Limited Area sprinkler systems

2009-03-31 Thread Todd Williams
The IBC mentions Limited Area sprinkler systems with a veiled 
reference being 20 sprinklers or less. However, there is no formal 
definition or description as to what they are or where they are 
allowed. Any thoughts or experience with this? I have a proposal on 
my desk for a partial system covering some sleeping rooms above a 
restaurant (for employees). The rest of the building is unprotected. 
Supposedly it is being required to renew their liquor permit. Since I 
doubt the Liquor Commission has jurisdiction over fire protection, 
I'm assuming that this is coming from the Fire Marshal.

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535 
___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: Limited Area sprinkler systems

2009-03-31 Thread Karen Purvis
I have done a few of these type systems. Usually the ones I have done
involve a mechanical room with a gas furnace or an elevator equipment room.

Karen Purvis
Senior Designer
Facility Systems Consultants
713 South Central Street,
Suite 101
Knoxville, TN 37902
ph.865-246-0164
fax 865-246-1084
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Todd Williams
Sent: Tuesday, March 31, 2009 7:44 AM
To: sprinklerforum@firesprinkler.org
Subject: Limited Area sprinkler systems

The IBC mentions Limited Area sprinkler systems with a veiled 
reference being 20 sprinklers or less. However, there is no formal 
definition or description as to what they are or where they are 
allowed. Any thoughts or experience with this? I have a proposal on 
my desk for a partial system covering some sleeping rooms above a 
restaurant (for employees). The rest of the building is unprotected. 
Supposedly it is being required to renew their liquor permit. Since I 
doubt the Liquor Commission has jurisdiction over fire protection, 
I'm assuming that this is coming from the Fire Marshal.

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535 
___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: Birdcage systems

2009-03-31 Thread Chris Cahill
Not an issue. In a birdcage the riser is not serving and area greater than
5000 sq.ft. (usually).  There may be dozens or dozens of dozens of risers.
And it's not exactly clear in the definitions but in a birdcage the vertical
piping more closely matches the definition of a branch line. 

Chris Cahill, P.E.
Fire Protection Engineer
Sentry Fire Protection, Inc.
 
763-658-4483
763-658-4921 fax
 
Email: chr...@sentryfiremn.com
 
Mail: P.O. Box 69
Waverly, MN 55390
 
Location: 4439 Hwy 12 SW
  Waverly, MN 55390
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Ed Kramer
Sent: Monday, March 30, 2009 10:06 PM
To: sprinklerforum@firesprinkler.org
Subject: Birdcage systems

Another post got me thinking (stand back).  Section 8.15.21 and its
commentary seem to require a multistory building be designed so each floor
can be isolated while leaving the remainder of the system operational.  If
that's the case, birdcage systems are doo-doo.   Now I've designed a lot of
these type systems, so no high horse here.  Just wondering how everybody
(especially  AHJ's) interprets or enforces this section.

 

Ed Kramer

Littleton, CO

___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: Limited Area sprinkler systems

2009-03-31 Thread Todd Williams
I've done a few of the partial systems according to NFPA 101, but as 
you say, it is just a couple of heads in a space. That tops out a 6 
sprinklers. However, the IBC one appears to go to 20. The one I have 
been asked to look at is 18.



At 08:32 AM 3/31/2009, you wrote:
I have done a few of these type systems. Usually the ones I have done
involve a mechanical room with a gas furnace or an elevator equipment room.

Karen Purvis
Senior Designer
Facility Systems Consultants
713 South Central Street,
Suite 101
Knoxville, TN 37902
ph.865-246-0164
fax 865-246-1084
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Todd Williams
Sent: Tuesday, March 31, 2009 7:44 AM
To: sprinklerforum@firesprinkler.org
Subject: Limited Area sprinkler systems

The IBC mentions Limited Area sprinkler systems with a veiled
reference being 20 sprinklers or less. However, there is no formal
definition or description as to what they are or where they are
allowed. Any thoughts or experience with this? I have a proposal on
my desk for a partial system covering some sleeping rooms above a
restaurant (for employees). The rest of the building is unprotected.
Supposedly it is being required to renew their liquor permit. Since I
doubt the Liquor Commission has jurisdiction over fire protection,
I'm assuming that this is coming from the Fire Marshal.

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535
___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080  
___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: PODs storage again

2009-03-31 Thread Ray Vance
Travis,

This product commodity falls within the same parameters as boat storage - there 
is no prescriptive requirement to follow.
In fact, NFPA has issued a statement this particular type of storage 
arrangement is outside the scope of NFPA-13.

That being said, I have done a fair amount of research into the PODS type 
storage arrangements for my own education and can offer the following as a 
starting point (guidelines) for your consideration.

(A) I spoke, at length, with Ms. Elley Klausbruckner at Klausbruckner and 
Assoc. regarding the general requirements for this PODS type storage and 
specifically about your particular type of storage arrangement. Ms. 
Klausbruckner is a fire protection engineer and specializes in HPR risk 
analysis and protection and has been involved in many warehouse storage 
arrangements of this PODS/Crate type storage, including the brand name PODS 
facilities.
(B) In all cases except one, they have designed the fire sprinkler system as an 
Exposed, Unnexpanded, Group-A plastic commodity storage arrangement.
(C) In all cases except one, they have designed utilizing ESFR sprinklers, 
unless the building construction prohibited the ESFR protection. In the 
scenario where the building construction would not allow ESFR, they designed 
utilizing the area/density method for the appropriate storage height.
(D) In the one case where they did NOT protect as a Group-A plastic commodity 
the pods/crates were constructed entirely of wood. In this scenario they 
required a letter from the owner of the facility that the amount of Group-A 
plastics within the pods/crates at any time were less than 5% to 15% by weight 
or 5% to 25% by volume. The crate itself was treated as part of the unit load 
and the entire unit load was classified as a Class-IV commodity.
(E) For reference, upholstered furniture is classified as a Class-IV commodity 
per the IFC 2303.5 (See IFC Figure 2303.7.4)
(F) Tyco Fire Products, per their own internal technical document also 
indicates ESFR protection for PODS type storage that have plastic tops on the 
containers.
(G) An analysis done by Rolf Jensen and Associates and written up in the 2006 
Edition of Fire Protection Engineering Magazine suggests the use of ESFR 
sprinklers for the Group-A plastics scenario as well, but also indicates a dual 
design area/density as another design option.

I know some of our esteemed colleagues are still not entirely comfortable with 
the determination of the protection schemes for this particular type of storage 
and there is NO prescriptive direction from NFPA on the subject. However, they 
have been and are being built all over the country and are being sprinklered in 
some fashion. We can only provide the protection scheme that is most consistant 
with the experts in our field, FP engineers with risk analysis experience, 
and provide the protection scheme as determined by them.

The consensus from my personal research, at least at this point, is to protect 
as an Exposed, Unexpanded, Group-A plastic commodity and provide ESFR 
protection if the building construction allows.

I implore those of you with the expertise above and beyond what Travis and I 
have to weigh in and provide your insights and experiences into this commodity 
storage.

As always, have and AWESOME day!

Ray Vance - SET
Wayne Automatic Fire Sprinklers, Inc.
www.waynefire.com
(407) 877-5563   office
(321) 436-2184   mobile

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org 
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Travis Mack, SET
Sent: 2009-03-30 5:30 PM
To: sprinklerforum@firesprinkler.org
Subject: PODs storage again

I tried to search the archives, but keep getting a file not found error.  I am 
looking at a PODs storage warehouse.  There was a lot of discussion on the 
forums a while back, but I can't access all of it.  The facility I am looking 
at has 24' storage.

What is the general concensus of the protection req'd for these areas?

Thanks in advance for your help.



Travis Mack, SET
___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: Limited Area sprinkler systems

2009-03-31 Thread Eric Shelton
Actually, the IBC section on limited area sprinkler systems goes up to 19 heads 
(fewer than 20).  It also requires a hydraulic calc with a simultaneous 
plumbing demand.


Eric J. Shelton, PE
Senior Fire Protection Engineer

Hankins and Anderson
Consulting Engineers
4880 Sadler Road Suite 300
Glen Allen, VA 23060
 
v: (804) 521.7105 f: (804) 217.8520
http://www.haengineers.com


 Do you really need to print this e-mail?


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org 
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Todd Williams
Sent: Tuesday, March 31, 2009 8:56 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Limited Area sprinkler systems

I've done a few of the partial systems according to NFPA 101, but as 
you say, it is just a couple of heads in a space. That tops out a 6 
sprinklers. However, the IBC one appears to go to 20. The one I have 
been asked to look at is 18.



At 08:32 AM 3/31/2009, you wrote:
I have done a few of these type systems. Usually the ones I have done
involve a mechanical room with a gas furnace or an elevator equipment room.

Karen Purvis
Senior Designer
Facility Systems Consultants
713 South Central Street,
Suite 101
Knoxville, TN 37902
ph.865-246-0164
fax 865-246-1084
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Todd Williams
Sent: Tuesday, March 31, 2009 7:44 AM
To: sprinklerforum@firesprinkler.org
Subject: Limited Area sprinkler systems

The IBC mentions Limited Area sprinkler systems with a veiled
reference being 20 sprinklers or less. However, there is no formal
definition or description as to what they are or where they are
allowed. Any thoughts or experience with this? I have a proposal on
my desk for a partial system covering some sleeping rooms above a
restaurant (for employees). The rest of the building is unprotected.
Supposedly it is being required to renew their liquor permit. Since I
doubt the Liquor Commission has jurisdiction over fire protection,
I'm assuming that this is coming from the Fire Marshal.

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535
___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080  
___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

RE: PODs storage again

2009-03-31 Thread Chris Cahill
The only hole in the thinking of the experts is their opinions are based
on WAG not SWAG to my knowledge.  I'm not suggesting they are wrong. I'd
trust their knowledge a bit more if they had some test data (which doesn't
exist) or at least some examples of fires and the outcome.  Sure would be
nice if they point to a fire with ESFR that was successfully contained.  Has
that happened and I'm not aware definitely probable. 

Think of it like this you see a problem with system and the contractor says
well I've always done it like that.  Doesn't make it right does it?  

And ESFR scares me a bit with its tendency to either work fully or burn the
place down.  At least with density systems there is a little reserve in my
experience. 

And I'm totally comfortable if Elley or Rolf sign the design as EOR.  Make
it LH and I'm cool with their design.  

Chris Cahill, P.E.
Fire Protection Engineer
Sentry Fire Protection, Inc.
 
763-658-4483
763-658-4921 fax
 
Email: chr...@sentryfiremn.com
 
Mail: P.O. Box 69
Waverly, MN 55390
 
Location: 4439 Hwy 12 SW
  Waverly, MN 55390

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Ray Vance
Sent: Tuesday, March 31, 2009 8:09 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: PODs storage again

Travis,

This product commodity falls within the same parameters as boat storage -
there is no prescriptive requirement to follow.
In fact, NFPA has issued a statement this particular type of storage
arrangement is outside the scope of NFPA-13.

That being said, I have done a fair amount of research into the PODS type
storage arrangements for my own education and can offer the following as a
starting point (guidelines) for your consideration.

(A) I spoke, at length, with Ms. Elley Klausbruckner at Klausbruckner and
Assoc. regarding the general requirements for this PODS type storage and
specifically about your particular type of storage arrangement. Ms.
Klausbruckner is a fire protection engineer and specializes in HPR risk
analysis and protection and has been involved in many warehouse storage
arrangements of this PODS/Crate type storage, including the brand name PODS
facilities.
(B) In all cases except one, they have designed the fire sprinkler system as
an Exposed, Unnexpanded, Group-A plastic commodity storage arrangement.
(C) In all cases except one, they have designed utilizing ESFR sprinklers,
unless the building construction prohibited the ESFR protection. In the
scenario where the building construction would not allow ESFR, they designed
utilizing the area/density method for the appropriate storage height.
(D) In the one case where they did NOT protect as a Group-A plastic
commodity the pods/crates were constructed entirely of wood. In this
scenario they required a letter from the owner of the facility that the
amount of Group-A plastics within the pods/crates at any time were less than
5% to 15% by weight or 5% to 25% by volume. The crate itself was treated as
part of the unit load and the entire unit load was classified as a Class-IV
commodity.
(E) For reference, upholstered furniture is classified as a Class-IV
commodity per the IFC 2303.5 (See IFC Figure 2303.7.4)
(F) Tyco Fire Products, per their own internal technical document also
indicates ESFR protection for PODS type storage that have plastic tops on
the containers.
(G) An analysis done by Rolf Jensen and Associates and written up in the
2006 Edition of Fire Protection Engineering Magazine suggests the use of
ESFR sprinklers for the Group-A plastics scenario as well, but also
indicates a dual design area/density as another design option.

I know some of our esteemed colleagues are still not entirely comfortable
with the determination of the protection schemes for this particular type of
storage and there is NO prescriptive direction from NFPA on the subject.
However, they have been and are being built all over the country and are
being sprinklered in some fashion. We can only provide the protection scheme
that is most consistant with the experts in our field, FP engineers with
risk analysis experience, and provide the protection scheme as determined by
them.

The consensus from my personal research, at least at this point, is to
protect as an Exposed, Unexpanded, Group-A plastic commodity and provide
ESFR protection if the building construction allows.

I implore those of you with the expertise above and beyond what Travis and I
have to weigh in and provide your insights and experiences into this
commodity storage.

As always, have and AWESOME day!

Ray Vance - SET
Wayne Automatic Fire Sprinklers, Inc.
www.waynefire.com
(407) 877-5563   office
(321) 436-2184   mobile

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Travis Mack,
SET
Sent: 2009-03-30 5:30 PM
To: sprinklerforum@firesprinkler.org
Subject: PODs storage again


Re: Limited Area sprinkler systems

2009-03-31 Thread Roland Huggins
As identified by Karen, the IBC allows some locations (such as furnace  
rooms) to be individually protected (or a higher degree of  
separation).  This is providing protection from this room to the rest  
of the building.  So I guess the sleeping room is such a hazard that  
the rest of the building needs protection from it?  More backwards  
thinking from a very qualified source.  Wear your pointed boots when  
you talk to them.

Roland

On Mar 31, 2009, at 4:43 AM, Todd Williams wrote:

 The IBC mentions Limited Area sprinkler systems with a veiled
 reference being 20 sprinklers or less. However, there is no formal
 definition or description as to what they are or where they are
 allowed. Any thoughts or experience with this? I have a proposal on
 my desk for a partial system covering some sleeping rooms above a
 restaurant (for employees). The rest of the building is unprotected.
 Supposedly it is being required to renew their liquor permit. Since I
 doubt the Liquor Commission has jurisdiction over fire protection,
 I'm assuming that this is coming from the Fire Marshal.

 Todd G. Williams, PE
 Fire Protection Design/Consulting
 Stonington, Connecticut
 www.fpdc.com
 860.535
 ___
 Sprinklerforum mailing list
 http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
 For Technical Assistance, send an email to: techsupp...@firesprinkler.org

 To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
 (Put the word unsubscribe in the subject field)


___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: PODs storage again

2009-03-31 Thread Chris Cahill
While true initially the HPR then is replaced next year by Billy Bob Joe's
Insurance and they sue the contractor when it fails.  HPR didn't legally
engineer it as they are not the EOR usually even though they often drive a
design, Codes don't cover it.  You are out on your own at that point.
proceed very cautiously is very wise.   

Chris Cahill, P.E.
Fire Protection Engineer
Sentry Fire Protection, Inc.
 
763-658-4483
763-658-4921 fax
 
Email: chr...@sentryfiremn.com
 
Mail: P.O. Box 69
Waverly, MN 55390
 
Location: 4439 Hwy 12 SW
  Waverly, MN 55390
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Roland
Huggins
Sent: Tuesday, March 31, 2009 10:59 AM
To: sprinklerforum@firesprinkler.org
Subject: Re: PODs storage again

  If the HPR insurance company makes a judgement call on how to  
protect it and it doesn't work, they pay for the loss.  IF this  
guidance is not in the published HPR Loss Prevention Data sheets, then  
the consult is making the judgement call.  Guess who will likely pay  
for the loss?  Now here's the scary part. If the contractor takes the  
responsibility and provides the judgement  call (typically considered  
consulting/engineering since guidance is not in 13 or other national  
standards) who will likely pay the claim?

The moral of the story is when NFPA 13 does not address it, proceed  
very cautiously.

Roland

On Mar 31, 2009, at 6:50 AM, Chris Cahill wrote:

 The only hole in the thinking of the experts is their opinions are  
 based
 on WAG not SWAG to my knowledge.  I'm not suggesting they are wrong.  
 I'd
 trust their knowledge a bit more if they had some test data (which  
 doesn't
 exist) or at least some examples of fires and the outcome.  Sure  
 would be
 nice if they point to a fire with ESFR that was successfully  
 contained.  Has
 that happened and I'm not aware definitely probable.

 Think of it like this you see a problem with system and the  
 contractor says
 well I've always done it like that.  Doesn't make it right does it?

 And ESFR scares me a bit with its tendency to either work fully or  
 burn the
 place down.  At least with density systems there is a little reserve  
 in my
 experience.

 And I'm totally comfortable if Elley or Rolf sign the design as  
 EOR.  Make
 it LH and I'm cool with their design.

 Chris Cahill, P.E.
 Fire Protection Engineer
 Sentry Fire Protection, Inc.

___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: RESIDENTIAL OCCUPANCY DRY SYSTEM

2009-03-31 Thread Thom McMahon
This requirement for 15 Sec. delivery in residential dry systems already
exists in NFPA 13 2007, Table 7.2.3.6.1

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Ed Kramer
Sent: Monday, March 30, 2009 8:51 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: RESIDENTIAL OCCUPANCY DRY SYSTEM

The NFPA 13 ROP and ROC both have items that should help clear up the issue.
IF the proposals are accepted as written, any sprinkler protecting a
dwelling unit (residential or QR) fed from a dry system will have to deliver
water within 15 sec.  (Reference section 7.2.3 and subsections)

Ed Kramer
Littleton, CO

 Art,
 
 Where does the 15 seconds come from? I can't find anything in 13. Is 
 it 101? is it a local requirement?
 

___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: PODs storage again

2009-03-31 Thread Thom McMahon
1. If you can get the insurer to spec the design, good.
2. If the EOR spec's the design, protect yourself as best you can. Refer all
questions of changes to them so they assume responsibility for every
decision.
3. If you as a contractor are asked to make the design decisions, Walk, Run,
take a plane to your favorite get away, but refuse the job.

Sometimes the best thing for both you and the customer is to not do the job,
as presented.

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926



-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Roland
Huggins
Sent: Tuesday, March 31, 2009 9:59 AM
To: sprinklerforum@firesprinkler.org
Subject: Re: PODs storage again

  If the HPR insurance company makes a judgement call on how to protect it
and it doesn't work, they pay for the loss.  IF this guidance is not in the
published HPR Loss Prevention Data sheets, then the consult is making the
judgement call.  Guess who will likely pay for the loss?  Now here's the
scary part. If the contractor takes the responsibility and provides the
judgement  call (typically considered consulting/engineering since guidance
is not in 13 or other national
standards) who will likely pay the claim?

The moral of the story is when NFPA 13 does not address it, proceed very
cautiously.

Roland


___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


Re: RESIDENTIAL OCCUPANCY DRY SYSTEM

2009-03-31 Thread Roland Huggins
true but the text is weakly worded.  The section that references the  
Table says based on the hazard not the type of sprinkler (as does  
the Table).  I believe the intent was for residential sprinklers (for  
which a 15 sec requirement exists as part of the listing test  
standard) but writing what you mean can be a challenge.  As pointed  
out by Ed, the 2010 clarifies it nicely.  It was an interesting  
evolution.  It started with the standard dry pipe rule: 60 sec for  
systems greater than 500 gal and said any size system protecting  
residential dwellings shall not exceed 60 sec.  Then it was pushed  
down to 15 sec.

Roland

On Mar 31, 2009, at 9:29 AM, Thom McMahon wrote:

 This requirement for 15 Sec. delivery in residential dry systems  
 already
 exists in NFPA 13 2007, Table 7.2.3.6.1

 Thom McMahon, SET

___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: Limited Area sprinkler systems

2009-03-31 Thread Thom McMahon
This is similar to the requirement for Basements over a certain area.
 
903.2.10.1 Stories and basements without openings.
An automatic sprinkler system shall be installed in every
story or basement of all buildings where the floor area
exceeds 1,500 square feet (139.4 m2) and where there is
not provided at least one of the following types of exterior
wall openings:
1. Openings below grade that lead directly to ground
level by an exterior stairway complying with Section
1009 or an outside ramp complying with Section
1010. Openings shall be located in each 50
linear feet (15 240 mm), or fraction thereof, of
exterior wall in the story on at least one side.
2. Openings entirely above the adjoining ground
level totaling at least 20 square feet (1.86 m2) in
each 50 linear feet (15 240 mm), or fraction
thereof, of exterior wall in the story on at least one
side.

You can have a sprinkler system that protects only the basement, or non
complying story. The code doesn't say to provide an automatic sprinkler
system for all buildings that contain, it says the story or basement
shall be protected with automatic sprinklers. (A Partial system, of at least
4 EC heads,[4 x 400 = 1600 SF] or 20 or more depending on the total area.)

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926



-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Roland
Huggins
Sent: Tuesday, March 31, 2009 10:07 AM
To: sprinklerforum@firesprinkler.org
Subject: Re: Limited Area sprinkler systems

As identified by Karen, the IBC allows some locations (such as furnace
rooms) to be individually protected (or a higher degree of separation).
This is providing protection from this room to the rest of the building.  So
I guess the sleeping room is such a hazard that the rest of the building
needs protection from it?  More backwards thinking from a very qualified
source.  Wear your pointed boots when you talk to them.

Roland

On Mar 31, 2009, at 4:43 AM, Todd Williams wrote:

 The IBC mentions Limited Area sprinkler systems with a veiled 
 reference being 20 sprinklers or less. However, there is no formal 
 definition or description as to what they are or where they are 
 allowed. Any thoughts or experience with this? I have a proposal on my 
 desk for a partial system covering some sleeping rooms above a 
 restaurant (for employees). The rest of the building is unprotected.
 Supposedly it is being required to renew their liquor permit. Since I 
 doubt the Liquor Commission has jurisdiction over fire protection, I'm 
 assuming that this is coming from the Fire Marshal.

 Todd G. Williams, PE
 Fire Protection Design/Consulting
 Stonington, Connecticut
 www.fpdc.com
 860.535
 ___
 Sprinklerforum mailing list
 http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
 For Technical Assistance, send an email to: 
 techsupp...@firesprinkler.org

 To Unsubscribe, send an email 
 to:sprinklerforum-requ...@firesprinkler.org
 (Put the word unsubscribe in the subject field)


___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


Re: Limited Area sprinkler systems

2009-03-31 Thread Todd Williams
This is me we're talking about. I'll wear hip waiters and carry a 
bazooka. I got a proposal a few years back for a 58 head system fed 
from 10 separate risers from the 3/4 public connection (6 heads off 
a domestic system times 10 systems, right?). Same town; I hope not 
the same guy.

I have no idea what the logic is behind this, but it's probably not 
sound. I was just wondering if there is anything in IBC that I am 
missing about the Limited Area systems



At 12:06 PM 3/31/2009, you wrote:
As identified by Karen, the IBC allows some locations (such as furnace
rooms) to be individually protected (or a higher degree of
separation).  This is providing protection from this room to the rest
of the building.  So I guess the sleeping room is such a hazard that
the rest of the building needs protection from it?  More backwards
thinking from a very qualified source.  Wear your pointed boots when
you talk to them.

Roland

On Mar 31, 2009, at 4:43 AM, Todd Williams wrote:

  The IBC mentions Limited Area sprinkler systems with a veiled
  reference being 20 sprinklers or less. However, there is no formal
  definition or description as to what they are or where they are
  allowed. Any thoughts or experience with this? I have a proposal on
  my desk for a partial system covering some sleeping rooms above a
  restaurant (for employees). The rest of the building is unprotected.
  Supposedly it is being required to renew their liquor permit. Since I
  doubt the Liquor Commission has jurisdiction over fire protection,
  I'm assuming that this is coming from the Fire Marshal.
 
  Todd G. Williams, PE
  Fire Protection Design/Consulting
  Stonington, Connecticut
  www.fpdc.com
  860.535
  ___
  Sprinklerforum mailing list
  http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
  For Technical Assistance, send an email to: techsupp...@firesprinkler.org
 
  To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
  (Put the word unsubscribe in the subject field)
 

___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080  
___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


Re: Limited Area sprinkler systems

2009-03-31 Thread Ed Vining
This sounds like something as ridiculous as I saw once.  A dorm above a
restaurant

Surely someone is trying to protect the sleeping rooms from a fire in the
restaurant.

And by sprinklering the rooms??

Ed Vining

On Tue, Mar 31, 2009 at 4:43 AM, Todd Williams t...@fpdc.com wrote:

 The IBC mentions Limited Area sprinkler systems with a veiled
 reference being 20 sprinklers or less. However, there is no formal
 definition or description as to what they are or where they are
 allowed. Any thoughts or experience with this? I have a proposal on
 my desk for a partial system covering some sleeping rooms above a
 restaurant (for employees). The rest of the building is unprotected.
 Supposedly it is being required to renew their liquor permit. Since I
 doubt the Liquor Commission has jurisdiction over fire protection,
 I'm assuming that this is coming from the Fire Marshal.

 Todd G. Williams, PE
 Fire Protection Design/Consulting
 Stonington, Connecticut
 www.fpdc.com
 860.535
 ___
 Sprinklerforum mailing list
 http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
 For Technical Assistance, send an email to: techsupp...@firesprinkler.org

 To Unsubscribe, send an email 
 to:sprinklerforum-requ...@firesprinkler.orgto%3asprinklerforum-requ...@firesprinkler.org
 (Put the word unsubscribe in the subject field)




-- 
Ed Vining
4819 John Muir Rd
Martinez CA 94553
925-228-8792
___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: RESIDENTIAL OCCUPANCY DRY SYSTEM

2009-03-31 Thread Tom Duross
I wish that existed many editions ago.  One of our clients have 20+ group
residences built in the 70's and 80's, more like large ranch houses, they
house severely mentally retarded adults.  Most have 3 or 4 DPV's and sch40
systems throughout the attics feeding uprights and dry pendents.  Some of
these systems we wait up to 2 minutes for a solid stream of water and
they're not very large which is the strange part, maybe 2500 SF.  We've done
work on them, accelerators, repaired broken pipe, air compressors, etc., and
even replaced some with perimeter soffitted cpvc wet systems.  I just
scratch my head (and get splinters) on some of these wondering about what
might happen if they ever had to wait that long.  I don't know if there was
some sort of loophole allowing really small pipe in those days (early 13R?)
but most were done by out of state contractors no longer around.

It's very humbling to spend time in one of these settings, even having a
retarded brother.  I had to go there on a Christmas Eve a few years ago for
a head that started leaking and the system tripped, they have to wheelchair
them out to vans with the heaters running, all freaked out, one at a time.
15 seconds is great.  I don't mean to blab on but if it was any kind of use
similar to this one, I'd find a way to provide a wet system if I could.

Tom


true but the text is weakly worded.  The section that references the
Table says based on the hazard not the type of sprinkler (as does
the Table).  I believe the intent was for residential sprinklers (for
which a 15 sec requirement exists as part of the listing test
standard) but writing what you mean can be a challenge.  As pointed
out by Ed, the 2010 clarifies it nicely.  It was an interesting
evolution.  It started with the standard dry pipe rule: 60 sec for
systems greater than 500 gal and said any size system protecting
residential dwellings shall not exceed 60 sec.  Then it was pushed
down to 15 sec.

Roland

On Mar 31, 2009, at 9:29 AM, Thom McMahon wrote:

 This requirement for 15 Sec. delivery in residential dry systems
 already
 exists in NFPA 13 2007, Table 7.2.3.6.1

 Thom McMahon, SET

___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


FW: [NJFireSafety] Upstate NY Group Home Fire - Sprinkler System Failure?

2009-03-31 Thread John Drucker
FYI

 

John Drucker

 

Sent: Monday, March 30, 2009 10:34 PM
Subject: [NJFireSafety] Upstate NY Group Home Fire - Sprinkler System
Failure?

 

An important fire that should be studied

Here is he local newspaper's accounts of the fire. A 13D system?

4 die as plan 'impractical'
State: Evacuation of group home not fast enough to ensure safety of
residents

By RICK KARLIN, Capitol bureau
Click byline for more stories by writer.
First published: Saturday, March 28, 2009

State officials knew it would be impractical to evacuate all nine
residents of the Adirondack group home that caught fire a week ago.

Tragically, they were correct: Four of the home's nine severely disabled
residents died in a pre-dawn blaze March 21 at the Office of Mental
Retardation and Developmental Disabilities' Riverview facility in Wells,
Hamilton County.

According to documents obtained by the Times Union, the Riverview residents
were too frail or immobile to be quickly evacuated in the event of a fire.
For that reason, the home received the slowest of three ratings ? prompt,
slow or impractical ? that OMRDD uses to describe how long an evacuation
should take.

The difficulty of a potential evacuation was anticipated from the very
beginning, said Patricia Martinelli, an OMRDD lawyer. That's the
population we built it for.

Only two of the residents had the ability to exit the ranch-style house
under their own power.

An impractical rating doesn't mean people can't be evacuated, but
represents an acknowledgement that it couldn't be done quickly enough to
ensure the residents' safety given the number of staff members in a
building.

As a result of the rating, and the fact that four of the residents had
previously lived in the notorious Willowbrook center in Staten Island,
Riverview was equipped with a sprinkler system, which is not required in all
OMRDD facilities.

Following a 1972 lawsuit over Willowbrook's conditions, former residents of
the center were accorded extra oversight.

State investigators are continuing to investigate the fire's cause, and it
remained unclear if the building's network of sprinklers and its water
supply functioned as they are supposed to.

We have every reason to believe at this point that they did function,
Martinelli said.

There were two overnight workers at Riverview, and there have been questions
about whether that was adequate given the immobility of the residents and
the impractical'' rating.

The real issue is what was the evacuation plan, and was it adequate,
including the number of staff? asked Beth Haroules, an NYCLU lawyer who
represents the former Willowbrook residents.

Their evacuation plan was inadequate because it clearly failed, she said.

In some OMRDD facilities, evacuation would be so difficult that residents
are supposed to remain in the building behind fire doors, and wait for help.

These so-called defend in place policies, which have been used in some
Central New York OMRDD facilities, are controversial.

It's Russian roulette, said Susan McLaughlin, a former advocate for the
Willowbrook class of residents.

McLaughlin said she had protested a defend in place-style policy that had
been proposed for a facility in Port Leyden, Lewis County. McLaughlin is
currently suing the state over what she contends is her firing for acting as
a whistleblower regarding OMRDD problems.

According to OMRDD documents, the Riverview facility, which was less than a
year old, was inspected by the state Dormitory Authority and underwent
periodic inspections by OMRDD.

For the most part, OMRDD sets its own standards for evacuation protocol. For
many smaller residences, fire drills call for evacuations within five or six
minutes. OMRDD oversees its own periodic safety inspections, once the
facility is certified by the state Dormitory Authority.

The emerging details of the fire suggests a scene of horror inside the
building as the two overnight workers tried desperately to get people out of
a house that was supposed to be relatively fire-resistant.

According to one report, two of those pulled out of the house suffered rug
burns as workers literally dragged them outside. And two of the dead
supposedly made it to the door of the house, but wandered back toward their
rooms in a disoriented state.

Eyewitness accounts suggested a fast-moving, all-consuming fire. A woman
walking her dog 2 miles away said she saw a red glow in the sky.

Sen. Elizabeth Little, R-Queensbury, surveyed the Riverview fire scene hours
after the blaze. Little said she spoke with one of the two employees on the
11 p.m.-7 a.m. shift, a woman who suffered a dislocated shoulder ? possibly
from trying to pull people to safety.

This is a brand-new house, and how it got so out of control so quickly is
unbelievable, Little said. Bedrooms had large windows at ground level. A
capable person could have lifted the window and stepped out.

It was a sturdy house, added Tony Abrantes, the Lake George builder who
put up the home. He didn't 

FW: CPVC

2009-03-31 Thread Chappell, Carl
Does anyone have any information regarding the request below?  Thanks in
advance.  

 

 

Carl Chappell

 



From: Chris Brown [mailto:cbr...@certifiedlifesafety.com] 
Sent: Tuesday, March 31, 2009 3:45 PM
To: Chappell, Carl
Subject: CPVC 

 

Carl,

 

Can you ask the sprinkler forum if anyone has read a case study
regarding the compounds (oils for protection) used inside steal pipe not
being compatible with CPVC?

 

Thank you,

 

Chris Brown
Managing Partner

 

Certified Life Safety, LLC
5880 West 319th Street
Louisburg, Kansas 66053
Telephone: 913.636.2260
Fax: 913.837.4195
Toll Free: 877.707.FIRE (3473)
Web: www.certifiedlifesafety.com 

 

Email Confidentiality Statement: This message and accompanying documents
are covered by the Electronic Communications Privacy Act, 18 U.S.C.
2510-2521, and contains information intended for the specified
individual(s) only.  This information is confidential.  If you are not
the intended recipient or an agent responsible for delivering it to the
intended recipient, you are hereby notified that you have received this
document in error and that any review, dissemination, copying, or the
taking of any action based on the contents of this information is
strictly prohibited.  If you have received this communication in error,
please notify us immediately by E-mail, and delete the original message.

___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


Re: CPVC

2009-03-31 Thread Forest Wilson
I would contact the manufacturers and lunizol.  
Sent from my Verizon Wireless BlackBerry

-Original Message-
From: Chappell, Carl cchapp...@rjagroup.com

Date: Tue, 31 Mar 2009 18:57:55 
To: sprinklerforum@firesprinkler.org
Subject: FW: CPVC 


Does anyone have any information regarding the request below?  Thanks in
advance.  

 

 

Carl Chappell

 



From: Chris Brown [mailto:cbr...@certifiedlifesafety.com] 
Sent: Tuesday, March 31, 2009 3:45 PM
To: Chappell, Carl
Subject: CPVC 

 

Carl,

 

Can you ask the sprinkler forum if anyone has read a case study
regarding the compounds (oils for protection) used inside steal pipe not
being compatible with CPVC?

 

Thank you,

 

Chris Brown
Managing Partner

 

Certified Life Safety, LLC
5880 West 319th Street
Louisburg, Kansas 66053
Telephone: 913.636.2260
Fax: 913.837.4195
Toll Free: 877.707.FIRE (3473)
Web: www.certifiedlifesafety.com 

 

Email Confidentiality Statement: This message and accompanying documents
are covered by the Electronic Communications Privacy Act, 18 U.S.C.
2510-2521, and contains information intended for the specified
individual(s) only.  This information is confidential.  If you are not
the intended recipient or an agent responsible for delivering it to the
intended recipient, you are hereby notified that you have received this
document in error and that any review, dissemination, copying, or the
taking of any action based on the contents of this information is
strictly prohibited.  If you have received this communication in error,
please notify us immediately by E-mail, and delete the original message.

___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


Re: CPVC

2009-03-31 Thread steve
Absolutely - some anti-MIC 1st generation coatings were identified as 
potentially incompatible, but I heard that has been reconciled in current 
products.  

Steve L. 



Sent from my Verizon Wireless BlackBerry

-Original Message-
From: Forest Wilson cherokeefire...@aol.com

Date: Tue, 31 Mar 2009 17:00:17 
To: sprinklerforum@firesprinkler.org
Subject: Re: CPVC


I would contact the manufacturers and lunizol.  
Sent from my Verizon Wireless BlackBerry 
-Original Message- 
From: Chappell, Carl cchapp...@rjagroup.com 
Date: Tue, 31 Mar 2009 18:57:55 
To: sprinklerforum@firesprinkler.org 
Subject: FW: CPVC 
 
Does anyone have any information regarding the request below?  Thanks in 
advance.  
  
  
Carl Chappell 
  
 
From: Chris Brown [mailto:cbr...@certifiedlifesafety.com 
mailto:cbr...@certifiedlifesafety.com ] 
Sent: Tuesday, March 31, 2009 3:45 PM 
To: Chappell, Carl 
Subject: CPVC 
  
Carl, 
  
Can you ask the sprinkler forum if anyone has read a case study 
regarding the compounds (oils for protection) used inside steal pipe not 
being compatible with CPVC? 
  
Thank you, 
  
Chris Brown 
Managing Partner 
  
Certified Life Safety, LLC 
5880 West 319th Street 
Louisburg, Kansas 66053 
Telephone: 913.636.2260 
Fax: 913.837.4195 
Toll Free: 877.707.FIRE (3473) 
Web: www.certifiedlifesafety.com 
  
Email Confidentiality Statement: This message and accompanying documents 
are covered by the Electronic Communications Privacy Act, 18 U.S.C. 
2510-2521, and contains information intended for the specified 
individual(s) only.  This information is confidential.  If you are not 
the intended recipient or an agent responsible for delivering it to the 
intended recipient, you are hereby notified that you have received this 
document in error and that any review, dissemination, copying, or the 
taking of any action based on the contents of this information is 
strictly prohibited.  If you have received this communication in error, 
please notify us immediately by E-mail, and delete the original message. 
___ 
Sprinklerforum mailing list 
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum 
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum 
For Technical Assistance, send an email to: techsupp...@firesprinkler.org 
To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org 
(Put the word unsubscribe in the subject field) 
___ 
Sprinklerforum mailing list 
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum 
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum 
For Technical Assistance, send an email to: techsupp...@firesprinkler.org 
To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org 
(Put the word unsubscribe in the subject field) 
  
__ Information from ESET NOD32 Antivirus, version of virus signature 
database 3971 (20090328)__ 
The message was checked by ESET NOD32 Antivirus. 
http://www.eset.com http://www.eset.com 
  
___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


RE: CPVC

2009-03-31 Thread Paul Johnson
Carl,

While I am not aware of any published case studies per-se, I do know you can
go to manufacturers' websites for good information.  For Spears, check out
www.spearsmfg.com and click the link for Flameguard information.  Scroll to
the bottom for their document on this topic.  For Blazemaster products, go
to www.systemcompatible.com. Click the systems compatible link and you'll
find their version of what you need.

I hope this helps...

Paul Johnson
Bardane, Inc. Visioning a competitive workforce
(407) 401-7154 - Office
(407) 399-5081 - Mobile 
pjohn...@bardane.net
www.bardane.net 
 
 
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Chappell,
Carl
Sent: Tuesday, March 31, 2009 7:58 PM
To: sprinklerforum@firesprinkler.org
Subject: FW: CPVC 

Does anyone have any information regarding the request below?  Thanks in
advance.  

 

 

Carl Chappell

 



From: Chris Brown [mailto:cbr...@certifiedlifesafety.com] 
Sent: Tuesday, March 31, 2009 3:45 PM
To: Chappell, Carl
Subject: CPVC 

 

Carl,

 

Can you ask the sprinkler forum if anyone has read a case study
regarding the compounds (oils for protection) used inside steal pipe not
being compatible with CPVC?

 

Thank you,

 

Chris Brown
Managing Partner

 

Certified Life Safety, LLC
5880 West 319th Street
Louisburg, Kansas 66053
Telephone: 913.636.2260
Fax: 913.837.4195
Toll Free: 877.707.FIRE (3473)
Web: www.certifiedlifesafety.com 

 

Email Confidentiality Statement: This message and accompanying documents
are covered by the Electronic Communications Privacy Act, 18 U.S.C.
2510-2521, and contains information intended for the specified
individual(s) only.  This information is confidential.  If you are not
the intended recipient or an agent responsible for delivering it to the
intended recipient, you are hereby notified that you have received this
document in error and that any review, dissemination, copying, or the
taking of any action based on the contents of this information is
strictly prohibited.  If you have received this communication in error,
please notify us immediately by E-mail, and delete the original message.

___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


Re: FW: CPVC

2009-03-31 Thread Todd Williams
Contact Blazemaster. They have a publication that lists compatible 
products. I recently picked up a hand out at a trade show.


At 07:57 PM 3/31/2009, you wrote:
Does anyone have any information regarding the request below?  Thanks in
advance.





Carl Chappell





From: Chris Brown [mailto:cbr...@certifiedlifesafety.com]
Sent: Tuesday, March 31, 2009 3:45 PM
To: Chappell, Carl
Subject: CPVC



Carl,



Can you ask the sprinkler forum if anyone has read a case study
regarding the compounds (oils for protection) used inside steal pipe not
being compatible with CPVC?



Thank you,



Chris Brown
Managing Partner



Certified Life Safety, LLC
5880 West 319th Street
Louisburg, Kansas 66053
Telephone: 913.636.2260
Fax: 913.837.4195
Toll Free: 877.707.FIRE (3473)
Web: www.certifiedlifesafety.com



Email Confidentiality Statement: This message and accompanying documents
are covered by the Electronic Communications Privacy Act, 18 U.S.C.
2510-2521, and contains information intended for the specified
individual(s) only.  This information is confidential.  If you are not
the intended recipient or an agent responsible for delivering it to the
intended recipient, you are hereby notified that you have received this
document in error and that any review, dissemination, copying, or the
taking of any action based on the contents of this information is
strictly prohibited.  If you have received this communication in error,
please notify us immediately by E-mail, and delete the original message.

___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080  
___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


Re: FW: [NJFireSafety] Upstate NY Group Home Fire - Sprinkler System Failure?

2009-03-31 Thread Todd Williams
John,

Please keep us informed of how this develops. I have done several 
similar type homes; the last one being for 6 multiple handicapped 
children that are not self rescuing.  All have been full 13 systems 
(wet). If there is a problem, I want to know about it. Fortunately, 
CT allows the locals to oversee pretty much everything and the State 
only gets involved for state-owned project or when asked. Never had a 
butt out line from the state to the locals. Very sad.



At 06:53 PM 3/31/2009, you wrote:
FYI



John Drucker



Sent: Monday, March 30, 2009 10:34 PM
Subject: [NJFireSafety] Upstate NY Group Home Fire - Sprinkler System
Failure?



An important fire that should be studied

Here is he local newspaper's accounts of the fire. A 13D system?

4 die as plan 'impractical'
State: Evacuation of group home not fast enough to ensure safety of
residents

By RICK KARLIN, Capitol bureau
Click byline for more stories by writer.
First published: Saturday, March 28, 2009

State officials knew it would be impractical to evacuate all nine
residents of the Adirondack group home that caught fire a week ago.

Tragically, they were correct: Four of the home's nine severely disabled
residents died in a pre-dawn blaze March 21 at the Office of Mental
Retardation and Developmental Disabilities' Riverview facility in Wells,
Hamilton County.

According to documents obtained by the Times Union, the Riverview residents
were too frail or immobile to be quickly evacuated in the event of a fire.
For that reason, the home received the slowest of three ratings ? prompt,
slow or impractical ? that OMRDD uses to describe how long an evacuation
should take.

The difficulty of a potential evacuation was anticipated from the very
beginning, said Patricia Martinelli, an OMRDD lawyer. That's the
population we built it for.

Only two of the residents had the ability to exit the ranch-style house
under their own power.

An impractical rating doesn't mean people can't be evacuated, but
represents an acknowledgement that it couldn't be done quickly enough to
ensure the residents' safety given the number of staff members in a
building.

As a result of the rating, and the fact that four of the residents had
previously lived in the notorious Willowbrook center in Staten Island,
Riverview was equipped with a sprinkler system, which is not required in all
OMRDD facilities.

Following a 1972 lawsuit over Willowbrook's conditions, former residents of
the center were accorded extra oversight.

State investigators are continuing to investigate the fire's cause, and it
remained unclear if the building's network of sprinklers and its water
supply functioned as they are supposed to.

We have every reason to believe at this point that they did function,
Martinelli said.

There were two overnight workers at Riverview, and there have been questions
about whether that was adequate given the immobility of the residents and
the impractical'' rating.

The real issue is what was the evacuation plan, and was it adequate,
including the number of staff? asked Beth Haroules, an NYCLU lawyer who
represents the former Willowbrook residents.

Their evacuation plan was inadequate because it clearly failed, she said.

In some OMRDD facilities, evacuation would be so difficult that residents
are supposed to remain in the building behind fire doors, and wait for help.

These so-called defend in place policies, which have been used in some
Central New York OMRDD facilities, are controversial.

It's Russian roulette, said Susan McLaughlin, a former advocate for the
Willowbrook class of residents.

McLaughlin said she had protested a defend in place-style policy that had
been proposed for a facility in Port Leyden, Lewis County. McLaughlin is
currently suing the state over what she contends is her firing for acting as
a whistleblower regarding OMRDD problems.

According to OMRDD documents, the Riverview facility, which was less than a
year old, was inspected by the state Dormitory Authority and underwent
periodic inspections by OMRDD.

For the most part, OMRDD sets its own standards for evacuation protocol. For
many smaller residences, fire drills call for evacuations within five or six
minutes. OMRDD oversees its own periodic safety inspections, once the
facility is certified by the state Dormitory Authority.

The emerging details of the fire suggests a scene of horror inside the
building as the two overnight workers tried desperately to get people out of
a house that was supposed to be relatively fire-resistant.

According to one report, two of those pulled out of the house suffered rug
burns as workers literally dragged them outside. And two of the dead