434-2968 <mailto:tston...@comcast.net> tston...@comcast.net From: Sprinklerforum On Behalf Of Mike Hairfield Sent: Thursday, April 4, 2019 12:11 PM To: Sprinklerforum Subject: Grooved Coupling for CPVC I have a local AHJ asking for a data sheet that

Grooved Coupling for CPVC

2019-04-04 Thread Mike Hairfield
I have a local AHJ asking for a data sheet that states that a standard grooved coupling is U/L listed and/or FM approved for that use. Have any of you guys ever seen this? Thanks, Mike ___ Sprinklerforum mailing list

Re: CPVC pipe passing thru ordinary interstitial space

2018-12-13 Thread Dewayne Martinez
I ran into this recently and it was pointed out to me that the floor assembly itself was UL rated fire assembly and if I ran the CPVC in the interstitial space it would have to comply with the OH rules of 400sf or less. I thought the same at first about it being protected per LH that it would

Re: CPVC pipe passing thru ordinary interstitial space

2018-12-13 Thread Steve Leyton
How are the sprinklers supplied in the Ordinary Hazard compartments below? In earlier editions of NFPA 13, you cannot run CPVC piping to Ordinary Hazard sprinklers covering areas greater than 400 ft². (For 2019 there is an allowance for up to 1000 ft² in private residential parking garages

Re: CPVC pipe passing thru ordinary interstitial space

2018-12-12 Thread off...@afpfiresprinkler.com
I missed to explain this part…. Thanks Steve. The concealed space will be sprinklered and yes I am proposing to install the sprinklers in the concealed space of the CPVC piping an as per the listing for CPVC pipe (i.e. piping max 6” above ceiling or insulation etc.) I’m also pointing to NFPA

RE: CPVC pipe passing thru ordinary interstitial space

2018-12-12 Thread Steve Leyton
Is the interstitial space combustible? If so, are you proposing to sprinkler the space with sprinklers that satisfy the listing limitations of the CPVC? Does the CPVC also supply the OH space below? [Steve Signature (3)] From: Sprinklerforum [mailto:sprinklerforum-boun

CPVC pipe passing thru ordinary interstitial space

2018-12-12 Thread off...@afpfiresprinkler.com
I have a job that’s a 2 story building with an A truss roof, 1st floor is retail and 2nd floor is residential, the entire building is being sprinklered as per NFPA 13. We want to install sidewalls with multiple CPVC risers and tie everything in 1st floor interstitial space, Question

Re: NFPA 13R - Garages - CPVC

2018-08-09 Thread Ben Young
*Sent:* Wednesday, August 08, 2018 1:02 PM >> >> >> *To:* sprinklerforum@lists.firesprinkler.org >> *Subject:* RE: NFPA 13R - Garages - CPVC >> >> >> >> *Your description of accessible by more than one dwelling unit is exactly >> the way I view it.

Re: NFPA 13R - Garages - CPVC

2018-08-08 Thread Ron Greenman
> > > *From:* Sprinklerforum [mailto: > sprinklerforum-boun...@lists.firesprinkler.org] *On Behalf Of *MFP > Design, LLC > *Sent:* Wednesday, August 08, 2018 1:02 PM > > > *To:* sprinklerforum@lists.firesprinkler.org > *Subject:* RE: NFPA 13R - Garages - CPVC > > >

RE: NFPA 13R - Garages - CPVC

2018-08-08 Thread Steve Leyton
] On Behalf Of MFP Design, LLC Sent: Wednesday, August 08, 2018 1:02 PM To: sprinklerforum@lists.firesprinkler.org Subject: RE: NFPA 13R - Garages - CPVC Your description of accessible by more than one dwelling unit is exactly the way I view it. But, I got shot down by the AHJ. Their response was: “What

RE: NFPA 13R - Garages - CPVC

2018-08-08 Thread Steve Leyton
it with phosphorus … or are they? SML From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of MFP Design, LLC Sent: Wednesday, August 08, 2018 1:02 PM To: sprinklerforum@lists.firesprinkler.org Subject: RE: NFPA 13R - Garages - CPVC Your description of accessible by more than

RE: NFPA 13R - Garages - CPVC

2018-08-08 Thread MFP Design, LLC
n Behalf Of Steve Leyton Sent: Wednesday, August 8, 2018 1:00 PM To: sprinklerforum@lists.firesprinkler.org Subject: RE: NFPA 13R - Garages - CPVC 13. My point is only to reinforce the intent of the standard(s) and also that the manufacturers will warrant the application. The word that’s in

RE: NFPA 13R - Garages - CPVC

2018-08-08 Thread Steve Leyton
it’s the intent of the book and the listing to allow the CPVC. SL From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Ben Young Sent: Wednesday, August 08, 2018 12:49 PM To: sprinklerforum@lists.firesprinkler.org Subject: Re: NFPA 13R - Garages - CPVC Just

Re: NFPA 13R - Garages - CPVC

2018-08-08 Thread Ben Young
extreme > measure. One jurisdiction (City of San Diego) has flat-out mandated steel > pipe in the those applications. Going forward, I hope this expands the > application for CPVC to at least homogenize the bill of materials in > attached residential projects. > > >

RE: NFPA 13R - Garages - CPVC

2018-08-08 Thread Steve Leyton
AHJs in the southwest requiring double layers of Type ‘X’ and other fairly extreme measure. One jurisdiction (City of San Diego) has flat-out mandated steel pipe in the those applications. Going forward, I hope this expands the application for CPVC to at least homogenize the bill of materials

RE: NFPA 13R - Garages - CPVC

2018-08-08 Thread MFP Design, LLC
This sounds good to me. I have sent in for an AFSA informal interp just to get a bit more ammo. This project has both 13R and 13 buildings on it. So, the 13 buildings, I will definitely have to go steel, but I’m going to try to get all of the 13R buildings as CPVC. Travis Mack, SET

Re: NFPA 13R - Garages - CPVC

2018-08-08 Thread Fire Design
I would agree with CPVC because of the manufacturer listing. However, if you were using a manufacturer that did not have that verbiage and you were back to your interpretation of 13R I think you are wrong in applying the aggregate for the 400 sq. ft. rule. 13R specifically calls out "

RE: NFPA 13R - Garages - CPVC

2018-08-08 Thread Bob
Travis, Based on the product listing, CPVC is appropriate. Thank you, Bob Knight, CET III 208-318-3057 From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of MFP Design, LLC Sent: Wednesday, August 08, 2018 9:57 AM To: sprinklerforum

RE: NFPA 13R - Garages - CPVC

2018-08-08 Thread Richard Carr
CPVC. Richard M. Carr, SET Project Manager/Design Diboco Fire Sprinklers, Inc. 325 Jackson Loop Road Flat Rock, NC 28731 rich...@diboco.com<mailto:rich...@diboco.com> 828-696-3400 828-696-2288 Fax 828-708-9118 Mobile [cid:image001.jpg@01D2E695.9A38B950] [cid:image002.png@01D2E695.9A

NFPA 13R - Garages - CPVC

2018-08-08 Thread MFP Design, LLC
. The spaces are ≤ 500 sq ft, so 7.2.2.1 allows us to limit the number of calculated sprinklers to all in a compartment to a maximum of 4. We are using QR sprinklers in these garages. Now, here is where the wrinkle comes. Are we permitted to use CPVC above the ceiling in these areas? The ceiling

Re: CPVC Seismic

2017-09-19 Thread Steve Leyton
rforum@lists.firesprinkler.org Subject: RE: CPVC Seismic What city in northern CA is letting you get away with 2013 code? Rocci Cetani III, CET Senior Designer Water-Based Fire Protections Systems Layout, Nicet Level III Northern California Fire Protection Services Inc. 16840 Joleen Way Bldg. A Morgan Hi

RE: CPVC Seismic

2017-09-19 Thread Rocci Cetani 3
8, 2017 8:46 PM To: sprinklerforum@lists.firesprinkler.org Subject: RE: CPVC Seismic Using 2013, and the area of concern will be supported with 2-hole CPVC straps. Thank you, Bob Knight, CET III 208-318-3057 From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.fires

RE: CPVC Seismic

2017-09-19 Thread Rocci Cetani 3
18, 2017 8:27 PM To: sprinklerforum@lists.firesprinkler.org Subject: RE: CPVC Seismic I had to step out for a couple of hours, but I'm back. I'm assuming that I can use the rods less than 6" rule and omit lateral bracing, right? That would leave 4-ways and longitudinal only, correct?

RE: CPVC Seismic

2017-09-18 Thread Bob
Using 2013, and the area of concern will be supported with 2-hole CPVC straps. Thank you, Bob Knight, CET III 208-318-3057 From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Travis Mack Sent: Monday, September 18, 2017 9:43 PM To: b

Re: CPVC Seismic

2017-09-18 Thread Travis Mack
3057 > > From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] > On Behalf Of MFP Design, LLC > Sent: Monday, September 18, 2017 4:31 PM > To: b...@firebyknight.com; sprinklerforum@lists.firesprinkler.org > Subject: RE: CPVC Seismic > > Really no different. I doubt y

RE: CPVC Seismic

2017-09-18 Thread Bob
forum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of MFP Design, LLC Sent: Monday, September 18, 2017 4:31 PM To: b...@firebyknight.com; sprinklerforum@lists.firesprinkler.org Subject: RE: CPVC Seismic Really no different. I doubt you will find longitudinal bracing listed for cpvc. You will

RE: CPVC Seismic

2017-09-18 Thread Rocci Cetani 3
Afcon is the only company with seismic attachments for CPVC Rocci Cetani III, CET Senior Designer Water-Based Fire Protections Systems Layout, Nicet Level III Northern California Fire Protection Services Inc. 16840 Joleen Way Bldg. A Morgan Hill, CA 93037 P-(408) 776-1580 EXT.111 F

RE: CPVC Seismic

2017-09-18 Thread MFP Design, LLC
Really no different. I doubt you will find longitudinal bracing listed for cpvc. You will have to put a short branch (same size as main) perpendicular to the main and brace that with a lateral brace to act as your longitudinal brace on the main. From: Sprinklerforum [mailto:sprinklerforum

CPVC Seismic

2017-09-18 Thread Bob
I'm about to do my first CPVC sway bracing calc's. This is in CA (a first for me as well), north of San Francisco. Are there any special issues that I need to consider, or do I approach this as if it's not much different than if it where steel? Thank you, Bob Knight, CET III 208-318

RE: CPVC: To Move, or Not To Move

2017-07-10 Thread Matthew J Willis
Hey Tom. Yes, some. I have had long attic runs before and I guess that is what I am envisioning. Pipe "breathing" as it were. The listed CPVC hangers allow the pipe to move freely for expansion and contraction. Down south, there are some big temp differences. If we lock i

Re: CPVC: To Move, or Not To Move

2017-07-10 Thread Tom Wellen
Matt, I understand that expansion loops are not that common. A layout usually provides enough offsets and changes in direction where long runs of CPVC pipe are not that common. But, they do happen. Where the straight CPVC run is sufficient length to require an expansion loop, provide bracing

RE: CPVC: To Move, or Not To Move

2017-07-10 Thread Matthew J Willis
urston Sent: Monday, July 10, 2017 9:11 AM To: Matthew J Willis <sprinklerforum@lists.firesprinkler.org> Subject: Re: CPVC: To Move, or Not To Move Hello Matthew, There are several ways shown in the manual about putting in offsets, making a corner, and I think it even shows the sizes n

Re: CPVC: To Move, or Not To Move

2017-07-10 Thread Charles Thurston
of CPVC to expand when we have hard strapped it to wood? Never braced CPVC so more curious than anything. R/ Matt Matthew J. Willis Project Manager Rapid Fire Protection Inc. 1530 Samco Road Rapid City, SD 57702 Office-605.348.2342 Direct Line-605.593.5063 Cell-605.391.2733 Fax

CPVC: To Move, or Not To Move

2017-07-10 Thread Matthew J Willis
Reading the Tech Update got me thinking. What do we do to address the need of CPVC to expand when we have hard strapped it to wood? Never braced CPVC so more curious than anything. R/ Matt Matthew J. Willis Project Manager Rapid Fire Protection Inc.<http://rapidfireinc.com/> 1530 Samc

RE: CPVC earthquake bracing

2017-06-19 Thread Rocci Cetani 3
Monday, June 19, 2017 9:27 AM To: sprinklerforum@lists.firesprinkler.org Subject: Re: CPVC earthquake bracing The primary answer has already been provided but thought it worth adding - unless it has changed recently, you’ll won’t find any longitudinal braces. You’ll be using lateral brac

RE: CPVC earthquake bracing

2017-06-19 Thread Rocci Cetani 3
Subject: Re: CPVC earthquake bracing It is required that you only use sway brace attachments that are listed for CPVC. Like listed solution for hangers and supports, the seismic fittings designed for use with plastic pipe have rolled edges and other features that prevent the damage you're descr

Re: CPVC earthquake bracing

2017-06-19 Thread Roland Huggins
n.com> wrote: > > It is required that you only use sway brace attachments that are listed for > CPVC. Like listed solution for hangers and supports, the seismic fittings > designed for use with plastic pipe have rolled edges and other features that > prevent the damage you're des

Re: CPVC earthquake bracing

2017-06-19 Thread Steve Leyton
It is required that you only use sway brace attachments that are listed for CPVC. Like listed solution for hangers and supports, the seismic fittings designed for use with plastic pipe have rolled edges and other features that prevent the damage you're describing. Check with your local

CPVC earthquake bracing

2017-06-19 Thread Rocci Cetani 3
My installers are trying to install EQ bracing on CPVC for a NFPA 13 system and aren't having much luck..they said that the fittings are gouging and digging into the CPVC (and no they are NOT using impacts) Anyone out there with some experience on bracing CPVC? This project was designed off

RE: CPVC Piping

2017-06-09 Thread Tieman, Joe
Tyco Blazemaster has this information in their IH1900 handbook starting on page 30. You can access the Installation Instructions on CPVC via the Tyco Fire website. Joseph L. Tieman / Director of Sales - U.S. - Water Products / Tyco Fire Protection Products Mobile: +1 412 576 9339 / Fax