Re: Stage/platform

2012-07-28 Thread bcasterline
Look on the bright side here Steve- if the AHJ declares it Ord Haz II, you could spec high temp, standard response heads, and the successful contractor can finally use those old pendent heads that've been taking up shop space. Is EVERYTHING ever finally said about ANY sprinkler code issue? :

Re: Stage/platform

2012-07-28 Thread bcasterline
one of these days: .008 GPM per sq.ft. per feet ceiling height over entire STAGE-FORM area, (1) 1.5" hose valve w/30' hose and extinguisher in cabinet centered on back wall, intermediate temp, standard coverage, QR heads. ___ Sprinklerforum mailin

an ice plug 'by the way'

2012-08-09 Thread bcasterline
for the same reason we do not want to screw a dry pend into a 1" C.I. 90 looking down, we should not screw a dry pend into a 1" pipe-o-let looking down--the top of the dry pend does not make it above the bottom of the pipe so after the hydro water sits on top of it and if it freezes it beco

Re: Remote Area Question

2012-08-23 Thread bcasterline
well... i'm not a lost cause yet. i'll give it some more thought. thanks. Quoting Roland Huggins : I was hoping I'd be able to convert you :) The question of the most demanding would be WHICH cross main you drop the rectangle on. Roland On Aug 23, 2012, at 1:48 PM, Brad Casterline wrote:

RE: Antifreeze Update

2012-08-28 Thread bcasterline
search this forum for 'calcium chloride'- there are issues with that too i know, but nothing that could not be resolved. the reason you mix it slowly is bcoz heat is generated, which tells me we "pre-combust" it. with a pressure tank as the approved water supply, bfp's, tapping fees, etc go

Re: thermal barrier

2012-09-01 Thread bcasterline
the old.edu in me suggests putting 1 head in the 47 and calling the other 2 bathrooms closets. ps- *persuing, not perusing ___ Sprinklerforum mailing list Sprinklerforum@firesprinkler.org http://fireball.firesprinkler.org/mailman/listinfo/sprinklerfo

Re: 4-WAY BRACING INCLUDING PRYING ACTION ON FASTNERS PER OSHPD'S OPA#601

2012-09-16 Thread bcasterline
George, I have never had to, am away from my desk, and would rather not aswer a question with a question, or be overly general, but I would like to know the extent of your problem-- how many "risers" (vertical pipes) do you have to brace? I have to admit I think there is some confusion on

Re: Sprinkler head Temperature requirement

2012-09-30 Thread bcasterline
all i got is some numbers: 27' ceiling height, 9" deflector distance, couch on fire in the middle of a large, open furniture showroom--- 286F, standard response- activation time = 188 seconds 286F, quick response- activation time = 172 seconds 212F, standard response- activation time = 97 sec

Re: Sprinkler head Temperature requirement

2012-09-30 Thread bcasterline
!EXACTLY! Ron :) I never try to predict anything, per se, I try to find the DIFFERENCE between scenarios, in this case the same Ceiling Height and Heat Release Rate versus sprinkler Temp and RTI. For a benchmark, I found the steady state HRR that would activate a 286 SR in ~180 seconds, wi

all i got is some numbers- Act II (final)

2012-10-01 Thread bcasterline
In the recent 'Temperature Rating...' post I said: 286 SR, activation time = 188 seconds 286 QR, activation time = 172 seconds 212 SR, activation time = 97 seconds 212 QR, activation time = 80 seconds This was with a fire directly under the head, with a fire that grew from 0 to ~1000 kilowatt/m2

RE: Fire pump annual test

2012-10-03 Thread bcasterline
Tom, I guess once we equate what goes out of the tachometer with what goes into the thermometer, the speed does not change-- the magic of the second law of thermodynamics! (or, as you put it-- 'Pump affinity'). Quoting Tom Duross : Brad, we measure rpm as a means of adjusting pressures to ra

Re: Fire pump annual test

2012-10-03 Thread bcasterline
thanks DJJ8389, that's what I thought. I guess electric motor drive is more consistent and closer to expectations than engine driven. As far as Tom's 'adjusting the pressure to rated speed' goes though, with electric we are at the mercy of the local Power and Light, whereas with engine driv

Re: Concealed space or not

2012-10-04 Thread bcasterline
Needs 4-6 heads, since it is a mechanical room, Ord. Haz. I. Non-accesible or limited access relates to FINISH (i.e., non-walkable ceilings). Walkable ceilings are called floors the next level up by A.H.Js. ___ Sprinklerforum mailing list Sprinkle

Re: Fire pump annual test

2012-10-06 Thread bcasterline
George, 78% efficient at overload.. not too shabby! Do you recall the rated RPM? If I assume a 14" impeller diam. I get 2600 RPM. I thought about converting the 400 speed reduction to the pump room temperature rise but said nahhh.. it would be negligible against the 1st law of testosterone, Lo

Re: Fire pump annual test

2012-10-06 Thread bcasterline
on 2nd thought (calc), 65-70% is closer, I bet. 78% is 4500 @ 170. by the way, what does PLD stand for? Quoting bcasterl...@fsc-inc.com: George, 78% efficient at overload.. not too shabby! Do you recall the rated RPM? If I assume a 14" impeller diam. I get 2600 RPM. I thought about converting t

Re: 13R balcony protection

2012-10-12 Thread bcasterline
words vs numbers, 'true' only at the middle of the aisle ___ Sprinklerforum mailing list Sprinklerforum@firesprinkler.org http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Re: 13R balcony protection

2012-10-14 Thread bcasterline
STINKY gets my vote Ron, as most descriptive for some of the numbers I have posted (the ones that come from the other end of my mouth). All I can say is excuse me. Today I will model a sidewall sticking out over a balcony, with and without overhangs and attic eaves, using different size BBQ

Re: Wood pellet manufacturing

2012-10-16 Thread bcasterline
First thing, verify the spelling? If it is pellets, OH2 for the actual manufacturing area and OH4.5 and double the outside hose for the areas where they get bunched up awaitng shipment. What are they used for anyway, sling-shot amo? Quoting Todd Williams : Any insight into protecting a w

Re: Wood pellet manufacturing

2012-10-20 Thread bcasterline
EH1 pipe scheduled tree system Todd, 17/32, 286, SSU-- over every sq ft under roof. What normal Sprinkler Contractor includes special nozzles to guard against auto-ignition in the hammermill? Talk about shielded! We all need all the work we can get these days. I'm pretty sure this has worke

Re: New Jersey

2012-11-04 Thread bcasterline
i look forward to the day when the east coast and the heart of the country are once again in equillibrium John. I survived a tornado in Ruskin Heights Missouri in 1957 so i can ONLY imagine the hardship for you and yours right now. Quoting John Drucker : Great sight yesterday, electrical r

Re: Pipe support spacing requirements for structural supports

2012-11-10 Thread bcasterline
instead of Standard for the Installation of Sprinkler Systems, how about "Benchmark to Determine Just how far from Reality the Actual Situation IS from what Is Written Here-In, Now let's See the Numbers"? Quoting Ron Greenman : Email needs a "Like" button. On Sat, Nov 10, 2012 at 6:46 AM,

RE: NFPA 25

2012-11-12 Thread bcasterline
I know of a contractor that sends an inspection fitter out to inspect the original installation! this fitter's feet DOES leave the floor, and scours the Standards for total compliance. This way, if the original installer loses the I.T,&M, nothing should come back to bite them so hard they g

Re: water storage tank: 300,000 gallon size: failure: FL not NY

2012-11-16 Thread bcasterline
the fill line would only have city water behind it, where-as the metered return would have the fire pump behind it, meaning the metered return could enter the tank anywhere and still prevail, but there would be an elevation where the fill would be unable to STUFF more water in-- interesting

Re: water storage tank: 300,000 gallon size: failure: FL not NY

2012-11-16 Thread bcasterline
on the other hand, a vortex might relieve pressure on the circumference. i think it was a matter of like chris said-- a vaccumnn was drawn, if only for an instant, allowing the weight of the ocean of air above it to CRUSH it. Quoting bcasterl...@fsc-inc.com: the fill line would only have ci

Re: water storage tank: 300,000 gallon size: failure: FL not NY

2012-11-17 Thread bcasterline
no way Bruce-- impossible to overfill or over-pressurize this type of water storage tank Quoting Bruce Verhei : Or the opposite. Tank provided with in adequate atomospheric ventilation, overfilled, and pressurized. But I'd much rather hear from someone who has facts than listen to my ow

Re: water storage tank: 300,000 gallon size: failure: FL not NY

2012-11-17 Thread bcasterline
i guess i could run some numbers BEFORE i run my mouth. i think it imploded as opposed to exploded-- is their any doubt it did one or the other? i got this weekend off, so i'll give it more thought, including the doubt. Quoting bcasterl...@fsc-inc.com: no way Bruce-- impossible to overfill

Re: water storage tank: 300,000 gallon size: failure: FL not NY

2012-11-17 Thread bcasterline
The tank did not burst. Tornados do not blow the roof off a house, even though the news might say it did. A slight atmospheric pressure difference does phenomenal things to structures. A full and pressurized (with water) tank would be like a reading at churn. So it either 'shivered' as Fran

Re: 2010 NFPA 13: high piled storage: in-rack and ceiling sprinklers: riser coverage areas: performance based

2012-11-24 Thread bcasterline
scot, play like there was not one single control valve in the whole sheebang, calc every head in the airspace above a certain floor area untill you find the most demanding (balanced at the ONE common point, then add 'system control valves based on ease of maitenance :). i think this is lik

RE: Sprinklers under platforms

2012-11-30 Thread bcasterline
does anybody else find the fact that the floor itself is an obstuction to pattern development a bit disturbing? at 6 feet between sprinklers with 7 inch max deflector above the floor, the 'dry spots' are going to be 2 or 3 feet long! Quoting rfletc...@aerofire.com: 8.15.6.1 refers to "comb

RE: Sprinklers under platforms

2012-11-30 Thread bcasterline
Perfect examples of the limitations of 13 as a Standard. Question: Does a 50" sqare ceiling cloud require heads above and below? Definatley below, but what if the distance from the main ceilinf to the cloud does not exceed 12", or 22"? For some reason, upon reading the original post I thoug

RE: Sprinklers under platforms

2012-11-30 Thread bcasterline
none of us likes gray Chris, least of all we engineering technicians, since our job is to ensure the intent of you EORs and AHJs is APPLIED to the physical reality of the field. To do this we need measuring devices (things with numbers on them). But if your intents do not come with numbers,

RE: Water damage from multiple opened sprinklers

2012-11-30 Thread bcasterline
Dear @riskmanage, there is no similar experience: this is a clear case of present/former drinking buddy vandalism. the report from the municipality is superfulous (a worker there noticed a spike in usage, shut it down, drove around town, saw no prob., brought it back up). By this time the

Re: advice

2012-12-13 Thread bcasterline
i vote for forgiveness all around, this one time. Quoting Justin Reid : And the reviewer stated it as though it was fact. This comment has the potential to harm this persons ability to conduct business and make a living. If Steve's remedy is not effective, I would think this has the potent

Re: Combustible Concealed Space

2012-12-18 Thread bcasterline
I don't get this, Rons. Are you talking about what NFPA 5000 was supposed to become 30 years ago? That was also the deadline for converting to metric. But since the American West was not won 25.4 millimeters by 25.4 millimeters, but inch by inch, and most systems are installed on Earth, we

Re: Combustible Concealed Space

2012-12-18 Thread bcasterline
not messing with you Ron-- i totally do not understand how words can better describe the built environment better than numbers, i.e., Code=Words, Standard=Numbers. i am terrible with numbers, as you know, and have warned me about (i was an English major when i dropped out of college), but i

Re: Combustible Concealed Space

2012-12-18 Thread bcasterline
the French invented the System Internationale, and decided MASS would be their ONE. In English, FORCE is ONE. Since pressure is force/area, and force is mass times acceleration, and 'most systems are installed on the Earth', why should sprinks convert? The beauty of multiples of ten is simply

let's get this forum started

2012-12-26 Thread bcasterline
who's had enough turkey/ham/brisket and specialty dishes for about a year? "It is what it will be minus what it was." ~~~Brad Casterline, circa 2 months ago~~~ ___ Sprinklerforum mailing list Sprinklerforum@firesprinkler.org http://fireball.firesprinkl

Re: Auxiliary Dry Pipe Question

2012-12-28 Thread bcasterline
Hey Vince! I think the intent of a main drain test is to check the 'status' of the automatic water supply near the source, at acceptance, and regulary to catch and unacceptable degradation. I might be wrong though, since i have only thought that for about 2 minutes so far. HNY 2 U 2! Brad

Re: Maximum in-rack sprinkler spacing - plastic over 25ft

2013-01-15 Thread bcasterline
GREAT SCOTT!! i mean, great, scott. i have to admit i cringed a bit at 5' spacing-- SIX is The Minimum! but that's when max deflector distance is also in play :) you have inspired me to post a test question (test because i already know the answer-- the job went out a couple years ago) Quotin

can an extended coverage pendent be used in a ceiling cloud with a slope of 3 in 12?

2013-01-15 Thread bcasterline
?.light hazard, 20x20 cloud, head listed as Quick Response at 20x20, centered in the cloud. ___ Sprinklerforum mailing list Sprinklerforum@firesprinkler.org http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Re: Maximum in-rack sprinkler spacing - plastic over 25ft

2013-01-15 Thread bcasterline
beside myself with... shame-- i mispelled your good name.. please forgive me scot. ___ Sprinklerforum mailing list Sprinklerforum@firesprinkler.org http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Re: FP/Building Development Services: what qualifications are required of new plan review hirees, and what qualities make for a good plan reviewer

2013-01-27 Thread bcasterline
to realize it takes a village to raise a good system. no single pe, tech, reviewer, installer, or inspector should think they alone can do that. since humility is an accurate estimate of one's ability and importance, i think you hit the nail on the head scot. (r.i.p., the perished, and comfo

RE: Window sprinklers

2013-02-21 Thread bcasterline
I think only horizontal mullions are considered an obstruction to wetting the glass. Also, in IBC 2013, the sprinkler equivalent for Fire Rated is no longer approved. Quoting Rod DiBona : Pretty sure you do. The mullion acts as a barrier. More than likely if you present the dilemma to the

Re: Window sprinklers

2013-02-21 Thread bcasterline
I beg the Forum's pardon. I should know better than to post from home (snow day in Kansas. I have a good memory, it's just short). I think vertical mullions not being an obstruction makes sense though, otherwise the listing would not distiguish? Quoting Justin Reid : IBC 2012, 703.4 Just

RE: Window sprinklers

2013-02-22 Thread bcasterline
Well.. each mullioned section would mean vertical, since horizontal are not allowed. This means the water has to run accross the glass, not just down. I saw the width of it running down, regardless of vertical mullions as the max horizontal spacing. I think a case for be made for not needin

Re: 10 Pipe Diameters

2013-03-07 Thread bcasterline
Generally speaking, sprinkler flows are in the turbulent range. For a double suction pump, water splits and enters the impeller eye from both sides. To avoid uneven wear on the bearings, the velocity at each side should be equal. Witn a vertical ell, this would be the case. For a horizontal

Re: Seismic and ASCE 7

2013-03-14 Thread bcasterline
I think the most important factor is "Is it an essential facility", like hospital, fire station, police station, after an event. a warehouse would not be. Quoting Ron Greenman : Hmmm, maybe just my West Coast interpretation. I've never done anything without bracing. Bracing has always been

Re: Seismic and ASCE 7

2013-03-14 Thread bcasterline
I would rather not leave it up to someone to tell me where it would be required, what with sink holes swallowing men as they sleep, and as the reward for a nice drive hitting the fairway (the increase in fracing and the New Madrid fault, etc). I would rather keep it almost as simple as plan

Re: Glycerine Viscosity in Centipoise?!?!?!

2013-03-24 Thread bcasterline
Ralphy, I made a spreadsheet a while back to work the Darcy-Weisbach friction loss formula 'by hand'. The kinematic viscosity is a required input, and is the absolute viscosity divided by the density. I wanted to be able to vary the temperature too, and since density is a function of temp

Re: Glycerine Viscosity in Centipoise?!?!?!

2013-03-24 Thread bcasterline
and p.s. regarding your 'hat in hand' feeling: "nothing about any of this is easy, and it never will be" ~me~ just now Quoting bcasterl...@fsc-inc.com: Ralphy, I made a spreadsheet a while back to work the Darcy-Weisbach friction loss formula 'by hand'. The kinematic viscosity is a require

Re: Glycerine Viscosity in Centipoise?!?!?!

2013-03-26 Thread bcasterline
"-- imagine parallel steel plates 1 foot apart (top and bottom), with a fluid in-between-- if the top plate is 1 square foot, the viscosity of the fluid would be a measure of the force required to slide the top plate with a velocity of 1 foot per second." Correction: the top plate does not

Re: Glycerine Viscosity in Centipoise?!?!?!

2013-03-26 Thread bcasterline
Ralphy, I predict you will be sizing an expansion chamber soon. Since chambers only come in so many sizes, and if you are uneasy about what the maximum static pressure at the chamber might be, you might consider this: maximum system static = ((vec - Delta L) * wp) / vec, where: vec = cham

numbers for low, moderate, and high

2013-03-28 Thread bcasterline
well--so far, a number for Low Heat Release Rate from NFPA 13, if Low means Light Hazard, and Light Hazard means .1 GPM/SQ FT: 744 kilowatt per square meter. The inherent safety factor here is that 100% of the fuel mass is converted to heat, i.e., not one ash or piece of soot left over anyw

Re: numbers for low, moderate, and high

2013-03-29 Thread bcasterline
I will try to type ledgeably using numbers that will leave no doubt. Before a proposed change proving equivalency can be considered, equivalent has to be established. I had almost lost hope thinking proving eqivalency meant first meeting a 3X safety factor, and it still might-- i still have

sprinkler thesaurus

2013-03-31 Thread bcasterline
NFPA 13: 1) The Red Book Escutcheon: 1) Canopy, 2) Beauty Ring Welded, threaded, female outlet: 1) Pipe-o-let Grooved coupling: 1) Vic, 2) Groover Drip Cup: 1) Slobber Cup, 2) Dookie Does that about cover it, or are there any other names for Velocity Check, Grooved Stubby, etc? ED? George? _

just for fun--sprinkler thesaurus

2013-03-31 Thread bcasterline
1) NFPA 13 a) The Red Book b) ? 2) Welded, Threaded, Female Outlet a) Pipe-O-Let b) ? 3) Escutheon a) Canopy, b) Beauty Ring c) ? 4) Grooved coupling? a) ? b) Vic 5) Dookie 6) Velocity Check 7) Grooved Stubby 8) thru 12) ? ___ Sprinklerforum mailin

Re: sprinkler thesaurus

2013-03-31 Thread bcasterline
ROSETTE! a new one on me-- i love it from down south no doubt? Quoting drm...@swbell.net: -Original Message- From: bcasterl...@fsc-inc.com Sent: Sunday, March 31, 2013 5:40 PM To: sprinklerforum@firesprinkler.org Subject: sprinkler thesaurus NFPA 13: 1) The Red Book Escutcheon: 1

Re: sprinkler thasaurus

2013-04-05 Thread bcasterline
new this week: rosette, mud leg, stub chuck, jodi blond. still nothing for velocity check... Mr. Vinning? Vince? ___ Sprinklerforum mailing list Sprinklerforum@firesprinkler.org http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Re: Is there enough room under a low ceiling for different, but similar, hydraulic designs?

2013-04-06 Thread bcasterline
good question Scot. I only have my '07 on me but I want to read parameter #2 as "For OH2 and less". Brad Quoting "å... " : 2010 NFPA 13 Was it the intention, to the best of our collective imaginations, that Section 11.2.3.2.3.1 meant to include *both* LH and OH hydraulic design areas (a

Re: Is there enough room under a low ceiling for different, but similar, hydraulic designs?

2013-04-07 Thread bcasterline
Thanks for this Scot! In pondering this I finally discovered what I believe is the equivalency and reasoning behind QR Reduction: It reduces the amount of time the fire department has to respond based on ceiling height. This makes total sense because the lower the ceiling the faster the hea

Re: Is there enough room under a low ceiling for different, but similar, hydraulic designs?

2013-04-07 Thread bcasterline
Bruce- I will go out on a Forum limb here and say regarding control mode of accidental fires in terms of water application versus burning rate there is only ONE BUFFER. It is huge, but it is not man-made. Imagine an abandoned wood shack in the middle of nowhwere, struck by lightning, non-s

Re: 9" deflector is the sweet spot

2018-02-03 Thread bcasterline
I guess a pdf in a Dropbox is not even really necessary. What I learned from actually doing the modeling is that a skylight turns otherwise unobstructed construction into obstructed when the sprinkler is directly below it-- like Pete cited ~below the main ceiling like the skylight wasn't the

Re: Church Steeple

2018-02-08 Thread bcasterline
I would see if the AHJ would consider calcing (2) at each of (11) levels = 22 + 1 at the peak = 23. This approximates .1/1950. The 2 would be on the 'remote' side from the vertical supply riser. I envision what is referred to as a Spill Plume fire for calculating smoke exhaust rates in high r

Re: Church Steeple

2018-02-11 Thread bcasterline
This would be phenomenally interesting to analyze using all the latest tools, including but not limited to: 1) FDS 2) any current/familiar hydraulics software (or by hand) 3) Sprink Fdt (sp?). Brad Quoting bcasterl...@fsc-inc.com: I would see if the AHJ would consider calcing (2) at each of (

Re: threaded union fitting - follow up

2018-02-13 Thread bcasterline
Makes sense Douglas. Matt: Mix - 1964 #8. Needles and Pins - The Searchers: http://www.youtube.com/watch?v=5rLqPtZUWJI&list=RD5rLqPtZUWJI Quoting Douglas Hicks : I don’t know about water, but gas piping is not allowed to have unions hidden in a wall. From: Matt Grise Sent: Tuesday, Februa

Re: threaded union fitting - follow up

2018-02-13 Thread bcasterline
I was a nine year old with a transistor Bruce... imma go all in or fold-- give me a minute b.. Quoting Bruce Verhei : Searchers, 1964. I’ll raise you one. Seekers, 1964, with pipes in lyrics. https://youtu.be/4mpJYIACehQ On Feb 13, 2018, at 22:18, bcasterl...@fsc-inc.com wrote: Makes sens

Re: threaded union fitting - follow up

2018-02-14 Thread bcasterline
November 1, 1954 here. And, actually, I like The Forum most when it is rough and tumble and rather ugly-- it reminds me of home, so, so far it's been a pretty good week. Quoting Bruce Verhei : I started on Earth in 56. Sent from my iPhone On Feb 13, 2018, at 23:21, bcasterl...@fsc-inc.co

Re: QR/SR Sprinklers

2018-02-15 Thread bcasterline
Might be a good thing to kick around a little bit!- Quoting Rocci 3 Cetani : Currently Brad Casterline is frantically working up a model, give it a few days and I’m sure he will post a response 😊 Rocci Cetani III, CET Senior Designer Water-Based Fire Protections Systems Layout, Nicet Level

Re: [EXTERNAL] Re: ESFR Heads in Concrete Tee's

2018-02-16 Thread bcasterline
I never saw a wall that didn't go all the way down to the floor. Brad. Quoting "Mark.Phelps" : So this minimum space rule applies to sprinklers under soffits and on either side of a lintel? I guess I have been of the understanding that this type of obstruction was effectively treated like a w

Re: [EXTERNAL] Re: ESFR Heads in Concrete Tee's

2018-02-16 Thread bcasterline
She's the kind of girl whows not too shy and she can tell lm her kind of guy Quoting Roland Huggins : I guess you could call the side of the soffit a baffle but since it doesn’t extend below the pendent it really isn’t. Roland Huggins, PE - Senior VP Engineering American Fire Sprinkler Assn. D

Re: Underground Dry System Pipe Type

2018-02-20 Thread bcasterline
I would not extend a dry system underground - there's worms and stuff down there. B. Quoting Richard Matsuda : Since the pipe is running underground, is PVC or CPVC acceptable? Those are already used for underground piping for free-standing FDC's.Just trying to think outside the box.rick

Re: Draining System below ground....

2018-02-22 Thread bcasterline
Mr Prahl been smokin hot here lately - on fire. Can I get a witness? b. Quoting "Prahl, Craig/GVL" : 40 gallon trash can and portable sump pump with hose to exterior or suitable drain. That or bucket brigade. :) Craig L. Prahl Fire Protection Group Lead/SME Direct - 864.920.7540 Fax - 864.

Re: Draining System below ground....

2018-02-22 Thread bcasterline
Quoting Matt Grise : I am also getting phishing notices. Matt -Original Message- From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Steve Leyton Sent: Thursday, February 22, 2018 4:59 PM To: sprinklerforum@lists.firesprinkler.org Subject: R

Re: Draining System below ground....

2018-02-23 Thread bcasterline
It's probably my dumba$$ fault. Time for me to unsubscribe. Later, Brad. Quoting Dale Wingard : Same thing happened to me a couple of weeks ago when I asked a question. Guessing that is why I didn't get a lot of responses. I did get 2 emails and 2 phone calls. Thanks Mark and Roland for y

Re: Underground & Stub-In Requirements

2018-03-05 Thread bcasterline
For some reason in Kansas anyway 4" is min. if no hydrant on it-- 6" if it supplies a hydrant too, as far as i remember. Brad. ps- does it really take the moderator over one week to approve an 'unsubscribe' nowadays? Quoting "Westbrook, Jay" : See the modification to NFPA 24 in the 120-3-3

Re: Underground & Stub-In Requirements

2018-03-05 Thread bcasterline
Thank you Steve. (suddenly i feel alive again!) Brad-- . Quoting Steve Leyton : If you unsubscribed because you thought you were the cause of the phishing advisory, I'm pretty sure it wasn't you. -Original Message- From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firespri

Re: Protection Area of Coverage for Sprinkler

2018-03-08 Thread bcasterline
Oh geez, here we go again. Now i'll never get to sleep. . Quoting Chris Born : 8.5.2.1.1 of the 2016 edition of NFPA 13 covers how to determine the area covered by a sprinkler. This seems to be pretty straightforward, but I’ve noticed some strange wording. Consider a building with exposed

Re: Protection Area of Coverage for Sprinkler

2018-03-08 Thread bcasterline
I say a beam only acts like a wall if you can't throw under it, and if the sprinkler is that close, the heat flow AT THE SPRINKLER, due to the beam is also OBSTRUCTED... very wall-like behavior. I could probably dig up some snapshots tomorrow. Brad. Quoting bcasterl...@fsc-inc.com: Oh geez

Re: PA nursing home fire with multiple fatalities

2018-03-12 Thread bcasterline
Quoting David Blackwell : Yes, it had a sprinkler system, but also multiple fatalities... "In deadly fire at West Chester nursing home, what went wrong?" Updated: March 2, 2018 — 4:00 PM EST http://www.philly.com/philly/news/breaking/west-chester-nursing-home-fire-barclay-friends-sprinkler-d

Re: PA nursing home fire with multiple fatalities

2018-03-12 Thread bcasterline
In other words, if all the ATF is saying is that the fire started outside on the patio then it did, and the Federal Prosecutors are moving on to other cases. If the toilets flushed the water supply for this hazard would have been enough to smash that fire-- if it had started inside. Maybe

Re: PA nursing home fire with multiple fatalities

2018-03-12 Thread bcasterline
'what-was-wanting' the challenge for the 'up-and-coming' i love you scot Quoting "å... " : Consider the waterflow test really was 90 psig static, 20 psig residual and 363 gpm. If the fire started outside, the elevation pressure loss to operating sprinklers is minimal (~ 4.5 psig); therefo

Re: Liquor Store

2018-03-14 Thread bcasterline
So far Bruce, yes. 45 years has not dulled Vincent's sense of humor (my first mentor- he kept me in stitches while instilling a love for this industry). This is a test post though -- I unsubscribed a while back- at least I tried. If it turns out to be like a failed suicide attempt I have to

Re: Existing 3/4" outlets

2018-03-15 Thread bcasterline
Does anyone make res heads with 3/4 npt? If so just replace the heads and let it overflow! The Standards only spell out minimums. Brad. Quoting Dewayne Martinez : I have a project that was originally designed as a OH II space that will now be turned into a light hazard residential exposed “lof

Re: Existing 3/4" outlets

2018-03-16 Thread bcasterline
I only found one maker of UPRIGHT RESIDENTIAL. I didn't see the npt, but K4.9 so probably not 3/4. Would a 3/4x0-2 sprig w/ 3/4x1/2 RC be legal? Brad. Quoting Matt Grise : If the system was previously able to provide OH2, is it a problem to have over discharge? Could you make sure all of the

Re: [EXTERNAL] RE: Existing 3/4" outlets

2018-03-16 Thread bcasterline
Kyle, if there is even a whiff of Residential about the occupancy the listed res should be used because, along with the quick response, res heads have a superior pattern, wetting not only the floor but high up on the walls too (curtains, bookshelves, the curio cabinets full of Russian Shado

Re: [EXTERNAL] RE: Existing 3/4" outlets

2018-03-16 Thread bcasterline
I just know from reading about the earliest development of Residential sprks it was recognized how important it was to get spray high up on the wall. So 'superior pattern for residential' and 'far superior level of protection for commercial' are different pages of the same book. (and i mea

Re: [EXTERNAL] RE: Existing 3/4" outlets

2018-03-16 Thread bcasterline
It's a head scratcher for sure. One of those Occupancy Classifications that's hard to pin down with just words, then apply all the rules that go along with that vagueness. B. Quoting "Kyle.Montgomery" : Well, it does give us something to think about. I wonder, though, does the residential s

Re: Calc' terminology

2018-03-21 Thread bcasterline
I think the words clean and dirty just refers to the density Steve, which you need to know to get from PSI to feet of head. 13 uses 62.4 lbs/ft^3 (it's not blatant, but I figured it out by rearanging other rules). Define 'algorithm'-- i don't see it in chapter 3... ;) B Quoting Steve Leyton

Re: [EXTERNAL] C?

2018-03-21 Thread bcasterline
The lab would not even need a biologist on staff Vince! They couldn't tell you what the C Factor was, but if they could measure the absolute roughness you could take it from there. I like Mark's idea of a mechanical tee coupon - send them that and they can measure the height/depth of the insid

Re: concealed space less than 6" deep

2018-03-28 Thread bcasterline
Thanks Ben. I looked at the book and searched through archives and it turns out the largest room in the thread I was remembering was a hotel room :) Brad. Quoting Ben Young : Bob, I see where you're coming from with this, but we've seen this in the past with NFPA (previously doing the 0.10

Re: concealed space less than 6" deep

2018-03-28 Thread bcasterline
nothing wrong- with green stuff flying out of a sprinks head bud i mean bob and ben-jam'n, i hope you know what to do now (i think 'reasonable degree of protection'... is in every ED). I know if I ever get another Motel 6 I will ask myself, "is this a 4 sprk calc or an 8 sprk calc?" Brad Q

Re: Unsubscribe

2018-03-28 Thread bcasterline
Dear Thom, if you have not already, please don't pull the trigger-- according to Roland, if you do it right the process is fully automatic! I can't understand, after such a nice post, and being in your position now, why you want to call it quits. . Quoting Thom Heller : Ron, thank you…….

Re: Vertical Opening

2018-03-29 Thread bcasterline
Is the opening required to be 'protected' from a building code standpoint? If it is, Then you look at the sprinkler rules, such as less than 1000 s.f. I hope this makes sense. Brad. Quoting JD Gamble : I have a situation where we have 900sq.ft. vertical opening communicating between two f

Re: Vertical Opening [EXTERNAL]

2018-03-29 Thread bcasterline
You should probably confirm it with every one J.D. but it seems to me if separation (protection, enclosure) is not required there would be no reason to use sprinklers as an alernative for providing that separation. It's been ten years since I last designed, calcd, and listed a water curtain

Re: Vertical Opening [EXTERNAL]

2018-03-29 Thread bcasterline
The vertical rules say when using sprinklers as the alternative something something -I'm away from my desk (so far away at home in bed). Confirm it! It's why I said, "I hope this makes sense" Brad. Quoting JD Gamble : Does that mean that the vertical rules don't apply for this opening? Get

Re: Vertical Opening

2018-03-30 Thread bcasterline
Quoting JD Gamble : "... a draft stop is not a viable solution due to head room "... my fear is these things being left open in a fire situation". When I got into fire modeling 12 years ago I did an activation comparison with and without a draft stop. I was curious to see how much longer

NFPA 13 prior to 1969 edition

2018-04-06 Thread bcasterline
Does anyone have access to 13 where the water curtain detail still required open sprinklers (deluge)? I'm curious if the draft stop is required. Besides smoke protecting the opening it occurred to me the other day the draft stop would help form a 'wall of water' by blocking ~9 gpm, making it

Re: [EXTERNAL] NFPA 13 prior to 1969 edition

2018-04-06 Thread bcasterline
Curiosity Kyle- I'm still stuck in last week, tweaking the vertical opening discussion, which, I must say, you had an excellent take on. Thanks, Brad. Quoting "Kyle.Montgomery" : Is this just for curiosity, or do you have a project using pre-1969 version of the code somehow? -Original

Re: NFPA 13 prior to 1969 edition

2018-04-06 Thread bcasterline
Thanks Scott. Yes, that does help zero in on when it went from open to closed sprinklers. I've recently modeled activation with and without a draft stop for 3,6,9,12,15, and 18 inch deflector distance, for 135F, 155F, 175F, and 200F Sprinklers 9" from edge of opening splitting the difference

Re: Exterior Play Area

2018-04-13 Thread bcasterline
I vote no sprinklers required -- open and noncombustible- the rockinghorse on a spring is like a newspaper machine - there will always be just one of them- not one today and twelve tomorrow. Brad. Quoting Steve Leyton : 8.15.7.5. From: Sprinklerforum [mailto:sprinklerforum-boun...@lists