Hi Larry,
I agree with you completely...I think the lab didn't see that peak going over
the limit line and therefore didn't QP. We only noticed now that they have
sent the report several weeks later. They're arguing that there is no need to
retest.
Thanks,
Mark
From: Larry K. Stillings
limit.
Any thoughts are appreciated.
Thanks,
Mark
-
This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send your e-mail to
EMC-PSTC@LISTSERV.IEEE.ORG
All emc-pst
Hi Brian,
Since this is machinery, typically IEC 60204-1 would be applied. Check out
clause 8.2.6 Additional requirements for electrical equipment having earth
leakage currents higher than 10 mA.
Best regards,
Mark Stultz | CMSE(r) | Sealed Air | AUTOBAG(r) brand Equipment | Streetsboro,
OH
Just a simple reminder, especially if anyone uses their employer or private
business devices to use AI tools: the information used for questions
immediately and forever becomes public property.
-Original Message-
From: Ralph McDiarmid
Sent: Wednesday, October 11, 2023 2:08 PM
To:
to be able to submit to FCC and ISED
databases.
Mark
From: Brian Gregory
Sent: Monday, October 9, 2023 1:44 PM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: [PSES] Timeframe for new FCC registration
Hello,
I'd like to have all options fleshed out prior to committing to a fairly
expensive quote for full
Wouldn't this fall under the requirement from 60204-1 clause 5.3.5 for Excepted
Circuits?
"Permanent warning label(s) shall be appropriately placed in proximity to the
operating means of the supply disconnecting device to draw attention to the
hazard"
Best regards,
Mark Stult
Hi Brian,
You may want to consider repeating test #3 after environmental conditioning.
The true test of a plating is corrosion resistance over time.
Best of luck,
Mark Stultz | CMSE | Sealed Air | Automated Packaging Systems | Streetsboro,
OH | 330-342-2402
From: Brian Kunde
Sent: Tuesday
scheduled for a vote.
Best regards,
Mark Stultz | CMSE(r) | Sealed Air | Automated Packaging Systems | Streetsboro,
OH | 330-342-2402
From: Richard Georgerian
Sent: Monday, 28 November, 2022 10:41 AM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: [PSES] Link to secondary legislation draft RE: [PSES] SI
Bridge-type milling and drilling machines;
o Metal forming presses;
o Newspaper printing presses;
Best regards,
Mark Stultz | CMSE(r) | Sealed Air | Automated Packaging Systems | Streetsboro,
OH | 330-342-2402
From: Brian Kunde
Sent: Tuesday, 26 July, 2022 10:36 AM
To: EMC-PSTC
.
Best regards,
Mark Stultz | CMSE(r) | Sealed Air | Automated Packaging Systems | Streetsboro,
OH | 330-342-2402
From: James Pawson (U3C)
Sent: Friday, 17 June, 2022 3:43 AM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Re: [PSES] Removable door panel grounding
CAUTION: This email originated from
In my experience, a single connection point is risky as it only takes a small
amount of corrosion to cause the machine to fail the 60204-1 ground bond test.
Mark Stultz | CMSE(r) | Sealed Air | Automated Packaging Systems | Streetsboro,
OH | 330-342-2402
From: Ken Javor
Sent: Thursday, 16
is installed. You'll need
the panel and gasket plated so that there is no corrosion that would increase
the contact resistance since this arrangement can't be considered gas-tight.
Best regards,
Mark Stultz | CMSE(r) | Sealed Air | Automated Packaging Systems | Streetsboro,
OH | 330-342-2402
From
this helps.
Mark
On 4/28/22 2:49 AM, Dürrer Bernd wrote:
Hi Ryan,
For the radio module that you describe, the following standards are
applicable:
ETSI EN 300 328 V2.2.2
(https://www.etsi.org/deliver/etsi_en/300300_300399/300328/02.02.02_60/en_300328v020202p.pdf)
is the applicable standard
could be present. There is some data out there for impact with
adults in industrial environments, but precious little... well, nothing
that I've found so far... involving contact with children.
Thanks,
Mark
On 2/23/22 8:01 PM, Douglas E Powell wrote:
Looks very interesting, I'll have to fit
injury, such as being more easily pushed down and hitting their head
on the floor. In fact, I am interested to know if there are others
out there who are aware of any data or studies regarding impact with
children.
Thanks,
Mark
Hi Doug:
Thanks for your comments.
What bothers me
with IP32, we typically make sure
that any water that enters the enclosure will be directly away from any
components therein and toward drain holes at the bottom of the enclosure.
Best regards,
Mark Stultz
From: Brian Kunde
Sent: Monday, 14 February, 2022 9:23 AM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Ted brings up a great point and it a good reminder that, in addition to the
standards, you need a cross-functional risk analysis. This is why I always
bring in a Service Tech from the field to take part in the risk analysis. They
have shown me several "tool holders" over the ye
need to be brought before the
committee.
Best regards,
Mark Stultz
From: Gary Tornquist <05big...@gmail.com>
Sent: Tuesday, 8 February, 2022 9:52 PM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: [PSES] Magnets as reliable fasteners
You don't often get email from 05big...@gmail.com<mai
Many thanks to all for the great conversation on this. I've learned quite a
bit!
Mark Stultz
From: MIKE SHERMAN
Sent: Thursday, 3 February, 2022 3:48 PM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Re: [PSES] Machinery Leakage Current
CAUTION: This email originated from outside
IEC 60335-1. Is there another
source for leakage current limits that is machinery-specific? There is nothing
in the type-C standard for this product type.
Thanks,
Mark Stultz
-
This message is from the IEEE Product Safety E
Hello,
Does anyone know of an ISO or IEC symbol for short circuit current rating? Is
it acceptable to abbreviate as SCCR or will this need translated?
Thanks,
Mark Stultz
-
This message is from the IEEE Product Safety
We build a top-level generic and then pack the power cord right before crating.
Where we run into issues is when we have a distributor in Europe or Asia
orders the machine based on their location but the end-user is in a different
country.
Mark Stultz | CMSE(r) | Sealed Air | Automated
Wonderful, Thanks!
Mark Stultz | CMSE® | Sealed Air | Automated Packaging Systems | Streetsboro,
OH | 330-342-2402
From: Graevinghoff Andreas (ETAS/NE)
Sent: Wednesday, July 14, 2021 12:13 PM
To: Stultz, Mark ; EMC-PSTC@LISTSERV.IEEE.ORG
Subject: RE: Demo exception for EAC certification
Machinery and many other products require EAC certification or declaration
prior to "placing on the market" in Russia or other EAEU countries. Does
anyone know if there is an exception for demo or trade show machines?
Thanks in advance,
Mark Stultz
10175 Philipp Parkway
Senior
Hello all,
Is it permissible to combined separate conductors to carry a load in parallel
within machinery? If it is allowable, what derating would be required? I
can't find reference to this in IEC 60204-1 or NFPA 79.
Many thanks,
Mark Stultz
10175 Philipp Parkway
Senior Mechanical
I believe Doug is going forward with the meeting. My mistake was sending a
calendar invite to the whole list rather than my personal calendar. Sorry for
the confusion.
Mark Stultz | CMSE® | Sealed Air | Automated Packaging Systems | Streetsboro,
OH | 330-342-2402
From: Bansi Patel
Sent
My apologies for the meeting spam...
Mark Stultz | CMSE(r) | Sealed Air | Automated Packaging Systems | Streetsboro,
OH | 330-342-2402
-Original Appointment-
From: Stultz, Mark <0f79f2e10e47-dmarc-requ...@listserv.ieee.org> On Behalf
Of Stultz, Mark
Sent: Tuesday, March 16,
:16010101T02
TZOFFSETFROM:-0800
TZOFFSETTO:-0700
RRULE:FREQ=YEARLY;INTERVAL=1;BYDAY=2SU;BYMONTH=3
END:DAYLIGHT
END:VTIMEZONE
BEGIN:VEVENT
ORGANIZER;CN="Stultz, Mark":mailto:mark.stu...@sealedair.com
ATTENDEE;ROLE=REQ-PARTICIPANT;PARTSTAT=NEEDS-ACTION;RSVP=TRUE;CN=doug emces
d.com:mailto:d...@
:16010101T02
TZOFFSETFROM:-0800
TZOFFSETTO:-0700
RRULE:FREQ=YEARLY;INTERVAL=1;BYDAY=2SU;BYMONTH=3
END:DAYLIGHT
END:VTIMEZONE
BEGIN:VEVENT
ORGANIZER;CN="Stultz, Mark":mailto:mark.stu...@sealedair.com
ATTENDEE;ROLE=REQ-PARTICIPANT;PARTSTAT=NEEDS-ACTION;RSVP=TRUE;CN=doug emces
d.com:mailto:d...@
Hello,
In an effort to get more accurate pre-compliance measurements, we're looking
into building an OATS setup. Does anyone know of any companies in the US that
will install/build one?
Thanks,
Mark Stultz
10175 Philipp Parkway
Senior Mechanical Development Engineer
Streetsboro, OH 44241
bells for me which is what
prompted re-reading the standards. This machine will be sold worldwide, but
mostly in the US, Canada, and the EU. We typically apply IEC 60204-1 for
electrical safety and EN 415-10 (Packaging Machinery: General).
Thanks,
Mark Stultz | CMSE® | Sealed Air | Automated
on connecting the bonding system this way? Is NFPA 79
as inflexible in this regard as I am reading it?
Thanks in advance,
Mark Stultz
10175 Philipp Parkway
Senior Mechanical Development Engineer
Streetsboro, OH 44241
CMSE® - Certified Machinery Safety Expert (TÜV NORD)
330-342-2402
Automated
.
Best regards,
Mark Stultz | CMSE(r) | Sealed Air | Automated Packaging Systems | Streetsboro,
OH | 330-342-2402
From: David Cereceres
Sent: Friday, November 20, 2020 1:45 PM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: [PSES] SPVD Interpretation
CAUTION: This email originated from outside
Anyone know where to find vector files (dxf, ai, pdf, et cetera) for the PSE
mark for Japan? Or dimension requirements?
Thanks,
[cid:image001.png@01D5F87E.2E1AE560]
Mark Stultz
10175 Philipp Parkway
Senior Mechanical Development Engineer
Streetsboro, OH 44241
CMSE® - Certified Machinery
Hello Kevin,
Thanks for the great explanation. Who is ultimately responsible for ensuring
that equipment is certified by a NRTL? Does the final responsibility fall on
the purchaser/end-user or on the manufacturer?
Best regards,
Mark Stultz | CMSE® | Sealed Air | Automated Packaging Systems
Hello,
Anyone know of a good tester for IEC 60204-1 and 60335-1 residual voltage
that's available in the US? I'm looking at
http://www.stanmax.nl/index.php/msom/ but not sure about leadtime from NL.
Thanks!
[cid:image001.png@01D5DA7B.4CAEE2E0]
Mark Stultz
10175 Philipp Parkway
Senior
John,
would be beneficial if you can share your earliest recollection of the dates,
besides stating it dates back much further.
Mark
From: John Woodgate
Organization: J M Woodgate and Associates
Reply-To: John Woodgate
Date: Monday, November 18, 2019 at 11:18 AM
To:
Subject: Re: [PSES] 80
t? Is it ground/bond
resistance?
Thanks,
[cid:image005.png@01D59097.7E4A7D10]
Mark Stultz
10175 Philipp Parkway
Senior Mechanical Development Engineer
Streetsboro, OH 44241
CMSE® - Certified Machinery Safety Expert (TÜV NORD)
330-342-2402
Automated Packaging Systems
[A picture contai
<mailto:paul.good...@era.co.uk>
http://blog.complianceandrisks.com/commentary-analysis/uk-reach-after-brexit
Mark Schmidt
From: Grasso, Charles [mailto:charles.gra...@dish.com]
Sent: Friday, August 2, 2019 4:03 PM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: [PSES] Trusted resources for RoHS/Reach
Hello e
is the job post. https://grnh.se/acfc73d22.
Please contact Jennifer Tran with all of the inquiries and responses.
jennifer.t...@spacex.com<mailto:jennifer.t...@spacex.com>; P: 310.970.3507
Thank you,
Mark Gandler
-
This m
with the red button? Someone suggested blue as a
background color because allegedly this is easier for color blind persons to
see.
What standard(s) does this requirement come from?
Thanks,
Mark
Mark Ortlieb
Sr. Product Safety Engineer
858-207-7591
Brain Corporation™
9401 Waples Street, Suite
they are?
Thanks,
Mark
Mark Ortlieb
Sr. Product Safety Engineer
Brain Corporation™
9401 Waples Street, Suite
100<https://maps.google.com/?q=9401+Waples+Street,+Suite+100+San+Diego,+CA%C2%A0+92121=gmail=g>
San Diego,
CA<https://maps.google.com/?q=9401+Waples+Street,+Suite+100+San+Diego,
Thanks Doug…
From: Doug Powell [mailto:doug...@gmail.com]
Sent: Wednesday, March 20, 2019 11:42 AM
To: Schmidt, Mark ; EMC-PSTC
Subject: Re: [PSES] PLINE 1610
You might try ATE Corp. They still rent these and may also have maintenance
shop services. Anyway, you could ask.
Best, Doug
for looking at it.
Thanks,
Mark
Please be advised that this email may contain confidential information. If you
are not the intended recipient, please notify us by email by replying to the
sender and delete this message. The sender disclaims that the content of this
email constitutes an offer
. This will be provided by the LSEM.
The Power Source will also be approved and qualified by the LSEM. Naturally, we
will assure that our components in their installation will not prohibit final
compliance requirements but.
Thanks again,
Mark
From: lauren.cr...@us.tel.com [mailto:lauren.cr
completed machinery is
placed on the market a CE mark is not required, so a Declaration of
Incorporation will be issued. This is an industrial application and one of the
pieces that will be part of this installation is BT compliant for USA, Canada,
EU, China, Japan and S. Korea. What would be my
n any moving part other than the door."”
Compliance Guide for Cabinet X-Ray Systems
https://www.fda.gov/MedicalDevices/ucm094358.htm
Mark
From: Nyffenegger, Dave [mailto:dave.nyffeneg...@bhemail.com]
Sent: Tuesday, February 5, 2019 12:31 PM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject:
All,
Just received the following link from a colleague, using the UKCA marking if
the UK leaves the EU without a deal. Links to part of the "[PSES] Brexit
requirements for UK manufacturers" a couple of weeks ago.
https://www.gov.uk/government/publications/prepare-to-use-the-ukca-
integrity which is
unlike the CE Mark. So to John’s point no I do not agree with your
interpretation of what I said.
From: Pete Perkins [mailto:0061f3f32d0c-dmarc-requ...@listserv.ieee.org]
Sent: Friday, January 18, 2019 11:58 AM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Re: [PSES] Brexit
: the manufacturer
is ultimately responsible for their product.
Mark
From: John Woodgate [mailto:j...@woodjohn.uk]
Sent: Friday, January 18, 2019 3:05 AM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Re: [PSES] Brexit requirements for UK manufacturers.
That puts the responsibility for compliance
Agreed, however this is typically done in the qualification and preliminary
test phase of system integration. You should always know what your
margins/limitations are. I believe the question focused on final test and in
that case you test to the requirements of the standards.
From: John Howe
have design's or systems that have 2 or 3 external power cords and
these of course are tested independently since end use intended configuration
is to supply AC with multiple AC Main connections.
Regards,
Mark
From: Larry K. Stillings [mailto:la...@complianceworldwide.com]
Sent: Wednesday, January
the action or process of providing someone or something with an “official
document” attesting to a status or level of achievement.
Thank you.
From: lauren.cr...@us.tel.com [mailto:lauren.cr...@us.tel.com]
Sent: Tuesday, October 09, 2018 10:51 AM
To: Schmidt, Mark; EMC-PSTC@LISTSERV.IEEE.ORG
Subject: RE
ropriately classified. If not be prepared to
add time and money to your program for addition testing.
Mark
From: Lauren Crane [mailto:lauren.cr...@us.tel.com]
Sent: Monday, October 08, 2018 4:04 PM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Re: [PSES] Does incorporated barcode scanner result in a
I believe UL/IEC 62133 would also be applicable to the battery pack and don’t
forget to contact your local shipping/transport company on li-on battery
requirements UN3480 and 3481.
Please be advised that this email may contain confidential information. If you
are not the intended recipient,
to be used with the toy -
what is Note 3 in section 1 (scope) of EN62115.
Mark
Please be advised that this email may contain confidential information. If you
are not the intended recipient, please notify us by email by replying to the
sender and delete this message. The sender disclaims that the content
Great Question.
No absolute answer but my opinion would be create awareness.
1. Generate an official legal disclosure agreement between both parties
with the understanding that your potential customer understands the fact this
is not yet compliant outside the US and they will assume
Ignorance can be achieved at all levels of management. Not sure escalating is
the best way forward. Just sayin.
From: John Allen [mailto:09cc677f395b-dmarc-requ...@ieee.org]
Sent: Friday, September 14, 2018 1:19 PM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Re: [PSES] How to lose another
James –
Thank you! I see they do a Stainless Steel M3 x 6mm long plain stud so I will
pass that onto our DO and see what they think: electrically it’s ideal for a
crocodile clip and pointed probe for a four terminal resistance test.
With best regards,
Mark
From: James Pawson (U3C)
Sent: 03
be used
on/in/through C-section steel prior to painting, that can subsequently be used
as an earth bond (at 10 A DC) test point, that will last for decades, and look
good?
Ever hopeful,
Mark
Mark Hone
Electrical Manager
TPG Maritime Ltd
[cid:image003.png@01D4436F.32931D80]Email: mark.h
Hi Scott,
Can’t remember for sure (since I no longer have access to a copy of the
standard) but IPC-A-610 may provide guidance on acceptability criteria for that.
Regards,
Mark
From: Scott Xe [mailto:scott...@gmail.com]
Sent: Wednesday, August 08, 2018 9:22 AM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Hi Mike,
SEV or ENEC Mark - Yes. It’s a corporate liability question or applied due
diligence to protect your consumer. How did you verify the certification to the
IEC standards? Either way I would think that your corporate layers would advise
100% to the letter of the law.
Which doesn’t help
Hey Mike,
Personally, I would accept that but…..
I will refer back to my “grey” statement.
Mark
From: msherma...@comcast.net [mailto:msherma...@comcast.net]
Sent: Friday, August 03, 2018 1:25 PM
To: Schmidt, Mark
Cc: EMC-PSTC
Subject: Re: SEV Mark Required for Swiss Adapter Plug?
"How di
Hi Brian,
“The good-old-days” Where have all the good times gone?
Legislation destroyed the essence of common sense practices and logic.
Influenced by power (monetary) and opinion which equates to politics. Yup, I
said the “P” word.
Regards,
Mark
From: Kunde, Brian [mailto:brian_ku
/jobdescription.html?jid=939161
Please contact me directly at mgand...@juniper.net<mailto:mgand...@juniper.net>
Thank you,
Mark Gandler (Hiring Manager)
-
This message is from the IEEE Product Safety Engineering Society em
Agree with Charles, you need to provide a compliant system to the end user.
This means test with the UPS since it plugs into the AC Mains.
Regards,
Mark
From: Grasso, Charles [mailto:charles.gra...@dish.com]
Sent: Tuesday, July 24, 2018 10:38 AM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Re: [PSES
Integrators of complex systems interfacing with other manufacturers equipment,
aerospace and military excluded and should provide a RAR. I am sure there are
other situations as well. If we look at Brian's intro to his question "Our
company makes Laboratory Equipment (test and measurement
Nice.
From: John Woodgate [mailto:j...@woodjohn.uk]
Sent: Thursday, May 17, 2018 3:59 PM
To: Schmidt, Mark; EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Re: [PSES] Customer Requests for Risk Assessments
An engineer and a lawyer argued about whose was the oldest profession. 'The
creation
with their time but to create chaos. Making corporate life
difficult and sometimes meaningless. There was a time where Company A produced
and sold a product and Company B said wow what a great product. The end.
Regards,
Mark Schmidt
From: Ken Javor [mailto:ken.ja...@emccompliance.com]
Sent
Hi Doug,
Yes, this is normal. I do not believe 3rd parties could influence or expedite
services with the ICASA due to the fact that they may be in violation of their
own anti-bribery polices. That couldn't happen could it?
Regards,
Mark
From: Kealey, Doug [mailto:doug.kea...@garmin.com]
Sent
I’d like to second John’s query, as I haven’t seen the explanation either.
If it has been posted, are EMC-PSTC postings being lost somewhere? I have
checked our company spam filters!
Regards,
Mark
From: John Woodgate [mailto:j...@woodjohn.uk]
Sent: 08 February 2018 14:15
To: EMC-PSTC
Sent from my Verizon Wireless 4G LTE smartphone
Original message
From: Michael Derby <micha...@acbcert.com>
Date: 02/09/2018 4:54 PM (GMT-05:00)
To: "Schmidt, Mark" <markschm...@xrite.com>, EMC-PSTC@LISTSERV.IEEE.ORG
Subject: RE: [PSES] FCC 433 MHz
---
Hi Ghery,
Thank you for your input.
Best Regards,
Mark
From: n6...@comcast.net [mailto:n6...@comcast.net]
Sent: Friday, February 09, 2018 3:40 PM
To: Schmidt, Mark; EMC-PSTC@LISTSERV.IEEE.ORG
Subject: RE: [PSES] FCC 433 MHz
Mark,
"It depends". What is the purpose you have in mind
Hello Group,
Can anyone tell me if 433 MHz is a restricted operating frequency for
commercial devices per the FCC? Thank you.
Best Regards,
Mark Schmidt
Please be advised that this email may contain confidential information. If you
are not the intended recipient, please notify us by email
otype for evaluation only" or is more
complex than that.
Best Regards,
Mark
Please be advised that this email may contain confidential information. If you
are not the intended recipient, please notify us by email by replying to the
sender and delete this message. The sender disclaims that t
Hi Grace,
My understanding is that the KN standards need to be purchased and are written
in Korean. I believe they are derived from the IEC but are not identical. You
may want to add KN35 to your list.
Regards,
Mark
From: Grace Lin [mailto:graceli...@gmail.com]
Sent: Tuesday, October 24, 2017
Hello Brian,
This was defined by a NRTL to be a Class III battery charger.
Thank you,
Mark
From: Brian O'Connell [mailto:oconne...@tamuracorp.com]
Sent: Wednesday, September 20, 2017 1:55 PM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Re: [PSES] Battery Charger
From: Schmidt, Mark
thanks for that. In talking
with some NRTL's and the direction they believe is appropriate can lead/mislead
you down a path that may not be logical one.
Thanks again,
Mark
From: Ted Eckert [mailto:ted.eck...@microsoft.com]
Sent: Wednesday, September 20, 2017 12:21 PM
To: Schmidt, Mark; EMC-PSTC
protection is in the 2 cell battery pack. Would have LED
indicator(s) for charge status. Size: approximately 5" x 3" x 2"
Are there any battery charger standards that may be applicable? Does this
battery charger need to be Listed or Recognized by NRTL. Any thoughts or inputs
are welcome?
be advantageous.
Mark
From: Schmidt, Mark [mailto:markschm...@xrite.com]
Sent: Friday, September 08, 2017 8:36 AM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: [External] Re: [PSES] [Commercial] [PSES] Labeling - battery operated
products
This message originated from the outside of our organization and was sent
to a distributor or another office
or branch of your company. This is not easily done and very complicated, I am
not an expert talk to your shipping company.
Mark
From: Amund Westin [mailto:am...@westin-emission.no]
Sent: Friday, September 08, 2017 12:35 AM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject
Thank you,
Mark
From: Ben Kim [mailto:benki...@yahoo.com]
Sent: Friday, September 08, 2017 12:03 AM
To: Schmidt, Mark; EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Re: [PSES] KC Mark E labeling
Hi Mark,
RRA notice 2015-26 and KATS announcement (date 4/26/2016) include this
information. Click
Thank you Ben,
Is there a link to this that is accessible? Is it on the RRA or KATS site?
Regards,
Mark
From: Ben Kim [mailto:benki...@yahoo.com]
Sent: Thursday, September 07, 2017 1:42 PM
To: Schmidt, Mark; EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Re: [PSES] KC Mark E labeling
Mark,
e-labelling
are designing the physical
label for this OEM right now. Do I have to keep the KC MSIP ID on the physical
label?
Thanks,
Mark
Please be advised that this email may contain confidential information. If you
are not the intended recipient, please notify us by email by replying to the
sender and delete
ated with a harmonised
standard that determines the conformity assessment procedure?
Best regards
Mark B
*From:* Michael Derby [mailto:micha...@acbcert.com]
*Sent:* 28 June 2017 23:02
*To:* EMC-PSTC@LISTSERV.IEEE.ORG
*Subject:* Re: [PSES] RED Harmonised Standards
If you have a transmitter-only de
parameters.”
So it IS a harmonised standard (no requirement for EU type approval
examination if applied in full) but it doesn’t give a presumption of
conformity (manufacturer may be required to do additional testing to ensure
receiver parameters meet article 3.2 requirements?).
Mark Bailey
limit but inside the UL 773 limit?
BR
Mark Bailey
-
This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send your e-mail to
<emc-p...@ieee.org>
All em
Hi Adam,
For quick connects, whatever you do, make sure it conforms to UL310 if your
product is attempting to meet the requirements of UL60950.
Regards,
Mark
From: Adam Dixon [mailto:lanterna.viri...@gmail.com]
Sent: Tuesday, February 21, 2017 7:45 AM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject
Hello Dieter,
My experience with Korea is that they only accept 10 meter measurements even
for KN 32. Not sure where you can get a Korean Standard in English. I doubt if
they are available unless you have it translated of course.
Regards,
Mark Schmidt
From: Paasche, Dieter [mailto:dieter.paas
Great discussion - thanks to all.
Sent from my Verizon Wireless 4G LTE smartphone
Original message
From: "ce-test, qualified testing bv - Gert Gremmen"
Date: 01/14/2017 6:06 AM (GMT-05:00)
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Re: [PSES] lowest
In the project that I am currently working on the main PC, HDMI cable and
Touchscreen is a subsystem of a larger system which includes hydraulics,
turntables, D65 lamps, power supplies and many other sources of potential
emissions for this device. Only the poorly constructed HDMI cable is the
cable for RF.
Thanks,
Mark
From: Ghery S. Pettit [mailto:n6...@comcast.net]
Sent: Wednesday, January 11, 2017 8:39 PM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Re: [PSES] lowest emissions 4k TV?
Brent,
I ran into a problem with HDMI cables back in 2014. It seems that the HDMI
specification
Hi John,
Would this be applicable for Light Industrial equipment as well?
Thank you.
From: John Woodgate [mailto:jmw1...@btinternet.com]
Sent: Tuesday, October 18, 2016 10:49 AM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Re: [PSES] Criteria for determining industrial vs. non-industrial for
EMC
if it did, I would migrate to it being an H field effect.
Mark
From: Doug Powell [mailto:doug...@gmail.com]
Sent: Thursday, September 15, 2016 10:36 AM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Re: [PSES] Fire ants
This topic is getting interesting.. I had originally thought it would be
received like one
to apply a CE mark on the component because it is a requirement of
the RoHS Directive. In addition since we plan on meeting the EMC Directive
requirements (good engineering practices) we must label the component with the
CE Mark and generate a DoC to the EMC and RoHS Directive. We have received
Hi Brian,
The EU does not require disclosure of an exemption, for China RoHS a disclosure
table is required. Always a good idea to have this information internally if
ever challenged.
Regards,
Mark
From: Kunde, Brian [mailto:brian_ku...@lecotc.com]
Sent: Thursday, May 12, 2016 10:34 AM
?
As part of the system compliance testing the desktop PSU will be included
in the desktop test set-up for radiated emissions and we'll do AC port
conducted emissions.testing.
Assuming the system passes I can then put the appropriate mark/ wording on
my product but am I also required to put the same mark
are required. Is this correct?
Thank you,
Mark Schmidt
-
This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send your e-mail to
<emc-p...@ieee.org>
All em
Carl,
In regard to your statement Another package may include plastic panels with no
inherent standalone function In this case there are no harmonized standards
that I am aware of for plastics so I will further assume that no CE Mark is
required.
Mark Schmidt
-Original Message-
From
Components
In message 119fa9545c6e264b830c4582886d1190c534d...@quimby.dw.local,
dated Thu, 27 Aug 2015, Mark Schmidt mark.schm...@dornerworks.com
writes:
In regard to your statement Another package may include plastic panels
with no inherent standalone function In this case there are no
harmonized