The reasonable and obvious action is to follow the same maximum area as driven by the density BUT the amusing part is that there was no actual guidance. This is a legacy from the old days when high piled had intended meaning. This was fixed at the recent ROP meeting.

Roland

On Aug 6, 2008, at 8:39 AM, Ray Vance wrote:

Unless I am sadly mistaken... And I regularly am ;-)

The function of maximum sprinkler spacing is either:

(1)a function of the required design density, as addressed by NFPA-13 and all the previously referenced tables... (2) or a function of the listing of the sprinkler you wish to utilize, (ie extended coverage, ESFR, etc)

It also appears to me that it doesn't matter whether it is high- piled storage or miscellaneous storage, by definition. The requirements are still predicated on the required design density (ie <0.25 gpm or >/= 0.25 gpm) OR the sprinkler's listing.

The only other caveat that comes into play are any other specific requirements or allowances for spacing in high-piled storage arrangements, such as in-rack sprinklers, etc.

Ray Vance