[Sprinklerforum] Re: Residential Sprinklers

2022-12-02 Thread Bobby Welch
PM To: Discussion list on issues relating to automatic fire sprinklers Subject: [Sprinklerforum] Re: Residential Sprinklers If the space above is an unprotected combustible space then it's 8, if the space is protected (sprinklered or fire rated or full of insulation) then it's 4

[Sprinklerforum] Re: Residential Sprinklers

2022-12-02 Thread Brett Peters
If the space above is an unprotected combustible space then it's 8, if the space is protected (sprinklered or fire rated or full of insulation) then it's 4 Thanks Brett Peters General Manager Installation & Design Proudline Fire Protection Services Ltd. br...@proudline.ca 780 490 7602

[Sprinklerforum] Re: Residential Sprinklers

2022-12-02 Thread Mike Morey
The standard specifically says “unsprinklered” when referring to the combustible concealed spaces and the 8 head requirement, so if you’re installing COINs I would say 4 is the right answer? Mike Morey CFPS 3229 • NICET S.E.T. 123677 Project Manager • Fire Protection Group Shambaugh & Son, LP

RE: Residential sprinklers

2021-12-02 Thread Cary Webber via Sprinklerforum
Carr Subject: RE: Residential sprinklers CAUTION: This email originated from outside of the organization. Do not click links or open attachments unless you can confirm the sender and know the content is safe. Viking has a residential upright. Richard M. Carr, SET Project Manager/Design

RE: Residential sprinklers

2021-12-02 Thread Richard Carr via Sprinklerforum
Viking has a residential upright. Richard M. Carr, SET Project Manager/Design Diboco Fire Sprinklers, Inc. 325 Jackson Loop Road Flat Rock, NC  28731 rich...@diboco.com 828-696-3400 828-696-2288 Fax 828-708-9118 Mobile -Original Message- From: Sprinklerforum On Behalf Of Trillium

Re: Residential Sprinklers in Stairs

2020-08-07 Thread Mark Phillips via Sprinklerforum
In a condo all residential heads within in the Unit In apartments Residential in the unit and extended coverage in hallways All other service areas QR heads Sent from my mobile device Please excuse spelling, grammar, and auto correction. Mark Phillips Branch Manager Fire Sprinkler Design,

RE: residential sprinklers

2019-01-07 Thread Trillium Fire Sprinkler Design Inc.
THANKS FOR ALL HEE HELP From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Taylor Schumacher Sent: January-07-19 1:32 PM To: sprinklerforum@lists.firesprinkler.org Subject: RE: residential sprinklers That is correct. I was unaware of this until my

RE: residential sprinklers

2019-01-07 Thread Travis Mack, SET, CFPS, CWBSP, RME-G
www.linkedin.com/in/travismack “The bitterness of poor quality remains long after the sweetness of low price is forgotten.” From: Sprinklerforum On Behalf Of Trillium Fire Sprinkler Design Inc. Sent: Monday, January 7, 2019 11:29 AM To: sprinklerforum@lists.firesprinkler.org Subject: RE: res

RE: residential sprinklers

2019-01-07 Thread Trillium Fire Sprinkler Design Inc.
AND USE THE GREATER OF THE 2. ANYONE DISAGREE? From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of cw bamford Sent: January-07-19 1:20 PM To: sprinklerforum@lists.firesprinkler.org Subject: Re: residential sprinklers For 18 x 18 use a 5.8 K 1/2"

RE: residential sprinklers

2019-01-07 Thread Travis Mack, SET, CFPS, CWBSP, RME-G
ong after the sweetness of low price is forgotten.” From: Sprinklerforum On Behalf Of cw bamford Sent: Monday, January 7, 2019 11:20 AM To: sprinklerforum@lists.firesprinkler.org Subject: Re: residential sprinklers For 18 x 18 use a 5.8 K 1/2" NPT or 7.6 K 3/4" NPT and

Re: residential sprinklers

2019-01-07 Thread cw bamford
Sent:* January-07-19 12:57 PM > *To:* Sprinklerforum > *Subject:* Re: residential sprinklers > > > > WHy not use a K5.6 residential sprinkler? > > > Todd G Williams, PE > > Fire Protection Design/Consulting > > Stonington, CT > > 860-535-2080 (of

RE: residential sprinklers

2019-01-07 Thread Trillium Fire Sprinkler Design Inc.
YES. I HAVE MANY OPTIONS. I JUST WANTED TO MAKE SUE I WAS READING THE CODE PROPERLY. THANKS FOR THE CONFIRMATION. From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Fpdcdesign Sent: January-07-19 12:57 PM To: Sprinklerforum Subject: Re: residential

Re: residential sprinklers

2019-01-07 Thread Fpdcdesign
WHy not use a K5.6 residential sprinkler? Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT 860-535-2080 (ofc) 860-553-3553 (fax) 860-608-4559 (cell) > > On Jan 7, 2019 at 12:53 PM, (mailto:st...@protectiondesign.com)>

RE: residential sprinklers

2019-01-07 Thread Steve Leyton
Sorry 'bout that last one. Assuming you stretch the spacing to 18' x 18' your math is correct. But you don't have to assume maximum listed areas of coverage, you use the actual S x L. If a residential sprinkler is spaced so that its area of coverage is 14' x 16'-9", you have to use a

RE: residential sprinklers

2019-01-07 Thread Steve Leyton
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Trillium Fire Sprinkler Design Inc. Sent: Monday, January 07, 2019 9:50 AM To: sprinklerforum@lists.firesprinkler.org Subject: residential sprinklers I HAVE A HOTEL THAT SAYS NFPA 13 DESIGN. IF I USE

RE: Residential Sprinklers

2018-03-06 Thread Reed A. Roisum, SET
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Steve Leyton Sent: Tuesday, March 6, 2018 10:25 AM To: sprinklerforum@lists.firesprinkler.org Subject: RE: Residential Sprinklers I would not get involved in such a toeing-the-line exercise. Just fire-protect the building per

RE: Residential Sprinklers

2018-03-06 Thread Steve Leyton
, i.e. life-safety. SL -Original Message- From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Reed A. Roisum, SET Sent: Tuesday, March 06, 2018 7:38 AM To: sprinklerforum@lists.firesprinkler.org Subject: RE: Residential Sprinklers Thank you. New

RE: Residential Sprinklers

2018-03-06 Thread MFP Design, LLC
after the sweetness of low price is forgotten." -Original Message- From: Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org> On Behalf Of Reed A. Roisum, SET Sent: Tuesday, March 6, 2018 8:38 AM To: sprinklerforum@lists.firesprinkler.org Subject: RE: Residential Sprinklers

RE: Residential Sprinklers

2018-03-06 Thread Reed A. Roisum, SET
| KFIengineers.com<http://www.kfiengineers.com> -Original Message- From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of John Paulsen Sent: Tuesday, March 6, 2018 8:22 AM To: sprinklerforum@lists.firesprinkler.org Subject: RE: Residential Spri

RE: Residential Sprinklers

2018-03-06 Thread John Paulsen
: Tuesday, March 6, 2018 9:14 AM To: Sprinklerforum <sprinklerforum@lists.firesprinkler.org> Subject: Re: Residential Sprinklers Reed, 6.7.7.1.3. (2007). Carries through in later versions (as far as I looked). I ran I. To a similar situation recently and we had to change

Re: Residential Sprinklers

2018-03-06 Thread Fpdcdesign
To: sprinklerforum@lists.firesprinkler.org > Subject: RE: Residential Sprinklers > > You can only have a maximum of 4 QR sprinklers per dwelling unit, not just > compartment. If you need more than 4 standard spray sprinklers, you can't > comply with 13R. > > > Travis Mac

RE: Residential Sprinklers

2018-03-06 Thread Reed A. Roisum, SET
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of MFP Design, LLC Sent: Monday, March 5, 2018 5:08 PM To: sprinklerforum@lists.firesprinkler.org Subject: RE: Residential Sprinklers You can only have a maximum of 4 QR sprinklers per dwelling unit, not just compartment. If you need more

RE: Residential Sprinklers

2018-03-05 Thread MFP Design, LLC
otten." -Original Message- From: Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org> On Behalf Of Art Tiroly Sent: Monday, March 5, 2018 4:00 PM To: sprinklerforum@lists.firesprinkler.org Subject: RE: Residential Sprinklers Using 5.6K QR heads will change the hydraulic calculat

RE: Residential Sprinklers

2018-03-05 Thread Art Tiroly
Using 5.6K QR heads will change the hydraulic calculations and minimum flows allowed by residential sprinklers. Art Tiroly ATCO Fire Protection/Tiroly 24400 Highland Rd CLE 44143 216-621-8899 216-570-7030 cell -Original Message- From: Sprinklerforum

Re: Residential Sprinklers

2018-03-05 Thread Ron Greenman
If someone asked me to interpret this I think I’d say 903.3.2 refers back to just 903.3.1 which directs you to 903.3.1.1 “unless otherwise permitted by Sections 903.3.1.2 and 903.3.1.3

RE: Residential Sprinklers and Fire Marshals

2016-06-03 Thread Steve Leyton
JD: I'm going to offer this up in the absence of any response. I don't think you're going to get any opinion from AHJ's in general except, "residential fire sprinklers save lives and are good for our community".From a fire service perspective, sprinklers also provide an exponentially

Re: Residential Sprinklers

2011-02-07 Thread George Medina Jr
Excellent! George Medina Jr. -Original Message- From: Cliff Whitfield cl...@fire-design.com To: sprinklerforum sprinklerforum@firesprinkler.org Sent: Sun, Feb 6, 2011 3:36 pm Subject: Residential Sprinklers Folks, Here is a link to an excellent article from the PME eNewsletter

RE: Residential Sprinklers

2011-02-06 Thread Rod DiBona
Interesting take on the possible litigation. I will be curious to see if any cases play out that way. Love his point of view. -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Cliff Whitfield Sent: Sunday,

Re: residential sprinklers on the TV

2010-10-27 Thread Ron Greenman
Nicely done. Hard to argue with the 1% and the firefighter says it's good and the insurance guy says save money. On Wed, Oct 27, 2010 at 1:04 PM, Rod DiBona r...@rapidfireinc.com wrote: Outstanding George!! We need more publicity like that. Rod DiBona Rapid Fire Protection -Original

RE: Residential Sprinklers on a dry System

2010-07-26 Thread Matt Grise
The residential dry pendant is approved for dry pipe systems! Matt Grisé PE*, LEED AP Sales Engineer Alliance Fire Protection *Licensed in KS MO 913.888.0647 ph 913.888.0618 f 913.927.0222 cell www. AFPsprink.com -Original Message- From: sprinklerforum-boun...@firesprinkler.org

RE: Residential Sprinklers on a dry System

2010-07-26 Thread Mike Hairfield
The residential area is a conditioned space above and below the ceiling, why can't we use residential pendents on return bends? Mike From: m...@afpsprink.com To: sprinklerforum@firesprinkler.org Date: Mon, 26 Jul 2010 13:36:35 -0500 Subject: RE: Residential Sprinklers on a dry System

RE: Residential Sprinklers on a dry System

2010-07-26 Thread Steve Leyton
...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Matt Grise Sent: Monday, July 26, 2010 11:37 AM To: 'sprinklerforum@firesprinkler.org' Subject: RE: Residential Sprinklers on a dry System The residential dry pendant is approved for dry pipe systems! Matt Grisé PE

RE: Residential Sprinklers for Dry Pipe Systems

2010-07-10 Thread Mike Cabral
: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Todd Williams Sent: Friday, July 09, 2010 6:40 AM To: sprinklerforum@firesprinkler.org Subject: RE: Residential Sprinklers for Dry Pipe Systems Always the last to know. However, I could

Re: Residential Sprinklers for Dry Pipe Systems

2010-07-09 Thread Todd Williams
There is no dry-type residential sprinkler that I could find on the Tyco web site. Never heard of one either. Unless this is something new, he may be blowing smoke up your whoops-a-daisy. My guess is that you are going to have to use QR sprinklers and a 1950 sqft design area. Could you split

RE: Residential Sprinklers for Dry Pipe Systems

2010-07-09 Thread Ken Holsopple (forum)
To: sprinklerforum@firesprinkler.org Subject: Re: Residential Sprinklers for Dry Pipe Systems There is no dry-type residential sprinkler that I could find on the Tyco web site. Never heard of one either. Unless this is something new, he may be blowing smoke up your whoops-a-daisy. My guess is that you

RE: Residential Sprinklers for Dry Pipe Systems

2010-07-09 Thread Mike Hairfield
It also states why use Commercial Dry Sprinklers in Residential Systems so in the past using non-residential sprinklers in R use Groups was OK? Mike Date: Fri, 9 Jul 2010 06:33:54 -0700 From: tm...@mfpdesign.com To: sprinklerforum@firesprinkler.org Subject: Re: Residential Sprinklers

RE: Residential Sprinklers for Dry Pipe Systems

2010-07-09 Thread Fletcher, Ron
...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Mike Hairfield Sent: Friday, July 09, 2010 6:33 AM To: AFSA SprinklerFORUM Subject: RE: Residential Sprinklers for Dry Pipe Systems Has to be dry pipe system only and TYCO has a new Dry pendent Residential Sprinklers TY2235

RE: Residential Sprinklers for Dry Pipe Systems

2010-07-09 Thread Todd Williams
/ And look under Latest News. Best Regards, Ken Holsopple -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Todd Williams Sent: Friday, July 09, 2010 9:29 AM To: sprinklerforum@firesprinkler.org Subject: Re: Residential

Re: Residential Sprinklers for Dry Pipe Systems

2010-07-09 Thread Dave Phelan
I see a few heads listed for dry service in residential systems .. Interesting but is there a specific DPV that must be used with a residential system? A listed head is great but the end result is still water delivery in 15 seconds and that seems pretty tough to achieve without carefully

Re: Residential Sprinklers for Dry Pipe Systems

2010-07-09 Thread Dave Phelan
When you look at the press release they mention at the very bottom to follow special bulletins TFP 460 and TFP 461 for listing and design information etc .. Those particular bulletins don't seem to be available off the TFP website but I'm also not an authorized dealer / installer. Can

RE: Residential Sprinklers for Dry Pipe Systems

2010-07-09 Thread George Church
...@firesprinkler.org] On Behalf Of Dave Phelan Sent: Friday, July 09, 2010 11:46 AM To: sprinklerforum@firesprinkler.org Subject: Re: Residential Sprinklers for Dry Pipe Systems I see a few heads listed for dry service in residential systems .. Interesting but is there a specific DPV that must be used

RE: Residential Sprinklers for Dry Pipe Systems

2010-07-09 Thread Steve Leyton
@firesprinkler.org Subject: Re: Residential Sprinklers for Dry Pipe Systems There is no dry-type residential sprinkler that I could find on the Tyco web site. Never heard of one either. Unless this is something new, he may be blowing smoke up your whoops-a-daisy. My guess is that you are going to have

Re: Residential Sprinklers for Dry Pipe Systems

2010-07-09 Thread Ron Greenman
...@firesprinkler.org] On Behalf Of Todd Williams Sent: Friday, July 09, 2010 6:40 AM To: sprinklerforum@firesprinkler.org Subject: RE: Residential Sprinklers for Dry Pipe Systems Always the last to know. However, I could not access either of the TFP documents referenced in the product description. Does

RE: Residential sprinklers

2010-04-03 Thread George Church
offer us much more than high wall wetting. glc -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of tom poisal Sent: Saturday, April 03, 2010 12:06 AM To: sprinklerforum@firesprinkler.org Subject: Re: Residential

RE: Residential sprinklers

2010-04-03 Thread lamarvaughn
To: sprinklerforum@firesprinkler.org Subject: Re: Residential sprinklers tony, first off why a 3000 sq ft remote area ? second - utilizing res spkrs will not let you reduce an area to be calculated wherein 13 requires; largest room, corridor heads etc. Tom Poisal, CET Fire Sprink Ink On 3/31

Re: Residential sprinklers

2010-04-03 Thread tom poisal
. glc -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of tom poisal Sent: Saturday, April 03, 2010 12:06 AM To: sprinklerforum@firesprinkler.org Subject: Re: Residential sprinklers tony, first off why

RE: Residential sprinklers

2010-04-03 Thread A.P.Silva
rooms to get the full 3000 sf. Any comments? Tony -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of tom poisal Sent: April 2, 2010 9:06 PM To: sprinklerforum@firesprinkler.org Subject: Re: Residential

Re: Residential sprinklers

2010-04-03 Thread Ron Greenman
10:33 AM To: sprinklerforum@firesprinkler.org Subject: RE: Residential sprinklers Tony: 11.2.3.1.4 Restrictions. Regardless of which of the two methods (density/area or room design method) is used, the following restrictions shall apply: (3)*Unless the requirements of 11.2.3.1.4(4) are met

Re: Residential sprinklers

2010-04-03 Thread Parsley Consulting
Tony, That's going to change in the 2010. Read this: 11.3.1.2* Unless the requirements of 11.2.3.1.4(4) are met for buildings having unsprinklered combustible concealed spaces, as described in 8.15.1.2 and 8.15.6, the minimum design area of sprinkler operation for that portion of the

Re: Residential sprinklers

2010-04-02 Thread tom poisal
tony, first off why a 3000 sq ft remote area ? second - utilizing res spkrs will not let you reduce an area to be calculated wherein 13 requires; largest room, corridor heads etc. Tom Poisal, CET Fire Sprink Ink On 3/31/10, Ed Kramer k...@frii.com wrote: Tony, for what it's worth, the

RE: Residential sprinklers

2010-03-31 Thread Ed Kramer
Tony, for what it's worth, the commentary to section 8.4.5.1 says Where corridors serve dwelling unit areas and other adjoining spaces, residential sprinklers would not be permitted within the corridor. The FAQ located in the margin next to that commentary asks Is it the intent of 8.4.5 to allow

RE: RESIDENTIAL SPRINKLERS IN NFPA #13

2009-10-26 Thread Reed Roisum
You are allowed to go to NFPA 13R for I-1 occupancies. IBC 2006 903.2.5 Group I. An automatic sprinkler system shall be provided throughout buildings with a Group I fire area. Exception: An automatic sprinkler system installed in accordance with Section 903.3.1.2 or 903.3.1.3 shall be allowed

RE: RESIDENTIAL SPRINKLERS IN NFPA #13

2009-10-23 Thread Dewayne Martinez
You can use them but must follow NFPA 13 rules for residential sprinklers. -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Ralphy Henderson Sent: Friday, October 23, 2009 1:26 PM To:

RE: Residential sprinklers

2009-02-26 Thread Jim Johnston
Scott, My company has done a lot of high end homes, I asked our residential superintendent to get me some pictures. I will gladly forward them to you. Jim Johnston, P.E. Fire Protection Engineer Inland Fire Protection, Inc 1100 Ahtanum Road Yakima, WA 98903 Phone 509-248-4471 Fax 509-248-1180

Re: Residential sprinklers in sloped ceiling over 8/12 pitch

2008-06-12 Thread Todd Williams - FPDC
This is a tough one. For 13D systems, I usually propose to calc 3 sprinklers instead of two and the AHJs have so far gone along. I can only think of one 13R system where that applied. The AHJ on that one went along with using the head requirements for the maximum pitch (I think the pitch was

Re: Residential sprinklers in sloped ceiling over 8/12 pitch

2008-06-12 Thread Ron Greenman
I can think of a few things. Since we're doing a 0.05 density we could go up to 0.06 or 0.07 at the maximum spacing (15x14 actual equals 16x16) kind of like FM degrades the co-efficient for hydrant outlets relative to NFPA. We could go up one area so if we'd normally be using the psi/gpm numbers

RE: Residential sprinklers in sloped ceiling over 8/12 pitch

2008-06-12 Thread herb
Dave In every instance we have to do a 3 head calc when there are at least 3 heads in the room where the steep pitched roof is (over 8:12). We've also had to use the UL listed flow required for the head up to 8:12 pitched ceilings which is 18gpm per head. These homes are also usually large homes

RE: Residential sprinklers in sloped ceiling over 8/12 pitch

2008-06-12 Thread Thom McMahon
Three AHJ's all different all 13D. #1 Requires 2 head calc for all homes under 5000 Sf @ 0.05 Requires 3 head calc over 5000 Sf @ 0.05 Requires 4 head calc for over 8/12 any size, also 0.10, also only recessed heads (He will accept recessed heads that are not listed for up to 8/12, but will not

Re: Residential sprinklers in sloped ceiling over 8/12 pitch

2008-06-12 Thread Ron Greenman
I like AHJ number three since he's not guess engineering. The more is better/save the building with a guess tweaked life safety system design is the second biggest deterrent (after the water guys and their 4 minimum residential lead-ins and the $14K one inch tap fees--my personal favorite although

RE: Residential Sprinklers and Beam Obstructions

2008-05-07 Thread Mike Brown (TECH- GVL)
, 2008 5:08 PM To: sprinklerforum@firesprinkler.org Subject: RE: Residential Sprinklers and Beam Obstructions I love these discussions cause I get to hear about the problems that the contractors have in designing these systems. Guess what...we (the AHJ) have the same problems trying to approve

RE: Residential Sprinklers and Beam Obstructions

2008-05-07 Thread Steve Leyton
To: sprinklerforum@firesprinkler.org Subject: RE: Residential Sprinklers and Beam Obstructions My point is that the NFPA 13D Committee should provide guidelines to follow in these situations. I do not care if they say calculate the room to light hazard as long as they put it in writing. But the way it is now

RE: Residential Sprinklers and Beam Obstructions

2008-05-07 Thread Eckard, Mark - Mark E
Re: obstruction to sprinkler spray pattern development in 13-D. First lets take a look at the purpose of NFPA-13D. Chapter 1.2 prevent flash over and to allow the occupants to escape during the 10 minute water supply. If too many sprinklers are operating in an area that has been

Re: Residential Sprinklers and Beam Obstructions

2008-05-07 Thread Thom McMahon
. 2560 Copper Ridge Dr Steamboat Springs, CO 80488-2136 Tel: 970-879-7952 Fax: 970-879-7926 - Original Message - From: Steve Leyton [EMAIL PROTECTED] To: sprinklerforum@firesprinkler.org Sent: Wednesday, May 07, 2008 7:42 AM Subject: RE: Residential Sprinklers and Beam Obstructions What

Re: Residential Sprinklers and Beam Obstructions

2008-05-07 Thread Ron Greenman
: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Mike Brown (TECH- GVL) Sent: Wednesday, May 07, 2008 6:10 AM To: sprinklerforum@firesprinkler.org Subject: RE: Residential Sprinklers and Beam Obstructions My point is that the NFPA 13D Committee should provide guidelines

Re: Residential Sprinklers and Beam Obstructions

2008-05-07 Thread bigtnp
Message- From: Eckard, Mark - Mark E [EMAIL PROTECTED] To: sprinklerforum@firesprinkler.org Sent: Wed, 7 May 2008 10:30 am Subject: RE: Residential Sprinklers and Beam Obstructions Re: obstruction to sprinkler spray pattern development in 13-D. First lets take a look at the purpose of NFPA

RE: Residential Sprinklers and Beam Obstructions

2008-05-07 Thread Steve Leyton
-Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Mike Brown (TECH- GVL) Sent: Wednesday, May 07, 2008 6:10 AM To: sprinklerforum@firesprinkler.org Subject: RE: Residential Sprinklers and Beam Obstructions My point is that the NFPA 13D Committee

RE: Residential Sprinklers and Beam Obstructions

2008-05-07 Thread Eckard, Mark - Mark E
, May 07, 2008 11:20 AM To: sprinklerforum@firesprinkler.org Subject: Re: Residential Sprinklers and Beam Obstructions Hi Mark, Your questions about the intent an function, even with some blocked spray pattern were concerns during the sloped and beamed ceiling testing that was done.? The Tyco

Re: Residential Sprinklers and Beam Obstructions

2008-05-07 Thread Thom McMahon
[EMAIL PROTECTED] To: sprinklerforum@firesprinkler.org Sent: Wednesday, May 07, 2008 9:35 AM Subject: RE: Residential Sprinklers and Beam Obstructions Except that we absolutely positively don't want to defer to 13. I get ___ Sprinklerforum mailing

Re: Residential Sprinklers and Beam Obstructions

2008-05-07 Thread Ron Greenman
Bob, Just to throw one of those ever present Pacific Northwest dark clouds into the mix I was talking to a guy from Tyco at a seminar a couple of months ago and asked if they had any conclusions regarding that report. He said that they hadn't been able to reproduce the result since that first

Re: Residential Sprinklers and Beam Obstructions

2008-05-06 Thread Todd Williams - FPDC
Bob, I've got a similar situation in a building with residential sprinklers designed to NFPA 13, only with soffits. Four sprinklers in a 60 sqft bathroom seems excessive. So far I haven't come up with anything to let me eliminate sprinklers. IAt 12:51 PM 5/6/2008, you wrote: I'm working

RE: Residential Sprinklers and Beam Obstructions

2008-05-06 Thread Joe Burtell
Look at Tyco's residential design guide for beams and pockets for their residential sprinklers. Best regards, Joe Burtell, SET, CFPS Burtell Fire Protection, Inc. Phone: 406.652.7697 Fax: 406.652.7743 Cell: 406.861.4507 Email: [EMAIL PROTECTED] Web Site: http://www.burtellfire.com

Re: Residential Sprinklers and Beam Obstructions

2008-05-06 Thread [EMAIL PROTECTED]
Bob, Is there a specific reason you can't use the type of residential sprinklers which are allowed to be installed either drilled through the beams, or installed adjacent to the bottom of the beams? From what you've described it seems as though the maximum depth of the pockets isn't more

RE: Residential Sprinklers and Beam Obstructions

2008-05-06 Thread Jamie Seidl
Some res heads will let you go 8 below the ceiling. With a 6 beam, stick one in the beam and let it go. -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Bob Knight Sent: Tuesday, May 06, 2008 12:52 PM To: sprinklerforum@firesprinkler.org Subject:

RE: Residential Sprinklers and Beam Obstructions

2008-05-06 Thread John O'Connor
Bob, Refer to Tyco data sheet TFP400 (for the LFII), page 4 of 8 where they discuss Beam Ceiling Design Criteria. You should be able to locate the heads in the bottom of the beams and avoid the pockets for obvious reasons. John -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL

Re: Residential Sprinklers and Beam Obstructions

2008-05-06 Thread Thom McMahon
Bob: We run into this all the time. First question are the beams structural? If the beams are decorative only drill the beams use your concealed heads and space as normal. While the beam rules for TYCO are ok, they have a lot of situations where you would have to tell the Arch. how to layout

Re: Residential Sprinklers and Beam Obstructions

2008-05-06 Thread Owen Evans
Hi Bob, I know you're using concealed but would your customer accept a sidewall in the beamed rooms? Owen Bob Knight [EMAIL PROTECTED] 05/06/08 9:50 AM I'm working on a home (13D) that has several rooms with the ceiling broken up by beam pockets. These vary in width from 2'8 to 3'3 o.c. with

RE: Residential Sprinklers and Beam Obstructions

2008-05-06 Thread Mike Brown (TECH- GVL)
: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Thom McMahon Sent: Tuesday, May 06, 2008 2:03 PM To: sprinklerforum@firesprinkler.org Subject: Re: Residential Sprinklers and Beam Obstructions Bob: We run into this all the time. First question are the beams structural? If the beams

Re: Residential Sprinklers and Beam Obstructions

2008-05-06 Thread Thom McMahon
-2136 Tel: 970-879-7952 Fax: 970-879-7926 - Original Message - From: Mike Brown (TECH- GVL) [EMAIL PROTECTED] To: sprinklerforum@firesprinkler.org Sent: Tuesday, May 06, 2008 12:58 PM Subject: RE: Residential Sprinklers and Beam Obstructions The NFPA 13D Committee in their wisdom

Re: Residential Sprinklers and Beam Obstructions

2008-05-06 Thread rahe . loftin
Please ignore. Sent to wrong party. Rahe Loftin - Original Message - From: rahe.loftin Sent: 05/06/2008 03:16 PM EST To: sprinklerforum sprinklerforum@firesprinkler.org Subject: Re: Residential Sprinklers and Beam Obstructions Please call them and tell them I am on the way

RE: Residential Sprinklers and Beam Obstructions

2008-05-06 Thread Matsuda, Richard
I love these discussions cause I get to hear about the problems that the contractors have in designing these systems. Guess what...we (the AHJ) have the same problems trying to approve them. I remembered a similar discussion saying something about not allowing them to build something that you

Re: Residential Sprinklers and Beam Obstructions

2008-05-06 Thread IPA
Sometimes, no matter how ridiculous it seems, it's better to just to install them in every pocket then at least you're covered liability wise. Also, when you get into these high dollar luxury homes with beams, slopes, fireplaces in every room etc.. aesthetics plays a very important role and the

RE: Residential Sprinklers in a 13 System

2008-02-15 Thread Travis Mack, SET
Use 0.10 density over the room, or the head listing, whichever is greater. If you head is protecting 20'x12' then the area is 240 sq ft. At 0.1 gpm, the requirement is 24 gpm. A 4.9k head at 20x20 is 20 gpm, so you use the 24 gpm. If the head was protecting 20'x6', then you would use the

Re: residential sprinklers / NFPA 13

2008-02-11 Thread Roland Huggins
I would call the 07 ed material CLARIFICATION on what was the original intent. Keep in mind that this applies only to the 0.1 density side of the residential criteria. It is interesting that for discharge criteria we treat the residential sprinkler as a hybrid having to meet both the