I use the excel sheet from Meyer Fire for main drain test, it tells me 698
gpm at 37 psi residual
Thanks
Brett Peters
General Manager Installation & Design
Proudline Fire Protection Services Ltd.
br...@proudline.ca
780 490 7602 office ext 202
780 490 7605 fax
780 777 0568 cell
780 718
____
> SprinklerForum mailing list:
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
> To unsubscribe send an email to
> sprinklerforum-le...@lists.firesprinkler.org
--
Thank You
Brett Peters
PFPS Ltd
(780) 777 0568
Sent From My i
We use a wall/roof thimble for all of our fire pump exhausts, I believe a 2
1/2" pipe requires a 14" hole for the thimble.
https://smssilencers.com/products/
Thanks
Brett Peters
General Manager Installation & Design
Proudline Fire Protection Services Ltd.
br...@proudline.c
0C is actually 32F and NFPA states that temperature must be
maintained above 5C or 40F for wet systems.
So if the temperature is only maintained at 2C or 36F then dry barrel
sprinklers would be required.
Thanks
Brett Peters
General Manager Installation & Design
Proudline Fire Protec
equipment.
Providing a separate control valve allows the piping to be shutdown quickly
without impairing ceiling-level protection for the entire area of the
building.*
I will be away from the office on Friday August 16th and will have limited
access to phone and email.
Thanks
Brett Peters
you think the client’s
> assertion has merit? Why or why not?
>
>
>
> Thanks.
>
>
>
> *Kyle Montgomery*
>
> *Aero Automatic Sprinkler Co.*
>
> kmontgom...@aerofire.com
>
>
>
> _____
> SprinklerForum mailing list:
> http
July 15, 16, 18, & 19, I will be available
only on Wednesday the 17th
Brett Peters
General Manager Installation & Design
Proudline Fire Protection Services Ltd.
br...@proudline.ca
780 490 7602 office ext 202
780 490 7605 fax
780 777 0568 cell
780 718 2676 24h
Visit us at www.proudline.ca
P
the 17th
Brett Peters
General Manager Installation & Design
Proudline Fire Protection Services Ltd.
br...@proudline.ca
780 490 7602 office ext 202
780 490 7605 fax
780 777 0568 cell
780 718 2676 24h
Visit us at www.proudline.ca
Proudline now offers ULc listed monitoring services, ple
erforum.lists.firesprinkler.org
> To unsubscribe send an email to
> sprinklerforum-le...@lists.firesprinkler.org
--
Thank You
Brett Peters
PFPS Ltd
(780) 777 0568
Sent From My iPhone
_
SprinklerForum mailing list:
https://lists.firespri
If the racking sprinklers are designed independent of the ceiling system
than it doesn't matter but if the racking sprinklers are designed as
supplemental coverage to the ceiling sprinklers than the ESFR rules would
apply, IMO
Thanks
Brett Peters
General Manager Installation &am
The last part of the sentence "unless required as part of a fire
separation" NFPA 30 requires it as part of the fire separation for the
horizontal barrier. "NFPA #30 2024 Section 16.6.2 Horizontal barriers of
plywood"
Thanks
Brett Peters
General Manager Installation &am
_
> SprinklerForum mailing list:
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
> To unsubscribe send an email to
> sprinklerforum-le...@lists.firesprinkl
t;+Oklahoma+City,+OK+73114?entry=gmail&source=g>
>
> 405-752-2330 Ext. 10230 Fax:405-752-2297
>
> License No: AR-FSS-162, LA-F415, OK-863 & 302, TX - ECR-1751432,
> ACR-1751168, SCR-G-0292
>
>
>
> [image: Firetrol Oklahoma City BACK]
>
>
>
>
>
>
Just because the max spacing is 16-6 doesn't mean it has to be that far
apart, with multiple row racking you may have to have them spaced at 8'-4
apart so that you don't go over the sqft requirement.
124/8.333=14'-10
Thanks
Brett Peters
General Manager Installation &am
Pressfit actually utilized Sch 5 galvanized pipe, there has been Sch 7
listed sprinkler pipe available for roughly 30 years, it was available when
I started in the industry.
Thanks
Brett Peters
General Manager Installation & Design
Proudline Fire Protection Services Ltd.
br...@proudlin
Saturday December 23 to
Tuesday January 2.
Thanks
Brett Peters
General Manager Installation & Design
Proudline Fire Protection Services Ltd.
br...@proudline.ca
780 490 7602 office ext 202
780 490 7605 fax
780 777 0568 cell
780 718 2676 24h
Visit us at www.proudline.ca
Proudline now offers ULc li
Also in section 9.2.3.7 Sprigs. Sprigs 4 ft (1.2 m) or longer shall be
restrained against lateral movement.
At one time it was only required in seismic areas but since 2013 it is
required on any sprigs 4' or longer, as I understand it.
Thanks
Brett Peters
General Manager Installation &am
9.3.6.6 Sprigs 4 ft (1.2 m) or longer shall be restrained against lateral
movement.
Thanks
Brett Peters
General Manager Installation & Design
Proudline Fire Protection Services Ltd.
br...@proudline.ca
780 490 7602 office ext 202
780 490 7605 fax
780 777 0568 cell
780 718 2676 24h
Visit u
I don't believe it states whether the spacing is along branches or between
Max spacing is 12'-0 but max coverage is still only 100sqft
Thanks
Brett Peters
General Manager Installation & Design
Proudline Fire Protection Services Ltd.
br...@proudline.ca
780 490 7602 office ext 20
independent sources.
Thanks
Brett Peters
General Manager Installation & Design
Proudline Fire Protection Services Ltd.
br...@proudline.ca
780 490 7602 office ext 202
780 490 7605 fax
780 777 0568 cell
780 718 2676 24h
Visit us at www.proudline.ca
Proudline now offers ULc listed monitoring serv
ition of a mezzanine.
So NOT an obstruction, it's a FLOOR ASSEMBLY, so you would protect the
floor below the mezzanine according to whatever hazard is present below it.
Thanks
Brett Peters
General Manager Installation & Design
Proudline Fire Protection Services Ltd.
br...@proudline.ca
780 490
I think that would depend on the municipality, most do not want the
sprinkler water going directly into the storm drains, drained to exterior
or into a waste drain
Thanks
Brett Peters
General Manager Installation & Design
Proudline Fire Protection Services Ltd.
br...@proudline.ca
780 490
by
> unintended recipients is strictly prohibited. If you have received this
> message in error, please notify us immediately by replying to the message
> and deleting it from your computer.
>
>
> --
>
>
> NOTICE - This communication may cont
nformation that is for the sole use of the intended recipient. Any
> viewing, copying or distribution of, or reliance on this message by
> unintended recipients is strictly prohibited. If you have received this
> message in error, please notify us immediately by replying to the message
> and deleting it from you
Taylor
That is exactly how I see it as well
I will be on Holidays from August 12th to 21st, returning to work on
Tuesday August 22nd
Thanks
Brett Peters
General Manager Installation & Design
Proudline Fire Protection Services Ltd.
br...@proudline.ca
780 490 7602 office ext 202
780 490 7605
y issue?
Trying to determine which is actually the "right" way to design the system
as there are cost implications.
I will be on Holidays from August 12th to 21st, returning to work on
Tuesday August 22nd
Thanks
Brett Peters
General Manager Installation & Design
Proudline Fire Pr
largest area but in my opinion the largest floor space doesn't
necessarily present as the most demanding.
I will be on Holidays from August 12th to 21st, returning to work on
Tuesday August 22nd
Thanks
Brett Peters
General Manager Installation & Design
Proudline Fire Protection Servic
hat is really
considered as producing the greatest hydraulic demand? I always choose
whatever gives me the greatest pressure loss not necessarily the larger
flow.
I will be on Holidays from August 12th to 21st, returning to work on
Tuesday August 22nd
Thanks
Brett Peters
General Manager Installation &
level and not interfere with movement. Just a thought.
I will be on Holidays from August 12th to 21st, returning to work on
Tuesday August 22nd
Thanks
Brett Peters
General Manager Installation & Design
Proudline Fire Protection Services Ltd.
br...@proudline.ca
780 490 7602 office ext 202
780
0% of rated flow
I will be on Holidays from August 12th to 21st, returning to work on
Tuesday August 22nd
Thanks
Brett Peters
General Manager Installation & Design
Proudline Fire Protection Services Ltd.
br...@proudline.ca
780 490 7602 office ext 202
780 490 7605 fax
780 777 0568 cell
780
pump shall be
operated at the greater of
100 percent of rated flow or the maximum flow demand of the fire protection
system(s) maximum
allowable discharge to determine its acceptance.
I will be on Holidays from August 12th to 21st, returning to work on
Tuesday August 22nd
Thanks
Brett Peters
If you look at FIGURE A.4.15.6 Right and Wrong Pump Suctions, one of the
diagrams does show something similar to what you are proposing.
I will be on Holidays from August 12th to 21st, returning to work on
Tuesday August 22nd
Thanks
Brett Peters
General Manager Installation & Design
Proud
y
may be required.
Thanks
Brett Peters
General Manager Installation & Design
Proudline Fire Protection Services Ltd.
br...@proudline.ca
780 490 7602 office ext 202
780 490 7605 fax
780 777 0568 cell
780 718 2676 24h
Visit us at www.proudline.ca
Proudline now offers ULc listed monitoring
s are
not capable of providing protection for Lithium fires.
Thanks
Brett Peters
General Manager Installation & Design
Proudline Fire Protection Services Ltd.
br...@proudline.ca
780 490 7602 office ext 202
780 490 7605 fax
780 777 0568 cell
780 718 2676 24h
Visit us at www.proudline.ca
Prou
FMAN*
>
> *DESIGNER*
>
> *NICET WBS 153613*
>
> _
> SprinklerForum mailing list:
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
> To unsubscribe send an email to
> sprinklerforum-le...@lists.fi
lerForum mailing list:
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
> To unsubscribe send an email to
> sprinklerforum-le...@lists.firesprinkler.org
--
Thank You
Brett Peters
PFPS Ltd
(780) 777 0568
Sent From My iPhone
_
nklerForum mailing list:
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
> To unsubscribe send an email to
> sprinklerforum-le...@lists.firesprinkler.org
--
Thank You
Brett Peters
PFPS Ltd
(780) 777 0568
Sent From My iPhone
___
> <http://www.linkedin.com/company/2077231>
>
> <http://www.twitter.com/indoeng_>
>
> <http://www.youtube.com/user/indochineengineering>
>
> phong_indochineengineering
>
>
>
>
>
>
> SprinklerForum mailing list:
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
> To unsubscribe send an email to
> sprinklerforum-le...@lists.firesprinkler.org
--
Thank You
Brett Peters
PFPS Ltd
(780) 777 0568
Sent F
Ok, but this would basically fall under the room design method in 13 then
and not require a phantom flow, unless I'm missing something, I have never
added a phantom flow to a paint booth.
Thanks
Brett Peters
General Manager Installation & Design
Proudline Fire Protection Service
emand shall include the discharge from the hydraulically
most remote adjacent sprinklers in a common 30.5 m (100 linear ft) area of
duct (horizontal and/or vertical).
(4) Sprinklers shall provide a minimum flow of 114 L/min (30 gpm) per
sprinkler at a minimum of 1 bar (15 psi) pressure.
Thanks
NFPA 13 12.3 Adjacent hazards
There is a section in there that shows have a 2'-0 deep draft curtain with
a 4'-0 Aisle below it
Can't remember exactly where it mentions ESFR's but I know I've read it
that this rule can be used to separate ESFR's from other design
though this is becoming less and less of a
concern but there are some companies that just can't have the disruption in
their data flow.
If money is not the concern than I usually try to steer someone towards the
Victaulic Vortex system.
Thanks
Brett Peters
General Manager Installation &
which
does have criteria for 20'-0 of storage but I don't see any information
specifically for pulp fiber.
Have you tried getting a meeting with their insurance company, they may
have some insight on what they want to see for protection.
Thanks
Brett Peters
General Manager Installatio
f the duct
Thanks
Brett Peters
General Manager Installation & Design
Proudline Fire Protection Services Ltd.
br...@proudline.ca
780 490 7602 office ext 202
780 490 7605 fax
780 777 0568 cell
780 718 2676 24h
Visit us at www.proudline.ca
Proudline now offers ULc listed monitoring services, pl
nkler Hydraulic Calculations
>
> Take a deep dive into advanced hydraulic principles for standpipe systems,
> fire pump assemblies, and water storage tanks. Learn more and register for
> the May 3-5 class here
> <https://www.firesprinkler.org/programs/advanced-sprinkler-hydraulic-cal
pecifically mentions free standing
>>> partitions, privacy curtains and "similar obstructions". I don't think
>>> duct-work is a similar obstruction. I would like to have my ducks in a row
>>> if this design approach should be questioned but also want to make su
I think you also need to look at the 18" requirement for the sprinkler
deflector clearance, if there is only 3" between the sprinkler and the duct
than the sprinkler cannot produce a proper spray pattern.
Thanks
Brett Peters
General Manager Installation & Design
Proudline F
Phong
>
> Mobile: +84 (0) 902 363 525
>
> _
> SprinklerForum mailing list:
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
> To unsubscribe send an email to
> sprinklerforum-le...@lists.firesprinkler.org
--
Tha
gt; Phone 604-888-0318
>
> Cel: 604-790-0938
>
> Email jcrawf...@phaserfire.ca
>
> Web: www.phaserfire.ca
>
>
>
> _
> SprinklerForum mailing list:
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
>
possibly but OHII covers 10'-0 of class IV commodity, personally I don't
see how the fire trucks or equipment in the apparatus bay would take you
past that.
Thanks
Brett Peters
General Manager Installation & Design
Proudline Fire Protection Services Ltd.
br...@proudline.ca
780 4
falls within the building code allowances for an unprotected building and
certainly with the tables for a building protected with a sprinkler system.
Thanks
Brett Peters
General Manager Installation & Design
Proudline Fire Protection Services Ltd.
br...@proudline.ca
780 490 7602 office ext
> Phone: 704.896.9989
>
> Fax: 704.896.1935
>
>
>
>
>
> _
> SprinklerForum mailing list:
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
> To unsubscribe send an email to
> sprinklerforum-le...@lists.firespr
If it's one second floor zone than it's a problem, if it's a standpipe
riser with 2 separate zone controls for each section of the 2nd floor then
it's fine
Thanks
Brett Peters
General Manager Installation & Design
Proudline Fire Protection Services Ltd.
br...@proudlin
> SprinklerForum mailing list:
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
> To unsubscribe send an email to
> sprinklerforum-le...@lists.firesprinkler.org
--
Thank You
Brett Peters
PFPS Ltd
(780) 777 0568
Sent From My iPhone
_
If the space above is an unprotected combustible space then it's 8, if the
space is protected (sprinklered or fire rated or full of
insulation) then it's 4
Thanks
Brett Peters
General Manager Installation & Design
Proudline Fire Protection Services Ltd.
br...@proudline.c
and becomes plugged, then it fails in a fire when you needed the
most.
https://www.ecscorrosion.com/resources/
Thanks
Brett Peters
General Manager Installation & Design
Proudline Fire Protection Services Ltd.
br...@proudline.ca
780 490 7602 office ext 202
780 490 7605 fax
780 777 0568 cell
That's a good idea actually, then you can throw back at the mechanical
engineer and say it was designed as per the tender drawings, if they
require a safety margin on the contract that would be in excess of the
tender requirements.
Thanks
Brett Peters
General Manager Installation &am
ender documents.
Mechanical engineers never like being told they are wrong, have to be
creative and give the mechanical engineer an out, so it's not their fault,
better chance of getting that change order.
Thanks
Brett Peters
General Manager Installation & Design
Proudline Fire Protectio
smaller as long as it's capable of providing the
required flow at a positive pressure.
Thanks
Brett Peters
General Manager Installation & Design
Proudline Fire Protection Services Ltd.
br...@proudline.ca
780 490 7602 office ext 202
780 490 7605 fax
780 777 0568 cell
780 718 2676 24h
Vi
The odd one goes into my spam box for some reason
Thanks
Brett Peters
General Manager Installation & Design
Proudline Fire Protection Services Ltd.
br...@proudline.ca
780 490 7602 office ext 202
780 490 7605 fax
780 777 0568 cell
780 718 2676 24h
Visit us at www.proudline.ca
Proudline
If you go with FM and the Tyco 33.6 then max height is 55'-0, idle wood
pallet storage over 35' in a building over 40'-0 (FM) protection criteria
it to protect as per group A plastics
Thanks
Brett Peters
General Manager Installation & Design
Proudline Fire Protecti
Had this discussion in a seminar about ESFR sprinklers, They
specifically direct a large amount of the water straight down for rack
penetration, that is why there is not allowed to be any obstructions
directly below the sprinklers, the cable tray needs to move.
Thanks
Brett Peters
General
;
>
> _
> SprinklerForum mailing list:
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
> To unsubscribe send an email to
> sprinklerforum-le...@lists.firesprinkler.org
--
Thank You
Brett Peters
PFPS L
IMO this is the architect's decision and the booth has to have suppression
in it.
Thanks
Brett Peters
General Manager Installation & Design
Proudline Fire Protection Services Ltd.
br...@proudline.ca
780 490 7602 office ext 202
780 490 7605 fax
780 777 0568 cell
780 718 2676 24h
Vi
o someone else to determine If
and where we are putting a sprinkler system in place.
Thanks
Brett Peters
General Manager Installation & Design
Proudline Fire Protection Services Ltd.
br...@proudline.ca
780 490 7602 office ext 202
780 490 7605 fax
780 777 0568 cell
780 718 2676 24h
Visit us
detail about this that
specifically talks about coolers and freezers having no exclusions from
protection, or the annex - A8.1.1
I believe the fire code refers to NFPA 13 for all sprinkler related codes.
Thanks
Brett Peters
General Manager Installation & Design
Proudline Fire Protection Serv
meter but if you know
of the obstructions beforehand and include them in the initial calculations
then you could pipe them with whatever works in the calculations.
Thanks
Brett Peters
General Manager Installation & Design
Proudline Fire Protection Services Ltd.
br...@proudline.ca
780 490 7602 o
Typically non storage sprinkler supplied with 1"
Storage type sprinkler supplied with same size as branch line (typical for
ESFR sprinklers)
Thanks
Brett Peters
General Manager Installation & Design
Proudline Fire Protection Services Ltd.
br...@proudline.ca
780 490 7602 office ext 20
Baffle or elevation change of at least 2’-0
On Tue, Aug 9, 2022 at 11:51 AM wrote:
> Can I assume that this elevation change would serve the same purpose as a
> draft curtain or would one still be needed?
>
> Bruce
>
>
>
> *From:* Brett Peters
> *Sent:* Tuesday, A
NFPA 13 12.3 - elevation change of at least 2'-0 and above an aisle with a
minimum of 2'-0 of clearance to each side of the center of the aisle.
Thanks
Brett Peters
General Manager Installation & Design
Proudline Fire Protection Services Ltd.
br...@proudline.ca
780 490 7602 offi
8.17.5.1 basically for clean up
Thanks
Brett Peters
General Manager Installation & Design
Proudline Fire Protection Services Ltd.
br...@proudline.ca
780 490 7602 office ext 202
780 490 7605 fax
780 777 0568 cell
780 718 2676 24h
Visit us at www.proudline.ca
Proudline now offers ULc li
8.15.20.5.3 a nipple not exceeding 4" in length of the same size as the
outlet shall be permitted provided that hydraulic calculations can verify
flow rate.
unless you are in a seismic area than nipples smaller than 1" in
diameter are not permitted.
Thanks
Brett Peters
Gener
FMG 8-1 2.4.2
Thanks
Brett Peters
General Manager Installation & Design
Proudline Fire Protection Services Ltd.
br...@proudline.ca
780 490 7602 office ext 202
780 490 7605 fax
780 777 0568 cell
780 718 2676 24h
Visit us at www.proudline.ca
On Tue, May 17, 2022 at 7:20 AM Fpdcdesign w
rea’ selection?
>
>
>
> Thanks!
>
>
>
> Matt
>
>
>
> _
> SprinklerForum mailing list:
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
> To unsubscribe send an email to
> spr
There are dry chemical systems specifically listed and designed for paint
booth applications, we do them all the time, the cost is double the cost
for sprinklers, unless you don't have or can't get the current system to
handle the paint booth demand.
Thanks
Brett Peters
Gener
Also Tyco has some 11.2k dry heads, I have used these on a couple of paint
booths, pricey but brings your pressure requirements down.
Thanks
Brett Peters
General Manager Installation & Design
Proudline Fire Protection Services Ltd.
br...@proudline.ca
780 490 7602 office ext 202
780 490 7605
NFPA 13 has limited information on the requirements for paint booths, need
to look through NFPA 33 to find all the requirements for sprinklers in
paint booths
Thanks
Brett Peters
General Manager Installation & Design
Proudline Fire Protection Services Ltd.
br...@proudline.ca
780 490 7602 of
Viking Supply has 8.0k dry sidewalls
Thanks
Brett Peters
General Manager Installation & Design
Proudline Fire Protection Services Ltd.
br...@proudline.ca
780 490 7602 office ext 202
780 490 7605 fax
780 777 0568 cell
780 718 2676 24h
Visit us at www.proudline.ca
On Mon, May 2, 2022 at
We've used a carriage bolt and fender washers
Thanks
Brett Peters
General Manager Installation & Design
Proudline Fire Protection Services Ltd.
br...@proudline.ca
780 490 7602 office ext 202
780 490 7605 fax
780 777 0568 cell
780 718 2676 24h
Visit us at www.proudline.ca
On Tue, Apr
ther areas
of the table look to be correct.
Thanks
Brett Peters
General Manager Installation & Design
Proudline Fire Protection Services Ltd.
br...@proudline.ca
780 490 7602 office ext 202
780 490 7605 fax
780 777 0568 cell
780 718 2676 24h
Visit us at www.proudline.ca
On Mon, Mar 28,
needs to determine an amount of water required to create the fire
separation. The water curtain requires 3gpm per lineal foot but as a fire
separation this may need to be increased.
Thanks
Brett Peters
General Manager Installation & Design
Proudline Fire Protection Services Ltd.
br...@proudli
sprinkler pipe rarely even sees any water flow!
Thanks
Brett Peters
General Manager Installation & Design
Proudline Fire Protection Services Ltd.
br...@proudline.ca
780 490 7602 office ext 202
780 490 7605 fax
780 777 0568 cell
780 718 2676 24h
Visit us at www.proudline.ca
On Mon, Mar 14