Based on one I did recently, yes. To segue to another concurrent thread, does this facility meet the criteria for an R occupancy, or would it be an I-1 occupancy? If it's I-1, it may need to be a full 13 system.

At 06:03 PM 6/14/2007, you wrote:
I have a two story retirement facility with dwelling unit wings and a large
common area with kitchen, restaurant style seating, lobbies, activity rooms,
etc. Am I correct in reading 13R 6.7.2.1 "Design Criteria - Outside Dwelling
Unit" as essentially requiring me to do a 1500 sq. ft. calc for the most
remote portion of the common area? The conditions of 6.7.2.2 are not met in
that many rooms exceed 500 sq. ft.