Check to see if the Architect applied the 200% allowance for a fully sprinkelred building, which I would think he could have with that size building. If he did, you would need to go with an NFPA 13 system, per the Code (IBC, anyway)


At 06:20 PM 6/14/2007, you wrote:
 I am not familiar enough with the bldg code requirements to comment, the
local Fire Marshall is OK with a 13R system. This is a fairly large wood
framed 35,000 sq. ft. per floor complex. The dwg cover sht says it's SBC R-2
Residential & A-2 Small Assembly (no stage), NFPA 101 New Apartment.

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Todd Williams
- work
Sent: Thursday, June 14, 2007 6:15 PM
To: [email protected]
Subject: RE: 13R RETIREMENT HOME

Based on one I did recently, yes. To segue to another concurrent thread,
does this facility meet the criteria for an R occupancy, or would it be an
I-1 occupancy? If it's I-1, it may need to be a full 13 system.


At 06:03 PM 6/14/2007, you wrote:
>I have a two story retirement facility with dwelling unit wings and a
>large common area with kitchen, restaurant style seating, lobbies,
>activity rooms, etc. Am I correct in reading 13R 6.7.2.1 "Design
>Criteria - Outside Dwelling Unit" as essentially requiring me to do a
>1500 sq. ft. calc for the most remote portion of the common area? The
>conditions of 6.7.2.2 are not met in that many rooms exceed 500 sq. ft.
>
>
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>To Unsubscribe, send an email
>to:[EMAIL PROTECTED]
>(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
860-535-2080
www.fpdc.com

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
860-535-2080
www.fpdc.com
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to