RE: Distilled spirits

2022-03-07 Thread Prahl, Craig/GVL via Sprinklerforum
Steve are you sure about that 1A classification? Flash point < 73 degrees (F) with a boiling point temp of <100 degrees (F)? 80% Ethyl Alcohol is a 1B. Craig Prahl | Jacobs | Group Lead/SME - Fire Protection | craig.pr...@jacobs.com | www.jacobs.com 1041 East Butler Road Greenville, South

RE: [EXTERNAL] Joining black carbon steel with stainless steel piping

2022-03-03 Thread Prahl, Craig/GVL via Sprinklerforum
piping. I bet they 90 over to some device and really have a ductile iron or such fitting connecting to the unit. > On Mar 3, 2022, at 8:22 AM, Prahl, Craig/GVL via Sprinklerforum > wrote: > > I spoke with a technical rep at Ames earlier in the week regarding this > quest

RE: 13D UG flush

2022-03-03 Thread Prahl, Craig/GVL via Sprinklerforum
I'd remind them that if there are any obstructions found in your aboveground system, they will be charged for any project delays, system repairs or other damages. I had a contractor do that on a project of mine and while doing a trip test (dry pipe system) we couldn't get the system to pass.

RE: [EXTERNAL] Re: Joining black carbon steel with stainless steel piping

2022-03-03 Thread Prahl, Craig/GVL via Sprinklerforum
;> environment is considered 'harsh', the anodic index delta must be smaller >>> (approximately 0.15 V) in which case, some sort of dielectric >>> fitting/sacrificial anode would be needed for joint longevity. >>>>> As I am not an expert, I suggest reaching out t

Joining black carbon steel with stainless steel piping

2022-02-28 Thread Prahl, Craig/GVL via Sprinklerforum
I've got a engineer asking about the joining of grooved stainless to grooved black carbon steel and if there needs to be a special dielectric or similar type of assembly used to join the two? I've been hunting on the interwebs and haven't found any type of special coupling or should the

RE: [EXTERNAL] Sprinkler in elevator pit.

2022-02-26 Thread Prahl, Craig/GVL via Sprinklerforum
Enclosed is four walls. If it doesn't have four walls around the cab it's a hoistway not an enclosed shaft. Craig Prahl | Jacobs | Group Lead/SME – Fire Protection | craig.pr...@jacobs.com | www.jacobs.com 1041 East Butler Road Greenville, South Carolina 29606 CONTACT BY: email or MS

RE: [EXTERNAL] 8 inch sprinkler pipe fall from factory ceiling

2022-02-24 Thread Prahl, Craig/GVL via Sprinklerforum
I've been involved in several system failure investigations. There are numerous causes. Things to look for: 1. Rolled grooves: were the grooves in the pipe determined to have been done correctly and to manufacturer's specifications? 2. Were coupling bolts torqued to proper spec. This one is a

RE: [EXTERNAL] Obstructed vs Unobstructed Construction

2022-02-16 Thread Prahl, Craig/GVL via Sprinklerforum
What are the depths of the joists, the depth of the insulation and the spacing between the joists? Craig Prahl | Jacobs | Group Lead/SME – Fire Protection | craig.pr...@jacobs.com | www.jacobs.com 1041 East Butler Road Greenville, South Carolina 29606 CONTACT BY: email or MS TEAMS

RE: Group III Aircraft hanger

2022-02-09 Thread Prahl, Craig/GVL via Sprinklerforum
So a couple of questions come to mind. Does the applicable local code require sprinklers? Does the owner want sprinklers even if the code doesn’t require them? Where is this building located? Remember, a wet system needs to be in a heated space, if the hangar is in a northern climate where

RE: Group III Aircraft hanger

2022-02-09 Thread Prahl, Craig/GVL via Sprinklerforum
Have you looked at NFPA 409 and the current Building/fire codes? Craig Prahl | Jacobs | Group Lead/SME - Fire Protection | craig.pr...@jacobs.com | www.jacobs.com 1041 East Butler Road Greenville, South Carolina 29606 CONTACT BY: email or MS TEAMS -Original Message- From:

RE: NFPA 13, 1978 Table 2.2.1 (B)

2022-02-09 Thread Prahl, Craig/GVL via Sprinklerforum
Thanks Cecil, The attachments didn't come through but several other members of the forum had sent me the tables. Craig Prahl | Jacobs | Group Lead/SME - Fire Protection | craig.pr...@jacobs.com | www.jacobs.com 1041 East Butler Road Greenville, South Carolina 29606 CONTACT BY: email or MS

NFPA 13, 1978 Table 2.2.1 (B)

2022-02-08 Thread Prahl, Craig/GVL via Sprinklerforum
I'm in the middle of a whse renovation project study and the original design used NFPA 231, it references 1978 NFPA 13, Table 2.2.1(B). Would anyone have a copy of the 1978 NFPA 13 and could send me a snapshot of that Table? I've looked on the NFPA site and they don't have versions available

RE: [EXTERNAL] RE: INDOOR SPORTS FACILITY FIELD HOUSE

2022-02-07 Thread Prahl, Craig/GVL via Sprinklerforum
Take it a step farther. You need to look at all the various areas within the building. For multi-use buildings, you can have various levels of hazards under one roof. This is one reason why you can't use the annex as an end-all of occupancies. Tall, open areas need to be looked at

RE: Commodity Classification

2022-02-01 Thread Prahl, Craig/GVL via Sprinklerforum
These things are like 98% plastic. Maybe the motherboard is or isn't a plastic, not really sure. I took one of ours apart after it was struck by lightning. There's no metal in it at all. Regardless of packaging, I would be calling it a Group A plastic commodity. Craig Prahl | Jacobs | Group

RE: [EXTERNAL] Peat Plant

2022-01-26 Thread Prahl, Craig/GVL via Sprinklerforum
Is this is a storage area or part of a processing area, different hazards are present depending on specifics. Craig Prahl | Jacobs | Group Lead/SME - Fire Protection | craig.pr...@jacobs.com | www.jacobs.com 1041 East Butler Road Greenville, South Carolina 29606 CONTACT BY: email or MS

RE: question about Storage height

2022-01-26 Thread Prahl, Craig/GVL via Sprinklerforum
The liquid is a corrosive, non-issue from our perspective. I would wager they don't have adequate secondary containment or spill control within the room where these are stored which is why they're using these IBC containment units. I'd be curious how many totes do they store in this area? If

RE: question about Storage height

2022-01-26 Thread Prahl, Craig/GVL via Sprinklerforum
You don't have 5 ft of commodity. The liquid within the tote is irrelevant to the hazard. You essentially have a plastic hazard that is 10 ft in height. Now, there are some schools of thought that derate the level of hazard due to the liquid acting as a heat sink and thereby providing a

RE: question about Storage height

2022-01-26 Thread Prahl, Craig/GVL via Sprinklerforum
I would be addressing this as plastic storage since the liquid is a non-flammable/combustible liquid and there is the presence of empty plastic containers. Craig Prahl | Jacobs | Group Lead/SME - Fire Protection | craig.pr...@jacobs.com | www.jacobs.com 1041 East Butler Road Greenville,

RE: [EXTERNAL] Re: Food trucks inside a building

2022-01-13 Thread Prahl, Craig/GVL via Sprinklerforum
Shielded fires wouldn't be my primary concern, fuel density and fire intensity would be my concerns. A little fire in a truck can be handled by a fire extinguisher. I'm not sure if food trucks are required to have anything other than that for fire control. But a fire in one of these units is

RE: Food trucks inside a building

2022-01-13 Thread Prahl, Craig/GVL via Sprinklerforum
First off, it needs to be determined based on the CODE or local ordinance if this is even allowed. Forget NFPA 13 for the moment. The fuel loading within a typical food truck is pretty high considering the amount of gasoline and propane in each truck. If you look at this simply from a

RE: [EXTERNAL] RE: Open or exterior corridors

2022-01-06 Thread Prahl, Craig/GVL via Sprinklerforum
ing Technician | Bamford Fire Sprinkler Co., Inc. P:785.825.7710 F:785.825.0667 A: 1383 W. North Street Salina, KS 67401 -Original Message- From: Sprinklerforum On Behalf Of Prahl, Craig/GVL via Sprinklerforum Sent: Wednesday, January 5, 2022 9:14 AM To: sprinklerforum@lists.fir

RE: Open or exterior corridors

2022-01-06 Thread Prahl, Craig/GVL via Sprinklerforum
rum On Behalf Of Prahl, Craig/GVL via Sprinklerforum Sent: Wednesday, January 5, 2022 9:14 AM To: sprinklerforum@lists.firesprinkler.org Cc: Prahl, Craig/GVL ; Matt Grise ; Kevin Hall Subject: RE: Thread connection holding on one thread only The depth of engagement to form a leakproof connectio

RE: Thread connection holding on one thread only

2022-01-05 Thread Prahl, Craig/GVL via Sprinklerforum
The depth of engagement to form a leakproof connection is dependent on the pipe diameter and system pressure. For general talking purposes per ASME B1.20.1, for NPT pipes, a 1.25" pipe is shown as having 11.5 threads per inch with the typical hand tightening limitation at 4.5 turns for a depth

RE: UFGS spec section 21 13 00.00 40 vs 21 13 13

2021-12-21 Thread Prahl, Craig/GVL via Sprinklerforum
Some engineers and engineering firms do not edit specs to make them specific to the project. They leave everything in the spec so they can just change a date and project number and issue it for any type of project and figure the contractor is supposed to figure out what applies and what

RE: [EXTERNAL] Re: Sprinkler protection in a freezer warehouse - with plastics

2021-12-15 Thread Prahl, Craig/GVL via Sprinklerforum
is week AFSA On Wed, Dec 15, 2021 at 2:49 AM Prahl, Craig/GVL via Sprinklerforum mailto:sprinklerforum@lists.firesprinkler.org>> wrote: I have searched the from the deepest depths to the highest heights within NFPA 13 for a solution and am coming up empty. We have a freezer warehouse, stor

RE: NFPA #30 Containment

2021-12-15 Thread Prahl, Craig/GVL via Sprinklerforum
James, I'm curious what is your plan for sprinkler protection of these materials? For many in the IB category water alone is virtually of no affect. Especially when it comes to those classified as hydrocarbons. I do hope the owner or someone provided you with SDS info on the materials. Craig

RE: [EXTERNAL] Re: NFPA #30 Containment

2021-12-15 Thread Prahl, Craig/GVL via Sprinklerforum
There are two categories when dealing with the spillage of hazardous materials. The first one is Spill Control the other is Secondary Containment. It needs to be established as to which is required. The establishment of the requirement for secondary containment defined within the IFC. NFPA

Sprinkler protection in a freezer warehouse - with plastics

2021-12-14 Thread Prahl, Craig/GVL via Sprinklerforum
I have searched the from the deepest depths to the highest heights within NFPA 13 for a solution and am coming up empty. We have a freezer warehouse, storing packaged meats on foam trays which are placed in plastic trays. The frozen meat per NFPA 13 is a class III, the kicker is the exposed,

RE: [EXTERNAL] RE: Fire Pumps and fire apparatus

2021-09-16 Thread Prahl, Craig/GVL via Sprinklerforum
825 direct 260.487.7824 / > cell 260.417.0625 / fax 260.487.7991 email mmo...@shambaugh.com > > > > -Original Message- > From: Sprinklerforum > On Behalf Of Prahl, Craig/GVL via Sprinklerforum > Sent: Wednesday, September 15, 2021 9:07 AM > To: sprinklerfor

RE: Fire Pumps and fire apparatus

2021-09-15 Thread Prahl, Craig/GVL via Sprinklerforum
(218) 279-2436 direct | (218) 310-2446 cell LHB, Inc. | PERFORMANCE DRIVEN DESIGN -Original Message- From: Sprinklerforum On Behalf Of Prahl, Craig/GVL via Sprinklerforum Sent: Wednesday, September 15, 2021 8:07 AM To: sprinklerforum@lists.firesprinkler.org Cc: Prahl, Craig/GVL ; BR

Fire Pumps and fire apparatus

2021-09-15 Thread Prahl, Craig/GVL via Sprinklerforum
I'd like to piggyback on this conversation since it migrated towards fire apparatus capabilities. I have a client with a multi-building industrial site which has a fire pump providing flow and pressure to a site wide fire loop which serves both hydrants and building sprinkler/standpipe

RE: Fire Pump Room Sprinkler Classification

2021-09-13 Thread Prahl, Craig/GVL via Sprinklerforum
If you look at the definitions in NFPA 13 of the various occupancies, the presence of diesel fuel (combustible liquid) would dictate an EH2. With electric pumps OH1 or OH2 would be fine. Craig Prahl | Jacobs | Group Lead/SME - Fire Protection | craig.pr...@jacobs.com | www.jacobs.com 1041 East

RE: [EXTERNAL] Transfer Switches

2021-08-30 Thread Prahl, Craig/GVL via Sprinklerforum
No. Just because a generator is present doesn't automatically require it to be connected to the fire pump. The requirement of secondary or backup power for an electric fire pump is directly related to the reliability of the primary power source and other factors, some which may be code driven,

RE: Fire Pump Backflow

2021-08-26 Thread Prahl, Craig/GVL via Sprinklerforum
I have doubts that the "engineer" has any clue what a jockey pump does or how it works. So, you'd have a connection on the suction side of the fire pump that typically connects back to the discharge side of the pump. Does the engineer think you are going to take and route another connection

RE: [EXTERNAL] Fire Pump Backflow

2021-08-25 Thread Prahl, Craig/GVL via Sprinklerforum
Does the water tank also provide water to potable systems or is it just dedicated to the fire sprinkler systems? This is the one reason why BFPs are not installed on the suction side of pumps. If it's required, take it out and put it on the discharge side. The question does come to mind in

RE: [EXTERNAL] Re: Clean Agent System

2021-08-23 Thread Prahl, Craig/GVL via Sprinklerforum
4.3.1.1.4 is where I usually take a stand and expect any function that is related to the operation of the CA system to originate within the CA system releasing panel. Now there have been times when things such as dampers and AHU shutdown have had primary control in BMS or a PLC and we had the

RE: [EXTERNAL] Re: Stub-up Material

2021-08-19 Thread Prahl, Craig/GVL via Sprinklerforum
therefore not be considered, nor relied upon, as such. Bob Caputo, President American Fire Sprinkler Association -Original Message- From: Sprinklerforum On Behalf Of Prahl, Craig/GVL via Sprinklerforum Sent: Tuesday, July 6, 2021 10:47 AM To: sprinklerforum@lists.firesprinkler.org Cc

RE: [EXTERNAL] Re: Stub-up Material

2021-07-06 Thread Prahl, Craig/GVL via Sprinklerforum
ttp://www.firesprinkler.org/trainers__;!!B5cixuoO7ltTeg!TVb4HhVqGQkfYgH1yXI2yMhPH9cH16hP1L-R9uVeY3LqbPxGbKfbNYKU13O-0Eqajw$ > for more information. On Tue, Jun 29, 2021 at 2:43 PM Prahl, Craig/GVL via Sprinklerforum < sprinklerforum@lists.firesprinkler.org> wrote: > I think t

RE: [EXTERNAL] Re: Stub-up Material

2021-06-29 Thread Prahl, Craig/GVL via Sprinklerforum
I think the question was related to the material, not the height of the extension above the slab. 1. Go to the manufacturer's data and see if it is listed to be installed above grade per UL and/or FM as a fire riser. 2. Exposure to elevated temperatures such as in a fire event can cause

RE: Calculating Parallel fire pumps

2021-06-21 Thread Prahl, Craig/GVL via Sprinklerforum
bafe511*7C0*7C0*7C636379016677342180=eGdMZGu2wXhUupGwgGTrqF3b54OP5*2BAZvlHhABSexWY*3D=0__;JSUlJSUlJSUlJSUlJSU!!B5cixuoO7ltTeg!TbhbVfeVYScuQbgWTaK5_QrjN4ennB3fPRXxf9fzmS-8Y1xry_7_iBOEHazg27rPDQ$ > From: Sprinklerforum On Behalf Of Prahl, Craig/GVL via Sprinklerforum Sent: Monday, Jun

RE: [EXTERNAL] RE: Calculating Parallel fire pumps

2021-06-21 Thread Prahl, Craig/GVL via Sprinklerforum
://www.fire-design.com__;!!B5cixuoO7ltTeg!VIFOlr4gzA-Y8WAyIEVFQ2jJrf3Kw-mUdrihyP89TzChefgrazPOYRPm8ChMruYeQw$ -Original Message- From: Sprinklerforum On Behalf Of Prahl, Craig/GVL via Sprinklerforum Sent: Monday, June 21, 2021 10:37 AM To: sprinklerforum@lists.firesprinkler.org Cc: Prahl, Craig

RE: Calculating Parallel fire pumps

2021-06-21 Thread Prahl, Craig/GVL via Sprinklerforum
dor? Matt -Original Message- From: Sprinklerforum On Behalf Of Prahl, Craig/GVL via Sprinklerforum Sent: Monday, June 21, 2021 9:37 AM To: sprinklerforum@lists.firesprinkler.org Cc: Prahl, Craig/GVL Subject: Calculating Parallel fire pumps We have a project in one of the Arab states. We are

Calculating Parallel fire pumps

2021-06-21 Thread Prahl, Craig/GVL via Sprinklerforum
We have a project in one of the Arab states. We are following a little bit of the UFC and some of the local codes. The owner wants two pumps selected at 50% of the required capacity instead of one pump as we would normally provide. His thought is that pump 1 comes on and runs at 50% of it's

RE: Fire Pump intake pipe screen

2021-06-02 Thread Prahl, Craig/GVL via Sprinklerforum
Check your email. Craig Prahl | Jacobs | Group Lead/SME - Fire Protection | craig.pr...@jacobs.com | www.jacobs.com 1041 East Butler Road Greenville, South Carolina 29606 CONTACT BY: email or MS TEAMS -Original Message- From: Sprinklerforum On Behalf Of James Crawford via

RE: Interstitial Space

2021-05-11 Thread Prahl, Craig/GVL via Sprinklerforum
I've had two projects recently with walkable ceilings, one was pharmaceutical and another microelectronics. Both had sprinklers above the walkable ceiling. One was an FM insured the other was not. The space is accessible and the whole purpose of the walkable ceiling was to aid in access to

RE: Interstitial Space

2021-05-11 Thread Prahl, Craig/GVL via Sprinklerforum
What's the occupancy classification of the occupied space below? Next question, what is the interstitial space being used for? Craig Prahl | Jacobs | Group Lead/SME - Fire Protection | craig.pr...@jacobs.com | www.jacobs.com 1041 East Butler Road Greenville, South Carolina 29606 CONTACT

RE: [EXTERNAL] Re: Available Pressure from Fire Water Storage Tank

2021-05-10 Thread Prahl, Craig/GVL via Sprinklerforum
You'd use the flow data you got from a nearby hydrant flow test. Typically I've not seen a ground tank that supplies a municipal system via gravity. In the municipal installations I've dealt with, a ground tank where there was no elevation difference had pumped supplies. Craig Prahl | Jacobs

RE: Available Pressure from Fire Water Storage Tank

2021-05-10 Thread Prahl, Craig/GVL via Sprinklerforum
The difference would be that you are NOT 100 ft above ground. You have a ground suction tank where the water level might only be a foot or two above ground. Apples and oranges. Craig Prahl | Jacobs | Group Lead/SME - Fire Protection | craig.pr...@jacobs.com | www.jacobs.com 1041 East Butler

RE: Hydrant barrel loss

2021-04-27 Thread Prahl, Craig/GVL via Sprinklerforum
Steve, did you get my email with hydrant info attached? Craig Prahl-- -Original Message- From: Sprinklerforum On Behalf Of Steve Leyton via Sprinklerforum Sent: Tuesday, April 27, 2021 12:46 PM To: BRUCE VERHEI ; sprinklerforum@lists.firesprinkler.org Cc: Steve Leyton ; Bob Caputo

RE: Fire Pump Sprk & Fire Flow Demand

2021-04-21 Thread Prahl, Craig/GVL via Sprinklerforum
Are site Fire Flow requirements (IFC Section 507) what you're referring to as "hydrant demand"? At minimum, the pump should be capable of flowing the sprinkler and related hose stream allowance flow rate combined. BUT, when there have been no municipal hydrants to be used for the actual

RE: [EXTERNAL] IEBC and NFPA 14

2021-03-31 Thread Prahl, Craig/GVL via Sprinklerforum
Correct. Requirements of the IEBC are specific as they relate to the new work being done in the existing building. It would be a massive financial disaster to require all existing buildings to come into compliance with current codes based solely on the adoption of a new code. Craig Prahl |

RE: [EXTERNAL] IEBC and NFPA 14

2021-03-31 Thread Prahl, Craig/GVL via Sprinklerforum
The IEBC is applied to an existing building when you are performing new work such as renovations or reconstruction within that existing building. The IEBC makes allowances for certain conditions and has less stringent requirements than the IBC when you are working in an existing building. You

RE: [EXTERNAL] IEBC and NFPA 14

2021-03-31 Thread Prahl, Craig/GVL via Sprinklerforum
If the IEBC was adopted by legislation without amendments, you would be required to comply with any and all NFPA Standards referenced in that Code which were applicable to your type of building or occupancy. BUT, this does not mean existing buildings have to now go and install systems that

RE: [EXTERNAL] Fire sprinkler protection in sugar refinery

2021-03-30 Thread Prahl, Craig/GVL via Sprinklerforum
Michael, when you say "flush heads" do you mean concealed type sprinklers with covers like often used in offices? If so, they are typically not Listed or Approved for anything but light hazard type occupancies. I would not consider this type of area to be LH. Craig Prahl | Jacobs | Group

RE: [EXTERNAL] Re: Question regarding protection of sprinkler heads in Sugar Refinery

2021-03-30 Thread Prahl, Craig/GVL via Sprinklerforum
Cellophane bags covering sprinklers will not initiate any kind of recall. This is a common practice for paint booths and is referenced within NFPA 13. The bags are to be no thicker than 0.003 inches or 0.08 mm. These bags must be cellophane or paper not just any type of plastic and should be

RE: Smoke Detectors

2021-03-18 Thread Prahl, Craig/GVL via Sprinklerforum
Carr, SET Project Manager/Design Diboco Fire Sprinklers, Inc. 325 Jackson Loop Road Flat Rock, NC 28731 rich...@diboco.com 828-696-3400 828-696-2288 Fax 828-708-9118 Mobile -Original Message- From: Sprinklerforum On Behalf Of Prahl, Craig/GVL via Sprinklerforum Sent: Thursday, March 18,

RE: Smoke Detectors

2021-03-18 Thread Prahl, Craig/GVL via Sprinklerforum
I searched NFPA 13, 15 and 72 and couldn't find anything referring to a separation between a detector and a sprinkler. Craig Prahl | Jacobs | Group Lead/SME - Fire Protection | craig.pr...@jacobs.com | www.jacobs.com 1041 East Butler Road Greenville, South Carolina 29606 CONTACT BY: email or

RE: [EXTERNAL] RE: Multiple System Calculation

2021-02-11 Thread Prahl, Craig/GVL via Sprinklerforum
otw$> From: Sprinklerforum mailto:sprinklerforum-boun...@lists.firesprinkler.org>> On Behalf Of Prahl, Craig/GVL via Sprinklerforum Sent: Thursday, February 11, 2021 1:20 PM To: b...@firebyknight.com<mailto:b...@firebyknight.com>; sprinklerforum@lists.firesprinkler.org<mail

RE: [EXTERNAL] RE: Multiple System Calculation

2021-02-11 Thread Prahl, Craig/GVL via Sprinklerforum
This is something that really needs to be looked at I future editions of NFPA 13. I know we've had this discussion many times. I would love to hear how this came about. It offers no benefit to an owner and only increases cost. Craig Prahl | Jacobs | Group Lead/SME – Fire Protection |

RE: Tissue Paper Wrapped in Plastic

2021-02-02 Thread Prahl, Craig/GVL via Sprinklerforum
w.firesprinkler.org*2fschools.=E,1,CkNDea30BW_p5PaehQxMO3eRwHYTkGmF9RG7CK-Tg6pAjv26sHa5xbez5VcvdrA3_bNOdsviMED4IPcjgtTOFLPwHIsX1h8miGVMY5w-Mm_pvxE,=1__;JSUlJQ!!B5cixuoO7ltTeg!TMNFcfNkcjX7Kv654ixgVlbqCccIDIF8jGkZYOVNeF8vyiO5jIz6UKWvfrtzClNI7g$ On Mon, Feb 1, 2021 at 2:50 PM Prahl, Craig/GVL vi

RE: Fluorine-Free Foams (FFF)

2021-02-01 Thread Prahl, Craig/GVL via Sprinklerforum
Contact one of the foam manufactures of the product. They can give you all the info you need. Craig Prahl | Jacobs | Group Lead/SME - Fire Protection | craig.pr...@jacobs.com | www.jacobs.com 1041 East Butler Road Greenville, South Carolina 29606 CONTACT BY: email or MS TEAMS -Original

RE: ESFR & Obstruction in Light Hazard

2021-02-01 Thread Prahl, Craig/GVL via Sprinklerforum
IMHO, if ESFRs are installed, ESFR obstruction rules should apply regardless of how they are currently using it. Is there a legally defendable argument for ignoring the ESFR rules? Craig Prahl | Jacobs | Group Lead/SME - Fire Protection | craig.pr...@jacobs.com | www.jacobs.com 1041 East

RE: Tissue Paper Wrapped in Plastic

2021-02-01 Thread Prahl, Craig/GVL via Sprinklerforum
Yes, the plastic is the material first exposed to the fire/ignition source. Craig Prahl | Jacobs | Group Lead/SME - Fire Protection | craig.pr...@jacobs.com | www.jacobs.com 1041 East Butler Road Greenville, South Carolina 29606 CONTACT BY: email or MS TEAMS -Original Message- From:

RE: Stand-Alone UPS protection design

2021-01-14 Thread Prahl, Craig/GVL via Sprinklerforum
So, I'll assume this battery assembly will be in some type of occupiable enclosure which will have environmental control. I would definitely not extend or try to tie it into any existing PreAction system. I would be looking at a stand alone suppression system, either clean agent or aerosol

RE: Stand-Alone UPS protection design

2021-01-14 Thread Prahl, Craig/GVL via Sprinklerforum
Steve, Can you provide a better description of this unit? How far from the building will it be located? Craig Prahl | Jacobs | Group Lead/SME - Fire Protection | craig.pr...@jacobs.com | www.jacobs.com 1041 East Butler Road Greenville, South Carolina 29606 CONTACT BY: email or MS TEAMS

RE: RV Storage

2021-01-11 Thread Prahl, Craig/GVL via Sprinklerforum
I concur. RVs represent a concealed hazard, boats not so much unless they are larger with cabins. Then consider the proximity of one unit to another. Any fire is going to involve several units. Even EH2 would probably be like spitting on a forest fire. Building height also plays a role.

RE: RV Storage

2021-01-11 Thread Prahl, Craig/GVL via Sprinklerforum
Clarify please. What storage is not going to exceed 12 ft? How high are the high bays? When you say RV are you talking about motorhomes and/or travel trailers? Craig Prahl | Jacobs | Group Lead/SME - Fire Protection | craig.pr...@jacobs.com | www.jacobs.com 1041 East Butler Road

RE: Open Grate Flooring - Calculations

2021-01-04 Thread Prahl, Craig/GVL via Sprinklerforum
Industrial buildings with open grating between levels can be a little more involved than just calculating a density/area. First, what's the hazard? Are ignitable liquids involved? At what levels? Any at high pressure (over 15 psig)? Is the building open sided or fully enclosed? How large

RE: [EXTERNAL] 23.4.4.2.5: What is the purpose and how does it apply?

2020-12-14 Thread Prahl, Craig/GVL via Sprinklerforum
lerforum > <mailto:sprinklerforum-boun...@lists.firesprinkler.org> On Behalf Of > Prahl, Craig/GVL via Sprinklerforum > Sent: Thursday, December 10, 2020 11:33 AM > To: mailto:sprinklerforum@lists.firesprinkler.org > Cc: Prahl, Craig/GVL <mailto:craig.pr...@jacobs.com>; James Lit

RE: [EXTERNAL] 23.4.4.2.5: What is the purpose and how does it apply?

2020-12-10 Thread Prahl, Craig/GVL via Sprinklerforum
161 > > > > -Original Message- > From: Sprinklerforum > <mailto:sprinklerforum-boun...@lists.firesprinkler.org> On Behalf Of > Prahl, Craig/GVL via Sprinklerforum > Sent: Thursday, December 10, 2020 11:33 AM > To: mailto:sprinklerforum@lists.firesprinkle

RE: [EXTERNAL] 23.4.4.2.5: What is the purpose and how does it apply?

2020-12-10 Thread Prahl, Craig/GVL via Sprinklerforum
Very good question. I've read discussions on this issue recently as well and really wonder what was the thought process behind including a non-existent flow value in the system design and calculations. I would love to hear the rationale for this section. Craig Prahl | Jacobs | Group Lead/SME

RE: [EXTERNAL] pump suction pressure

2020-12-07 Thread Prahl, Craig/GVL via Sprinklerforum
Consult the pump manufacturer (if you don't have the information) and find out what the minimum acceptable NPSH is for that pump. It can vary based on pump design and selection criteria but if the suction pressure falls below the mfgrs. NPSH you can end up with pump cavitation and destroy the

RE: Class IIIB Liquids

2020-11-30 Thread Prahl, Craig/GVL via Sprinklerforum
First thing is that you need to know what you're dealing with. Some ignitable liquids can be handled using a standard water based sprinkler systems designed for EHII. Others may need the addition of foam to control a fire due to them not being a miscible liquid. Think water on a cooking oil

RE: Class IA Flammable Liquids

2020-11-09 Thread Prahl, Craig/GVL via Sprinklerforum
If my main concern is assigning a proper fire protection design criteria and it's not your typical hazardous chemical, I start with the MSDS/SDS and look at the fire fighting section. Now that won't tell you what density to use but what it will tell you is what acceptable means for

RE: [EXTERNAL] Re: Class IA Flammable Liquids

2020-11-05 Thread Prahl, Craig/GVL via Sprinklerforum
1A materials are fairly uncommon. Often they are mislabeled due to people only looking at the flash point and not at the boiling point of the liquid. In cosmetics 1B is common. You need to know exactly what the material is. Request a SDS on the material. NFPA doesn't get into comparing

Fire pump suction diffusers

2020-10-22 Thread Prahl, Craig/GVL via Sprinklerforum
2019 edition of NFPA 20 has references to the acceptable use of suction diffusers on fire pumps. Does anyone have a model or mfgr. of a listed one? I've been looking but still haven't found one yet. Craig Prahl | Jacobs | Group Lead/SME – Fire Protection | 864.676.5252 |

RE: [EXTERNAL] Seed Cleaning Plant

2020-10-15 Thread Prahl, Craig/GVL via Sprinklerforum
You're gonna have to provide a WHOLE Lot more info than that. There are numerous processes, different types of seeds, different types of cleaning/hulling processes etc., etc., etc., etc There is no one size fits all sprinkler density answer. Craig Prahl | Jacobs |

RE: [EXTERNAL] Re: Submittal Packages

2020-10-08 Thread Prahl, Craig/GVL via Sprinklerforum
that should be provided to the installing contractor before they can begin their work. On Thu, Oct 8, 2020 at 12:39 PM Prahl, Craig/GVL via Sprinklerforum < sprinklerforum@lists.firesprinkler.org> wrote: > You cannot select a fire pump when no water flow test has been done, > you don’t h

RE: [EXTERNAL] Re: Submittal Packages

2020-10-08 Thread Prahl, Craig/GVL via Sprinklerforum
of the EOR. Look at the requirements for the owners certificate. All that should be provided to the installing contractor before they can begin their work. On Thu, Oct 8, 2020 at 12:39 PM Prahl, Craig/GVL via Sprinklerforum < sprinklerforum@lists.firesprinkler.org> wrote: > You cannot sele

RE: [EXTERNAL] Re: Submittal Packages

2020-10-08 Thread Prahl, Craig/GVL via Sprinklerforum
YMvEVomaeod3w$> 8201 Norman Center Drive, Suite 500 \ Minneapolis-St. Paul, MN 55437 *Registered in: LA, MD, MN, PA, TX, & UT **NICET IV - Water-Based Systems Layout -Original Message- From: Sprinklerforum mailto:sprinklerforum-boun...@lists.firesprinkler.org>> On Behalf

RE: [EXTERNAL] Re: Submittal Packages

2020-10-08 Thread Prahl, Craig/GVL via Sprinklerforum
ou need to know and never miss another issue. On Thu, Oct 8, 2020 at 11:08 AM Prahl, Craig/GVL via Sprinklerforum < sprinklerforum@lists.firesprinkler.org> wrote: > Just a general question. > > Do you submit your shop drawing package to the EOR as one package or > do you s

Submittal Packages

2020-10-08 Thread Prahl, Craig/GVL via Sprinklerforum
Just a general question. Do you submit your shop drawing package to the EOR as one package or do you submit components first and then later the layout drawings and calcs? Craig Prahl | Jacobs | Group Lead/SME – Fire Protection | 864.676.5252 | craig.pr...@jacobs.com | www.jacobs.com 1041 East

RE: ESFR and Obstructed Construction

2020-10-06 Thread Prahl, Craig/GVL via Sprinklerforum
What is the ESFR system design basis? Racks or other storage or what? Craig Prahl | Jacobs | Group Lead/SME - Fire Protection | 864.676.5252 | craig.pr...@jacobs.com | www.jacobs.com 1041 East Butler Road Greenville, South Carolina 29606 -Original Message- From: Sprinklerforum On

RE: ESFR and Obstructed Construction

2020-10-06 Thread Prahl, Craig/GVL via Sprinklerforum
The minimum for ESFRs has to do with skipping. Same goes for CMSA type sprinklers. NFPA 13 Handbook- "Skipping occurs when the sprinklers do not operate in a normal pattern and when sprinklers some distance from the fire operate before those sprinklers closest to the fire. Air movement and

RE: [EXTERNAL] Seed Hopper/Bulk Container

2020-09-22 Thread Prahl, Craig/GVL via Sprinklerforum
Contents aren't as significant as the containers. Depending on their state, (powder, meal, bulk, etc.) agricultural contents like these tend to represent more of an explosion hazard when they are being processed and handled than fire hazard while being stored. Some dried but unprocessed beans

RE: Seismic Special Inspection Requirements

2020-09-21 Thread Prahl, Craig/GVL via Sprinklerforum
Those are related to the capability of the structure and should be determined by a structural engineer. The analysis of the structure is outside a sprinkler contractors scope. #1 is kind of worded weirdly since one should typically be more concerned with the specific structural element you'd

Smart Plant 3D for fire protection design

2020-09-17 Thread Prahl, Craig/GVL via Sprinklerforum
Does anyone have any familiarity with using Smart Plant 3D for fire protection design? We've got great experience with REVIT but are being pushed into using SP3D because it works great for piping and of course we know there's no difference between process piping and sprinkler piping. Are there

RE: [EXTERNAL] Tire Carousel

2020-09-15 Thread Prahl, Craig/GVL via Sprinklerforum
and see what they offer. Thank you, Bob Knight, CET III Fire by Knight, LLC 208-318-3057 -Original Message- From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Prahl, Craig/GVL via Sprinklerforum Sent: Tuesday, September 15, 2020 11:22 AM To: b

RE: [EXTERNAL] Tire Carousel

2020-09-15 Thread Prahl, Craig/GVL via Sprinklerforum
Is it an enclosed or open array? These typically are not specifically addressed in NFPA 13. I have typically leaned on FM data sheets for design guidance on these special types of storage. Craig Prahl | Jacobs | Group Lead/SME - Fire Protection | 864.676.5252 | craig.pr...@jacobs.com |

RE: [EXTERNAL] Re: Non-Combustible Concealed Space

2020-09-10 Thread Prahl, Craig/GVL via Sprinklerforum
It's good this is being clarified and defined in the upcoming edition. Hopefully that will resolve the confusion on this issue once and for all. But, now back to 2020.. Craig Prahl | Jacobs | Group Lead/SME – Fire Protection | 864.676.5252 | craig.pr...@jacobs.com | www.jacobs.com

RE: Non-Combustible Concealed Space

2020-09-10 Thread Prahl, Craig/GVL via Sprinklerforum
Playing the devil's advocate here, one could argue that the presence of an electrically energized air handler negates the part stating "minimal combustible loading", that this is actually a mechanical closet not just a "concealed space". Craig Prahl | Jacobs | Group Lead/SME - Fire

RE: Code requiring inclusion of possible concurrent flow

2020-09-10 Thread Prahl, Craig/GVL via Sprinklerforum
A residential boat dock? Craig Prahl | Jacobs | Group Lead/SME - Fire Protection | 864.676.5252 | craig.pr...@jacobs.com | www.jacobs.com 1041 East Butler Road Greenville, South Carolina 29606 -Original Message- From: Sprinklerforum On Behalf Of Hinson, Ryan via Sprinklerforum

RE: [EXTERNAL] RE: Ethanol unloading exposure protection

2020-09-03 Thread Prahl, Craig/GVL via Sprinklerforum
Ben, Since we don’t' have a drawing or layout of what is where, there's going to be a lot of speculation and possibly misdirection when it comes to suggestions. So you'll have to sort through it all and find the applicable stuff. NFPA 80A provides direction on exposure protection

RE: [EXTERNAL] Re: C-Clamp Hangers

2020-08-26 Thread Prahl, Craig/GVL via Sprinklerforum
What do the specs say you're supposed to use in place of c-clamps? Craig Prahl | Jacobs | Group Lead/SME - Fire Protection | 864.676.5252 | craig.pr...@jacobs.com | www.jacobs.com 1041 East Butler Road Greenville, South Carolina 29606 > -Original Message- > From: Sprinklerforum > On

RE: [EXTERNAL] Re: Window Sprinklers

2020-08-25 Thread Prahl, Craig/GVL via Sprinklerforum
I wouldn't install a non-conforming component no matter who said they'd take liability. For me to install it knowing it's not right still can still result in some level of liability no matter how much I might protest. Unless the manufacturer responsible for the listing of the product issues a

RE: [EXTERNAL] Re: Window Sprinklers

2020-08-25 Thread Prahl, Craig/GVL via Sprinklerforum
The horizontal mullions create a horizontal barrier to the water run-down of the window sprinklers. So the architect is probably figuring that if they have window sprinklers located up high near the top of the frame and those wet the glass down to the mullion and then they have another row of

RE: Testing of existing systems (solution!)

2020-08-20 Thread Prahl, Craig/GVL via Sprinklerforum
The language in 2019 NFPA 13, 27.1.2 was already stated in the 2016 edition in 25.2.1.4 and 25.2.1.4.2. Craig Prahl | Jacobs | Group Lead/SME - Fire Protection | 864.676.5252 | craig.pr...@jacobs.com | www.jacobs.com 1041 East Butler Road Greenville, South Carolina 29606 -Original

RE: [EXTERNAL] Re: Testing of existing systems

2020-08-19 Thread Prahl, Craig/GVL via Sprinklerforum
Exactly. That statement should be made in your bid under Exceptions and Clarifications. No responsibility or liability related to leaks in existing systems if 200 psi pressure test is required. Craig Prahl | Jacobs | Group Lead/SME - Fire Protection | 864.676.5252 | craig.pr...@jacobs.com |

RE: [EXTERNAL] Re: Testing of existing systems

2020-08-19 Thread Prahl, Craig/GVL via Sprinklerforum
Sometimes it's not about how good of a job your fitters did but the unknown age and condition of the existing system piping you're tying into. There are times when a 200 psi test is all it takes to open up pinholes and create leaks. Now the owner looks at you as being responsible and you're

RE: [EXTERNAL] Re: Flexible assembly for Novec 1230 at seismic separation joint

2020-08-17 Thread Prahl, Craig/GVL via Sprinklerforum
z5PQ$ > > Think they can be mounted horizontally and vertically. > > On Mon, Aug 17, 2020 at 10:44 AM Prahl, Craig/GVL via Sprinklerforum < > sprinklerforum@lists.firesprinkler.org> wrote: > > > Has anyone had to provide a flexible assembly on a NOVEC 1230 system > wh