I agree and that's the approach I've always taken. Hydraulic calculations
are one of the many deciding factors for me. I've learned closer spacing
allows smaller pipe sizes, to a point of course. The rub for him is that 13
has segregated storage from the rest. He didn't question it when 231 and
231C was around (why not?). For him it's just a matter of documentation.
He's a realistic thinker so he's not being hard nosed and will accept what
has been discussed here.

Thanks to Joe B., Joseph S. Ron F. and you Craig for all your input. A big
help.



Russell Rewis
Brown Automatic Sprinklers, Inc.
107C Hemlock Street
Valdosta, Georgia 31601
229-244-8130
[EMAIL PROTECTED]

"And that's where it's going to be because if it's just ceiling sprinkler
coverage, OH is OH and EH is EH regardless of the occupancy.  So there's no
reason to repeat the info specifically in the storage section of 13 when the
limitations of the specific sprinkler type and spacing is listed elsewhere
in the document.  There aren't any specific spacing rules for storage versus
non-storage areas for standard sprinklers.  Sprinkler spacing are based on
their listings.

The only specific spacing data in 13 is related to in-rack sprinklers.
The AHJ just isn't going to see it in that section.

Craig L. Prahl, CET"