The section say's you can omit them from the calc (They still must be
installed) when the design area exceeds the Minimum (1500 SF). You don't
meet or exceed the Min. therefore you must include them in your calc as well
as install them. You've been kicked back to 14.4.4.4.
"Air Tight" which could add to
the discussion, as far as if a fire could grow inside them. Or If a fire
outside could penetrate to the contents in any reasonable time.
Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
Have you considered High-X foam if your water supply is challenged?
Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
- Original Message -
From: "Todd Williams - FPDC" <[EMAIL PROTECTED]>
To:
Sent: Mon
"Exposed" and possibility of Mechanical damage.
Me, as long as our AHJ's will accept the braided Hydraulic hose we'll keep
using it.
Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
- Original Message -
f the
compressor, and we have not seen any failures in this product, or at either
connection. Usually we hard pipe from the compressor to the AMD and then run
the hose from the AMD to the DPV.
Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 97
tial movement, well so is
vibration.
Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
- Original Message -
From: "Roland Huggins" <[EMAIL PROTECTED]>
To:
Sent: Monday, February 11, 2008 9:54 AM
Subject
This would also seem to limit the use of the approved connections of
theAmerican Plywood Assoc. APA for composite wood joist construction.
http://www.apawood.org/level_c.cfm?content=pub_searchresults&pK=Sprinkler%20Installation&pT=Yes&pD=Yes&pF=Yes&CFID=6816509&CFTOKE
of our own
tenant fit outs that it just stated making sense. If your not in the
original remote area, and that area has already been tenant occupied get a
set of those calc's and see what they required. If you are in the remote
area, do the calc.
Thom McMahon
Firetech, Inc.
2560 Copper Rid
Of f the top of my head we're currently doing 8 projects of type V
construction. This is far more common than most people think. (Mostly mixed
use) 3000sf design on one floor, 4 head Res. on the next.
Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel
AIA G-716 (2004)
Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
- Original Message -
From: "Brian Harris" <[EMAIL PROTECTED]>
To:
Sent: Wednesday, February 06, 2008 1:48 PM
Subject: RFI's
Roland:
If the Committee is considering changes to the Res. / 3000 Sf application
area, would that come as a TIA to the 2007, or wait for the next full cycle?
I was talking to another committee member that thought it would move pretty
fast, to correct what they saw as a flaw.
Thom McMahon
http://www.gemplers.com/search/Rust+Converter We've used this on large
flanged fittings, and it works pretty well.
Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
- Original Message -
From: "Jamie Seid
Just a few of the recent topic's of this forum that will be presented at NFPA
World.
Fire test for compact mobile shelving systems
Sprinkler activation with low speed high volume fans (AKA Big Ass Fans)
And many other fun choices for inquiring minds.
Thom McMahon
Firetech, Inc.
2560 C
FDT is the base program for the Quell systems and the accuracy is right on!
(Tyco put a lot into this programs development, and studied a lot of
existing systems and ran comparisons to actual.)
Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Reza:
As Ron points out the FDT program is expensive, but you may actually save
the cost of the program in this one installation if you can reduce from 4
dry systems to just 2. We all need tools to do what we do and FDT is just
another tool.
Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
erior hose allowance, especially if you
have a combination standpipe.
Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
- Original Message -
From: "John O'Connor" <[EMAIL PROTECTED]>
To:
Sent: Thu
There was also an article in FPC mag. and I believe it was also in sprinkler
age on the effect of ceiling fans on water distribution.
Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
- Original Message -
From: "
tween your
soffits, probably a HSW you can meet the obstructions because your deflector
is even with the bottom of the soffits so your spray will cover under the
obstructions.
Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
x27;t say what to do
with elevators in homes.
Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
- Original Message -
From: "Karen Purvis" <[EMAIL PROTECTED]>
To:
Sent: Monday, January 28, 2008 2:39 PM
Subjec
n the street from a
new one lately?)
So maybe we should be asking our customers how long they want it to last. I
think in most cases the answer will be "Until I sell it".
Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
lling to bet that while there
were some very bad water source's early in this century, that today
pollution is far more wide spread. And lets not forget our little genie in
the bottle nuclear waster.
Hard to nail down a source when there are so many possibilities.
Thom McMahon
Firetech, In
Go to Google Earth, Have Kinko's print out a 24x36 of the area, and insert a
sign off location for all those people.
I bet it costs less than going to Sacramento.
Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
- Ori
anything like
that, or does that also depend upon the specific microbe?
Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
- Original Message -
From: "George Church" <[EMAIL PROTECTED]>
To:
Sent: Tuesday, Janua
pped doing inspections, but I still think the training was
worth while. Everyone is different, but if I did it again I'd send my best
guy first, and see if he thinks its worth it for others.
Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fa
. If
we're busy we just use the data to size it and if we get the job so much the
better, extra money in our pocket.
Yes we are still working with the goal not to become a "Non-Profit"
Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-79
and socket type fitting the most
corrosion resistant?
What we really need is a RLS (Relative Life Span) table that addresses the
types of pipe and the joining method's we use today.
Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-79
different.
Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
- Original Message -
From: "Todd Williams - FPDC" <[EMAIL PROTECTED]>
To:
Sent: Tuesday, January 22, 2008 5:53 AM
Subject: Re: When a Spec i
The other one I really like is when they say "Materials shall be as
specified in Div. 15010".
You may see this as "Confrontational" but I'd rather be in his face before
we bid than after we get the project, and I need a lawyer to argue for me.
Sometimes it's ju
ip any possible issue's with 2002.
Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
- Original Message -
From: "Jeff Hewitt" <[EMAIL PROTECTED]>
To:
Sent: Friday, January 18, 2008 12:45 PM
Subject:
will accept the new Standard if presented as an alternate.
Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
- Original Message -
From: "Kurt Kingston" <[EMAIL PROTECTED]>
To:
Sent: Friday, January 18, 2008
We currently are doing a panel construction parking structure under a mixed
use building, and are relying on the fire proofing to fill those voids.
The spray on application generally does a pretty good job.
Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel
Off the top of my head (6'-2"+) I'd say a pilot line deluge system, similar
to a covered conveyor system. But hey that's just me.
Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
- Original Message
Don't forget that as of Jan 1, 2008 computer generated hydraulic reports
shall be as per NFPA 13, 2007 22.3.5.
So while not requiring a listing for hydraulic programs, NFPA 13 does
require a specific minimum format and order.
Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Sp
sleeved bore.
The boring machine was driven off course by the large boulders under the
road bed, and we eventually abandoned this method, ended up digging up two
city blocks of sidewalk (Vs. the 80LF across the Hwy.) to connect to another
city main in a side street. All of our water mains are
the system into two smaller systems to avoid the delivery time
issue entirely.
Good Luck!
Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
- Original Message -
From: "Charles Thurston" <[EMAIL PROTECT
requirement, EH seems a bid of over kill. What is the replacement value of
the building? The cows? The hay? Product interruption? If these are not very
high costs, an excessive system may not be in the owner best interest. Ask
the insurance underwriter, he's insuring all this value.
Thom Mc
e of the cover plate does
move star HGF-3752-1 one million light years out of position, will it even
be noticeable to the unaided human eye? Planetariums give the visual
"Effect" of standing in place an looking out into space, not the reality.
My 2 cents and worth about 1/2 of that
d for some
suppression, but not to support the standpipe.
Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
- Original Message -
From: "Greg McGahan" <[EMAIL PROTECTED]>
To:
Sent: Thursday, January 10, 2008
se in testing Dry Manual
standpipes?
Thanks for any help
Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
yer, ice may form and restrict flow, when water is
introduced into the system. )
Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
- Original Message -
From: "Randy Knutson" <[EMAIL PROTECTED]>
To:
Sent: Friday
See Croker 6641 or 6642, Potter Roemer 5850 or 5852 or other mfg.
Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
- Original Message -
From: "Dewayne Martinez" <[EMAIL PROTECTED]>
To:
Sent: Friday, D
If they just weren't so few and far up north.
Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
- Original Message -
From: "Mark Sornsin" <[EMAIL PROTECTED]>
To:
Sent: Friday, December 21, 200
Another unsprinklered federal office building?
Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http
The Mechanical code OSHA and Health dept. set limits on the temp. under
these hoods. Typically about 100'F with occasional 120'F. Hood chem systems
still tend to use 212'F release links, unless there is a lot of open flame.
Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamb
at 1 in 3 occur the
water supply will arrive much faster since the source is now much closer to
the operating area.
Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
- Original Message -
From: "Ed Vining" <[
Also always consider this, When the weather gets bad they'll move the Bar-BQ
grill under that deck on the patio and keep on grilling.
Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
- Original Message -
From: &q
and shield
assemblies make it more user friendly than rock-wool where you can have "Hot
Hangers".
Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
- Original Message -
From: "Frans Stoop" <[EMAIL PROTECT
MIC the tiny rat's of steel pipe!
Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
- Original Message -
From: "John Drucker" <[EMAIL PROTECTED]>
To:
Sent: Saturday, December 15, 2007 4:26 AM
application area are made without adjustment to the density)
Also chapter 21 gives specific area/density designs for specific
application's which should always be reviewed for appropriateness.
Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax
We've done Auto Spray booths with High Velocity round ducts on the exhaust
using Flex heads duct mate product and had very good success and fit.
Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
- Original Me
us shouldn't wait for it to be "Code" before we adopt good practices. So
before you climb up that curve, ask yourself "Do Ya Feel Lucky?"
Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
- Ori
Didn't Roland hit on this subject at AFSA PX and say something like the
building had to be "Auxiliary" to the main building. Something like a pump
house or such.
Roland feel free to chime in any time?
Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 8048
e domestic
as well as the sprinklers are required to be supervised.
Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
- Original Message -
From: "Chris Cahill" <[EMAIL PROTECTED]>
To:
Sent: Monday, November
tell if its
working?)
Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
- Original Message -
From: "John Drucker" <[EMAIL PROTECTED]>
To:
Sent: Monday, November 26, 2007 11:24 AM
Subject: RE: Wow - Info-
The minimum Psi used to be 10Psi for storage occupancies with the ELO 231.
Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
- Original Message -
From: "Joe Burtell" <[EMAIL PROTECTED]>
To:
Sent: Tues
Looks like they dropped the 10 Psi requirement, last seen in 2-01 cut
sheets.
Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
- Original Message -
From: "Joe Burtell" <[EMAIL PROTECTED]>
To:
Sent: T
d
be very interesting to understand how their testing differs from NFPA 13's.
Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
- Original Message -
From: "Bill Minkel" <[EMAIL PROTECTED]>
To:
Sent:
dditional heads
requested by the Arch.
Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
- Original Message -
From: "Greg McGahan" <[EMAIL PROTECTED]>
To:
Sent: Friday, November 16, 2007 4:36 PM
Subj
Oh the under 21 age group, if I remember right the second highest at risk
group in a fire after the over 55 age group.
Yeah they're fast when they are not impaired, but with that age group just
being a teenager could very well be the only impairment you'd need to
consider.
Th
Oops 8.15.8.1.2
Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
- Original Message -
From: "Thom McMahon" <[EMAIL PROTECTED]>
To:
Sent: Friday, November 16, 2007 1:14 PM
Subject: Re: 13 vs 13R; 10
NFPA 2007 8.15.1.2 Sprinklers shall be required in bathrooms of limited care
facilities and nursing homes as defined in NFPA 101.
Pretty clear that you should be doing it.
Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
Anything less than 21' deep and all he needs is a length of 1" to suck air
thru.
Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
- Original Message -
From: "Dennis Browning" <[EMAIL PROTECT
wide that head could protect the entire area
under those risers. (Depending upon occupancy and spacing, head type ect.)
Your next head would be in the highest ceiling. There are so many variables,
that you'll need to check very carefully before you try to apply this, and
skip heads in the
some time educating
him/her. You'll probably end up around 250 Gpm total for 30 heads.
Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
- Original Message -
From: "A.P.Silva" <[EMAIL PROTECTED]>
these split rings is
actually 900 Lbs -250=650/5 = 130 Lbs actual load for the water filled pipe.
Even 11/4" LW pipe is only about 2.2 Lbs per LF water filled.
You may wish to check with some engineering library for the MSS standards,
and verify that they do indeed use 5x as a safe
Your ceiling still has to meet ASTM C 635 and be installed in accordance
with ASTM C 636. Check out the part (9.2.1.3.3.3) where Flees hoses were
limited to 6' or less than 6', otherwise you have to put a hanger on it. And
we're not even talking seismic yet.
Thom McMahon
Fire
rger) Hilti will come and do a test pull for
you, before you order 2000 pieces and find you need 3" into concrete to meet
load vs 11/2"
(Other fine brands sold by associate members may also perform
satisfactorily)
Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 8
it, if un restrained.
I don't believe that the committee, considered drops this long attached to
"Flex Heads" up to 5'-0" long when they were considering restraint
requirements. Might make a good proposal.
Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Ste
Not with a quick bolt, but with HILTI studs shot into concrete.
Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
- Original Message -
From: "Bill Minkel" <[EMAIL PROTECTED]>
To:
Sent: Thursday, Novemb
be a superior
solution, and potentially a lower cost means to meet the requirements.
Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
- Original Message -
From: "Bobby Gillett" <[EMAIL PROTECTED]>
I told you about the heads we found with caulked on cover plates 2" below
the cup didn't I?
Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
- Original Message -
From: "George Church" <[EMAIL
Colorado requires 10 PSI or 10% (Which ever is less) safety factor for all
calc's except 13D systems.
Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
- Original Message -
From: "Chris Cahill" <[EMA
Actually many of these applications are such that were this option not
available they would opt. to leave out protection, or have to install an
expensive alternative system. This choice is usually made by the
Arch/owner's rep. not the Sprinkler guy.
Thom McMahon
Firetech, Inc.
2560 C
Also the ICC evaluation service report on window sprinklers is available on
line, but I'm not sure if your required to be a member to access it.
Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
- Original Me
If plumbers are registered or lic. in Pa maybe you could have the Rotorooter
guy sign off?
Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
- Original Message -
From: "George Church" <[EMAIL PROTECTED
o not provide sprinklers under wall hung
cabinets (Kitchen cabinets)
Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
- Original Message -
From: "Richard Mote" <[EMAIL PROTECTED]>
To:
Sent: Tuesday
as an obstruction to a spray pattern from a sidewall on the
opposite
wall. If this is the case, I guess we also have to consider the wall as
an
obstruction to the spray pattern. Must be a rule for this somewhere.
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] O
en that condition is
not present.
If a soffit is low enough for the spray from a HSW to hit it, it will
prevent wall wetting, and disrupt the development of the spray pattern that
would be developed if it were not present.
Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO
n you will have
to meet the rules of Table 8.10.7.1.3 "Positioning of sprinklers to avoid
obstructions (residential sidewall sprinklers) This is as directed
8.10.7.1.3 for obstructions more than 8'-0" from the sprinkler.
Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steambo
l have
to meet the rules of Table 8.10.7.1.3 "Positioning of sprinklers to avoid
obstructions (residential sidewall sprinklers) This is as directed
8.10.7.1.3 for obstructions more than 8'-0" from the sprinkler.
Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Spring
I don't believe that any of the major MFG have one you'll probably have to
build your own by-pass with a 3/4" DCV and Meter around the 11/2" DCV.
Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
--
Yes they do! The Fire X trol line is both UL and asme compliant. (If you
have attended the AFSA convention in Phoenix, you should have received or
will shortly receive the CD for sizing , listing and product selection) For
those not in attendance look on line.
Thom McMahon
Firetech, Inc.
2560
John:
I believe that NJ is one of the states that enacted Dorm sprinkler
requirements after the Seton Hall Fire. Is that correct? Do you know how
many other states have enacted similar ordinances?
Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879
George can tell ya but then as per the TYCO agreement he'd have to Kill ya.
Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
- Original Message -
From: "Chris Cahill" <[EMAIL PROTECTED]>
To:
Se
quirement to do this but we have always felt the this
is protection for the "Main Route of Egress" which only makes sense if your
entire system is only to provide enough time for the occupants to safely
leave the home. What have others been doing and why?
Thom McMahon
Firetech, Inc.
At .5 density I think you've reached the bottom of the flow switch range
anyway, so it probably won't alarm.
Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
- Original Message -
From: "Ken H
ethods to reduce the pipe
exposure temperatures. These pipe and fittings are not intended to be
installed in outdoor applications."
This would be similar to installing CPVC in a flat roof made of TJI's, and
filled with Insul.
Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamb
Come on G: They still let you bid work. That's the contractors equivalent of
"Fear Factor" everything else we do is just to see how good we guess.
Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
- O
G:
We haven't been able to get a .005 density out of Res. heads for several
years now, since they made everyone go to 0.05.
Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
- Original Message -
From: "Geo
If you have to chose between the two, use the spacing as if the wall were
solid, and ask to install a baffle from the top of the wall down 2'-0" to
stop the cold solder. If visibility is an issue use a clear element for the
baffle such as glass or poly carbonate sheets.
Thom McMaho
(Most AHJ's don't allow the heads
to be added as a retrofit, with a 1/2" nipple to a 1x1/2 ell or such, they
rightly believe that if the area was always intended to have a tenant fit
out with the possibilities of a lower ceiling then that should have been
allowed for in the origin
Wilkins , Watts, Armstrong, Victaulic and others
Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
- Original Message -
From: "Todd Williams - FPDC" <[EMAIL PROTECTED]>
To:
Sent: Monday, October 1
George:
Sorry no experience with 13R Fire Pumps, I know TALCO advertises them, but
we've never had a need for one. On their 13D pumps they have always given us
what we wanted regardless of if it was "Stock" or "Standard", which ours
usually aren't.
Thom McMa
fire if it
starts low.
Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
- Original Message -
From: <[EMAIL PROTECTED]>
To:
Sent: Thursday, October 11, 2007 9:36 AM
Subject: RE: Polyester film
Polyester fil
Tom:
www.misco.com makes digital refractor to read both.
Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
- Original Message -
From: "Tom Duross" <[EMAIL PROTECTED]>
To:
Sent: Wednesday, October
Chris:
I believe that this is also to verify the pressure drop across a BFP device
where it is used as the riser check with the requirement for full forward
flow test connection, if the gauges are any good you could read the pressure
drop. (13 committee members help?)
Thom McMahon
Firetech
front of the
RPZ, then the spike hits a closed valve and goes elsewhere, much larger
pressure loss than either a single check or double check assembly, but the
big advantage is "Set it and Forget it" if it saves just one 90 min. drive
its worth it.
Thom McMahon
Firetech, Inc.
2560 Coppe
the final solution was? If my memory hasn't gone entirely, I think they just
gave the property owners a time extension, not an exemption.
Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
- Original Message -
Fr
ted to the "War On TERROR!" I can't see any lessen
of the protection of the nations water supply no matter what the statistic's
are, or say. We must be afraid, we must be very afraid. (Especially if it
sells more backflow prevetors.)
Thom McMahon
Firetech, Inc.
2560 Copper
ably will. Once again you need to "Educate your Owner" its a
never ending job, but still a very important part of our business. They
don't have to like it, but if they understand the under lying reasons, it
may soften the financial blow.
Thom McMahon
Firetech, Inc.