RE: Backflow requirement

2008-09-26 Thread Fletcher, Ron
Thanks, Thom. -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Thom McMahon Sent: Friday, September 26, 2008 10:02 AM To: sprinklerforum@firesprinkler.org Subject: RE: Backflow requirement Yes! It makes sense as a question. The reason you most often see a

RE: viscosities

2008-09-18 Thread Fletcher, Ron
The beatings will continue until the viscosity changes. Ron Fletcher -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Roland Huggins Sent: Thursday, September 18, 2008 12:29 PM To: sprinklerforum@firesprinkler.org Subject: Re: viscosities Since the

Backflow requirement

2008-09-18 Thread Fletcher, Ron
Does anyone know the history of requiring backflow preventers on sprinkler systems? I just attended a meeting at the city of Phoenix regarding their backflow requirement. The discussion turned to where does/did the backflow requirement come from and is there an EPA, Health Dept. or Federal mandate

RE: Backflow requirement

2008-09-18 Thread Fletcher, Ron
-Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Fletcher, Ron Sent: Thursday, September 18, 2008 4:31 PM To: sprinklerforum@firesprinkler.org Subject: Backflow requirement Does anyone know the history of requiring backflow preventers on sprinkler systems? I just

RE: The sky is falling

2008-09-12 Thread Fletcher, Ron
Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926 -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Fletcher, Ron Sent: Tuesday, September 09, 2008 10:28 AM To: sprinklerforum@firesprinkler.org Subject: RE: The sky

RE: The sky is falling

2008-09-09 Thread Fletcher, Ron
in a similar situation. WWW.powers.com Bill Minkel, Sprinkler Designer Member NFPA Dallas, TX -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Fletcher, Ron Sent: Tuesday, September 09, 2008 9:39 AM To: sprinklerforum@firesprinkler.org Subject: RE: The sky

RE: The sky is falling

2008-09-09 Thread Fletcher, Ron
, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926 -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Fletcher, Ron Sent: Monday, September 08, 2008 2:50 PM To: sprinklerforum@firesprinkler.org Subject: RE: The sky is falling Hi Thom, Do you know if ACI 318-05

RE: The sky is falling

2008-09-09 Thread Fletcher, Ron
a rod with a deck insert similar to the Tolco fig. 107F. Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926 -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Fletcher, Ron Sent

RE: The sky is falling

2008-09-09 Thread Fletcher, Ron
-Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Fletcher, Ron Sent: Tuesday, September 09, 2008 9:39 AM To: sprinklerforum@firesprinkler.org Subject: RE: The sky is falling Thom, Yeah I understand the reason for the cracked concrete, although I have not heard

The sky is falling

2008-09-08 Thread Fletcher, Ron
Anyone else out there heard from Hilti about no longer using their HDI to hang pipe from the bottom of cracked concrete in seismic categories C-F? We had a (the sky/pipe is falling) presentation from Hilti about using their new TZ Kwik Bolt instead of the HDI, HDI-P or powder drive pins. They

Recall: The sky is falling

2008-09-08 Thread Fletcher, Ron
Fletcher, Ron would like to recall the message, The sky is falling. ___ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [EMAIL PROTECTED] To Unsubscribe, send

RE: The sky is falling

2008-09-08 Thread Fletcher, Ron
. Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926 -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Fletcher, Ron Sent: Monday, September 08, 2008 1:45 PM

RE: Panel Construction vs room less than 300 sqft.

2008-08-07 Thread Fletcher, Ron
-gender specific) think? Roland On Aug 6, 2008, at 3:03 PM, Fletcher, Ron wrote: Okay, this is really reaching but what to heck. A 10'x15' light hazard room with a duct (bottom @24) running down the center and sometimes turning or teeing off at 90 degrees would require two and sometimes three

RE: Panel Construction vs room less than 300 sqft.

2008-08-07 Thread Fletcher, Ron
We plan on reviewing it with the AHJ prior to plan submittal. Hopefully all will be okay. I will post whatever the AHJ (Tempe) has to say. Free golf is good and 120F shouldn't be a problem. The big ticket item will be the cost of cold beverages, to avoid dehydration. Ron Fletcher Aero Automatic

Panel Construction vs room less than 300 sqft.

2008-08-06 Thread Fletcher, Ron
Okay, this is really reaching but what to heck. A 10'x15' light hazard room with a duct (bottom @24) running down the center and sometimes turning or teeing off at 90 degrees would require two and sometimes three sprinklers to comply with the obstruction rules. If each wall is considered a

RE: Floating Ceilings

2008-08-05 Thread Fletcher, Ron
You can have an unlimited number 2'x4' return air grills in the ceiling without adding sprinklers above but put a 4 wide slot around edge of the room and sprinklers are required. Go figure. Where do you get a plenum thus requiring sprinklers? Ron Fletcher Aero Automatic Sprinkler Phoenix, AZ

RE: Floating Ceilings

2008-08-05 Thread Fletcher, Ron
Okay, here is an actual case in design now, I'm not making this up. The room is 27'x 27' with 2 ft. wide gap between the walls and ceiling on three sides. Two sides have sheet rock from the ceiling to the deck. The third side has return air grills set on edge vertically for the full 25 ft.

RE: New topic

2008-08-05 Thread Fletcher, Ron
Try 8.6.2.2.1(c) '07 Ed. -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Russell Sent: Tuesday, August 05, 2008 2:16 PM To: sprinklerforum@firesprinkler.org Subject: RE: New topic Well, classifying the stored item only gives me the Class 1 ,2, etc. but I

RE: Gauge Calibration

2008-08-01 Thread Fletcher, Ron
I'm looking forward to the day when all the gauges are digital and we won't have to guess if the pitot pressure from the 4 hydrant butt is 28.4 or 28.8 (lmao). It could be critical if your local sprinkler scientist won't let you slide on 31 gpm. Happy Friday everyone, Ron Fletcher Aero Automatic

RE: Gauge Calibration

2008-08-01 Thread Fletcher, Ron
What he said, plus the pitot pressure tables in NFPA #291 are titled Theoretical Discharge Through Circular Orifices emphasis on Theoretical. It's yet another case of, calc with a computer, measure with micrometer, mark with chalk and chop off with axe. Ron Fletcher Aero Automatic Phoenix, AZ

RE: Water Supply

2008-07-31 Thread Fletcher, Ron
So you have run into a sprinkler scientist (AHJ). I feel your pain. Balancing the flow in a system is a lost art completely ignored by the computer programs we use today. Computer programs bump up the end head pressure to create equal pressures at a flow split. Without knowing the particulars of

RE: FIRE PUMP WITH PRESSURE REDUCING VALVE

2008-07-30 Thread Fletcher, Ron
How about PRV's in high rise buildings, are 50 PRV's better than one or two in the case of 07-#14? The standard can't possibly deal with every scenario of water supply versus demand. Ron Fletcher Aero Automatic Sprinkler Phoenix, AZ -Original Message- From: [EMAIL PROTECTED]

RE: FIRE PUMP WITH PRESSURE REDUCING VALVE with a TWIST

2008-07-30 Thread Fletcher, Ron
We have installed surge suppressors but only when required by the specifications. They are usually for the military and are installed between the underground and the valve header. I have never seen a problem with surge in a sprinkler system. Even aircraft hangars with large deluge systems and very

RE: Fire Flow Calculation

2008-07-25 Thread Fletcher, Ron
contractor to take responsibility for the soils condition. On Thu, Jul 24, 2008 at 3:42 PM, Fletcher, Ron [EMAIL PROTECTED] wrote: It seems we are doing the fire flow calculations for more and more projects. In the not so distant past it was enough to furnish a flow test and graph it out to 20 psi

RE: Fire Flow Calculation

2008-07-25 Thread Fletcher, Ron
. www.waynefire.com -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Fletcher, Ron Sent: Wednesday, July 23, 2008 4:36 PM To: sprinklerforum@firesprinkler.org Subject: Fire Flow Calculation Looking for help to determine required fire flow. New addition

RE: Standpipe/Stair arrangement

2008-07-24 Thread Fletcher, Ron
Of Fletcher, Ron Sent: Wednesday, July 23, 2008 3:32 PM To: sprinklerforum@firesprinkler.org Subject: Standpipe/Stair arrangement This is a tough one to put into words, drawings would better explain. We have a stair tower (one of three) in a hotel that has two entrance/exits on the first through fourth

RE: Fire Flow Calculation

2008-07-24 Thread Fletcher, Ron
Sprinklers, Inc. www.waynefire.com -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Fletcher, Ron Sent: Wednesday, July 23, 2008 4:36 PM To: sprinklerforum@firesprinkler.org Subject: Fire Flow Calculation Looking for help to determine required fire flow. New

RE: Standpipe/Stair arrangement

2008-07-24 Thread Fletcher, Ron
be in the stairwell! -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Fletcher, Ron Sent: Thursday, July 24, 2008 1:34 PM To: sprinklerforum@firesprinkler.org Subject: RE: Standpipe/Stair arrangement Yep, we are putting valves on the floor landing for one half

RE: Fire Flow Calculation

2008-07-24 Thread Fletcher, Ron
:[EMAIL PROTECTED] On Behalf Of Fletcher, Ron Sent: Thursday, July 24, 2008 1:37 PM To: sprinklerforum@firesprinkler.org Subject: RE: Fire Flow Calculation I think I have tried the ISO method before and unless I did something wrong (easily) the fire flows I ended up with for large buildings were greater

Fire Flow Calculation

2008-07-23 Thread Fletcher, Ron
Looking for help to determine required fire flow. New addition to hospital is 200k sqft. 150k sqft existing building with 50k sqft of the 150k not sprinklered. Construction type is I-FR. Ron Fletcher Aero Automatic Phoenix, AZ ___ Sprinklerforum mailing

RE: Fire Flow Calculation

2008-07-23 Thread Fletcher, Ron
not get the nice reduction?.. Is this what you are looking for ? R/ Matt -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Fletcher, Ron Sent: Wednesday, July 23, 2008 3:36 PM To: sprinklerforum@firesprinkler.org Subject: Fire Flow Calculation Looking

RE: Fire Flow Calculation

2008-07-23 Thread Fletcher, Ron
- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Fletcher, Ron Sent: Wednesday, July 23, 2008 5:09 PM To: sprinklerforum@firesprinkler.org Subject: RE: Fire Flow Calculation It's for fire flow from hydrants. I guess I'm wondering if we can pro-rate the unsprinklered percentage. If we

RE: Fire Flow Calculation

2008-07-23 Thread Fletcher, Ron
PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Fletcher, Ron Sent: Wednesday, July 23, 2008 3:22 PM To: sprinklerforum@firesprinkler.org Subject: RE: Fire Flow Calculation I was afraid of that. So it will be 6000 gpm. Thanks for the help. Ron -Original Message- From: [EMAIL PROTECTED

Standpipe/Stair arrangement

2008-07-23 Thread Fletcher, Ron
This is a tough one to put into words, drawings would better explain. We have a stair tower (one of three) in a hotel that has two entrance/exits on the first through fourth floors and one door on the other 27 floors. There is no dividing wall between the stairs. Imagine two people enter through

RE: Increasing Area of Operation

2008-07-21 Thread Fletcher, Ron
And don't forget the spacing requirements for slopes greater than 4/12. -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Brian Harris Sent: Monday, July 21, 2008 6:29 AM To: sprinklerforum@firesprinkler.org Subject: RE: Increasing Area of Operation Thanks

RE: FDC Connection

2008-07-18 Thread Fletcher, Ron
Supplemental? If 150 psi is pumped into the FDC the riser check will close making the FDC the only supply. Ron Fletcher Aero Automatic Phoenix, AZ -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Thom McMahon Sent: Friday, July 18, 2008 7:45 AM To:

RE: FDC Connection

2008-07-18 Thread Fletcher, Ron
Of Fletcher, Ron Sent: Friday, July 18, 2008 9:05 AM To: sprinklerforum@firesprinkler.org Subject: RE: FDC Connection Supplemental? If 150 psi is pumped into the FDC the riser check will close making the FDC the only supply. Ron Fletcher Aero Automatic Phoenix, AZ -Original Message- From: [EMAIL

RE: FDC Connection

2008-07-18 Thread Fletcher, Ron
picture. One final thought... Is is quitting time yet ;-) Ray Vance Chief Engineering Tech. Wayne Automatic Fires Sprinklers, Inc. www.waynefire.com -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Fletcher, Ron Sent: Friday, July 18, 2008 1:40 PM

RE: FD Pumper Suction Hose

2008-07-09 Thread Fletcher, Ron
Thank you Chris, it is good to hear from the voice of experience. Ron Fletcher -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Chris Cahill Sent: Wednesday, July 09, 2008 9:05 AM To: sprinklerforum@firesprinkler.org Subject: RE: FD Pumper Suction Hose

RE: Pressure reducing valve location for a fire pump

2008-07-09 Thread Fletcher, Ron
If your over pressure condition is strictly at churn and your hydraulic demand is less than 175 psi at flow I would suggest a pump with a PLD. They really work and are the best (I think) solution when dealing with a steep supply curve or mandatory pressure reductions imposed by the local AHJ. The

FD Pumper Suction Hose

2008-07-08 Thread Fletcher, Ron
Does anyone have experience with 4 pumper truck suction hose of the soft variety? According to a City FPE Phoenix FD requires 20 psi (flowing) at private hydrants to avoid collapsing the soft suction hose. Sounds fishy to me but I have no way of knowing. I can understand not taking the city main

RE: Sand or silt clogging strainers

2008-07-07 Thread Fletcher, Ron
) Fletcher, Ron [EMAIL PROTECTED] Sent by: [EMAIL PROTECTED] 06/24/2008 04:08 PM Please respond to sprinklerforum To sprinklerforum@firesprinkler.org cc Subject RE: Sand or silt clogging strainers Hi Thom, Sorry the main is 12 and we opened hydrants to verify fire flow at about 4,200 gpm

Sand or silt clogging strainers

2008-06-24 Thread Fletcher, Ron
We have 1500 gpm diesel pump equipped with a PLD. While running at full flow the strainers to the PLD and in the cooling line become clogged with sand or fine silt causing the engine to over heat and the PLD to fail. The city pressure and volume is not sufficient to adequately flush the 16 dead

RE: Sand or silt clogging strainers

2008-06-24 Thread Fletcher, Ron
No help, we are on our own. -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Todd Williams - FPDC Sent: Tuesday, June 24, 2008 7:37 AM To: sprinklerforum@firesprinkler.org Subject: Re: Sand or silt clogging strainers Would the local fire department be any

RE: Sand or silt clogging strainers

2008-06-24 Thread Fletcher, Ron
Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Fletcher, Ron Sent: Tuesday, June 24, 2008 10:19 AM To: sprinklerforum@firesprinkler.org Subject: Sand or silt clogging strainers We have 1500 gpm diesel pump equipped with a PLD. While running at full flow the strainers

RE: Sand or silt clogging strainers

2008-06-24 Thread Fletcher, Ron
Hi Thom, Sorry the main is 12 and we opened hydrants to verify fire flow at about 4,200 gpm. The strainer to the PLD and in the cooling line plugged up and we had rocks o-plenty. Then one day the pump started for an unknown reason, overheated, burst into flame and would have burnt down the pump

RE: Sand or silt clogging strainers

2008-06-24 Thread Fletcher, Ron
zebra mussels (sp?). Admittedly, I have only glanced over the responses. Here's the link: http://www.hellanstrainer.com/ I hope this helps. James L.(Jim) Roberts, PE/SET Fluor Corporation 100 Fluor Daniel Drive - C104F Greenville, SC 29607 864.281.5149 864.281.4916(Fax) Fletcher, Ron

RE: Sprinkler MixMatch

2008-06-19 Thread Fletcher, Ron
Why not re-calc with K81 and see if the pipe sizes still work? You are not mixing orifice sizes for balancing so there is now rule against. Ron Fletcher Aero Automatic Phoenix, AZ -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Aydin ÖZKAYA Sent:

RE: When all horizontal pipe hangers are supports from below

2008-06-09 Thread Fletcher, Ron
Haven't done any for quite a while but in the old days doing deluge system on outdoor equipment like pumps, transformers, heaters etc... We used structural shapes like small I Beams with plate on the bottom and a concrete pier or if a slab available we anchored the plate to the slab. I believe the

RE: 200 psi test for components rated 175

2008-05-30 Thread Fletcher, Ron
six -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Gregg Key Sent: Friday, May 30, 2008 8:37 AM To: sprinklerforum@firesprinkler.org Subject: Re: 200 psi test for components rated 175 Speaking of such test, How many systems are installed with a means

Exposed unexpanded plastic

2008-05-08 Thread Fletcher, Ron
We have an existing building with Viking large drop heads at .45/2000. Storage is being changed to 18 ft high Group A unexpanded plastic. 40 oz cups nested inside each other, shrink wrapped on four sides, cardboard over the top on pallets on the floor, 32 ft. roof, no racks. We want to add a pump

RE: Exposed unexpanded plastic

2008-05-08 Thread Fletcher, Ron
. Prahl, CET Fire Protection Group Mechanical Department CH2MHILL Lockwood Greene 1500 International Drive PO Box 491, Spartanburg, SC 29304-0491 Direct - 864.599.4102 Fax - 864.599.8439 [EMAIL PROTECTED] http://www.ch2m.com Fletcher, Ron wrote: We have an existing building with Viking large

RE: Exposed unexpanded plastic

2008-05-08 Thread Fletcher, Ron
- 864.599.4102 Fax - 864.599.8439 [EMAIL PROTECTED] http://www.ch2m.com Fletcher, Ron wrote: We have an existing building with Viking large drop heads at .45/2000. Storage is being changed to 18 ft high Group A unexpanded plastic. 40 oz cups nested inside each other, shrink wrapped on four sides

RE: engineering decisions

2008-04-24 Thread Fletcher, Ron
What Roland said plus. Item 1 cut the part about densities required. If they identify the hazard we contractors can find the densities. Then classified as per the fire risk What does that mean, how do you do it and how does it apply to 13? And as per what the hell does that mean (rant), as

RE: Seismic bracing of sprinkler pipng in exterior tank farm

2008-04-21 Thread Fletcher, Ron
Structure? Are the pipe racks verticals not fire proofed. The pipe racks I have seen have supports every 20-25 feet so we used u-bolts or something similar. Vessels usually require pipe stands bolted to concrete pads or on separate concrete piers. For larger vessels we would attach to the exterior

RE: Seismic bracing of sprinkler pipng in exterior tank farm

2008-04-21 Thread Fletcher, Ron
[EMAIL PROTECTED] http://www.ch2m.com -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Fletcher, Ron Sent: Monday, April 21, 2008 3:48 PM To: sprinklerforum@firesprinkler.org Subject: RE: Seismic bracing of sprinkler pipng in exterior tank farm Structure

RE: High Storage / High Celing

2008-04-14 Thread Fletcher, Ron
Check with Tyco. I heard they are developing a Kbig ESFR good to 50 ft. or something along that line. Ron Fletcher Aero Automatic Phoenix, AZ -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of SISPROFUEGO, C.A. - José Prada Sent: Sunday, April 13, 2008

RE: defintion

2008-04-14 Thread Fletcher, Ron
It's the conveyor that goes to the room with the rotating knives. Lol Or Baggage claim, starbucks, ticketing, starbucks, concourse, starbucks, gates and starbucks. Ron Fletcher Aero Automatic Phoenix, AZ -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf

FM Density for Group A nonexpanded exposed solid pile

2008-04-10 Thread Fletcher, Ron
Sorry to interupt the bucket brigade but what say the forum for 18 ft. palletized storage in a 35 ft. bldg? I find .6/2500 for favorable factors and it sends you in a circle for no favorable factors. NFPA is 1.1/2500 or ESFR. Something doesn't compute (probably me). Ron Fletcher Aero Automatic

RE: FM Density for Group A nonexpanded exposed solid pile

2008-04-10 Thread Fletcher, Ron
PROTECTED] http://www.ch2m.com -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Fletcher, Ron Sent: Thursday, April 10, 2008 3:45 PM To: sprinklerforum@firesprinkler.org Subject: FM Density for Group A nonexpanded exposed solid pile Sorry to interupt

RE: FM Density for Group A nonexpanded exposed solid pile

2008-04-10 Thread Fletcher, Ron
Lockwood Greene 1500 International Drive PO Box 491, Spartanburg, SC 29304-0491 Direct - 864.599.4102 Fax - 864.599.8439 [EMAIL PROTECTED] http://www.ch2m.com -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Fletcher, Ron Sent: Thursday, April 10, 2008 4

RE: Failed Bucket Test

2008-04-09 Thread Fletcher, Ron
PROTECTED] On Behalf Of Fletcher, Ron Sent: Tuesday, April 08, 2008 11:42 AM To: sprinklerforum@firesprinkler.org Subject: RE: Failed Bucket Test Are the new numbers from the same hydrants? -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Brian Harris Sent

RE: Is there a problem with the forum?

2008-03-19 Thread Fletcher, Ron
yes -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Thomas Reinhardt Sent: Wednesday, March 19, 2008 1:01 PM To: sprinklerforum@firesprinkler.org Subject: Is there a problem with the forum? Thanks Tom Reinhardt Wheeling Fire Inspector Wheeling, IL

RE: Residential Upright

2008-03-12 Thread Fletcher, Ron
I don't know of an upright but I think Globe makes a residential pendent listed for 8 or 12 deflector distance, I can't remember for sure. We have used them in loft style exposed systems because of the problem achieving the 4 deflector distance listed for most residential heads. Good luck. Ron

RE: Fuel Tank Rooms

2008-03-10 Thread Fletcher, Ron
OH2 sounds good to me. As long as the total amount of Class II in the room is less than the maximum allowable quantity per IFC the use of the room remains classified the same as the rest of the building. I believe the MAQ is 660 gallons before the occupancy would change to H requiring extra hazard

RE: Omitting sprinklers from skylights

2008-02-27 Thread Fletcher, Ron
23 sqft per head in a light hazard corridor should be enough. With 7 psi you have a 0.66 density. The skylight section is poorly written. We ran into a project with four 2'x2' skylights two feet apart. The letter of the standard would require a head in each but we left them out and the AHJ didn't

RE: Life Safety Code

2008-02-08 Thread Fletcher, Ron
Don't know about an NFPA Forum but you can try here http://www.eng-tips.com/index.cfm. Look in the NFPA (fire) Code Issues forum. Ron Fletcher Aero Automatic Phoenix, AZ -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of [EMAIL PROTECTED] Sent: Friday,

RE: Who's the most important person?

2008-02-06 Thread Fletcher, Ron
Is this a trick question? Ron Fletcher -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of [EMAIL PROTECTED] Sent: Wednesday, February 06, 2008 10:35 AM To: sprinklerforum@firesprinkler.org Subject: Who's the most important person? Who makes the most money

RE: 3 alarm Fire @ Monte Carlo now in las vegas

2008-01-25 Thread Fletcher, Ron
CNN is interviewing the public safety officer with LVPD. He said fire was on the outside and roof of the bldg. firefighters were hanging out of the windows with hose lines spraying the fire. You can see it on cnn.com.live -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL

RE: Calculation Input...

2008-01-25 Thread Fletcher, Ron
-Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Tambini, Ed Sent: Friday, January 25, 2008 12:55 PM To: sprinklerforum@firesprinkler.org Subject: RE: Calculation Input... account for change in pipe type as required, don't count flow switch if over 2

3 alarm Fire @ Monte Carlo now in las vegas

2008-01-25 Thread Fletcher, Ron
___ Sprinklerforum mailing list Sprinklerforum@firesprinkler.org http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)

RE: 3 alarm Fire @ Monte Carlo now in las vegas

2008-01-25 Thread Fletcher, Ron
News is saying it started on top of the hotel and spread down. -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of å... Sent: Friday, January 25, 2008 1:11 PM To: sprinklerforum@firesprinkler.org Subject: 3 alarm Fire @ Monte Carlo now in las vegas it

RE: NFPA 13, 2002 A.3.7.1 (4)

2008-01-17 Thread Fletcher, Ron
Maybe I'm missing something. Why not call panel construction beam and girder if the beams are less than 7.5 ft apart? The only difference between the two definitions is that panel has to form pockets to collect heat and beam and girder doesn't, plus beam and girder can still have steel decking on

Diesel Fuel Tank Overfill Protection

2007-12-14 Thread Fletcher, Ron
Anyone out there been required to install overfill protection on a UL Listed diesel fuel tank inside a pump room? IFC 3404 sounds like it is written for large bulk storage tanks not 187 gallon fire pump fuel tanks. Ron Fletcher Aero Automatic Phoenix, AZ

Diesel Fuel Tank Overfill Protection

2007-12-14 Thread Fletcher, Ron
Anyone out there been required to install overfill protection on a UL Listed diesel fuel tank inside a pump room? IFC 3404 sounds like it is written for large bulk storage tanks not 187 gallon fire pump fuel tanks. Ron Fletcher Aero Automatic Phoenix, AZ

RE: Diesel Fuel Tank Overfill Protection

2007-12-14 Thread Fletcher, Ron
PROTECTED] On Behalf Of Fletcher, Ron Sent: Friday, December 14, 2007 8:56 AM To: sprinklerforum@firesprinkler.org Subject: Diesel Fuel Tank Overfill Protection Anyone out there been required to install overfill protection on a UL Listed diesel fuel tank inside a pump room? IFC 3404 sounds like

2006 IFC - Smoke and Heat Vents

2007-10-30 Thread Fletcher, Ron
In a high piled storage building may the 400 ft. egress dimension be used without vents if the building is equipped with ESFR sprinklers? 910.1 Exception 2: smoke and heat vents shall not be required in areas of buildings using ESFR sprinklers. Section 1016.2: allows an increase in egress

RE: 2006 IFC - Smoke and Heat Vents

2007-10-30 Thread Fletcher, Ron
To: sprinklerforum@firesprinkler.org Subject: 2006 IFC - Smoke and Heat Vents my opinion is yes. scot deal excelsior fire On 10/30/07, Fletcher, Ron [EMAIL PROTECTED] wrote: In a high piled storage building may the 400 ft. egress dimension be used without vents if the building is equipped with ESFR

RE: 2006 IFC - Smoke and Heat Vents

2007-10-30 Thread Fletcher, Ron
55390 Location: 4439 Hwy 12 SW Waverly, MN 55390 -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Fletcher, Ron Sent: Tuesday, October 30, 2007 12:54 PM To: sprinklerforum@firesprinkler.org Subject: RE: 2006 IFC - Smoke and Heat Vents Thanks

RE: Quell

2007-10-25 Thread Fletcher, Ron
15 - K17's @ 52psi -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Chris Cahill Sent: Thursday, October 25, 2007 12:40 PM To: sprinklerforum@firesprinkler.org Subject: Quell Anybody have a ballpark gpm required for these systems? I know they are

RE: Ames In-Build Riser

2007-10-22 Thread Fletcher, Ron
Try http://www.amesfirewater.com/products/_productsFull.asp?pid=363 -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Bob Knight Sent: Monday, October 22, 2007 1:28 PM To: sprinklerforum@firesprinkler.org Subject: Ames In-Build Riser This will be the

RE: Fire Pump Test Header Valve Supervision

2007-10-19 Thread Fletcher, Ron
Why monitor the hose gates? Monitor the big valve inside unless it is a wet test header without a main control valve. Ron Fletcher Aero Automatic Phoenix, AZ -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of John Drucker Sent: Friday, October 19, 2007 8:13

RE: Fire Flow requirements

2007-10-03 Thread Fletcher, Ron
I deal with this problem everyday here in Phoenix. Table B105.1 list the required fire flows based on total square feet of the largest building on a site. B105.2 Exception allows up to a 50% reduction in fire flow for buildings sprinklered in accordance with 903. It doesn't sound like the AHJ has

RE: ESFR greater than 24 obstruction

2007-10-03 Thread Fletcher, Ron
ESFR obstruction rules really suck don't they. I believe FM discounts obstructions located more than 36 inches below the deflector unless the offending obstruction is directly over the flue space of a storage rack. Hypothetical: If the duct ran through the rack at an elevation where it had

RE: ESFR greater than 24 obstruction

2007-10-03 Thread Fletcher, Ron
I know the requirement, I just think it needs to be refined a bit or applied with some thought given to the actual situation. A 32 round duct 12 ft down from the deck and in an aisle should not be treated the same as a 32 duct 4 ft down and over the longitudinal flue of a rack. Let us delve into

RE: Mezzanine/ ESFR

2007-09-24 Thread Fletcher, Ron
, September 21, 2007 8:35 AM To: sprinklerforum@firesprinkler.org Subject: Re: Mezzanine/ ESFR This is where NFPA 13 diverged from FM. 13:8.4.6.4.1 requires said draft stop for when adjacent spray sprinklers are SR. Roland On Sep 20, 2007, at 3:56 PM, Fletcher, Ron wrote: Joe

RE: Mezzanine/ ESFR

2007-09-20 Thread Fletcher, Ron
starts near the edge of the mezzanine, the heat that would be expected to operate control mode sprinklers if they were there will operate ESFRs at the ceiling, as well.. Joe Fletcher, Ron wrote: Sprinklers below and ESFR above just like an office area. The mezzanine is too big

RE: pump test header location

2007-09-19 Thread Fletcher, Ron
What about money as a reason? Ron Fletcher Aero Automatic Phoenix, AZ -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of [EMAIL PROTECTED] Sent: Wednesday, September 19, 2007 12:58 PM To: sprinklerforum@firesprinkler.org Subject: RE: pump test header

RE: Mezzanine/ ESFR

2007-09-19 Thread Fletcher, Ron
Forget the ESFR's. Just sprinkler the mezzanine. Ron Fletcher Aero Automatic Phoenix, AZ -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Jimmy Waite Sent: Wednesday, September 19, 2007 12:25 PM To: sprinklerforum@firesprinkler.org Subject: Mezzanine/

RE: pump test header location

2007-09-19 Thread Fletcher, Ron
- 864.599.8439 [EMAIL PROTECTED] http://www.lg.com -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Fletcher, Ron Sent: Wednesday, September 19, 2007 4:08 PM To: sprinklerforum@firesprinkler.org Subject: RE: pump test header location What about money as a reason

RE: Mezzanine/ ESFR

2007-09-19 Thread Fletcher, Ron
. underneath the mezzanine? You said it was too low, what then would be the height threshold? Thanks so much for your help. Jimmy Waite -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Fletcher, Ron Sent: Wednesday, September 19, 2007 4:18 PM

RE: pump test header location

2007-09-19 Thread Fletcher, Ron
Guess we're lucky round here, if it works it's okay. Sometimes we have to calc the line between the pump and the header but it always works and is always pointless. Measure the flow at the header and pressure at the pump so friction loss doesn't matter. Ever have a diesel pump with 80 ft. of

RE: Fire Pump

2007-09-13 Thread Fletcher, Ron
I have seen only one such system and coincidently it was used at nursing home. Five or six high volume wells, each with their own pump supplied water to very large buried vertical pipe. A vertical turbine fire pump was installed to provide the hydrants and sprinklers. Smaller pumps were used for

RE: 8.6.7 Ceiling Pockets

2007-09-11 Thread Fletcher, Ron
Ed, A new guy here put a sprinkler in each skylight and I challenged him on why. He pointed to 8.6.7 and asked if they could be omitted where it said that. Damned if I could find anything in 13. Ron Fletcher Aero Automatic Phoenix, AZ -Original Message- From: [EMAIL PROTECTED]

RE: Obstruction issue

2007-08-27 Thread Fletcher, Ron
If the baffles are 8 ft. long how wide are they? The real question should be are only three levels of sprinklers adequate for light hazard? Ron Fletcher Aero Automatic Sprinkler Phoenix, AZ -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Todd Williams

RE: Ceiling Clouds throughout Band / Choir Room

2007-08-15 Thread Fletcher, Ron
8.6.5.2.1.4* For light and ordinary hazard occupancies, structural members only shall be considered when applying the requirements of 8.6.5.2.1.3. If the panels are not greater than 4ft wide I would let it go. If sprinklers are of value beneath the 4x4 clouds then we have solved the long standing

RE: Ceiling Clouds throughout Band / Choir Room

2007-08-15 Thread Fletcher, Ron
Granted the clouds may not allow a sprinkler to effectively extinguish a fire below such an assembly but when did extinguishment become a requirement and how will a sprinkler installed in a 4x4 panel prevent diversion of combustion gasses? We call them feel good sprinklers, they won't go off

RE: Ceiling Clouds throughout Band / Choir Room

2007-08-15 Thread Fletcher, Ron
George, I'm usually with you on your answers but not this time. Reality - Submit the COR, get the extra, install the heads in the clouds. Fire in band room, sprinklers installed in clouds fail to activate for lack of heat collection. Sprinklers at roof deck control fire until arrival of FD.

RE: Ceiling Clouds throughout Band / Choir Room

2007-08-15 Thread Fletcher, Ron
end up in court defending a system that controlled a fire, than one that didn't. Thom McMahon Firetech, Inc. 2560 Copper Ridge Dr Steamboat Springs, CO 80488-2136 Tel: 970-879-7952 Fax: 970-879-7926 - Original Message - From: Fletcher, Ron [EMAIL PROTECTED] To: sprinklerforum

RE: Dry System with Pendents

2007-07-30 Thread Fletcher, Ron
The only thing I have ever been able to find is in the handbook 9-125 18th edition. Dry-pipe systems should only be used in areas subject to freezing temperatures. I have had an AHJ use this as justification for a slightly different application. Isn't there something about insulation not being a