Thanks, Thom.
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Thom
McMahon
Sent: Friday, September 26, 2008 10:02 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Backflow requirement
Yes! It makes sense as a question. The reason you most often see a
The beatings will continue until the viscosity changes.
Ron Fletcher
-Original Message-
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Roland Huggins
Sent: Thursday, September 18, 2008 12:29 PM
To: sprinklerforum@firesprinkler.org
Subject: Re: viscosities
Since the
Does anyone know the history of requiring backflow preventers on
sprinkler systems? I just attended a meeting at the city of Phoenix
regarding their backflow requirement. The discussion turned to where
does/did the backflow requirement come from and is there an EPA, Health
Dept. or Federal mandate
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Fletcher,
Ron
Sent: Thursday, September 18, 2008 4:31 PM
To: sprinklerforum@firesprinkler.org
Subject: Backflow requirement
Does anyone know the history of requiring backflow preventers on
sprinkler systems? I just
Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel: 970-879-7952
Fax: 970-879-7926
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Fletcher,
Ron
Sent: Tuesday, September 09, 2008 10:28 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: The sky
in a similar situation.
WWW.powers.com
Bill Minkel, Sprinkler Designer
Member NFPA
Dallas, TX
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Fletcher,
Ron
Sent: Tuesday, September 09, 2008 9:39 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: The sky
, CO 80488
Tel: 970-879-7952
Fax: 970-879-7926
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Fletcher,
Ron
Sent: Monday, September 08, 2008 2:50 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: The sky is falling
Hi Thom,
Do you know if ACI 318-05
a
rod with a deck insert similar to the Tolco fig. 107F.
Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel: 970-879-7952
Fax: 970-879-7926
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Fletcher,
Ron
Sent
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Fletcher,
Ron
Sent: Tuesday, September 09, 2008 9:39 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: The sky is falling
Thom,
Yeah I understand the reason for the cracked concrete, although I have
not heard
Anyone else out there heard from Hilti about no longer using their HDI
to hang pipe from the bottom of cracked concrete in seismic categories
C-F? We had a (the sky/pipe is falling) presentation from Hilti about
using their new TZ Kwik Bolt instead of the HDI, HDI-P or powder drive
pins. They
Fletcher, Ron would like to recall the message, The sky is falling.
___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]
To Unsubscribe, send
.
Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel: 970-879-7952
Fax: 970-879-7926
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Fletcher,
Ron
Sent: Monday, September 08, 2008 1:45 PM
-gender specific) think?
Roland
On Aug 6, 2008, at 3:03 PM, Fletcher, Ron wrote:
Okay, this is really reaching but what to heck.
A 10'x15' light hazard room with a duct (bottom @24) running down the
center and sometimes turning or teeing off at 90 degrees would require
two and sometimes three
We plan on reviewing it with the AHJ prior to plan submittal. Hopefully
all will be okay. I will post whatever the AHJ (Tempe) has to say.
Free golf is good and 120F shouldn't be a problem. The big ticket item
will be the cost of cold beverages, to avoid dehydration.
Ron Fletcher
Aero Automatic
Okay, this is really reaching but what to heck.
A 10'x15' light hazard room with a duct (bottom @24) running down the
center and sometimes turning or teeing off at 90 degrees would require
two and sometimes three sprinklers to comply with the obstruction rules.
If each wall is considered a
You can have an unlimited number 2'x4' return air grills in the ceiling
without adding sprinklers above but put a 4 wide slot around edge of
the room and sprinklers are required. Go figure.
Where do you get a plenum thus requiring sprinklers?
Ron Fletcher
Aero Automatic Sprinkler
Phoenix, AZ
Okay, here is an actual case in design now, I'm not making this up. The
room is 27'x 27' with 2 ft. wide gap between the walls and ceiling on
three sides. Two sides have sheet rock from the ceiling to the deck. The
third side has return air grills set on edge vertically for the full 25
ft.
Try 8.6.2.2.1(c) '07 Ed.
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Russell
Sent: Tuesday, August 05, 2008 2:16 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: New topic
Well, classifying the stored item only gives me the Class 1 ,2, etc. but
I
I'm looking forward to the day when all the gauges are digital and we
won't have to guess if the pitot pressure from the 4 hydrant butt is
28.4 or 28.8 (lmao). It could be critical if your local sprinkler
scientist won't let you slide on 31 gpm.
Happy Friday everyone,
Ron Fletcher
Aero Automatic
What he said, plus the pitot pressure tables in NFPA #291 are titled
Theoretical Discharge Through Circular Orifices emphasis on
Theoretical. It's yet another case of, calc with a computer, measure
with micrometer, mark with chalk and chop off with axe.
Ron Fletcher
Aero Automatic
Phoenix, AZ
So you have run into a sprinkler scientist (AHJ). I feel your pain.
Balancing the flow in a system is a lost art completely ignored by the
computer programs we use today. Computer programs bump up the end head
pressure to create equal pressures at a flow split. Without knowing the
particulars of
How about PRV's in high rise buildings, are 50 PRV's better than one or
two in the case of 07-#14? The standard can't possibly deal with every
scenario of water supply versus demand.
Ron Fletcher
Aero Automatic Sprinkler
Phoenix, AZ
-Original Message-
From: [EMAIL PROTECTED]
We have installed surge suppressors but only when required by the
specifications. They are usually for the military and are installed
between the underground and the valve header. I have never seen a
problem with surge in a sprinkler system. Even aircraft hangars with
large deluge systems and very
contractor to take
responsibility for the soils condition.
On Thu, Jul 24, 2008 at 3:42 PM, Fletcher, Ron [EMAIL PROTECTED]
wrote:
It seems we are doing the fire flow calculations for more and more
projects. In the not so distant past it was enough to furnish a flow
test and graph it out to 20 psi
.
www.waynefire.com
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Fletcher,
Ron
Sent: Wednesday, July 23, 2008 4:36 PM
To: sprinklerforum@firesprinkler.org
Subject: Fire Flow Calculation
Looking for help to determine required fire flow. New addition
Of Fletcher,
Ron
Sent: Wednesday, July 23, 2008 3:32 PM
To: sprinklerforum@firesprinkler.org
Subject: Standpipe/Stair arrangement
This is a tough one to put into words, drawings would better explain.
We have a stair tower (one of three) in a hotel that has two
entrance/exits on the first through fourth
Sprinklers, Inc.
www.waynefire.com
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Fletcher,
Ron
Sent: Wednesday, July 23, 2008 4:36 PM
To: sprinklerforum@firesprinkler.org
Subject: Fire Flow Calculation
Looking for help to determine required fire flow. New
be in the stairwell!
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Fletcher,
Ron
Sent: Thursday, July 24, 2008 1:34 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Standpipe/Stair arrangement
Yep, we are putting valves on the floor landing for one half
:[EMAIL PROTECTED] On Behalf Of Fletcher,
Ron
Sent: Thursday, July 24, 2008 1:37 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Fire Flow Calculation
I think I have tried the ISO method before and unless I did something
wrong (easily) the fire flows I ended up with for large buildings were
greater
Looking for help to determine required fire flow. New addition to
hospital is 200k sqft. 150k sqft existing building with 50k sqft of the
150k not sprinklered. Construction type is I-FR.
Ron Fletcher
Aero Automatic
Phoenix, AZ
___
Sprinklerforum mailing
not
get the nice reduction?.. Is this what you are looking for ?
R/
Matt
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Fletcher,
Ron
Sent: Wednesday, July 23, 2008 3:36 PM
To: sprinklerforum@firesprinkler.org
Subject: Fire Flow Calculation
Looking
-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Fletcher,
Ron
Sent: Wednesday, July 23, 2008 5:09 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Fire Flow Calculation
It's for fire flow from hydrants. I guess I'm wondering if we can
pro-rate the unsprinklered percentage. If we
PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Fletcher,
Ron
Sent: Wednesday, July 23, 2008 3:22 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Fire Flow Calculation
I was afraid of that. So it will be 6000 gpm.
Thanks for the help.
Ron
-Original Message-
From: [EMAIL PROTECTED
This is a tough one to put into words, drawings would better explain.
We have a stair tower (one of three) in a hotel that has two
entrance/exits on the first through fourth floors and one door on the
other 27 floors. There is no dividing wall between the stairs. Imagine
two people enter through
And don't forget the spacing requirements for slopes greater than 4/12.
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Brian
Harris
Sent: Monday, July 21, 2008 6:29 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Increasing Area of Operation
Thanks
Supplemental? If 150 psi is pumped into the FDC the riser check will
close making the FDC the only supply.
Ron Fletcher
Aero Automatic
Phoenix, AZ
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Thom
McMahon
Sent: Friday, July 18, 2008 7:45 AM
To:
Of Fletcher,
Ron
Sent: Friday, July 18, 2008 9:05 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: FDC Connection
Supplemental? If 150 psi is pumped into the FDC the riser check will
close making the FDC the only supply.
Ron Fletcher
Aero Automatic
Phoenix, AZ
-Original Message-
From: [EMAIL
picture.
One final thought... Is is quitting time yet ;-)
Ray Vance
Chief Engineering Tech.
Wayne Automatic Fires Sprinklers, Inc.
www.waynefire.com
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Fletcher,
Ron
Sent: Friday, July 18, 2008 1:40 PM
Thank you Chris, it is good to hear from the voice of experience.
Ron Fletcher
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Chris
Cahill
Sent: Wednesday, July 09, 2008 9:05 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: FD Pumper Suction Hose
If your over pressure condition is strictly at churn and your hydraulic
demand is less than 175 psi at flow I would suggest a pump with a PLD.
They really work and are the best (I think) solution when dealing with a
steep supply curve or mandatory pressure reductions imposed by the local
AHJ. The
Does anyone have experience with 4 pumper truck suction hose of the
soft variety? According to a City FPE Phoenix FD requires 20 psi
(flowing) at private hydrants to avoid collapsing the soft suction hose.
Sounds fishy to me but I have no way of knowing.
I can understand not taking the city main
)
Fletcher, Ron [EMAIL PROTECTED] Sent by:
[EMAIL PROTECTED]
06/24/2008 04:08 PM
Please respond to sprinklerforum
To
sprinklerforum@firesprinkler.org
cc
Subject
RE: Sand or silt clogging strainers
Hi Thom,
Sorry the main is 12 and we opened hydrants to verify fire flow at
about
4,200 gpm
We have 1500 gpm diesel pump equipped with a PLD. While running at full
flow the strainers to the PLD and in the cooling line become clogged
with sand or fine silt causing the engine to over heat and the PLD to
fail. The city pressure and volume is not sufficient to adequately flush
the 16 dead
No help, we are on our own.
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Todd
Williams - FPDC
Sent: Tuesday, June 24, 2008 7:37 AM
To: sprinklerforum@firesprinkler.org
Subject: Re: Sand or silt clogging strainers
Would the local fire department be any
Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Fletcher,
Ron
Sent: Tuesday, June 24, 2008 10:19 AM
To: sprinklerforum@firesprinkler.org
Subject: Sand or silt clogging strainers
We have 1500 gpm diesel pump equipped with a PLD. While running at full
flow the strainers
Hi Thom,
Sorry the main is 12 and we opened hydrants to verify fire flow at
about 4,200 gpm. The strainer to the PLD and in the cooling line plugged
up and we had rocks o-plenty.
Then one day the pump started for an unknown reason, overheated, burst
into flame and would have burnt down the pump
zebra mussels (sp?).
Admittedly, I have only glanced over the responses.
Here's the link:
http://www.hellanstrainer.com/
I hope this helps.
James L.(Jim) Roberts, PE/SET
Fluor Corporation
100 Fluor Daniel Drive - C104F
Greenville, SC 29607
864.281.5149
864.281.4916(Fax)
Fletcher, Ron
Why not re-calc with K81 and see if the pipe sizes still work? You are not
mixing orifice sizes for balancing so there is now rule against.
Ron Fletcher
Aero Automatic
Phoenix, AZ
-Original Message-
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Aydin ÖZKAYA
Sent:
Haven't done any for quite a while but in the old days doing deluge
system on outdoor equipment like pumps, transformers, heaters etc... We
used structural shapes like small I Beams with plate on the bottom and a
concrete pier or if a slab available we anchored the plate to the slab.
I believe the
six
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Gregg Key
Sent: Friday, May 30, 2008 8:37 AM
To: sprinklerforum@firesprinkler.org
Subject: Re: 200 psi test for components rated 175
Speaking of such test, How many systems are installed with a means
We have an existing building with Viking large drop heads at .45/2000.
Storage is being changed to 18 ft high Group A unexpanded plastic. 40 oz
cups nested inside each other, shrink wrapped on four sides, cardboard
over the top on pallets on the floor, 32 ft. roof, no racks. We want to
add a pump
. Prahl, CET
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC 29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.ch2m.com
Fletcher, Ron wrote:
We have an existing building with Viking large
- 864.599.4102 Fax -
864.599.8439 [EMAIL PROTECTED] http://www.ch2m.com
Fletcher, Ron wrote:
We have an existing building with Viking large drop heads at
.45/2000.
Storage is being changed to 18 ft high Group A unexpanded plastic. 40
oz cups nested inside each other, shrink wrapped on four sides
What Roland said plus.
Item 1 cut the part about densities required. If they identify the
hazard we contractors can find the densities. Then classified as per
the fire risk What does that mean, how do you do it and how does it
apply to 13? And as per what the hell does that mean (rant), as
Structure? Are the pipe racks verticals not fire proofed. The pipe racks
I have seen have supports every 20-25 feet so we used u-bolts or
something similar. Vessels usually require pipe stands bolted to
concrete pads or on separate concrete piers. For larger vessels we would
attach to the exterior
[EMAIL PROTECTED]
http://www.ch2m.com
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Fletcher,
Ron
Sent: Monday, April 21, 2008 3:48 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Seismic bracing of sprinkler pipng in exterior tank farm
Structure
Check with Tyco. I heard they are developing a Kbig ESFR good to 50 ft. or
something along that line.
Ron Fletcher
Aero Automatic
Phoenix, AZ
-Original Message-
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of SISPROFUEGO,
C.A. - José Prada
Sent: Sunday, April 13, 2008
It's the conveyor that goes to the room with the rotating knives. Lol
Or
Baggage claim, starbucks, ticketing, starbucks, concourse, starbucks,
gates and starbucks.
Ron Fletcher
Aero Automatic
Phoenix, AZ
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf
Sorry to interupt the bucket brigade but what say the forum for 18 ft.
palletized storage in a 35 ft. bldg? I find .6/2500 for favorable
factors and it sends you in a circle for no favorable factors. NFPA is
1.1/2500 or ESFR. Something doesn't compute (probably me).
Ron Fletcher
Aero Automatic
PROTECTED]
http://www.ch2m.com
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Fletcher,
Ron
Sent: Thursday, April 10, 2008 3:45 PM
To: sprinklerforum@firesprinkler.org
Subject: FM Density for Group A nonexpanded exposed solid pile
Sorry to interupt
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC 29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.ch2m.com
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Fletcher,
Ron
Sent: Thursday, April 10, 2008 4
PROTECTED] On Behalf Of Fletcher,
Ron
Sent: Tuesday, April 08, 2008 11:42 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Failed Bucket Test
Are the new numbers from the same hydrants?
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Brian
Harris
Sent
yes
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Thomas
Reinhardt
Sent: Wednesday, March 19, 2008 1:01 PM
To: sprinklerforum@firesprinkler.org
Subject: Is there a problem with the forum?
Thanks
Tom Reinhardt
Wheeling Fire Inspector
Wheeling, IL
I don't know of an upright but I think Globe makes a residential pendent
listed for 8 or 12 deflector distance, I can't remember for sure. We
have used them in loft style exposed systems because of the problem
achieving the 4 deflector distance listed for most residential heads.
Good luck.
Ron
OH2 sounds good to me. As long as the total amount of Class II in the
room is less than the maximum allowable quantity per IFC the use of the
room remains classified the same as the rest of the building. I believe
the MAQ is 660 gallons before the occupancy would change to H
requiring extra hazard
23 sqft per head in a light hazard corridor should be enough. With 7 psi
you have a 0.66 density. The skylight section is poorly written. We ran
into a project with four 2'x2' skylights two feet apart. The letter of
the standard would require a head in each but we left them out and the
AHJ didn't
Don't know about an NFPA Forum but you can try here
http://www.eng-tips.com/index.cfm. Look in the NFPA (fire) Code Issues
forum.
Ron Fletcher
Aero Automatic
Phoenix, AZ
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
[EMAIL PROTECTED]
Sent: Friday,
Is this a trick question?
Ron Fletcher
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
[EMAIL PROTECTED]
Sent: Wednesday, February 06, 2008 10:35 AM
To: sprinklerforum@firesprinkler.org
Subject: Who's the most important person?
Who makes the most money
CNN is interviewing the public safety officer with LVPD. He said fire was on
the outside and roof of the bldg. firefighters were hanging out of the windows
with hose lines spraying the fire. You can see it on cnn.com.live
-Original Message-
From: [EMAIL PROTECTED] [mailto:[EMAIL
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Tambini,
Ed
Sent: Friday, January 25, 2008 12:55 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Calculation Input...
account for change in pipe type as required, don't count flow switch if
over 2
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
News is saying it started on top of the hotel and spread down.
-Original Message-
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of å...
Sent: Friday, January 25, 2008 1:11 PM
To: sprinklerforum@firesprinkler.org
Subject: 3 alarm Fire @ Monte Carlo now in las vegas
it
Maybe I'm missing something. Why not call panel construction beam and
girder if the beams are less than 7.5 ft apart? The only difference
between the two definitions is that panel has to form pockets to collect
heat and beam and girder doesn't, plus beam and girder can still have
steel decking on
Anyone out there been required to install overfill protection on a UL
Listed diesel fuel tank inside a pump room? IFC 3404 sounds like it is
written for large bulk storage tanks not 187 gallon fire pump fuel
tanks.
Ron Fletcher
Aero Automatic
Phoenix, AZ
Anyone out there been required to install overfill protection on a UL
Listed diesel fuel tank inside a pump room? IFC 3404 sounds like it is
written for large bulk storage tanks not 187 gallon fire pump fuel
tanks.
Ron Fletcher
Aero Automatic
Phoenix, AZ
PROTECTED] On Behalf Of Fletcher,
Ron
Sent: Friday, December 14, 2007 8:56 AM
To: sprinklerforum@firesprinkler.org
Subject: Diesel Fuel Tank Overfill Protection
Anyone out there been required to install overfill protection on a UL
Listed diesel fuel tank inside a pump room? IFC 3404 sounds like
In a high piled storage building may the 400 ft. egress dimension be
used without vents if the building is equipped with ESFR sprinklers?
910.1 Exception 2: smoke and heat vents shall not be required in areas
of buildings using ESFR sprinklers.
Section 1016.2: allows an increase in egress
To: sprinklerforum@firesprinkler.org
Subject: 2006 IFC - Smoke and Heat Vents
my opinion is yes.
scot deal
excelsior fire
On 10/30/07, Fletcher, Ron [EMAIL PROTECTED] wrote:
In a high piled storage building may the 400 ft. egress dimension be
used without vents if the building is equipped with ESFR
55390
Location: 4439 Hwy 12 SW
Waverly, MN 55390
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Fletcher, Ron
Sent: Tuesday, October 30, 2007 12:54 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: 2006 IFC - Smoke and Heat Vents
Thanks
15 - K17's @ 52psi
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Chris
Cahill
Sent: Thursday, October 25, 2007 12:40 PM
To: sprinklerforum@firesprinkler.org
Subject: Quell
Anybody have a ballpark gpm required for these systems? I know they are
Try http://www.amesfirewater.com/products/_productsFull.asp?pid=363
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Bob
Knight
Sent: Monday, October 22, 2007 1:28 PM
To: sprinklerforum@firesprinkler.org
Subject: Ames In-Build Riser
This will be the
Why monitor the hose gates? Monitor the big valve inside unless it is a
wet test header without a main control valve.
Ron Fletcher
Aero Automatic
Phoenix, AZ
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of John
Drucker
Sent: Friday, October 19, 2007 8:13
I deal with this problem everyday here in Phoenix. Table B105.1 list the
required fire flows based on total square feet of the largest building
on a site. B105.2 Exception allows up to a 50% reduction in fire flow
for buildings sprinklered in accordance with 903. It doesn't sound like
the AHJ has
ESFR obstruction rules really suck don't they. I believe FM discounts
obstructions located more than 36 inches below the deflector unless the
offending obstruction is directly over the flue space of a storage rack.
Hypothetical:
If the duct ran through the rack at an elevation where it had
I know the requirement, I just think it needs to be refined a bit or
applied with some thought given to the actual situation. A 32 round
duct 12 ft down from the deck and in an aisle should not be treated the
same as a 32 duct 4 ft down and over the longitudinal flue of a rack.
Let us delve into
, September 21, 2007 8:35 AM
To: sprinklerforum@firesprinkler.org
Subject: Re: Mezzanine/ ESFR
This is where NFPA 13 diverged from FM. 13:8.4.6.4.1 requires said
draft stop for when adjacent spray sprinklers are SR.
Roland
On Sep 20, 2007, at 3:56 PM, Fletcher, Ron wrote:
Joe
starts near the edge of the mezzanine, the heat that would be
expected to operate control mode sprinklers if they were there will
operate ESFRs at the ceiling, as well..
Joe
Fletcher, Ron wrote:
Sprinklers below and ESFR above just like an office area. The
mezzanine is too big
What about money as a reason?
Ron Fletcher
Aero Automatic
Phoenix, AZ
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
[EMAIL PROTECTED]
Sent: Wednesday, September 19, 2007 12:58 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: pump test header
Forget the ESFR's. Just sprinkler the mezzanine.
Ron Fletcher
Aero Automatic
Phoenix, AZ
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Jimmy
Waite
Sent: Wednesday, September 19, 2007 12:25 PM
To: sprinklerforum@firesprinkler.org
Subject: Mezzanine/
- 864.599.8439
[EMAIL PROTECTED]
http://www.lg.com
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Fletcher,
Ron
Sent: Wednesday, September 19, 2007 4:08 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: pump test header location
What about money as a reason
. underneath the mezzanine? You
said it was too low, what then would be the height threshold?
Thanks so much for your help.
Jimmy Waite
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Fletcher,
Ron
Sent: Wednesday, September 19, 2007 4:18 PM
Guess we're lucky round here, if it works it's okay. Sometimes we have to calc
the line between the pump and the header but it always works and is always
pointless. Measure the flow at the header and pressure at the pump so friction
loss doesn't matter.
Ever have a diesel pump with 80 ft. of
I have seen only one such system and coincidently it was used at nursing
home. Five or six high volume wells, each with their own pump supplied
water to very large buried vertical pipe. A vertical turbine fire pump
was installed to provide the hydrants and sprinklers. Smaller pumps were
used for
Ed, A new guy here put a sprinkler in each skylight and I challenged him
on why. He pointed to 8.6.7 and asked if they could be omitted where it
said that. Damned if I could find anything in 13.
Ron Fletcher
Aero Automatic
Phoenix, AZ
-Original Message-
From: [EMAIL PROTECTED]
If the baffles are 8 ft. long how wide are they?
The real question should be are only three levels of sprinklers adequate
for light hazard?
Ron Fletcher
Aero Automatic Sprinkler
Phoenix, AZ
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Todd
Williams
8.6.5.2.1.4* For light and ordinary hazard occupancies, structural
members only shall be considered when applying the requirements of
8.6.5.2.1.3.
If the panels are not greater than 4ft wide I would let it go. If
sprinklers are of value beneath the 4x4 clouds then we have solved the
long standing
Granted the clouds may not allow a sprinkler to effectively extinguish a fire
below such an assembly but when did extinguishment become a requirement and
how will a sprinkler installed in a 4x4 panel prevent diversion of combustion
gasses?
We call them feel good sprinklers, they won't go off
George, I'm usually with you on your answers but not this time.
Reality - Submit the COR, get the extra, install the heads in the
clouds. Fire in band room, sprinklers installed in clouds fail to
activate for lack of heat collection. Sprinklers at roof deck control
fire until arrival of FD.
end up in court defending a system that controlled a
fire, than one that didn't.
Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
- Original Message -
From: Fletcher, Ron [EMAIL PROTECTED]
To: sprinklerforum
The only thing I have ever been able to find is in the handbook 9-125
18th edition. Dry-pipe systems should only be used in areas subject to
freezing temperatures. I have had an AHJ use this as justification for
a slightly different application.
Isn't there something about insulation not being a