Dapr,
The Installation Guidelines of the CPVC will give you the criteria for
installing CPVC exposed rather than 13R.
Greg McGahan
Genesis Fire Services, LLC.
From: Dapr Jones
Sent: Friday, April 26, 2024 10:57 AM
To: Discussion list on issues relating
A multi-family fit up project will have existing to remain upper floor and
new first floor apt. units. Currently the building is not sprinkled and
will have a new sprinkler system.
The contractor wants to run the new sprinkler pipe exposed using CPVC in
the existing upper level units.
NFPA 13R
n.com
> www.FergusonFire.com
>
> From: Brett Peters
> Sent: Tuesday, May 30, 2023 2:01 PM
> To: Discussion list on issues relating to automatic fire sprinklers
>
> Subject: [Sprinklerforum] Re: CPVC Exposed
>
> In these situations I always go back to the GC or build
.com/>
From: Brett Peters
Sent: Tuesday, May 30, 2023 2:01 PM
To: Discussion list on issues relating to automatic fire sprinklers
Subject: [Sprinklerforum] Re: CPVC Exposed
In these situations I always go back to the GC or building owner, project was
bid to code and there was no d
To: Discussion list on issues relating to automatic fire sprinklers
>
> Subject: [Sprinklerforum] Re: CPVC Exposed
>
> You can hang me out to dry if you wish but I would agree with the AHJ about
> the isolation valves at the bottom of the risers.
>
> The only purpose of
lating to automatic fire sprinklers
Subject: [Sprinklerforum] Re: CPVC Exposed
You can hang me out to dry if you wish but I would agree with the AHJ about the
isolation valves at the bottom of the risers.
The only purpose of an isolation valve is to shutoff the riser for repairs so
it needs a
Can you wrap the exposed pipe with fireproofing or find a spray-on product that
is compatible with CPVC?
Rick Matsuda
> On May 30, 2023, at 10:01 AM, Brett Peters wrote:
>
>
> In these situations I always go back to the GC or building owner, project was
&
If you are only talking about 1 or 2 closets, it would probably just be better
to swap it out for a 1’ piece of 1” steel pipe with an elbow , transition to
the CPVC in the neighboring room and walk away.
>
> On May 30, 2023 at 3:52 PM, mail
fax 260.487.7991
email mmo...@shambaugh.com
[cid:image001.png@01D99310.B44E2400]
From: Brett Peters
Sent: Tuesday, May 30, 2023 4:01 PM
To: Discussion list on issues relating to automatic fire sprinklers
Subject: [Sprinklerforum] Re: CPVC Exposed
In these situations I always go back to th
nt to push another issue with them, but:
>
>
>
> Is it permissible to install exposed CPVC in a mechanical closet of ±40 sq
> ft? Light hazard, the piping can be installed exposed provided that
> certain criteria are met with sprinklers, spacing, etc. The listings go on
> to state
is the only one that
sees how the standard is correctly interpreted. So, it is likely a mute point
to push another issue with them, but:
Is it permissible to install exposed CPVC in a mechanical closet of ±40 sq ft?
Light hazard, the piping can be installed exposed provided that certain
criteria
Thank you guys. That answers it.
From: J H
Sent: Monday, December 12, 2022 9:02 AM
To: Discussion list on issues relating to automatic fire sprinklers
Subject: [EXTERNAL] [Sprinklerforum] Re: Hydraulic Calculations for CPVC - Tees
- Straight-through Flow
A little more clarification
A little more clarification to Taylor's response: It's only req'd for a 13D
system IF you're using the simplified calculation method using only the
static pressure. 13D then points you to their charts for friction loss
which includes CPVC tees on the run. If you're calculating a 13D system
using
for CPVC - Tees -
Straight-through Flow
NFPA 13 clearly states that "fitting loss for straight-through flow in a tee or
cross shall not be included". But some of the manufacturer's data for CPVC
products specifically lists equivalent lengths for these fittings (tee on the
ru
NFPA 13 clearly states that "fitting loss for straight-through flow in a tee or
cross shall not be included". But some of the manufacturer's data for CPVC
products specifically lists equivalent lengths for these fittings (tee on the
run) as well as for couplings.
So, are those
Ah… right! So is the goal to nitrogen purge when the system is drained?
Matt
From: Kyle.Montgomery
Sent: Thursday, April 21, 2022 5:10 PM
To: Matt Grise ; sprinklerforum@lists.firesprinkler.org
Subject: RE: [EXTERNAL] [Sprinklerforum] Re: Nitrogen and CPVC
It’s a WET system. So, no, I don’t
klerforum@lists.firesprinkler.org>
Subject: [Sprinklerforum] Nitrogen and CPVC
I am looking for thoughts on nitrogen corrosion for a wet system that has both
CPVC and steel pipes. I read most manufacturers only allow air or nitrogen at
no more than 15 PSI for pre-testing only. So I am wondering how nitrogen
We know vaping in CA.
But seriously folks... I wouldn't take my (or Cecil's, no offense) opinion
for more than you're paying for it with regard to CPVC compatibility. Reach
out to Lubrizol or Spears, highest level tech support you can connect with.
Steve
From: Sprinkler Academy - C Bilbo
Joe,
Filling the system with nitrogen prior to filling with water would permit
"sparging" of the N2 with the H2O. You could very well leave 14 psi of
nitrogen on the CPVC system prior to filling with water. This would achieve an
added protective for your metal piping.
But, yo
Good question. Sorry, thoughts on applying it to CPVC.
Best regards,
*Joe Burtell, SET, CFPS*
[image: Burtell Fire_Small]
Phone | Fax | Mobile| Text *406-204-4653 <++1-406-204-4653>*
116 N. 11th Street | Billings, MT 59101
Email: j...@burtellfire.com
Web Site: http://www.burtellfi
Are you seeking thoughts on applying it to CPVC or thoughts on the practice of
Nitrogen inerting wet systems?
Steve
From: Joe Burtell
Sent: Thursday, April 21, 2022 8:29 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: [Sprinklerforum] Nitrogen and CPVC
I am looking for thoughts
I am looking for thoughts on nitrogen corrosion for a wet system that has
both CPVC and steel pipes. I read most manufacturers only allow air or
nitrogen at no more than 15 PSI for pre-testing only. So I am wondering how
nitrogen pressure can be used at all when you have a wet CPVC system?
Best
SHOULD or SHALL?
Mwahahahaha...
-Original Message-
From: Sprinklerforum On Behalf
Of Dewayne Martinez via Sprinklerforum
Sent: Friday, January 21, 2022 2:17 PM
To: sprinklerforum@lists.firesprinkler.org
Cc: Dewayne Martinez
Subject: [EXTERNAL] RE: [External]RE: Exposed CPVC pipe
@lists.firesprinkler.org
Cc: Matt Grise
Subject: [External]RE: Exposed CPVC pipe and residential upright sprinklers
They are a newer product... maybe have not been added to the install guide yet?
Have you called a manufacturer?
Matt Grise
Alliance Fire Protection
130 w 9th Ave
North Kansas City, MO
913.526.7443
Sprinklerforum
Date: 1/21/22 12:34 PM (GMT-06:00)
To: sprinklerforum@lists.firesprinkler.org
Cc: Dewayne Martinez
Subject: Exposed CPVC pipe and residential upright sprinklers
I don't see an option for using residential upright sprinkler on exposed CPVC
pipe in any of the manufactures installation
upright sprinklers with
exposed CPVC.
Thank you,
Dewayne Martinez
Fire Protection Design Manager
TOTAL Mechanical
Building Integrity
W234 N2830 Paul Rd.
Pewaukee, WI 53072
dmarti...@total-mechanical.com
Ph: 262-522-7110
Cell: 414-406-5208
http://www.total-mechanical.com
and one wouldn't
use uprights? I don't know but am curious to see where this goes. Definitely a
question for the CPVC manufacturers though.
Cary Webber CFPS Director, Technical Services
Reliable Automatic Sprinkler Co., Inc.
1470 Smith Grove Road, Liberty, SC 29657
Tel: 864-843-5161
I don't see an option for using residential upright sprinkler on exposed CPVC
pipe in any of the manufactures installation manuals. Am I missing something
or is QR uprights my only option?
Thank you,
Dewayne Martinez
Fire Protection Design Manager
TOTAL Mechanical
Building Integrity
W234
@lists.firesprinkler.org
Cc: r...@westernslopefire.com
Subject: RE: CPVC Fitting
Look at spears data
Flame guard fittings
-Original Message-
From: Sprinklerforum On Behalf
Of Taylor Schumacher via Sprinklerforum
Sent: Tuesday, November 09, 2021 2:06 PM
To: sprinklerforum@lists.firesprinkler.org
Cc
klerforum
Sent: Tuesday, November 9, 2021 4:06 PM
To: sprinklerforum@lists.firesprinkler.org
Cc: Taylor Schumacher
Subject: RE: CPVC Fitting
BE ADVISED - This email originated outside EMCOR.
Seems silly that a threaded female x threaded female fitting in CPVC would even
exist?
Taylor S
Look at spears data
Flame guard fittings
-Original Message-
From: Sprinklerforum On Behalf
Of Taylor Schumacher via Sprinklerforum
Sent: Tuesday, November 09, 2021 2:06 PM
To: sprinklerforum@lists.firesprinkler.org
Cc: Taylor Schumacher
Subject: RE: CPVC Fitting
Seems silly
Seems silly that a threaded female x threaded female fitting in CPVC would even
exist?
Taylor Schumacher
-Original Message-
From: Sprinklerforum On Behalf
Of Scott Futrell via Sprinklerforum
Sent: Tuesday, November 09, 2021 2:18 PM
To: sprinklerforum@lists.firesprinkler.org
Cc
in restrooms.
No problem.
It’s not only allowed. With the flexibility of CPVC it just should be a rare
problem.
The other? No clearance needed in rated GWB walls. Not a problem. Did we get
all the broken GWB caused by metallic pipe bouncing around? Hahaha. Good one.
Best.
Bruce V.
> On 03/02/2
DwICAg=wn3mZQLIuInh2ClcJ0_DIA=GIS2RCKGscVLbU61DuFzgH3FhC3Vepu3l9fL3Gu7k2M=kET3jiqTJ6JW_ld5XkRiekWZHQ2WimpLjdKEFra2uCw=NN_TTIhrWT1Cy0JBrjosYNByYYG0-bqvGZL9_wr9tTQ=
>> >
>> <#m_-3296756546440371397_DAB4FAD8-2DD7-40BB-A1B8-4E2AA1F9FDF2>
>>
>> On Tue, Mar 2, 2021 at 10:39 AM Kyle.Montgomery
-email?utm_medium=email_source=link_campaign=sig-email_content=webmail_term=link>
> <#m_-3296756546440371397_DAB4FAD8-2DD7-40BB-A1B8-4E2AA1F9FDF2>
>
> On Tue, Mar 2, 2021 at 10:39 AM Kyle.Montgomery via Sprinklerforum <
> sprinklerforum@lists.firesprinkler.org> wrote:
>
inklerforum <
sprinklerforum@lists.firesprinkler.org> wrote:
> When installing a CPVC system in a seismic area (area where seismic
> bracing is required) are there any special considerations needed for the
> drops to sprinkler heads? In the past, with steel pipe systems we've ofte
When installing a CPVC system in a seismic area (area where seismic bracing is
required) are there any special considerations needed for the drops to
sprinkler heads? In the past, with steel pipe systems we've often utilized
flexible sprinkler connections to avoid any concern about differential
Ken W. did this article a couple years ago. Afocn/Anvil and Tolco/Eaton
have some braces.
https://sprinklerage.com/seismic-bracing-of-cpvc-pipe/
"ABOUT THE AUTHOR: Ken Wagoner, C.F.P.E., C.W.B.S.P, S.E.T. "
Seismic Bracing of CPVC Pipe
August 29, 2018
please note comments:
IMPORT
Scott makes a great point. CPVC piping has to be free to move.
Thanks,
John
John August Denhardt, PE
*Vice President, Engineering and Technical Services*
*American Fire Sprinkler Association*
m: p: 301-343-1457
214-349-5965 ext 121
w: firesprinkler.org
<https://www.facebook.
straps used to secure CPVC acted as seismic
> bracing? I don't know where I've heard that and couldn't find anything in
> the standard. Is this correct?
>
> Also, if you have a 1"x8'-6" riser to a single horizontal sidewall
> sprinkler would that technically be an 'armove
Just remember to allow for thermal expansion and contraction. It can get very
ugly if the CPVC is restrained and thermal expansion and contraction has not
been appropriately allowed for. This applies when a building is warm in the
summer during construction and then air conditioning is turned
Personally, I would provide the restraint and be done. As Travis said,
apply the less than 6" criteria and you should be good with the CPVC
hangers.
9.3.5.8.5 Four-way bracing shall not be required where risers penetrate
intermediate floors in multistory buildings where
the clearance
December 30, 2020 12:28 PM
> To: sprinklerforum@lists.firesprinkler.org
> Cc: Matthew J Willis
> Subject: RE: CPVC EQ Bracing - 2 hole straps and another question
>
> To my knowledge, the 2 hole strap is listed as a hanger only. Not for
> seismic.
>
> The second question is a
vorite ferguson.com features. Apple iOS devices or Android devices**
From: Sprinklerforum on behalf
of Matthew J Willis via Sprinklerforum
Sent: Wednesday, December 30, 2020 12:27:54 PM
To: sprinklerforum@lists.firesprinkler.org
Cc: Matthew J Willis
Subject: RE: CPVC EQ B
...@lists.firesprinkler.org]
On Behalf Of Matthew J Willis via Sprinklerforum
Sent: Wednesday, December 30, 2020 12:28 PM
To: sprinklerforum@lists.firesprinkler.org
Cc: Matthew J Willis
Subject: RE: CPVC EQ Bracing - 2 hole straps and another question
To my knowledge, the 2 hole strap is listed as a hanger only
H via Sprinklerforum
Sent: Wednesday, December 30, 2020 12:13 PM
To: sprinklerforum@lists.firesprinkler.org
Cc: J H
Subject: CPVC EQ Bracing - 2 hole straps and another question
Hello,
I thought that two hole straps used to secure CPVC acted as seismic bracing? I
don't know where I've heard that a
Hello,
I thought that two hole straps used to secure CPVC acted as seismic
bracing? I don't know where I've heard that and couldn't find anything in
the standard. Is this correct?
Also, if you have a 1"x8'-6" riser to a single horizontal sidewall
sprinkler would that technically be a
Some of you guys mentioned bushings or "other method to prevent chafing". Can
we elaborate on that? I've seen bushings used where CPVC is run in a wall and
passes through metal studs, but I don't think I've seem them installed in this
scenario. Is that really a requirement
forum
Sent: Wednesday, September 30, 2020 6:39 AM
To: Sprinkler Forum
Cc: Mike Hairfield
Subject: Hangers for CPVC Pipe going through TGI Joists
The TGI Joists are spaced 16" apart, does NFPA-13 require hangers on the
CPVC pipe since
the TGI joists are supporting
e: Hangers for CPVC Pipe going through TGI Joists
Agree - the structure is the support. Restraints or chafing protectuion might
be needed.
Thanks,
John
John August Denhardt, PE
*Vice President, Engineering and Technical Services*
*American Fire Sprinkler Association*
m: p: 301-343-1457
214-349-5965
e to side movement expected.
>
> R/
> Matt
>
> -Original Message-
> From: Sprinklerforum On
> Behalf Of Mike Hairfield via Sprinklerforum
> Sent: Wednesday, September 30, 2020 6:39 AM
> To: Sprinkler Forum
> Cc: Mike Hairfield
> Subject: Hangers for CPVC Pipe goi
To: Sprinkler Forum
Cc: Mike Hairfield
Subject: Hangers for CPVC Pipe going through TGI Joists
The TGI Joists are spaced 16" apart, does NFPA-13 require hangers on the CPVC
pipe since the TGI joists are supporting the pipe?
Mike
___
Sprinkler
The TGI Joists are spaced 16" apart, does NFPA-13 require hangers on the CPVC
pipe since
the TGI joists are supporting the pipe?
Mike
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinf
Any edition 10 and after...,
We have a situation where we are using hangers less than 6" on our entire
system.
Yes, we comply with the other items.
Since this omits Lateral bracing, I was looking into restraints.
Are the spacing requirements for Restraints still in play? Or does the reduced
My CPVC documentation states to user only flex couplings, not standard rigid.
And I will give them one heart, and I will put a new spirit within you; and I
will take the stony heart out of their flesh, and will give them an heart of
flesh
Eze 11:19
> On Apr 4, 2019, at 11:24 AM, Dale Wing
e: 973-670-2627
m...@knssprinkler.com<mailto:m...@knssprinkler.com>
From: Sprinklerforum On Behalf
Of Mike Hairfield
Sent: Thursday, April 4, 2019 12:11 PM
To: Sprinklerforum
Subject: Grooved Coupling for CPVC
I have a local AHJ asking for a data sheet that states that a standard grooved
Blazemaster has a grooved CPVC adapter. Contact the Viking Rep and ask them
what coupling is approved for that fitting.
Victaulic also has a line of grooved CPVC fittings but these don't appear to be
for Sprinkler systems.
Craig Prahl | Jacobs | Group Lead - Fire Protection | 864.676.5252
Try contacting your CPVC manufacturer and they should be able to provide you
with a statement that the grooved adapter was made to be used with a standard
coupling.
Dale F. Wingard, SET
Designer Commercial/Marine Division
NICET IV #76284
Water-based Systems
Hiller Systems
A Division
Check out Rasco. Cover sheet indicates UL Listing.
From: Sprinklerforum On
Behalf Of Mike Hairfield
Sent: Thursday, April 4, 2019 12:19 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Grooved Coupling for CPVC
Done that and I could not find anyone that has coupling
for CPVC
Check with your supplier or down load their grooved literature.
Regards,
G. Tim Stone
G. Tim Stone Consulting, LLC
NICET Level III Engineering Technician
Fire Protection Sprinkler Design
and Consulting Services
117 Old Stage Rd. - Essex Jct., VT. 05452
CELL: (802) 373-0638
TEL: (802) 434-2968
<mailto:tston...@comcast.net> tston...@comcast.net
From: Sprinklerforum On
Behalf Of Mike Hairfield
Sent: Thursday, April 4, 2019 12:11 PM
To: Sprinklerforum
Subject: Grooved Coupling for CPVC
I have a local AHJ asking for a data sheet that
I have a local AHJ asking for a data sheet that states that a standard grooved
coupling is
U/L listed and/or FM approved for that use.
Have any of you guys ever seen this?
Thanks,
Mike
___
Sprinklerforum mailing list
I ran into this recently and it was pointed out to me that the floor assembly
itself was UL rated fire assembly and if I ran the CPVC in the interstitial
space it would have to comply with the OH rules of 400sf or less. I thought
the same at first about it being protected per LH that it would
How are the sprinklers supplied in the Ordinary Hazard compartments below? In
earlier editions of NFPA 13, you cannot run CPVC piping to Ordinary Hazard
sprinklers covering areas greater than 400 ft². (For 2019 there is an
allowance for up to 1000 ft² in private residential parking garages
I missed to explain this part…. Thanks Steve.
The concealed space will be sprinklered and yes I am proposing to install
the sprinklers in the concealed space of the CPVC piping an as per the
listing for CPVC pipe (i.e. piping max 6” above ceiling or insulation etc.)
I’m also pointing to NFPA
Is the interstitial space combustible? If so, are you proposing to sprinkler
the space with sprinklers that satisfy the listing limitations of the CPVC?
Does the CPVC also supply the OH space below?
[Steve Signature (3)]
From: Sprinklerforum [mailto:sprinklerforum-boun
I have a job that’s a 2 story building with an A truss roof, 1st floor is
retail and 2nd floor is residential, the entire building is being
sprinklered as per NFPA 13.
We want to install sidewalls with multiple CPVC risers and tie everything
in 1st floor interstitial space, Question
*Sent:* Wednesday, August 08, 2018 1:02 PM
>>
>>
>> *To:* sprinklerforum@lists.firesprinkler.org
>> *Subject:* RE: NFPA 13R - Garages - CPVC
>>
>>
>>
>> *Your description of accessible by more than one dwelling unit is exactly
>> the way I view it.
>
>
> *From:* Sprinklerforum [mailto:
> sprinklerforum-boun...@lists.firesprinkler.org] *On Behalf Of *MFP
> Design, LLC
> *Sent:* Wednesday, August 08, 2018 1:02 PM
>
>
> *To:* sprinklerforum@lists.firesprinkler.org
> *Subject:* RE: NFPA 13R - Garages - CPVC
>
>
>
] On
Behalf Of MFP Design, LLC
Sent: Wednesday, August 08, 2018 1:02 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: NFPA 13R - Garages - CPVC
Your description of accessible by more than one dwelling unit is exactly the
way I view it. But, I got shot down by the AHJ. Their response was: “What
it
with phosphorus … or are they?
SML
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of MFP Design, LLC
Sent: Wednesday, August 08, 2018 1:02 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: NFPA 13R - Garages - CPVC
Your description of accessible by more than
n Behalf
Of Steve Leyton
Sent: Wednesday, August 8, 2018 1:00 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: NFPA 13R - Garages - CPVC
13. My point is only to reinforce the intent of the standard(s) and also that
the manufacturers will warrant the application.
The word that’s in
it’s
the intent of the book and the listing to allow the CPVC.
SL
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of Ben Young
Sent: Wednesday, August 08, 2018 12:49 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: NFPA 13R - Garages - CPVC
Just
extreme
> measure. One jurisdiction (City of San Diego) has flat-out mandated steel
> pipe in the those applications. Going forward, I hope this expands the
> application for CPVC to at least homogenize the bill of materials in
> attached residential projects.
>
>
>
AHJs in the southwest requiring double
layers of Type ‘X’ and other fairly extreme measure. One jurisdiction (City of
San Diego) has flat-out mandated steel pipe in the those applications. Going
forward, I hope this expands the application for CPVC to at least homogenize
the bill of materials
This sounds good to me. I have sent in for an AFSA informal interp just to get
a bit more ammo.
This project has both 13R and 13 buildings on it. So, the 13 buildings, I will
definitely have to go steel, but I’m going to try to get all of the 13R
buildings as CPVC.
Travis Mack, SET
I would agree with CPVC because of the manufacturer listing. However, if
you were using a manufacturer that did not have that verbiage and you were
back to your interpretation of 13R I think you are wrong in applying the
aggregate for the 400 sq. ft. rule. 13R specifically calls out "
Travis,
Based on the product listing, CPVC is appropriate.
Thank you,
Bob Knight, CET III
208-318-3057
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of MFP Design, LLC
Sent: Wednesday, August 08, 2018 9:57 AM
To: sprinklerforum
CPVC.
Richard M. Carr, SET
Project Manager/Design
Diboco Fire Sprinklers, Inc.
325 Jackson Loop Road
Flat Rock, NC 28731
rich...@diboco.com<mailto:rich...@diboco.com>
828-696-3400
828-696-2288 Fax
828-708-9118 Mobile
[cid:image001.jpg@01D2E695.9A38B950]
[cid:image002.png@01D2E695.9A
. The spaces are ≤ 500 sq ft, so 7.2.2.1 allows us to
limit the number of calculated sprinklers to all in a compartment to a maximum
of 4. We are using QR sprinklers in these garages.
Now, here is where the wrinkle comes. Are we permitted to use CPVC above the
ceiling in these areas? The ceiling
rforum@lists.firesprinkler.org
Subject: RE: CPVC Seismic
What city in northern CA is letting you get away with 2013 code?
Rocci Cetani III, CET
Senior Designer
Water-Based Fire Protections Systems Layout, Nicet Level III
Northern California Fire Protection Services Inc.
16840 Joleen Way Bldg. A
Morgan Hi
8, 2017 8:46 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: CPVC Seismic
Using 2013, and the area of concern will be supported with 2-hole CPVC straps.
Thank you,
Bob Knight, CET III
208-318-3057
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.fires
18, 2017 8:27 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: CPVC Seismic
I had to step out for a couple of hours, but I'm back.
I'm assuming that I can use the rods less than 6" rule and omit lateral
bracing, right?
That would leave 4-ways and longitudinal only, correct?
Using 2013, and the area of concern will be supported with 2-hole CPVC straps.
Thank you,
Bob Knight, CET III
208-318-3057
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of Travis Mack
Sent: Monday, September 18, 2017 9:43 PM
To: b
3057
>
> From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
> On Behalf Of MFP Design, LLC
> Sent: Monday, September 18, 2017 4:31 PM
> To: b...@firebyknight.com; sprinklerforum@lists.firesprinkler.org
> Subject: RE: CPVC Seismic
>
> Really no different. I doubt y
forum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of MFP Design, LLC
Sent: Monday, September 18, 2017 4:31 PM
To: b...@firebyknight.com; sprinklerforum@lists.firesprinkler.org
Subject: RE: CPVC Seismic
Really no different. I doubt you will find longitudinal bracing listed for
cpvc. You will
Afcon is the only company with seismic attachments for CPVC
Rocci Cetani III, CET
Senior Designer
Water-Based Fire Protections Systems Layout, Nicet Level III
Northern California Fire Protection Services Inc.
16840 Joleen Way Bldg. A
Morgan Hill, CA 93037
P-(408) 776-1580 EXT.111
F
Really no different. I doubt you will find longitudinal bracing listed for
cpvc. You will have to put a short branch (same size as main) perpendicular
to the main and brace that with a lateral brace to act as your longitudinal
brace on the main.
From: Sprinklerforum [mailto:sprinklerforum
I'm about to do my first CPVC sway bracing calc's. This is in CA (a first
for me as well), north of San Francisco.
Are there any special issues that I need to consider, or do I approach this
as if it's not much different than if it where steel?
Thank you,
Bob Knight, CET III
208-318
Hey Tom.
Yes, some.
I have had long attic runs before and I guess that is what I am envisioning.
Pipe "breathing" as it were. The listed CPVC hangers allow the pipe to move
freely for expansion and contraction. Down south, there are some big temp
differences.
If we lock i
Matt,
I understand that expansion loops are not that common. A layout usually
provides enough offsets and changes in direction where long runs of CPVC pipe
are not that common. But, they do happen.
Where the straight CPVC run is sufficient length to require an expansion loop,
provide bracing
urston
Sent: Monday, July 10, 2017 9:11 AM
To: Matthew J Willis <sprinklerforum@lists.firesprinkler.org>
Subject: Re: CPVC: To Move, or Not To Move
Hello Matthew,
There are several ways shown in the manual about putting in offsets, making a
corner, and I think it even shows the sizes n
of CPVC to expand when we have hard strapped
it to wood?
Never braced CPVC so more curious than anything.
R/
Matt
Matthew J. Willis
Project Manager
Rapid Fire Protection Inc.
1530 Samco Road
Rapid City, SD 57702
Office-605.348.2342
Direct Line-605.593.5063
Cell-605.391.2733
Fax
Reading the Tech Update got me thinking.
What do we do to address the need of CPVC to expand when we have hard strapped
it to wood?
Never braced CPVC so more curious than anything.
R/
Matt
Matthew J. Willis
Project Manager
Rapid Fire Protection Inc.<http://rapidfireinc.com/>
1530 Samc
Monday, June 19, 2017 9:27 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: CPVC earthquake bracing
The primary answer has already been provided but thought it worth adding -
unless it has changed recently, you’ll won’t find any longitudinal braces.
You’ll be using lateral brac
Subject: Re: CPVC earthquake bracing
It is required that you only use sway brace attachments that are listed for
CPVC. Like listed solution for hangers and supports, the seismic fittings
designed for use with plastic pipe have rolled edges and other features that
prevent the damage you're descr
n.com> wrote:
>
> It is required that you only use sway brace attachments that are listed for
> CPVC. Like listed solution for hangers and supports, the seismic fittings
> designed for use with plastic pipe have rolled edges and other features that
> prevent the damage you're des
It is required that you only use sway brace attachments that are listed for
CPVC. Like listed solution for hangers and supports, the seismic fittings
designed for use with plastic pipe have rolled edges and other features that
prevent the damage you're describing. Check with your local
My installers are trying to install EQ bracing on CPVC for a NFPA 13 system
and aren't having much luck..they said that the fittings are gouging and
digging into the CPVC (and no they are NOT using impacts) Anyone out there
with some experience on bracing CPVC? This project was designed off
Tyco Blazemaster has this information in their IH1900 handbook starting on page
30. You can access the Installation Instructions on CPVC via the Tyco Fire
website.
Joseph L. Tieman / Director of Sales - U.S. - Water Products / Tyco Fire
Protection Products
Mobile: +1 412 576 9339 / Fax