Re: [PSES] [EXTERNAL] RE: Clearances >30 kHz

2023-07-26 Thread Boštjan Glavič
julij 26, 2023 10:43:29 pop. Za: Boštjan Glavič Kp: EMC-PSTC@LISTSERV.IEEE.ORG Zadeva: RE: [EXTERNAL] RE: Clearances >30 kHz Hello Boštjan, Appreciate your reply. I have since learned that Table 10 and Table 11 are for the Working Voltages. Table 14 is what you mentioned, Withstand Voltag

Re: [PSES] [EXTERNAL] RE: Clearances >30 kHz

2023-07-26 Thread Ryan Jazz
Jazz ; EMC-PSTC@LISTSERV.IEEE.ORG Subject: [EXTERNAL] RE: Clearances >30 kHz Dear Ryan, Table 10 - input is your temporary overvoltage. Normally 2000Vpk for mains voltages up to 250Vac Table 11 - input is your working voltage Table 14 - input is your transient voltage - defined by OVC (for OVC II 25

Re: [PSES] Clearances >30 kHz

2023-07-25 Thread Boštjan Glavič
and 15 are dominating. I hope this helps. Best regards, Boštjan From: Ryan Jazz Sent: Wednesday, July 26, 2023 12:39 AM To: EMC-PSTC@LISTSERV.IEEE.ORG Subject: [PSES] Clearances >30 kHz CAUTION: This email originated from outside of our organisation. Do not click links or open attachme

Re: [PSES] Clearances >30 kHz

2023-07-25 Thread Scott Aldous
015/02/UL_WP_Final_Effects-of-High-Frequency-Voltage-Stress-on-Air-Insulation-and-Solid-Insulation_v4_HR.pdf> is a paper from UL from 2010 (so before IEC 62368-1 3rd Edition was published) that has an example based on the IEC 60664 series standards. You will notice that the example calculates c

Re: [PSES] Clearances >30 kHz

2023-07-25 Thread John Woodgate
Remarkable difference between 29.9 kHz and 30.1 kHz! On 2023-07-25 23:39, Ryan Jazz wrote: Dear Members, Hope you can help me understand the requirement for the clearance needed between the bottom PCB of power supply to metal chassis. Looking up UL 62368-1 Third Edition, and using the

[PSES] Clearances >30 kHz

2023-07-25 Thread Ryan Jazz
Dear Members, Hope you can help me understand the requirement for the clearance needed between the bottom PCB of power supply to metal chassis. Looking up UL 62368-1 Third Edition, and using the 'Voltage up to an including peak' of 2000 V for overvoltage category II Table 10 for <30 kHz. I see

Re: [PSES] UL840 and required clearances

2020-10-12 Thread Boštjan Glavič
quired clearances Hi Boštjan, Note that clause 8 of the standard is relevant for controlled overvoltages. 8.7 states that the clearances from Table 8.1 are appropriate for circuits that are "protected for the rated impulse withstand voltage peak identified in Table 8.1. The switching test detailed

Re: [PSES] UL840 and required clearances

2020-10-12 Thread Scott Aldous
Hi Boštjan, Note that clause 8 of the standard is relevant for controlled overvoltages. 8.7 states that the clearances from Table 8.1 are appropriate for circuits that are "protected for the rated impulse withstand voltage peak identified in Table 8.1. The switching test detailed in Secti

[PSES] UL840 and required clearances

2020-10-11 Thread Boštjan Glavič
Dear experts, I hope you can help me with determination of required clearances. Product is intended for connection to 3P 480V, 60Hz system, OVCIII. After Input EMI filter (with SPD) and rectifier, unit has a resonant circuit which generates high voltages, up to 2300Vpk towards ground (PE

[PSES] UL840 and required clearances

2020-10-09 Thread Boštjan Glavič
Dear experts, I hope you can help me with determination of required clearances. Product is intended for connection to 3P 480V, 60Hz system, OVCIII. After Input EMI filter (with SPD) and rectifier, unit has a resonant circuit which generates high voltages, up to 2300Vpk towards ground (PE

Re: [PSES] POE creepage clearances

2012-11-26 Thread Joe Randolph
Hi Ian: I think the short answer to your question is that under 60950 there are no requirements for creepage and clearance distance between the Ethernet circuit and ordinary SELV circuits that are user-contactable. This is because under 60950, Ethernet is classified as an SELV circuit. There are

Re: [PSES] POE creepage clearances

2012-11-26 Thread JIM WIESE
for international safety standards which may impose creepage and Clearance distances. Also people forget there can be a lot of current coming from a shared PoE DC supply and eventhough safety requirement creepage and clearances do not apply between the high and low voltage rails it is good to impose

Re: [PSES] POE creepage clearances

2012-11-26 Thread Ron Pickard
. Best regards, Ron From: Joe Randolph [mailto:j...@randolph-telecom.com] Sent: Monday, November 26, 2012 12:43 PM To: EMC-PSTC@LISTSERV.IEEE.ORG Subject: Re: [PSES] POE creepage clearances Hi Ian: I think the short answer to your question is that under 60950 there are no requirements

Re: [PSES] POE creepage clearances

2012-11-26 Thread Joe Randolph
and Clearance distances. Also people forget there can be a lot of current coming from a shared PoE DC supply and eventhough safety requirement creepage and clearances do not apply between the high and low voltage rails it is good to impose separation so you don’t have a fire. Jim Jim Wiese Senior

Re: [PSES] POE creepage clearances

2012-11-26 Thread Ralph . McDiarmid
rpick...@equinoxpayments.com To: EMC-PSTC@LISTSERV.IEEE.ORG, Date: 11/26/2012 12:38 PM Subject: Re: [PSES] POE creepage clearances Hi Joe, I agree that an Ethernet circuit would be considered to be an SELV circuit and that would be true if the POE circuit were completely on premise generally

Re: [PSES] POE creepage clearances

2012-11-26 Thread Ron Pickard
@LISTSERV.IEEE.ORG Subject: Re: [PSES] POE creepage clearances The external DC power supply needs to be SELV too, not just energy limited. ___ Ralph McDiarmid | Schneider Electric | Solar Business | CANADA

Re: [PSES] POE creepage clearances

2012-11-26 Thread Bill Owsley
: [PSES] POE creepage clearances The external DC power supply needs to be SELV too, not just energy limited. ___ Ralph McDiarmid  |  Schneider Electric   |  Solar Business  |   CANADA  |   Regulatory Compliance Engineering

Re: [PSES] POE creepage clearances

2012-11-26 Thread Richard Nute
-electric.com ; EMC-PSTC@LISTSERV.IEEE.ORG Subject: Re: [PSES] POE creepage clearances SELV is 60 vdc but not if outdoor or wet environment - right ??? Then it drops to 30 vdc? So Ethernet is inside only for easy compliance ?? Maybe one can extend the inside environment to an outside application

[PSES] POE creepage clearances

2012-11-23 Thread Mcburney, Ian
Dear colleagues We are developing a hand held product that is powered from +48V DC over Ethernet or from an external +12V DC wall wart PSU. The maximum internal voltage will be the +48V POE. Can anyone let me know what the creepage and clearance requirements between the primary Ethernet

Re: [PSES] POE creepage clearances

2012-11-23 Thread John Woodgate
In message 7b970d3d82cee74c920c2e6b0d3b837720be4...@sn2prd0610mb358.namprd06.prod.o utlook.com, dated Fri, 23 Nov 2012, Mcburney, Ian ian.mcbur...@dmh-global.com writes: We are developing a hand held product that is powered from +48V DC over Ethernet or from an external +12V DC wall wart PSU.

Re: [PSES] POE creepage clearances

2012-11-23 Thread Mcburney, Ian
-global.com www.allen-heath.com A DMH Pro Company. -Original Message- From: emc-p...@ieee.org [mailto:emc-p...@ieee.org] On Behalf Of John Woodgate Sent: 23 November 2012 11:40 To: EMC-PSTC@LISTSERV.IEEE.ORG Subject: Re: POE creepage clearances In message 7b970d3d82cee74c920c2e6b0d3b837720be4

Re: [PSES] POE creepage clearances

2012-11-23 Thread John Woodgate
In message 7b970d3d82cee74c920c2e6b0d3b837720be5...@sn2prd0610mb358.namprd06.prod.o utlook.com, dated Fri, 23 Nov 2012, Mcburney, Ian ian.mcbur...@dmh-global.com writes: I have not started applying IEC 62368-1 as the testing agency I use has not recommend it. Is IEC 62368-1 the preferred

Re: [PSES] IEC 61010-1 (2010) Altitude Correction for Clearances

2011-12-27 Thread Richard Nute
than 3000 meters. Best wishes for the New Year! Rich -Original Message- From: emc-p...@ieee.org [mailto:emc-p...@ieee.org] On Behalf Of dougp01 Sent: Monday, December 26, 2011 2:51 PM To: EMC-PSTC Subject: IEC 61010-1 (2010) Altitude Correction for Clearances All, I am interested

[PSES] IEC 61010-1 (2010) Altitude Correction for Clearances

2011-12-26 Thread dougp01
All, I am interested to hear views of this forum on the question of altitude correction and interpolation. For the record, the highest altitude I have ever evaluated for product safety is 3,500 meters. Using IEC 664 for altitude correction, it has always been my understanding that

RE: EN 61010-1 - Clearances

2007-11-14 Thread emc-p...@ieee.org
-407-6872 Fax: 970-407-5872 From: emc-p...@ieee.org [mailto:emc-p...@ieee.org] On Behalf Of Aldous, Scott Sent: Wednesday, November 14, 2007 8:52 AM To: iun...@servomex.com; emc-p...@ieee.org Subject: RE: EN 61010-1 - Clearances Regarding Case 1 (and any other where voltages do not exceed

RE: EN 61010-1 - Clearances

2007-11-14 Thread emc-p...@ieee.org
. Is the 5V accessible? What happens if the output of the inverter is shorted to the input - are hazardous voltages per 6.3.1 accessible for any length of time? Regarding clearances from the output of the inverter to other circuits, the same basic rules apply as for Cases 1 and 2 - table 5 would

EN 61010-1 - Clearances

2007-11-13 Thread emc-p...@ieee.org
Dear All, I have three questions regarding the calculation of clearances in accordance with the requirements of EN 61010-1. Can anybody out there help please? Case 1 - Mains input transformer (230 Vac rms, Over-voltage category 2) supplies an ac to dc converter providing +15 Vdc output

Re: force deflections and clearances

2007-07-11 Thread emc-p...@ieee.org
In message 000301c7c3c3$d21b44f0$d600a...@tamuracorp.com, dated Wed, 11 Jul 2007, Brian O'Connell oconne...@tamuracorp.com writes: While we wait for the 'whenever' period to expire, does anyone know of a reasonably-priced seminar for HBSE intended for a (somewhat) experienced compliance person

RE: force deflections and clearances

2007-07-11 Thread emc-p...@ieee.org
) experienced compliance person ? Perhaps a good book ? luck, Brian -Original Message- From: emc-p...@ieee.org [mailto:emc-p...@ieee.org]On Behalf Of John Woodgate Sent: Wednesday, July 11, 2007 3:18 AM To: emc-p...@ieee.org Subject: Re: force deflections and clearances

Re: force deflections and clearances

2007-07-11 Thread emc-p...@ieee.org
In message be3336be85968d49be01e66d6e365b1e020f8...@sjc1amfpew01.am.sanm.corp, dated Tue, 10 Jul 2007, Tarver, Peter peter.tar...@sanmina-sci.com writes: 60065, while easier on the volumetric real estate budget, requires some good basic reinforcement applied to the mechanical design in the

force deflections and clearances

2007-07-10 Thread emc-p...@ieee.org
effective clearances that provide (at least) reinforced insulation. The standards are IEC 60950-1:2005 and IEC 60065:1998 (I don't have a copy of the 2001 version). In 60950-1, the method is to apply a force of 250 N using a 30 mm diameter circular plane surface. This corresponds to a pressure

Re: DERIVATION OF CREEPAGE AND CLEARANCES

2003-04-28 Thread Rich Nute
Hi Gordon: Does anyone know from where the values for creepage and clearances given in EN61010-1 (safety requirements for electrical equipment for measurement, control and laboratory use - part 1 general requirements) are derived i.e. are there other standards below 61010

Re: DERIVATION OF CREEPAGE AND CLEARANCES

2003-04-25 Thread John Woodgate
I read in !emc-pstc that Gordon,Ian ian.gor...@bocedwards.com wrote (in E1BA0362B28ED211A1E80008C71EA3060206FBB9@EXC_EAS01) about 'DERIVATION OF CREEPAGE AND CLEARANCES' on Fri, 25 Apr 2003: Does anyone know from where the values for creepage and clearances given in EN61010-1 (safety

RE: DERIVATION OF CREEPAGE AND CLEARANCES

2003-04-25 Thread FastWave
www.productsafeT.com -Original Message- From: Gordon,Ian [mailto:ian.gor...@bocedwards.com] Sent: Friday, April 25, 2003 5:11 AM To: 'IEEE EMC-PSTC GROUP' Subject:DERIVATION OF CREEPAGE AND CLEARANCES All Does anyone know from where the values for creepage and clearances given in EN61010-1

DERIVATION OF CREEPAGE AND CLEARANCES

2003-04-25 Thread Gordon,Ian
All Does anyone know from where the values for creepage and clearances given in EN61010-1 (safety requirements for electrical equipment for measurement, control and laboratory use - part 1 general requirements) are derived i.e. are there other standards below 61010 in this respect? Thanks Ian

Need help on additional clearances in IEC 60950

2000-03-18 Thread POWELL, DOUG
Hello esteemed colleagues, In IEC 60950:1999 table 2J; EN 60950:1992 table 4; UL 1950:1998 table 4 and several previous versions of each of these, I am having trouble interpreting the Additional Clearances Table, sometimes referred to as repetitive peak clearances. All these standards derive

Clearances

1999-06-23 Thread Arun Kaore
not be the premier line of defence against voltage stress breakdowns when reduced creepages/ clearances are delibrately designed in. Arun Kaore EMC Engineer ADI Limited Systems Group Test Evaluation Centre Forrester Road, St Marys, NSW 2760 P O Box: 315, St Marys NSW 1790 Tel: 61 2 9673 8375 Fax: 61 2 9673