From: Steve Leyton
Sent: Tuesday, January 16, 2024 8:34 AM
To: Discussion list on issues relating to automatic fire sprinklers
Subject
Is the spacing of 12' in building less than 30' in table 14.2.8.2.1 of the 2019
NFPA 13 along the branchline or can it be between the branchlines? I feel it's
along the branchline but can't find my confirmation.
Joe
Burtell | SET, CFPS
Fire Sprinkler Manager
D
C
406-204-4653
406-861-4507
3004
and almost no fire
load is present due to egress.
Look very close ate the FAQ of 7.2.1, NFPA 13R requires only that the design
discharge, number of design sprinklers, sprinkler coverage, and position of
sprinklers comply with NFPA 13, for areas outside the dwelling.
Joe
Burtell | SET, CFPS
Fire
I do need clearance and I use
flex couplings because I don't have the clearance necessary, do I have to add
additional lateral bracing because of the flexible couplings? The hole is not
used to support the pipe, there will be hangers to the tops of the steel
I-beams.
2019 NFPA 13
Joe
Burtell |
I agree with Steve here and to add my two cents, it is a lot lighter and makes
for a quicker and easier installation. It's probably half of the weight. I
order GxG OS valves all the time and there are no lead times.
Joe
Burtell | SET, CFPS
Fire Sprinkler Manager
D
C
406-204-4653
406-861-4507
I don’t disagree with you, but I can’t help to think that we don’t apply this
logic with in-racks. If I have aerosols, other flammable liquids, etc.. I
threat that different than the overhead, different design, different sprinklers.
Joe
Burtell | SET, CFPS
Fire Sprinkler Manager
D
C
406-204
or they can be
different (CMDA, etc..)
Joe
Burtell | SET, CFPS
Fire Sprinkler Manager
D
C
406-204-4653
406-861-4507
From: Prahl, Craig
Sent: Tuesday, August 29, 2023 9:28 AM
To: Discussion list on issues relating to automatic fire sprinklers
Subject: [Sprinklerforum] Re: ESFR Below Mezzanine
is really
treated like an obstruction? I think it would be treated like in-racks would
and have its own design based on what's under the mezzanine.
Joe
Burtell | SET, CFPS
Fire Sprinkler Manager
D
C
406-204-4653
406-861-4507
3004 1st Ave South
Billings,
MT 59101
Office: 406-652-7697
In the past, I have done (2) ceiling flanges, one on the top and one on the
bottom of the grate to make a sandwich.
Best regards,
*Joe Burtell, SET, CFPS*
[image: Burtell Fire_Small]
Phone | Fax | Mobile| Text *406-204-4653 <++1-406-204-4653>*
116 N. 11th Street | Billings, MT 59101
Good question. Sorry, thoughts on applying it to CPVC.
Best regards,
*Joe Burtell, SET, CFPS*
[image: Burtell Fire_Small]
Phone | Fax | Mobile| Text *406-204-4653 <++1-406-204-4653>*
116 N. 11th Street | Billings, MT 59101
Email: j...@burtellfire.com
Web Site: http://www.burtellfi
regards,
*Joe Burtell, SET, CFPS*
[image: Burtell Fire_Small]
Phone | Fax | Mobile| Text *406-204-4653 <++1-406-204-4653>*
116 N. 11th Street | Billings, MT 59101
Email: j...@burtellfire.com
Web Site: http://www.burtellfire.com
*“**The bitterness of poor quality remains long
Yes, the commodity is exposed and unexpanded and 2016 is the current
edition in Montana.
Best regards,
*Joe Burtell, SET, CFPS*
[image: Burtell Fire_Small]
Phone | Fax | Mobile| Text *406-204-4653 <++1-406-204-4653>*
116 N. 11th Street | Billings, MT 59101
Email: j...@burtellfire.co
ve done designs for these before.
Best regards,
*Joe Burtell, SET, CFPS*
[image: Burtell Fire_Small]
Phone | Fax | Mobile| Text *406-204-4653 <++1-406-204-4653>*
116 N. 11th Street | Billings, MT 59101
Email: j...@burtellfire.com
Web Site: http://www.burtellfire.com
*“**The bitterness of poor
to the
correct section, please?
Best regards,
*Joe Burtell, SET, CFPS*
[image: Burtell Fire_Small]
Phone | Fax | Mobile| Text *406-204-4653 <++1-406-204-4653>*
116 N. 11th Street | Billings, MT 59101
Email: j...@burtellfire.com
Web Site: http://www.burtellfire.com
*“**The bitterness of poor q
I would think you have to space to the walls or have the walls stop 18"
below the ceiling which it appears it does. The obstructions change for
things below 18" and the chart stops at 18" as well.
Best regards,
*Joe Burtell, SET, CFPS*
[image: Burtell Fire_Small]
Phone | Fax
to have enough pressure to initially open the backflow until the
fire pump can get going to keep water moving. I just didn't want to try all
these things if someone on the forum already did and failed. That is the
beauty of all you smart people on here.
Best regards,
*Joe Burtell, SET, CFPS*
[image
Yes, we have pottable water being taken from the same tanks. This is a
rural high school and this is their own water system that feeds the school.
So I need the backflow for that reason.
Best regards,
*Joe Burtell, SET, CFPS*
[image: Burtell Fire_Small]
Phone | Fax | Mobile| Text *406-204-4653
regards,
*Joe Burtell, SET, CFPS*
[image: Burtell Fire_Small]
Phone | Fax | Mobile| Text *406-204-4653 <++1-406-204-4653>*
116 N. 11th Street | Billings, MT 59101
Email: j...@burtellfire.com
Web Site: http://www.burtellfire.com
*“**The bitterness of poor quality remains long
pancy and should not be treated as such when applying 9.2.10. Often
the presence of an access hatch or other means to allow for equipment
maintenance is misconstrued as allowing occupancy of such a space.
Best regards,
*Joe Burtell, SET, CFPS*
[image: Burtell Fire_Small]
Phone | Fax | Mobile| Text
Could you treat it as a non-combustible concealed space below a floor with
no fueled-fired devices?
Best regards,
*Joe Burtell, SET, CFPS*
[image: Burtell Fire_Small]
Phone | Fax | Mobile| Text *406-204-4653 <++1-406-204-4653>*
116 N. 11th Street | Billings, MT 59101
Em
Can you use a dry system for protection for Idle Pallets? I know ESFR has
to be wet but what if I'm using CMDA?
Best regards,
*Joe Burtell, SET, CFPS*
[image: Burtell Fire_Small]
Phone | Fax | Mobile| Text *406-204-4653 <++1-406-204-4653>*
116 N. 11th Street | Billings, MT 59101
Em
I would really watch if they are listed for use in obstructed construction,
most are just smooth flat, just FYI.
Best regards,
*Joe Burtell, SET, CFPS*
[image: Burtell Fire_Small]
Phone | Fax | Mobile| Text *406-204-4653 <++1-406-204-4653>*
116 N. 11th Street | Billings, MT 59101
Em
NFPA 13 only allows omission for hotels and motels, so I think the answer
is, there is no omission allowed in the "condo" areas.
Best regards,
*Joe Burtell, SET, CFPS*
[image: Burtell Fire_Small]
Phone | Fax | Mobile| Text *406-204-4653 <++1-406-204-4653>*
116 N. 11th Stree
If the FAQ is true, then what is the point of 23.4.4.2.4? One says it has
to be 1500 no matter what and the other says you just apply the extra GPM
at the furthest branchline? Don't they contradict each other?
Best regards,
*Joe Burtell, SET, CFPS*
[image: Burtell Fire_Small]
Phone | Fax
design area (Area/Density design method) until you run out
of ordinary hazard or reach the minimum design area.
Best regards,
*Joe Burtell, SET, CFPS*
[image: Burtell Fire_Small]
Phone | Fax | Mobile| Text *406-204-4653 <++1-406-204-4653>*
116 N. 11th Street | Billings, MT 59101
Em
Thanks, guys, that is what I was thinking as well.
Best regards,
*Joe Burtell, SET, CFPS*
[image: Burtell Fire_Small]
Phone | Fax | Mobile| Text *406-204-4653 <++1-406-204-4653>*
116 N. 11th Street | Billings, MT 59101
Email: j...@burtellfire.com
Web Site: http://www.burtellfi
says it does not apply.
Best regards,
*Joe Burtell, SET, CFPS*
[image: Burtell Fire_Small]
Phone | Fax | Mobile| Text *406-204-4653 <++1-406-204-4653>*
116 N. 11th Street | Billings, MT 59101
Email: j...@burtellfire.com
Web Site: http://www.burtellfire.com
*“**The bitterness of poor q
I agree. Yes, the assemblies are required to be rated.
Best regards,
*Joe Burtell, SET, CFPS*
[image: Burtell Fire_Small]
Phone | Fax | Mobile| Text *406-204-4653 <++1-406-204-4653>*
116 N. 11th Street | Billings, MT 59101
Email: j...@burtellfire.com
Web Site: http://www.burtellfi
million, it is now void of it's listing which the building code
and NFPA required to be listed for such use. The last part is the liability
as a small contractor. The architect does not want to spend the money to
put in the proper glass.
Best regards,
*Joe Burtell, SET, CFPS*
[image: Burtell Fire_Small
I have an architect that wants to put additional window sprinklers below a
horizontal mullion. I am absolutely against this idea as it's not listed or
approved for this. Has anyone run into this situation?
Best regards,
*Joe Burtell, SET, CFPS*
[image: Burtell Fire_Small]
Phone | Fax | Mobile
Mike, I was a classic SprinkCAD user and beta test for about 10 years, I
am now an AutoSPRINk and beta tester. You can contact me off the forum for
any info. I would not use anything but AutpSPRINK.
Best regards,
*Joe Burtell, SET, CFPS*
[image: Burtell Fire_Small]
Phone | Fax | Mobile| Text
NFPA 25 2014 13.6.2.2 Where hydrants or inside hose stations are located
downstream of the backflow pre-
venter, the forward flow test shall include hose stream demand.
I guess this answers the question, now to get this into 13.
Best regards,
*Joe Burtell*
On Tue, Aug 13, 2019 at 8:58 PM J H
The is a restaurant with only hydrants upstream of the backflow and no
inside hose stations.
Best regards,
*Joe Burtell*
On Tue, Aug 13, 2019 at 4:46 PM Bruce Verhei via Sprinklerforum <
sprinklerforum@lists.firesprinkler.org> wrote:
> Does the outside hose allowance flow through
allowance only. It does not state that but I have an AHJ requiring the
outside hose allowance to be applied to the forward flow. Does anyone have
any information that better defines what hose allowance would be applicable?
Best regards,
*Joe Burtell
I have a warehouse storing "stretch wrap" on pallets. This is used to
encapsulate pallet loads. The manufacturer does not say what it's made from.
[image: image.png]
I am assuming it's some type of poly. Does anyone have any thoughts on if
this would be a group A plastic?
Best rega
no jurisdictions that give guidance, it's all per 13.
Best regards,
*Joe Burtell, SET, CFPS*
[image: Burtell Fire_Small]
Phone | Fax | Mobile| Text *406-204-4653 <++1-406-204-4653>*
116 N. 11th Street | Billings, MT 59101
Email: j...@burtellfire.com
Web Site: http://www.burtellfi
need to be?
Best regards,
*Joe Burtell, SET, CFPS*
[image: Burtell Fire_Small]
Phone | Fax | Mobile| Text *406-204-4653 <++1-406-204-4653>*
116 N. 11th Street | Billings, MT 59101
Email: j...@burtellfire.com
Web Site: http://www.burtellfire.com
*“**The bitterness of poor quality remains
Are there any restrictions on using power-driven studs for branchline
restraint? In the diagram, they show what looks like a wedge bolt anchor
but I can't see where there is any size or requirements given for fasteners
used for branchline restraint.
[image: image.png]
Best regards,
*Joe Burtell
Is there anything in NFPA 13 that discusses auto peaking if you have a grid
in let's say an office space that is all cut up? Seems almost impossible to
do it without drawings remote areas manually and calculating several groups
of rooms.
Best regards,
*Joe Burtell, SET, CFPS*
[image: Burtell
.
The 2 in. (50 mm) clearance ensures that a fire fighter wearing thick fire
gloves can easily operate the valve. Where a pressure-reducing valve (PRV)
is used, a deeper cabinet might be necessary due to the size of the PRV.
Best regards,
*Joe Burtell, SET, CFPS*
[image: Burtell Fire_Small]
Phone
[image: image.png]
Best regards,
*Joe Burtell, SET, CFPS*
[image: Burtell Fire_Small]
Phone | Fax | Mobile| Text *406-204-4653 <++1-406-204-4653>*
116 N. 11th Street | Billings, MT 59101
Email: j...@burtellfire.com
Web Site: http://www.burtellfire.com
*“**The bitterness of poor q
sults impossible
to correlate.
A better solution would be a means to test the full flow of the backflow
device that is separate from the main drain that allows for proper
drainage."
Does this seem the opposite of 16.10.4.8?
Best regards,
*Joe Burtell, SET, CFPS*
[image: Burtell Fire_Small]
P
into it.
To further this discussion, if I have a riser room with 10 riser and the
drains are all tied together, there is no requirement to upsize that drain
pipe that I can see. So why one and not the other?
Best regards,
*Joe Burtell, SET, CFPS*
[image: Burtell Fire_Small]
Phone | Fax | Mobile| Text *406-204
This is a building code driven issue. It is going to depend on what the
architect did for fire-resistive ratings. It would be up to the A team to
tell you what is required. In some section, listed sprinklers are now
required.
Best regards,
*Joe Burtell, SET, CFPS*
**PLEASE NOTE NEW PHONE
in the existing sprinkler system, this section is not intended to
require the replacement of existing standard-response sprinklers with
quick-response sprinklers.
If he wants to argue it's a light hazard, that's what you have to get past
for these to apply.
Best regards,
*Joe Burtell, SET, CFPS*
**PLEASE
what he wants.
Best regards,
*Joe Burtell, SET, CFPS*
**PLEASE NOTE NEW PHONE NUMBER**
[image: Burtell Fire_Small]
Phone | Fax | Mobile| Text *406-204-4653 <++1-406-204-4653>*
116 N. 11th Street | Billings, MT 59101
Email: j...@burtellfire.com
Web Site: http://www.burtellfi
I would agree. That rule did also not apply to composite wood joists in
previous editions, so your logic is on track. Some of the listed concealed
space sprinkles are listed for other construction types but it's another to
pay for the special sprinklers.
Best regards,
*Joe Burtell, SET, CFPS
be isolated and tested at not less than 200 psi (13.8
bar) for 2 hours.
25.2.1.4.2 Modifications that cannot be isolated, such as relocated drops,
shall require testing
at system working pressure.
Best regards,
*Joe Burtell, SET, CFPS*
**PLEASE NOTE NEW PHONE NUMBER**
[image: Burtell Fire_Small
I'm not saying to regulate at a local level, it should be done by UL, FM,
IBC, IFC, etc... We didn't have this toxic stuff we have today 50 years ago.
Best regards,
*Joe Burtell, SET, CFPS*
[image: Burtell Fire_Small]
Phone | Fax | Mobile| Text *406-545-0784 <++1-406-545-0784>*
116 N
are a major problem with fires, I agree with Steve. I'm sure the
walls of the band practice booth are full of plastics and foam, should they
be OH or EX? Maybe a better approach would be to not allow these toxic
materials in the first place?
Best regards,
*Joe Burtell, SET, CFPS*
[image: Burtell
was a
distribution storage room for new mats, that would be different.
Best regards,
*Joe Burtell, SET, CFPS*
[image: Burtell Fire_Small]
Phone | Fax | Mobile| Text *406-545-0784 <++1-406-545-0784>*
116 N. 11th Street | Billings, MT 59101
Email: j...@burtellfire.com
Web Site: http://www.burtellfi
in installations connecting the sprinkler system piping to
sprinklers shall be installed
in accordance with the requirements of the listing, including any
installation instructions.
Best regards,
*Joe Burtell, SET, CFPS*
[image: Burtell Fire_Small]
Phone | Fax | Mobile| Text *406-545-0784 <++1-
Does anyone have any information supporting high school wrestling, fitness,
and weight rooms being OH2 due to the rubber floors or foam mats? It seems
overkill to me but new information is always coming out.
Best regards,
*Joe Burtell, SET, CFPS*
[image: Burtell Fire_Small]
Phone | Fax
Anyone have a datasheet or friction loss for a GRINNELL MODEL E-2, 4
IN.-1931 TO 1971
Best regards,
*Joe Burtell, SET, CFPS*
[image: Burtell Fire_Small]
Phone | Fax | Mobile| Text *406-545-0784 <++1-406-545-0784>*
116 N. 11th Street | Billings, MT 59101
Email: j...@burtellfire.co
If the rule is not in NFPA 13D, you cannot just apply NFPA 13. It does not
mean it's not to be looked at but NFPA 13D is only worried about life
safety, property protection is not it's primary objection.
Best regards,
*Joe Burtell, SET, CFPS*
[image: Burtell Fire_Small]
Phone | Fax | Mobile
I would check out C-AIRE, they make great compressors.
Best regards,
*Joe Burtell, SET, CFPS*
[image: Burtell Fire_Small]
Phone | Fax | Mobile| Text *406-545-0784 <++1-406-545-0784>*
116 N. 11th Street | Billings, MT 59101
Email: j...@burtellfire.com
Web Site: http://www.burtellfi
Me personally, I would treat the beam as a wall, the spray pattern cannot
carry over to the next row on the other side, so why would I carry over its
dimension for the SxL
Best regards,
*Joe Burtell, SET, CFPS*
[image: Burtell Fire_Small]
Phone | Fax | Mobile| Text *406-545-0784 <++1-406-
Is the spacing along the branchline measured along the floor or the roof
pitch?
Best regards,
*Joe Burtell, SET, CFPS*
[image: Burtell Fire_Small]
Phone | Fax | Mobile| Text *406-545-0784 <++1-406-545-0784>*
116 N. 11th Street | Billings, MT 59101
Email: j...@burtellfire.com
We
I have you done any test for stray electrical currents or improper
bonding/grounding?
Best regards,
*Joe Burtell, SET, CFPS*
[image: Burtell Fire_Small]
Phone | Fax | Mobile| Text *406-545-0784 <++1-406-545-0784>*
116 N. 11th Street | Billings, MT 59101
Email: j...@burtellfire.co
This is a new installation. The manufacturer is AC and they get their
motors from US motors. Where does the exemption come from?
Best regards,
*Joe Burtell, SET, CFPS*
[image: Burtell Fire_Small]
Phone | Fax | Mobile| Text *406-545-0784 <++1-406-545-0784>*
116 N. 11th Street | Billin
I am being told this by the motor manufacturer. They say they have to do
this by DOE requirements.
Best regards,
*Joe Burtell, SET, CFPS*
[image: Burtell Fire_Small]
Phone | Fax | Mobile| Text *406-545-0784 <++1-406-545-0784>*
116 N. 11th Street | Billings, MT 59101
Em
moved it to Premium. Only motors with B design codes can be
used for fire pumps. A special motor that would meet this requirement was
a special build"
Best regards,
*Joe Burtell, SET, CFPS*
[image: Burtell Fire_Small]
Phone | Fax | Mobile| Text *406-545-0784 <++1-406-545-0784>*
11
moved it to Premium. Only motors with B design codes can be
used for fire pumps. A special motor that would meet this requirement was
a special build"
Best regards,
*Joe Burtell, SET, CFPS*
[image: Burtell Fire_Small]
Phone | Fax | Mobile| Text *406-545-0784 <++1-406-545-0784>*
11
I would get the manufacturers data sheet. It should have a side profile
with the heat zones shown so you can see what the temps are and how far out
and above.
Best regards,
*Joe Burtell, SET, CFPS*
[image: Burtell Fire_Small]
Phone | Fax | Mobile| Text *406-545-0784 <++1-406-545-0784>
A slope greater than 2/12 is beyond NFPA. He would need to install a flat
ceiling in order to use NFPA 13 and rack storage.
Best regards,
*Joe Burtell, SET, CFPS*
[image: Burtell Fire_Small]
Phone | Fax | Mobile| Text *406-545-0784 <++1-406-545-0784>*
116 N. 11th Street | Billings, MT
I use Print2CAD and it works fairly well for the most part.
http://www.backtocad.com/pdf-to-dwg-converter.html
Best regards,
*Joe Burtell, SET, CFPS*
[image: Burtell Fire_Small]
Phone | Fax | Mobile| Text *406-545-0784 <++1-406-545-0784>*
116 N. 11th Street | Billings, MT 59101
Em
Some are in cardboard boxes, no packaging. Some of the raw windshields and
windshields in cardboard boxes are on wood pallets.
Best regards,
*Joe Burtell, SET, CFPS*
[image: Burtell Fire_Small]
Phone | Fax | Mobile| Text *406-545-0784 <++1-406-545-0784>*
116 N. 11th Street | Billin
Yes, these are automotive windshields for passenger and commercial vehicles.
Best regards,
*Joe Burtell, SET, CFPS*
[image: Burtell Fire_Small]
Phone | Fax | Mobile| Text *406-545-0784 <++1-406-545-0784>*
116 N. 11th Street | Billings, MT 59101
Email: j...@burtellfire.com
Web Site
Can anyone tell where in the code or what windshields are classified as for
protection in racks? Would they be Class 1,2,3,4 or Group A, etc...
Best regards,
*Joe Burtell, SET, CFPS*
[image: Burtell Fire_Small]
Phone | Fax | Mobile| Text *406-545-0784 <++1-406-545-0784>*
116 N. 11th
in-rack control
valve in order to
limit the extent of any single impairment.
I would say, yes or it moved?
Best regards,
*Joe Burtell, SET, CFPS*
[image: Burtell Fire_Small]
PH: 406-652-7697
Fax: 406-652-7743 | Cell: 406-861-4507
Email: j...@burtellfire.com
Web Site: http
the overall
distance between
hangers does not exceed the requirements in Table 9.2.2.1(a) and Table
9.2.2.1(b). The cumu-
lative distance includes changes in horizontal direction. Multiple
consecutive sections of pipe
should be permitted to omit hangers.
[image: Inline image 1]
Best regards,
*Joe
Thanks Cecil but I am only referring to existing homes and buildings. I know
what to do with any new stuff. Just remember the mistakes Central made and
what it cost them with the recalls. I see this as the same thing. NFPA has
made a big mistake and they just get to walk away?
Joe Burtell
I am not aware of any such product. I heard a rumor Lubrizol was working on
something. I would like to thank NFPA for making such a mess out of this
anti-freeze issue. What am I supposed to tell the owner when he asks me who
is going to pay for this on existing systems?
Joe Burtell
me
looking like the stupid one. NFPA needs to do 100% better for existing
systems. They leave me hanging with all the liability.
Joe Burtell
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of George Church
Sent
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Joe Burtell
Sent: Thursday, March 17, 2011 11:15 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: antifreeze solutions
Ya, maybe back in 2001 they could have
All NFPA did was transfer the real world problem onto contractors to figure
out what to do with existing systems. They simply washed their hands of the
liability and left it up to the contractor to fend for themselves. What's
next for this industry? How many black eyes can we keep taking?
Joe
no
options but antifreeze. Am I supposed to tell them I'm sorry but I can't
help you and now they are on their own. This is where NFPA screwed all of us
and the pooch. Enough about this, I'll step off my soap box.
Joe Burtell
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
or removed.
Pay attention to the Last sentence, REMOVED.
Joe Burtell
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Thom
Sent: Monday, March 07, 2011 9:32 AM
To: sprinklerforum@firesprinkler.org
Subject: RE
hoistway door
sill are in vertical alignment.
(a) Elevator electrical equipment shall be weatherproof (Type 4 as specified in
NEMA 250).
(b) Elevator wiring, except traveling cables, shall be identified for use in
wet locations in accordance with the
requirements in NFPA 70.
Joe Burtell
Elevator machine rooms can only have sprinkler pipe feeding sprinklers for
that room only. Pipes that are foreign to that room like FDC or main drain
lines are not allowed.
Joe Burtell
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun
Can anyone give me a source for buying No. 12, 440 lb wire for use with
doing restraint for branchlines?
Best regards,
Joe Burtell, SET, CFPS
Burtell Fire Protection
Phone: 406.652.7697
Fax: 406.652.7743
Cell: 406.861.4507
Email: j...@burtellfire.com
Web Site: http://www.burtellfire.com
Can someone tell be if soldered joints are allowed by NFPA 13 for pre-action
systems or is only brazed joints allowed. It looks like melting temps are
the issue between the different methods.
Best regards,
Joe Burtell, SET, CFPS
Burtell Fire Protection
Phone: 406.652.7697
Fax: 406.652.7743
Cell
Where did the underground clearance for underground move to in the 07' or
10' of NFPA 13?
Best regards,
Joe Burtell, SET, CFPS
Burtell Fire Protection
Phone: 406.652.7697
Fax: 406.652.7743
Cell: 406.861.4507
Email: j...@burtellfire.com
Web Site: http://www.burtellfire.com
No, the clearance from the foundation concrete floor.
Joe Burtell
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Richard
Lindner
Sent: Wednesday, January 26, 2011 12:17 PM
To: sprinklerforum
Thanks Thom. 9.3.4 does reference other pipes but not underground
specifically. A.23.1.6.2 is what I was looking for.
Joe Burtell
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Thom
Sent: Wednesday
for in-rack sprinklers.
16.6.3.6 Water demand at point of supply shall be calculated separately for
in-rack and ceiling sprinklers and shall be based on the greater demand.
These all call for the overhead NOT to be balanced with the in-rack but
nothing is mentioned for scheme E.
Best regards,
Joe
Can someone reply off line if they received this original message below. Any
takes to answer the original question?
Joe Burtell
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Joe Burtell
Sent: Monday
is less than 5 gal
(18.9 L), one of the following arrangements shall be provided:
Best regards,
Joe Burtell, SET, CFPS
Burtell Fire Protection
Phone: 406.652.7697
Fax: 406.652.7743
Cell: 406.861.4507
Email: j...@burtellfire.com
Web Site: http://www.burtellfire.com
Please consider the environment
Here is what our local fire marshal got back from the ICC
Subject: IFC 904.2 question
Hi Scott,
I have a question for you.
Section 904.2 states that Automatic fire-extinguishing systems shall not be
considered alternatives for the purposes of exceptions or reductions allowed
by other
Does anyone out there have a handy excel file that would automatically
calculate the air maintenance device cut-in, cut-out and the PS-40 high and
low settings based on the static pressure plugged into the formula?
Best regards,
Joe Burtell, SET, CFPS
Burtell Fire Protection
Phone: 406.652.7697
be
of 1⁄2 in. (15 mm) nominal size.
Best regards,
Joe Burtell, SET, CFPS
Burtell Fire Protection
Phone: 406.652.7697
Fax: 406.652.7743
Cell: 406.861.4507
Email: j...@burtellfire.com
Web Site: http://www.burtellfire.com
Please consider the environment before printing this email
To anyone who wants I can forward 2 good pictures that we can debate whether
it's bonding or grounding.
Joe Burtell
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Sprinkler
Academy - C Bilbo
Sent: Monday
it meets one of the exceptions I would say it requires sprinklers above
the ceiling as well.
Best regards,
Joe Burtell, SET, CFPS
Burtell Fire Protection
Phone: 406.652.7697
Fax: 406.652.7743
Cell: 406.861.4507
Email: j...@burtellfire.com
Web Site: http://www.burtellfire.com
please don't print
,
Joe Burtell, SET, CFPS
Burtell Fire Protection
Phone: 406.652.7697
Fax: 406.652.7743
Cell: 406.861.4507
Email: j...@burtellfire.com
Web Site: http://www.burtellfire.com
please don't print this e-mail unless you really need to
___
Sprinklerforum
said a
word.
Best regards,
Joe Burtell, SET, CFPS
Burtell Fire Protection
Phone: 406.652.7697
Fax: 406.652.7743
Cell: 406.861.4507
Email: j...@burtellfire.com
Web Site: http://www.burtellfire.com
please don't print this e-mail unless you really need to
-Original Message-
From
NFPA 13 02'
A.8.3.3.1 When renovations occur in an existing building and no changes are
made in the existing
sprinkler system, this section is not intended to require the replacement of
existing standard
sprinklers with quick-response sprinklers.
Might work for you.
Best regards,
Joe Burtell
The extra pressure required, does it not come from the big red pumper truck
parked in front of the burning building?
Best regards,
Joe Burtell, SET, CFPS
Burtell Fire Protection
Phone: 406.652.7697
Fax: 406.652.7743
Cell: 406.861.4507
Email: j...@burtellfire.com
Web Site: http
on their use?
Joe Burtell
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Steve Leyton
Sent: Thursday, November 05, 2009 1:32 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: NFPA 14i
Not if it's a high
Are the jockey and fire pump not using sensing lines?
Joe Burtell
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Todd Williams
Sent: Monday, November 02, 2009 9:07 AM
To: sprinklerforum@firesprinkler.org
Sure seems like CPVC is too fragile for something as serious as fire
protection. The list of compatible products is far from complete. When
Ridgid dark cutting oil is not on the list, seems something is not right.
Joe Burtell
-Original Message-
From: sprinklerforum-boun
1 - 100 of 192 matches
Mail list logo