What about Midnight SPDs?
Todd
On February 7, 2022 7:37:04 PM "Glenn Burt" wrote:
I am not seeing how ferrites can stop EMP. The frequencies involved will affect
diode junction level electronics.
Ferrites may lessen the induced surge picked up by the conductors between the
array and
has anyone successfully done this without removing the inverter from the wall?
todd
On Sunday, February 14, 2021 6:26pm, "Foxfire Energy"
said:
Fan replacement is easier than boards
Sent from my iPhone
On Feb 14, 2021, at 9:00 PM, John Blittersdorf
wrote:
Hi Ron,
Yes it is
"But the transformers are dedicated to the dc voltage and are not
interchangeable between the 12, 24, and 48 volt inverters. The turn ratios are
different."
This is valuable information Lones... thank you for stepping in and clarifying
this.
Todd
On Monday, March 9, 2020 10:08am,
I wrote to Allan off list, but will mention my suggestion here for others too.
Outback still makes and sells the 3 circuit boards for the FX series of
inverters (i just bought a spare set for our GVFX3648 for ~$800.00).
Changing 2 of the 3 cards would make this into a 48 volt inverter. The
hi bruce,
william miller has one he is going to send me.
the most this unit ever sells is 1300 watts so the 2 kW limit isn't a problem,
but because it is sealed the heat seems to kill off the internal fan in about
18 months... and it is a pain to replace.
i thought outback would sell me
i have a weird request...
i have customer with a sealed GFX-2024 who has long complained about the
internal fan's short (1.5 year) service life. i am thinking about changing this
to a vented unit but would need to buy a different top half of the fx case...
one with a hole for the fan's
i run my wifi router through this high gain panel antenna around 1/8 mile and
get 4 bars of signal strength at my security camera. wireless internet is high
frequency, so needs a clear path. this means removing tree branches and other
obstructions;
todd
[
thanks for the advice ray... this is easily 10 years old.
and while this is off the wall it will get a new internal fan and transformer
temp sensor (that failed 2 years ago).
i will look at the ac board relays when it is open too.
todd
On Monday, October 28, 2019 5:12pm, "Ray" said:
thanks for the reply jerry,
nope, no changes...
the first thing i did was to swap mates and saw the same readings. outback
customer support said they thought it was the control board (because ac boards
rarely fail), so i will do that tomorrow... but thought some wrences might have
seen this
wrenches,
i have a GVFX3648 that is acting weird,
rather then the mate normally showing:
AC <-> DC which shows the inverter's total power processing,
minus "AC load"
equals "Selling"
now the AC <-> DC shows nothing and "AC load" = "Selling" are identical (both
track the same level of
ahem... i need to correct this with my personal experience.
perhaps this is an exception, but my 24 year old sunfrost RF-12 is still going
strong, 100% problem free...
and it gets better efficiency than advertised:
it uses 390 watt hours/ day = 142 kWh/year
while solar pv is less expensive
Michael and I have noticed this kind of damage tends to be more common on shallow angled roofs. Less than 6/12 is for sure designed to fail.
todd
On Monday, August 26, 2019 2:46pm, "Michael Morningstar" said:
Todd Cory and I have seen this many times. Around here, I won’t let the bottom edge
what is the battery voltage when trying to charge? maybe the BMS says they
don't need any charging?
todd
On Saturday, August 3, 2019 2:35pm, "Mac Lewis" said:
Hi Wrenches,
I've got an issue that I'm remotely trying to troubleshoot but I must be
missing something.
Specs:
Off-grid
Dual
isn't there a formula like head in feet X gpm divided by 10 = approximate
wattage?
todd
On Wednesday, July 10, 2019 7:10pm, "Jerry Shafer"
said:
You need head (pressure) and GPM, clean degree free, no silt, a catch basin to
stall the water, big pipe long run, try to keep the
and the yellow "line tie" led should be on.
todd
On Sunday, November 11, 2018 9:30pm, "Ray" said:
I'm sure you did this, but did you set menu 9 (Inverter Setup) - Grid Usage to
"SELL" ? Its a whole separate menu heading than "Battery Selling". That was
always a bit of a pain to
On Friday, November 2, 2018 12:40pm, "Michael Morningstar"
said:
William,
When one is doing a lot of bending of rigid conduit, where the finished length
of pipe needs to be determined, after all bends are made, and threading happens
first due to bends interfering with the threading
inverters and charge controllers are another story.
todd
On Monday, June 18, 2018 10:10am, "Jerry Shafer"
said:
Wrenches
Consider distance first EMP's may damage the baypass diodes but per the testing
we have submitted to the military there was no damage to the cells modules
Jerry
" I am looking forward to the migration away from Lead Acid in the years ahead!
"
i gotta reply (off list) to this. as i have said before, i LOVE my flooded lead
calcium wet cells. no, they aren't sexy li-ons, but they are proven technology
for my grid-tied with battery backup application.
increased corrosion from chlorine gas would likely be an issue too.
todd
On Wednesday, June 21, 2017 7:53pm, "Daniel Duffield" said:
> Our go to 3M all weather pressure sensitive adhesive tape (double sided) a
> product
> called VHB and it's performance has
this might be unnecessary/ old school, but after i crimp i solder too
(oxidation happens).
todd
On Monday, November 14, 2016 1:16pm, "Ray Walters" said:
Here's the lug you would use for the inverter and batteries [
while we are seeking schematics, id love one for the array technology tracker's
control circuit. im pretty good with a soldering iron and could probably bench
repair these for my old customers... probably doable w/o the schematic, but
much easier with.
thanks,
todd
mount shasta energy
wrenches,
i did some follow-up with array technology regarding the sales and service of
home scale trackers. the good news is these services are still available (see
the forwarded message below).
todd
mount shasta energy services
On Monday, September
im not sure why i am even suggesting this, but have you tried twisting the
separate string's pairs before running them through the conduit?
todd
On Wednesday, September 7, 2016 6:55pm, "Matt Partymiller"
said:
> Thanks for all the questions and
i have bought from these folks and never had any problems.
todd
[ http://www.visionmetering.com/refurbished-electric-meters/ ](
http://www.visionmetering.com/refurbished-electric-meters/ )
On Sunday, August 21, 2016 2:13pm, "Drake"
said:
Hello
i built a system for a friend's seasonal (summer) off-grid residence in alaska.
my instructions were simple:
leave the pv input & cc output breakers "on" and the load breakers (inverter,
dc sunfrost etc) "off".
there was never a problem with winter freezing (even at -40f) until one year
whoops, was that a flag terminal? i looked at it wrong and thought it was a post terminal.
todd
On Wednesday, January 20, 2016 2:01pm, toddc...@finestplanet.com said:
On Wednesday, January 20, 2016 1:53pm, "Kristopher Schmid" said:
Greetings,
Do any of you
On Wednesday, January 20, 2016 1:53pm, "Kristopher Schmid" said:
Greetings,
Do any of you battery gurus have a suggestion for a method of removing a bolt remnant that is corroded into a flag terminal. Both sides snapped off flush with the flag. I was thinking try to
i am curious if any other wrenches install or recommend fire extinguishers in
the equipment room for their installations, particularly for battery based
systems. if so, what would be the best kind? dry chemical extinguishers make a
hell of a mess. c02 units might be better?
thanks,
todd
as i understand it agm batteries are lead calcium. my personal experience has
shown me that lead calcium is THE battery for ups systems.
to reiterate previous emails about this:
i have two grid tied systems here at home, both with battery backup (outback
gvfx series) inverters. one has 1986
except, "let it melt" on shallow angle roof mounts often yields this:
todd
On Wednesday, December 9, 2015 1:48pm, "Benn Kilburn" said:
Dana,
SESA (Solar Energy Society of Alberta) has been providing a great service to anyone interested in Solar Energy for many
benn,
yes, this has happened to me on two sites (until i learned this type of mount does not work). one had mitsubishi modules and another evergreen modules. other colleagues here have had these painful "learning opportunities" too. both of these jobs were for customers who insisted on roof,
worst case scenario, a battery based inverter system trying to power the grid
would immediately shutdown on overload as the "infinite load" of the grid would
look like a dead short.
also, all utility workers treat lines as "live" and routinely short out feeders
before working on them... so
i have a set of their fc420's flooded, lead calcium... which is (imo) the
perfect battery for grid tie with battery backup. i add water every other year,
and equalize every 6 months. these are from 2008 and still going strong.
another system i have has a 1986 vintage set (made by "globe
afaik the first example of "AC coupling" was when one of these "trace
microsines" was plugged into the off grid system (sw4024?) at richard perez's
home back in ~1995?
todd
On Thursday, September 17, 2015 4:54pm, "b...@midnitesolar.com"
said:
>
> Yep. The
i have had this happen, but only with one very elderly customer who didnt know
what he was doing. he is 93 now, and has wisely hired a neighbor to maintain
his system.
having people press buttons who dont understand their function or correct
settings is a recipe for problems. a ruined
sadly, all we have left is hopium
On Monday, June 29, 2015 12:36pm, Kirk Herander k...@vtsolar.com said:
Here’s the reply I just got back from Solaredge:
“As this stands ATM Tesla has only announced the product, not finished
developing it. As Tesla finalizes it the details will
wow, engenius. thanks for posting this.
[ http://connectder.com/products ]( http://connectder.com/products )
todd
On Monday, May 25, 2015 4:48pm, John Blittersdorf
john.blittersd...@gmail.com said:
Bill,
One clean way to do it would be to use a ConnectDER, but the max input is
but under a surge like a lightning strike wouldn't the diodes open rather than
short?
i always considered the pv's to be the least likely thing to be damaged from
lightning and inverters and charge controllers (electronics) to be the most
vulnerable. what in a pv would fail? an intercell
and if you do, please report back to the list with your experiences with them
as pole mounts are mostly what i do.
todd
On Wednesday, May 20, 2015 3:16pm, Mac Lewis maclew...@gmail.com said:
Hi Richard,
A relatively new pole mount racking manufacturer called MT Solar has a pole
mount
this is more cornucopian bullshit... trying to avoid finite planet realities... like the solar roadway nonsense that was circulating ~6 months ago. the sad part is so few people understand that.
todd
On Saturday, May 2, 2015 4:25pm, "Dan Fink" danbo...@gmail.com said:
UN-fortunately I predict
drill a tiny hole in the delivery line at the top of the casing, so when the
water is not pumping it will empty into the well... yes, some will leak when
the pump is running but the only other non-automatic option is a seasonal
drain valve.
todd
On Wednesday, April 8, 2015 7:47pm, Mac
two words... "pole mounts"
todd
On Friday, March 27, 2015 10:11am, "Kristopher Schmid" sol...@legacysolar.com said:
Ignoring the effect of roofing material friction and tilt angle, i would surmise that the array being "open-backed" would reduce heat build up and actually decrease the snow
my old whisper controller has 3, full wave bridge rectifiers (with capacitors
in parallel) connected to the wild, 3 phase ac input... and a 4 way light
switch used to short out the three wild ac legs for the brake. should be easy
to build one.
todd
On Friday, February 6, 2015
im not sure how the "brand-x" inverters work, but my home system's gvfx3648 suffers from high line voltage, where often when selling at max, the line voltage at the inverter will creep up to the 130 vac limit. when this happens, the inverter doesn'tcycle off and on as suggestedbelow, but it
the 2:1 transformer also offers ac isolation. im not so sure id want the hot
line of 120vac, via a diode, on the dc part of a system.
this configuration (known as the DT Kludge) was a common (and expensive)
workaround for outback fx series inverters which unfortunately only had one ac
input.
try digikey or mouser electronics
todd
On Monday, October 20, 2014 1:51pm, Corey Shalanski
cshalan...@joule-energy.com said:
Wrenches,
Since my previous post (see below) we have recovered the faulty modules and are
now looking to replace the diodes in order to make them functional
If you are not going to be using a PV-direct arrangement, there is not much
advantage in using the Flex pumps.
except efficiency. i have two wells at home and the grundfos sqflex pumps 50'
of additional head at the same flow rate, using 30% less energy as compared to
the standard, 3/4 hp
perhaps i am not understanding the set-up, but why feed a ups with a ups?
doesnt the sunny island already provide ups capabilities for the loads
connected to it?
todd
On Sunday, October 12, 2014 7:40am, Tump t...@swnl.net said:
Thats the best fix I've heard yet!
Document then DUMP
this is where i get mine:http://www.visionmetering.com/products/refurbished-electric-meters/
On Monday, September 29, 2014 7:12am, "Christopher Warfel" cwar...@entech-engineering.com said:
Bill, The refurbished utility meter is the lowest cost option that meets the requirements of accuracy for
i saw a commercial unit doing this here in mountshasta about 12 years ago.
the gas (from gasified wood) was fed into a ford engine, which turned a dc
generator charging a small buffer bank of batteries. a standard trace sw4024
did the selling to the grid. the grid interface was the easy part.
perhaps i'm just an old school old fart, but i still think flooded, lead
calcium cells are the best solution for battery back-up grid ties. i have a set
from 1986, replaced when they ended their 20 year service life from our local
hydroelectric plant... still going strong. i am also finding
i have the same thing in my greenhouse...
on a 24 volt dc system, i wired in a switch to change my two fans from parallel
(noisy and excessive air movement) to series. i run them in series 99% of the
time... plenty of air, less noise and long life on the brushes. (of course this
is only an
In any case, a 10 kW battery system, will probably exceed most grid connected
battery systems, and the whole issue is moot.
shouldnt battery capacity be in kWh?
todd
On Wednesday, July 2, 2014 5:00pm, Christopher Warfel
cwar...@entech-engineering.com said:
I am not familiar with
here is the direct link:
http://enphase.com/global/files/Enphase_Application-Note_AC-Coupled-Battery-Based-Systems.pdf
On Thursday, May 29, 2014 10:21am, Nick Soleil nsol...@enphaseenergy.com
said:
Hi Drake,
I'm happy to discuss the ins-and-outs of this with you by phone. My
not trying to be dumb here, but what's the attraction to lithium ion batteries?
todd
On Thursday, February 27, 2014 3:44pm, Larry Crutcher, Starlight Solar Power
Systems la...@starlightsolar.com said:
Jay,
I'm an authorized dealer of GBS systems and we stock and sell them here in
to further complicate things, i have seen regulator oscillation problems with
2 in series.
todd
On Monday, February 17, 2014 2:30pm, Ray Walters r...@solarray.com said:
Alot of these generator setups need 2 regulators, so usually the regular
one stays at the tank, size the
this is good advice, but beware: if you set the time too low, the inverter will
never go to sleep. this is an issue with grid tie units where you do not want
the inverter wasting power, running all night long.
todd
On Tuesday, February 11, 2014 7:03am, Doug Wells
i would love to see a spectrum analyzer's view of the fx's harmonics. does
anyone have this available?
interesting (and sad) how silent outback is on this list now.
todd
On Monday, February 10, 2014 9:37pm, Exeltech exelt...@yahoo.com said:
Bruce,
The capacitors may or may not
the only ones i have on a dimmer are in the bathroom and they flicker. being we
are grid tied (GVFX-3648) and the grid is up, i suspect this is because of a
bad dimmer/lamp combo.
anyone find the RFI from led lamps a problem? i have to shut all mine off when
using the 2 meter ham rig.
todd
i remember hearing there was one brand which had a tiny hydro generator,
operated by the flowing water, which was used to light the burner... yet, no
one mentioned them?
todd
On Tuesday, October 1, 2013 5:48am, Bill Loesch solar1onl...@charter.net
said:
Hi Dick,
Following
whoops... i think so. thanks for the correction!
todd
On Friday, September 27, 2013 4:32pm, August Goers aug...@luminalt.com said:
Here's a good place to go to find mileage:
[http://www.fueleconomy.gov/feg/Find.do?action=sbsid=32557]
a good guesstimate is 3 to 4 kWh/mile
todd
On Friday, September 27, 2013 3:05pm, Ray Walters r...@solarray.com said:
We did a charging station for a Chevy Volt earlier this year. We
actually ran the charger for about a week to come up with the design,
based on their
As SCE wrote in a July memo for solar and storage contractors
([https://www.sce.com/wps/wcm/connect/7bfb9fcc-b277-4646-9ac2-7700e03914bf/Battery_Backed_Storage_NEM_Eligibility.pdf?MOD=AJPERES]
PDF), “if a renewable generator is modified so that the battery storage system
is integrated into the
thanks for the ideas jay!
the fan comes on and off with the aux output led on the board where the in/out
ac wires connect, so i do not believe this is an issue with the fan.
as i mentioned below:
when i set the aux control from 'auto' to 'on' the fan comes on and stays on...
well,
wrenches...
im having a vexing problem with an outback system and cannot seem to get any
help from outback... so, im posting this here in hopes some wrench knows more
about the 'cool fan' option than i do.
this is a sealed gtfx2524 system... so it has the 'turbo fan' connected to the
off-grid systems where the loads are enormous,
i realize this is not popular now in these days of solar is so cheap, but i
will not work for people who wont conserve or be efficient.
as we all know, pv contains lots of embedded energy and to my thinking...
having it power waste is simply
If the customer wants a mega system and is willing to pay for
it, why is it our business to judge them?
hi ray,
is it judging them? or simply saying:
i do this work because i believe in trying to make a more sustainable world...
and i will not enable waste. i do not care what these
so sorry list members, this was supposed to be off list.
todd
On Friday, August 16, 2013 8:51pm, toddc...@finestplanet.com said:
If the customer wants a mega system and is willing to pay for
it, why is it our business to judge them?
hi ray,
is it judging them? or simply saying:
inefficient? they are better then lead antimony, but are considered 'shallow
cycle', so i never take them down more than 50%.
todd
On Thursday, July 18, 2013 5:44am, Drake
drake.chamber...@redwoodalliance.org said:
Are they too inefficient for off grid?
Drake
At 05:53 PM
for standby (bbgt) systems, please consider wet cell lead calcium cells. i have
a 23 year old set still going strong.
lead antimony will go 12 years... if you are lucky!
todd
On Wednesday, July 17, 2013 2:06pm, Drake
drake.chamber...@redwoodalliance.org said:
snip
They have been a
im looking for a spare set of brushes (i assume you mean slip ring assembly)
too.
todd
On Thursday, June 20, 2013 5:47pm, Mac Lewis maclew...@gmail.com said:
Hello Wrenches,
Does anyone know of a way to get Whisper 100 parts? Specifically, I need a
full brush assembly. Please
so it might be possible to power the pump array direct and also charge
batteries through a hv mppt charge controller at the same time??
todd
On Wednesday, June 5, 2013 8:18pm, jay peltz j...@asis.com said:
Hi Todd
As bob-0 and Larry have said
And the sqflex is a mppt unit,
ok wrenches... here is a hair brained idea i came up with.
i have this customer with the grundfos pump being powered, array direct by 10
astropower 75's in series... so around 170 vdc.
what would happen if a hv mppt charge controller were paralleled with the panel
output feeding the pump?
my experience mirrors this too. this was my first ac module installation and
other than dpw screwing up the mount, and the clunky datalogger/internet
interface, the system has performed flawlessly.
todd
On Friday, May 31, 2013 6:28am, Dave Palumbo d...@independentpowerllc.com
said:
good point dan... i wonder how frameless modules are intended to be mounted?
todd
On Thursday, May 30, 2013 4:00pm, Exeltech exelt...@yahoo.com said:
I agree with Allen, and would like to add a related comment. Foam boards are
thermally insulative in nature. If affixed to the PV
We were hired just to install the system by a local firm that designed and
sold the system and have had a bear of a time getting paid from anyone.
this is why i never touch materials i do not sell, or install designs i did not
do.
todd
On Tuesday, May 7, 2013 10:57pm, Jesse Dahl
wrenches,i have a customer who is wanting to add more modules to an existing
array. he currently has isofoton 150/S/24s which are 41.25 X 48.25. does
anyone have any possibilities on where to find 6 of these?thanks,todd
Sent from Finest Planet WebMail.
this is probably a hair brained question, but has anyone ever tried paralleling
the connections within the series strings?
yes, more cables, but might this reduce the multiple parallel string
unbalancing issues?
todd
On Monday, April 29, 2013 3:53pm, Wayne Irwin
our power outages generally come from bad weather too... and of course when the
weather is bad the pv does next to nothing. so for emergency backup, i
recommend a generator.
todd
On Friday, April 26, 2013 10:33am, Bill Turberville billt...@ece-llc.com
said:
Not very often, and
this is an incorrect myth.
todd
On Friday, April 26, 2013 12:30pm, Bill Turberville billt...@ece-llc.com
said:
Batteries actually do better if they are cycled than if they just sit there.
He may actually extend his battery life. What kind of batteries is he using?
From:
my biggest issue with bbgt systems is the inefficiency. my 4.3 kW (stc) array
typically sells 2.8 kW.
5 years of tracking dc input versus ac output shows the obfx inverter runs
around 87% efficiency. add battery maintenance and the extra wiring to split
off backed up loads and the economics
please... and id love to see the harmonics too!
thanks,
todd
On Tuesday, April 16, 2013 5:19pm, Chris Mason cometenergysyst...@gmail.com
said:
If it is useful to you, I can grab a waveform from my scope connected to my
outback and post it.
On Tue, Apr 16, 2013 at 3:27 PM, All
the customer had some guy come in with 'a meter'. there was no mention of
frequency or scale for the ranges listed below. and of course... the man with
the meter also sells the 'filters' which help the problem he finds - sigh. here
is the pertinent paragraph in her letter to me:
As you know,
i wish i knew what this guy was measuring... rfi, emi, emf, af? it could even
be the pwm off the fm80.
i dont think an inverter could change any emf to the house as that (gauss) is
dependent on current flow. but if there is some rfi from the inverter/cc,
riding the 60 hZ ac cables... that
in addition, i am looking for a spare blade set for the same unit (whisper
100). i heard there was a warehouse full of these parts when swwp went out of
business... why they dont answer emails or phone messages is a mystery. i'd
think they would want to sell what they can. if anyone has any
here is the link:
[http://www.luminousrenewable.com/] http://www.luminousrenewable.com/
On Friday, April 5, 2013 2:00pm, Roy Butler r...@four-winds-energy.com said:
The Whisper line, at least the 200 and 500, went to Luminous, a large
battery manufacturer in India.
when i have seen this (battery post melting) in the past it was from a faulty
(high resistance) battery connection... usually a poorly crimped lug.
todd
On Monday, March 25, 2013 9:15am, SunHarvest e...@harvesthesun.com said:
Larry,
Thanks for your reply. For some reason the
i have set up wireless bridges for ip to remote locations and my experience
with this has me leaning towards no dice william.
these links run in the 2.3 gHz and up range which is line-of-sight only. trees
will even attenuate the signal, so total blockage with the earth looks grim.
have a
about 10 years ago - after a particularly heavy duty (more than usual) mount
shasta snow storm, the county raised the snow load specifications here from
40#/sq ft to 60#/sq ft... which made all existing roofs substandard, so while
they are grandfathered in, adding 2 to 3 #/sq ft for solar
it sounds like my experience with this company about 10 years ago when i
installed one of their 8 kW units as a grid back up for a customer. the battery
charger was wired wrong out of the box... and they would not help me with
troubleshooting... so i figured it out on my own. about 6 months
wrenches,
i am working on a design for an off grid camp. they need a new generator as the
one they have is a total pos.
i am interested in suggestions for a commercial grade, 10 to 15 kW propane
fueled unit. are kohler and onan still the best thing going or am i living in
the past?
or heavy snow... the supports are clear out on the ends.
todd
On Friday, January 18, 2013 5:09pm, Chris Daum ch...@oasismontana.com said:
So how does the Zep stuff's testing do in winds in excess of 100 mph?
I saw a nice demo and display of their goods in at the Anaheim 2009 SPI,
one of my biggest gripes about the outback fx series is only one ac input...
this was a major step backwards from its trace sw series predecessor.
if someone is going to want battery back up on a grid tied system, they surely
are going to want the ability to back that up with a generator. the
how about wisely locating the rf in a non-heated space to reduce/eliminate the
winter run time?
todd
On Wednesday, January 9, 2013 12:22pm, Dave Palumbo
d...@independentpowerllc.com said:
Howie,
I usually agree to the Kenmore/Sears recommendation but the closest Sears is
coming
i have done this on a particularly problematic installation here in our heavy
mount shasta snow country - where the deep snow would freeze to ice on the
module, and as it crept down the array, it would peel off the bottom edge of
the module frame, usually resulting in broken glass/destroyed
no experience with this, but led lights pretty much wipe out 2 meter operations.
todd
On Sunday, December 23, 2012 7:31am, Lee Bristol
leebris...@standardsolar.com said:
Mr Friends,
Does anyone have experience with Enphase 215 inverters on a roof interfering
with a Ham radio
this brings up a probably off topic subject regarding efficiency. i have always
considered efficiency and conservation to be job one... especially on off grid
systems... but with modules so inexpensive... does this still make sense? for
example, i have an off grid customer who i suggested get
here in mount shasta woo-woo land, there are loads of folks who hate
fluorescent lighting (never mind that they never notice fixtures with cfl's in
them). they are all smiley though about leds (go figure).
my experience with leds is the lumens/watt is still no greater than a good
cfl/hid
I have never had good results with roof mounted pv in our heavy (mount shasta)
snow area. the snow tends to creep down the glass and peel the bottom of the
frame off the module... and then the glass breaks as it has no support in that
area.
so, around here... i do pole mounts WAY up in
the engineering called for 8 sch 80... and some super strong rebar in the
base. i subbed out the mount so dont have all the details easily accessible...
but if i recall, the hole is like 6' deep and 5 feet square. it seemed
inadequate to me, but it was engineered, so i guess good to go.
todd