Re: Paint Booth Exhaust Stack

2017-03-16 Thread rongreenman .
Is the offset an offset or a horizontal run? On Thu, Mar 16, 2017 at 3:09 PM, James Crawford wrote: > The exhaust stack has a total length of 20’-0”, there is a head at the top > of the stack and heads behind the filters, the fan is located at the base > of the stack.

Re: Concealed Combustible Spaces with Gyp Bd?

2017-03-16 Thread rongreenman .
Is it that obvious? On Thu, Mar 16, 2017 at 2:25 PM, Mick Dugal wrote: > Obviously I'm talking about the concealed space above the dropped ceiling. > > > On Thu, Mar 16, 2017 at 1:57 PM, wrote: > >> A corridor is not a concealed space. Is

Re: Fire pump removal

2017-03-16 Thread Bruce Verhei
I hate to make a decision or recommendation without knowing the whole picture, and on a forum such as this it's impossible. But a sprinkler system is such an integral part of the evaluation of a building, and occupancy, that it would be unlikely that the business would be allowed to stay open

RE: Paint Booth Exhaust Stack

2017-03-16 Thread James Crawford
The exhaust stack has a total length of 20'-0", there is a head at the top of the stack and heads behind the filters, the fan is located at the base of the stack. Thank you James Crawford Phaser Fire Protection Ltd. Phone 604-888-0318 Fax 604-888-4732 Cel 604-790-0938 Email

RE: Paint Booth Exhaust Stack

2017-03-16 Thread James Crawford
We have a head at the top but as it comes down they had to offset to miss a joist so there are 2 90 degree bends and a small pup piece that make up 24” center to center, just trying to see if we need a head in the offset. Thank you James Crawford Phaser Fire Protection Ltd.

RE: Paint Booth Exhaust Stack

2017-03-16 Thread Art Tiroly
Is that the total duct length or is there a riser to the roof? Are there heads in the plenum behind the filter? Where is the exhaust fan? Art Tiroly ATCO Fire Protection/Tiroly 24400 Highland Rd CLE 44143 216-621-8899 216-570-7030 cell From: Sprinklerforum

Re: Paint Booth Exhaust Stack

2017-03-16 Thread rongreenman .
My read on this would be that if you gave a sprinkler in the middle of a 24" horizontal duct you have 12" on center. Don't you need one at the top of each vertical run? On Thu, Mar 16, 2017 at 1:47 PM James Crawford wrote: > NFPA #33 (2016 ed) section 9.4.6 (2)

Re: Concealed Combustible Spaces with Gyp Bd?

2017-03-16 Thread Mick Dugal
Obviously I'm talking about the concealed space above the dropped ceiling. On Thu, Mar 16, 2017 at 1:57 PM, wrote: > A corridor is not a concealed space. Is the rest of the area around the > corridor sprinklered? What does this corridor serve? Is it for egress? > > > >

RE: Information

2017-03-16 Thread Rocci Cetani 3
Ken Wagoner is the seismic guru! Rocci Cetani III, CET Designer Water-Based Fire Protections Systems Layout, Nicet Level III Northern California Fire Protection Services Inc. 16840 Joleen Way Bldg. A Morgan Hill, CA 93037 P-(408) 776-1580 EXT.111 F-(408) 776-1590

Re: Information

2017-03-16 Thread Parsley Consulting
Mel, Phone me when you get a moment, and I'll help as best I can. *Ken Wagoner, SET *Parsley Consulting*** *350 West 9th Avenue, Suite 206 *Escondido, California 92025 *Phone 760-745-6181* Visit our website *** On 03/16/2017 1:54 PM, Mel Herrell wrote:

RE: Fire pump removal

2017-03-16 Thread John O'Connor
Dewayne, I was involved many years ago with an existing hospital, being retrofitted with new sprinklers. Existing fire pump was for standpipes, and had to be upgraded in both boost pressure and volume. Anyway, it was going to be out about three weeks while the old came out and we put in the

RE: Concealed Combustible Spaces with Gyp Bd?

2017-03-16 Thread Craig.Prahl
A corridor is not a concealed space. Is the rest of the area around the corridor sprinklered? What does this corridor serve? Is it for egress? Craig L. Prahl Fire Protection Group Lead/SME CH2M 200 Verdae Blvd. Greenville, SC 29607 Direct - 864.920.7540 Fax - 864.920.7129 CH2MHILL Extension

Re: Information

2017-03-16 Thread Mel Herrell
Travis and all Yes. Are you asking for some one to teach you how to space/calculate the bracing? I guess I am looking too see if I am doing correctly. I was trying to build my confidence in the process. Thanks Best regards Melvin On Thu, Mar 16, 2017 at 3:31 PM, Travis Mack, SET

Paint Booth Exhaust Stack

2017-03-16 Thread James Crawford
NFPA #33 (2016 ed) section 9.4.6 (2) Horizontal Exhaust ducts shall have sprinklers located on 12'-0" centers beginning no more that 6'-0" from the duct entrance. If the horizontal run is only 2'-0" do you require a sprinkler head to protect this section of the duct, (is there a minimum

Concealed Combustible Spaces with Gyp Bd?

2017-03-16 Thread Mick Dugal
Would a wood framed corridor rocked with 2 layers of 5/8" gyp bd (a UL listed assembly) and a dropped acoustical grid ceiling still require sprinklers? Would NFPA 13 :8.15.1.2.10 permit the exclusion of sprinklers from such a space? 8.15.1.2.10 Concealed spaces where rigid materials are used

Re: Information

2017-03-16 Thread Travis Mack, SET
Yes. Are you asking for some one to teach you how to space/calculate the bracing? Are you asking for material data sheet information? As Craig stated, your question is very broad. Travis Mack, SET MFP Design, LLC 2508 E Lodgepole Drive Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107

RE: Information

2017-03-16 Thread Craig.Prahl
That’s a real broad question. What kind of information? Craig L. Prahl Fire Protection Group Lead/SME CH2M 200 Verdae Blvd. Greenville, SC 29607 Direct - 864.920.7540 Fax - 864.920.7129 CH2MHILL Extension 77540 craig.pr...@ch2m.com From: Sprinklerforum

RE: Information

2017-03-16 Thread Tim Stone
Melvin, The Structural Engineer of record should provide you the Seismic design data. Then Chapter 9 tells you how to do it. Tim From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Mel Herrell Sent: Thursday, March 16, 2017 4:14 PM To:

Re: Information

2017-03-16 Thread Mel Herrell
Thanks Chapter 9 of NFPA I was thinking there may have been a process or a list? Best regards Melvin On Thu, Mar 16, 2017 at 2:28 PM, Tim Stone wrote: > NFPA 13, Chapter 9. > > > > Regards, > > *G. Tim Stone* > > > > *G. Tim Stone Consulting, LLC* > > *NICET Level III

RE: Information

2017-03-16 Thread Tim Stone
NFPA 13, Chapter 9. Regards, G. Tim Stone G. Tim Stone Consulting, LLC NICET Level III Engineering Technician Fire Protection Sprinkler Design and Consulting Services 117 Old Stage Rd. - Essex Jct., VT. 05452 CELL: (802) 373-0638 TEL: (802) 434-2968 Fax: (802)

Re: Information

2017-03-16 Thread Travis Mack, SET
Chapter 9 in NFPA 13 Travis Mack, SET MFP Design, LLC 2508 E Lodgepole Drive Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 email:tm...@mfpdesign.com http://www.mfpdesign.com https://www.facebook.com/pages/MFP-Design-LLC/92218417692 Send large files to us via:

Information

2017-03-16 Thread Mel Herrell
Where may I get some information on Seismic for sprinklers? Best regards Melvin ___ Sprinklerforum mailing list Sprinklerforum@lists.firesprinkler.org http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Dry Horizontal sidewalls

2017-03-16 Thread Mick Dugal
I've got a question about installation of dry horizontal sidewall sprinklers. Is it permitted to install them at an angle? Not aiming up or down but side to side? I have an odd shaped canopy that I'm trying to cover with dry sprinklers but one particular area is lacking coverage. If I could angle

RE: Inspectors Test Discharge

2017-03-16 Thread Ed Kramer
NFPA 13 (2016) section 6.1.1.5 may help. -Original Message- From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of proud-texan Sent: Thursday, March 16, 2017 9:31 AM To: sprinklerforum@lists.firesprinkler.org Subject: Inspectors Test Discharge We have

Re: Fire pump removal - Character set not allowed

2017-03-16 Thread Mark Phillips
They rent temp pumps Sent from my Verizon 4G LTE Droid On Mar 16, 2017 9:36 AM, Dewayne Martinez wrote: I have a project in which there will be long term removal (3-6months)of the existing fire pump for building improvements. We need to keep the systems in

Re: Inspectors Test Discharge

2017-03-16 Thread Jeremy Blocker
As odd as it sounds you should probably check with the plumbing/building department in addition to the ahj. Here in Colorado we ran into an issue where the plumbing code referenced this and said nothing but steel for Its, Aux drains and main drains. Jeremy Blocker Sent from my iPhone 6 >

RE: Fire pump removal

2017-03-16 Thread Dewayne Martinez
This is a historical building that has been sinking for the last 50 + years because it was built on a filled in swamp. Original footings are wood that are now being replaced with concrete. The entire lower level has to be gutted and dug up hence the removal of the fire pump. There is no option

Re: Inspectors Test Discharge

2017-03-16 Thread fpdcdesign
I'm assuming you mean post IT valve. I have seen CPVC (stick with the listed stuff) used on drains. If you do, don't forget the sprinkler adapter on the end. I don't see why it would be a problem. Check with the AHJ and see if he/she is OK with it. Todd G Williams, PE Fire

Re: Fire pump removal

2017-03-16 Thread Greg McGahan
You can sometimes rent a trailer mounted fire pump in many instances. We have not done it, but we have followed the trail before and found out that some pump manufacturers have them available. Greg McGahan Living Water Fire Protection, LLC 1160 McKenzie Road

RE: Fire pump removal

2017-03-16 Thread Steve Leyton
I guess “a little more information” would be helpful. The implication is that the fire pump room and the equipment located there is being displaced by these improvements but the building is intended to be at least partially occupied during the impairment.Why didn’t anyone point out to

Inspectors Test Discharge

2017-03-16 Thread proud-texan
We have a customer that has 40 existing systems and wants to re-pipe all of his inspectors test valves. However, he wants to use either PVC or CPVC piping for the discharge piping. Since this pipe is normally dry and not subject to system pressure, does anyone have an "expert" opinion on

re: Fire pump removal

2017-03-16 Thread Maurice Marvi
Not knowing more specifics, it is hard to tell, but as an Insurance Company Risk Engineer I would recommend bringing in the insurer as well as the Fire Department, and local Building Department. Maurice Marvi From: "Dewayne Martinez"

RE: Fire pump removal

2017-03-16 Thread Scott Futrell
I’d say we need more information first. You wrote, removal…of the existing fire pump. Why? Replacement? What precludes keeping it in service? Change in occupancy? And more… Scott Office: (763) 425-1001 x 2 Cell: (612) 759-5556 From: Sprinklerforum

Re: Fire pump removal

2017-03-16 Thread fpdcdesign
What is the AHJ going to accept? Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT 860-535-2080 (ofc) 860-553-3553 (fax) 860-608-4559 (cell) > > On Mar 16, 2017 at 9:35 AM, (mailto:dmarti...@total-mechanical.com)> wrote: > > > >

Fire pump removal

2017-03-16 Thread Dewayne Martinez
I have a project in which there will be long term removal (3-6months)of the existing fire pump for building improvements. We need to keep the systems in service and this building is considered a high rise (110ft). What are some of my options? I thought possibly just using the incoming city