RE: ESFR obstruction in non-storage

2015-06-11 Thread RFletcher
We deal with this all the time. Lacking any direction in 13 it just comes down 
to what the AHJ will accept? It's ridiculous to not allow standard SSP 
obstruction rules for ESFR's if there is no storage but that is my opinion as a 
contractor.

We are just completing a demo and retrofit of a 450,000 sqft S1 occupancy. The 
previous tenant moved out and the owner decided to replace the existing FP 
systems. The old systems were from the early 70's and were badly corroded and 
fittings were constantly failing. Some mezzanines were removed but they left 
the existing lights, conduits, cable trays, unit heaters, insulated hot water 
supply and return pipes and some steel framing used to support equipment that 
was removed. The building is completely empty and retro fit with 16.8 ESFR's. 
The rational for this is to call the new ESFR systems core and shell so when 
the owner gets a tenant the obstructions can be dealt with based on the use of 
the building. Almost every light fixture is an obstruction per ESFR rules as 
are the unit heaters and hot water pipes. If the core and shell concept 
weren't allowed the owner would have to completely replace the heating and 
lighting systems in a vacant building.

Ron F

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Matt Grise
Sent: Thursday, June 11, 2015 6:02 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: ESFR obstruction in non-storage

Watch out for smoke vent and draft curtain requirements if  you remove the ESFR.

Matt Grisé PE*, LEED AP, NICET II  
Sales Engineer 
Alliance Fire Protection 
130 w 9th Ave.
North Kansas City, MO 64116

*Licensed in KS  MO 
 
913.888.0647 ph 
913.888.0618 f 
913.927.0222 cell 
www. AFPsprink.com 
 

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of craig.pr...@ch2m.com
Sent: Thursday, June 11, 2015 8:00 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: ESFR obstruction in non-storage

If you're going to rework the existing ESFR system and respace the sprinklers 
why not just change them out to a non-ESFR sprinkler?

Craig L. Prahl 
Fire Protection Group Lead
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29303
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
craig.pr...@ch2m.com

On Thu, Jun 11, 2015 at 6:57 AM, sprinklerforum@lists.firesprinkler.org
sprinklerforum@lists.firesprinkler.org wrote:
I'm did the research yesterday in FM 2-0 and in the AFSA informal interps, but 
I wanted to make sure I'm not missing something here...

Can I get a confirmation that you are still required to meet obstruction 
criteria for ESFR (storage) sprinkler heads even when they're being used to 
protect a non-storage occupancy?

I see nothing in 2-0 about the use of storage sprinkler in non-storage 
occupancies, but I know that NFPA 13 covers this. I think that the listing 
criteria of the ESFR heads is what drives the obstruction rules, so these must 
be complied with to use the heads for say, a manufacturing occupancy.

Backstory: we have a customer that is converting rack storage to manufacturing, 
and they're putting in a lot of cable trays for the machinery. Wide cable 
trays, double stacked cable trays, offset trays, etc. Nothing over 10 feet 
wide, but very full cable trays that almost always are over 2 feet wide. The 
building is about 24' high, and the trays will be down at 12' so plenty of 
clear space.

The customer is FM insured, so we're giving them the option to either install 
barriers under the trays and space the roof-level sprinklers every
8 ft or to leave the barriers out and put the roof-level heads under the trays 
every 4 ft (and also following the maximum square footage allowances in FM 2-0 
of course).

Before I deliver this great news, I just wanted to make sure I didn't miss 
something in my reading of 2-0.

I'm guessing, as well, that I can simply ignore the obstruction rules relating 
to the placement of obstructions over flue spaces and other storage-specific 
items.

Thanks in advance for any assistance with this!

Benjamin Young
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

RE: Light or Ordinary Hazard

2015-05-08 Thread RFletcher
Wouldn't 8.3.2.1 ('13) apply? It allows ordinary and intermediate temperature 
to be used throughout buildings. Doesn't 8.3.2.1 make it okay to use 
intermediate temperature throughout the nursing home? 
Ron F 

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Mark A. Sornsin, P.E.
Sent: Friday, May 08, 2015 7:05 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Light or Ordinary Hazard

The related thread reminded me of this story of AHJ over-reach (some have read 
this before):

Years ago in my contracting days we designed a system for an addition to 
nursing home. It included a second floor 'mechanical room.' Out of habit we 
designed this to OH-1. It proved a bit difficult to design given the sloped 
ceiling and weak water supply, but we got it done.  After the installation was 
complete we were told by the owner that the State Dept. of Health came through 
and instructed them to replace the intermediate temp sprinklers in this room 
with ordinary temp heads. We intervened and explained we designed to OH-1 so 
the int. temp heads were allowed by 13. They replied that the room is an air 
handling space with no fuel-fired equipment and no storage allowed by state 
rules. Therefore it is actually a Light Hazard space; and since it is a nursing 
facility and life safety is paramount, the sprinklers must be replaced.

This remains the best personal example of an AHJ being technically correct but 
missing the bigger picture. The 200 deg. QR sprinklers, as we know, do not 
significantly delay sprinkler operation as compared to the 155 deg. QR heads. 
This is an unoccupied space located upstairs from the not-so-mobile residents 
of this otherwise one-story facility. We have designed 50% more water flow with 
more closely spaced sprinklers. Replacing the sprinklers was a complete waste 
of the owner's money.

Moral: sometimes the standards clearly tell you what to do; sometimes they 
clearly don't tell you what not to do; and other times you just have to be able 
to see the overall intent and act accordingly. This last point requires more 
than a cursory knowledge of the standards in question. Don't be like the AHJ in 
this example.
Mark A. Sornsin, P.E. | Karges-Faulconbridge, Inc. | Fire Protection Engineer | 
Fargo, ND | direct: 701.552.9905 | mobile: 701.371.5759 | 
http://www.kfiengineers.com

__
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com 
__
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Light or Ordinary Hazard

2015-05-08 Thread RFletcher
New in the 2010 Edition. It's explained very clearly in the 2010 Handbook. the 
standard now groups ordinary and intermediate temperature sprinklers together 
and allows intermediate temperature sprinklers throughout the building, 
reducing the need for multiple types of sprinklers.
Ron F

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Roland Huggins
Sent: Friday, May 08, 2015 8:44 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Light or Ordinary Hazard

that is a relative recent change

Roland Huggins, PE - VP Engineering
American Fire Sprinkler Assn.   ---  Fire Sprinklers Saves Lives
Dallas, TX
http://www.firesprinkler.org http://www.firesprinkler.org/





 On May 8, 2015, at 8:10 AM, rfletc...@aerofire.com rfletc...@aerofire.com 
 wrote:
 
 Wouldn't 8.3.2.1 ('13) apply? It allows ordinary and intermediate temperature 
 to be used throughout buildings. Doesn't 8.3.2.1 make it okay to use 
 intermediate temperature throughout the nursing home? 
 Ron F 

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Re: Heat Tracing

2015-04-22 Thread RFletcher
Heat trace? Florida?

Ron fletcher Sent from my iPhone

 On Apr 22, 2015, at 12:37 PM, Pete Schwab pe...@waynefire.com wrote:
 
 I am searching for an installer of heat tracing (Listed for fire protection) 
 in Florida
 If you have a contact you can share it is greatly appreciated.
 Thanks
 
 Peter Schwab
 VP of Purchasing and Engineering technologies
 
 Wayne Automatic Fire Sprinklers Inc.
 222 Capitol Court
 Ocoee, Fl 34761
 
 Mobile: (407) 468-8248
 Direct: (407) 877-5570
 Fax: (407) 656-8026
 
 www.waynefire.com
 
 
 
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: NFPA 409 2011 6.1., 6.1.2, 7.2

2015-04-17 Thread RFletcher
My hard copy of 409-2011 edition is the same as Greg quoted. 6.1.2 Group I 
aircraft hangar storage and service area shall be provided with protection in 
accordance with 6.1.1 or with automatic sprinkler protection as specified in 
Section 7.2 and 7.8. When I pull up 409 go on line 6.1.2 is as you say for 
unfueled aircraft. I hate it when this happens.
Ron F

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Frans Stoop
Sent: Thursday, April 16, 2015 5:11 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: NFPA 409 2011 6.1., 6.1.2,  7.2

Gregg,

6.1.2 is about unfueled aircraft only. See the definition of Unfueled Aircraft 
in 3.3.15.

Best regards,

Frans Stoop
TOS architecture  fire protection
Netherlands f.st...@tosfire.com
Tel. +31-24-324 0112


At 17:08 16-4-2015 +, you wrote:
That is the confusion on my part.  By 6.1.2 stating OR I would assume 
that it is either a foam type system OR a standalone wet pipe system.  
Since 7.2  7.8 do not mention any type of foam requirements, the OR 
indicates to me that is one or the either. So you either go 6.1.1 for a 
foam type system or 7.2 for a wet pipe system.  7.2 indicates to me 
that you can do a Group I hangar without foam.

Thanks,
Gregg Fontes
Cen-Cal Fire Systems, Inc.
209-334-9119
-Original Message-
From: Sprinklerforum
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of 
mphe...@aerofire.com
Sent: Thursday, April 16, 2015 9:44 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: NFPA 409 2011 6.1., 6.1.2,  7.2

I believe you are correct with exception that you then have to provide 
low level AFFF via monitors etc.

Mark at Aero
602 820-7894

Sent from my iPhone

  On Apr 16, 2015, at 9:17 AM, Gregg Fontes gr...@cen-calfire.com wrote:
 
  Chapter 6 - Protection of Group I Aircraft Hangars:  6.1.1 The
 protection of aircraft storage and servicing areas for Group I 
 aircraft hangars shall be in accordance with any one of the
 following: (1), (2), or (3).  All three of these are some type of foam 
 application.  Then comes 6.1.2; Group I aircraft hangar storage and 
 service area shall be provided with protection in accordance with 
 6.1.1 or with automatic sprinkler protection as specified in Sections 
 7.2 and 7.8.  7.2 Closed-Head Water Sprinkler System for Aircraft 
 Storage and Servicing Areas.
 
  So base on the above, if I am not missing something or skipping
 something, you are allowed to either design a foam type system
 6.1.1 or a standard closed-head wet pipe fire sprinkler system (no
 foam) per the requirements of 7.2 and 7.8.  Am I understanding this correctly?
 
  Thanks,
  Gregg Fontes
  Cen-Cal Fire Systems, Inc.
  209-334-9119

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Re: Bottom of elevator shaft protection

2015-04-01 Thread RFletcher
Just curious, do you have a code reference for mech rooms as OH1?

Ron fletcher Sent from my iPhone

 On Apr 1, 2015, at 6:35 AM, Matthew J Willis ma...@rapidfireinc.com wrote:
 
 I had the 10 in parenthesis, my apologies
 
 Also I forgot to add.., OH1 because it is a mechanical room after all.
 
 R/
 Matt
 
 Matthew J. Willis
 Project Manager
 Rapid Fire Protection Inc.
 1805 Samco Road
 Rapid City, SD 57702
 Office-605.348.2342
 Cell-605.391.2733
 Fax:-605.348.0108
 
 
 
 -Original Message-
 From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] 
 On Behalf Of John Denhardt
 Sent: Wednesday, April 01, 2015 7:28 AM
 To: 'sprinklerforum@lists.firesprinkler.org'
 Subject: RE: Bottom of elevator shaft protection
 
 What year is your reference? NFPA 13 - 2013?
 
 John
 
 -Original Message-
 From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] 
 On Behalf Of Matthew J Willis
 Sent: Wednesday, April 01, 2015 9:01 AM
 To: sprinklerforum@lists.firesprinkler.org
 Subject: RE: Bottom of elevator shaft protection
 
 Ordinary if not hydraulic. EHI if combustible hydraulic fluid is used.
 
 A.5.4.1 (10)
 
 R/
 Matt
 
 Matthew J. Willis
 Project Manager
 Rapid Fire Protection Inc.
 1805 Samco Road
 Rapid City, SD 57702
 Office-605.348.2342
 Cell-605.391.2733
 Fax:-605.348.0108
 
 
 
 -Original Message-
 From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] 
 On Behalf Of Mike Hairfield
 Sent: Wednesday, April 01, 2015 5:35 AM
 To: sprinklerforum@lists.firesprinkler.org
 Subject: RE: Bottom of elevator shaft protection
 
 Some AHJ's classify it as Extra Hazard because of the Hydraulic Fluid, I 
 wouldsay ordinary hazard but never light hazard.
 Mike 
 
 From: ssorr...@performancefire.com
 To: sprinklerforum@lists.firesprinkler.org
 Subject: Bottom of elevator shaft protection
 Date: Wed, 1 Apr 2015 11:31:30 +
 
 Question,
 Would the bottom of the elevator shaft be considered light or ordinary 
 hazard ? We have an elevator shaft 15-'4 wide, one head would be acceptable 
 as light hazard but not as ordinary hazard.
 
 
 Stephen J. Sorrell, CET
 NICET# 77901 Level III
 E mail: 
 ssorr...@performancefire.commailto:ssorr...@performancefire.com
 
 Performance Fire Protection, LLC
 Corporate Office
 179 Gasoline Alley -  PO Box 4510
 Mooresville, NC 28117
 Phone: 704-663-1664  Fax: 704-663-1652 Cell : 704-309-1242
 
 Web: www.performancefire.comhttp://www.performancefire.com
 Licensed in NC, SC, VA, TN, GA, AL
 
 Performance on Every Level.
 
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
 er.org
 
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
 
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
 
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Large pumping capacity

2015-03-26 Thread RFletcher
With 3 pumps, 2 needed and one backup the suction and discharge header should 
be sized for 2 pumps. 16 pipe would result in a suction velocity of less than 
10 fps, I believe that is the recommended limit in NFPA 20. All common pipe 
subject to the full flow of two pumps should be sized accordingly.
Ron F

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Travis Mack
Sent: Thursday, March 26, 2015 12:25 PM
To: sprinklerfo...@firesprinkler.org
Subject: Large pumping capacity

I am working on a project where there is a fairly large demand.  The EOR has 
determined there are to be (3) 3000 gpm pumps.  These are all installed 
parallel.  One of the pumps is to be a backup pump. The design has not been 
finalized, but the system demand (overhead sprinklers and grate foam nozzles) 
is somewhere around 6000 gpm. That is why we have two 3000 gpm pumps in 
parallel to create a 6000 gpm pumping capacity.  
There were some errors in the EOR pump room design that led to a few other 
questions.  We are getting conflicting information from the EOR and the pump 
guys.  The arrangement is that the pumps share a common suction header and a 
common discharge header.

Per NFPA 20, a 3000 gpm pump needs a 12 discharge.  The EOR showed 10 
discharge piping and equipment, so this is what flagged some questions with the 
pump room design.  The questions are now:

1 - Should the test header be sized to accommodate a 6000 gpm pump, or a
3000 gpm pump?  The pump guy says that the common discharge header must be 
sized for the combined pumping capacity.  The EOR states that it is only based 
on 1 pump flowing.  I seem to agree with the pump guy, in that you need to test 
with both pumps flowing so you can test your water supply as well to show you 
can get the full 150% flow from the water supply.  It is easy to size the 
piping so that the recommended velocities in NFPA 20 are not exceeded.  It is 
just a question as to what is the basis.

2 - Should the common discharge header that the pumps tie in to be sized based 
on 3000 gpm pump or 6000 gpm pump?  I believe that the common piping (after the 
pump discharge valve) only needs to be sized based on hydraulic calculations.

3 - These are diesel pumps.  The individual relief valves are tied into a 
common discharge header.  How should this be sized?  Based on 3000 or
6000 gpm pumps?

We are awaiting input from the authority having jurisdiction as well on this 
topic.  The biggest issue is the pump test header and relief valve discharge 
piping.  There are more issues of now trying to fit 12 
valves/pipe/fittings on the discharge side of a pump in a room that was tight 
to begin with and was designed for 10 discharge equipment.

Part of the issue is that NFPA 20 only goes to 5000 gpm tables for sizing pump 
room piping/equipment.  The EOR is stating that the NICET tech is to correct 
anything in the pump room and provide it per NFPA 20.  However, since we have a 
6000 gpm total capacity, it is not possible to size things based on the summary 
table in NFPA 20 if it is to be based on 6000 gpm.

I am just interested as to the thoughts of the guys on this forum.

--
Travis Mack, SET
MFP Design, LLC
2508 E Lodgepole Drive
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
email:tm...@mfpdesign.com

http://www.mfpdesign.com
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to us via: https://www.hightail.com/u/MFPDesign

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: ESFR Sprinkler Heads

2015-03-19 Thread RFletcher
We always split the systems where the K factor changes. However, if the 
addition is small the total area is under 40k sqft you would probably have to 
change all the heads on that system to K17.
Ron F 

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of James Crawford
Sent: Thursday, March 19, 2015 11:21 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: ESFR Sprinkler Heads

Thanks Roland

The AHJ has impose a greater reduction and if I use the new pressures the 
existing system is 3 psi short.

My concern with using two different K factor heads is the overlap area where 
two different pressures would be required causing over discharge on the K17 
heads.


Thank you


James Crawford
Phaser Fire Protection Ltd.
Phone  604-888-0318
Fax 604-888-4732
Cel 604-790-0938
Email  jcrawf...@phaserfire.ca


-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Roland Huggins
Sent: Thursday, March 19, 2015 11:05 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: ESFR Sprinkler Heads

you can have multiple design basis covering different portions of a building.  
They could present different K-factors or types of sprinklers.
There are explicit requirements that address the interface between them.

What do you mean the AHJ has dropped the pressure?  Does that mean the water 
purveyor has dropped the pressure to the area or that the AHJ has imposed a 
greater reduction on the actual supply as a safety factor.  In other words, is 
the existing system still providing adequate protection (not an issue for 
imposed reductions) ?


Roland Huggins, PE - VP Engineering
American Fire Sprinkler Assn.   ---  Fire Sprinklers Saves Lives
Dallas, TX
http://www.firesprinkler.org http://www.firesprinkler.org/





 On Mar 19, 2015, at 9:40 AM, James Crawford jcrawf...@phaserfire.ca
wrote:
 
 We are doing an addition to an existing warehouse, the existing 
 warehouse is protected with ESFR K14 uprights, since the building was 
 constructed the AHJ has dropped the water pressures in the area by 10 psi.
 
 
 
 Due to the pressure drop I cannot use the K14 heads for the addition, 
 can you mix ESFR sprinkler heads in the same warehouse area, I would 
 need K17 heads for the addition, The addition would be open to the 
 existing warehouse space. Or do I need to change all the heads in the 
 existing warehouse to match?
 
 
 
 
 
 Thank you
 
 
 
 
 
 James Crawford
 
 Phaser Fire Protection Ltd.
 
 Phone  604-888-0318
 
 Fax 604-888-4732
 
 Cel 604-790-0938
 
 Email  jcrawf...@phaserfire.ca
 
 
 
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
 er.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Re: Underground Piping Under Slab

2015-02-20 Thread RFletcher
Makes it more fun proving to a contractor that it's a NEW change.

Ron fletcher Sent from my iPhone

 On Feb 20, 2015, at 3:01 PM, Roland Huggins rhugg...@firesprinkler.org 
 wrote:
 
 NFPA has at least temporarily stopped flagging the sections that have 
 changed.  Not sure how long this will continue.  IT has been expressed pretty 
 loudly that having the changes identified is highly desirable.
 
 
 Roland Huggins, PE - VP Engineering
 American Fire Sprinkler Assn.   ---  Fire Sprinklers Saves Lives
 Dallas, TX
 http://www.firesprinkler.org http://www.firesprinkler.org/
 
 
 
 
 
 On Feb 20, 2015, at 11:45 AM, David Blackwell david.blackw...@llr.sc.gov 
 wrote:
 
 When comparing NFPA 10.6.3.1 in my hard copy versions of the code and 
 handbook, I noticed that while the language of 10.6.3.1 has changed in the 
 2013 edition to clarify the 10 ft distance, but the section was not marked 
 as new in either the printed code, the handbook or the PDF version available 
 through NFPA All-Access...  
 
 Respectfully,
 
 
 David W. S. Blackwell, II, PE, CFPE, CFI I
 Chief Engineer
 Office of State Fire Marshal
 SC Department of Labor, Licensing,  Regulation, 141 Monticello Trail, 
 Columbia, SC 29203
 Telephone: 803.896.9800 [Office] 803.896.9833 [Direct]
 Fax: 803.896.9806 [Office]
 Email:   david.blackw...@llr.sc.gov
 Website:  http://www.scfiremarshal.llronline.com/
 
 
 Please note that you can sign up to receive automatic information on SC 
 Division of Fire and Life Safety current events, policies, laws and 
 procedures by visiting our Web site at:  
 http://www.scfiremarshal.llronline.com/
 
 -Original Message-
 From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] 
 On Behalf Of rfletc...@aerofire.com
 Sent: Friday, February 13, 2015 9:33 AM
 To: sprinklerforum@lists.firesprinkler.org
 Subject: RE: Underground Piping Under Slab
 
 10.6.3.1*  (13 Ed.) 
 The requirements of 10.6.2(2) and 10.6.2(3) shall not apply where fire 
 service mains enter under the building no more than 10 ft (3 m) as measured 
 from the outside edge of the building to the center of the vertical pipe.
 Ron F
 
 -Original Message-
 From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] 
 On Behalf Of Bill Brooks
 Sent: Friday, February 13, 2015 6:51 AM
 To: sprinklerforum@lists.firesprinkler.org
 Subject: RE: Underground Piping Under Slab
 
 The new NFPA exception formatting is interesting.  10.6.1 categorically 
 states not to do something, yet 10.6.2 allows it.  Elimination of 10.6.1 
 seems the thing to do and would not change the intent.  After all it's 
 impossible to meet 10.6.1 unless you put the stub up in an exterior 
 enclosure and route it through the exterior wall.  Even the language in
 10.6.3 is an exception to 10.6.1.  How much inside the building is too much?
 
 If this is important it should be submitted as a Building, Plumbing, 
 Mechanical Code change and removed from NFPA 13.
 
 So, like we see on TV, you should now clarify your meeting comments to say 
 what you really meant was that as long as the plumbing inspector is OK with 
 the special precautions so are you.
 
 Bill Brooks
 
 -Original Message-
 From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
 On Behalf Of Brian Harris
 Sent: Thursday, February 12, 2015 4:57 PM
 To: sprinklerforum@lists.firesprinkler.org
 Subject: Underground Piping Under Slab
 
 I understand it's not typical to run the fire main under the building slab 
 but if it's a must there are some precautions that must be taken as shown in
 10.6.2 (2007). My question is are the (3) provisions that are mentioned all 
 required or as a bare minimum? I'm working on a project and the architect 
 has located the riser room in the center of the building, approximately 15'
 from the outside wall. I brought it to their attention that it's not the 
 best idea and provided them the above code reference. Instead of 
 appreciating the heads up I'm now the redheaded step child, go figure.
 
 Brian Harris, CET
 BVS Systems Inc.
 Sprinkler Division
 bvssystemsinc.comhttp://bvssystemsinc.com/
 Phone: 704.896.9989
 Fax: 704.896.1935
 
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
 
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
 
 

RE: Underground Piping Under Slab

2015-02-13 Thread RFletcher
10.6.3.1*  (13 Ed.) 
The requirements of 10.6.2(2) and 10.6.2(3) shall not apply where fire service 
mains enter under the building no more than 10 ft (3 m) as measured from the 
outside edge of the building to the center of the vertical pipe.
Ron F

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Bill Brooks
Sent: Friday, February 13, 2015 6:51 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Underground Piping Under Slab

The new NFPA exception formatting is interesting.  10.6.1 categorically states 
not to do something, yet 10.6.2 allows it.  Elimination of 10.6.1 seems the 
thing to do and would not change the intent.  After all it's impossible to meet 
10.6.1 unless you put the stub up in an exterior enclosure and route it through 
the exterior wall.  Even the language in
10.6.3 is an exception to 10.6.1.  How much inside the building is too much?

If this is important it should be submitted as a Building, Plumbing, Mechanical 
Code change and removed from NFPA 13.

So, like we see on TV, you should now clarify your meeting comments to say 
what you really meant was that as long as the plumbing inspector is OK with the 
special precautions so are you.

Bill Brooks

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Brian Harris
Sent: Thursday, February 12, 2015 4:57 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Underground Piping Under Slab

I understand it's not typical to run the fire main under the building slab but 
if it's a must there are some precautions that must be taken as shown in
10.6.2 (2007). My question is are the (3) provisions that are mentioned all 
required or as a bare minimum? I'm working on a project and the architect has 
located the riser room in the center of the building, approximately 15'
from the outside wall. I brought it to their attention that it's not the best 
idea and provided them the above code reference. Instead of appreciating the 
heads up I'm now the redheaded step child, go figure.

Brian Harris, CET
BVS Systems Inc.
Sprinkler Division
bvssystemsinc.comhttp://bvssystemsinc.com/
Phone: 704.896.9989
Fax: 704.896.1935

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: NFPA 13 FM Mix

2015-02-12 Thread RFletcher
Many times we have done two submittals. One to the AHJ with all NFPA 
requirements and another to FM with their requirements. One example is the 
local AHJ may require a 10% reduction to the flow test and .2/1500 for OH2. FM 
does not mandate any reduction to the flow test but will require .2/2500 for 
HC2. The new FM data sheets have some rules that are contrary to NFPA but 
usually they are more restrictive.
Ron F

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of John Denhardt
Sent: Thursday, February 12, 2015 6:28 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: NFPA 13  FM Mix

But in some-storage cases you not comply with both with out using NFPA's 
equivalency approach. 

Sent from my iPhone

 On Feb 12, 2015, at 8:25 AM, Cahill, Christopher ccah...@burnsmcd.com 
 wrote:
 
 You are most likely legally obligated to provide the minimums of NFPA 13.  
 You may sign a contract to provide more, but not less.  FM or silly PE 
 requirements might be examples.  
 
 Chris Cahill, PE*
 Associate Fire Protection Engineer
 Burns  McDonnell
 Phone:  952.656.3652
 Fax:  952.229.2923
 ccah...@burnsmcd.com
 www.burnsmcd.com
 *Registered in: MN
 
 
 Proud to be #14 on FORTUNE's 2014 List of 100 Best Companies to Work 
 For
 
 
 -Original Message-
 From: Sprinklerforum 
 [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of 
 Gregg Fontes
 Sent: Wednesday, February 11, 2015 6:03 PM
 To: sprinklerforum@lists.firesprinkler.org
 Subject: NFPA 13  FM Mix
 
 I have a quick question that I need a fast answer to.  Where is it in NFPA 13 
 2013 Edition that you cannot mix the two design standards?   (I.E. you either 
 design per NFPA 13 or FM Global. You cannot pick and choose.)
 
 Thanks,
 Gregg Fontes
 Cen-Cal Fire Systems, Inc.
 209-334-9119
 
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
 er.org ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
 er.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Re: Relocate sprinklers with drops RETORT

2015-02-06 Thread RFletcher
Like shipping, unpacking and installation only applies the proper and necessary 
stress for the sprinkler to operate as intended. Or maybe the engineering is so 
precise that the sprinkler can only stand the rigors of being threaded into a 
fitting once and then it's useless. Or maybe there are sprinkler manufacturers 
reps on the 13 committee that know how fragile and un-robust sprinklers are? 
Why would you build something could only be threaded in once? I'm glad they 
don't manufacture pipe or fittings.

Ron fletcher Sent from my iPhone

 On Feb 6, 2015, at 4:43 PM, John Denhardt jdenha...@stricklandfire.com 
 wrote:
 
 Mark - well said. I totally agree. 
 
 Sent from my iPhone
 
 On Feb 6, 2015, at 6:29 PM, Mark A. Sornsin, P.E. masorn...@kfi-eng.com 
 wrote:
 
 My two cents is that it is not only the potential stress to the sprinkler 
 from removal/replacement, but the potential for damage during handling.  
 This is especially true for QR sprinklers.
 
 From the EOR perspective, I have them replaced with new regardless of if it 
 could be kept in a drop.
 
 I understand there may be differing perspectives when you are in a 
 competitive bid that doesn't address the issue, or you have an owner griping 
 about every dollar spent.
 
 Mark A. Sornsin, P.E. | Karges-Faulconbridge, Inc. | Fire Protection 
 Engineer | Fargo, ND | direct: 701.552.9905 | mobile: 701.371.5759 | 
 http://www.kfiengineers.com
 
 -Original Message-
 From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] 
 On Behalf Of accentf...@aol.com
 Sent: Friday, February 06, 2015 4:05 PM
 To: sprinklerforum@lists.firesprinkler.org
 Subject: Re: Relocate sprinklers with drops RETORT
 
 Good afternoon, All:
 
 I thought a previous discussion revealed that currently IF the sprinkler 
 stays in the RC, weld-o-let, fitting, etc., then it can be  reinstalled if 
 the sprinkler has not actually been removed from the original  
 fitting/outlet.
 I believe the concern was the amount of 'stress' applied to the  sprinkler 
 when trying to remove it - and possible damage resulting from the  'torque'.
 Previously, everyone seemed to be on board with this  approach.
 
 Cordially-
 
 Jerry
 _accentfire@aol.com_ (mailto:accentf...@aol.com)
 
 *Jerry D. Watts, SFPE
 President  Co-Founder
 ACCENT FIRE ENGINEERING INT'L. Ltd.**
 Santa Fe, New Mexico USA
 (800) 503.1961 nationwide
 
 *New Mexico Journeyman Sprinklerfitter Lic.  #08228
 
 **Licensed Fire Protection Engineers -  Architects/Inspectors/Fire
 Investigators:  AZ  CA  CO   NM  NV  NY  TX  UT  KS  MD  MS
 
 
 
 In a message dated 2/6/2015 2:04:42 P.M. Mountain Standard Time, 
 pe...@waynefire.com writes:
 
 Based on  the 2nd draft, this is what the 2016 language will say unless it 
 is  Successfully NITMAM ed
 
 6.2.1.1*
 When a sprinkler is removed  from a fitting or welded outlet, it shall not 
 be reinstalled except as  permitted by 6.2.1.1.1.
 6.2.1.1.1
 Dry sprinklers shall be  permitted to be reinstalled when removed in 
 accordance with the manufacturer's  installation and maintenance 
 instructions.
 
 A.6.2.1.1
 Sprinklers should be permitted to be reinstalled when the sprinkler being 
 removed from the system remains attached to the original fitting or welded 
 outlet, provided care has been taken to ensure the sprinkler has not been 
 damaged. Flexible hose connections are considered a fitting.
 In new  installations, where sprinklers are installed on pendent drop 
 nipples or  sidewall sprinklers prior to final cut-back, protective caps 
 and/or straps  should remain in place until after the drop nipple has been 
 cut to fit to the  final ceiling elevation.
 
 This is my opinion only and does not  constitute the official opinion of the 
 NFPA.
 
 Peter Schwab
 VP of  Purchasing  Engineering Technologies
 
 Wayne Automatic Fire  Sprinklers Inc.
 222 Capitol Court
 Ocoee, Fl 34761
 
 Mobile: (407)  468-8248
 Direct: (407) 877-5570
 Fax: (407)  656-8026
 
 www.waynefire.com
 
 
 
 
 -Original  Message-
 From: Sprinklerforum
 [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of michael 
  G
 Sent: Friday, February 06, 2015 3:56 PM
 To:  sprinklerforum@lists.firesprinkler.org
 Subject: RE: Relocate sprinklers  with drops
 
 I would have to agree with Richard,  He is not pulling  the head out of the 
 piping, the Boss of the sprinkler is taking no extra  strain and there is no 
 extra stress added on the sprinkler head its  self.  Only the piping is 
 being removed, cut threaded and  reinstalled.  We basically do this when we 
 install a system
 
 We  run the branch line, install a 0-2 and elbow, the drop and a head with 
 the  support ring installed already, so that when we do our initial testing 
 for  leaks, the drops are tested all the way to the sprinkler head. The 
 reason for  this is, 1) to eliminate the number of potential leaks at the 
 end of the job  while conducting the final pressure test. 2) if there is a 
 bad head or  

RE: foam delivery times

2015-01-30 Thread RFletcher
I have always just done cowboy math to give them a rough idea of delivery time. 
Volume of system piping/demand gpm=approximate time (500 gallon volume/1000 gpm 
demand = .5x60=30 seconds) to get water to the last generator. There will 
typically be at least one timed discharge test with just water and another with 
foam so the calculated time is really of no consequence.

They usually want to see the flow for the overhead sprinkler system simulated 
during the HEF test by discharging the calculated supply gpm from the test 
header. It can be a little tricky if the pull station used to activate the 
system also starts the pumps. We would flow the test header before the test and 
wire the valve handles in position after the required flow was achieved. Then 
close the test header control valve. When the deluge valve tripped for the test 
we would quickly open the test header control valve to simulate both HEF and 
sprinkler flow together.
Ron F

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Fairchild, Jack
Sent: Friday, January 30, 2015 12:31 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: foam delivery times

I met with Mike Mohomet and the rest of the sprinkFDT group while working on my 
Great Adventure analysis.  They told me the programs listing limited them to 
four heads.

Jack Fairchild


___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Hot box or other types of exterior fire riser enclosures

2015-01-27 Thread RFletcher
We build what we call a pump in a box 10'X18' but it could be made smaller to 
house only risers. They are structurally designed for the conditions at the 
intended location, all metal siding and roof with a structural steel base. 
Pre-piped, insulated, heated, lighting, fire alarm conduit and an electrical 
breaker panel. Routinely we build 1,500 and 2,000 gpm diesel pumps, deliver 
them on a truck and crane into place. The riser only house could probably be 
pretty small, maybe 5'X5'. Can't say how serviceable they would be if a valve 
had to be replaced but I'm sure everything could made accessible enough to 
operate and test.
Ron F

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of craig.pr...@ch2m.com
Sent: Tuesday, January 27, 2015 9:43 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Hot box or other types of exterior fire riser enclosures

Got an Industrial site, mix of flammable processes and non-hazardous processes. 
 Multiple buildings, open sided structures, no walls.  Location is in the 
south.  Freezing is possible.  

Original scope has typical block buildings for the fire risers.  Some buildings 
have two systems, others may have 3-5 systems.

Space on the layout is tight and of course Fire Protection is the one that they 
are looking at to reduce footprint.  They had three 12x10 buildings in estimate 
for the various areas.

What was asked about is using a Hot Box or similar smaller heated enclosure to 
just house the system valves and riser components.  No room inside for much 
more than that.  Real tight and compact.  To work on systems would require the 
box to be opened for access.

Anyone used anything like this?  

My main concern is structural integrity against fire. 

This is a FM insured facility so that could play into the decision.

My preference is a building, not a gingerbread house.

Any info or experience or possible vendors of such would be appreciated.

Craig L. Prahl 
Fire Protection Group Lead
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29303
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
craig.pr...@ch2m.com

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Bracing for Pipe on Pipe Stands

2015-01-08 Thread RFletcher
We have started running the bypass line on the floor instead of over the pump 
as usual so that it can be braced to the floor. Sometimes there isn't anything 
around a pump to brace to other than the floor. We also brace the legs of the 
fuel tank to the wall or floor.
Ron F

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of J. Scott Mitchell, PE
Sent: Wednesday, January 07, 2015 8:52 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Bracing for Pipe on Pipe Stands

Doesn't NFPA 13 allow engineer certified bracing components to be used in lieu 
of listed components?

Sent from my Verizon Wireless 4G LTE smartphone

div Original message /divdivFrom: Jerry Van Kolken 
jvankol...@mfpc.us /divdivDate:01/07/2015  4:43 PM  (GMT-06:00) 
/divdivTo: sprinklerforum@lists.firesprinkler.org /divdivSubject: 
Bracing for Pipe on Pipe Stands /divdiv /divI've been looking for an 
exception for installing bracing on pipe on a pipe stand with either a full 
clamp or U-bolt holding the piping to that stand. I can't find any references. 
The closest reference would be NFPA 13 9.3.5.5.11 (13ed), but the way its word 
make think only U-bolts that have the 30 deg bend would work. Is there another 
reference? 



Jerry Van Kolken

Millennium Fire Protection Corp.

101 Copperwood Way, Suite H

Oceanside, CA 92058

(760) 722-2722 FX 722-2730



___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Re: Pressure Relief Valve on Wet Pipe System

2015-01-07 Thread RFletcher
Things are a pain. They have to be plugged for the 200# test. Then drain the 
system to reconnect. We put a ball valve before the relief so we can test and 
reconnect without draining.

Ron fletcher Sent from my iPhone

 On Jan 7, 2015, at 12:05 PM, Aaron Peck amp...@me.com wrote:
 
 I wonder if I've been doing it wrong all along since 2010, but NFPA 13, 2013
 Ed. 7.1.2.1 require a pressure relief valve on ALL wet pipe sprinkler
 systems? I can't tell you how many times in the past none have been
 installed. Granted they might not have been all designed according to 2010+,
 but just surprised this hasn't jumped out at me before.
 
 
 
 Looking back the 2007 code mentions only in gridded wet pipe systems then
 2010 eliminates the word gridded as well as the 2013 code reads the same
 as 2010. What's strange is my 2010 Hand book doesn't denote that as a
 changed section, actually none show up. Does the Hand book remove those that
 are there in the standard version?
 
 
 
 Well I learned something knew.
 
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Re: Conveyor equipment in storage occupancies

2015-01-05 Thread RFletcher
What edition of 13 are you using?

Ron fletcher Sent from my iPhone

 On Jan 5, 2015, at 12:16 PM, Steve Leyton st...@protectiondesign.com wrote:
 
 So ... I get hired to write a tech report on an S-1 occupancy and it's
 pretty straightforward since the existing (brand new and never occupied)
 building is furnished throughout with ESFR.   There are no complications
 and I get the report approved and ... the client just contacted me in a
 panic asking for a new report or an addendum to the previous one that
 addresses their conveyor equipment.   That they somehow NEVER mentioned
 or showed on any of the plans that I was given for reference.I have
 a nagging suspicion that they may have been trying to sneak it into the
 building but ...  it's also possible that I'm getting paranoid in my
 mid-life crisis. 
 
 
 
 Anyway, besides the obvious regarding obstructions as they pertain to
 ESFR, can anyone tell me if there are any trap doors in this application
 that I might want to know about before taking a meeting with the client
 and the fire official?   I came away from a brief telecon with the
 vendor for the equipment a bit concerned, as he couldn't offer me
 anything of substance regarding connection points for sprinkler piping
 under the widest belts and platforms (he's checking and will get back to
 me).In all these years I've never fire protected a system like this;
 have done rollers, push-backs, luggage handling systems at two major
 airports, dry cleaning handling systems, rotating retail clothing
 fixtures, etc., etc. but not a storage conveyor.   Just want to be sure
 there's no ticking IED's that I haven't accounted for ...
 
 
 
 Happy New Year everybody!
 
 
 
 Steve Leyton
 
 PROTECTION DESIGN  CONSULTING
 
 2851 Camino del Rio South, Suite 210
 
 San Diego, CA 92108
 
 ---
 
 Ph:   619.255.8964 - ext. 102
 
 Fax:  619.255.9364
 
 Cell:  619.972.5696
 
 
 
 
 
 
 
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: A Poll of the Experienced

2014-12-09 Thread RFletcher
I did the flow test. S-170 R-155, 3950 gpm through a 4 diffuser. The best part 
was at a meeting when the Fire Marshall said that they may reject our plans 
because required fire flow is 4,000 gpm and the flow test was 50 gpm short. I 
am not kidding. Luckily we they approved our plans despite the short fall. They 
have responsibility for an industrial park with probably 20-30  ESFR buildings 
400k sqft. The more I travel to new jurisdictions the more I learn.
Ron F

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of craig.pr...@ch2m.com
Sent: Tuesday, December 09, 2014 2:59 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: A Poll of the Experienced

Through a 6 lead to the hydrant, right?  LOL

No problem, we can calculate that..

Craig L. Prahl 
Fire Protection Group Lead
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29303
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
craig.pr...@ch2m.com


-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of mphe...@aerofire.com
Sent: Tuesday, December 09, 2014 3:20 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: A Poll of the Experienced

For the record, one jurisdiction we work in requires that the 4000 GPM fire 
flow be deliverable through a single 4 hydrant butt, and of course with 20 psi 
residual in the main.

Mark at Aero
602 820-7894

Sent from my iPad

On Dec 8, 2014, at 3:27 PM, Steve Leyton 
st...@protectiondesign.commailto:st...@protectiondesign.com wrote:

Chris - if I have a branch line with three 25K ESFR sprinklers and a similarly 
sized branch line (say it's 3 nominal) with three 5.6K sprinklers, which group 
of sprinklers will discharge more water at 75psi?   Hydrants are supplied by a 
pipe of fixed size, which has inherent capacity as well as limits.  If we 
accept that the lateral to the hydrant has an absolute maximum capacity, then 
the number of open ports won't facilitate more flow.  But within that 
threshold, if there are two 4 ports then it affords the FD some options, such 
as taking 2,000 gpm (or more) from one hydrant without needing a high residual 
pressure to do that, whether it's one or two or three engines.   My references 
to strategies and hydrant types was intended to be in that context.

The point of site and infrastructure planning is, in part, to allow for as many 
eventualities as possible, which include some of what you allude to toward the 
end of your comment.  Hydrants get damaged, aren't regularly maintained, can be 
obstructed countless ways, etc., etc.   Overdesigning fewer hydrants proves a 
more demanding condition hydraulically and may be the only option if a site 
that requires 4K GPM only has three hydrants for whatever reason.

SL


-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Cahill, Christopher
Sent: Monday, December 08, 2014 10:37 AM
To: 
sprinklerforum@lists.firesprinkler.orgmailto:sprinklerforum@lists.firesprinkler.org
Subject: RE: A Poll of the Experienced

If you have two 4 ports you can take a LOT of water from that hydrant at 
modest residual pressures. Huh?  The number/size of openings don't have a 
correlation to the residual pressure. You are still stuck with the same curve 
of the available water supply. What you said is if I put in 6 connections I'd 
get more water at the same residual vs. 4?  That's the way I read it anyway.

I can almost say universally you don't get any more water out of a hydrant with 
2-4 connections than 2-2.5 plus 1-4.  The amount of water one can get out of 
a single hydrant is more limited by the fire truck connected to it.  The only 
real exception is if two trucks connect to the same hydrant.  Then 2-4 would 
be better but I'd bet not by a lot. IOW 10,000 gpm won't practically go through 
a 1,500 gpm fire truck. And fire flow provided grows with arriving trucks.  In 
most cases the next truck goes to the next hydrant up the street to get more 
water.  Otherwise, in most cases you have to shut down the first hydrant to 
connect the second truck.

Are there exceptions, sure, a lot of varying scenarios.  For example, you could 
run out of hydrants in practical proximity, some departments may be able to 
afford 4 valves they hook to the hydrant before they turn it on to allow a 
second connection if necessary, or things are burning down anyway and stopping 
flow to connect a second hydrant is NBD.

Chris Cahill, PE*
Associate Fire Protection Engineer
Burns  McDonnell
Phone:  952.656.3652
Fax:  952.229.2923
ccah...@burnsmcd.commailto:ccah...@burnsmcd.com
www.burnsmcd.comhttp://www.burnsmcd.com
*Registered in: MN


Proud to be #14 on FORTUNE's 2014 List of 100 Best Companies to Work For





-Original Message-
From: Sprinklerforum 

Re: transverse flue space clarification

2014-12-09 Thread RFletcher
If there are rack uprights with horizontal and diagonal bracing but no 
permanent fixed solid shelving I would say that you have transverse flue 
spaces. My 2 cents.

Ron fletcher Sent from my iPhone

 On Dec 9, 2014, at 5:25 PM, Greg McGahan g...@livingwaterfp.com wrote:
 
 Storage of non-typical objects  - ie car parts of all different shape and
 sizes on wire rack shelves...
 
 There are no pallets or standard sized boxes  etc therefore there is a lot
 of open spaces between items. What does this do to the definition and
 requirements for transverse flue spaces?
 
 Are the vertical frames automatically flue spaces or in this scenario is it
 possible that there just aren't any definable transverse flue spaces?
 
 Thanks,
 
 Greg McGahan
 Living Water Fire Protection, LLC http://www.livingwaterfp.com
 1160 McKenzie Road
 Cantonment, FL 32533
 850-937-1850
 fax 850-937-1852
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: A Poll of the Experienced

2014-12-08 Thread RFletcher
Absolutely agree with you about the non-value of extrapolating the flow test 
beyond the observed flow. The part I'm not so sure I would agree with is 
requiring the 20 psi minimum at the onsite hydrants. The IFC commentary notes 
that the 20 psi is used because it is the recommended minimum pressure for 
fire engine use by the water authorities in order to minimize the possibility 
of creating a negative pressure in the water main and the resulting damage to 
the water supply system. Many of the buildings we are involved in require 
4,000 gpm. They have private fire loops around the property with usually two 
connections (with BFP's)  to the city water system. Doing the hydraulics 
flowing 1,000 gpm @ 20 psi for the most demanding four hydrants usually 
requires a minimum pressure of around 45-50 psi at the city connections. I 
don't see how taking the pressure in the private fire loop below 20 would 
damage anything in the municipal system because the pressure would always be 
above 20 psi at the connection to the city mains. I don't know about the effect 
on the pumper truck but I think as long as they have water at any pressure they 
will continue pumping.
Ron F

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of craig.pr...@ch2m.com
Sent: Monday, December 08, 2014 6:52 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: A Poll of the Experienced

Ah, Fire Flow.  Now you will gets heads spinning.

First, let's start with the basics.  There are at least five methods used by 
various authorities to determine Fire Flow.  So if you are dealing with this, 
be sure Appendix B is the correct method used by the local/state fire 
authority.  Section 507 in the IFC states that Fire Flow is to be determined by 
an Approved Method.  AHJ will provide or confirm that approved method.  
Appendix B is not part of the Code and is not always adopted through the legal 
adoption process, that's why you have to ask, you can't assume.

But let's say we're past that and Appendix B is the approved method.

The next step is you need to also verify that the local AHJ will permit the 
flow reduction rate based on sprinklers, do not assume that to be the case.  
I'm assuming that you might have a warehouse with a fairly high hazard level if 
you're using ESFR so in cases such as that or where chemicals or other high 
hazards are present I have had the AHJ deny the reduction.  So be sure, don't 
assume you can apply the reduction.

So you've gone down the chart and found your building requires 8000 gpm for 4 
hours.   The city supply or private fire service system needs to be able to 
provide that flow and duration to the fire loop serving the hydrants.   A 
minimum of 20 psi residual needs to be available at every hydrant on the loop.  
This is will be the suction pressure for pumper apparatus.   You can assume 
that in an event that would require 8000 gpm there will be multiple pumpers 
connected to multiple hydrants.  

The other issue when dealing with a municipal supply is make sure they can 
ACTUALLY supply the demand.  I've had too many single outlet flow tests and the 
testing agency extrapolated the curve to show they can meet the demand.  I 
reject those tests.  When conducting follow-up tests involving multiple 
hydrants, more often than not was it proven that the municipality could not 
actually flow that much water through their system.   Extrapolated tests are 
worthless.  You need real data.

So the 20 psi pressure needs to be at the hydrants.

Fire flow is the water needed to actually fight the fire through the use of 
manual hand hose lines.  This is totally separate and unrelated to sprinkler 
flow and hose stream allowance.

I was involved with a project for a warehouse where the fire fight lasted 13 
hours, needless to say they used a LOT of water.   

This is one topic where the majority of fire protection engineers and designers 
have not been educated.  It is a Code requirement, not an option as most think. 
  



Craig L. Prahl 
Fire Protection Group Lead
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29303
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
craig.pr...@ch2m.com


-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of mphe...@aerofire.com
Sent: Friday, December 05, 2014 9:29 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: A Poll of the Experienced

I think I agree with you, but to be very specific, let's assume I'm designing a 
new building on a greenfield site which is served by a public water system. The 
building is type V construction, 600,000 square feet and fully protected with 
ESFR sprinklers. Table B105.2 indicated a fire flow rate of 8000 GPM, reduced 
to 4000 GPM for sprinkler credit, at minimum 20psi. My question is, WHERE is 
this 4000 GPM at 20 psi measured? At the city water main connection? Or 

RE: Balancing In-Rack Sprinklers

2014-12-04 Thread RFletcher
Sounds like you are K'ing the overhead system into the racks, if should the 
other way around. K the racks into the overhead system. Personally I would 
revisit the calc's and make them balance. A 15 psi difference is too far apart.
Ron F

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of B.J. Newlin
Sent: Thursday, December 04, 2014 1:55 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Balancing In-Rack Sprinklers

To balance the demand pressure with an overhead system isn't all I need is to 
create a k-factor at the point the in-racks tie into the overhead system?

 

I have done this, but the pressure demand for the in-rack system is still 15 
psi less than the pressure at that junction point for the overhead system.
Is that ok, or did I do something incorrectly?

 

For example 203 is the junction node.  At that point the overhead system demand 
is 99.09 psi with ~1450 gpm flowing.

 

I come up with a k factor of  145.66 (1450/sqrt of 99.09).

 

When I insert this K at the node and run my calcs, I end up with only 84.2 psi 
at node 203 for the in-racks.  I assume this is acceptable since I think I'm 
doing everything properly, but I can't figure out how to explain it to the FM 
rep.

 

Any help would be appreciated. (Below is what i believe is the applicable code 
text)

 

 

 

23.4.2.4 Hydraulic Junction Points.

23.4.2.4.1 Pressures at hydraulic junction points shall balance

within 0.5 psi (0.03 bar).

23.4.2.4.2 The highest pressure at the junction point, and

the total flows as adjusted, shall be carried into the calculations.

23.4.2.4.3 Pressure balancing shall be permitted through the

use of a K-factor developed for branch lines or portions of

systems using the formula in 23.4.2.5.

23.4.2.5 K-Factor Formula. K-factors, flow from an orifice, or

pressure from an orifice shall be determined on the basis of

the following formula:

K

Q

P n =

where:

Kn = equivalent K at a node

Q = flow at the node

P = pressure at the node

 

B.J. Newlin

Service Sales

Aegis Fire Protection LLC

bjnew...@aegisfirepro.com

P (913) 825-0343

F (913) 322-4475

C (913) 238-0035

 

Whoever is careless with the truth in small matters cannot be trusted with 
important matters 
― Albert Einstein 

 

 

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Contradiction if FDC codes? NFPA 13 2013

2014-11-25 Thread RFletcher
noun: supplement; plural noun: supplements - something that completes or 
enhances something else when added to it.

How can the possibly pressure be supplemented? Using enough pressure to open 
the FDC check valve will close the valve in the riser. The rule should be 
changed to either calculated or just require a 4 2-way FDC for everything.

There are buildings in Phoenix with 12 -  2 1/2  FDC inlets because of an old 
amendment requiring one 2.5 inlet for every 250 gpm system demand. The rule 
was changed when the FD figured out that a pumper truck only carried enough 
equipment to connect to four inlets.
Ron F

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Tim Stone
Sent: Tuesday, November 25, 2014 6:56 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Contradiction if FDC codes? NFPA 13 2013

NFPA  13 is a minimum design /installation Standard, NOT A CODE.

Fire department Pump Trucks are equipped with variable pressure pumps which 
enables the pump operator to increase extra boost when needed.
I don't see any contradiction.
 
Regards,
G. Tim Stone

G. Tim Stone Consulting, LLC
NICET Level III Engineering Technician
Fire Protection Sprinkler Design
and Consulting Services

    117 Old Stage Rd. - Essex Jct., VT. 05452
CELL: (802) 373-0638   TEL: (802) 434-2968   Fax: (802) 434-4343
   tston...@comcast.net

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Cory Power
Sent: Tuesday, November 25, 2014 8:39 AM
To: sprinklerfo...@firesprinkler.org
Subject: Contradiction if FDC codes? NFPA 13 2013

Could someone explain to me the intent behind this code and if the Annex is 
contradicting?

8.17.2* Fire Department Connections.

8.17.2.3* Size. The size of the pipe for the fire department connection shall 
be in accordance with one of the following:

(3) For hydraulically calculated systems, the fire department connection shall 
be permitted to be less than 4 in.
(100 mm) and no less than the size of system riser, where serving one system 
riser.

A.8.17.2.3 The purpose of a fire department connection is to supplement the 
pressure to an automatic fire sprinkler system.
It is not the intent to size the fire department connection piping based on 
system demand. For multiple system risers supplied by a manifold, the fire 
department connection need not be larger than that for an individual system.

---
This email has been checked for viruses by Avast antivirus software.
http://www.avast.com

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


CA Title 8

2014-11-11 Thread RFletcher
We have been working in CA for some years now and it seems like something new 
and counterintuitive comes up every time we start a new project. A GC is 
telling us we have to get a  CA Department of Industrail Relations, Division of 
Occupational Safety  Health (CAL/OSHA) safety permit. It is apparently 
required for doing any work greater than 36' above the floor. The web site says 
that the permit is for Buildings/Structures, Scaffolding/Falsework, 
Demolition, Trenches/Excavations I commented to the GC that we were doing a 
sprinkler system and it shouldn't be confused with Falsework but he missed 
the pun and said we had to get a permit. Have anyone had experience with this 
permit requirement.
Ron F
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: FM Global requirements

2014-11-10 Thread RFletcher
If your contract requires you to meet both I would double check everything you 
do against the FM Global data sheets. We have come across some differences that 
are, let's say counterintuitive. For instance FM no longer seems to recognize 
concrete twin tee construction like NFPA does. FM limits the deflector distance 
to 22 max and doesn't allow 1 below the bottom of the tee like NFPA. Also the 
FM hazard classifications can result in some unusual area densities, like a 
parking garage at .30/1000. Recently we had to do two submittals, one to the 
AHJ using NFPA and one to FM with their requirements. It really gets 
interesting when a core and shell job done to NFPA becomes a FM Global property 
for TI. FM will write a review letter that lists deficiencies in the core and 
shell based on their base requirements. We are just finishing a job where FM 
even recommended moving the existing riser locations requiring new underground 
lead-ins. As Craig said most of FM's requirements are negotiable, they are not 
an AHJ.
Ron F 

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Todd - Work
Sent: Monday, November 10, 2014 3:16 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: FM Global requirements

What Craig said, but FM typically does not recognize QR sprinkler reductions.

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
www.fpdc.com
860-535-2080 (ofc)

 On Nov 10, 2014, at 11:40 AM, craig.pr...@ch2m.com craig.pr...@ch2m.com 
 wrote:
 
 One thing that needs to be understood is that FM is not an AHJ, they make 
 recommendations not requirements.  
 
 FM should provide a letter or review of the project and provide 
 recommendations to the owner.  Then the owner takes those recommendations and 
 tells you as the contractor which ones they want to consider.  It's not a 
 blanket set of requirements.  You should not have to determine which Data 
 Sheets to follow and which not and to what extent.  
 
 I have had some clients that negotiate everything with the FM rep., others 
 take all the recommendations at 100% so your results may vary.
 
 Also I have found that FM opinions and directions vary depending on which 
 office and which individuals you deal with.  
 
 This is not a slam or criticism of any of the FM people I've dealt with over 
 the years.  Just an observation.
 
 So you need to let the owner know there may be changes but he needs to get 
 with the FM rep, receive FM's recommendations and then the owner directs 
 which ones he wants you to employ.
 
 Craig L. Prahl
 Fire Protection Group Lead
 CH2MHILL
 Lockwood Greene
 1500 International Drive
 Spartanburg, SC  29303
 Direct - 864.599.4102
 Fax - 864.599.8439
 CH2MHILL Extension  74102
 craig.pr...@ch2m.com
 
 
 -Original Message-
 From: Sprinklerforum 
 [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of 
 Dewayne Martinez
 Sent: Monday, November 10, 2014 11:27 AM
 To: sprinklerforum@lists.firesprinkler.org
 Subject: FM Global requirements
 
 I have a project that may be switching to FM global requirements.  I haven’t 
 worked with FM for a while so what are the main differences between NFPA 13 
 and FM?  The plans have already been approved by the AHJ so the owner is 
 looking for any potential cost impact.  I know that the products used should 
 be FM approved.  I did take a reduced design area for my light hazard areas.
 
 Thanks,
 
 
 
 Dewayne
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
 er.org ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
 er.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Expansion Joint vs. Seismic Expansion Joint

2014-10-22 Thread RFletcher
I have always thought every USACoE project required seismic bracing no matter 
the location. I believe (going by memory) that a coupling is required within 2 
ft. of an expansion joint and the 6 elbow thing at a seismic joint.
Ron F 

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Aaron Peck
Sent: Tuesday, October 21, 2014 10:25 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Expansion Joint vs. Seismic Expansion Joint

I seem to remember there's no difference. Except on this project I have an 
irregular expansion line and the USACoE plans only indicate expansion joints on 
the mains, allowing branch lines to cross it without a problem.

This project doesn't require seismic bracing. So any thoughts if I should bring 
it up about the branch lines crossing it? They are 2 in size to 1.

Sent from my iPhone
Aaron M. Peck, SET Fire Protection
Skype +1(202)407-9079
Cambodia +855(0)78700407

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Shadowed area behind built in cabinet and in widow sill

2014-10-06 Thread RFletcher
1.7 New Technology Nothing in this standard shall be intended to restrict new 
technologies or alternate arrangements... Based on the recently discussed 
conservative committee actions I would think that anything in the later 
editions of 13 should be allowed as an alternate arrangement.  Say something 
in 2002 edition that was later proved to be wrong through full scale testing. 
Would you force a licensed contractor to install it wrong because the AHJ 
hasn't adopted the standard with the new data with the  corrections? Or as a 
licensed contractor would you knowingly install something that has been proven 
to be wrong by today's standards because it was okay in the 2002 editionRon F 

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Mark A. Sornsin, P.E.
Sent: Monday, October 06, 2014 6:50 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Shadowed area behind built in cabinet and in widow sill

There are two lines of reasoning I have seen on matters such as this:
1.We aren't following the newer NFPA 13 - period.
2.The newer standard may have what the NFPA committee believes to be the best 
criteria, but the ICC and our local codes folks have not weighed in on the 
changes to the standard. Therefore, we cannot accept those 'clarifications.'

WE may KNOW that the changes won't affect the future code revisions; but the 
AHJ doesn't know and most times won't take the chance.

Mark A. Sornsin, P.E. | Karges-Faulconbridge, Inc. | Fire Protection Engineer | 
Fargo, ND | direct: 701.552.9905 | mobile: 701.371.5759 | 
http://www.kfiengineers.com

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of svang...@aerofire.com
Sent: Friday, October 03, 2014 7:02 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Shadowed area behind built in cabinet and in widow sill

We are bound to NFPA 13 (2002).  We have an ECHSW above the door in a room.  On 
the opposite wall is a window and sill that does not create an additional floor 
area.  There is a built in cabinet that partially obstructs the window sill and 
creates a shadow of 2 sq.ft. between the cabinet and the window over the window 
sill.  We informed the AHJ that per NFPA 13 (2007) 8.5.3.2.4 sprinklers are 
spaced to walls and not windows if they do not create additional floor area.  
We also pointed to NFPA 13 (2013) 8.1.1(3)  A.8.1.1(3) which indicate shadow 
areas are acceptable so long as the other obstruction guidelines are followed.  
The AHJ stated they cannot accept the newer standard clarifications on this 
issue.

Is there something I am missing in NFPA 13 (2002) that states this design is 
acceptable?

  Thanks,

Sean




___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

__
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com 
__

__
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com 
__
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Shadowed area behind built in cabinet and in widow sill

2014-10-06 Thread RFletcher
I will more than likely be admonished for this, again. But it's more likely the 
hole occupied by an uniformed, unqualified or unreasonable AHJ.
Ron F

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Bill Brooks
Sent: Monday, October 06, 2014 7:56 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Shadowed area behind built in cabinet and in widow sill

I see some worms peeking through the lid of the can.  Is this going to spiral 
us down the EOR hole again or is this another hole occupied by sprinkler 
designers/contractors?

Bill Brooks

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of rfletc...@aerofire.com
Sent: Monday, October 06, 2014 10:34 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Shadowed area behind built in cabinet and in widow sill

1.7 New Technology Nothing in this standard shall be intended to restrict new 
technologies or alternate arrangements... Based on the recently discussed 
conservative committee actions I would think that anything in the later 
editions of 13 should be allowed as an alternate arrangement.  Say something 
in 2002 edition that was later proved to be wrong through full scale testing. 
Would you force a licensed contractor to install it wrong because the AHJ 
hasn't adopted the standard with the new data with the corrections? Or as a 
licensed contractor would you knowingly install something that has been proven 
to be wrong by today's standards because it was okay in the 2002 editionRon F 

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Mark A. Sornsin, P.E.
Sent: Monday, October 06, 2014 6:50 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Shadowed area behind built in cabinet and in widow sill

There are two lines of reasoning I have seen on matters such as this:
1.We aren't following the newer NFPA 13 - period.
2.The newer standard may have what the NFPA committee believes to be the best 
criteria, but the ICC and our local codes folks have not weighed in on the 
changes to the standard. Therefore, we cannot accept those 'clarifications.'

WE may KNOW that the changes won't affect the future code revisions; but the 
AHJ doesn't know and most times won't take the chance.

Mark A. Sornsin, P.E. | Karges-Faulconbridge, Inc. | Fire Protection Engineer | 
Fargo, ND | direct: 701.552.9905 | mobile: 701.371.5759 | 
http://www.kfiengineers.com

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of svang...@aerofire.com
Sent: Friday, October 03, 2014 7:02 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Shadowed area behind built in cabinet and in widow sill

We are bound to NFPA 13 (2002).  We have an ECHSW above the door in a room.
On the opposite wall is a window and sill that does not create an additional 
floor area.  There is a built in cabinet that partially obstructs the window 
sill and creates a shadow of 2 sq.ft. between the cabinet and the window over 
the window sill.  We informed the AHJ that per NFPA 13 (2007) 8.5.3.2.4 
sprinklers are spaced to walls and not windows if they do not create additional 
floor area.  We also pointed to NFPA 13 (2013) 8.1.1(3) 
A.8.1.1(3) which indicate shadow areas are acceptable so long as the other 
obstruction guidelines are followed.  The AHJ stated they cannot accept the 
newer standard clarifications on this issue.

Is there something I am missing in NFPA 13 (2002) that states this design is 
acceptable?

  Thanks,

Sean




___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

__
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com 
__

__
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com 
__
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org

RE: Pressure Limiting Drivers

2014-10-02 Thread RFletcher
Very effective, we use them all the time. 
Ron F

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Mike Hairfield
Sent: Thursday, October 02, 2014 10:48 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Pressure Limiting Drivers

I've used them on numerous projects.
Saves lots of water during the 30 minute weekly run.
Mike

 Date: Thu, 2 Oct 2014 11:44:48 -0600
 From: silva...@shaw.ca
 To: sprinklerforum@lists.firesprinkler.org
 Subject: Pressure Limiting Drivers
 
 I have a diesel engine driven fire pump that will have a pressure of about 
 200 psi at churn, including the city supply. My first thought was using a 
 pressure reducing valve downstream of the fire pump. But the pump supplier 
 suggested using a pressure limiting driver on the fire pump. anyone used one 
 before? Any NFPA restrictions?
 
 Thanks,
 
 Tony 
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
  
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Pressure Limiting Drivers

2014-10-02 Thread RFletcher
They add $3-5k to the price of a pump. Depending on static versus residual they 
can really payoff in usable pressure without having to be concerned with the 
churn pressure.
Ron F 

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of John Denhardt
Sent: Thursday, October 02, 2014 11:57 AM
To: 'sprinklerforum@lists.firesprinkler.org'
Subject: RE: Pressure Limiting Drivers

Very effective - makes a nice system.  However, it does add cost.  I personally 
see these types of systems be specified more due to their benefits.

John

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of rfletc...@aerofire.com
Sent: Thursday, October 02, 2014 2:17 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Pressure Limiting Drivers

Very effective, we use them all the time. 
Ron F

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Mike Hairfield
Sent: Thursday, October 02, 2014 10:48 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Pressure Limiting Drivers

I've used them on numerous projects.
Saves lots of water during the 30 minute weekly run.
Mike

 Date: Thu, 2 Oct 2014 11:44:48 -0600
 From: silva...@shaw.ca
 To: sprinklerforum@lists.firesprinkler.org
 Subject: Pressure Limiting Drivers
 
 I have a diesel engine driven fire pump that will have a pressure of about 
 200 psi at churn, including the city supply. My first thought was using a 
 pressure reducing valve downstream of the fire pump. But the pump supplier 
 suggested using a pressure limiting driver on the fire pump. anyone used one 
 before? Any NFPA restrictions?
 
 Thanks,
 
 Tony 
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
  
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: No Longitudinal Bracing

2014-09-19 Thread RFletcher
If it is in a seismic zone. We do 4 ways at the top of risers only even though 
Phoenix is not in a seismic zone. Maybe that is what he saw.
Ron F

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Steve Leyton
Sent: Friday, September 19, 2014 10:43 AM
To: sprinklerforum@lists.firesprinkler.org; sprinklerfo...@firesprinkler.org
Subject: RE: No Longitudinal Bracing

There isn't an exception for longitudinal bracing.  The exception for lateral 
bracing is where the distance from the point of anchorage
(concrete deck, in this case) to the top of pipe is 6 or less.   The
standard used to say where rods were 6 or less, but now it's the distance from 
the anchor to top of pipe, which means rods measurably
less than 6.   The scenario you describe requires at least longitudinal
bracing.

SML

 




-Original Message-
From: Sprinklerforum
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Owen Evans
Sent: Friday, September 19, 2014 10:35 AM
To: sprinklerfo...@firesprinkler.org
Subject: No Longitudinal Bracing

So I enter a new underground parking area and look up at the fire sprinkler 
piping hanging from a concrete deck. As I look I notice there is no bracing 
other than a 4X at the top of the riser. From the top of the riser it travels 
out about 4' feet and makes a 90 degree turn and travels about 15'. At that 
point it makes a 90 degree turn at a T and makes it's longest run of 
approximately 70'. From there it makes a 90 degree turn for a run of 
approximately 40'. All the hangers are less than 6 so that explains the no 
lateral bracing. My question is, what about longitudinal bracing? I looked in 
13 chapter 9 and it appears that longitudinal bracing would be required. Am I 
missing something? I work exclusively with 13D systems, I don't do commercial 
but I am interested in this situation.


Owen Evans
First-In Residential Design
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Water Velocity

2014-09-16 Thread RFletcher
Ironic that the ETL also requires surge tanks. Belt and suspenders or ignorance?
Ron F

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Reed A. Roisum, C.E.T.
Sent: Tuesday, September 16, 2014 10:32 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Water Velocity

It isn't always engineer ignorance driving the 20 fps.  Air Force ETL 02-15 
requires it for one.

Reed A. Roisum, C.E.T. | Karges-Faulconbridge, Inc. | Fire Protection Designer 
| Fargo, ND | direct: 701.552.9903 | mobile: 701.388.1352 | 
http://www.kfiengineers.com

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Lamar Vaughn
Sent: Tuesday, September 16, 2014 12:04 PM
To: Sprinkler Forum
Subject: Re: Water Velocity

It would really be good if this thread could be shared with the engineering 
community at large. I STILL get specifications that require a maximum velocity 
of 20 fps. Very costly, especially when you have a good water supply.

Lamar Vaughn, SET

On Tue, Sep 16, 2014 at 12:03 PM, Roland Huggins rhugg...@firesprinkler.org
 wrote:

 actually the difference between the results for D-W and H-W does not 
 vary consistently (alas there is not a linear relationship).  To 
 require using D-W at very high velocities is unnecessarily 
 conservative.  At these velocities the pressure loss is so high that 
 it is self regulating so typically occurs only is limited sections of 
 the system.  With all the averaging etc that our process entails, why 
 get anal on ONE piece of the puzzle?  Having said that, one could 
 argue that one should account for the velocity pressure in the 
 discharge calc at high velocities BUT that is needed only when you 
 really have such velocities (like in a water spray
 deluge) verses seeing an assigned value from our process.


 Roland Huggins, PE - VP Engineering
 American Fire Sprinkler Assn.   ---  Fire Sprinklers Saves Lives
 Dallas, TX
 http://www.firesprinkler.org





 On Sep 15, 2014, at 1:56 PM, Damien Shannon damshan...@gmail.com wrote:

  So purely along the lines of Andy Rooney's 'have you ever wondered why'
 :)
  ... FM Datasheet 2-0, while not limiting the allowable velocity, 
  does require that when velocity exceed 30ft/sec, that the 
  calculation be performed via the Darcy-Weisbach Method rather than the 
  Hazen-Williams.
  Entertainment value only, but would seem that the variance between
 results
  in Hazen-Williams versus Darcy-Weisbach become more apparent with 
  higher velocities.
  The 30ft/sec limitation (for application of Hazen-Williams
  calculations)
 in
  FM 2-0 is strangely close to the 10m/sec (32.8ft/sec) limitation in 
  EN
  12845 Rules for Automatic Sprinkler Installations (previously BS 5306).
 
 

 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org

 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
 er.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

__
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com 
__

__
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com 
__
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: flex-coupling at water tank

2014-09-12 Thread RFletcher
I have seen a gimbal type arrangement used above ground outside. I guess if 
freezing is an issue a hot box or putting it in a vault would be an option. I 
have some pictures if that would help. Sorry I don't have any manufacturer or 
model information. They were used on a COE job on an Army base.
Ron F

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of å... 
Sent: Friday, September 12, 2014 9:40 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: flex-coupling at water tank

Is there any experience with review comments or specifications calling for a 
flexible coupling on a welded steel discharge pipe supplying water to a fire 
pump?

2010 IBC;  2010 NFPA:  U.S. Government job:  Category 4 Occupancy
(essential)
Two independent water supplies (municipal underground and above ground tank) 
Frequency of seismic events in this area:  very low, and not strong 10% and 30% 
of gravity for the 1 and 0.2 second period spectral response acceleration.

NFPA 22 is the hammer used to justify asking for the flexible coupling.
The only mention of flexible coupling in NFPA 22 is at Figure Annex B.1.x, for 
underground fiberglass tanks.

I have not seen a flex coupling for a water tank to separate steel 
piping-that-is-fixed-to-the-ground and steel-pipe-that-is-fixed-to-the-tank,  
whether the tank be for water, liquid petroleum or LNG tanks.  Maybe the 
Japanese do it, but I have not seen it in California quake country, either.


*Questions:*
1.  Is there a nationally accepted practice whereby flex-joints are required 
between tanks and their ground based piping?
2.  Are flexible connections listed for outdoor service where freezing and 
​strong solar radiation are present?
3.  Would not seismic bracing be sufficient (a method most of the OG industry 
engages) rather than a flex joint ?  Bracing against seismic event is the 
approach taken by OG, and seems to be the intent of NFPA 22 (Sections 
13.5.2.2.  and for anchor bolts 5.3.2) 2.  Since we are outside, not indoors, 
do the requirements of NFPA 13 ​bracing apply (there is no direct reference 
from NPFA 22 to NFPA 13 with regards to earthquake bracing) apply, since there 
is no structure with which to make a comparison of equivalence [3],[4]?

[1].  IBC-2006-Figure1613_5(01) one second period spectral response [2].  
2013/2010 NFPA 24 12.2.5 To minimize or prevent pipe breakage where subject to 
earthquakes, aboveground pipe shall be protected in accordance with the seismic 
requirements of NFPA 13.
[3].  2010/2013 NFPA 13  Section 9.3.1.2 Alternative methods of providing 
earthquake protection of sprinkler systems based on a seismic analysis 
certified by a registered professional engineer such that system performance 
will be at least equal to that of the *building structure* under expected 
seismic  forces shall be permitted.
[4].  2013/2010 NFPA 13 Section 9.3.3.1 An approved seismic separation assembly 
shall be installed where sprinkler piping, regardless of size,  *crosses 
building seismic separation joints *at ground level and above.

Additional references
2013 NFPA 22 4.12.4.1 Tank structures shall comply with the local building code 
for seismic requirements.
4.12.4.2 Specific design criteria shall be contained in the appropriate chapter 
for the particular tank, or in local codes, whichever is more stringent.
5.3.1 Tanks shall meet the requirements for resistance to earthquake damage in 
accordance with the earthquake design provisions of AWWA D100.
​

Personally, I think corrosion, and not earthquake would have been a better 
​focus of taxpayer money .
​Maybe the specification writers thought to include an internal tank liner AND 
a passive cathodic protection system, to extend the tank life to at least a 
hundredth of the 1000-year earthquake we are designing for .

​Scot Deal
Excelsior Fire/Risk Engineering
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: fume hood / dust collector - sprinklers in?

2014-09-08 Thread RFletcher
Battlefield earth?

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of rongreenman .
Sent: Monday, September 08, 2014 9:42 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: fume hood / dust collector - sprinklers in?

Brad, I had an AHJ like that: sprinklers are better than no sprinklers always 
make a customer sprinkler a building that contained a 1000F degree molten salt 
bath process. even though the manufacturer said that water and molten salt 
don't mix. The AHJ's solution was to shield the machine from the sprinklers. 
That comprised a $37,000.00 hood that left about three feet of floor on either 
side, and eight feet at the ends protected by the sprinklers. The machine 
itself had four levels of redundancy against thermostat failure and each 
thermostat was an electronic device that reported it's condition to a central 
processor that was also in a fail-safe mode. harder to get the thing to turn on 
than to shut down. Stupid, stupid rat creatures. A beer to the first one that 
can name the reference for the quoted materials (without using the internet).


On Mon, Sep 8, 2014 at 7:06 AM, Brad Casterline bcasterl...@fsc-inc.com
wrote:

 Just throw some heads in there like you knew they were required. If 
 Woodrow Call was the AHJ he might say better to have heads and not 
 need them than to need them and not have them

  On Sep 8, 2014, at 8:56 AM, Bill Brooks 
  bill.bro...@brooksfpe.com
 wrote:
 
  Another case of the difference between when required and how to 
  do
 it.  The International Mechanical Code (2012) Sections 510 (Hazardous 
 Exhaust Systems) and Section 511 (Dust, Stock and Refuse Conveying 
 Systems) provide guidance on this.  Again, it shouldn't be up to a 
 sprinkler contractor to figure out whether sprinklers should be 
 installed but only to install per the appropriate standard.  As with 
 most of these issues, we don't know if there is a design professional 
 on this job or whether your regular customer has just installed a new 
 process and has called you to do what's required.  At a minimum you 
 should have a copy of the IMC which is enforced for this location.
 
  So, someone (you??) must assess the installation per IMC Section
 510/511  from end to end.  There is a suppression system reference in 
 Section 510.7.  Some determination needs to be made as to whether the 
 materials are nonflammable and noncombustible under all conditions 
 and at any concentration then make the call on suppression.  The 
 entire exhaust system must be engineered to meet the performance 
 characteristics in the IMC.
 
  Of course, local code amendments will govern as well as any local 
  AHJ,
 insurance requirements etc.
 
  Sprinkler contractors have a long history of being the can-do guys, 
  with
 no good way to transfer scope responsibility to the right place.
 
  Bill Brooks
 
  William N. Brooks, P.E.
  Brooks Fire Protection Engineering Inc.
  372 Wilett Drive
  Severna Park, MD 21146-1904
  410-544-3620
  410-544-3032 FAX
  412-400-6528 Cell
 
 
 
  -Original Message-
  From: Sprinklerforum [mailto:
 sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Dewayne 
 Martinez
  Sent: Monday, September 08, 2014 7:43 AM
  To: sprinklerforum@lists.firesprinkler.org
  Subject: fume hood / dust collector - sprinklers in?
 
  I have a job where they have a small furnace to create molten metal 
  for
 castings.  There is a hood (2x8ft) above the area where they take the 
 used probes  and clean them off.  This duct work goes outside to a 
 dust collector.  How do I determine if sprinklers are needed in the 
 hood and ductwork?
 
  Thanks,
 
  Dewayne
  ___
  Sprinklerforum mailing list
  Sprinklerforum@lists.firesprinkler.org
 
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
 er.org
 
  ___
  Sprinklerforum mailing list
  Sprinklerforum@lists.firesprinkler.org
 
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
 er.org ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org

 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
 er.org




--
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

rgreen...@bates.ctc.edu

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC

They are happy men whose natures sort with their vocations. -Francis Bacon, 
essayist, philosopher, and statesman (1561-1626)

A problem well stated is a problem half solved. -Charles F. Kettering, inventor 
and engineer (1876-1958) ___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org

RE: Seismic bracing

2014-09-05 Thread RFletcher
Some jurisdictions around here require what we call feel good bracing. They 
don't require calculations, or that the building be designed to any seismic 
standard, they just want the minimum bracing. If we want a green tag we have to 
put it in. I guess in this case the question would be if the only requirement 
is local dictate can you install at the max spacing and not do any calc's 
provided it is acceptable to the AHJ?  
Ron F

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Parsley Consulting
Sent: Friday, September 05, 2014 5:11 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Seismic bracing

Stephen,
 I don't believe the AHJ you're dealing with has thought this decision 
through very carefully.  They seem to be equating seismic bracing with 
seismic protection, which includes such other features as flexible couplings, 
clearance requirements, seismic separation assemblies, restraint of branch 
lines, and certain hanger requirements in a building protected against seismic 
damage.  Section 9.3 covers more than just seismic bracing.
 I would recommend you ask the AHJ if they're going to require all of the 
features in NFPA 13 for seismic protection, or just lateral, longitudinal and 
riser bracing.
 It's also relevant to note that if you're going to provide seismic bracing 
you have to make sure you comply with 9.3.5.1.2 (2007), which requires the 
structure to be able to withstand the applied seismic loads.  Based on what 
you've described I would wager a few dollars that they could not do so.
 And, if you still have a mandate to brace, ask the AHJ to provide the Ss 
value for the building, per 9.3.5.6.2.
 Craig Prahl is correct, in that a requirement for seismic protection of a 
building is based on the location of the building in a seismic zone, and it's 
occupancy or use.  While it isn't a complicated set of data to find and apply 
correctly, you're not a structural or soils engineer, and that is certainly not 
your responsibility.
 This is a bad idea without something more to back it up.  You did mention 
that the building code requires it, can you be more specific?
*Ken Wagoner, SET*
**Parsley Consulting***
*350 West 9th Avenue, Suite 206
*Escondido, California 92025
*Phone 760-745-6181*
Visit our website http://www.parsleyconsulting.com/ *** On 9/5/2014 8:31 AM, 
Steve Sorrell wrote:
 Sorry,  should have read 2007 edition

 Stephen J. Sorrell, CET
 NICET# 77901 Level III
 E mail: ssorr...@performancefire.com

 Performance Fire Protection, LLC
 Corporate Office
 179 Gasoline Alley -  PO Box 4510
 Mooresville, NC 28117
 Phone: 704-663-1664  Fax: 704-663-1652 Cell : 704-309-1242

 Web: www.performancefire.com
 Licensed in NC, SC, VA, TN, GA, AL

 Performance on Every Level.


 -Original Message-
 From: Sprinklerforum 
 [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of 
 craig.pr...@ch2m.com
 Sent: Friday, September 05, 2014 8:33 AM
 To: sprinklerforum@lists.firesprinkler.org
 Subject: RE: Seismic bracing

 The AHJ can't just require it.  His preference is not relevant.  Also 
 seismic bracing is not based on Zones or Maps anymore, hasn't been for quite 
 a while.

 I'm curious why you're using the 2000 edition of NFPA 13.

 Anyway back to seismic.

 Seismic requirements are determined based on a number of factors originating 
 out of the Building Code Chapter 16.  It's not just an arbitrary decision.

 There needs to be a geotech (soils) report, the building needs to be 
 classified as to its use/function and you go from there.

 So there are engineering questions to be answered before there a requirement 
 for bracing is established.

 I've had to provide bracing on new work in an existing building, it made no 
 sense since the building structure wasn't design for the loading and the rest 
 of the system was not protected but it was required by the code so it had to 
 be done.  Was it required on the original install, did someone just miss it 
 assuming the site wasn't in the zone, who knows.

 There is a lot of misinterpretation on the part of design professionals 
 regard when it's required and when it's not.

 Craig L. Prahl
 Fire Protection Group Lead
 CH2MHILL
 Lockwood Greene
 1500 International Drive
 Spartanburg, SC  29303
 Direct - 864.599.4102
 Fax - 864.599.8439
 CH2MHILL Extension  74102
 craig.pr...@ch2m.com


 -Original Message-
 From: Sprinklerforum 
 [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of 
 Steve Sorrell
 Sent: Friday, September 05, 2014 8:13 AM
 To: sprinklerforum@lists.firesprinkler.org
 Subject: Seismic bracing

 I need some help with a seismic problem.
 I am making modifications to a 1970's sprinkler system in NC, we are using 
 the 2000 ed of NFPA  13.
 There is no seismic bracing on this system.
 I have had to add some new main in various areas.
 The local AHJ is requiring that only the new sprinkler 

RE: Seismic bracing

2014-09-05 Thread RFletcher
If I did I would have a pile of hold harmless up to the ceiling. We call them 
piping alignment braces, you know to help keep the piping in a straight line. 
Where's the liability in installing too many supports?
Ron F

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Jim Davidson
Sent: Friday, September 05, 2014 8:43 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Seismic bracing

Ron,

I hope you have a hold harmless letter from the building owner and or developer 
because the sprinkler contractor will be the one in the cross hairs of the 
legal system when something goes wrong. The AHJ has no liability unless you 
can prove gross negligence on the AHJ part.

Why assume the liability.

Have a fire safe day!

Regards

Jim 

DAVIDSON ASSOCIATES

Fire Protection Engineering P. O. Box 4002
Code ConsultantsGreenville, DE  19807
(302) 994-9500
Fax (302) 994-3414

CONFIDENTIALITY
This report and any attachments are confidential and also may be privileged.
If you are not the named recipient, or have otherwise received this report in 
error, please destroy the report, notify the sender immediately, and do not 
disclose its contents to any other person, use them for any purpose, or store 
or copy them in any medium.
Thank you for your cooperation.

-Original Message-
From: Sprinklerforum
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of 
rfletc...@aerofire.com
Sent: Friday, September 05, 2014 11:16 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Seismic bracing

Some jurisdictions around here require what we call feel good bracing.
They don't require calculations, or that the building be designed to any 
seismic standard, they just want the minimum bracing. If we want a green tag we 
have to put it in. I guess in this case the question would be if the only 
requirement is local dictate can you install at the max spacing and not do any 
calc's provided it is acceptable to the AHJ?  
Ron F

-Original Message-
From: Sprinklerforum
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Parsley 
Consulting
Sent: Friday, September 05, 2014 5:11 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Seismic bracing

Stephen,
 I don't believe the AHJ you're dealing with has thought this decision 
through very carefully.  They seem to be equating seismic bracing with 
seismic protection, which includes such other features as flexible couplings, 
clearance requirements, seismic separation assemblies, restraint of branch 
lines, and certain hanger requirements in a building protected against seismic 
damage.  Section 9.3 covers more than just seismic bracing.
 I would recommend you ask the AHJ if they're going to require all of the 
features in NFPA 13 for seismic protection, or just lateral, longitudinal and 
riser bracing.
 It's also relevant to note that if you're going to provide seismic bracing 
you have to make sure you comply with 9.3.5.1.2 (2007), which requires the 
structure to be able to withstand the applied seismic loads.  Based on what 
you've described I would wager a few dollars that they could not do so.
 And, if you still have a mandate to brace, ask the AHJ to provide the Ss 
value for the building, per 9.3.5.6.2.
 Craig Prahl is correct, in that a requirement for seismic protection of a 
building is based on the location of the building in a seismic zone, and it's 
occupancy or use.  While it isn't a complicated set of data to find and apply 
correctly, you're not a structural or soils engineer, and that is certainly not 
your responsibility.
 This is a bad idea without something more to back it up.  You did mention 
that the building code requires it, can you be more specific?
*Ken Wagoner, SET*
**Parsley Consulting***
*350 West 9th Avenue, Suite 206
*Escondido, California 92025
*Phone 760-745-6181*
Visit our website http://www.parsleyconsulting.com/ *** On 9/5/2014
8:31 AM, Steve Sorrell wrote:
 Sorry,  should have read 2007 edition

 Stephen J. Sorrell, CET
 NICET# 77901 Level III
 E mail: ssorr...@performancefire.com

 Performance Fire Protection, LLC
 Corporate Office
 179 Gasoline Alley -  PO Box 4510
 Mooresville, NC 28117
 Phone: 704-663-1664  Fax: 704-663-1652 Cell : 704-309-1242

 Web: www.performancefire.com
 Licensed in NC, SC, VA, TN, GA, AL

 Performance on Every Level.


 -Original Message-
 From: Sprinklerforum
 [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of 
 craig.pr...@ch2m.com
 Sent: Friday, September 05, 2014 8:33 AM
 To: sprinklerforum@lists.firesprinkler.org
 Subject: RE: Seismic bracing

 The AHJ can't just require it.  His preference is not relevant.
Also seismic bracing is not based on Zones or Maps anymore, hasn't been for 
quite a while.

 I'm curious why you're using the 2000 edition of NFPA 13.

 Anyway back to seismic.

 Seismic requirements are 

RE: Seismic bracing

2014-09-05 Thread RFletcher
Seems to me the AHJ's need the education more than the contractors.
Ron F

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of wmens...@comcast.net
Sent: Friday, September 05, 2014 8:58 AM
To: sprinklerforum
Subject: Re: Seismic bracing



Oh boy, here we go again.  Every time the subject of seismic bracing / 
protection comes up, it shows that there is a general lack of understanding 
among contractors and designers (myself included) as to when it is required, 
what is required, and how to do it correctly. 
We need more education - just reading NFPA13 is not enough.  Can anyone suggest 
any good classes available out there? 

Thanks 

Bill Menster 

- Original Message -

From: rfletc...@aerofire.com
To: sprinklerforum sprinklerforum@lists.firesprinkler.org
Sent: Friday, September 5, 2014 11:10:38 AM
Subject: RE: Seismic bracing 

Some jurisdictions around here require what we call feel good bracing. They 
don't require calculations, or that the building be designed to any seismic 
standard, they just want the minimum bracing. If we want a green tag we have to 
put it in. I guess in this case the question would be if the only requirement 
is local dictate can you install at the max spacing and not do any calc's 
provided it is acceptable to the AHJ? Ron F 

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Parsley Consulting
Sent: Friday, September 05, 2014 5:11 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Seismic bracing 

Stephen,
     I don't believe the AHJ you're dealing with has thought this decision 
through very carefully.  They seem to be equating seismic bracing with 
seismic protection, which includes such other features as flexible couplings, 
clearance requirements, seismic separation assemblies, restraint of branch 
lines, and certain hanger requirements in a building protected against seismic 
damage.  Section 9.3 covers more than just seismic bracing. 
     I would recommend you ask the AHJ if they're going to require all of the 
features in NFPA 13 for seismic protection, or just lateral, longitudinal and 
riser bracing. 
     It's also relevant to note that if you're going to provide seismic bracing 
you have to make sure you comply with 9.3.5.1.2 (2007), which requires the 
structure to be able to withstand the applied seismic loads.  Based on what 
you've described I would wager a few dollars that they could not do so. 
     And, if you still have a mandate to brace, ask the AHJ to provide the Ss 
value for the building, per 9.3.5.6.2. 
     Craig Prahl is correct, in that a requirement for seismic protection of a 
building is based on the location of the building in a seismic zone, and it's 
occupancy or use.  While it isn't a complicated set of data to find and apply 
correctly, you're not a structural or soils engineer, and that is certainly not 
your responsibility. 
     This is a bad idea without something more to back it up.  You did mention 
that the building code requires it, can you be more specific? 
*Ken Wagoner, SET*
**Parsley Consulting***
*350 West 9th Avenue, Suite 206
*Escondido, California 92025
*Phone 760-745-6181*
Visit our website http://www.parsleyconsulting.com/ *** On 9/5/2014 8:31 AM, 
Steve Sorrell wrote: 
 Sorry,  should have read 2007 edition
 
 Stephen J. Sorrell, CET
 NICET# 77901 Level III
 E mail: ssorr...@performancefire.com
 
 Performance Fire Protection, LLC
 Corporate Office
 179 Gasoline Alley -  PO Box 4510
 Mooresville, NC 28117
 Phone: 704-663-1664  Fax: 704-663-1652 Cell : 704-309-1242
 
 Web: www.performancefire.com
 Licensed in NC, SC, VA, TN, GA, AL
 
 Performance on Every Level. 
 
 
 -Original Message-
 From: Sprinklerforum
 [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of 
 craig.pr...@ch2m.com
 Sent: Friday, September 05, 2014 8:33 AM
 To: sprinklerforum@lists.firesprinkler.org
 Subject: RE: Seismic bracing
 
 The AHJ can't just require it.  His preference is not relevant.  Also 
 seismic bracing is not based on Zones or Maps anymore, hasn't been for quite 
 a while. 
 
 I'm curious why you're using the 2000 edition of NFPA 13. 
 
 Anyway back to seismic. 
 
 Seismic requirements are determined based on a number of factors originating 
 out of the Building Code Chapter 16.  It's not just an arbitrary decision. 
 
 There needs to be a geotech (soils) report, the building needs to be 
 classified as to its use/function and you go from there. 
 
 So there are engineering questions to be answered before there a requirement 
 for bracing is established. 
 
 I've had to provide bracing on new work in an existing building, it made no 
 sense since the building structure wasn't design for the loading and the rest 
 of the system was not protected but it was required by the code so it had to 
 be done.  Was it required on the original install, did someone just 

RE: Seismic bracing

2014-09-05 Thread RFletcher
Since it is an existing building I doubt any of the things you have listed will 
be done. I guess I look at getting it done without doing any harm so the owner 
can use the building. The alternative appears to be telling the owner it's not 
their responsibility and that he has to get an architect, structural engineer, 
soils report and have as builts done for the whole building and so on and so on 
so that the sprinkler contractor can properly design a sway brace.
Ron F

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Jim Davidson
Sent: Friday, September 05, 2014 9:28 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Seismic bracing

The seismic design classification should be determined by the structural 
engineer who determines the SDC of the site. Once the SDC is determined then 
you can go into either, ASCE 7 or Chapter 16 of the IBC, to determine the 
building's importance factor and other determining factors to decide when 
earthquake bracing is required. For example in most cases a building has a SDC 
of C then the mechanical and electrical systems with an importance factor of 
less than 1.5 do not have to seismically brace the systems however systems with 
an importance factor equal to or greater than 1.5 (fire alarm, sprinkler, fire 
pump, stair tower pressurization, etc) are required to be seismically braced. 
Then you can go to NFPA 13 or the IBC for the details on bracing and the zone 
of influence calculations required. 

Because of the soil and underground geological analysis the structural engineer 
will need to determine the SDC of the site.

Regards

Jim   

DAVIDSON ASSOCIATES

Fire Protection Engineering P. O. Box 4002
Code ConsultantsGreenville, DE  19807
(302) 994-9500
Fax (302) 994-3414

CONFIDENTIALITY
This report and any attachments are confidential and also may be privileged.
If you are not the named recipient, or have otherwise received this report in 
error, please destroy the report, notify the sender immediately, and do not 
disclose its contents to any other person, use them for any purpose, or store 
or copy them in any medium.
Thank you for your cooperation.


-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of wmens...@comcast.net
Sent: Friday, September 05, 2014 12:16 PM
To: sprinklerforum
Subject: Re: Seismic bracing



Oh boy, here we go again.  Every time the subject of seismic bracing / 
protection comes up, it shows that there is a general lack of understanding 
among contractors and designers (myself included) as to when it is required, 
what is required, and how to do it correctly. 
We need more education - just reading NFPA13 is not enough.  Can anyone suggest 
any good classes available out there? 

Thanks 

Bill Menster 

- Original Message -

From: rfletc...@aerofire.com
To: sprinklerforum sprinklerforum@lists.firesprinkler.org
Sent: Friday, September 5, 2014 11:10:38 AM
Subject: RE: Seismic bracing 

Some jurisdictions around here require what we call feel good bracing. They 
don't require calculations, or that the building be designed to any seismic 
standard, they just want the minimum bracing. If we want a green tag we have to 
put it in. I guess in this case the question would be if the only requirement 
is local dictate can you install at the max spacing and not do any calc's 
provided it is acceptable to the AHJ? Ron F 

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Parsley Consulting
Sent: Friday, September 05, 2014 5:11 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Seismic bracing 

Stephen,
     I don't believe the AHJ you're dealing with has thought this decision 
through very carefully.  They seem to be equating seismic bracing with 
seismic protection, which includes such other features as flexible couplings, 
clearance requirements, seismic separation assemblies, restraint of branch 
lines, and certain hanger requirements in a building protected against seismic 
damage.  Section 9.3 covers more than just seismic bracing. 
     I would recommend you ask the AHJ if they're going to require all of the 
features in NFPA 13 for seismic protection, or just lateral, longitudinal and 
riser bracing. 
     It's also relevant to note that if you're going to provide seismic bracing 
you have to make sure you comply with 9.3.5.1.2 (2007), which requires the 
structure to be able to withstand the applied seismic loads.  Based on what 
you've described I would wager a few dollars that they could not do so. 
     And, if you still have a mandate to brace, ask the AHJ to provide the Ss 
value for the building, per 9.3.5.6.2. 
     Craig Prahl is correct, in that a requirement for seismic protection of a 
building is based on the location of the building in a seismic zone, and it's 
occupancy or use.  

RE: ESFR Table 17.2.3.1 NFPA 13 2013

2014-08-22 Thread RFletcher
I disagree. S-1 occupancies have roof slopes less than 2/12 so they are 
considered flat and I have seen many ceilings that are sloped greater than 
2/12. Also there are warehouses with a couple high bays of 50-60' with the rest 
of the building at 40'-36'. Applying NFPA's interpretation would mean that the 
40' area would have to be area density with in-racks because ESFR's could not 
be used in the high bays.

Designing all systems for the highest roof area doesn't make any sense. Where 
does it stop? Do we have to use ESFR's under a 20' high mezzanine in a 40' 
warehouse?
Ron F

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Brad Casterline
Sent: Thursday, August 21, 2014 7:27 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: ESFR Table 17.2.3.1 NFPA 13 2013

Peak indicates sloped and I think that is what bothers the TC. If it was flat 
there would be no diff between a ceiling and a roof. Several months ago Mr 
Scandaliato (sp?) alluded to having some inside info about this. I offered up a 
case of beer if he could put it in a nutshell but it likely ended up in his 
junk mail, being from me and all.

 On Aug 21, 2014, at 9:04 PM, rfletc...@aerofire.com wrote:
 
 Wouldn't be the first time I thought the NFPA interp was wrong and I think 
 that again now.
 
 Ron fletcher Sent from my iPhone
 
 On Aug 21, 2014, at 4:34 PM, Steven P. Biship sbis...@pacificfireeng.com 
 wrote:
 
 I actually called NFPA a couple weeks ago for an unofficial interpretation
 for this exact subject with regards to ESFR sprinkler installations.  
 I was told that the term Maximum Ceiling/Roof Height found in the 
 tables applies to the maximum building height of the structure, 
 regardless of the area of storage.  I personally don't agree but that was 
 what I was told.
 
 Steven P. Biship, FPE, CFPS
 4214 Floyd Drive
 Corona, Ca. 92883
 
 P: 951-427-3781
 F: 951-427-3655
 C: 714-984-4346
 
 -Original Message-
 From: Sprinklerforum 
 [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
 On Behalf Of Parsley Consulting
 Sent: Thursday, August 21, 2014 3:57 PM
 To: sprinklerforum@lists.firesprinkler.org
 Subject: Re: ESFR Table 17.2.3.1 NFPA 13 2013
 
 Greg,
 I would look at the definition of ceiling height in 3.3.3:
 
   3.3.3 Ceiling Height. The distance between the floor and the
   underside of the ceiling above (or roof deck) within the area.
 
 It would seem to me that this definition backs up the perspective 
 that Ron has added.
 
 Has nothing to do with the roof height, only the height of the 
 ceiling in the area of storage.
 
 If a storage area in a high rise had an 28' ceiling, and yet the 
 building was 22 floors high, you certainly would not design based on 
 a 22 story ceiling height.
 
 Just one perspective.
 *Ken Wagoner, SET
 *Parsley Consulting***
 *350 West 9th Avenue, Suite 206
 *Escondido, CA 92025-5053
 *Phone 760.745.6181*
 Visit our website http://www.parsleyconsulting.com/ *** On 
 8/21/2014 3:46 PM, rfletc...@aerofire.com wrote:
 I would say the maximum height is meant to apply the area of storage 
 and
 not the maximum height of the entire building. A.17.2.3 Storage in 
 single-story or multistory buildings can be permitted, provided the 
 maximum ceiling/roof height as specified in chapter 12 is satisfied 
 for each storage area. If there were a high bay above 48' with in 
 racks and the remainder of the building was at 40' would you use area 
 density with in racks in the 40'
 area because there are no ESFR's listed for greater than 48'?
 Ron F
 
 -Original Message-
 From: Sprinklerforum
 [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of 
 Gregg Fontes
 Sent: Thursday, August 21, 2014 2:06 PM
 To: sprinklerforum@lists.firesprinkler.org
 Subject: ESFR Table 17.2.3.1 NFPA 13 2013
 
 A question has come up that in Table 17.2.3.1 the column that states
 Maximum Ceiling/Roof Height applies to the maximum Ceiling/Roof 
 height of the building, not the storage area. As an example, if a 
 warehouse has cartoned expanded plastics storage to 25' high in a 
 portion of the warehouse that has a roof/ceiling height of under 32', 
 but the ridge height of the building is 33'-0, they are suggesting 
 that the cartoned expanded plastic cannot be stored in the building  
 because the ridge height (not the area of
 storage) is above 32'.  There reasoning is that the table applies to 
 the entire building, not the area of storage.  Therefore if the 
 highest point of the building exceeds the list table height, even 
 though the storage area roof height is under the table height, the 
 table cannot apply.  Is this a correct assumption or is the maximum 
 height meant to apply to the area of storage?
 
 
 
 Thanks,
 Gregg Fontes
 Cen-Cal Fire Systems, Inc.
 209-334-9119
 
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 

RE: ESFR Table 17.2.3.1 NFPA 13 2013

2014-08-21 Thread RFletcher
I would say the maximum height is meant to apply the area of storage and not 
the maximum height of the entire building. A.17.2.3 Storage in single-story or 
multistory buildings can be permitted, provided the maximum ceiling/roof height 
as specified in chapter 12 is satisfied for each storage area. If there were a 
high bay above 48' with in racks and the remainder of the building was at 40' 
would you use area density with in racks in the 40' area because there are no 
ESFR's listed for greater than 48'?
Ron F

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Gregg Fontes
Sent: Thursday, August 21, 2014 2:06 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: ESFR Table 17.2.3.1 NFPA 13 2013

A question has come up that in Table 17.2.3.1 the column that states Maximum 
Ceiling/Roof Height applies to the maximum Ceiling/Roof height of the building, 
not the storage area. As an example, if a warehouse has cartoned expanded 
plastics storage to 25' high in a portion of the warehouse that has a 
roof/ceiling height of under 32', but the ridge height of the building is 
33'-0, they are suggesting that the cartoned expanded plastic cannot be stored 
in the building  because the ridge height (not the area of storage) is above 
32'.  There reasoning is that the table applies to the entire building, not the 
area of storage.  Therefore if the highest point of the building exceeds the 
list table height, even though the storage area roof height is under the table 
height, the table cannot apply.  Is this a correct assumption or is the maximum 
height meant to apply to the area of storage?  



Thanks,
Gregg Fontes
Cen-Cal Fire Systems, Inc.
209-334-9119

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Re: ESFR Table 17.2.3.1 NFPA 13 2013

2014-08-21 Thread RFletcher
Wouldn't be the first time I thought the NFPA interp was wrong and I think that 
again now.

Ron fletcher Sent from my iPhone

 On Aug 21, 2014, at 4:34 PM, Steven P. Biship sbis...@pacificfireeng.com 
 wrote:
 
 I actually called NFPA a couple weeks ago for an unofficial interpretation
 for this exact subject with regards to ESFR sprinkler installations.  I was
 told that the term Maximum Ceiling/Roof Height found in the tables applies
 to the maximum building height of the structure, regardless of the area of
 storage.  I personally don't agree but that was what I was told.
 
 Steven P. Biship, FPE, CFPS
 4214 Floyd Drive
 Corona, Ca. 92883
 
 P: 951-427-3781
 F: 951-427-3655
 C: 714-984-4346
 
 -Original Message-
 From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
 On Behalf Of Parsley Consulting
 Sent: Thursday, August 21, 2014 3:57 PM
 To: sprinklerforum@lists.firesprinkler.org
 Subject: Re: ESFR Table 17.2.3.1 NFPA 13 2013
 
 Greg,
 I would look at the definition of ceiling height in 3.3.3:
 
3.3.3 Ceiling Height. The distance between the floor and the
underside of the ceiling above (or roof deck) within the area.
 
 It would seem to me that this definition backs up the perspective that Ron
 has added.
 
 Has nothing to do with the roof height, only the height of the ceiling in
 the area of storage.
 
 If a storage area in a high rise had an 28' ceiling, and yet the building
 was 22 floors high, you certainly would not design based on a 22 story
 ceiling height.
 
 Just one perspective.
 *Ken Wagoner, SET
 *Parsley Consulting***
 *350 West 9th Avenue, Suite 206
 *Escondido, CA 92025-5053
 *Phone 760.745.6181*
 Visit our website http://www.parsleyconsulting.com/ *** On 8/21/2014 3:46
 PM, rfletc...@aerofire.com wrote:
 I would say the maximum height is meant to apply the area of storage and
 not the maximum height of the entire building. A.17.2.3 Storage in
 single-story or multistory buildings can be permitted, provided the maximum
 ceiling/roof height as specified in chapter 12 is satisfied for each storage
 area. If there were a high bay above 48' with in racks and the remainder of
 the building was at 40' would you use area density with in racks in the 40'
 area because there are no ESFR's listed for greater than 48'?
 Ron F
 
 -Original Message-
 From: Sprinklerforum 
 [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of 
 Gregg Fontes
 Sent: Thursday, August 21, 2014 2:06 PM
 To: sprinklerforum@lists.firesprinkler.org
 Subject: ESFR Table 17.2.3.1 NFPA 13 2013
 
 A question has come up that in Table 17.2.3.1 the column that states
 Maximum Ceiling/Roof Height applies to the maximum Ceiling/Roof height of
 the building, not the storage area. As an example, if a warehouse has
 cartoned expanded plastics storage to 25' high in a portion of the warehouse
 that has a roof/ceiling height of under 32', but the ridge height of the
 building is 33'-0, they are suggesting that the cartoned expanded plastic
 cannot be stored in the building  because the ridge height (not the area of
 storage) is above 32'.  There reasoning is that the table applies to the
 entire building, not the area of storage.  Therefore if the highest point of
 the building exceeds the list table height, even though the storage area
 roof height is under the table height, the table cannot apply.  Is this a
 correct assumption or is the maximum height meant to apply to the area of
 storage?
 
 
 
 Thanks,
 Gregg Fontes
 Cen-Cal Fire Systems, Inc.
 209-334-9119
 
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
 er.org ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
 er.org
 
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
 
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Re: ESFR Sprinkler in Racks.

2014-08-14 Thread RFletcher
It was an unusual condition. 8 ft deep ssingle rack against a wall, no flues, 
plywood barrier fit tight to the wall. Mattresses below and cartooned stge 
above. Added to existing ESFR Whse 

Ron fletcher Sent from my iPhone

 On Aug 14, 2014, at 7:24 AM, Roland Huggins rhugg...@firesprinkler.org 
 wrote:
 
 You must some mighty skinny people to walk around within the flues. Amazed 
 that approach was accepted considering its definition and leaves questions 
 like ceiling height for the ESFR.  
 
 
 Roland Huggins, PE - VP Engineering
 American Fire Sprinkler Assn.   ---  Fire Sprinklers Saves Lives
 Dallas, TX
 http://www.firesprinkler.org
 
 
 
 
 
 On Aug 13, 2014, at 5:03 PM, rfletc...@aerofire.com 
 rfletc...@aerofire.com wrote:
 
 Last time we did one we called the solid shelf a mezzanine and put the 
 correct density under with ESFR at roof.
 
 Ron fletcher Sent from my iPhone
 
 On Aug 13, 2014, at 3:34 PM, Roland Huggins rhugg...@firesprinkler.org 
 wrote:
 
 open
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
 
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Re: ESFR Sprinkler in Racks.

2014-08-13 Thread RFletcher
Last time we did one we called the solid shelf a mezzanine and put the correct 
density under with ESFR at roof.

Ron fletcher Sent from my iPhone

 On Aug 13, 2014, at 3:34 PM, Roland Huggins rhugg...@firesprinkler.org 
 wrote:
 
 open
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Texas code set

2014-07-29 Thread RFletcher
Too funny. I once saw a set of plans reviewed by Andy that said Rejected - Do 
Not Resubmit until redrawn by an experienced designer. Or something to that 
effect. I went to his office one time, there were plans everywhere.
Ron F

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of David Autry
Sent: Tuesday, July 29, 2014 5:36 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Texas code set

Ya'll should have been around when the Texas State Board of Insurance ran 
things. Andy was one tough cookie to get plans approved. After a couple of 
tries you'd get this stamped on your drawings:

Seek professional help




David Autry

Meininger Fire Protection Inc.
2521 W L St. Suite No.4
Lincoln, Ne 68522
Voice (402) 466-2616
Fax (402) 466-2617
da...@mfp-inc.com

-Original Message-
From: Sprinklerforum
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Todd 
Williams
Sent: Tuesday, July 29, 2014 7:31 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Texas code set

Did this guy make fertilizer in West?

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860-535-2080
www.fpdc.com


 On Jul 29, 2014, at 8:12 AM, craig.pr...@ch2m.com wrote:

 What I found out from doing several projects in Texas is that there is
no statewide adopted code except the Life Safety Code.

 Local jurisdictions are allowed to adopt and enforce as they see fit, 
 or
they may do nothing at all.

 So as stated before, you have to go to the local AHJ and see if they
have adopted anything or enforce anything.  What I was told in my cases was 
that as EOR we could choose to use whatever version of the Codes we wanted as 
long as we used the whole code and didn't cherry pick pieces and parts from 
different editions.  Beyond that, no direction or reviews, or permits or 
inspections.

 A couple of projects I knew of had H occupancy bldgs. with 
 corrosives
over the MAQ, no flammables or combustibles.  H requires sprinklers, but 
since there was no local code enforcement, the owner was able to declare 
themselves as AHJ.  He didn't feel sprinklers were warranted for a bldg.
that didn't contain any combustibles regardless of what any Code may have 
required and directed the EOR not to include any mention of them in his package.



 Craig L. Prahl
 Fire Protection Group Lead
 CH2MHILL
 Lockwood Greene
 1500 International Drive
 Spartanburg, SC  29303
 Direct - 864.599.4102
 Fax - 864.599.8439
 CH2MHILL Extension  74102
 craig.pr...@ch2m.com


 -Original Message-
 From: Sprinklerforum
 [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of 
 Steve Leyton
 Sent: Monday, July 28, 2014 6:26 PM
 To: AFSA Sprinkler Forum (AFSA SprinklerFORUM)
 Subject: Texas code set

 Can someone please point me to a website or give me a run-down on
 current adopted codes and standards (13,14,20,24,72) in Texas?   What
 edition of the code and is it called the Texas Building Code or IBC 
 with
amendments?  I saw one website that referenced both IBC and UFC ... any help is 
appreciated.



 SL



 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
 er.org ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
 er.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.o
rg
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Segue to AHJ's from CPVC Underground

2014-07-21 Thread RFletcher
Anything would be better than here's your badge and unlimited authority. One 
the biggest problems I find is that the higher up the chain of command we go 
the less they know about codes and plan review. The Chief tries to hire 
experienced people and is reluctant to overrule them because he/she doesn't 
know the codes and trusts that the reviewer does. We can appeal to the county 
board but they probably don't have a single person on it that knows what a 
sprinkler head looks like. Or we can go to the state fire marshal but he will 
probably tell us that so and so is autonomous and he can't tell him what to do. 
The king is never wrong.

I hope I can find a way to make them accountable, I know I am going to try and 
try.

The most ironic part of this whole mess. We can buy new 2000 gpm pump cases 
that will produce slightly less pressure that the 1500's. The net pressure at 
2000 from the 2000 or 1500 will be within 1 or 2 psi of each other. Spend $50k 
for no tangible difference. This just pisses me off.
Ron F   
-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of John Drucker
Sent: Monday, July 21, 2014 5:48 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Segue to AHJ's from CPVC Underground

or NCPCCI or ICC.

John Drucker - Mobile Email
jdruc...@redbanknj.orgmailto:jdruc...@redbanknj.org
Cell/Text 732-904-6823


David Autry da...@mfp-inc.com wrote:

Don't you have to work for a contractor to achieve NICET Level III?

At a bare minimum they should be NFPA Fire Plan Examiner AND NFPA Fire 
Inspector certified.


David Autry

Meininger Fire Protection Inc.
2521 W L St. Suite No.4
Lincoln, Ne 68522
Voice (402) 466-2616
Fax (402) 466-2617
da...@mfp-inc.com


-Original Message-
From: Sprinklerforum
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Cahill, 
Christopher
Sent: Sunday, July 20, 2014 6:12 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Segue to AHJ's from CPVC Underground

I prefer to have said it this way, government plan check inspectors should be 
certified to the same level or HIGHER than those they regulate. NICET III to 
have sprinkler license, NICET III to plan check or inspect.

Chris

-Original Message-
From: Sprinklerforum
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Owen Evans
Sent: Saturday, July 19, 2014 2:28 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Segue to AHJ's from CPVC Underground

No.


Government plan check inspectors should be state certified on all aspects of 
their job.


A local fire inspector (who does not know what he is doing) approved at final a 
head pocking through a jagged hole in the stucco ceiling without an escutcheon. 
I brought this to the attention of the fire marshal, the fire chief, and the 
city council. The fire chief brought in an outside AHJ to review it. The 
outside AHJ advised that escutcheons are ornamental only and not even required 
by code. The fire chief advised the city council of what the outside AHJ had 
said and went on to say that it was erroneous of me to claim the escutcheon was 
required. I call this the Harry and Lloyed (Dumb  Dumber) syndrome . Just 
because Harry (the dumb outside AHJ) says it, Lloyed (the dumber fire chief and 
fire marshal) believes it true. The original inspector, the fire marshal, the 
fire chief, and the outside AHJ never bothered to check the fire code or 
sprinkler listing. It was a semi-recessed head listed with its escutcheon. But 
guess who the city council believed? The big man with the g
   old badge...until I provided code reference and the sprinkler manufacturers 
listing. But guess what that got me? Everybody is pissed off because I (really 
they) made them(selves) look bad.


Extremely frustrated,
Owen Evans



-Original Message-
From: Bob b...@firebyknight.com
To: sprinklerforum sprinklerforum@lists.firesprinkler.org
Sent: Sat, Jul 19, 2014 11:49 am
Subject: RE: Segue to AHJ's from CPVC Underground


What does unwritten policy have to do with anything?  If it's not an adopted 
code amendment can they enforce it legally?

Thank You,

Bob Knight, CET III
208-318-3057
www.Firebyknight.comhttp://www.Firebyknight.com


-Original Message-
From: Sprinklerforum
[mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of rfletc...@aerofire.com
Sent: Saturday, July 19, 2014 6:15 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Segue to AHJ's from CPVC Underground

The stance of the AHJ is that their unwritten policy is pumps can only be used 
at 100%. They also believe that 1500 gpm pumps will only produce 1500 gpm, and 
we have to use 2 2000 gpm pumps to get 4000 gpm. They don't think pressure is 
even a factor.

Ron fletcher Sent from my iPhone

 On Jul 19, 2014, at 5:00 AM, Johnson, Duane (NIH/OD/ORS) [C]
johnson...@mail.nih.gov wrote:

 There are so many things wrong here. But, you may be able to make this

RE: Segue to AHJ's from CPVC Underground

2014-07-21 Thread RFletcher
To show how futile it is here is word for word the letter they wrote minus the 
names and places.

Per our discussion on 7/14/2014 regarding the Fire Pumps at Blah Blah Parkway, 
Project Blah Blah, within Blah Blah industrial center, Blah Blah Blah Fire 
Protection District is exercising its right to withdraw the approval of the 
Fire Sprinkler Plans based on several factors..

1. During previous discussion with Mr. So and So there was a mutual understand 
that Mr. So and So would provide Balh Blah Fire Protection District with 
contacts to a Fire Protection Engineer in which he did not do.

2. When the plans were submitted, we were led to believe that the pumps in the 
submittal were capable of supplying 2,250 GPM at 100% capacity, which would 
have exceeded our need for 4,000 GPM. Once the plans were submitted, the pump 
curve test, with the delivery of the pumps, we discovered they were 1,500 GPM 
not 2,250 GPM and that the 2,250 GPM that was supplies to us was at 150% of the 
capacity of the pump.

3. The building requires 8,000 GPM as a basic fire flow.

Per Blah Blah Fire Protection Districts Adopted Fire Code Appendix B 105.2 Fire 
Flow Requirements for buildings: a reduction in fire flow of up to 50 percent. 
As approved, is allowed when the building is provided with an approved 
automatic sprinkler system.

This would make the requirement 4,000 GPM or (a combination of two 2,000 GPM 
pumps that are capable of 4,000 GPM at 100 percent of the pumps rated capacity)

4. NFPA 20 A4.8 The performance of the pump when applied at capacities over 140 
percent of rated capacity can be adversely affected by the suction conditions. 
Application of the pump at capacities less than 90 percent of the rate capacity 
is NOT recommended.

The selection and application of the fire pump should not be confused with the 
pump operating conditions. With proper suction conditions the pump can operate 
at any point of is characteristic curve from shutoff to 150 percent of its 
rated capacity.

5. UFC-P1003.2.1.17.6 Pump Size states that Fire pumps shall be sized at their 
rated UL or FM capacity at 100 percent of the required flow.

At this time, Blah blah Fire Protection District is denying said plans and is 
requesting a re-submittal of new plans that exceed IFC, UFC , and NFPA 
standards.

Sincerely,
The Badge

To top it off UFC isn't even listed as an adopted code, they only list IFC. 
They did ask if I could get a registered FPE to write a letter about the pump 
size. I said yes and they said it won't help and that they want the pumps 
changed anyway. I'm not kidding. This is really how the conversation went.
Ron F


-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of John Drucker
Sent: Monday, July 21, 2014 5:48 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Segue to AHJ's from CPVC Underground

or NCPCCI or ICC.

John Drucker - Mobile Email
jdruc...@redbanknj.orgmailto:jdruc...@redbanknj.org
Cell/Text 732-904-6823


David Autry da...@mfp-inc.com wrote:

Don't you have to work for a contractor to achieve NICET Level III?

At a bare minimum they should be NFPA Fire Plan Examiner AND NFPA Fire 
Inspector certified.


David Autry

Meininger Fire Protection Inc.
2521 W L St. Suite No.4
Lincoln, Ne 68522
Voice (402) 466-2616
Fax (402) 466-2617
da...@mfp-inc.com


-Original Message-
From: Sprinklerforum
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Cahill, 
Christopher
Sent: Sunday, July 20, 2014 6:12 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Segue to AHJ's from CPVC Underground

I prefer to have said it this way, government plan check inspectors should be 
certified to the same level or HIGHER than those they regulate. NICET III to 
have sprinkler license, NICET III to plan check or inspect.

Chris

-Original Message-
From: Sprinklerforum
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Owen Evans
Sent: Saturday, July 19, 2014 2:28 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Segue to AHJ's from CPVC Underground

No.


Government plan check inspectors should be state certified on all aspects of 
their job.


A local fire inspector (who does not know what he is doing) approved at final a 
head pocking through a jagged hole in the stucco ceiling without an escutcheon. 
I brought this to the attention of the fire marshal, the fire chief, and the 
city council. The fire chief brought in an outside AHJ to review it. The 
outside AHJ advised that escutcheons are ornamental only and not even required 
by code. The fire chief advised the city council of what the outside AHJ had 
said and went on to say that it was erroneous of me to claim the escutcheon was 
required. I call this the Harry and Lloyed (Dumb  Dumber) syndrome . Just 
because Harry (the dumb outside AHJ) says it, Lloyed (the dumber fire chief and 
fire marshal) believes it true. The original 

RE: Motor operated valve controller

2014-07-21 Thread RFletcher
Can you rig up something that uses whatever level sensing devices the tank 
already has? Otherwise they now make a sonic sensor that can mount to the 
inside top of the tank. You should be able to get a signal from it to operate a 
valve.
Ron F

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Craig Leadbetter
Sent: Monday, July 21, 2014 7:57 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Motor operated valve controller

So it appears that Cal-Val is probably the right solution. Unfortunately the 
MOV's are already in place.


On Mon, Jul 21, 2014 at 8:44 AM, John Denhardt jdenha...@stricklandfire.com
 wrote:

 Same here.  Cla-valve.

 -Original Message-
 From: Sprinklerforum [mailto:
 sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of David 
 Autry
 Sent: Monday, July 21, 2014 8:39 AM
 To: sprinklerforum@lists.firesprinkler.org
 Subject: RE: Motor operated valve controller

 Never used a motor operated one.
 I've always used a Cla-Val Altitude Valve.


 David Autry

 Meininger Fire Protection Inc.
 2521 W L St. Suite No.4
 Lincoln, Ne 68522
 Voice (402) 466-2616
 Fax (402) 466-2617
 da...@mfp-inc.com

 -Original Message-
 From: Sprinklerforum
 [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of 
 Craig Leadbetter
 Sent: Monday, July 21, 2014 7:34 AM
 To: sprinklerforum@lists.firesprinkler.org
 Subject: Motor operated valve controller

 I am looking for a motor operated valve controller to automaitically 
 fill a water tank. Can anyone point me in the right direction?

 Thanks

 --
 Craig Leadbetter
 Safeguard of Marquette
 PO Box 116
 Marquette, MI 49855

 (O) 906-475-9955
 (F) 906-475-5474
 (C) 906-362-5393

 craigleadbet...@gmail.com
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
 er.o
 rg
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprink
 ler.org ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org

 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
 er.org ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org

 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
 er.org




--
Craig Leadbetter
Safeguard of Marquette
PO Box 116
Marquette, MI 49855

(O) 906-475-9955
(F) 906-475-5474
(C) 906-362-5393

craigleadbet...@gmail.com
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Re: Blazemaster CPVC Underground

2014-07-21 Thread RFletcher
I feel your pain.
Ron F 

Ron fletcher Sent from my iPhone

 On Jul 21, 2014, at 12:10 PM, Tony Liddic 
 tony.lid...@mrhsprinklerdesign.com wrote:
 
 AHJ has spoken with Mfr Rep directly and has basically decided to forgo
 common sense.
 
 The only way he will approve it is if NFPA 13R includes this situation
 specifically, ie. CPVC piping shall be permitted to be installed
 underground below breezeways on system side of riser.
 
 Thanks,
 
 Tony Liddic, CET
 MRH Sprinkler Design LLC
 356 Laurel Glen Dr.
 Springboro, OH  45066
 937-369-7926
 http://mrhsprinklerdesign.com
 tony.lid...@mrhsprinklerdesign.com
 
 
 
 On Mon, Jul 21, 2014 at 1:22 PM, Fairchild, Jack 
 jfairch...@ballinger-ae.com wrote:
 
 Is it written somewhere that steel is allowed for underground use on the
 system side?
 
 Jack Fairchild
 
 
 -Original Message-
 From: Sprinklerforum [mailto:
 sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Tim Stone
 Sent: Saturday, July 19, 2014 4:43 PM
 To: sprinklerforum@lists.firesprinkler.org
 Subject: FW: Blazemaster CPVC Underground
 
 FYI
 
 
 
 Regards,
 
 G. Tim Stone
 
 
 
 G. Tim Stone Consulting, LLC
 
 NICET Level III Engineering Technician
 
 Fire Protection Sprinkler Design
 
 and Consulting Services
 
 
 
117 Old Stage Rd. - Essex Jct., VT. 05452
 
 CELL: (802) 373-0638   TEL: (802) 434-2968   Fax: (802) 434-4343
 
   tston...@comcast.net mailto:
 tston...@comcast.net
 
 
 
 From: Lemire, Mark [mailto:mark.lem...@lubrizol.com]
 Sent: Friday, July 18, 2014 9:02 PM
 To: Tim Stone
 Subject: Fwd: Blazemaster CPVC Underground
 
 
 
 Good evening,
 
 
 
 Please review John's comments who us one of Lubrizol's Field Tech
 Specialist.
 
 
 
 Have a great weekend!
 
 Mark E. Lemire
 
 Piping System Consultant
 
 The Lubrizol Corporation
 
 Representing FlowGuard GoldR, BlazeMasterR and CorzanR CPVC piping systems
 
 603-738-3101
 
 603-934-3360 fax
 
 mark.lem...@lubrizol.com mailto:mark.lem...@lubrizol.com
 
 www.lubrizolcpvc.com http://www.lubrizolcpvc.com
 
 
 
 
 Begin forwarded message:
 
 From: Pritchard, John john.pritch...@lubrizol.com mailto:
 john.pritch...@lubrizol.com 
 Date: July 18, 2014 at 10:06:15 AM EDT
 To: Lemire, Mark mark.lem...@lubrizol.com mailto:
 mark.lem...@lubrizol.com 
 Subject: RE: Blazemaster CPVC Underground
 
 I e-mailed Peter because the original e-mail was from his territory.
 
 
 
 The AHJ is 100 wrong.
 
 
 
 CPVC is approved for underground.
 
 
 
 13R allows any material approved for Underground water.
 
 
 
 The way the system is being run which is common in my part of the country
 the CPVC pipe is part of the sprinkler system and it is approved for
 underground installations. The AHJ needs to be educated
 
 
 
 
 
 John Pritchard
 
 Piping Systems Consultant
 
 The Lubrizol Corporation
 
 Representing FlowGuard GoldR, BlazeMasterR and CorzanR CPVC piping systems
 
 224-735-3042  office
 
 312-215-2089  cell
 
 224-735-3043 fax
 
 mailto:john.pritch...@lubrizol.com john.pritch...@lubrizol.com
 
 http://www.lubrizolcpvc.com/ www.lubrizolcpvc.com
 
 
 
 From: Lemire, Mark
 Sent: Friday, July 18, 2014 9:03 AM
 To: Pritchard, John
 Subject: Fwd: Blazemaster CPVC Underground
 
 
 
 Any comments!
 
 Mark Lemire
 
 Piping Systems Consultant
 
 The Lubrizol Corporation
 
 Representing FlowGuard Gold, BlazeMaster and Corzan CPVC piping systems
 
 603-738-3101 cell
 
 603-934-3360 fax
 
 Email: mark.lem...@lubrizol.com mailto:mark.lem...@lubrizol.com
 
 Website: www.lubrizolcpvc.com http://www.lubrizolcpvc.com
 
 
 Begin forwarded message:
 
 From: Tim Stone tston...@comcast.net mailto:tston...@comcast.net 
 Date: July 18, 2014 at 10:00:55 AM EDT
 To: mark.lem...@lubrizol.com mailto:mark.lem...@lubrizol.com 
 Subject: FW: Blazemaster CPVC Underground
 
 Mark,
 
 The attached email is from The AFSA Forum.
 
 Can you way in?
 
 Regards,
 G. Tim Stone
 
 G. Tim Stone Consulting, LLC
 NICET Level III Engineering Technician
 Fire Protection Sprinkler Design
 and Consulting Services
 
117 Old Stage Rd. - Essex Jct., VT. 05452
 CELL: (802) 373-0638   TEL: (802) 434-2968   Fax: (802) 434-4343
   tston...@comcast.net mailto:
 tston...@comcast.net
 
 -Original Message-
 From: Sprinklerforum [mailto:
 sprinklerforum-boun...@lists.firesprinkler.org]
 On Behalf Of rfletc...@aerofire.com mailto:rfletc...@aerofire.com
 Sent: Friday, July 18, 2014 9:46 AM
 To: sprinklerforum@lists.firesprinkler.org
 mailto:sprinklerforum@lists.firesprinkler.org
 Subject: RE: Blazemaster CPVC Underground
 
 That's a good one. I'll add that to my so you think you have heard
 everything list. Like saying it's approved below a valve but not above.
 Does he have a code reference or is this it just their opinion? Can you
 have someone from the manufacturer call them?
 Ron F
 
 -Original Message-
 From: Sprinklerforum [mailto:
 sprinklerforum-boun...@lists.firesprinkler.org]
 On Behalf Of Tony 

Re: Segue to AHJ's from CPVC Underground

2014-07-20 Thread RFletcher
I am filing an appeal, for all the good it will do. Have to get CofO then I can 
fight the the good but futile fight.

Ron fletcher Sent from my iPhone

 On Jul 20, 2014, at 5:10 PM, John Drucker - Home john.druc...@verizon.net 
 wrote:
 
 Actually you get a notice of violation, order to pay penalty, order to
 vacate and the building posted at each entrance. Disregarding the order may
 be chargeable as defiant trespass of a lawful order (which it is because the
 fact is you don't have a CO to occupy) which becomes a criminal matter, the
 hole is getting deeper.  Keep in mind the CO notice of violation, penalty
 and vacate orders are a slam dunk for the code official since the first
 question at the hearing is; do you have a Certificate of Occupancy ?,
 which is the matter at hand. Of course the only answer other than lying is
 No.  The next question will be did you appeal the code officials
 determination on the fire pump ? again the answer, other than lying is No
 to which the judge or board says; why not ? The appeal on the fire pump
 can't even be heard because there is no appeal since the aggrieved party
 never filed one. Typically judges or boards cant order a CO issued in
 violation of the regulations which require all inspections to be completed
 and signed off, especially for fire.  Of course cooler heads will prevail
 and the directive will be to get everyone to solve the problem which is
 where we started.
 
 Besides all that we get requests from financial institutions, insurance
 companies and other vested interests every day for proof of certificate of
 occupancy prior to occupancy.
 
 Guys either get everyone together and solve it or FILE THE APPEAL it's not
 going to go away.  Let me off this ride I'm getting dizzy.   
 
 PS as for the public, the angst will turn against the person(s) who occupied
 without a CO not the code official simply by virtue that the public's
 response will be  I had to get permits, inspections and a CO before
 occupancy why don't they, who do they think they are , special ?   
 
 PSS, we agree to disagree but were still friends.
 
 John
 
 John Drucker, CET
 Assistant Construction Official
 Fire Protection Subcode Official
 Building/Fire/Electrical Inspector
 Borough of Red Bank
 Red Bank, New Jersey
 
 
 
 
 
 
 
 -Original Message-
 From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
 On Behalf Of Cahill, Christopher
 Sent: Sunday, July 20, 2014 7:06 PM
 To: sprinklerforum@lists.firesprinkler.org
 Subject: RE: Segue to AHJ's from CPVC Underground
 
 Theoretically at best If an owner occupies without the COO, he/ she is
 subject to arrest by armed marshals.  Reality is you get a ticket for an
 ordinance violation.  About the same as a ticket for your long grass.
 Getting a ticket is a GOOD thing if you are right. You get to a judge to put
 the executive branch in their place. If you wait for the obstinate official
 to issue a COO you may never get use of your building or in front of a
 judge.
 
 Chris
 
 
 -Original Message-
 From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
 On Behalf Of Forest Wilson
 Sent: Saturday, July 19, 2014 6:06 PM
 To: sprinklerforum@lists.firesprinkler.org
 Subject: Re: Segue to AHJ's from CPVC Underground
 
 The COO is more than just a formality.
 If an owner occupies without the COO, he/ she is subject to arrest by armed
 marshals.
 It doesnt matter if its a mall owner or a small homeowner out in the middle
 of nowhere.
 If she/he resists arrest or removal they may be killed, and at the very
 minimum imprisoned.
 Why would any sensible owner risk that over a piece of paper?
 
 A friend of mine is a roofing contractor.
 They had a regional contract with a fast food chain; one of the projects was
 in the greater Chicago area. They needed a sign off but the AHJ would not
 schedule the inspection. Finally he went down to her office and she told
 him: WE dont like you here (he was non union) and dont want you here.
 He agreed to never do business in her jurisdiction again; in return she went
 out and signed off on the roof inspection.
 
 Since you are the out of town contractor, have you considered that perhaps
 the AHJ is sending you a similar message of staying out of town and not
 biting into the locals work?
 
 
 On 7/19/2014 6:54 PM, John Drucker - Home wrote:
 Bob,
 
 Unfortunately they can indirectly by withholding a certificate of 
 approval, compliance or occupancy.  Most property owners need this 
 document for closing, insurance or tenancy and or their attorney 
 advises them that they will or have now broken an adopted law or 
 regulation.  So despite the illegitimacy of the code officials claim 
 the property owner or tenant has now legitimately broken the rules by 
 occupying without a certificate of occupancy and or certificate of 
 approval. In other words the enforcing agency holds the cards.
 
 Code Enforcement is a legal process and like all or most legal 

Re: Segue to AHJ's from CPVC Underground

2014-07-19 Thread RFletcher
The stance of the AHJ is that their unwritten policy is pumps can only be used 
at 100%. They also believe that 1500 gpm pumps will only produce 1500 gpm, and 
we have to use 2 2000 gpm pumps to get 4000 gpm. They don't think pressure is 
even a factor.

Ron fletcher Sent from my iPhone

 On Jul 19, 2014, at 5:00 AM, Johnson, Duane (NIH/OD/ORS) [C] 
 johnson...@mail.nih.gov wrote:
 
 There are so many things wrong here. But, you may be able to make this work 
 regardless. Did you take your 75% reduction in fire flow based on the fully 
 sprinklered exception in B105.2? If you are starting at 4000 gpm, the 
 required flow can be reduced to 1500 gpm if fully sprinklered. Doesn't that 
 work with your pumps?  
 
 Duane
 
 - Original Message -
 From: Johnson, Duane (NIH/OD/ORS) [C]
 Sent: Saturday, July 19, 2014 07:51 AM Eastern Standard Time
 To: 'sprinklerforum@lists.firesprinkler.org' 
 sprinklerforum@lists.firesprinkler.org
 Subject: Re: Segue to AHJ's from CPVC Underground
 
 Has Annex B been adopted?  See 101.2.1? 
 
 Duane
 
 - Original Message -
 From: mphe...@aerofire.com [mailto:mphe...@aerofire.com]
 Sent: Saturday, July 19, 2014 07:35 AM Eastern Standard Time
 To: sprinklerforum@lists.firesprinkler.org 
 sprinklerforum@lists.firesprinkler.org
 Subject: Re: Segue to AHJ's from CPVC Underground
 
 Hi John,
 What Ron didn't say is that the AHJ is trying to connect chapter 5 of the IFC 
 and table B105.2 fire flow requirements to our sprinkler system pumps. We 
 conceded early on to furnish a redundant pump because it was specified that 
 way, but the FM is expecting the fire pumps to provide the 4000 GPM from 
 B105.2 at the sprinkler (ESFR) demand pressure (165 PSI) and do so at the 
 100% design point of the fire pump. We submitted our design with two 1500 GPM 
 pumps piped in parallel along with calcs for the storage sprinklers flowing 
 at around 165 PSI at the pump discharge. The city water system which supplies 
 the project flow tested at 5700 GPM at 74 PSI from two 4 hydrant butts. No 
 one at the AHJ's office understands how to read a fire code, or any other 
 code for that matter. They are Code Alchemist, taking a paragraph from 
 chapter 5,  table from the annex, and numbers from our calcs, mix 'em all 
 together in an AHJ beaker and BOOM!! Minimum code requirement. See? This 
 stuff ain
 't
  all that hard.
 
 Mark at Aero
 602 820-7894
 
 Sent from my iPad
 
 On Jul 19, 2014, at 2:24 AM, John Drucker 
 jdruc...@redbanknj.orgmailto:jdruc...@redbanknj.org wrote:
 
 Like how you wrote;  everything is per code except we have.  Except ?, 
 Are you/they saying that having two pumps rather than one is a violation; 
 I.e.  4000 GPM at 160 vs 4000 at 165 and you're short 5 psi ?  So two code 
 violations, two pumps and short 5 psi. Now before you chop my head off, 
 consider two things wheres the one pump and 165 psi coming from ? Somehow 
 apparently this has been planted in the ahjs head, I'm certain he/she didn't 
 come up with it on there own. Now you're stuck.  Frankly and using common 
 sense are you hitting demand, does everything fit and work together, is the 
 principal designer and owner ok with it ?  Move forward.
 
 John Drucker - Mobile Email
 jdruc...@redbanknj.orgmailto:jdruc...@redbanknj.orgmailto:jdruc...@redbanknj.org
 Cell/Text 732-904-6823
 
 
 rfletc...@aerofire.commailto:rfletc...@aerofire.com wrote:
 
 How about everything is per code except we have two pumps rather than one.and 
 we have 4000 GM at 160 psi instead of.4000 gpm at 165 psi. Most ignorant 
 thing I have ever seen. Just found out the chief told plan reviewer no more 
 written correspondence. I guess because they don't want a written orecord of 
 their stupidity. Please forgive my frustration but I just don't know where to 
 go from here..
 
 Ron fletcher Sent from my iPhone
 
 On Jul 18, 2014, at 4:24 PM, John Drucker - Home 
 john.druc...@verizon.netmailto:john.druc...@verizon.net wrote:
 
 Ron, et.al.
 
 I don't know the particulars of your situation but we have a saying; there's
 your side, their side and the truth.  Perhaps there's an issue with the code
 itself,  a local amendment or interpretation. There's got to be something
 driving this.
 
 Case in point about a reference standard, NFPA-72 speaks of wall mounted
 smoke detectors/alarms and calls out a distance yet the illustration in the
 annex is worded differently than the code.
 
 29.8.3.3 Wall Mounting. Smoke alarms or smoke detectors mounted on walls
 shall be located NOT FARTHER than 12 in. (300 mm) from the adjoining ceiling
 surface.
 
 Yet the annex A.29.8.3 notes;  Measurements shown are to the closest edge
 of the detector.
 
 According to the annex this would place part or most of the alarm or
 detector FARTHER than 12 in. from the adjoining ceiling surface.
 
 It's important to note that Annex A opens with the following statement;
 
 Annex A is not a part of the requirements of this NFPA document but is
 included for 

Re: Segue to AHJ's from CPVC Underground

2014-07-19 Thread RFletcher
It's a mystery. An AHJ in a different jurisdiction but in same metro area said 
she didn't know if she would accept our flow test for the sprinkler Sys because 
we only flowed 3871 gpm and that they require 4000. The civil engineer had 
already modeled 4000 gpm for there drawings. Must be something in the water 
(hehe).

Ron fletcher Sent from my iPhone

 On Jul 19, 2014, at 5:32 AM, Johnson, Duane (NIH/OD/ORS) [C] 
 johnson...@mail.nih.gov wrote:
 
 The question still stands why 4000? 
 
 Duane
 
 - Original Message -
 From: rfletc...@aerofire.com [mailto:rfletc...@aerofire.com]
 Sent: Saturday, July 19, 2014 08:15 AM Eastern Standard Time
 To: sprinklerforum@lists.firesprinkler.org 
 sprinklerforum@lists.firesprinkler.org
 Subject: Re: Segue to AHJ's from CPVC Underground
 
 The stance of the AHJ is that their unwritten policy is pumps can only be 
 used at 100%. They also believe that 1500 gpm pumps will only produce 1500 
 gpm, and we have to use 2 2000 gpm pumps to get 4000 gpm. They don't think 
 pressure is even a factor.
 
 Ron fletcher Sent from my iPhone
 
 On Jul 19, 2014, at 5:00 AM, Johnson, Duane (NIH/OD/ORS) [C] 
 johnson...@mail.nih.gov wrote:
 
 There are so many things wrong here. But, you may be able to make this work 
 regardless. Did you take your 75% reduction in fire flow based on the fully 
 sprinklered exception in B105.2? If you are starting at 4000 gpm, the 
 required flow can be reduced to 1500 gpm if fully sprinklered. Doesn't that 
 work with your pumps?  
 
 Duane
 
 - Original Message -
 From: Johnson, Duane (NIH/OD/ORS) [C]
 Sent: Saturday, July 19, 2014 07:51 AM Eastern Standard Time
 To: 'sprinklerforum@lists.firesprinkler.org' 
 sprinklerforum@lists.firesprinkler.org
 Subject: Re: Segue to AHJ's from CPVC Underground
 
 Has Annex B been adopted?  See 101.2.1? 
 
 Duane
 
 - Original Message -
 From: mphe...@aerofire.com [mailto:mphe...@aerofire.com]
 Sent: Saturday, July 19, 2014 07:35 AM Eastern Standard Time
 To: sprinklerforum@lists.firesprinkler.org 
 sprinklerforum@lists.firesprinkler.org
 Subject: Re: Segue to AHJ's from CPVC Underground
 
 Hi John,
 What Ron didn't say is that the AHJ is trying to connect chapter 5 of the 
 IFC and table B105.2 fire flow requirements to our sprinkler system pumps. 
 We conceded early on to furnish a redundant pump because it was specified 
 that way, but the FM is expecting the fire pumps to provide the 4000 GPM 
 from B105.2 at the sprinkler (ESFR) demand pressure (165 PSI) and do so at 
 the 100% design point of the fire pump. We submitted our design with two 
 1500 GPM pumps piped in parallel along with calcs for the storage sprinklers 
 flowing at around 165 PSI at the pump discharge. The city water system which 
 supplies the project flow tested at 5700 GPM at 74 PSI from two 4 hydrant 
 butts. No one at the AHJ's office understands how to read a fire code, or 
 any other code for that matter. They are Code Alchemist, taking a 
 paragraph from chapter 5,  table from the annex, and numbers from our calcs, 
 mix 'em all together in an AHJ beaker and BOOM!! Minimum code requirement. 
 See? This stuff ai
 n
 't
 all that hard.
 
 Mark at Aero
 602 820-7894
 
 Sent from my iPad
 
 On Jul 19, 2014, at 2:24 AM, John Drucker 
 jdruc...@redbanknj.orgmailto:jdruc...@redbanknj.org wrote:
 
 Like how you wrote;  everything is per code except we have.  Except ?, 
 Are you/they saying that having two pumps rather than one is a violation; 
 I.e.  4000 GPM at 160 vs 4000 at 165 and you're short 5 psi ?  So two code 
 violations, two pumps and short 5 psi. Now before you chop my head off, 
 consider two things wheres the one pump and 165 psi coming from ? Somehow 
 apparently this has been planted in the ahjs head, I'm certain he/she didn't 
 come up with it on there own. Now you're stuck.  Frankly and using common 
 sense are you hitting demand, does everything fit and work together, is the 
 principal designer and owner ok with it ?  Move forward.
 
 John Drucker - Mobile Email
 jdruc...@redbanknj.orgmailto:jdruc...@redbanknj.orgmailto:jdruc...@redbanknj.org
 Cell/Text 732-904-6823
 
 
 rfletc...@aerofire.commailto:rfletc...@aerofire.com wrote:
 
 How about everything is per code except we have two pumps rather than 
 one.and we have 4000 GM at 160 psi instead of.4000 gpm at 165 psi. Most 
 ignorant thing I have ever seen. Just found out the chief told plan reviewer 
 no more written correspondence. I guess because they don't want a written 
 orecord of their stupidity. Please forgive my frustration but I just don't 
 know where to go from here..
 
 Ron fletcher Sent from my iPhone
 
 On Jul 18, 2014, at 4:24 PM, John Drucker - Home 
 john.druc...@verizon.netmailto:john.druc...@verizon.net wrote:
 
 Ron, et.al.
 
 I don't know the particulars of your situation but we have a saying; there's
 your side, their side and the truth.  Perhaps there's an issue with the code
 itself,  a local amendment or interpretation. 

Re: Segue to AHJ's from CPVC Underground

2014-07-19 Thread RFletcher
The AHJ told me I don't care what the codes say. Do it my way or no CofO. I 
am appealing to the State FM while arranging to change the pumps to 2000 gpm. 
We have a written notice from the GC to get our plans approved. The GC has 
tried to reason with the badge. That's when he was told they would accept a 
fire watch until the pumps are changed.

Ron fletcher Sent from my iPhone

 On Jul 19, 2014, at 5:57 AM, Johnson, Duane (NIH/OD/ORS) [C] 
 johnson...@mail.nih.gov wrote:
 
 And A.4.8. 
 
 Duane
 
 - Original Message -
 From: Johnson, Duane (NIH/OD/ORS) [C]
 Sent: Saturday, July 19, 2014 08:56 AM Eastern Standard Time
 To: 'sprinklerforum@lists.firesprinkler.org' 
 sprinklerforum@lists.firesprinkler.org
 Subject: Re: Segue to AHJ's from CPVC Underground
 
 See NFPA 20:4.8.1. 
 
 Duane
 
 - Original Message -
 From: mphe...@aerofire.com [mailto:mphe...@aerofire.com]
 Sent: Saturday, July 19, 2014 08:42 AM Eastern Standard Time
 To: sprinklerforum@lists.firesprinkler.org 
 sprinklerforum@lists.firesprinkler.org
 Subject: Re: Segue to AHJ's from CPVC Underground
 
 The project is a 700k sq ft type Vb construction. B105.2 calls out 8000 GPM 
 fire flow. The locally adopted reduction is 50%, so 8000 x50% =4000 GPM. They 
 are correct about the flow rate. They just don't understand that that is what 
 is required from the municipal water system to the site for manual fire 
 fighting. They believe that out sprinkler booster pumps need to produce 4000 
 GPM at their 100% design point, and feel that operating a fire pump in excess 
 odors design point of 100% is somehow bad. 
 Mark at Aero
 
 Sent from my iPhone
 
 On Jul 19, 2014, at 5:32 AM, Johnson, Duane (NIH/OD/ORS) [C] 
 johnson...@mail.nih.gov wrote:
 
 The question still stands why 4000? 
 
 Duane
 
 - Original Message -
 From: rfletc...@aerofire.com [mailto:rfletc...@aerofire.com]
 Sent: Saturday, July 19, 2014 08:15 AM Eastern Standard Time
 To: sprinklerforum@lists.firesprinkler.org 
 sprinklerforum@lists.firesprinkler.org
 Subject: Re: Segue to AHJ's from CPVC Underground
 
 The stance of the AHJ is that their unwritten policy is pumps can only be 
 used at 100%. They also believe that 1500 gpm pumps will only produce 1500 
 gpm, and we have to use 2 2000 gpm pumps to get 4000 gpm. They don't think 
 pressure is even a factor.
 
 Ron fletcher Sent from my iPhone
 
 On Jul 19, 2014, at 5:00 AM, Johnson, Duane (NIH/OD/ORS) [C] 
 johnson...@mail.nih.gov wrote:
 
 There are so many things wrong here. But, you may be able to make this work 
 regardless. Did you take your 75% reduction in fire flow based on the fully 
 sprinklered exception in B105.2? If you are starting at 4000 gpm, the 
 required flow can be reduced to 1500 gpm if fully sprinklered. Doesn't that 
 work with your pumps?  
 
 Duane
 
 - Original Message -
 From: Johnson, Duane (NIH/OD/ORS) [C]
 Sent: Saturday, July 19, 2014 07:51 AM Eastern Standard Time
 To: 'sprinklerforum@lists.firesprinkler.org' 
 sprinklerforum@lists.firesprinkler.org
 Subject: Re: Segue to AHJ's from CPVC Underground
 
 Has Annex B been adopted?  See 101.2.1? 
 
 Duane
 
 - Original Message -
 From: mphe...@aerofire.com [mailto:mphe...@aerofire.com]
 Sent: Saturday, July 19, 2014 07:35 AM Eastern Standard Time
 To: sprinklerforum@lists.firesprinkler.org 
 sprinklerforum@lists.firesprinkler.org
 Subject: Re: Segue to AHJ's from CPVC Underground
 
 Hi John,
 What Ron didn't say is that the AHJ is trying to connect chapter 5 of the 
 IFC and table B105.2 fire flow requirements to our sprinkler system pumps. 
 We conceded early on to furnish a redundant pump because it was specified 
 that way, but the FM is expecting the fire pumps to provide the 4000 GPM 
 from B105.2 at the sprinkler (ESFR) demand pressure (165 PSI) and do so at 
 the 100% design point of the fire pump. We submitted our design with two 
 1500 GPM pumps piped in parallel along with calcs for the storage 
 sprinklers flowing at around 165 PSI at the pump discharge. The city water 
 system which supplies the project flow tested at 5700 GPM at 74 PSI from 
 two 4 hydrant butts. No one at the AHJ's office understands how to read a 
 fire code, or any other code for that matter. They are Code Alchemist, 
 taking a paragraph from chapter 5,  table from the annex, and numbers from 
 our calcs, mix 'em all together in an AHJ beaker and BOOM!! Minimum code 
 requirement. See? This stuff a
 i
 n
 't
 all that hard.
 
 Mark at Aero
 602 820-7894
 
 Sent from my iPad
 
 On Jul 19, 2014, at 2:24 AM, John Drucker 
 jdruc...@redbanknj.orgmailto:jdruc...@redbanknj.org wrote:
 
 Like how you wrote;  everything is per code except we have.  Except ?, 
 Are you/they saying that having two pumps rather than one is a violation; 
 I.e.  4000 GPM at 160 vs 4000 at 165 and you're short 5 psi ?  So two 
 code violations, two pumps and short 5 psi. Now before you chop my head 
 off, consider two things wheres the one pump and 165 psi 

Re: Segue to AHJ's from CPVC Underground

2014-07-19 Thread RFletcher
Wouldn't say the GC is sitting with the badge. He took a run at, found it to be 
futile and is now rightly concerned about turning the bldg over on time.
I'm sure at this point that we will change the pumps to 2000's and wait for the 
badge to go away before going back. We don't want lose money and customer.

Ron fletcher Sent from my iPhone

 On Jul 19, 2014, at 6:27 AM, John Drucker jdruc...@redbanknj.org wrote:
 
 It doesn't help, the public doesn't understand codes and a smart media 
 relations person will point out public and firefighter safety being 
 compromised over money which in the end is what this is all about.  When 
 refuted the point will be made to the contractor that if the pump 
 manufacturer was willing to provide the pumps for no charge and pick up the 
 labor most would install just like they did after Tyco ponied up for o ring 
 sprinkler replacement. Money changes everything. Like I said everyone needs 
 to sheath their swords and work this out, apparently the GC has already 
 conceded, so he's sitting with the FM.
 
 John Drucker - Mobile Email
 jdruc...@redbanknj.orgmailto:jdruc...@redbanknj.org
 Cell/Text 732-904-6823
 
 
 Cahill, Christopher ccah...@burnsmcd.com wrote:
 
 Ever thought about you and a few other contractors getting together with a 
 reporter? Nice little article about the abuses of government should help.
 
 
 Chris Cahill
 Fire Protection Engineer
 Burns  McDonnell
 952-656-3652
 ccah...@burnsmcd.com
 
 
  Original message 
 From: mphe...@aerofire.com
 Date:07/19/2014 8:09 AM (GMT-06:00)
 To: sprinklerforum@lists.firesprinkler.org
 Subject: Re: Segue to AHJ's from CPVC Underground
 
 This is where the universe starts to wobble, and then slip into a black hole. 
 I sent them this very section to show that our design MEETS their code. They 
 sent that section back to me to show that it DOESN'T. Then told us to do it 
 their way, or appeal to the State Fire Marshal.
 
 Sent from my iPhone
 
 On Jul 19, 2014, at 5:57 AM, Johnson, Duane (NIH/OD/ORS) [C] 
 johnson...@mail.nih.gov wrote:
 
 And A.4.8.
 
 Duane
 
 - Original Message -
 From: Johnson, Duane (NIH/OD/ORS) [C]
 Sent: Saturday, July 19, 2014 08:56 AM Eastern Standard Time
 To: 'sprinklerforum@lists.firesprinkler.org' 
 sprinklerforum@lists.firesprinkler.org
 Subject: Re: Segue to AHJ's from CPVC Underground
 
 See NFPA 20:4.8.1.
 
 Duane
 
 - Original Message -
 From: mphe...@aerofire.com [mailto:mphe...@aerofire.com]
 Sent: Saturday, July 19, 2014 08:42 AM Eastern Standard Time
 To: sprinklerforum@lists.firesprinkler.org 
 sprinklerforum@lists.firesprinkler.org
 Subject: Re: Segue to AHJ's from CPVC Underground
 
 The project is a 700k sq ft type Vb construction. B105.2 calls out 8000 GPM 
 fire flow. The locally adopted reduction is 50%, so 8000 x50% =4000 GPM. 
 They are correct about the flow rate. They just don't understand that that 
 is what is required from the municipal water system to the site for manual 
 fire fighting. They believe that out sprinkler booster pumps need to produce 
 4000 GPM at their 100% design point, and feel that operating a fire pump in 
 excess odors design point of 100% is somehow bad.
 Mark at Aero
 
 Sent from my iPhone
 
 On Jul 19, 2014, at 5:32 AM, Johnson, Duane (NIH/OD/ORS) [C] 
 johnson...@mail.nih.gov wrote:
 
 The question still stands why 4000?
 
 Duane
 
 - Original Message -
 From: rfletc...@aerofire.com [mailto:rfletc...@aerofire.com]
 Sent: Saturday, July 19, 2014 08:15 AM Eastern Standard Time
 To: sprinklerforum@lists.firesprinkler.org 
 sprinklerforum@lists.firesprinkler.org
 Subject: Re: Segue to AHJ's from CPVC Underground
 
 The stance of the AHJ is that their unwritten policy is pumps can only be 
 used at 100%. They also believe that 1500 gpm pumps will only produce 1500 
 gpm, and we have to use 2 2000 gpm pumps to get 4000 gpm. They don't think 
 pressure is even a factor.
 
 Ron fletcher Sent from my iPhone
 
 On Jul 19, 2014, at 5:00 AM, Johnson, Duane (NIH/OD/ORS) [C] 
 johnson...@mail.nih.gov wrote:
 
 There are so many things wrong here. But, you may be able to make this 
 work regardless. Did you take your 75% reduction in fire flow based on the 
 fully sprinklered exception in B105.2? If you are starting at 4000 gpm, 
 the required flow can be reduced to 1500 gpm if fully sprinklered. Doesn't 
 that work with your pumps?
 
 Duane
 
 - Original Message -
 From: Johnson, Duane (NIH/OD/ORS) [C]
 Sent: Saturday, July 19, 2014 07:51 AM Eastern Standard Time
 To: 'sprinklerforum@lists.firesprinkler.org' 
 sprinklerforum@lists.firesprinkler.org
 Subject: Re: Segue to AHJ's from CPVC Underground
 
 Has Annex B been adopted?  See 101.2.1?
 
 Duane
 
 - Original Message -
 From: mphe...@aerofire.com [mailto:mphe...@aerofire.com]
 Sent: Saturday, July 19, 2014 07:35 AM Eastern Standard Time
 To: sprinklerforum@lists.firesprinkler.org 
 sprinklerforum@lists.firesprinkler.org
 Subject: Re: Segue to 

Re: Segue to AHJ's from CPVC Underground

2014-07-19 Thread RFletcher
Had a FPE registered in the state call the badge. They talked for an hour and 
the FPE thought he was making some headway. Badge said he would email something 
outlining their unpublished policies. 15 minutes later he called back and said 
the chief told him not put a anything in writing. End of conversation.

Ron fletcher Sent from my iPhone

 On Jul 19, 2014, at 7:08 AM, John Drucker jdruc...@redbanknj.org wrote:
 
 Now we're talking but instead of a letter ask the pump mfg to press the flesh 
 with the AHJ.  The rep is fresh viewpoint and will bring technical expertise 
 to the table and typically some handout material. The FM saves face and gets 
 a way out. PS just the FM and the pump rep, since others will by human nature 
 blurt out I told you so which will undo gained ground.
 
 John Drucker - Mobile Email
 jdruc...@redbanknj.orgmailto:jdruc...@redbanknj.org
 Cell/Text 732-904-6823
 
 
 Ben Young derblitzkrie...@gmail.com wrote:
 
 I don't know the specifics of the pumps you're using, but my understanding
 is that normally its more efficient for most pumps to run from 100% to 150%
 and better for the long-term life as well.  Would a letter or discussion
 with the pump manufacturer have any impact on their reasoning do you think,
 or would it just be fuel on the fire?
 
 I feel for you guys, and hope there's something you can do to work this
 out.  We have our fair share of issues with AHJs in PA where there's no
 state FM to go to.
 
 Sometimes it feels like the wild west.
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Re: Segue to AHJ's from CPVC Underground

2014-07-19 Thread RFletcher
That's what I've been doing. The worst part besides the money is the wasted 
time and resources. I should be doing something productive, instead I'm trying 
to fix stupid.

Ron fletcher Sent from my iPhone

 On Jul 19, 2014, at 9:51 AM, Rod DiBona r...@rapidfireinc.com wrote:
 
 As I have watched this thread too many stories have come to mind. At the end 
 of the day there is only one explanation Ron, and I suppose you know this 
 well. A cost benefit analysis done by those that you have to make the 
 explanation to. Weighing the schedule impact, future political impact, time 
 it would take to appeal and potential attorney fees vs the $50k. Really too 
 bad that this even has to be considered, but I have had to do it all too 
 often. One tack is to prepare the paperwork and make the first step with the 
 appearance that the decision has been made to take it to the top regardless 
 of the previously mentioned impacts. Sometimes this forces the same type of 
 cost / benefit from the other side and is a catalyst for compromise. Ughhh. 
 Hope you can get this one worked out.
 
 Rod at Rapid
 
 -Original Message-
 From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] 
 On Behalf Of rfletc...@aerofire.com
 Sent: Friday, July 18, 2014 8:36 PM
 To: sprinklerforum@lists.firesprinkler.org
 Subject: Re: Segue to AHJ's from CPVC Underground
 
 Okay you explain the $40-50k hit to the bottom line
 
 Ron fletcher Sent from my iPhone
 
 On Jul 18, 2014, at 7:32 PM, Brad Casterline bcasterl...@fsc-inc.com 
 wrote:
 
 Best not to dwell on any one project too much
 
 On Jul 18, 2014, at 9:28 PM, rfletc...@aerofire.com wrote:
 
 Can't say how much this pisses me off.
 
 Ron fletcher Sent from my iPhone
 
 On Jul 18, 2014, at 7:19 PM, Brad Casterline bcasterl...@fsc-inc.com 
 wrote:
 
 You're alright like most of us the psychology part of sprinkler work just 
 makes you want to throw up in your mouth a little bit ,  right?
 
 On Jul 18, 2014, at 9:09 PM, rfletc...@aerofire.com wrote:
 
 How about everything is per code except we have two pumps rather than 
 one.and we have 4000 GM at 160 psi instead of.4000 gpm at 165 psi. Most 
 ignorant thing I have ever seen. Just found out the chief told plan 
 reviewer no more written correspondence. I guess because they don't want 
 a written orecord of their stupidity. Please forgive my frustration but I 
 just don't know where to go from here.. 
 
 Ron fletcher Sent from my iPhone
 
 On Jul 18, 2014, at 4:24 PM, John Drucker - Home 
 john.druc...@verizon.net wrote:
 
 Ron, et.al.
 
 I don't know the particulars of your situation but we have a 
 saying; there's your side, their side and the truth.  Perhaps 
 there's an issue with the code itself,  a local amendment or 
 interpretation. There's got to be something driving this.
 
 Case in point about a reference standard, NFPA-72 speaks of wall 
 mounted smoke detectors/alarms and calls out a distance yet the 
 illustration in the annex is worded differently than the code.
 
 29.8.3.3 Wall Mounting. Smoke alarms or smoke detectors mounted on 
 walls shall be located NOT FARTHER than 12 in. (300 mm) from the 
 adjoining ceiling surface.
 
 Yet the annex A.29.8.3 notes;  Measurements shown are to the 
 closest edge of the detector.
 
 According to the annex this would place part or most of the alarm 
 or detector FARTHER than 12 in. from the adjoining ceiling surface.
 
 It's important to note that Annex A opens with the following 
 statement;
 
 Annex A is not a part of the requirements of this NFPA document 
 but is included for informational purposes only. This annex 
 contains explanatory material, numbered to correspond with the 
 applicable text paragraphs
 
 Yet when brought to NFPA's attention the answer from the NFPA 
 representative was interpreted from the Annex material.  This is 
 clearly incorrect, the annex and the illustration are not part of the 
 code.  In either case fix the
 code language or the annex.   The same happens in I Code Commentaries and
 various subject matter books that often interpret, amend or 
 supplement the actual code language.  In a nutshell our codes and 
 standards have become a maze of requirements, exceptions and 
 interpretations.  This should be a warning flag to the code 
 community.  Perhaps the code official has just reached his limit 
 and is instead relying on empirical experience in the face of confusion.
 
 I have situation at this very moment on two different projects 
 that impose an operational issue for the fire department, one that 
 the code is not considering.  However my approach is to get 
 everyone around the table do some brainstorming and come up with an 
 equitable technical solution.
 Perhaps by finding the root cause of your situation the stakeholders will
 put down their swords and solve the problem.   Food for thought.
 
 Best wishes, always available should the need arise.
 
 Sincerely,
 
 John
 
 John Drucker, CET
 Assistant Construction 

Re: Segue to AHJ's from CPVC Underground

2014-07-19 Thread RFletcher
Certainly it has occurred to me but I would hope that isn't the case. There are 
some union and some non in the area. While some may not like that we are in 
their backyard I prefer to think that this issue is just a lack of 
sophistication on ths part of the badge. 

Ron fletcher Sent from my iPhone

 On Jul 19, 2014, at 4:06 PM, Forest Wilson cherokeefire...@aol.com wrote:
 
 The COO is more than just a formality.
 If an owner occupies without the COO, he/ she is subject to arrest by armed 
 marshals.
 It doesnt matter if its a mall owner or a small homeowner out in the middle 
 of nowhere.
 If she/he resists arrest or removal they may be killed, and at the very 
 minimum imprisoned.
 Why would any sensible owner risk that over a piece of paper?
 
 A friend of mine is a roofing contractor.
 They had a regional contract with a fast food chain; one of the projects was 
 in the greater Chicago area. They needed a sign off but the AHJ would not 
 schedule the inspection. Finally he went down to her office and she told him: 
 WE dont like you here (he was non union) and dont want you here.
 He agreed to never do business in her jurisdiction again; in return she went 
 out and signed off on the roof inspection.
 
 Since you are the out of town contractor, have you considered that perhaps 
 the AHJ is sending you a similar message of staying out of town and not 
 biting into the locals work?
 
 
 On 7/19/2014 6:54 PM, John Drucker - Home wrote:
 Bob,
 
 Unfortunately they can indirectly by withholding a certificate of approval,
 compliance or occupancy.  Most property owners need this document for
 closing, insurance or tenancy and or their attorney advises them that they
 will or have now broken an adopted law or regulation.  So despite the
 illegitimacy of the code officials claim the property owner or tenant has
 now legitimately broken the rules by occupying without a certificate of
 occupancy and or certificate of approval. In other words the enforcing
 agency holds the cards.
 
 Code Enforcement is a legal process and like all or most legal processes in
 the United States the aggrieved must petition for relief, in code
 enforcement parlance by filing an appeal.  The appeal allows the appellant
 to present his/her position to an independent body who will render a
 decision in favor of the appellant or the government.  I cant speak for
 other states but in New Jersey decisions of boards of appeals are binding on
 the enforcing agency, but this is important they don't set precedent and or
 amend the code. In other words one could win an appeal in one jurisdiction
 only to have to go through the process in another.  As for the state level
 unless theirs maleficence the state cannot overrule a local enforcing agency
 since the local enforcing agencies appointment bestows approval authority to
 the local enforcing agency.
 
 There is good reason for this, to avoid undue political influence, approve
 this project but not this one.  So what's a contractor to do, file an
 appeal, that's the proper route, but keep in mind that boards of appeal
 typically set aside cost of compliance issues much like requests for
 variations cannot be based on financial hardship. So be sure the code
 official is imposing above and beyond the adopted code including any
 interpretive authority bestowed to the code official.   Those in the
 electrical field know all too well about NEC;
 
 NEC 90.4 Enforcement. This Code is intended to be suitable for mandatory
 application by governmental bodies that exercise legal jurisdiction over
 electrical installations, including signaling and communications systems,
 and for use by insurance inspectors. The authority having jurisdiction for
 enforcement of the Code has the responsibility for making interpretations of
 the rules, for deciding on the approval of equipment and materials, and for
 granting the special permission contemplated in a number of the rules. By
 special permission, the authority having jurisdiction may waive specific
 requirements in this Code or permit alternative methods where it is assured
 that equivalent objectives can be achieved by establishing and maintaining
 effective safety. This Code may require new products, constructions, or
 materials that may not yet be available at the time the Code is adopted. In
 such event, the authority having jurisdiction may permit the use of the
 products, constructions, or materials that comply with the most recent
 previous edition of this Code adopted by the jurisdiction.
 
 So there you have it in a nutshell, I'm not siding with either party just
 presenting information.  Best wishes.
 
 Sincerely,
 
 John Drucker, CET
 Assistant Construction Official
 Fire Protection Subcode Official
 Building/Fire/Electrical Inspector
 Borough of Red Bank
 Red Bank, New Jersey
 Email: jdruc...@redbanknj.org
 Cell/Text: 732-904-6823
 
 
 
 
 -Original Message-
 From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]

RE: Blazemaster CPVC Underground

2014-07-18 Thread RFletcher
That's a good one. I'll add that to my so you think you have heard everything 
list. Like saying it's approved below a valve but not above. Does he have a 
code reference or is this it just their opinion? Can you have someone from the 
manufacturer call them?
Ron F 

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Tony Liddic
Sent: Friday, July 18, 2014 6:18 AM
To: sprinklerforum
Subject: Blazemaster CPVC Underground

I have a client that does a lot of typical apartment building in various 
jurisdictions. The buildings are 3 stories with breezeways 1/3 of the way down 
the length of the building.

They are 13R systems and the client has always used Blazemaster CPVC. They run 
a main down the center of the 1st floor, drop below the breezeway underground 
then back up in a wall on the other side. This has never been an issue until 
now.

An AHJ is stating that the CPVC is not approved for underground use on the 
system side of the riser, only the supply side.

Any thoughts?

Thanks,

Tony Liddic, CET
MRH Sprinkler Design LLC
356 Laurel Glen Dr.
Springboro, OH  45066
937-369-7926
http://mrhsprinklerdesign.com
tony.lid...@mrhsprinklerdesign.com
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Blazemaster CPVC Underground

2014-07-18 Thread RFletcher
I wish there was a way to deal with abusive AHJ's. It seems like every time we 
go into a new jurisdiction we have to waste time and money proving what we 
already know to be a fact. Then their ego gets hurt and they get stubborn.
Ron F

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Tony Liddic
Sent: Friday, July 18, 2014 6:52 AM
To: sprinklerforum
Subject: Re: Blazemaster CPVC Underground

Bonus Points for this AHJ:

Just heard from the client that they did another project exactly like this
10 months ago in the same jurisdiction. Same argument came up and AHJ approved 
the installation then!!!

Apparently he doesn't want to approve it again.

Thanks,

Tony Liddic, CET
MRH Sprinkler Design LLC
356 Laurel Glen Dr.
Springboro, OH  45066
937-369-7926
http://mrhsprinklerdesign.com
tony.lid...@mrhsprinklerdesign.com



On Fri, Jul 18, 2014 at 9:49 AM, Tony Liddic  
tony.lid...@mrhsprinklerdesign.com wrote:

 He tried to claim NFPA 13R (2010) 5.3

 5.3* Underground Pipe. Any type of pipe or tube acceptable under the 
 plumbing code for underground supply pipe shall be acceptable as 
 underground supply for the system when in- stalled between the point 
 of connection and the system riser.

 I replied that this section of NFPA 13R simply allows the pipe between 
 supply and system riser to be anything allowed in the plumbing code 
 instead of having a dedicated chapter for underground as in NFPA 13. 
 This does not, however, have any effect on materials after the system riser.

 I also sent him the section from Tyco's Installation manual that 
 applies to Underground installations.

 He must not have liked my response because now he is simply stating 
 that CPVC is only allowed underground before the riser. His argument 
 is that the Tyco Manual mentions underground service and not 
 sprinkler system piping.

 Thanks,

 Tony Liddic, CET
 MRH Sprinkler Design LLC
 356 Laurel Glen Dr.
 Springboro, OH  45066
 937-369-7926
 http://mrhsprinklerdesign.com
 tony.lid...@mrhsprinklerdesign.com



 On Fri, Jul 18, 2014 at 9:47 AM, mphe...@aerofire.com wrote:

 How would the pipe know which side of the riser it's on?
 Mark at Aero

 Sent from my iPhone

  On Jul 18, 2014, at 6:18 AM, Tony Liddic 
 tony.lid...@mrhsprinklerdesign.com wrote:
 
  I have a client that does a lot of typical apartment building in 
  various jurisdictions. The buildings are 3 stories with breezeways 
  1/3 of the
 way
  down the length of the building.
 
  They are 13R systems and the client has always used Blazemaster CPVC.
 They
  run a main down the center of the 1st floor, drop below the 
  breezeway underground then back up in a wall on the other side. 
  This has never
 been
  an issue until now.
 
  An AHJ is stating that the CPVC is not approved for underground use 
  on
 the
  system side of the riser, only the supply side.
 
  Any thoughts?
 
  Thanks,
 
  Tony Liddic, CET
  MRH Sprinkler Design LLC
  356 Laurel Glen Dr.
  Springboro, OH  45066
  937-369-7926
  http://mrhsprinklerdesign.com
  tony.lid...@mrhsprinklerdesign.com
  ___
  Sprinklerforum mailing list
  Sprinklerforum@lists.firesprinkler.org
 
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprink
 ler.org ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org

 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprink
 ler.org



___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Segue to AHJ's from CPVC Underground

2014-07-18 Thread RFletcher
It's Friday so I figured I'd whine on the forum.  To set the stage, prior to 
the letter I am referring to we had approved permitted drawings from the AHJ. 
The following is a quote from a letter we received from that same AHJ.

At this time , Blah Blah Blah Fire Protection District is denying said plans 
and is requesting a re-submittal of new plans that exceed IFC, UFC, and NFPA 
standards. Nowhere in the body of the letter does he say exactly how we are to 
EXCEED IFC, UFC and NFPA. In the letter they basically outline that what was 
submitted meets the all of the codes. I was told by the author of the letter at 
a meeting the day before that he didn't care what the code said because he is 
the AHJ and per Section 104 of the IFC he can make us do whatever he wants. 
Then he said do it my way or there will be no Certificate of Occupancy.  We 
are 4-5 weeks away from a CofO and the change involves increasing the size of 
two new diesel pumps that are being installed. The fire chief told us to go to 
the State Fire Marshal if we wanted to appeal. I'm a bit frustrated with AHJ's 
right now.

Ron F
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Segue to AHJ's from CPVC Underground

2014-07-18 Thread RFletcher
Yikes, that isn't very encouraging. The chief told us to go to the State FM is 
we wanted to appeal so there might be some hope.
Ron F
-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Roland Huggins
Sent: Friday, July 18, 2014 10:25 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Segue to AHJ's from CPVC Underground

The last discussion I was around regarding a local AHJ and the State FM, the 
local effectively told the State that their opinion had no bearing on the 
outcome.


Roland Huggins, PE - VP Engineering
American Fire Sprinkler Assn.   ---  Fire Sprinklers Saves Lives
Dallas, TX
http://www.firesprinkler.org





On Jul 18, 2014, at 10:03 AM, rfletc...@aerofire.com rfletc...@aerofire.com 
wrote:

 The fire chief told us to go to the State Fire Marshal if we wanted to 
 appeal. I'm a bit frustrated with AHJ's right now.
 
 Ron F

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Segue to AHJ's from CPVC Underground

2014-07-18 Thread RFletcher
I told him that IFC didn't give him the power to do what he thinks. That's when 
he gave me the ultimatum. Can you believe he wrote a letter saying that we have 
to EXCEED the adopted codes?
Ron F

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Cahill, Christopher
Sent: Friday, July 18, 2014 10:26 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Segue to AHJ's from CPVC Underground

Wow, and he doesn't even know what that section says.

 The fire code official is hereby authorized to enforce the provisions of this 
code and shall have the authority to render interpretations of this code, and 
to adopt policies, procedures, rules and regulations in order to clarify the 
application of its provisions. Such interpretations, policies, procedures, 
rules and regulations shall be in compliance with the intent and purpose of 
this code and shall not have the effect of waiving requirements specifically 
provided for in this code.

Enforce THIS code... shall be in compliance with the intent and purpose of THIS 
code.  I don't see where he gets HIS code in place of THIS code. And 
interpretation are only allowed to CLARIFY.  What's not clear is the issue.

Private contractor AHJ or gov't employed AHJ?  Reason being is the contract 
doesn't have the same liability protections usually.  IOW you can sue a contact 
AHJ easier than the gov't.  I'd suggest you have your attorney reply.  

Hope you have an owner willing to tell them they are moving in without CofO.  
'Cuz that's the way it really gets in front of a judge.  He's right in that he 
can hold the CofO.  That's a powerful tool.  Only the owner can push this and 
move in.  Then the AHJ writes a ticket and you get to go to the judge (assuming 
the City attorney doesn't squash it) to explain how the gov't is wrong on the 
basis of denying the CofO.  I've had a few AHJ's cave when an owner tells them 
we'll see you in court.  But sadly most owners cave and write a check for the 
unlawful requirement. 

And consider this, the local sprink chapter in MN hired a lawyer a few years 
ago to write a white paper about the law and legal limits of what AHJ's can 
actually do.  It was mailed to every AHJ in the State. I'm out of contracting 
now so I don't know how effective it was but at least it made them aware we 
weren't a bunch of dumb contractors that will fall for their every whim.   

Chris Cahill, PE*
Associate Fire Protection Engineer 
Burns  McDonnell
Phone:  952.656.3652
Fax:  952.229.2923
ccah...@burnsmcd.com
www.burnsmcd.com
*Registered in: MN


Proud to be #14 on FORTUNE's 2014 List of 100 Best Companies to Work For





-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of rfletc...@aerofire.com
Sent: Friday, July 18, 2014 12:04 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Segue to AHJ's from CPVC Underground

It's Friday so I figured I'd whine on the forum.  To set the stage, prior to 
the letter I am referring to we had approved permitted drawings from the AHJ. 
The following is a quote from a letter we received from that same AHJ.

At this time , Blah Blah Blah Fire Protection District is denying said plans 
and is requesting a re-submittal of new plans that exceed IFC, UFC, and NFPA 
standards. Nowhere in the body of the letter does he say exactly how we are to 
EXCEED IFC, UFC and NFPA. In the letter they basically outline that what was 
submitted meets the all of the codes. I was told by the author of the letter at 
a meeting the day before that he didn't care what the code said because he is 
the AHJ and per Section 104 of the IFC he can make us do whatever he wants. 
Then he said do it my way or there will be no Certificate of Occupancy.  We 
are 4-5 weeks away from a CofO and the change involves increasing the size of 
two new diesel pumps that are being installed. The fire chief told us to go to 
the State Fire Marshal if we wanted to appeal. I'm a bit frustrated with AHJ's 
right now.

Ron F
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Re: Segue to AHJ's from CPVC Underground

2014-07-18 Thread RFletcher
All too true and I really enjoyed your metaphor with compost. I am trying give 
the badge what he wants. Schedule is the biggest issue. I just found out thAt I 
can buy two new pump cases keeping the same engines and have them re- labeled 
as 2000 gpm. Cost without labor $20-25k. The badge did tell the GC that there 
is no way they will allow two 1500 gpm diesel PLD's on temp basis but he will 
accept a 24 hour fire watch. It's like doing fire protection on crack.
Ron fletcher Sent from my iPhone

 On Jul 18, 2014, at 3:30 PM, Forest Wilson cherokeefire...@aol.com wrote:
 
 I just returned from a month long vacation; when I was gone the city 
 Lawnmower cop issued a ticket for not mowing the grass in my yard.
 When I returned, I met with the Lawnmower Cop and another Code cop (who just 
 issued a ticket to a business friend for flying a flag in front of his 
 convenience store without a flag permit).
 The Lawnmower Cop also demanded that I remove plants that I planted between 
 the city sidewalk and the street; However, last year I ased if there was a 
 regulation against planting there and was given the green light by his 
 partner. Fortunately, I saved this in an email and showed it to the lawnmower 
 cops.
 It was at that point that Lawnmower cop explained to me that your compost 
 bin in the back is too much and we dont like your mulch and on and on.
 He made it very clear that I could fight him on one thing but then he would 
 harass me non stop and never go away, all with the power of government at his 
 command.
 
 So...I dropped the subject and did with the Lawnmower Cops asked of me.
 
 The recent post about an owner taking occupancy without a COO: Most would not 
 do this because if they do, they are subject to arrest by armed officers.
 It is safer to just do whatever the government agent says to.
 
 There used to be a fire inspector in the Cleveland area that insisted on 
 accompanying contractors on EVERY NFPA 25 inspection. The man was a racist 
 and I had to endure listening to his garbage (as did the owner reps) talk 
 about minorities while just trying to do an inspection and move on to the 
 next job. If either of us complained we would of just had problems doing work 
 in his jurisdiction.
 
 Same thing with contracting. As a licensed contractor, there is immense 
 potential liability.
 Yet AHJ are immune from liability (from an old English law doctrine that the 
 king can do no wrong. )
 So why argue with someone that is immune from legal consequences? Why spend 
 the money (which cant be recovered) to fight something he wants done?
 It's better to just do what he says and move on to the next job...and NEVER 
 bid work in that jurisdiction again.
 
 
 On 7/18/2014 5:04 PM, Taylor, Galen wrote:
 Speaking as an AHJ, WE expect architects, engineers, land developers and 
 contractors to comply with all applicable laws, codes, regulations and 
 ordinances relative to your project. YOU have every right to expect the same 
 from us.
 
 You should not shy away from expressing your concern/complaint to the next 
 higher authority until you've reached the top of the food chain. At the end 
 of the day everyone will have gained from the experience. It only takes one 
 of you to make life easier for the next guy. Occasionally, I have been able 
 to educate an architect, engineer or contractor; but I have been privileged 
 countless time to learn from them.
 
 On behalf of AHJ's everywhere, I apologize for the difficulties you all have 
 endured.
 
 Galen Taylor
 County of Los Angeles Fire Department
 Fire Prevention Engineering
 323-890-4339
 galen.tay...@fire.lacounty.gov
 
 -Original Message-
 From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] 
 On Behalf Of Jeremy Frazier
 Sent: Friday, July 18, 2014 1:31 PM
 To: sprinklerforum@lists.firesprinkler.org
 Subject: RE: Segue to AHJ's from CPVC Underground
 
 The best way to fight that is  to look up the law that adopts the adopted 
 code.  See if the law even gives the power to exceed the adopted codes.
 Then go to the town/city council talk and have a chat. (changes per state) 
 Be honest, tell the financial impact of such a decision and there is no 
 basis in the code, the fmo is exceeding his scope and show them a letter.
 I've seen FMOs steamrolled this way, when they actually were 100% 
 right(which is disappointing),  so I imagine it would work the same way if 
 they are 100% wrong.  Of course a pissing match with the AHJ  will never end 
 well.
 
 -Original Message-
 From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
 On Behalf Of rfletc...@aerofire.com
 Sent: Friday, July 18, 2014 1:55 PM
 To: sprinklerforum@lists.firesprinkler.org
 Subject: RE: Segue to AHJ's from CPVC Underground
 
 I told him that IFC didn't give him the power to do what he thinks. That's 
 when he gave me the ultimatum. Can you believe he wrote a letter saying that 
 we have to EXCEED the adopted codes?

Re: Segue to AHJ's from CPVC Underground

2014-07-18 Thread RFletcher
How about everything is per code except we have two pumps rather than one.and 
we have 4000 GM at 160 psi instead of.4000 gpm at 165 psi. Most ignorant thing 
I have ever seen. Just found out the chief told plan reviewer no more written 
correspondence. I guess because they don't want a written orecord of their 
stupidity. Please forgive my frustration but I just don't know where to go from 
here.. 

Ron fletcher Sent from my iPhone

 On Jul 18, 2014, at 4:24 PM, John Drucker - Home john.druc...@verizon.net 
 wrote:
 
 Ron, et.al.
 
 I don't know the particulars of your situation but we have a saying; there's
 your side, their side and the truth.  Perhaps there's an issue with the code
 itself,  a local amendment or interpretation. There's got to be something
 driving this.
 
 Case in point about a reference standard, NFPA-72 speaks of wall mounted
 smoke detectors/alarms and calls out a distance yet the illustration in the
 annex is worded differently than the code.
 
 29.8.3.3 Wall Mounting. Smoke alarms or smoke detectors mounted on walls
 shall be located NOT FARTHER than 12 in. (300 mm) from the adjoining ceiling
 surface.
 
 Yet the annex A.29.8.3 notes;  Measurements shown are to the closest edge
 of the detector.
 
 According to the annex this would place part or most of the alarm or
 detector FARTHER than 12 in. from the adjoining ceiling surface.
 
 It's important to note that Annex A opens with the following statement;
 
 Annex A is not a part of the requirements of this NFPA document but is
 included for informational purposes only. This annex contains explanatory
 material, numbered to correspond with the applicable text paragraphs
 
 Yet when brought to NFPA's attention the answer from the NFPA representative
 was interpreted from the Annex material.  This is clearly incorrect, the
 annex and the illustration are not part of the code.  In either case fix the
 code language or the annex.   The same happens in I Code Commentaries and
 various subject matter books that often interpret, amend or supplement the
 actual code language.  In a nutshell our codes and standards have become a
 maze of requirements, exceptions and interpretations.  This should be a
 warning flag to the code community.  Perhaps the code official has just
 reached his limit and is instead relying on empirical experience in the face
 of confusion. 
 
 I have situation at this very moment on two different projects that impose
 an operational issue for the fire department, one that the code is not
 considering.  However my approach is to get everyone around the table do
 some brainstorming and come up with an equitable technical solution.
 Perhaps by finding the root cause of your situation the stakeholders will
 put down their swords and solve the problem.   Food for thought.
 
 Best wishes, always available should the need arise.
 
 Sincerely,
 
 John
 
 John Drucker, CET
 Assistant Construction Official
 Fire Protection Subcode Official
 Building/Fire/Electrical Inspector
 Borough of Red Bank
 Red Bank, New Jersey
 Email: jdruc...@redbanknj.org
 Cell/Text: 732-904-6823
 
 Safe Buildings Save Lives !
 
 
 
 
 
 
 
 
 
 
 
 
 -Original Message-
 From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
 On Behalf Of rfletc...@aerofire.com
 Sent: Friday, July 18, 2014 1:04 PM
 To: sprinklerforum@lists.firesprinkler.org
 Subject: Segue to AHJ's from CPVC Underground
 
 It's Friday so I figured I'd whine on the forum.  To set the stage, prior to
 the letter I am referring to we had approved permitted drawings from the
 AHJ. The following is a quote from a letter we received from that same AHJ.
 
 At this time , Blah Blah Blah Fire Protection District is denying said
 plans and is requesting a re-submittal of new plans that exceed IFC, UFC,
 and NFPA standards. Nowhere in the body of the letter does he say exactly
 how we are to EXCEED IFC, UFC and NFPA. In the letter they basically
 outline that what was submitted meets the all of the codes. I was told by
 the author of the letter at a meeting the day before that he didn't care
 what the code said because he is the AHJ and per Section 104 of the IFC he
 can make us do whatever he wants. Then he said do it my way or there will
 be no Certificate of Occupancy.  We are 4-5 weeks away from a CofO and the
 change involves increasing the size of two new diesel pumps that are being
 installed. The fire chief told us to go to the State Fire Marshal if we
 wanted to appeal. I'm a bit frustrated with AHJ's right now.
 
 Ron F
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
 
 
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___

Re: Segue to AHJ's from CPVC Underground

2014-07-18 Thread RFletcher
Can't say how much this pisses me off.

Ron fletcher Sent from my iPhone

 On Jul 18, 2014, at 7:19 PM, Brad Casterline bcasterl...@fsc-inc.com 
 wrote:
 
 You're alright like most of us the psychology part of sprinkler work just 
 makes you want to throw up in your mouth a little bit ,  right?
 
 On Jul 18, 2014, at 9:09 PM, rfletc...@aerofire.com wrote:
 
 How about everything is per code except we have two pumps rather than 
 one.and we have 4000 GM at 160 psi instead of.4000 gpm at 165 psi. Most 
 ignorant thing I have ever seen. Just found out the chief told plan reviewer 
 no more written correspondence. I guess because they don't want a written 
 orecord of their stupidity. Please forgive my frustration but I just don't 
 know where to go from here.. 
 
 Ron fletcher Sent from my iPhone
 
 On Jul 18, 2014, at 4:24 PM, John Drucker - Home 
 john.druc...@verizon.net wrote:
 
 Ron, et.al.
 
 I don't know the particulars of your situation but we have a saying; there's
 your side, their side and the truth.  Perhaps there's an issue with the code
 itself,  a local amendment or interpretation. There's got to be something
 driving this.
 
 Case in point about a reference standard, NFPA-72 speaks of wall mounted
 smoke detectors/alarms and calls out a distance yet the illustration in the
 annex is worded differently than the code.
 
 29.8.3.3 Wall Mounting. Smoke alarms or smoke detectors mounted on walls
 shall be located NOT FARTHER than 12 in. (300 mm) from the adjoining ceiling
 surface.
 
 Yet the annex A.29.8.3 notes;  Measurements shown are to the closest edge
 of the detector.
 
 According to the annex this would place part or most of the alarm or
 detector FARTHER than 12 in. from the adjoining ceiling surface.
 
 It's important to note that Annex A opens with the following statement;
 
 Annex A is not a part of the requirements of this NFPA document but is
 included for informational purposes only. This annex contains explanatory
 material, numbered to correspond with the applicable text paragraphs
 
 Yet when brought to NFPA's attention the answer from the NFPA representative
 was interpreted from the Annex material.  This is clearly incorrect, the
 annex and the illustration are not part of the code.  In either case fix the
 code language or the annex.   The same happens in I Code Commentaries and
 various subject matter books that often interpret, amend or supplement the
 actual code language.  In a nutshell our codes and standards have become a
 maze of requirements, exceptions and interpretations.  This should be a
 warning flag to the code community.  Perhaps the code official has just
 reached his limit and is instead relying on empirical experience in the face
 of confusion. 
 
 I have situation at this very moment on two different projects that impose
 an operational issue for the fire department, one that the code is not
 considering.  However my approach is to get everyone around the table do
 some brainstorming and come up with an equitable technical solution.
 Perhaps by finding the root cause of your situation the stakeholders will
 put down their swords and solve the problem.   Food for thought.
 
 Best wishes, always available should the need arise.
 
 Sincerely,
 
 John
 
 John Drucker, CET
 Assistant Construction Official
 Fire Protection Subcode Official
 Building/Fire/Electrical Inspector
 Borough of Red Bank
 Red Bank, New Jersey
 Email: jdruc...@redbanknj.org
 Cell/Text: 732-904-6823
 
 Safe Buildings Save Lives !
 
 
 
 
 
 
 
 
 
 
 
 
 -Original Message-
 From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
 On Behalf Of rfletc...@aerofire.com
 Sent: Friday, July 18, 2014 1:04 PM
 To: sprinklerforum@lists.firesprinkler.org
 Subject: Segue to AHJ's from CPVC Underground
 
 It's Friday so I figured I'd whine on the forum.  To set the stage, prior to
 the letter I am referring to we had approved permitted drawings from the
 AHJ. The following is a quote from a letter we received from that same AHJ.
 
 At this time , Blah Blah Blah Fire Protection District is denying said
 plans and is requesting a re-submittal of new plans that exceed IFC, UFC,
 and NFPA standards. Nowhere in the body of the letter does he say exactly
 how we are to EXCEED IFC, UFC and NFPA. In the letter they basically
 outline that what was submitted meets the all of the codes. I was told by
 the author of the letter at a meeting the day before that he didn't care
 what the code said because he is the AHJ and per Section 104 of the IFC he
 can make us do whatever he wants. Then he said do it my way or there will
 be no Certificate of Occupancy.  We are 4-5 weeks away from a CofO and the
 change involves increasing the size of two new diesel pumps that are being
 installed. The fire chief told us to go to the State Fire Marshal if we
 wanted to appeal. I'm a bit frustrated with AHJ's right now.
 
 Ron F
 ___
 Sprinklerforum mailing 

Re: Segue to AHJ's from CPVC Underground

2014-07-18 Thread RFletcher
Okay you explain the $40-50k hit to the bottom line

Ron fletcher Sent from my iPhone

 On Jul 18, 2014, at 7:32 PM, Brad Casterline bcasterl...@fsc-inc.com 
 wrote:
 
 Best not to dwell on any one project too much
 
 On Jul 18, 2014, at 9:28 PM, rfletc...@aerofire.com wrote:
 
 Can't say how much this pisses me off.
 
 Ron fletcher Sent from my iPhone
 
 On Jul 18, 2014, at 7:19 PM, Brad Casterline bcasterl...@fsc-inc.com 
 wrote:
 
 You're alright like most of us the psychology part of sprinkler work just 
 makes you want to throw up in your mouth a little bit ,  right?
 
 On Jul 18, 2014, at 9:09 PM, rfletc...@aerofire.com wrote:
 
 How about everything is per code except we have two pumps rather than 
 one.and we have 4000 GM at 160 psi instead of.4000 gpm at 165 psi. Most 
 ignorant thing I have ever seen. Just found out the chief told plan 
 reviewer no more written correspondence. I guess because they don't want a 
 written orecord of their stupidity. Please forgive my frustration but I 
 just don't know where to go from here.. 
 
 Ron fletcher Sent from my iPhone
 
 On Jul 18, 2014, at 4:24 PM, John Drucker - Home 
 john.druc...@verizon.net wrote:
 
 Ron, et.al.
 
 I don't know the particulars of your situation but we have a saying; 
 there's
 your side, their side and the truth.  Perhaps there's an issue with the 
 code
 itself,  a local amendment or interpretation. There's got to be something
 driving this.
 
 Case in point about a reference standard, NFPA-72 speaks of wall mounted
 smoke detectors/alarms and calls out a distance yet the illustration in 
 the
 annex is worded differently than the code.
 
 29.8.3.3 Wall Mounting. Smoke alarms or smoke detectors mounted on walls
 shall be located NOT FARTHER than 12 in. (300 mm) from the adjoining 
 ceiling
 surface.
 
 Yet the annex A.29.8.3 notes;  Measurements shown are to the closest edge
 of the detector.
 
 According to the annex this would place part or most of the alarm or
 detector FARTHER than 12 in. from the adjoining ceiling surface.
 
 It's important to note that Annex A opens with the following statement;
 
 Annex A is not a part of the requirements of this NFPA document but is
 included for informational purposes only. This annex contains explanatory
 material, numbered to correspond with the applicable text paragraphs
 
 Yet when brought to NFPA's attention the answer from the NFPA 
 representative
 was interpreted from the Annex material.  This is clearly incorrect, the
 annex and the illustration are not part of the code.  In either case fix 
 the
 code language or the annex.   The same happens in I Code Commentaries and
 various subject matter books that often interpret, amend or supplement the
 actual code language.  In a nutshell our codes and standards have become a
 maze of requirements, exceptions and interpretations.  This should be a
 warning flag to the code community.  Perhaps the code official has just
 reached his limit and is instead relying on empirical experience in the 
 face
 of confusion. 
 
 I have situation at this very moment on two different projects that impose
 an operational issue for the fire department, one that the code is not
 considering.  However my approach is to get everyone around the table do
 some brainstorming and come up with an equitable technical solution.
 Perhaps by finding the root cause of your situation the stakeholders will
 put down their swords and solve the problem.   Food for thought.
 
 Best wishes, always available should the need arise.
 
 Sincerely,
 
 John
 
 John Drucker, CET
 Assistant Construction Official
 Fire Protection Subcode Official
 Building/Fire/Electrical Inspector
 Borough of Red Bank
 Red Bank, New Jersey
 Email: jdruc...@redbanknj.org
 Cell/Text: 732-904-6823
 
 Safe Buildings Save Lives !
 
 
 
 
 
 
 
 
 
 
 
 
 -Original Message-
 From: Sprinklerforum 
 [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
 On Behalf Of rfletc...@aerofire.com
 Sent: Friday, July 18, 2014 1:04 PM
 To: sprinklerforum@lists.firesprinkler.org
 Subject: Segue to AHJ's from CPVC Underground
 
 It's Friday so I figured I'd whine on the forum.  To set the stage, prior 
 to
 the letter I am referring to we had approved permitted drawings from the
 AHJ. The following is a quote from a letter we received from that same 
 AHJ.
 
 At this time , Blah Blah Blah Fire Protection District is denying said
 plans and is requesting a re-submittal of new plans that exceed IFC, UFC,
 and NFPA standards. Nowhere in the body of the letter does he say exactly
 how we are to EXCEED IFC, UFC and NFPA. In the letter they basically
 outline that what was submitted meets the all of the codes. I was told by
 the author of the letter at a meeting the day before that he didn't care
 what the code said because he is the AHJ and per Section 104 of the IFC he
 can make us do whatever he wants. Then he said do it my way or there will
 be no Certificate of Occupancy.  We are 4-5 weeks away from a CofO 

Re: Segue to AHJ's from CPVC Underground

2014-07-18 Thread RFletcher
I call ittroglydite infeztation

Ron fletcher Sent from my iPhone

 On Jul 18, 2014, at 7:56 PM, Todd - Work t...@fpdc.com wrote:
 
 My favorite is home rule (aka we can make up whatever the heck we want) 
 places like Texas. Did a small job for a company in a place around Houston. 
 Was supposed to be a small group home designed to 13D. A new Fire Marshal 
 came in half way through the project and changed the requirements to 13R and 
 rejected the previously approved plans. 
 
 Todd G Williams, PE
 Fire Protection Design/Consulting
 Stonington, CT
 www.fpdc.com
 860-535-2080 (ofc)
 
 On Jul 18, 2014, at 10:43 PM, Brad Casterline bcasterl...@fsc-inc.com 
 wrote:
 
 I was just thinking about that and all I got is , out of nowhere pops a 
 brilliant young engineering intern, on a Spring Morning in Kansas, barefoot, 
 w/ her blue jeans rolled up to her knees, hollering out pump pitot readings, 
 so, sorry Ron.
 
 On Jul 18, 2014, at 9:35 PM, rfletc...@aerofire.com wrote:
 
 Okay you explain the $40-50k hit to the bottom line
 
 Ron fletcher Sent from my iPhone
 
 On Jul 18, 2014, at 7:32 PM, Brad Casterline bcasterl...@fsc-inc.com 
 wrote:
 
 Best not to dwell on any one project too much
 
 On Jul 18, 2014, at 9:28 PM, rfletc...@aerofire.com wrote:
 
 Can't say how much this pisses me off.
 
 Ron fletcher Sent from my iPhone
 
 On Jul 18, 2014, at 7:19 PM, Brad Casterline bcasterl...@fsc-inc.com 
 wrote:
 
 You're alright like most of us the psychology part of sprinkler work 
 just makes you want to throw up in your mouth a little bit ,  right?
 
 On Jul 18, 2014, at 9:09 PM, rfletc...@aerofire.com wrote:
 
 How about everything is per code except we have two pumps rather than 
 one.and we have 4000 GM at 160 psi instead of.4000 gpm at 165 psi. Most 
 ignorant thing I have ever seen. Just found out the chief told plan 
 reviewer no more written correspondence. I guess because they don't 
 want a written orecord of their stupidity. Please forgive my 
 frustration but I just don't know where to go from here.. 
 
 Ron fletcher Sent from my iPhone
 
 On Jul 18, 2014, at 4:24 PM, John Drucker - Home 
 john.druc...@verizon.net wrote:
 
 Ron, et.al.
 
 I don't know the particulars of your situation but we have a saying; 
 there's
 your side, their side and the truth.  Perhaps there's an issue with 
 the code
 itself,  a local amendment or interpretation. There's got to be 
 something
 driving this.
 
 Case in point about a reference standard, NFPA-72 speaks of wall 
 mounted
 smoke detectors/alarms and calls out a distance yet the illustration 
 in the
 annex is worded differently than the code.
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: FM Approved 8.0 K spray nozzle

2014-07-10 Thread RFletcher
8K spray nozzle is pretty odd device if you can't use standard spray 
sprinklers. Tyco D3's only go to 7.2K. I would talk to the FM rep about an 
alternative. I don't see why they would object If you can prove the impingement 
at the required density with smaller K Factor nozzles. Especially if none exist 
at 8K.
Ron F

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Hinson, Ryan
Sent: Thursday, July 10, 2014 1:22 PM
To: sprinklerfo...@firesprinkler.org
Cc: Hathaway, Bryan
Subject: FM Approved 8.0 K spray nozzle

A project we are working on appears to require FM approved 8.0K spray nozzles 
in a deluge system for protection of a boiler feed pump per FM Data Sheet 7-101 
Steam Turbines and Electric Generators Section 2.4.2.C.  This was mandated by a 
FM rep.  The only one we can find is the BETE Type N.  Its spray pattern 
diverges too quickly for us to provide the necessary density over the footprint 
of the unit when using the cutsheet info over the area of protection at the 
axial distance required.  The use of standard sprinklers would require location 
over the top of the protected unit.  This is not an option.  Are there any 
other FM approved 8.0K nozzles out there with a narrower spray profile?

Thank you,

Ryan L. Hinson, PE*, SET
Senior Fire Protection Engineer, Fire Protection Engineering Group Burns  
McDonnell
Direct: 952-656-3662
Mobile: 320-250-5404
Fax: 952-229-2923
www.burnsmcd.comBLOCKED::www.burnsmcd.com
*Registered in MN


Proud to be #14 on FORTUNE's 2014 List of 100 Best Companies to Work For

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Re: Cooler Calc

2014-06-28 Thread RFletcher
We did a 45' high 40k sq ft beer cooler with ESFR's. After it was up and 
running we put temp recorders in front of reefer units. 30' up, 15' up and on 
floor. Recorded every 30 minutes for 5 days. Nothing varied more than one 
degree. Some one told me that the reefer units could not produce the BTU's 
needed to lower the temp to 30F. We have done many coolers with wet systems. 
The only incident I remember is a head went off when a unit went into defrost.

Ron fletcher Sent from my iPhone

 On Jun 28, 2014, at 10:14 AM, Scott A Futrell sco...@ffcdi.com wrote:
 
 How cold is the air conditioning the space?  Are pipes and sprinklers in 
 front of, or near colder air used to maintain 38 degrees?
 
 Scott
 
 Office: (763) 425-1001 x 12
 Cell: (612) 759-5556
 
 -Original Message-
 From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] 
 On Behalf Of Brad Casterline
 Sent: Saturday, June 28, 2014 11:06 AM
 To: sprinklerforum@lists.firesprinkler.org
 Subject: Re: Cooler Calc
 
 Maybe that's where John D's AND READILY MAINTAINED thinking comes in-- even 
 after a failure like that you would have several hours before the pipe froze 
 solid.
 
 On Jun 28, 2014, at 10:47 AM, Richard Mote rich...@rowesprinkler.com wrote:
 
 I was told about 20 years ago by someone that installs walk in coolers and 
 freezers, that the only difference between was the setting on the 
 thermostat. If the thermostat malfunctions a 38°F cooler can very quickly 
 become a freezer.   
 
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Re: Cooler Calc

2014-06-28 Thread RFletcher
38F. Yes an ESFR wet with 2 drops through the deck.

Ron fletcher Sent from my iPhone

 On Jun 28, 2014, at 3:21 PM, Bobby Gillett bo...@livingwaterfp.com wrote:
 
 What temp was your beer cooler?
 You put a wet system in with ESFR's?
 
 Thank you,
 
 Bobby Gillett
 Living Water Fire Protection
 Cantonment, FL
 
 Sent from my iPhone
 
 On Jun 28, 2014, at 2:52 PM, rfletc...@aerofire.com wrote:
 
 We did a 45' high 40k sq ft beer cooler with ESFR's. After it was up and 
 running we put temp recorders in front of reefer units. 30' up, 15' up and 
 on floor. Recorded every 30 minutes for 5 days. Nothing varied more than one 
 degree. Some one told me that the reefer units could not produce the BTU's 
 needed to lower the temp to 30F. We have done many coolers with wet systems. 
 The only incident I remember is a head went off when a unit went into 
 defrost.
 
 Ron fletcher Sent from my iPhone
 
 On Jun 28, 2014, at 10:14 AM, Scott A Futrell sco...@ffcdi.com wrote:
 
 How cold is the air conditioning the space?  Are pipes and sprinklers in 
 front of, or near colder air used to maintain 38 degrees?
 
 Scott
 
 Office: (763) 425-1001 x 12
 Cell: (612) 759-5556
 
 -Original Message-
 From: Sprinklerforum 
 [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Brad 
 Casterline
 Sent: Saturday, June 28, 2014 11:06 AM
 To: sprinklerforum@lists.firesprinkler.org
 Subject: Re: Cooler Calc
 
 Maybe that's where John D's AND READILY MAINTAINED thinking comes in-- even 
 after a failure like that you would have several hours before the pipe 
 froze solid.
 
 On Jun 28, 2014, at 10:47 AM, Richard Mote rich...@rowesprinkler.com 
 wrote:
 
 I was told about 20 years ago by someone that installs walk in coolers and 
 freezers, that the only difference between was the setting on the 
 thermostat. If the thermostat malfunctions a 38°F cooler can very quickly 
 become a freezer.   
 
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Cooler Calc

2014-06-27 Thread RFletcher
A couple questions. If it is a cooler why do you need dry pendent heads? And if 
it has to be dry heads and they are on a wet system the RA could still be 
reduced couldn't it?

Ron F

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Bob
Sent: Friday, June 27, 2014 11:29 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Cooler Calc

Ron,
Yes this is a remodel adding only the cooler.  The existing ceiling demand was 
well above the .2 need in the cooler.

Thank You,

Bob Knight, CET III
208-318-3057
www.Firebyknight.com



-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of rongreenman .
Sent: Friday, June 27, 2014 12:11 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Cooler Calc

If the job is just the cooler then I think all the heads is sufficient within 
the perimeter of the cooler. If it's a part of the larger job you need to calc 
all the possible design areas. Not knowing the layout I can't say but maybe the 
ceiling somewhere is a design area, the cooler is potentially a design area, 
etc. But he's nuts if he thinks you need to add other sprinklers not in the 
fire area to make the fire area be 1500 sqft.
Real is real. Math is math. Often the twin don't meet.


On Fri, Jun 27, 2014 at 11:03 AM, Mike Hill mi...@phoenixfp.net wrote:

 I don't suppose that you are lucky enough to have a fire rated cooler.

 Common sense would say that you calculate the cooler.

 Common practice would say calculate the cooler and/or a 1500 sq. ft. 
 area outside of the cooler.

 Mike Hill

 -Original Message-
 From: Sprinklerforum [mailto:
 sprinklerforum-boun...@lists.firesprinkler.org]
 On Behalf Of Bob
 Sent: Friday, June 27, 2014 1:47 PM
 To: sprinklerforum@lists.firesprinkler.org
 Subject: RE: Cooler Calc

 His stand is that I have one of three options that I have not used:
 (1) Density/area curves of Figure 11.2.3.1.1 in accordance with the 
 density/area method of 11.2.3.2
 (2) The room that creates the greatest demand in accordance with the 
 room design method of 11.2.3.3
 (3) Special design areas in accordance with 11.2.3.4

 Keep in mind that this is a jurisdiction that has told me in the past 
 that you can't use the exceptions in 13 (this was before they became 
 part of the body), and that they can't use common sense.



 Thank You,

 Bob Knight, CET III
 208-318-3057
 www.Firebyknight.com



 -Original Message-
 From: Sprinklerforum [mailto:
 sprinklerforum-boun...@lists.firesprinkler.org]
 On Behalf Of Tim Stone
 Sent: Friday, June 27, 2014 11:41 AM
 To: sprinklerforum@lists.firesprinkler.org
 Subject: RE: Cooler Calc

 The Cooler is a closed in room with a space above. You calculate all 
 the heads inside the cooler if less than 1500 SF. If the area outside 
 the cooler is fully sprinklered then you probably have performed calcs 
 already. I'd ask the AHJ to review NFPA 13.

 Regards,
 G. Tim Stone

 G. Tim Stone Consulting, LLC
 NICET Level III Engineering Technician Fire Protection Sprinkler 
 Design and Consulting Services

 117 Old Stage Rd. - Essex Jct., VT. 05452
 CELL: (802) 373-0638   TEL: (802) 434-2968   Fax: (802) 434-4343
tston...@comcast.net

 -Original Message-
 From: Sprinklerforum [mailto:
 sprinklerforum-boun...@lists.firesprinkler.org]
 On Behalf Of Bob
 Sent: Friday, June 27, 2014 1:12 PM
 To: sprinklerforum@lists.firesprinkler.org
 Subject: Cooler Calc

 I have a 1,392 sf cooler.  I calc'ed the entire area of the cooler and 
 submitted.  The AHJ is telling me that I need to calc additional 
 sprinklers at the ceiling to have a 1500 sf design area.  I don't 
 think I need to do this, I was looking at this as a separate fire 
 area, and I don't see it being much different than not adding heads 
 below ducts or other large obstructions.  Do I need to calc additional 
 sprinklers at the ceiling for this application?

 Thank You,

 Bob Knight, CET III
 208-318-3057
 www.Firebyknight.com





 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org

 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
 er.org

 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org

 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
 er.org

 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org

 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
 er.org

 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org

 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
 er.org




--
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College

RE: Cooler Calc

2014-06-27 Thread RFletcher
Exactly, we do 38F coolers with ESFR's. Never had a ..., I better not say that 
might jinx it. 
Ron F

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of John Denhardt
Sent: Friday, June 27, 2014 11:49 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Cooler Calc

If the area is not subject to freezing, no need for dry sprinklers.  NFPA 13 
only requires dry sprinklers or other method when the area is subject to 
freezing AND can not be readily maintained above 40 degrees F.

The above is my personal opinion .


John

Fire sprinklers save lives

Sent from my iPad

On Jun 27, 2014, at 11:42 AM, Bob b...@firebyknight.com wrote:

 Ron,
 The temperature is maintained at 38F.  The sprinklers used were EC OH 
 SR dry sprinklers.
 
 Thank You,
 
 Bob Knight, CET III
 208-318-3057
 www.Firebyknight.com
 
 
 
 -Original Message-
 From: Sprinklerforum 
 [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
 On Behalf Of rfletc...@aerofire.com
 Sent: Friday, June 27, 2014 12:37 PM
 To: sprinklerforum@lists.firesprinkler.org
 Subject: RE: Cooler Calc
 
 A couple questions. If it is a cooler why do you need dry pendent 
 heads? And if it has to be dry heads and they are on a wet system the 
 RA could still be reduced couldn't it?
 
 Ron F
 
 -Original Message-
 From: Sprinklerforum 
 [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
 On Behalf Of Bob
 Sent: Friday, June 27, 2014 11:29 AM
 To: sprinklerforum@lists.firesprinkler.org
 Subject: RE: Cooler Calc
 
 Ron,
 Yes this is a remodel adding only the cooler.  The existing ceiling 
 demand was well above the .2 need in the cooler.
 
 Thank You,
 
 Bob Knight, CET III
 208-318-3057
 www.Firebyknight.com
 
 
 
 -Original Message-
 From: Sprinklerforum 
 [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
 On Behalf Of rongreenman .
 Sent: Friday, June 27, 2014 12:11 PM
 To: sprinklerforum@lists.firesprinkler.org
 Subject: Re: Cooler Calc
 
 If the job is just the cooler then I think all the heads is sufficient 
 within the perimeter of the cooler. If it's a part of the larger job 
 you need to calc all the possible design areas. Not knowing the layout 
 I can't say but maybe the ceiling somewhere is a design area, the 
 cooler is potentially a design area, etc. But he's nuts if he thinks 
 you need to add other sprinklers not in the fire area to make the fire area 
 be 1500 sqft.
 Real is real. Math is math. Often the twin don't meet.
 
 
 On Fri, Jun 27, 2014 at 11:03 AM, Mike Hill mi...@phoenixfp.net wrote:
 
 I don't suppose that you are lucky enough to have a fire rated cooler.
 
 Common sense would say that you calculate the cooler.
 
 Common practice would say calculate the cooler and/or a 1500 sq. ft.
 area outside of the cooler.
 
 Mike Hill
 
 -Original Message-
 From: Sprinklerforum [mailto:
 sprinklerforum-boun...@lists.firesprinkler.org]
 On Behalf Of Bob
 Sent: Friday, June 27, 2014 1:47 PM
 To: sprinklerforum@lists.firesprinkler.org
 Subject: RE: Cooler Calc
 
 His stand is that I have one of three options that I have not used:
 (1) Density/area curves of Figure 11.2.3.1.1 in accordance with the 
 density/area method of 11.2.3.2
 (2) The room that creates the greatest demand in accordance with the 
 room design method of 11.2.3.3
 (3) Special design areas in accordance with 11.2.3.4
 
 Keep in mind that this is a jurisdiction that has told me in the past 
 that you can't use the exceptions in 13 (this was before they became 
 part of the body), and that they can't use common sense.
 
 
 
 Thank You,
 
 Bob Knight, CET III
 208-318-3057
 www.Firebyknight.com
 
 
 
 -Original Message-
 From: Sprinklerforum [mailto:
 sprinklerforum-boun...@lists.firesprinkler.org]
 On Behalf Of Tim Stone
 Sent: Friday, June 27, 2014 11:41 AM
 To: sprinklerforum@lists.firesprinkler.org
 Subject: RE: Cooler Calc
 
 The Cooler is a closed in room with a space above. You calculate all 
 the heads inside the cooler if less than 1500 SF. If the area outside 
 the cooler is fully sprinklered then you probably have performed 
 calcs already. I'd ask the AHJ to review NFPA 13.
 
 Regards,
 G. Tim Stone
 
 G. Tim Stone Consulting, LLC
 NICET Level III Engineering Technician Fire Protection Sprinkler 
 Design and Consulting Services
 
117 Old Stage Rd. - Essex Jct., VT. 05452
 CELL: (802) 373-0638   TEL: (802) 434-2968   Fax: (802) 434-4343
   tston...@comcast.net
 
 -Original Message-
 From: Sprinklerforum [mailto:
 sprinklerforum-boun...@lists.firesprinkler.org]
 On Behalf Of Bob
 Sent: Friday, June 27, 2014 1:12 PM
 To: sprinklerforum@lists.firesprinkler.org
 Subject: Cooler Calc
 
 I have a 1,392 sf cooler.  I calc'ed the entire area of the cooler 
 and submitted.  The AHJ is telling me that I need to calc additional 
 sprinklers at the ceiling to have a 1500 sf design area.  I don't 
 think I need to do 

RE: Underground Piping

2014-06-25 Thread RFletcher
In the friction loss formula found in 13-23.4.2.1.1 (13 Ed) I would use Q 
squared rather than Q to 1.85.
Ron F

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Rahe Loftin - 7PMC
Sent: Wednesday, June 25, 2014 3:50 PM
To: SprinklerFORUM
Subject: Underground Piping

In the Hydraulics chapter of the 3rd edition of the SFPE Handbook, the 
following verbiage occurs “It has been noted, however, that in rough pipes head 
loss varies with flow (and velocity) to the power of 2 rather than the power of 
1.85 characteristic of smooth pipes.”


The question is, shouldn't we use a water supply testing graph based on an 
exponent of 2 instead of 1.85 since we do not know the condition of the 
underground pipe?

Rahe Loftin
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Re: Location of Flow Test in Calc's

2014-06-19 Thread RFletcher
We do completely different drawings for the install crews. They don't need the 
hyd nodes or remote areas. Submittal plans have lots of info that isn't needed 
for installation.

Ron fletcher Sent from my iPhone

 On Jun 19, 2014, at 6:38 AM, craig.pr...@ch2m.com craig.pr...@ch2m.com 
 wrote:
 
 It would really depend on how close the test point was to the point of 
 connection of the run-in to the main.  If the test point is 100 feet away and 
 there's nothing between, then no biggie.
 
 I take my calcs back through the UG main to the test point.  What does it 
 hurt, be sure of your calcs and there's no question on accuracy. 
 
 If the test point was back at a pump across the campus, his theory is blown.
 
 I'm constantly amazed at the quality of shop drawings lately.  The field 
 crews must do a lot of cussing at the designers based on some of the junk 
 that's produced.
 
 Craig L. Prahl 
 Fire Protection Group Lead
 CH2MHILL
 Lockwood Greene
 1500 International Drive
 Spartanburg, SC  29303
 Direct - 864.599.4102
 Fax - 864.599.8439
 CH2MHILL Extension  74102
 craig.pr...@ch2m.com
 
 
 
 -Original Message-
 From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] 
 On Behalf Of Brian Harris
 Sent: Thursday, June 19, 2014 9:19 AM
 To: sprinklerforum@lists.firesprinkler.org
 Subject: Location of Flow Test in Calc's
 
 Was just told by one of our new designers that he was taught that it didn't 
 matter where the flow test was taken on the underground that you just need to 
 take it back to the tie in point at the main  that everywhere he's worked 
 does it that way. News to me, any of you guys do it that way? If so how do 
 you account for the loss in the underground to the test hydrant, elevation, 
 etc ?
 
 Brian Harris, CET
 BVS Systems Inc.
 Sprinkler Division
 bvssystemsinc.comhttp://bvssystemsinc.com/
 Phone: 704.896.9989
 Fax: 704.896.1935
 
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: High Pressure ESFR

2014-06-16 Thread RFletcher
I have not heard one. Be great if there was though.
Ron F

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Richard Mote
Sent: Monday, June 16, 2014 6:23 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: High Pressure ESFR

I am in need of some ESFR K=16.8's with a high pressure rating.
Headed out the door to look at a job so I haven't got time to search, I am 
hoping someone will know off the top of their head. Please don't anyone take 
the time to research, if I don't get an answer I'll look it up tonight when I 
get back.

Richard Mote ET
Design Manager
Rowe Sprinkler Systems, Inc.
PO Box 407
Middleburg, PA 17842
P- 877-324-ROWE
F- 570-937-6335
rich...@rowesprinkler.commailto:rich...@rowesprinkler.com
www.rowesprinkler.comhttp://www.rowesprinkler.com/

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: DRY HUMOR from NFPA

2014-05-30 Thread RFletcher
I can hear it now, the book says, shall be internally galvanized so there 
can't be any galvanizing on the outside of the pipe. The stuff we get is coated 
on the outside as well. How would an inspector tell if it was only galvanized 
on the inside? Maybe the next edition of 13 they can add a requirement for a 
sight glass every some many feet so an inspector could verify the pipe is 
internally galvanized. Happy Friday.
Ron F   

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of rongreenman .
Sent: Friday, May 30, 2014 9:23 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: DRY HUMOR from NFPA

Richard is correct. This numbering system is known as a decimal outline (as 
opposed to the more common alphanumeric style) and follows Topic, Subtopic, 
Sub-subtopic, etc. Each lower entry refers to the next higher entry, etc.
If a specific topic type falls under two different higher topics or subtopics 
then it must be noted in both places, and with a see also
reference.


On Fri, May 30, 2014 at 9:08 AM, Richard Mote rich...@rowesprinkler.com
wrote:

 It has always been my understanding that any specific requirements in 
 a sub section refer the that section only IE: 8.4.7.2.1 only applies 
 to section 8.4.7  Large Drop Sprinklers. I have had some AHJ's try to 
 apply things like this across the board, but I can usually get a 
 clarification from NFAP to settle the matter.

 Richard Mote ET
 Designer
 Rowe Sprinkler Systems, Inc.
 PO Box 407
 Middleburg, PA 17842
 P- 877-324-ROWE
 F- 570-937-6335
 rich...@rowesprinkler.com
 www.rowesprinkler.com



 -Original Message-
 From: Sprinklerforum [mailto:
 sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Vince 
 Sabolik
 Sent: Friday, May 30, 2014 11:51 AM
 To: sprinklerforum@lists.firesprinkler.org
 Subject: DRY HUMOR from NFPA


 8.4.7.2* Galvanized Pipe.
 8.4.7.2.1 Where steel pipe is used in preaction and dry pipe systems, 
 piping materials shall be limited to internally galvanized steel.

 Please straighten me out! This applies to CMSA heads only?

 Galvanized pipe, where used in a normal dry system must be figured at 
 a C=100??

 Thanks!

 West Tech Fire Protection, Inc.
 11351 Pearl Road   / Strongsville, Ohio   44136
 Phone 440 238-4800Fax 440 238-4876
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org

 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
 er.org ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org

 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
 er.org




--
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

rgreen...@bates.ctc.edu

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC

They are happy men whose natures sort with their vocations. -Francis Bacon, 
essayist, philosopher, and statesman (1561-1626)

A problem well stated is a problem half solved. -Charles F. Kettering, inventor 
and engineer (1876-1958) ___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: telecom rooms

2014-05-29 Thread RFletcher
I'd tell the engineer to site the code section that prohibits the pipe passing 
through. It's ridiculous but I have seen AHJ's interpret the thing about no 
unnecessary equipment to mean the pipe can enter but not leave an electrical 
equipment room. I don't think there is any code at all about pipe in a telecom 
room.
Ron F

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Jerry Van Kolken
Sent: Thursday, May 29, 2014 8:29 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: telecom rooms

I only have a copy of 08' NEC 110.26, but according to that any elec. Panels 
you need to be 6'-0 above, or clear the equipment, unless there is a ceiling 
in the room. I don't know if that applies to telecom panels. The only time I've 
been told I can't run through a telecom room is military projects so it might 
be a UFC requirement.

Jerry Van Kolken
Millennium Fire Protection
(760) 722-2722

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Travis Mack
Sent: Thursday, May 29, 2014 8:18 AM
To: sprinklerfo...@firesprinkler.org
Subject: telecom rooms

Is there anything in any code/standard that prohibits sprinkler piping from 
passing through telecom rooms?  I don't have access to the NEC right now.  I 
can't locate anything in NFPA 13 that would prohibit it.

I am on a project where due to phasing, I have to run a branch line through the 
telecom room to supply 2 sprinklers on the other side of it for this phase.  
The engineer says you can't do it. I thought I remember something in the NEC 
saying that sprinkler piping was acceptable to pass through these electric and 
telecom rooms.  I just can't run over panels.

--
Travis Mack, SET
MFP Design, LLC
2508 E Lodgepole Drive
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
email:tm...@mfpdesign.com

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Mixing EC-QR and SC-QR sprinklers in the same area

2014-05-28 Thread RFletcher
Yes, they can be mixed. We do it all the time. SC in entry and EC in sleeping 
room.
Ron F

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Pete Schwab
Sent: Wednesday, May 28, 2014 8:49 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Mixing EC-QR and SC-QR sprinklers in the same area

Did you mean to say EC Standard response with QR elements mixed with standard 
coverage QR?


Peter Schwab
VP of Purchasing  Engineering Technologies

Wayne Automatic Fire Sprinklers Inc.
222 Capitol Court
Ocoee, Fl 34761

Mobile: (407) 468-8248
Direct: (407) 877-5570
Fax: (407) 656-8026

www.waynefire.com



We're hiring great people at all of our locations!  Please check out our 
website for the details! 

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Sean Lockyer
Sent: Wednesday, May 28, 2014 11:19 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Mixing EC-QR and SC-QR sprinklers in the same area

Can Extended Coverage Quick Response Sprinklers and Standard Coverage Quick 
Response Sprinklers be mixed in the same compartment ? Even though QR and SR 
cannot be mixed within the same compartment (I.E.-Room) there is no rule 
precluding the mixing of EC-QR and SC-QR heads as far as I know.

Does anyone here have any experience in this area ?

  Sean Lockyer
      Project Designer   4617 Parkbreeze 
Court
  Cell    386-279-1197  Orlando, 
Florida 32808
  slock...@aitlifesafety.com      Phone:  407-816-9101
  www.AITLifeSafety.com   Fax:     
407-816-9104


___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Sheet Metal Pipe Sleeves

2014-05-19 Thread RFletcher
Have you tried Grainger?
Ron F

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Richard Mote
Sent: Monday, May 19, 2014 11:14 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Sheet Metal Pipe Sleeves

Someone missed the spec that called for sleeves when passing through gyp board 
walls, pipe is installed. In the past I have gotten sheet metal wraparound 
sleeves that can be install after the fact. GC says they will except those now 
I can't find anyone that carry's them. The last job I used them on was in 
Memphis about 15 years ago.

Richard Mote ET
Designer
Rowe Sprinkler Systems, Inc.
PO Box 407
Middleburg, PA 17842
P- 877-324-ROWE
F- 570-937-6335
rich...@rowesprinkler.commailto:rich...@rowesprinkler.com
www.rowesprinkler.comhttp://www.rowesprinkler.com/

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Thermal Barrier for Bathrooms

2014-05-16 Thread RFletcher
Seems like something that makes sense for wood frame buildings but not so much 
for noncombustible construction. The runaway shower enclosure fire had never 
occurred to me, guess I lack the imagination. 
Ron F

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Mark A. Sornsin, P.E.
Sent: Friday, May 16, 2014 8:49 AM
To: sprinklerfo...@firesprinkler.org
Subject: RE: Thermal Barrier for Bathrooms

Roland,

Isn't the concern that fire will spread to the unprotected concealed space, 
spreading heat and smoke to other parts of the building - potentially igniting 
other shower enclosures leading to mass hysteria and dogs and cats living 
together?  Whereas, the open door adjacent to the unprotected bathroom leads to 
a sprinkler-protected space.

Mark A. Sornsin, P.E. | Karges-Faulconbridge, Inc. | Fire Protection Engineer | 
Fargo, ND | direct: 701.552.9905 | mobile: 701.371.5759 | 
http://www.kfiengineers.com

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Roland Huggins
Sent: Thursday, May 15, 2014 5:48 PM
To: SprinklerFORUM
Subject: Re: Thermal Barrier for Bathrooms

That is my understanding (despite the fact that a door is not required to the 
adjacent room).  Never said it ad to be logical.

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Test Header Calc

2014-05-15 Thread RFletcher
Why not just read the gauges on the pump?
Ron F

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Brian Harris
Sent: Thursday, May 15, 2014 8:22 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Test Header Calc

I'm running a theoretical calc on a pump test header to try and determine if 
the existing pump is running at or near its rating, there are (4) 2-1/2 hose 
valves flowing 375 gallons each. The question I have is what pressure would be 
plugged into the calc's for each valve? I have a test chart that shows me a 
2-1/2 orifice flowing roughly 400 gpm will have a 5 pitot reading. I've 
searched for threads on converting pitot to a residual pressure and it doesn't 
seem there is any direct correlation. I've also seen post that say a pitot 
reading and the residual are pretty close at pressure under 40 psi. Any help 
would be greatly appreciated.

Brian Harris, CET
BVS Systems Inc.
Sprinkler Division
bvssystemsinc.comhttp://bvssystemsinc.com/
Phone: 704.896.9989
Fax: 704.896.1935

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Test Header Calc

2014-05-15 Thread RFletcher
Okay, what am I missing? There are gauges on the suction and discharge sides of 
the pump, right?
Ron F

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Tim Stone
Sent: Thursday, May 15, 2014 8:36 AM
To: Sprinklerforum@lists.firesprinkler.org
Subject: RE: Test Header Calc

Brian,

I just performed this on a warehouse project with a diesel fire pump taking 
suction from a municipal water supply. The EOR wanted to know the pressures on 
the Suction Flange of the pump.
I started off with 375 GPM on each test header valve and assigned a pressure of 
47 PSI to one of the valves with just a flow on the rest. 
Adjust the starting pressure for your needs. 

Regards,
G. Tim Stone

G. Tim Stone Consulting, LLC
NICET Level III Engineering Technician
Fire Protection Sprinkler Design
and Consulting Services

    117 Old Stage Rd. - Essex Jct., VT. 05452
CELL: (802) 373-0638   TEL: (802) 434-2968   Fax: (802) 434-4343
   tston...@comcast.net

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Brian Harris
Sent: Thursday, May 15, 2014 11:22 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Test Header Calc

I'm running a theoretical calc on a pump test header to try and determine if 
the existing pump is running at or near its rating, there are (4) 2-1/2
hose valves flowing 375 gallons each. The question I have is what pressure 
would be plugged into the calc's for each valve? I have a test chart that shows 
me a 2-1/2 orifice flowing roughly 400 gpm will have a 5 pitot reading. I've 
searched for threads on converting pitot to a residual pressure and it doesn't 
seem there is any direct correlation. I've also seen post that say a pitot 
reading and the residual are pretty close at pressure under 40 psi. Any help 
would be greatly appreciated.

Brian Harris, CET
BVS Systems Inc.
Sprinkler Division
bvssystemsinc.comhttp://bvssystemsinc.com/
Phone: 704.896.9989
Fax: 704.896.1935

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Test Header Calc

2014-05-15 Thread RFletcher
Tim, So based on 47 psi at one test valve and just a flow on the rest, what was 
the pressure on the suction flange of the pump? Can't you just plot 1500 gpm on 
flow test curve and subtract the friction and elevation losses between the 
supply and pump? 

Brian, Pitot the discharge for each outlet, adjust the valves to control the 
required gpm, record the total gpm, read the discharge gauge on the pump and 
subtract the pressure on the suction gauge from the pressure on the discharge 
gauge?
I'm glad tomorrow is Friday. Ron F

-Original Message-
From: Tim Stone [mailto:tston...@comcast.net] 
Sent: Thursday, May 15, 2014 8:51 AM
To: Ronl.Fletcher; Sprinklerforum@lists.firesprinkler.org
Subject: RE: Test Header Calc

Ron,
In my case the EOR was worried about negative pressures on the suction flange 
before the sprinkler contractor ordered the pump.

Regards,
G. Tim Stone

G. Tim Stone Consulting, LLC
NICET Level III Engineering Technician
Fire Protection Sprinkler Design
and Consulting Services

    117 Old Stage Rd. - Essex Jct., VT. 05452
CELL: (802) 373-0638   TEL: (802) 434-2968   Fax: (802) 434-4343
   tston...@comcast.net

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of rfletc...@aerofire.com
Sent: Thursday, May 15, 2014 11:43 AM
To: Sprinklerforum@lists.firesprinkler.org
Subject: RE: Test Header Calc

Okay, what am I missing? There are gauges on the suction and discharge sides of 
the pump, right?
Ron F

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Tim Stone
Sent: Thursday, May 15, 2014 8:36 AM
To: Sprinklerforum@lists.firesprinkler.org
Subject: RE: Test Header Calc

Brian,

I just performed this on a warehouse project with a diesel fire pump taking 
suction from a municipal water supply. The EOR wanted to know the pressures on 
the Suction Flange of the pump.
I started off with 375 GPM on each test header valve and assigned a pressure of 
47 PSI to one of the valves with just a flow on the rest. 
Adjust the starting pressure for your needs. 

Regards,
G. Tim Stone

G. Tim Stone Consulting, LLC
NICET Level III Engineering Technician
Fire Protection Sprinkler Design
and Consulting Services

    117 Old Stage Rd. - Essex Jct., VT. 05452
CELL: (802) 373-0638   TEL: (802) 434-2968   Fax: (802) 434-4343
   tston...@comcast.net

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Brian Harris
Sent: Thursday, May 15, 2014 11:22 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Test Header Calc

I'm running a theoretical calc on a pump test header to try and determine if 
the existing pump is running at or near its rating, there are (4) 2-1/2
hose valves flowing 375 gallons each. The question I have is what pressure 
would be plugged into the calc's for each valve? I have a test chart that shows 
me a 2-1/2 orifice flowing roughly 400 gpm will have a 5 pitot reading. I've 
searched for threads on converting pitot to a residual pressure and it doesn't 
seem there is any direct correlation. I've also seen post that say a pitot 
reading and the residual are pretty close at pressure under 40 psi. Any help 
would be greatly appreciated.

Brian Harris, CET
BVS Systems Inc.
Sprinkler Division
bvssystemsinc.comhttp://bvssystemsinc.com/
Phone: 704.896.9989
Fax: 704.896.1935

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org



___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Thermal Barrier for Bathrooms

2014-05-15 Thread RFletcher
I just ran this very thing by the forum. The consensus was the barrier has to 
isolate the shower enclosure from the wall cavity so the sheet rock would have 
to be on both sides of the stud.
Ron F 

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Chris Born
Sent: Thursday, May 15, 2014 2:18 PM
To: sprinklerfo...@firesprinkler.org
Subject: Thermal Barrier for Bathrooms

I'm looking for a quick sanity check.  We are an A/E firm designing new college 
dormitories.  These dorms typically contain four bedroom suites with two 
bathrooms in each suite.  The 1987 edition of 2013 is applicable, and the 
bathrooms are less than 55 square feet.  In order to omit sprinklers from the 
bathrooms, 13:8.25.8.1.1 requires walls and ceilings to be noncombustible or 
limited combustible materials with a 15 minute thermal barrier, including walls 
and ceilings behind shower enclosures and tubs.  

The buildings are noncombustible construction, with concrete floors, metal 
studs and drywall, etc.  If the shower enclosure abuts metal studs and there is 
drywall on the other side of the studs, does that satisfy the requirement or 
does the drywall have to separate the shower enclosure from the studs?

I think I know the answer/intent, but I'm interested in opinions or specific 
references because I either have to convince the AHJ or the general contractor 
(design-build project).

Christopher Born, P.E.
Director, Fire Protection Engineering
Clark Nexsen
Norfolk, VA

Sent from my iPad
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Can a hydrant flow from the pumper connection be used for the hydraulic calculations ?

2014-05-14 Thread RFletcher
2012 IFC - APPENDIX B: B201.1 Definitions
FIRE-FLOW.  The flow rate of a water supply, measured at 20 PSI residual 
pressure that is available for fire-fighting.
Ron F

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of John Drucker - Home
Sent: Wednesday, May 14, 2014 2:09 PM
To: 'Fyremarshal34'; 'Mark A. Sornsin, P.E.'
Cc: sprinklerforum@lists.firesprinkler.org
Subject: RE: Can a hydrant flow from the pumper connection be used for the 
hydraulic calculations ?

American Water Works Association (AWWA) Manual M31 provides the 20 psi residual 
reference. 

John

John Drucker, CET
Assistant Construction Official
Fire Protection Subcode Official
Building/Fire/Electrical Inspector
Borough of Red Bank
Red Bank, New Jersey
Email: jdruc...@redbanknj.org
Cell/Text: 732-904-6823



-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Fyremarshal34
Sent: Wednesday, May 14, 2014 11:41 AM
To: Mark A. Sornsin, P.E.
Cc: sprinklerforum@lists.firesprinkler.org
Subject: Re: Can a hydrant flow from the pumper connection be used for the 
hydraulic calculations ?

The 20 PSI limit is actually based on the federal Clean Water Act and some 
states have also adopted as law or regulation. I know NJ has it as regulation. 

Dave Herbert
Retired from NJ
Fire guy in the Sunshine State
Guest

Sent from my iPhone

 On May 14, 2014, at 9:53, Mark A. Sornsin, P.E. masorn...@kfi-eng.com 
 wrote:
 
 Craig, it has been my understanding that the 20psi number represents the 
 lowest residual pressure fire departments 'generally' want to see when 
 drawing from a municipal supply - to avoid the potential for collapsing mains 
 at some higher elevation than where the water is being drawn. There are 
 exceptions such as in flat areas like Fargo where they can safely drop below 
 20 psi in most circumstances. So the flow at 20psi generally represents the 
 maximum flow rate they can safely achieve at that point on the system.
 
 It is a 'fictional' number since in most cases they are using extrapolation 
 to get to it.  On the other hand, it's not all that fictional if your test 
 from which the extrapolation is run produced a 25% pressure drop from the 
 static.  That drop helps define an accurate 'slope' on the N^1.85 graph. 
 Determining the flow at 20 psi does not warrant multiple significant digits - 
 certainly fewer than in sprinkler design (which should use a couple at most). 
 The extrapolation won't be that far off from reality.
 
 Mark A. Sornsin, P.E. | Karges-Faulconbridge, Inc. | Fire Protection Engineer 
 | Fargo, ND | direct: 701.552.9905 | mobile: 701.371.5759 | 
 http://www.kfiengineers.com
 
 -Original Message-
 From: craig.pr...@ch2m.com [mailto:craig.pr...@ch2m.com]
 Sent: Wednesday, May 14, 2014 8:42 AM
 To: Mark A. Sornsin, P.E.; sprinklerforum@lists.firesprinkler.org
 Subject: RE: Can a hydrant flow from the pumper connection be used for the 
 hydraulic calculations ?
 
 And there's another point of discussion, how about that extrapolation at 20 
 psi.
 
 What is the value of that number in reality?
 
 I've seen 20 psi flow rates that we knew without any doubt were unachievable 
 by the municipal water supply yet when trying to convince an owner that the 
 water supply would not meet his system demand and the site would require a 
 pump and tank, they would quickly point to the 20 psi flow rate and say 
 there, see we've got lots of water!   It just confuses the uninformed.
 
 I've also seen the additional data point of how much flow you get when at 0 
 psi.  I'm still trying to get my head around that one.  Maybe someone can 
 explain it.
 
 So why put these fictional numbers on a test report?
 
 
 
 Craig L. Prahl, CET
 Fire Protection Group Lead
 CH2MHILL
 Lockwood Greene
 1500 International Drive
 Spartanburg, SC  29303
 Direct - 864.599.4102
 Fax - 864.599.8439
 CH2MHILL Extension  74102
 craig.pr...@ch2m.com
 
 
 
 -Original Message-
 From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] 
 On Behalf Of Mark A. Sornsin, P.E.
 Sent: Wednesday, May 14, 2014 9:34 AM
 To: sprinklerforum@lists.firesprinkler.org
 Subject: RE: Can a hydrant flow from the pumper connection be used for the 
 hydraulic calculations ?
 
 Steve - you seem to be off on a tangent and did not understand the question. 
 Its o.k. - that happens at your age.
 
 I agree with Travis. I have done several water flow tests using the 4-1/2 
 port.  Apply the proper coefficients and life is good. Of course, flowing 
 that port can have logistical problems due to the large amount of water 
 and/or damage cause by the discharge - so be careful, plan accordingly, or 
 find an alternative approach if necessary.
 
 But he raises another peeve of mine. Further to Ron's comments, why do we 
 have to reduce residual pressure to the point of being at least 25% lower 
 than the static? If my 

RE: Can a hydrant flow from the pumper connection be used for the hydraulic calculations ?

2014-05-13 Thread RFletcher
We use the 4 pumper connections for flow tests all the time. In Phoenix we 
have to calculate the 4,000 gpm fire flow onto the site and out of the private 
hydrants and I don't like doing hydraulic calc's out to 4,000 gpm using a graph 
from a 1,300 gpm flow test. The city water supply tends to compensate for 
greater demands by opening PRV's. The standard 1.85 curve we use is not 
accurate beyond the actual flow point (my opinion) from the test so we request 
flow tests with two or three 4 pumpers running. It's the desert so we have 
lots of free water?

Had an interesting comment from an FPE with Phoenix the other day about the 25% 
minimum between the static and residual. The Fire Dept. wasn't going to accept 
a flow test taken by the city water dept. because it didn't comply with the 25% 
pressure drop. The gpm from flow test was greater than our system demand. The 
problem seems to have gone away. Maybe the FPE hit his forehead with the palm 
of his hand and the light came on.

I have never paid any attention to the 25% requirement. When calculating system 
demand only I always try to get a flow test with a flow that is above the 
system + hose demand. No surprises then.
Ron F

-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Travis Mack
Sent: Tuesday, May 13, 2014 2:12 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Can a hydrant flow from the pumper connection be used for the 
hydraulic calculations ?

Are you asking if you can do a flow test from the pumper connection?  If so, 
then sure you can.  You just need to modify the coefficient based on your pitot.

How are you inflating the gpm?  If you measure 1200 gpm from the 2½ and you 
measure 2000 gpm from the 4.5, how is that inflating flow?  You should 
typically have a lower residual pressure when flowing the pumper connection 
than the 2½ connection.

If you are looking to 291 for direction, are you getting the required 25% drop 
in static and residual from your 2½ flow?  If not, what do you do?  You are 
required to open up additional hydrants to get the flow.  
So, to get additional flow, you can also flow from the pumper connection.

Maybe I am misunderstanding your question.

Travis Mack, SET
MFP Design, LLC
2508 E Lodgepole Drive
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
email:tm...@mfpdesign.com

On 5/13/2014 1:47 PM, Sean Lockyer wrote:
 Here is an interesting question: In the event that you do not have an 
 adequate amount of water flow (in terms of GPM) is it acceptable to flow the 
 4-1/2 pumper connection in lieu of the standard 2-1/2 connection on the 
 side ? I know that in NFPA 291 it is recommended to only blow off the 2-1/2 
 outlet but when you blow off the pumper connection there is a formula used to 
 reduce it. However, even after the formula reduction you still have a far 
 higher amount of water (once again, in terms of GPM). My question is this, 
 can you use that GPM in your hydraulic calculations ? I would have to think 
 that most AHJ's would be hesitant to allow this to be used since you are 
 artificially inflating the water supply.

 What does everyone else think ?

Sean Lockyer
Project Designer   4617 Parkbreeze 
 Court
Cell386-279-1197  Orlando, 
 Florida 32808
slock...@aitlifesafety.com  Phone:  
 407-816-9101
www.AITLifeSafety.com   Fax: 
 407-816-9104



 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
 er.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


8.15.8.1.1 Bathrooms (2013)

2014-04-30 Thread RFletcher
States in part a 15 minute thermal barrier rating, including the walls and 
ceilings behind any shower enclosure or tub.  Questions is, can there be a 
steel stud between the shower enclosure and the 15 minute barrier?
Ron F

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


CA Title 19 Chapter 5

2014-04-18 Thread RFletcher
Anyone know if California Title 19 requires an inspector to write up spacing 
and placement issues or is it just for operation of the system per NFPA 25?
Ron F 

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Re: CA Title 19 Chapter 5

2014-04-18 Thread RFletcher
Thanks Steve. Thought you would know.
Ron f

Sent from my iPhone

 On Apr 18, 2014, at 4:43 PM, Steve Leyton st...@protectiondesign.com 
 wrote:
 
 Many local AHJs want you to inform, but the state did not amend the NFPA 25 
 separation of design deficiencies from the ITM tasks.
 
 
 Steve 
 
  Original message 
 From: rfletc...@aerofire.com 
 Date:04/18/2014  3:19 PM  (GMT-08:00) 
 To: sprinklerforum@lists.firesprinkler.org
 Subject: CA Title 19 Chapter 5 
 
 Anyone know if California Title 19 requires an inspector to write up spacing 
 and placement issues or is it just for operation of the system per NFPA 25?
 Ron F 
 
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Obstructions against wall EC's

2014-04-11 Thread RFletcher
Just noticed Figure 8.8..1.2(c), 2013, it's new. It is also added for standard 
and residential heads. I tried to look up the ROP/ROC's but I lost my link and 
I can never find them through the menu system.

The figure indicates a minimum depth of 18 for an obstruction (soffit) against 
a wall. I'm curious because there is no minimum distance listed for the 
sprinkler away from the side of the obstruction. Doing the math in Figure 
8.8.5.1.2)(b) a 17 deep by 24 wide obstruction would require an A dimension 
of 33. The counterintuitive part for me is that some  obstructions 18 deep 
and 24 wide could require a sprinkler beneath if with the minimum A dimension 
in Figure (b) isn't met but if the obstruction were 1 deeper it wouldn't 
require a sprinkler. Maybe I'm over analyzing or am I missing something.

Ron F  

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Obstructions against wall EC's Fig. 8.8.5.2.2(c)

2014-04-11 Thread RFletcher
Glad you have submitted the comment. It will make more sense with those changes.
Ron F 

-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org 
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Larry 
Keeping
Sent: Friday, April 11, 2014 9:26 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Obstructions against wall EC's Fig. 8.8.5.2.2(c)

For the next (2016) edition I filed a Public Input asking for the 18 minimum 
be dropped and for the S dimension to be changed to 1/2 S.
As per the First Draft Report, that was accepted, but of course it is 
susceptible to change during the Second round of deliberations.

Larry Keeping, P.Eng.

Professional Loss Control
3413 Wolfedale Road, Suite 6
Mississauga, Ontario
L5C 1V8

Phone:   905-949-2755, ext. 204
Fax:905-949-1752

E-mail:lkeep...@plcfire.com


-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org 
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of 
rfletc...@aerofire.com
Sent: April-11-14 10:34 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Obstructions against wall EC's

Just noticed Figure 8.8..1.2(c), 2013, it's new. It is also added for standard 
and residential heads. I tried to look up the ROP/ROC's but I lost my link and 
I can never find them through the menu system.

The figure indicates a minimum depth of 18 for an obstruction (soffit) against 
a wall. I'm curious because there is no minimum distance listed for the 
sprinkler away from the side of the obstruction. Doing the math in Figure 
8.8.5.1.2)(b) a 17 deep by 24 wide obstruction would require an A dimension 
of 33. The counterintuitive part for me is that some  obstructions 18 deep 
and 24 wide could require a sprinkler beneath if with the minimum A dimension 
in Figure (b) isn't met but if the obstruction were 1 deeper it wouldn't 
require a sprinkler. Maybe I'm over analyzing or am I missing something.

Ron F  

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Re: Diesel fuel tank

2014-04-09 Thread RFletcher
Is there.no exception in 20 if A double wall uL 142 tank.
Ron f

Sent from my iPhone

 On Apr 9, 2014, at 7:27 AM, Richard Mote rich...@rowesprinkler.com wrote:
 
 We had the builder layup 3 or 4 courses of 8 CMU block and had them coat the 
 inside with a fuel proof coating. On one job they basically had the inside 
 fiber glassed.
 We just told the GC what was required in terms of cubic feet of containment, 
 and put back on them to build it.
 
 
 Richard Mote ET
 Design Manager
 Rowe Sprinkler Systems, Inc.
 
 
 
 -Original Message-
 From: sprinklerforum-boun...@lists.firesprinkler.org 
 [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of 
 Martinez, Dewayne
 Sent: Wednesday, April 09, 2014 8:33 AM
 To: sprinklerforum@lists.firesprinkler.org
 Subject: RE: Diesel fuel tank
 
 Was the containment nothing more than concrete curbs around the tank?
 
 -Original Message-
 From: sprinklerforum-boun...@lists.firesprinkler.org
 [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Bobby 
 Gillett
 Sent: Wednesday, April 09, 2014 7:30 AM
 To: sprinklerforum@lists.firesprinkler.org
 Subject: Re: Diesel fuel tank
 
 The last couple FM projects I did also required both, and the containment 
 dike had to contain 130% of the capacity of the tank.
 
 Bobby Gillett
 *Living Water Fire Protection, LLC*
 1160 McKenzie Rd.
 Cantonment, FL 32533
 (850) 937-1850
 livingwaterfp.com  http://livingwaterfp.com/
 
 
 On Wed, Apr 9, 2014 at 7:07 AM, Richard Mote
 rich...@rowesprinkler.comwrote:
 
 The last couple of FM jobs I've done required both a double wall tank 
 and a containment dike.
 
 NFPA 20, 2010 11.4.1.2.4 Fuel tansk shall be enclosed with a wall, 
 curb or dike sufficient to hold the entire capacity of the tank.
 
 This isn't in the 2007 edition at least not in the fuel tank section, 
 so it must be new.
 
 Richard Mote ET
 Design Manager
 Rowe Sprinkler Systems, Inc.
 
 
 
 
 -Original Message-
 From: sprinklerforum-boun...@lists.firesprinkler.org [mailto:
 sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Martinez,
 
 Dewayne
 Sent: Wednesday, April 09, 2014 7:45 AM
 To: SprinklerFORUM
 Subject: Diesel fuel tank
 
 We have an existing system with a diesel fuel pump and tank(280gpm) 
 that was installed back in 1991.  The insurance carrier is requesting 
 that either a new duel wall tank or a dike containment system be
 installed.
 I have looked through NFPA 20 and didn't see anything requiring
 either.
 Should I be looking in a different place?
 
 Thanks,
 
 Dewayne
 
 
 
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
 er.org ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
 er.org
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
 .org
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
 

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Re: pump test header valves

2014-04-09 Thread RFletcher
Or, if possible keep headed in the pump room without valves, run hoses out to a 
truck mounted test rack with hose gates on the rack. This way the person 
reading the pitot can adjust the valves,
Sent from my iPhone3200
USA Parkway
McCarran‎ NV‎ 89434
United States

 On Apr 9, 2014, at 12:49 PM, John Denhardt jdenha...@stricklandfire.com 
 wrote:
 
 Funny but true story:
 
 I had a client who was worried about security with the test header 
 penetrating the exterior of the building.  They had us remove the test header 
 after each test and store in the fire pump/mechanical room.  We were 
 instructed to install a blind flange using sealant on the bolts so the blind 
 flange would not be easily removed.  Well, the client decided to have the 
 area cleaned up.  To everyone surprise, when showed up for the annual fire 
 pump system test, no test header was in the room.  After the investigation, 
 the employee that cleaned the room said he did not know what it was but it 
 was big, heavy and had brass valves.  He made the decision to throw it away.
 
 Amazing - you can not make this stuff up!
 
 John
 
 
 John August Denhardt, P.E., FSFPE 
 Strickland Fire Protection Incorporated 
 5113 Berwyn Road 
 College Park, Maryland 20740 
 Office Telephone Number:  301-474-1136 
 Mobile Telephone Number:  301-343-1457 
 FIRE SPRINKLERS SAVE LIVES - Can you live without them?
 
 -Original Message-
 From: sprinklerforum-boun...@lists.firesprinkler.org 
 [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of David 
 Autry
 Sent: Wednesday, April 09, 2014 2:32 PM
 To: sprinklerforum@lists.firesprinkler.org
 Subject: RE: pump test header valves
 
 LOL, I was think of one that I did, that had sixteen (16) valves.
 
 
 David Autry
 
 Meininger Fire Protection Inc.
 2521 W L St. Suite No.4
 Lincoln, Ne 68522
 Voice (402) 466-2616
 Fax (402) 466-2617
 da...@mfp-inc.com
 
 -Original Message-
 From: sprinklerforum-boun...@lists.firesprinkler.org
 [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of
 rongreenman .
 Sent: Wednesday, April 09, 2014 12:43 PM
 To: sprinklerforum@lists.firesprinkler.org
 Subject: Re: pump test header valves
 
 Too bad, I was liking the 2 1/2 plastic pipe caps idea a lot. The
 removing the entire test header is Ok but that has to be at least two and
 probably three guys on anything bigger that a couple of three valves.
 
 
 On Wed, Apr 9, 2014 at 10:20 AM, Bobby McCullough 
 bo...@atlantasprinkler.com wrote:
 
 My mistake.  The 2.5 plastic caps are hose threads  installed on the
 valve where only the caps were stolen, which is common.  I only have a
 few projects with valves stolen  there we used threaded ductile caps
 on the nipples  locked the valves in the pump room.
 
 -Original Message-
 From: sprinklerforum-boun...@lists.firesprinkler.org
 [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of
 Ben Young
 Sent: Wednesday, April 09, 2014 12:05 PM
 To: sprinklerforum@lists.firesprinkler.org
 Subject: Re: pump test header valves
 
 Bobby,
 
 Do you mean screw-on PVC caps, or the plastic break caps for FDC snoots?
 
 Thanks for the feeback everyone, I didn't realize this was so common.
 I'll have to start recommending this to some of our clients in high
 theft areas from now on.
 
 
 Benjamin Young
 
 
 On Wed, Apr 9, 2014 at 9:50 AM, Bobby McCullough
 bo...@atlantasprinkler.com
 wrote:
 
 We use 2.5 plastic caps.  Not much value at the scrap yard.  Take
 the
 
 valves in the pump room and use a bicycle cable  lock to keep them
 from wandering off.
 
 Bobby McCullough
 Atlanta Sprinkler
 
 
 -Original Message-
 From: sprinklerforum-boun...@lists.firesprinkler.org
 [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of
 Morey, Mike
 Sent: Wednesday, April 09, 2014 8:49 AM
 To: sprinklerforum@lists.firesprinkler.org
 Subject: RE: pump test header valves
 
 They make test header outlets with male threaded outlets (basically
 the opposite of an FDC) with hose caps that you remove and then
 screw on hose valves that have a female swivel on the inlet side.
 Of course
 
 there's still the risk of someone stealing the hose caps and/or
 brass adapteer fittings that provide the male hose thread, but at
 least the valves aren't sitting out there too.
 
 Mike Morey, CFPS, SET
 Planner Scheduler/Designer
 BMWC Constructors, Inc.
 1740 W. Michigan St, Indianapolis, IN 46222
 O: 317.651.0596 | C: 317.586.8111
 mo...@bmwc.com | www.bmwc.com
 
 
 From: sprinklerforum-boun...@lists.firesprinkler.org
 sprinklerforum-boun...@lists.firesprinkler.org on behalf of Ben
 Young derblitzkrie...@gmail.com
 Sent: Wednesday, April 09, 2014 8:40 AM
 To: sprinklerforum@lists.firesprinkler.org
 Subject: pump test header valves
 
 Last week I was at an ASCET meeting where a pump presentation was
 given.
 
 Someone asked the presenter if it was allowed to remove the test
 header valves and keep them in the 

RE: heat collector vs heat director

2014-03-25 Thread RFletcher
Love engineer humor.
Ron f

From: sprinklerforum-boun...@lists.firesprinkler.org 
[sprinklerforum-boun...@lists.firesprinkler.org] on behalf of Todd - Work 
[t...@fpdc.com]
Sent: Tuesday, March 25, 2014 9:40 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: heat collector vs heat director

 Slightly disagree; I think 98.2399875875% of the time.  :)

In theory

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
www.fpdc.com
860-535-2080 (ofc)
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Re:

2014-03-25 Thread RFletcher
We use intermediate for everything unless specifically forbiden. Have to watch 
out cuz  some heads not available in intermediate.

- Original Message -
From: Jim Adams [mailto:tfscolor...@aol.com]
Sent: Tuesday, March 25, 2014 01:11 PM
To: sprinklerforum@lists.firesprinkler.org 
sprinklerforum@lists.firesprinkler.org
Subject: 


Ifyou have a closet solely with a washer/dryer should you put a standard temp 
orintermediate temp head in it ?  FCU and hot water heater rooms are veryclear 
to use intermediate temp heads..
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: 1978 NFPA 13 question

2014-03-24 Thread RFletcher
NFPA #13, 1978, A-1-7.3.3 Warehouses having moderate to higher combustibility 
of content, such as household furniture , paint, general, a=storage, whisky etc.
Ron F

-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org 
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of David Autry
Sent: Monday, March 24, 2014 11:45 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: 1978 NFPA 13 question

In my 1983 Edition, .26/4000 is above the Extra Hazard Group 1. It may have 
come from 231C?

David Autry

Meininger Fire Protection Inc.
2521 W L St. Suite No.4
Lincoln, Ne 68522
Voice (402) 466-2616
Fax (402) 466-2617
da...@mfp-inc.com

-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of 
craig.pr...@ch2m.com
Sent: Monday, March 24, 2014 1:33 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: 1978 NFPA 13 question

I'm looking for the definition of what was covered by an Ordinary Hazard Group 
3 classification based on the 1978 NFPA 13.

I have a warehouse designed at .26/4000 with 600 gpm hose stream allowance, 
Ordinary Hazard Group 3.  It was a preaction system with area heat detection.  
(non-heated whse).

Trying to figure out what the EOR was basing the design on as far as 
anticipated type of storage.

25 ft high piled (no racks), 35 ft high ceiling.

Craig L. Prahl, CET
Fire Protection Group Lead
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29303
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
craig.pr...@ch2m.com

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.o
rg
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


P-A System Pendent Sprks

2014-03-13 Thread RFletcher
Here is a new one, for me anyway. Had a designer ask if it was okay to use 
exposed pendents on a pre-action system. He had it designed with uprights but 
due to field conditions the pipe was installed higher than designed and the 
foreman changed the heads to pendent. 13 says pendents have to be on return 
bends but there is no ceiling. No freezing to worry about here in Phoenix.
Ron F   

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: P-A System Pendent Sprks

2014-03-13 Thread RFletcher
No drops just a 1/2 head in a threaded tee or elbow. We are not us nitrogen.
Ron F

-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org 
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Matt Grise
Sent: Thursday, March 13, 2014 9:03 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: P-A System Pendent Sprks

There could be a corrosion issue if there is water trapped in the drops - are 
you using nitrogen supervision?

Matt Grisé PE*, LEED AP, NICET II  
Sales Engineer 
Alliance Fire Protection 
130 w 9th Ave.
North Kansas City, MO 64116

*Licensed in KS  MO 

913.888.0647 ph 
913.888.0618 f 
913.927.0222 cell 
www. AFPsprink.com 


-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org 
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of 
rfletc...@aerofire.com
Sent: Thursday, March 13, 2014 10:59 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: P-A System Pendent Sprks

Here is a new one, for me anyway. Had a designer ask if it was okay to use 
exposed pendents on a pre-action system. He had it designed with uprights but 
due to field conditions the pipe was installed higher than designed and the 
foreman changed the heads to pendent. 13 says pendents have to be on return 
bends but there is no ceiling. No freezing to worry about here in Phoenix.
Ron F   

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: occupancy classification vs occupancy hazard

2014-03-12 Thread RFletcher
The interchangeable one I like most is expansion joint and seismic joint. Can't 
tell you how many times I have had AHJ's and EOR's write us up for not having a 
seismic joint in our pipe where it crossed an expansion joint. Actually had a 
structural engineer tell me there was no difference between the two. Sorry for 
going off topic.
Ron F

-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org 
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Curtis 
Tower
Sent: Wednesday, March 12, 2014 5:43 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: occupancy classification vs occupancy hazard

It seems that semantics are everything in this industry; however, certain terms 
tend to be used interchangeably by certain people.  Code vs. Standard, hazard 
occupancy vs. IFC occupancy group, etc.  I've had very heated discussions with 
GC's and MEP's concerning the differences.  I once had a full blown argument 
with an individual over a community center project in a small Texas town 
which was blanket classified as IFC Group A-3.  As we later found out, every 
third weekend, this community center, which had a large, multi-court gymnasium 
would be hosting a swap-meet inside.  

Now, correct me if I'm wrong, but what would have been considered a light 
hazard occupancy per the standard is being utilized as an IFC Group M or 
S-1 occupancy which would necessitate a higher density requirement per the 
standard.  Given that it's a swap-meet there is absolutely no telling what 
sort of commodities might be present.  I imagine that the commodities would not 
exceed 8'0 under most any circumstance and the majority of the merchandising 
would be on collapsible tables, but I was attempting to apply a conservative 
approach by implementing an ordinary hazard II density.

Curtis Tower

-Original Message-
From: Brad Casterline [mailto:bcasterl...@fsc-inc.com] 
Sent: Monday, March 10, 2014 10:48 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: occupancy classification vs occupancy hazard

Humble enough, Sir Roland.
I will have to think quite a bit more about everything else you said, however.

 On Mar 10, 2014, at 10:09 AM, Roland Huggins rhugg...@firesprinkler.org 
 wrote:
 
 I would encourage not embracing the defining examples that residential is 
 life safety and storage is property protection and everything else is mushy 
 in-between ground.  It’s the system type that dictates the objective.  All 
 NFPA 13 systems for all sprinkler types and for all occupancies and uses are 
 considered both life safety and property protection.  
 
 As for the confusion over 5.1.1 and 5.1.2, that text has been in the standard 
 since Napoleon was a corporal.  That means if one wanted an exact explanation 
 of what was meant, the folks that crafted this sentence are gone and the 
 current batch could / might / probably (pick one) will have something 
 different assigned to those words.  My interpretation has always been that 
 the phrase occupancy hazard is a sprinkler term and does not address or 
 influence the building design as dictated by the building code and their 
 associated use of terms. 
 
 The text in the annex has nothing to do with the issue of comparing what 
 these 2 sections are trying to say.  Notice the asterisk is on the title 5.1. 
 so it’s discussing the assignment of an occupancy classification.  It rightly 
 points out that an office is generally a light hazard occupancy but there can 
 and will be areas that exceed the fuel load for LH.  As such, that area would 
 be a higher occupancy hazard classification.
 
 As Galen commented, it is unfortunate that the term occupancy was included.  
 Calling it simply X hazard classification would have worked just fine but 
 changing it now would take an act of congress.  Ummm they may actually be 
 willing to look at this since they aren’t doing anything else of significance.
 
 As a member of NFPA 13, I probably should add the TC caveat that this is not 
 to be considered a formal interpretation of NFPA or any of its technical 
 committees but just my humble opinion.  Well opinion anyways.
 
 Roland
 
 Roland Huggins, PE - VP Engineering
 American Fire Sprinkler Assn.   ---  Fire Sprinklers Saves Lives
 Dallas, TX
 http://www.firesprinkler.org
 
 
 
 
 
 On Mar 10, 2014, at 6:54 AM, Brad Casterline bcasterl...@fsc-inc.com wrote:
 
 Yups. If it's not Residential or Storage, it's too mushy.
 
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org

RE: occupancy classification vs occupancy hazard

2014-03-12 Thread RFletcher
Nor do we usually receive the bid package early enough to ask questions and get 
answers.
Ron F

-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org 
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Steven Cook
Sent: Wednesday, March 12, 2014 10:11 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: occupancy classification vs occupancy hazard

Dave - 

I find when submitting pre-bid RFIs regarding non-applicable requirements in 
the bid packages, most are not addressed, and some engineers (will not name 
them) got offended about being called out on some of it.  One we see 
frequently -  applying hanger rod diameters and hanger spacing required for 
plumbing (assuming) to sprinkler specs.

Disregarding specs made me think of a funny story from a project a long time 
ago - I had a general contractor insert a note in the middle of his weekly 
meeting minutes that were emailed to the team, stating if anyone actually is 
reading these and calls me stating so, I will give them $50.  Not a single 
person called.  

STEVE COOK 
TG Gallagher


-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org 
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of David 
Sornsin
Sent: Wednesday, March 12, 2014 12:54 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: occupancy classification vs occupancy hazard

I worked for Rapid Fire last year and when putting together a bid, I found it 
interesting that the spec for an elementary school had verbiage that I had 
written 9 years prior while doing the FPE thing with Mark Sornsin.  An 
engineering firm had subbed out a High Expansion Foam job to us, and our spec 
apparently then became the basis for their standard sprinkler spec.

Contractors in this industry are so used to schlock spec's that they too
often ignore items added by legitimate EOR's.   If all contractors actually
questioned the ME's prior to bid, and copied the Architect, it would put 
pressure on the ME's to clean up their act and actually modify the spec as 
needed by the current job.  But few contractors have time, and the ones who are 
used to bidding off certain EOR's 'know' what's enforced and what isn't, 
thereby giving them a competitive advantage versus anybody not familiar with 
that particular engineer.

When I worked with Mark we used to joke about adding a clause at the
beginning of each spec:   Note: We really, really, really, really mean
what we say in this spec.

David M. Sornsin
Sornsin Fire Design  Consulting
Fargo ND
701.371.0643
david.sorn...@gmail.com




On Wed, Mar 12, 2014 at 10:40 AM, Mark A. Sornsin, P.E.  
masorn...@kfi-eng.com wrote:

 Agreed.  Though these questions are best asked during the bidding 
 process, not during shops review.

 Mark A. Sornsin, P.E. | Karges-Faulconbridge, Inc. | Fire Protection 
 Engineer | Fargo, ND | direct: 701.552.9905 | mobile: 701.371.5759 | 
 http://www.kfiengineers.com

 -Original Message-
 From: sprinklerforum-boun...@lists.firesprinkler.org [mailto:
 sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of 
 craig.pr...@ch2m.com
 Sent: Wednesday, March 12, 2014 10:10 AM
 To: sprinklerforum@lists.firesprinkler.org
 Subject: RE: occupancy classification vs occupancy hazard

 When you have to specify a non-standard design criteria it's best to 
 provide some clarification in the documentation as to why you chose 
 what you did.  It could help prevent these types of questions (or at 
 least minimize them somewhat).

 Craig L. Prahl, CET
 Fire Protection Group Lead
 CH2MHILL
 Lockwood Greene
 1500 International Drive
 Spartanburg, SC  29303
 Direct - 864.599.4102
 Fax - 864.599.8439
 CH2MHILL Extension  74102
 craig.pr...@ch2m.com



 -Original Message-
 From: sprinklerforum-boun...@lists.firesprinkler.org [mailto:
 sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Mark A.
 Sornsin, P.E.
 Sent: Wednesday, March 12, 2014 10:49 AM
 To: sprinklerforum@lists.firesprinkler.org
 Subject: RE: occupancy classification vs occupancy hazard

 My comparable story relates to a small town community wellness center. 
 It included Gymnasium spaces, swimming, etc.  We were hired only to 
 provide a 'performance specification', but we thought it might be 
 novel to include performance criteria...

 For the gymnasium we talked with the architect about potential uses 
 beyond athletics, and he confirmed that there could be trade shows, 
 receptions, etc.  We specified OH II.  The contractor submitted shops 
 to the Fire Marshal who commented that the Gymnasium didn't require 
 OHII, just Light haz., so naturally the contractor wanted us to allow 
 the LH design. I don't blame them, but this highlights what we're discussing 
 on this thread:
 classification and hazard are different animals. Sometimes a 
 gymnasium, is just a gymnasium; sometimes a banana, is just a banana; 
 and sometimes the engineer has done his homework and specifies a 

RE: Diesel Pump Generic Questions

2014-03-07 Thread RFletcher
I have never heard of a soft start diesel. I guess they could put a damper on 
the governor to prevent the throttle from opening quickly but I don't know what 
good it would do. Any pressure surge would be negligible unless there was a big 
air pocket in the system somewhere.

For me it depends on the application. For big distribution centers, 500,000 
sqft, I prefer diesel pumps with a pressure limiting drive. We can size the 
pump to produce 175 psi at the discharge flange. ESFR's don't yet come rated to 
250 psi (Tyco, Viking, Reliable, are you listening?). For almost any other 
application electric is good enough.

When larger pumps are required, say 2500 gpm the motors can get so big the cost 
of the electric service into the pump room can be quite pricey. High horsepower 
electric pumps with an automatic transfer switch and a wye delta closed 
transition start can cost as much as a diesel pump.
Ron F 

-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org 
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Cahill, 
Christopher
Sent: Friday, March 07, 2014 1:22 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Diesel Pump Generic Questions

Is there a way or such a thing as soft starting a diesel?

I seem to recall a LONG time ago FM had a report out concluding 25%+ of diesel 
pump would fail during a fire.  Now I could be wrong on the long, FM, 25%.  
Does anybody else recall something along these lines current or old?

I admit I am biased against diesel pumps, cost more, require more maintenance 
and I believe are less reliable mostly due to the maintenance that rarely gets 
done properly.  I suppose I'd agree they are more reliable IF maintained.  I 
also have a surge pressure issue.  But the most important thing is I'm open 
minded either way for someone to school me.  I could be off base or there is 
supporting justification.

And no, we have yet to delve into the reliable power question officially.  I 
was told by the PM and other discipline leads we're using diesel but no one can 
tell me why exactly.  So I'm making a case for either contingency.

Chris Cahill, PE*
Associate Fire Protection Engineer
Burns  McDonnell
Phone:  952.656.3652
Fax:  952.229.2923
ccah...@burnsmcd.commailto:ccah...@burnsmcd.com
www.burnsmcd.comhttp://www.burnsmcd.com/
*Registered in: MN


Proud to be #14 on FORTUNE's 2014 List of 100 Best Companies to Work For




___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Modifying sprinklers

2014-03-05 Thread RFletcher
It's done all the time. Do the hydro test then knock out the links.
Ron F

-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org 
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of 
craig.pr...@ch2m.com
Sent: Wednesday, March 05, 2014 7:25 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Modifying sprinklers

Received a shop drawing stating that for the deluge system, the contractor 
would purchase standard fused sprinklers and remove the fusible link.

Now I can't find specific NFPA verbiage that would prohibit this but seems to 
me that a sprinkler that is listed for LH or OH occupancies would not be 
acceptable for an EH deluge system just by popping the link out.  Wouldn't this 
also be modifying the sprinkler post production?

Maybe this is done all the time, but what say ye?


I found this statement in 13,
8.4.4 Open Sprinklers.
8.4.4.1 Open sprinklers shall be permitted to be used in deluge systems to 
protect special hazards or exposures or in other special locations.

Seems kind of like a DUH, statement.  What other type of sprinkler would you 
use for deluge other than open?


Craig L. Prahl

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


  1   2   3   4   >