Lothar,
Of all the DofC's I've witnessed in my travels that have been generated from
test labs, very few have required the manufacturer's signature. In fact, they
were signed by an officer of the test lab. However, to be fair, these DofC's
issued from test labs may be only intended for
To all,
Well, the responses died off earlier than I anticipated.
With information that I had plus what had been provided by the respondents, I
have compiled a list of all the EMC books identified in this query and
tabluated the list to include Author, Title, Copyright date, Publisher,
Hi George,
A main difference is Annex ZB (normative) found in EN60950. There are some
clause 6 deviations in there. Also, although Annexes NA and ZC are
informative,
you might want to be aware of them, too. None of these annexes are found in
UL1950.
I hope this helps.
Best
To all,
I am interested in knowing (and maybe others are, too) about the really good
EMC books that are out and about. They may be practical, theoretical or
anywhere in between. Areas of interest are, but are not limited to PWBs,
backplanes and systems with considerations for design,
Ed et al,
It seems to me that this thread is growing into a mountain and as a whole is
providing a lot of individuals with the opportunity of allowing themselves to
get more confused on this, oops excuse me, these subjects. Let's try to
separate these subjects and maybe put some order to
Hi Graham,
I don't mean to be sarcastic, but Dear All should've read Dear All
Canadians or For Canadians Only. That would've prevented me/possibly others
from wasting my/their time trying to register on this site.
After entering the required information to register with this service, I
James,
I believe the standard you want is ISO 7779 Measurement of airborne noise
emitted by computer and business equipment. In a past life I had to use this
standard and in it are specific measurement criteria. Some criteria from
memory
are number and placement of microphones,
Hi Jeff,
The GPS directive is designated as 92/59/EEC (an html copy of it is attached).
It's posting info in the Official journal is NO. L 228 , 11/08/1992 P.
0024-0032. Sorry, I can't seem to find it again on the web. But, searching on
the following web site may produce it for you.
Hi Doug,
First, I have to ask a couple of questions. You mentioned that this product
will be CE compliant. If so and if this accessory is aimed at the EU, why then
would it have North American NEMA 110V outlets? Or, does this product when CE
marked have outlets acceptable for CE marking?
Roger et al,
Richard is correct. However, according to Industry Canada's web site, ICES-003
is now at Issue 3 dated Nov 22, 1997. Also, the suggested wording can be found
in the Annex.
Best regards,
Ron Pickard
ron_pick...@hypercom.com
__ Reply Separator
To all,
I happened to be browzing around the Eur-Lex web site today and came across
the
following quite by accident (I was searching for telecommunication terminal
equipment):
299A0204(01)
99/78/EC: Agreement on mutual recognition between the European Community and
the United States
Hi John et al,
You email has raised some questions regarding this new directive. With the
introduction of the RTTE directive (99/5/EC), how does it interplay with the
TTE Satellite Earth Station Equipment directive (98/13/EC)? Are they
exclusionary? Does one supercede the other? Can
Hi Brian,
Whizzy, eh? Well, I think that most of us resemble that remark. :-)
First, UL and CSA are but two of the 17 NRTLs that are accredited by the
Occupational Safety and Health Adminstration (OSHA) which is a part of the US
Department of Labor.
Anyway, according to OSHA
In one of my past lives, there was a safety inspector (agency not divulged
here) that adamantly defended his interpretation of the 94V marking on PWBs as
a voltage rating of the PWB. He even wrote us up for this for not having a
high
enough voltage rating. This guy, too, is still in the
Peter,
Some experiences I have had in past lives follow each of your questions. My
responses are brief due to lack of time. I hope this helps.
Anyone else, please feel free to comment.
Best regards,
Ron Pickard
ron_pick...@hypercom.com
__ Reply Separator
To all,
I have just heard that by 6/99 the BCIQ will be departing from requiring EMC
testing only at approved labs to accepting test data from labs in countries
where an MRA exists. These labs must have NVLAP or similar accreditations. I
have also heard that a US-Taiwan MRA is now in
-
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.org
with the single line: unsubscribe emc-pstc (without the
quotes). For help, send mail to ed.pr...@cubic.com,
j...@gwmail.monarch.com, ri...@sdd.hp.com, or
Lisa,
Personally, I would like the term CE approved be stricken from all spoken
and
written language. But unfortunately, the term has so pervaded the lingo of
today, I suppose it has to be true, eh? CE self declaration should include a
signed declaration of conformity with supporting
Hi Ray,
ISO7000 Graphical Symbols for use on Equipment may be the standard you're
looking for. It has a ton of symbols (many of which you have no doubt seen
before).
Best regards and happy holidays,
Ron Pickard
ron_pick...@hypercom.com
__ Reply
Hi Tony,
Try pointing your web browzer to:
http://europa.eu.int/eur-lex/en/search.html
Type in the directive you're interested in and click on search. Look for the
directive you typed in and open it. The selection may be a bit confusing as
the
results are coded, but you can see the
Hi Peter Rich,
1. I disagree with Rich in that this circuit cannot be an ELV interconnection
circuit. ELV circuits are not permitted as such in 2.10.2 of UL1950 (IEC950
clones) There is a single exception to this in 2.10.3. But, since this is a
coaxial cable connection intended for
Hello from not quite sunny (today anyway) Arizona,
The following request is being forwarded from our corporate HR department. The
areas of compliance here are EMC (un/intentional radiators), safety and
telecom
requirements representing a multitude of countries. Please note that this
I will also second that.
We have turned away from using yellow zinc coating, as well. We found that the
yellow zinc coating was prone to early oxidation which had a purple color.
This
oxidation was evident on most surfaces, but was most prevalent at the joining
surfaces (Murphy's Law).
Hi Terry,
Please excuse this reply including the group, but as some contact details were
omitted from my original posting as you noted, I thought it appropriate to
send
them to the group.
You asked
I know you asked we contact CCL but I was wondering if the seminar is worth
To all that might be interested,
Communication Certification Lab (CCL) is putting on a Conformity Assessment
seminar on October 29 30, 1998 in Salt Lake City.
I will be attending and have attended this seminar in the past. I've always
been able to use the information presented.
If
Peter,
In a past life, I had control of a screen room with double screened walls. The
manufacturer had specified connection of both screens at a single point to a
dedicated ground rod. But, it was originally connected to ground via the
electrical conduit of the power mains due to
Hi Moshe,
You asked:
Where can I get the text (or a summary) of the GR1089?
I believe Bellcore is the only place you can get the document. However, a
brief
summary of this document, such as it is, can be found at:
http://telecom-info.bellcore.com/site-cgi/ido/index.html
Just
Hello to all,
I need some assistance. particularly from those versed in the National
Electric
Code (NEC).
I've been researching the NEC and in particular Acticle 800-4. Equipment,
which states:
Equipment intended to be electrically connected to a telecommunications
network shall
Hi Tania,
Thank you for the detailed response. I was posing these question in devil's
advocate fashion and thought responses such as yours would be very useful to
members of the group.
Best regards,
Ron Pickard
ron_pick...@hypercom.com
__ Reply Separator
Hjalmar,
This document can be puurchased directly from ANSI (see below).
American National Standards Institute
1430 Broadway
New York, NY 10018
212-642-4900 tel, stds order - press 1
212-302-1286 fax
http://web.ansi.org/default_js.htm
Good luck.
Best regards,
Ron Pickard
To all that are fairly intimate with US safety requirements,
Here are some curiosity questions that have been nagging at me for a while:
Other than what can be found in the National Electric Code (Article 800-4, I
believe), the 1910 OSHA regulations and virtually all municipality electric
Thanks to all who have responded to this query thus far.
To carry this thread along, I'll pose another question, which is:
Does anyone know if there are any local, county and/or state jurisdictions
that
go beyond, or are in addition to, those regulations of OSHA and/or the NEC?
If
Jim,
But then we'd all have to pay royalties for using the WM (ugh...). Would the
collected funds be thrown into the bottomless depository in Dayton? And I
thought the IRS was powerful. :-)
Best regards,
Ron Pickard
ron_pick...@hypercom.com
__ Reply
Hi John,
Your mark? I guess your opinions are not exactly unbiased.
You seem to be much too serious going into a weekend. My experience has shown
that Friday is either a day of catching your breath from the scenarios of the
week, or having to run faster to catch up until you run off the
Hi Neil,
First, is a one-off a single on-of-a-kind unit?
Second, where one goes, usually more will follow.
I am not familiar with the specific requirements for test equipment in the US,
however, FCC Part 18 may be more appropriate. It may be wise for you to look
into Subpart I of FCC
Dan et al,
Yes, OM, WM, or any other single mark would be much preferred over the current
system.
But, let's keep things in perspective. Years back (well, maybe not that far
back), it seemed that every counrty had its own unique approval scheme, which
included unique standards,
Jeff,
Yes I agree with you in that placing standard PCs in an industrial
environment is certainly not a wise move.
Remember that the overlying emphasis of the EMC Directive is to establish a
minimum set of requirements for an intended enviroment a manufacturer is
targeting for a
Hi Jim,
It's nice to hear from you.
So, that bothers you, huh?
I believe that that EN50082-1 provision was provided because there is no one
that knows the product as well as the manufacturer. I also believe that its
writers knew that, too. Having others outside of the manufacturer
Hi Jim,
First, I've been unable to access their web site.
It has been my experience in a past life that SABS will accept EMC test data
from any internationally recognized test lab. SABS has also accepted EMC test
data from AUSTEL accredited test labs as well. There are/were a few AUSTEL
Tony,
First, I'm confused. If you know that your product complies with FCC Part 15
and UL19050, why are you asking EMC and safety certification guidance in the
US? Or, are you just making the statement?
Anyway, compliance with IEC950 does not equate to compliance with UL1950.
There
Richard et al,
To respond:
An excellent question!
Yes it was.
Let me ask one or two of my own here.
1. Are we sure that both Sweden and Norway are currently EU members ?
Not just IEC members ?
IEC members? Actually, Sweden is a recent member of the EU. Norway is not an
EU
Hi Don,
You asked: (marked with 's)
As a manufacturer of products which primarily consist of other manufacturer's
discrete parts our experience has been when submitting product for testing
approvals, is to provide the testing bodies with all available information
related to the discrete
Hi Ron, h..., great name.
First, you haven't let us know what type of product this will become.
Second, The vendor claims to meet the EMC and LV directives? Is there actual
documentation in addition to the CE marking to support this claim?
Second, you've not stated if this power
Hi Jim,
The equation that Ted supplied to you to pass on to us on the emc-pstc turned
invisible, at least for me. Would you be kind enough to type the equation out
and resend it so that those of us with the invisible equation can know what
Ted
was referring to?
Thanks
Best
Jim,
You are correct in that IEC950/EN60950/etc. does not specify primary wiring
color schemes, but only the earth conductor(s). Actually, UL1950 does not
specify black/white either. That is accomplished in the NEC.
Conversely in the international markets, I believe the blue/brown color
Hi Scott,
Yeah, you presume correctly. It dawned on me about 5 seconds after I clicked
the send button. You know, when something stupid's been done and all you can
say is A.. I was a victim of inverted thinking, however
temporarily. That darned send button should have
Hi Scott,
In your last posting, you said:
Also had another failure problem. This time, one system and three testers.
Two testers failed the system while one passed it. This problem was with
ramp rate. That is, how long it takes to go from zero volts to 1,500 VAC.
Again, there is no
Hi Richard,
The UL report will contain a list of Conditions of Acceptability
for a Recognized part which must be observed when the item is
incorporated. These conditions can sometimes be a real pain.
Amen.
Let me give you an example - dc fans. I have seen some where no
locked rotor test had
Doug,
You asked:
I have recently been in discussions about what is the real
difference between UL Recognized and UL Approved. In this
instance it was about wire but I believe that it applies to
most any product.
UL Approved? What does that mean anyway?
It is my understanding that UL
Hi Chas,
I have a question regarding dual manufacturers names
on a regulatory label.
Dual maunfacturers?
From an EMC perspective:
The situation is that Company A wishes to buy product from
Company B and resell using Company As name and model number.
In order to save time, Company
Gary,
Third party witness testing? Which agency out there will accept testing
witnessed by someone else?
It is my understanding that any testing to obtain a safety approval, UL
Listing
in this case, must be one of the following:
1. UL performs testing,
2*. Manufacturer performs
Brian,
Here's the differences in a small nutshell:
FCC CE
Radiated Emissions x x
Conducted Emissions x x
Immunity x
There are differences in frequency and emission
Hello from quite sunny Arizona,
Is there a published collection of commonly used translations of phrases used
for product labeling or in manuals, but primarily used for safety markings?
Such a listing would be preferred to come from reputable translation services
(UL, CSA, IEC, ???).
Mona,
I was thumbing thru Compliance Engineering's 1997 Reference Guide today and
came across a 2-page chart detailing European Low-Power Frequency
Allocations
(in the Telecom section). It's on pages E50 and E51, comprises 11 countries
and
has a frequency range of 0Hz to 246GHz.
No
Gary,
I don't believe that there's a specific format for TCFs, however, the contents
of a TCF are described in the guidelines for the EMC Directive (see 8.2). The
guidelines can be obtained from many sources with one being:
http://www.emc-journal.co.uk/newguide.html
As to format of
Jim,
I agree with Peter in that much care must be given to the anticipated
interpretation of any symbol, but especially those relating to safety.
As Peter said The general understanding of the meaning [of the symbol] is not
always obvious. This would be especially true for any newly
Hi Dwight,
It's nice to hear that you're still alive.
These instructions, among others for all sorts of FCC forms, can be downloaded
from the FCC web site at the following web address:
http://www.fcc.gov/formpage.html;.
I hope this helps.
Best regards,
Ron Pickard
Ed et al,
The following info was obtained fresh from the NTIA web site below:
http://www.ntia.doc.gov/osmhome/allochrt.html;
To order the Spectrum Wall Chart from the Government Printing Office,
specify the following:
1996 Spectrum Wall Chart
Brian,
You have cited the only reference that might construe concern of these
fingers, however, I do not know what you mean by if correctly
designed-in. You also did not elaborate on the performance difference
between the 2 gasket materials.
Please
Ed,
Why don't you try your local department store. They have get them from
somewhere.
On the other hand, anyone know how to contact the Crash Test Dummy
University for recent graduates? :-
Best regards,
Ron Pickard
Jim,
Here are the answers to your questions and concerns, respectively.
I was not aware that Canada had adopted CISPR 22. Can anyone confirm
this, as well as answer Dave's question regarding having to meet
conducted emissions limits starting at 150 KHz?
Hello from overcast Arizona today.
I need your assistance in finding a symbol, if one exists, that
indicates that a connection to the PSTN is neither allowed nor
intended.
I am aware of the marking found in Annex VII of 91/263/EEC. This
symbol or
62 matches