Unless I am sadly mistaken... And I regularly am ;-) The function of maximum sprinkler spacing is either:
(1)a function of the required design density, as addressed by NFPA-13 and all the previously referenced tables... (2) or a function of the listing of the sprinkler you wish to utilize, (ie extended coverage, ESFR, etc) It also appears to me that it doesn't matter whether it is high-piled storage or miscellaneous storage, by definition. The requirements are still predicated on the required design density (ie <0.25 gpm or >/= 0.25 gpm) OR the sprinkler's listing. The only other caveat that comes into play are any other specific requirements or allowances for spacing in high-piled storage arrangements, such as in-rack sprinklers, etc. Ray Vance Chief Engineering Tech. Wayne Automatic Fire Sprinklers, Inc. www.waynefire.com -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Roland Huggins Sent: Wednesday, August 06, 2008 10:59 AM To: sprinklerforum@firesprinkler.org Subject: Re: New topic Round 2 Also add Table 8.8.2.1.2 for Extended Coverage for Storage Here's a related wrinkle. Well actual the text says High PIled storage which is defined as storage greater than 12 ft high. What about Group A plastic greater than 5 ft (which falls in full storage vs Class I-IV going to Chap 13 - Misc and the Occupancy Hazard Approach) Roland On Aug 6, 2008, at 4:03 AM, Jay Stough wrote: > Try table 8.6.2.2.1(d). > > Joseph C. Stough SET, CFPS _______________________________________________ Sprinklerforum mailing list Sprinklerforum@firesprinkler.org http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) ----------------------------------------------------------------------- Wayne Automatic Fire Sprinklers, Inc. 2006 Inductee into 'The Players Hall of Fame' at The Great Games of Business http://www.greatgame.com Wayne Automatic Fire Spinklers, Inc. 'Best Places to Work' http://tinyurl.com/ov335 by Orlando Business Journal _______________________________________________ Sprinklerforum mailing list Sprinklerforum@firesprinkler.org http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)