Well, classifying the stored item only gives me the Class 1 ,2, etc. but I
do not see anywhere that the class is associated with a particular sprk.
s.f. like Class 1, with double row racks less than twenty feet high,
non-encapsulated, no in-rack sprk. I don't have a specific project but
rather an ahj wanting to see it in the standard. All I can find that states
anything pertaining to sprk. s.f. is not in the section pertaining to
storage. Only for light, ordinary, extra hazard and other than standard
sprk. such as large drop or ESFR.
 

Russell Rewis
Brown Automatic Sprinklers, Inc.
107C Hemlock Street
Valdosta, Georgia 31601
229-244-8130
[EMAIL PROTECTED]

"You need to provide a bit more info.  When dealing with storage occupancies
you need to clarify what is being stored, how it's being stored (racks,
shelves, bins, on floor, pallets), in what type of container (box, crate,
tote, jars, etc.), encapsulated, heights of said commodities, etc.

Once you've established the what, where, and how then you can go deeper into
13 and find how the area is classified.  For some commodities it could be
spacing of 130 sq. ft, for others it could be limited to 100 sq. ft.

Storage takes some analysis to determine what the appropriate approach will
be."





_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to