Re: [RE-wrenches] Enphase Gateway causing lamp to flicker

2023-12-12 Thread John Blittersdorf via RE-wrenches
My guess is that the lamp is too sensitive. I find that the cheapest LED bulb from home depot flicker whether using inverter power or generator power. All other LEDs in the house work fine. Like a fool, I keep buying the cheap ones. I totally agree with Andrew " While I can understand the need

Re: [RE-wrenches] Enphase Gateway causing lamp to flicker

2023-12-11 Thread August Goers via RE-wrenches
d center so > you can put a filter on the feeder to that subpanel. > > > > William > > > > *From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On > Behalf Of *AE Solar via RE-wrenches > *Sent:* Monday, December 11, 2023 6:56 AM > *To:* RE-wrenches

Re: [RE-wrenches] Enphase Gateway causing lamp to flicker

2023-12-11 Thread Solar Energy Solutions via RE-wrenches
you can put a filter on the feeder to that subpanel. William From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of AE Solar via RE-wrenchesSent: Monday, December 11, 2023 6:56 AMTo: RE-wrenchesCc: AE SolarSubject: [RE-wrenches] Enphase Gateway causing lamp to flicker

Re: [RE-wrenches] Enphase Gateway causing lamp to flicker

2023-12-11 Thread William Miller via RE-wrenches
-wrenches] Enphase Gateway causing lamp to flicker Wrenches We have a project where the homeowner has some of those bedside lamps where you touch them to turn them on/off/dim (rather than having a switch). It seems like when the Enphase Gateway is powered up it causes the lights to freak out. Once we

[RE-wrenches] Enphase Gateway causing lamp to flicker

2023-12-11 Thread AE Solar via RE-wrenches
Wrenches We have a project where the homeowner has some of those bedside lamps where you touch them to turn them on/off/dim (rather than having a switch). It seems like when the Enphase Gateway is powered up it causes the lights to freak out. Once we flip the breaker to the Gateway off the lamp

Re: [RE-wrenches] Enphase failure

2023-04-13 Thread Jason Szumlanski via RE-wrenches
There's always the Cellular connection option (if available there). Jason Szumlanski Principal Solar Designer | Florida Solar Design Group NABCEP Certified Solar Professional (PVIP) Florida State Certified Solar Contractor CVC56956 On Thu, Apr 13, 2023 at 9:01 AM Jay via RE-wrenches <

Re: [RE-wrenches] Enphase failure

2023-04-13 Thread Jay via RE-wrenches
A follow up on this I talked to a buddy at a large company that installs enphase. He said the issue is that the firmware fails without the web for updates. He’s seen it lots of times. Which means this project will have to get web connected to hopefully fix it. I haven’t found in the

Re: [RE-wrenches] Enphase failure

2023-04-12 Thread rick--- via RE-wrenches
Jay, What’re you seeing with the Enphase Toolkit? rick brown SolShine Energy Alternatives, LLC Electrical & Solar Contracting Services www.SolShineEnergy.com O: 540.235.3095 M: 540.808.9502 VA Class A Contractor Lic# 2705147660 VA Master Electrician Lic# 2710062762 VA Alternative Energy Systems

[RE-wrenches] Enphase failure

2023-04-12 Thread Jay via RE-wrenches
Hi all I’m just starting to try and figure out a failed enphase system that was just noticed to be off line a few days ago. 12 x IQ7A 400 watt panels The install is 20’ from the main transformer/load center. 1000 amp commercial panel There is no monitoring because they couldn’t get cat 5

Re: [RE-wrenches] Enphase ACM to rail mount plate

2023-02-24 Thread Jason Szumlanski via RE-wrenches
What Mac is saying is there is no metal flange on the microinverters that are attached to AC modules. They just snap into a plastic flange adhered to the backsheet. It's just a plastic case with no way to attach it to rails or a panel frame. William's solution requires a microinverter with a

Re: [RE-wrenches] Enphase ACM to rail mount plate

2023-02-23 Thread James Rudolph via RE-wrenches
Hey Mac, If you have rails beneath the module wouldn't it be easier to mount an inverter there with a bolt that fastens to rail? William's solution looks great, but I thought to ask because this would be cheaper and easier to wire. Have a great day everyone  James B. Rudolph Independent

Re: [RE-wrenches] Enphase ACM to rail mount plate

2023-02-23 Thread Jason Szumlanski via RE-wrenches
millersolar.com >> >> CA Lic. 773985 >> >> >> >> >> >> *From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On >> Behalf Of *Mac Lewis via RE-wrenches >> *Sent:* Thursday, February 23, 2023 9:56 AM >> *To:* RE-wrenc

Re: [RE-wrenches] Enphase ACM to rail mount plate

2023-02-23 Thread Mac Lewis via RE-wrenches
; > CA Lic. 773985 > > > > > > *From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On > Behalf Of *Mac Lewis via RE-wrenches > *Sent:* Thursday, February 23, 2023 9:56 AM > *To:* RE-wrenches > *Cc:* Mac Lewis > *Subject:* [RE-wrenches] Enphase

Re: [RE-wrenches] Enphase ACM to rail mount plate

2023-02-23 Thread William Miller via RE-wrenches
*From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On Behalf Of *Mac Lewis via RE-wrenches *Sent:* Thursday, February 23, 2023 9:56 AM *To:* RE-wrenches *Cc:* Mac Lewis *Subject:* [RE-wrenches] Enphase ACM to rail mount plate Hello Wrenches, We are in the middle of planning

[RE-wrenches] Enphase ACM to rail mount plate

2023-02-23 Thread Mac Lewis via RE-wrenches
Hello Wrenches, We are in the middle of planning for a full solar panel replacement at a house with AC modules. It was a Solaria 355 with an Enphase IQ7+. Solaria is going to replace the modules with a standard module, not an AC module (MC4 cabling not an Q Cable to J-box). This seems OK but

Re: [RE-wrenches] Enphase consumption data

2022-12-21 Thread Jason Szumlanski via RE-wrenches
It is my understanding that you cannot have the consumption CTs enabled without the production CT enabled. When the solar is connected on the load side of the consumption CTs as it is in this case, the production CTs are required to make the math work. It cannot use the microinverter readings for

[RE-wrenches] Enphase consumption data

2022-12-20 Thread Dave Tedeyan via RE-wrenches
Hi All, I have a system where the solar panels (with Enphase IQ8) are on a detached garage and the IQ gateway is in the house. The gateway is in the house so that it can gather consumption data, and there is an internet connection there. There are other loads in the garage, so it is impossible to

[RE-wrenches] Enphase IQ8 to ESS Ratio

2022-12-06 Thread Jason Szumlanski via RE-wrenches
I have seen in press releases that there is no limit to the number of IQ8 microinverters on the roof relative to the battery size. I can't remember if I saw this in Enphase marketing or directly in the documentation. But in reality, there is a limit. It's 64A of inverter output current since the

Re: [RE-wrenches] Enphase

2022-09-26 Thread August Goers via RE-wrenches
We're still installing Tesla Powerwalls in the SF Bay with good results. I perform price and feature comparisons from time to time and find that most other manufacturers are still playing catchup with the Powerwall. We're also experimenting with the Powerwall+ system which is significantly cheaper

Re: [RE-wrenches] Enphase

2022-09-26 Thread Jason Szumlanski via RE-wrenches
I only leave for Cat 5. Haha. In all seriousness, I feel some level of obligation to be here as an "essential worker" in situations like this. I'm 2 hours south of Tampa, we will get wet, but the winds shouldn't be anything close to Irma 5 years ago. I have confidence in the Enphase systems

Re: [RE-wrenches] Enphase

2022-09-26 Thread MDElectricSolar via RE-wrenches
After installing 4 or 5 of them I avoid them, too complicated, too many comm issues, too many hours on the phone with tech support, too many days wasted with no compensation. Michael D Nelson MD Electric & Solar, Inc. 707-684-0064 mobile 707-884-1862 office www.mdelectricsolar.com

Re: [RE-wrenches] Enphase

2022-09-26 Thread Kirk Herander via RE-wrenches
Get out of there dude, my brother lives in Tampa I told him to do the same thing. On Mon, Sep 26, 2022 at 7:30 PM Jason Szumlanski via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > I should probably write this in 48 hours after Hurricane Ian passes by > here. But I'll give you a

Re: [RE-wrenches] Enphase

2022-09-26 Thread Jason Szumlanski via RE-wrenches
I should probably write this in 48 hours after Hurricane Ian passes by here. But I'll give you a couple of personal opinions. Complicated? No. It's pretty dead simple since there is no DC aspect to consider. But there are a lot of little things, I'll call them quirks, to learn and understand to

[RE-wrenches] Enphase

2022-09-26 Thread Drake Chamberlin via RE-wrenches
Hello All, Looking into the Enphase Ensemble system, I'm not sure that is a direction I want to take. It seems that they are extremely complicated and require a 30 hour training course to commission. Once installed, are they reliable? Do they require on going tweaks and firmware upgrades?

[RE-wrenches] Enphase IQ8+ max continuous output

2022-08-11 Thread Carl Adams via RE-wrenches
Hello Wrenches, I am having an issue with a utility submission. We are using the IQ8+ on the project. The SolarEdge Spec sheet shows 0.290 kW as max continuous output. The utility rejected this saying they are using 0.298 kW based on the CA energy commission rating. Looking for clarification

Re: [RE-wrenches] Enphase String Breaker Heating Up

2022-08-05 Thread Richard Scott via RE-wrenches
Check the breaker screw length and threads of the bus bar. I have seen where either the screw is just slightly too long and bottoms out or the threads don't go all the way down. This causes the screw to be able to pass the torque test but in reality it's not fully applying pressure to the breaker

Re: [RE-wrenches] Enphase String Breaker Heating Up

2022-08-04 Thread Darryl Thayer via RE-wrenches
Hello, breakers are thermal-magnetic the current heats the breaker; if the current is high enough for long enough, a solder pot inside melts; this current and excessive heat causes other breakers to open Are you sure the string current is less than 80% of the breaker rating and the wire

Re: [RE-wrenches] Enphase String Breaker Heating Up

2022-08-04 Thread Jay via RE-wrenches
Seems to me this has come up before. With bad breakers as probable cause. I don’t know if the heat has caused buss damage Might go for CH or QO breakers instead BR style. Jay > On Aug 4, 2022, at 8:08 PM, Jerry Shafer via RE-wrenches > wrote: > >  > Jason > Is the installation designed

Re: [RE-wrenches] Enphase String Breaker Heating Up

2022-08-04 Thread Jerry Shafer via RE-wrenches
Jason Is the installation designed for 208 as you have greater limitations then 240, so now replace the buss and all the breakers, after that run currents tests and see what you have. I had a 3 phase that the tin cam off the buss and looked like a plazma cutter due to the exposed aluminum Fun

Re: [RE-wrenches] Enphase Max Distance

2022-07-26 Thread Mac Lewis via RE-wrenches
ement System >> <https://enphase.com/en-us/products-and-services/envoy> >> NABCEP Certified Solar PV Installer #03262011-300 >> California C10 Licensed Electrician #986315 >> >> -- >> *From:* RE-wrenches on >> behalf o

Re: [RE-wrenches] Enphase Max Distance

2022-07-26 Thread rick--- via RE-wrenches
ia > RE-wrenches <mailto:re-wrenches@lists.re-wrenches.org>> > Sent: Thursday, July 21, 2022 3:53 PM > To: RE-wrenches <mailto:re-wrenches@lists.re-wrenches.org>> > Cc: r...@solshineenergy.com <mailto:r...@solshineenergy.com> > mailto:r...@solshineenergy.com>>

Re: [RE-wrenches] Enphase Max Distance

2022-07-25 Thread Mac Lewis via RE-wrenches
rom:* RE-wrenches on behalf > of rick--- via RE-wrenches > *Sent:* Thursday, July 21, 2022 3:53 PM > *To:* RE-wrenches > *Cc:* r...@solshineenergy.com > *Subject:* [RE-wrenches] Enphase Max Distance > > EXTERNAL EMAIL - Use caution when responding, clicking, and/or downl

Re: [RE-wrenches] Enphase Max Distance

2022-07-25 Thread Nick Soleil via RE-wrenches
11-300 California C10 Licensed Electrician #986315 From: RE-wrenches on behalf of rick--- via RE-wrenches Sent: Thursday, July 21, 2022 3:53 PM To: RE-wrenches Cc: r...@solshineenergy.com Subject: [RE-wrenches] Enphase Max Distance EXTERNAL EMAIL - Use cautio

[RE-wrenches] Enphase Max Distance

2022-07-21 Thread rick--- via RE-wrenches
Wrenches, What is the furthest that anyone has placed their IQ-based system from the gateway? Enphase recommends up to 250’. We’ve done ~350’ without issue. Anyone gone further? Thanks in advance. rick brown SolShine Energy Alternatives, LLC Electrical & Solar Contracting Services

Re: [RE-wrenches] Enphase IQ7 versus IQ8

2022-07-13 Thread Drake Chamberlin via RE-wrenches
Certified Solar PV Installer #03262011-300 California C10 Licensed Electrician #986315 - From: RE-wrenches on behalf of Jay via RE-wrenches Sent: Tuesday, July 12, 2022 3:54 PM To: RE-wrenches Cc: Jay Subject: Re: [RE-wrenches] Enphase IQ7 versus IQ8 EXTERNAL EMAIL - Use

Re: [RE-wrenches] Enphase IQ7 versus IQ8

2022-07-12 Thread Jason Szumlanski via RE-wrenches
s on behalf > of Jay via RE-wrenches > *Sent:* Tuesday, July 12, 2022 3:54 PM > *To:* RE-wrenches > *Cc:* Jay > *Subject:* Re: [RE-wrenches] Enphase IQ7 versus IQ8 > > *EXTERNAL EMAIL* - *Use caution when responding, clicking, and/or > downloading attachments.* > > &g

Re: [RE-wrenches] Enphase IQ7 versus IQ8

2022-07-12 Thread Nick Soleil via RE-wrenches
11-300 California C10 Licensed Electrician #986315 From: RE-wrenches on behalf of Jay via RE-wrenches Sent: Tuesday, July 12, 2022 3:54 PM To: RE-wrenches Cc: Jay Subject: Re: [RE-wrenches] Enphase IQ7 versus IQ8 EXTERNAL EMAIL - Use caution when resp

Re: [RE-wrenches] Enphase IQ7 versus IQ8

2022-07-12 Thread Jay via RE-wrenches
E-wrenches >> Sent: Tuesday, July 12, 2022 11:38 AM >> To: RE-wrenches >> Cc: Jason Szumlanski >> Subject: [RE-wrenches] Enphase IQ7 versus IQ8 >> >> >> >> I am trying to figure out why it is a good idea we use the IQ8 in anything >> other than a

Re: [RE-wrenches] Enphase IQ7 versus IQ8

2022-07-12 Thread Jason Szumlanski via RE-wrenches
via RE-wrenches > *Sent:* Tuesday, July 12, 2022 11:38 AM > *To:* RE-wrenches > *Cc:* Jason Szumlanski > *Subject:* [RE-wrenches] Enphase IQ7 versus IQ8 > > > > I am trying to figure out why it is a good idea we use the IQ8 in anything > other than a solar only backup

Re: [RE-wrenches] Enphase IQ7 versus IQ8

2022-07-12 Thread Mark Frye via RE-wrenches
Do you need the additional switch if you use the Enphase battery? From: RE-wrenches On Behalf Of Jason Szumlanski via RE-wrenches Sent: Tuesday, July 12, 2022 11:38 AM To: RE-wrenches Cc: Jason Szumlanski Subject: [RE-wrenches] Enphase IQ7 versus IQ8 I am trying to figure out why

[RE-wrenches] Enphase IQ7 versus IQ8

2022-07-12 Thread Jason Szumlanski via RE-wrenches
I am trying to figure out why it is a good idea we use the IQ8 in anything other than a solar only backup scenario. If there are Enphase batteries involved, wouldn't the IQ7 do the same job on the roof? In a straight grid tied scenario, again the IQ7 would do the exact same thing. You would not

Re: [RE-wrenches] Enphase production CT with Sunpower PVS5

2022-07-01 Thread Nick Soleil via RE-wrenches
Hi Dave, I don’t know the specifications of the PVS6 production CT, but it is highly unlikely that it is a mA CT with 2000:1 winding ratio like the Enphase production CT. You should try to source a Sunpower CT. Nick Soleil Sr Product Manager Enphase Energy 707-321-2937 On Jul 1, 2022, at

[RE-wrenches] Enphase production CT with Sunpower PVS5

2022-07-01 Thread Dave Tedeyan via RE-wrenches
Hi All, I am expanding on an existing Sunpower system, with non Sunpower equipment (SMA inverters). In order to get their consumption monitoring to work properly, I would like to install a production CT for the PVS5. Does anyone know whether you can use an Enphase production CT with a Sunpower

[RE-wrenches] Enphase

2022-04-15 Thread Jay via RE-wrenches
I’ve been following the enphase thread. I’ve used AP systems before and so far reliable and much less expensive. Their new DS3 inverters are much less expensive and larger capacity But to the point of starting voltage MPPT range and watts DS3 voltage range: DS3 S/L 16-60v, DS3 26-60v MPPT

Re: [RE-wrenches] Enphase Legacy micro replacement

2022-04-15 Thread Kirk Herander via RE-wrenches
Thanks that is exactly my request to Enphase, that they verify software compatibility. On Fri, Apr 15, 2022 at 12:48 PM Jason Szumlanski via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > Kirk, > > We have seen many of the conversion kits not work out of the box. I > believe it is a

Re: [RE-wrenches] Enphase Legacy micro replacement

2022-04-15 Thread Jason Szumlanski via RE-wrenches
Kirk, We have seen many of the conversion kits not work out of the box. I believe it is a firmware/software mismatch issue. If you call Enphase, ask them to make sure the Envoy software is compatible with the conversion kit microinverter and update all software. This should resolve the issue.

[RE-wrenches] Enphase Legacy micro replacement

2022-04-15 Thread Kirk Herander via RE-wrenches
I have been dealing with a legacy Enphase system ever since the installation about 11-12 years ago. And I stopped using Enphase after the massive failure rate of these first gen M190 inverters. Almost all of them have been replaced at least once, the good news is I only have about -15- of the

Re: [RE-wrenches] Enphase IQ8

2022-04-14 Thread Jason Szumlanski via RE-wrenches
gt;> California C10 Licensed Electrician #986315 >>> >>> -- >>> *From:* RE-wrenches on >>> behalf of Marco Mangelsdorf via RE-wrenches < >>> re-wrenches@lists.re-wrenches.org> >>> *Sent:* Thursday, April 14, 2022 8

Re: [RE-wrenches] Enphase IQ8

2022-04-14 Thread Nicholas Welch via RE-wrenches
wrenches on >> behalf of Marco Mangelsdorf via RE-wrenches < >> re-wrenches@lists.re-wrenches.org> >> *Sent:* Thursday, April 14, 2022 8:25 AM >> *To:* RE-wrenches >> *Cc:* Marco Mangelsdorf >> *Subject:* [RE-wrenches] Enphase IQ8 >> &g

Re: [RE-wrenches] Enphase IQ8

2022-04-14 Thread Marco Mangelsdorf via RE-wrenches
lectrician #986315 > > -- > *From:* RE-wrenches on behalf > of Marco Mangelsdorf via RE-wrenches > *Sent:* Thursday, April 14, 2022 8:25 AM > *To:* RE-wrenches > *Cc:* Marco Mangelsdorf > *Subject:* [RE-wrenches] Enphase IQ8 > > *EXTERNAL EMA

Re: [RE-wrenches] Enphase IQ8

2022-04-14 Thread Nick Soleil via RE-wrenches
behalf of Marco Mangelsdorf via RE-wrenches Sent: Thursday, April 14, 2022 8:25 AM To: RE-wrenches Cc: Marco Mangelsdorf Subject: [RE-wrenches] Enphase IQ8 EXTERNAL EMAIL - Use caution when responding, clicking, and/or downloading attachments. Aloha all, Was looking over the new IQ8 l

[RE-wrenches] Enphase IQ8

2022-04-14 Thread Marco Mangelsdorf via RE-wrenches
Aloha all, Was looking over the new IQ8 line-up. And couldn't find a model that's compatible with 96-cell mods (and the associated higher Vmp). Is there an IQ8 model that's a good match for 96-celled mods? Or is that model exclusive to the deal Enphase has with SunPower to provide micros for

Re: [RE-wrenches] Enphase IQ8 systems

2022-04-13 Thread Jason Szumlanski via RE-wrenches
I believe that applies to all microinverters from the M215 to the IQ8. The available power is additive as long as there is battery capacity and the micro inverters are not off due to the battery being at full capacity. If the battery is at full capacity, the IQ8 should still be able to supplement

[RE-wrenches] Enphase IQ8 systems

2022-04-13 Thread Mac Lewis via RE-wrenches
Good Morning Wrenches, I am working through the Enphase training for their battery system while simultaneously designing a backup system. Cart is in front of the horse just a bit! Does anyone know if you are using an IQ8 roof top micro, does its output capacity add to the battery output

[RE-wrenches] Enphase Regional Sales Rep

2022-02-04 Thread Lou Russo
Aloha All, Does anyone have the contact info for the Enphase sales rep for Hawaii ( I believe the same person is in charge of Northern CA as well) ? The number I have does not work and customer support was of no help. ___ List sponsored by Redwood

Re: [RE-wrenches] Enphase Envoy -Microinverters not reporting

2022-01-10 Thread Christopher Warfel
I find they drop out over time due to networking issues and eventually will reconnect and catch up on data. Right now, about 20% of my systems installed in the past 5 years are having some issue with a microinverter or network. In a couple of days, they probably will reconnect and the emails

Re: [RE-wrenches] Enphase Monthly Reporting Software Update Remove Site ID in Subject Line?

2021-12-14 Thread Jason Szumlanski
011-300 > > California C10 Licensed Electrician #986315 > -- > *From:* RE-wrenches > on behalf of Christopher > Warfel > *Sent:* Thursday, October 28, 2021 7:16 AM > *To:* re-wrenches@lists.re-wrenches.org > > *Subject:* [RE-wrenches] E

Re: [RE-wrenches] Enphase Monthly Reporting Software Update Remove Site ID in Subject Line?

2021-12-14 Thread Christopher Warfel
986315 *From:* RE-wrenches on behalf of Christopher Warfel *Sent:* Thursday, October 28, 2021 7:16 AM *To:* re-wrenches@lists.re-wrenches.org *Subject:* [RE-wrenches] Enphase Monthly Reporting Software Update Remove Site ID in Subjec

Re: [RE-wrenches] Enphase Monthly Reporting Software Update Remove Site ID in Subject Line?

2021-10-28 Thread Jason Szumlanski
That's probably Steve Kinerk. Really bright guy. I've interacted with him before. I wouldn't want to share his direct contact info, however, as I understand their need to limit direct inquiries to employees. This is such a simple template change that you'd think someone could handle in under an

Re: [RE-wrenches] Enphase Monthly Reporting Software Update Remove Site ID in Subject Line?

2021-10-28 Thread Nick Soleil
ursday, October 28, 2021 7:16 AM To: re-wrenches@lists.re-wrenches.org Subject: [RE-wrenches] Enphase Monthly Reporting Software Update Remove Site ID in Subject Line? EXTERNAL EMAIL - Use caution when responding, clicking, and/or downloading attachments. Five months ago, our Enphase m

[RE-wrenches] Enphase Monthly Reporting Software Update Remove Site ID in Subject Line?

2021-10-28 Thread Christopher Warfel
Five months ago, our Enphase monthly reports removed the site name from the Subject line.  After many, many emails and phone calls, today I was told their software engineers were aware of the problem and they were not going to fix it. They were working on "more important things", so too bad, I

[RE-wrenches] Enphase IQ Max Distance

2021-10-27 Thread r...@solshineenergy.com
Good morning Wreches. What’s the furthest distance anyone has placed Enphase micros from the Envoy? We’ve done ~300’ without any issues related to comms or performance. Thanks, rick brown SolShine Energy Alternatives, LLC Electrical & Solar Contracting Services www.SolShineEnergy.com Cave

[RE-wrenches] Enphase IQ7 and IQ Battery 10?

2021-10-19 Thread Great Northern Solar
Dear Wrenches…. Any one have experience with Enphase IQ7 and IQ Battery 10… Reliable, long lived? Programable Storage for more than backup? Thanks! C. Energetically, Christopher LaForge Great Northern Solar 77480 Evergreen Road, Suite #1 Port Wing, WI 54865 715-774-3374

Re: [RE-wrenches] Enphase Envoy CR2032 battery

2021-09-21 Thread Steve Higgins
Usually, they are what keep the CMOS powered up... They are supposed to have only a 5-year life but tend to last longer than that. They are not generally fun to change, I've broken my share on the outback mates...

Re: [RE-wrenches] Enphase Envoy CR2032 battery

2021-09-21 Thread r...@solshineenergy.com
Many batteries on circuit boards are for the Real-Time Clock (RTC) in the event that the main power source is absent. I believe that’s the case for the Envoy. rick brown SolShine Energy Alternatives, LLC Electrical & Solar Contracting Services www.SolShineEnergy.com Check, Virginia 24072 O:

Re: [RE-wrenches] Enphase Envoy CR2032 battery

2021-09-21 Thread Benn Kilburn
SolarEdge uses the same battery in their inverters, and same, they’ve never been an issue. I’d assume it saves the date and perhaps other settings if/when there is no energy source connected to it. On Tue, Sep 21, 2021 at 6:20 AM Jason Szumlanski < ja...@floridasolardesigngroup.com> wrote: >

[RE-wrenches] Enphase Envoy CR2032 battery

2021-09-21 Thread Jason Szumlanski
Does anyone know the purpose of this battery on the circuit board. I have never had to change on or inquire what it does. I'm just curious. Jason ___ List sponsored by Redwood Alliance Pay optional member dues here: http://re-wrenches.org List

Re: [RE-wrenches] Enphase Enpower Smart Switch as service disconnect

2021-09-13 Thread Jason Szumlanski
* RE-wrenches on behalf > of Jason Szumlanski > *Sent:* Friday, September 10, 2021 11:27 AM > *To:* RE-wrenches > *Subject:* Re: [RE-wrenches] Enphase Enpower Smart Switch as service > disconnect > > *EXTERNAL EMAIL* - *Use caution when responding, clicking, and/or > downlo

Re: [RE-wrenches] Enphase Enpower Smart Switch as service disconnect

2021-09-13 Thread Nick Soleil
021 11:27 AM To: RE-wrenches Subject: Re: [RE-wrenches] Enphase Enpower Smart Switch as service disconnect EXTERNAL EMAIL - Use caution when responding, clicking, and/or downloading attachments. Yeah, I know it's service rated here, but I wanted to make sure it would work functionally. I gues

[RE-wrenches] Enphase Ensemble with four Encharge 10

2021-09-10 Thread Jason Szumlanski
When installing a system with more than two Encharge 10 batteries, a separate load center needs to be used to combine AC battery output. It would just require two 2-pole breakers in a MLO panel. But I believe both of those breakers would need to be fastened down. If anyone is doing this, are you

Re: [RE-wrenches] Enphase Enpower Smart Switch as service disconnect

2021-09-10 Thread Jason Szumlanski
Yeah, I know it's service rated here, but I wanted to make sure it would work functionally. I guess it's no different than a service rated generator ATS in that you can install the ATS without the generator and just have it there for future use. Thanks all for the feedback. Jason Szumlanski

Re: [RE-wrenches] Enphase Enpower Smart Switch as service disconnect

2021-09-10 Thread Eric Smiley
The spec sheet indicates it is rated as Service Equipment in the US but not in Canada. :-( *Eric Smiley,* Project Manager e...@vecoop.ca T: 250.703.6004 <+12507036004> T: 888.386.0116 <+18883860116> *VIRIDIANENERGY.CA * * * On Fri, 10

Re: [RE-wrenches] Enphase Enpower Smart Switch as service disconnect

2021-09-10 Thread Jason Szumlanski
Yes, I plan to install both a main breaker and a load breaker because both will be necessary in my ultimate design. I don't plan on installing an Envoy at this time. So I can't do any of the commissioning tasks. I will let you know how it goes. On Fri, Sep 10, 2021, 12:50 PM Rebekah Hren wrote:

Re: [RE-wrenches] Enphase Enpower Smart Switch as service disconnect

2021-09-10 Thread Rebekah Hren
I don't see why not, I have one I'm experimenting with in my garage now and it passes power through the bus prior to commissioning. I would make sure to add the Eaton BR main breaker in the Enpower at whatever amperage required for a more trustworthy discontent than the relay manual switch. It

[RE-wrenches] Enphase Enpower Smart Switch as service disconnect

2021-09-10 Thread Jason Szumlanski
Does anyone know if you can use the Smart Switch as a simple service disconnect if not installing solar and batteries now and have it work out of the box without any commissioning? I have a client building a new house and they are going to add solar and batteries after the certificate of

Re: [RE-wrenches] Enphase Battery Storage System Opinion

2021-07-06 Thread Jerry Shafer
>From what l hear, They just raised the price, lead time is next year, the only 25 year warranty is on the inverters, Jerry On Tue, Jul 6, 2021, 10:57 AM Christopher Warfel < cwar...@entech-engineering.com> wrote: > We have designed our first Enphase approved battery system, but I don't > recall

[RE-wrenches] Enphase Battery Storage System Opinion

2021-07-06 Thread Christopher Warfel
We have designed our first Enphase approved battery system, but I don't recall any discussion on them here. I'd like to hear from installers that have installed the technology.  Could anyone with experience let me know their opinion of the package?  Thank you, Chris --            

[RE-wrenches] Enphase Meter Wizard Mandatory as of July 15

2021-06-24 Thread Jason Szumlanski
I just received this email, as I'm sure many of you have. I would encourage you to reach out to your Enphase rep and push back on this insane decision. The installer toolkit has enough quirks, bugs, delays, and issues already. Adding more delay by enforcing the meter wizard is not installer

Re: [RE-wrenches] Enphase IQ7A 3 phase limitations

2021-03-04 Thread Jason Szumlanski
Mac Lewis was nice enough to run some Helioscope simulations for me (thank you, Mac). The numbers were almost identical to PVWATTS in that per kW, you get about 1% less energy yield with a 420W/IQ7A than a 385W/IQ7+ when operating at 208Vac. Given that the IQ7A is more costly, and presumably the

Re: [RE-wrenches] Enphase IQ7A 3 phase limitations

2021-03-04 Thread Will White
Jason, You should dig into the PVWatts help documentation. They get into pretty good detail on how their calculations work. You might find the answer you're looking for there. Thanks, Will -- *Will White* Curriculum Developer e: w...@solarenergy.org w: www.solarenergy.org p: 802-272-3092

Re: [RE-wrenches] Enphase IQ7A 3 phase limitations

2021-03-04 Thread Mac Lewis
Hi Jason, I think Helioscope is more suited for this analysis. If you send me the location, tilt, orientation, array type (roof or ground) and modules that you'd like to compare, I can quickly model this for you. Quite easy to do. They also have a month free trial I believe if you would like to

Re: [RE-wrenches] Enphase IQ7A 3 phase limitations

2021-03-03 Thread Dave Tedeyan
Then just as a follow up, I looked at the SMA-41 datasheet. This shows that it runs at it's highest efficiency when the output power / rated power is about 0.4 to 0.6, and the only real loss in efficiency comes when you are running at about 0.1 and below. On Wed, Mar 3, 2021, 8:35 PM Dave

Re: [RE-wrenches] Enphase IQ7A 3 phase limitations

2021-03-03 Thread Dave Tedeyan
I've never really trusted PVWatts on this. I just did a quick test using my location in the northeast, with all the standard values and then just changing the DC to AC ratio. It's telling me that a ratio of 1.5 is almost exactly the same as a ratio of 1, and that around 1.3 is best. You actually

Re: [RE-wrenches] Enphase IQ7A 3 phase limitations

2021-03-03 Thread Jason Szumlanski
olar Wind Works > > NABCEP PV Installation Professional > > Cell 530-448-9692 > > www.solarwindworks.com > > ch...@solarwindworks.com > > > > *From:* RE-wrenches *On > Behalf Of *Jay > *Sent:* Wednesday, March 03, 2021 12:46 PM > *To:* RE-wrenches >

Re: [RE-wrenches] Enphase IQ7A 3 phase limitations

2021-03-03 Thread Jason Szumlanski
I've used that document many times when clients question the ratio. I wish I knew exactly how the PVWATTS ratio calculation worked. I know there's information on how this is all done, but I don't really have the time or inclination to study it. I'm wondering if someone knows how accurate It is.

Re: [RE-wrenches] Enphase IQ7A 3 phase limitations

2021-03-03 Thread Chris Worcester
NABCEP PV Installation Professional Cell 530-448-9692 www.solarwindworks.com ch...@solarwindworks.com From: RE-wrenches On Behalf Of Jay Sent: Wednesday, March 03, 2021 12:46 PM To: RE-wrenches Subject: Re: [RE-wrenches] Enphase IQ7A 3 phase limitations Emphase has a white paper

Re: [RE-wrenches] Enphase IQ7A 3 phase limitations

2021-03-03 Thread Jay
Emphase has a white paper showing production vs module size and locations around the country. I don’t know if it’s more accurate than pv watts but you might check it out. Jay Peltz power. > On Mar 3, 2021, at 12:13 PM, Jason Szumlanski > wrote: > >  > I'm wondering how accurate the DC to

Re: [RE-wrenches] Enphase IQ7A 3 phase limitations

2021-03-03 Thread Jason Szumlanski
I'm wondering how accurate the DC to AC ratio is when using PVWATTS. I did a quick PVWATTS analysis at my local area using a typical commercial roof tilt and found that using a 420W module on an IQ7A versus a 385W module on an IQ7+ yields almost identical results. The 420W module has 1% less

Re: [RE-wrenches] Enphase IQ7A 3 phase limitations

2021-03-02 Thread Chris Worcester
...@solarwindworks.com From: RE-wrenches On Behalf Of Jason Szumlanski Sent: Tuesday, March 02, 2021 7:00 AM To: RE-wrenches Subject: [RE-wrenches] Enphase IQ7A 3 phase limitations I was surprised to learn that the IQ7A is limited to 290 W continuous at 208 volts. That pretty much puts

Re: [RE-wrenches] Enphase IQ7A 3 phase limitations

2021-03-02 Thread r...@solshineenergy.com
Oops, that’s at 240V. My mistake. rick brown SolShine Energy Alternatives, LLC Electrical & Solar Contracting Services www.SolShineEnergy.com Check, Virginia 24072 O: 540.235.3095 M: 540.808.9502 VA Class A Contractor Lic# 2705147660 VA Master Electrician Lic# 2710062762 VA Alternative Energy

Re: [RE-wrenches] Enphase IQ Envoy Distance for Monitoring

2021-03-02 Thread Kirk Herander, VSE
I've done the original Envoy at > 300 feet and was fine. Kirk Herander / kirkh@vermont.solar [mailto:kirkh@vermont.solar] Owner|Principal, VT Solar, LLC Celebrating our 30th Anniversary 1991-2021!! www.vermont.solar

[RE-wrenches] Enphase IQ7A 3 phase limitations

2021-03-02 Thread Jason Szumlanski
I was surprised to learn that the IQ7A is limited to 290 W continuous at 208 volts. That pretty much puts Enphase out of the running for light commercial jobs with new high-powered 72 cell panels. Any thoughts on this? Jason ___ List sponsored by

Re: [RE-wrenches] Enphase IQ Envoy Distance for Monitoring

2021-03-01 Thread Jason Szumlanski
half Of *Dave Tedeyan > *Sent:* Monday, March 1, 2021 10:08 AM > *To:* RE-wrenches > *Subject:* Re: [RE-wrenches] Enphase IQ Envoy Distance for Monitoring > > > > Along what Glenn is saying - I have often used wireless radios to get wifi > to the array. I used to use the Eng

Re: [RE-wrenches] Enphase IQ Envoy Distance for Monitoring

2021-03-01 Thread Jason Szumlanski
ers successfully to ge >> internet to a remotely located array. >> >> -Glenn >> Sent from my 'smart'phone, so please excuse typos and spelling errors. >> >> -- Original message-- >> *From: *Jason Szumlanski >> *Date: *Mon, Mar 1, 2021 10:39 AM &

Re: [RE-wrenches] Enphase IQ Envoy Distance for Monitoring

2021-03-01 Thread Jason Szumlanski
> *To: *RE-wrenches; > *Cc: * > *Subject:*[RE-wrenches] Enphase IQ Envoy Distance for Monitoring > > How far has anyone ever put an IQ Envoy from an array and successfully > monitored it? > > I am planning a ground mount that is 300 feet from a home with 12/240V > service. The br

Re: [RE-wrenches] Enphase IQ Envoy Distance for Monitoring

2021-03-01 Thread William Miller
AM *To:* RE-wrenches *Subject:* Re: [RE-wrenches] Enphase IQ Envoy Distance for Monitoring Along what Glenn is saying - I have often used wireless radios to get wifi to the array. I used to use the Engenius ENH202 all the time and they were great, but last I checked the prices went up. I have

Re: [RE-wrenches] Enphase IQ Envoy Distance for Monitoring

2021-03-01 Thread Dave Tedeyan
ternet to a remotely located array. > > -Glenn > Sent from my 'smart'phone, so please excuse typos and spelling errors. > > -- Original message-- > *From: *Jason Szumlanski > *Date: *Mon, Mar 1, 2021 10:39 AM > *To: *RE-wrenches; > *Cc: * > *Subject:*[RE-wrenches] Enph

Re: [RE-wrenches] Enphase IQ Envoy Distance for Monitoring

2021-03-01 Thread Glenn Burt
-wrenches] Enphase IQ Envoy Distance for MonitoringHow far has anyone ever put an IQ Envoy from an array and successfully monitored it?I am planning a ground mount that is 300 feet from a home with 12/240V service. The branch circuits will have an AC combiner panel on a rack at the array with 2

Re: [RE-wrenches] Enphase IQ Envoy Distance for Monitoring

2021-03-01 Thread August Goers
Hi Jason - I don't have the answer to your question because we've mounted the monitoring box out by the array for similar applications to what you described. I would suggest that if you mount your envoy far from the array, that at least you run a spare 1" PVC with some pull points out to the array

Re: [RE-wrenches] Enphase IQ Envoy Distance for Monitoring

2021-03-01 Thread r...@solshineenergy.com
Jason, We recently completed a ground-mount array ~350’ from the Envoy and all micros are able to report. > On Mar 1, 2021, at 8:47 AM, Jason Szumlanski > wrote: > > How far has anyone ever put an IQ Envoy from an array and successfully > monitored it? > > I am planning a ground mount