Re: [PSES] SCCR Rating Question

2024-05-16 Thread Ralph McDiarmid
se_industrial_whitepaper_increase_sccr.pdf Best regards, Rich From: Ralph McDiarmid mailto:rmm.priv...@gmail.com> > Sent: Tuesday, May 14, 2024 11:41 AM To: EMC-PSTC@LISTSERV.IEEE.ORG <mailto:EMC-PSTC@LISTSERV.IEEE.ORG> Subject: Re: [PSES] SCCR Rating Ques

Re: [PSES] SCCR Rating Question

2024-05-15 Thread Ralph McDiarmid
Brian: See the very last line of: https://www.mouser.com/pdfDocs/littelfuse_industrial_whitepaper_increase_sccr.pdf Best regards, Rich From: Ralph McDiarmid mailto:rmm.priv...@gmail.com> > Sent: Tuesday, May 14, 2024 11:41 AM To: EMC-PSTC@LISTSERV.IEEE.ORG <mai

Re: [PSES] SCCR Rating Question

2024-05-14 Thread Ralph McDiarmid
Could this number to used to select a suitable circuit breaker and so the interrupting voltage is an important parameter? The nameplate rating on the machine should be the information an electrician needs during installation and selection of wire size and type. Ralph From: Brian

Re: [PSES] IEC 62368-1: To understand chapter 5.4.11

2024-05-08 Thread Ralph McDiarmid
The IEC store has IEC TR 62368-2:2019 RLV for 553 Swiss Francs. Ouch. From: John Woodgate Sent: Wednesday, May 8, 2024 1:37 PM To: EMC-PSTC@LISTSERV.IEEE.ORG Subject: Re: [PSES] IEC 62368-1: To understand chapter 5.4.11 You can get 62368-2 from:

Re: [PSES] Couple of loosely related safety questions

2024-04-27 Thread Ralph McDiarmid
Brian, for a rigorous determination of creepage and of clearance you need to also determine and assign: 1. Over-voltage Category ( affects Clearance ) 2. Pollution Degree ( micro-environment affecting Creepage ) 3. Basic (simple separation) or Reinforced (protective separation)

Re: [PSES] OJEC list of harmonised standards

2024-04-17 Thread Ralph McDiarmid
Hi Ralph, Is this what you are looking for? https://single-market-economy.ec.europa.eu/single-market/european-standards/ harmonised-standards_en Greetings, Bart From: Ralph McDiarmid mailto:rmm.priv...@gmail.com> > Sent: woensdag 17 april 2024 19:04 To: EM

Re: [PSES] OJEC list of harmonised standards

2024-04-17 Thread Ralph McDiarmid
Can someone provide a link to this list. I have searched eur-lex.europa.eu website without success. Ralph - This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. To post a message to

Re: [PSES] Radiated Emissions - How many points to QP?

2024-04-05 Thread Ralph McDiarmid
to use an average detector for radiated emissions between 30 and 1000 MHz? On 4/5/2024 6:39 PM, Ralph McDiarmid wrote: I’m having trouble with “Of those disturbances above (L-20dB), where L is the limit level in logarithmic units, the disturbance levels and the frequencies of at least the six

Re: [PSES] I would like to hear your thoughts please

2024-04-05 Thread Ralph McDiarmid
That has been my experience with CB Scheme, E-mark, and product safety in the USA using an NRTL. Namely, pick worst-case with justifications, talk with your certifier, and reach an understanding. If they won't budge and insist on full testing of every variant, move to another certifier who is

Re: [PSES] Radiated Emissions - How many points to QP?

2024-04-05 Thread Ralph McDiarmid
I'm having trouble with "Of those disturbances above (L-20dB), where L is the limit level in logarithmic units, the disturbance levels and the frequencies of at least the six highest disturbances shall be recorded." Does this CISPR measurement methods standard expect you to record the six

Re: [PSES] GFCI Receptacles

2024-04-05 Thread Ralph McDiarmid
NFPA can be viewed free online, however, CSA C22.1, C22.3, and C22.3 appear to be by purchase only. Ralph From: Don Gies <2f2a08db2fba-dmarc-requ...@listserv.ieee.org> Sent: Friday, April 5, 2024 11:20 AM To: EMC-PSTC@LISTSERV.IEEE.ORG Subject: Re: [PSES] GFCI Receptacles Hi

Re: [PSES] Fire codes related to batteries

2024-04-05 Thread Ralph McDiarmid
And, NFPA provides free, online, read-only access to all their standards. So does UL. Ralph From: Don Gies <2f2a08db2fba-dmarc-requ...@listserv.ieee.org> Sent: Friday, April 5, 2024 11:02 AM To: EMC-PSTC@LISTSERV.IEEE.ORG Subject: Re: [PSES] Fire codes related to batteries Hi

Re: [PSES] UL 62133-2 Battery Standard + V-1 plastic enclosure

2024-03-21 Thread Ralph McDiarmid
Many product safety standards require vertical flame rating for polymeric material forming part or all of the enclosure. I’m surprized it doesn’t require V-0 or 5VA. It’s seems to be about containing a fire inside the enclosure. Ralph From: emcl...@gmail.com Sent: Thursday, March

Re: [PSES] 61010-1 hazardous live classification

2024-02-26 Thread Ralph McDiarmid
Then again, what is the effective value of the 42Vpeak pulsed d.c. ? Does it exceed the Vrms limit at your highest duty ratio? You mentioned a 0.01% minimum on-time, but what is the maximum? From: James Pawson (U3C) Sent: Monday, February 26, 2024 5:38 AM To: EMC-PSTC@LISTSERV.IEEE.ORG

Re: [PSES] 61010-1 hazardous live classification

2024-02-26 Thread Ralph McDiarmid
standards is already a simplification. See IEC 60479-1 and -2. You can find the free preview of IEC 60479-1 here <https://webstore.iec.ch/preview/info_iec60479-1%7Bed1.0%7Den.pdf> , with a good high level discussion in the scope. On Mon, Feb 26, 2024 at 2:26 PM Ralph McDiarmid mailto:rm

Re: [PSES] 61010-1 hazardous live classification

2024-02-26 Thread Ralph McDiarmid
I suspect many of the standards committee have merely adopted the Vpeak limit from other standards without giving it much thought. Note that 42.4Vpk is just root2 x 30Vrms. That seems to be all there is to it and I doubt it's mere coincidence. (60Vdc/30Vrms/42.4Vpk found in several standards)

Re: [PSES] 61010-1 hazardous live classification

2024-02-26 Thread Ralph McDiarmid
An immaculate analysis and air-tight conclusion, as I see it. From: James Pawson (U3C) Sent: Monday, February 26, 2024 5:38 AM To: EMC-PSTC@LISTSERV.IEEE.ORG Subject: [PSES] 61010-1 hazardous live classification Hello all, I hope this safety question is a fairly simple one for

Re: [PSES] IEC 62368-3

2024-01-19 Thread Ralph McDiarmid
In the 3rd edition of IEC 62368-1, it reads, “Additional requirements for equipment having the capability to supply DC power over commonly used communication cables, such as USB or Ethernet (PoE), are given in IEC 62368-3.” Ralph From: peterh...@aol.com

Re: [PSES] Products requiring dielectric voltage withstand test on RJ45 and XLR sockets

2024-01-17 Thread Ralph McDiarmid
If you test that connector with the blunt test probe (aka finger probe) using the procedure described in the standard and it does not touch the connector pins (and you have minimum clearance) then your certifier should reconsider the dielectric test level. Many standards still use basic and

Re: [PSES] Is certification 'voided' by improper operational conditions?

2024-01-08 Thread Ralph McDiarmid
Hi Lauren, MCCB (molded case circuit breakers) get hot when they are run close to their handle rating, even open bench. If installed in a panel (dead air space) at 40C ambient temperature, I would expect they would easily exceed 50C on their molded case long before say 3 hours have expired

Re: [PSES] [EXTERNAL] [PSES] General Product Safety Directive (GPSD)

2023-11-01 Thread Ralph McDiarmid
On Wed, Nov 1, 2023 at 1:20 PM John Woodgate mailto:j...@woodjohn.uk> > wrote: Somewhere in all the Byzantine rules, there is a ban on applying the CE mark if no Directive or Regulation that demands it applies to the product. On 2023-11-01 19:58, Ralph McDiarmid wrote: Furthermore,

Re: [PSES] [EXTERNAL] [PSES] General Product Safety Directive (GPSD)

2023-11-01 Thread Ralph McDiarmid
What is meant by “safety information on the Declaration of Conformity”? A DofC contains a list of applicable EU directives and standards. I’ve never been asked to draft a DofC for signature with “safety information” in it. Furthermore, I have not found anything document which says that you

Re: [PSES] 2 simple questions on EMC

2023-11-01 Thread Ralph McDiarmid
The EMC standard with which I am familiar (CISPR11, EN55022) are well written and provide examples of best practice setup and how to arrange excess cable length. I suggest going over the standard with the test technician at the EMC lab to better understand the requirement. If it were my

Re: [PSES] safety under single fault

2023-10-11 Thread Ralph McDiarmid
" This incident serves to remind us that in our field of product safety, we require the product to be safe even in the event of a failure of any single component. " Maybe better to claim "product safety compliant under any single-fault". It's quite a reach and perhaps not appropriate to claim

Re: [PSES] safety under single fault

2023-10-11 Thread Ralph McDiarmid
if anyone uses their employer or private business devices to use AI tools: the information used for questions immediately and forever becomes public property. -Original Message- From: Ralph McDiarmid Sent: Wednesday, October 11, 2023 2:08 PM To: EMC-PSTC@LISTSERV.IEEE.ORG Subject: Re

Re: [PSES] safety under single fault

2023-10-11 Thread Ralph McDiarmid
Obviously, even an "antiquated design with a single point of failure", gets an air worthiness certificate by the FAA. However, LFP batteries need a fault-tolerant battery management system and tons of testing called out in UL1973 3rd edition. Not all aircraft need single-fault tolerance. I

Re: [PSES] safety under single fault

2023-10-11 Thread Ralph McDiarmid
Here's what ChatGPT 3.5 says about fault-tolerance and general aviation aircraft: Fault-tolerance systems in general aviation aircraft can enhance safety, but their inclusion is not mandatory for all such aircraft. The need for fault-tolerance systems depends on several factors, including the

Re: [PSES] AI & Regulatory Compliance

2023-10-10 Thread Ralph McDiarmid
(519) 729-5704 "All animals except man know that the ultimate joy of life is to enjoy it." -- Samuel Butler On Oct 10, 2023, at 14:15, Ralph McDiarmid mailto:rmm.priv...@gmail.com> > wrote: Physicians have used AI (expert systems) in their offices for many yea

Re: [PSES] AI & Regulatory Compliance

2023-10-10 Thread Ralph McDiarmid
Which is another way of saying that ChatGPT and other similar AI are tools used by professionals to assist with improving their productivity, but not something to be used in lieu of a professional. (at least not in this decade). That time may come, but I suspect engineering jobs are safe for

Re: [PSES] AI & Regulatory Compliance

2023-10-10 Thread Ralph McDiarmid
I would add that about 9 out of 10 power engineers I’ve worked with over the years are equally confused with the “convention” of power factor and sign convention of real and reactive power flow. Microelectronics engineers also often get the sign convention wrong when considering current source

Re: [PSES] AI & Regulatory Compliance

2023-10-10 Thread Ralph McDiarmid
Very interesting demo of its capabilities. I am wondering if the $20 per month version of ChatGPT might be worthwhile. Ralph From: Dan Roman <0d75e04ed751-dmarc-requ...@listserv.ieee.org> Sent: Monday, October 9, 2023 7:21 PM To: EMC-PSTC@LISTSERV.IEEE.ORG Subject: Re: [PSES] AI &

Re: [PSES] AI & Regulatory Compliance

2023-10-10 Thread Ralph McDiarmid
“Even so, I do find them useful as a starting point for writing White Papers and PowerPoint slides or procedural documents at the paragraph-level, for internal distribution. “ I do the same. It’s useful now, even though not perfect, and AI is only going to get better and that will happen

Re: [PSES] AW: [PSES] Directives that require the CE Marking

2023-10-08 Thread Ralph McDiarmid
Best regards Charlie Charlie Blackham Sulis Consultants Ltd Tel: +44 (0)7946 624317 Web: https://sulisconsultants.com/ Registered in England and Wales, number 05466247 From: Ralph McDiarmid mailto:rmm.priv...@gmail.com> > Sent: Friday, October 6, 2023 10:59 PM To: EM

Re: [PSES] AW: [PSES] Directives that require the CE Marking

2023-10-06 Thread Ralph McDiarmid
Here’s what ChatGPT told me about this directive: The General Product Safety Directive (2001/95/EC) in the European Union (EU) is a legal framework designed to ensure the safety of consumer products placed on the EU market. It sets out general requirements for the safety of products,

Re: [PSES] KC certification

2023-10-05 Thread Ralph McDiarmid
Here’s what ChatGPT recommends: In South Korea, to obtain KC (Korea Certification) registration for a Class III radio device, you will need to follow a specific process to ensure your product complies with the country's regulatory requirements. Here are the general steps you should

Re: [PSES] SV: [PSES] Radio receivers under RED? Yes

2023-10-05 Thread Ralph McDiarmid
eceive and determine some information from the received signal then it would be “radio equipment” under RED Best regards Charlie Charlie Blackham Sulis Consultants Ltd Tel: +44 (0)7946 624317 Web: https://sulisconsultants.com/ Registered in England and Wales, number 05466247 From:

Re: [PSES] SV: [PSES] Radio receivers under RED? Yes

2023-10-04 Thread Ralph McDiarmid
Given the reasoning you propose, your spectrum analyser, as an unintentional radiator, should be out of scope of the RED. If it were, then all television and radio receivers would also fall under the RED. From: Amund Westin Sent: Wednesday, October 4, 2023 10:51 AM To:

[PSES] seeing postings

2023-09-27 Thread Ralph McDiarmid
I see that I had to set something up on the list server so that I can see my own postings. - This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. To post a message to the list, send your

Re: [PSES] EMI filtering for 600V AC mains system

2023-09-27 Thread Ralph McDiarmid
Circuit simulation (Pspice or similar) would allow you to find highest working voltage on each capacitor under normal and under single-fault conditions including component tolerances and line voltage variation.  In this country, a nominal 347/600V service has voltage variation limits of 550V to

[PSES] test message only

2023-09-27 Thread Ralph McDiarmid
- This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. To post a message to the list, send your e-mail to All emc-pstc postings are archived and searchable on the web at:

Re: [PSES] Reliability/Fault analysis tools?

2023-09-27 Thread Ralph McDiarmid
Brian, As a good starting point, I recommend reading the following: UL991 : Safety-Related Controls Employing Solid-State Devices CSA C22.2 No. 0.8 : Safety Functions Incorporating Electronic Technology There is functional safety analysis software available, but some may have a hefty price

Re: [PSES] 50Hz Product and the EMC Directive

2023-09-27 Thread Ralph McDiarmid
The phrase, “as to ensure that”, implies some testing would be needed for both emissions and immunity. The directive doesn’t insist on testing, but to meet the “essential requirements” testing would seem the only way to reinforce a claim of compliance. Ralph McDiarmid (Vancouver) From

Re: [PSES] 50Hz Product and the EMC Directive

2023-09-27 Thread Ralph McDiarmid
The phrase, “as to ensure that”, implies some testing would be needed for both emissions and immunity. The directive doesn’t insist on testing, but in order to meet the “essential requirements” testing would seem the only way to reinforce a claim of compliance. From:

[PSES] audio amplifier tests - UL 1711

2023-09-14 Thread Ralph McDiarmid
Anyone know the technical justification for the percent THD limit calculation in clause 35.2 in UL1711 ? Without HTML, the plain text reads: THD (%) = 20 x e^(-0.000189(f-2800)) where f is the bandwidth in Hz. Seems a strange way to specify THD as a function of audio amplifier

Re: [PSES] DFMEA Component Selection

2023-08-30 Thread Ralph McDiarmid
I would only add that those details need to be consider during design, not after the design. Ralph From: Douglas Nix <0bb8ff993b10-dmarc-requ...@listserv.ieee.org> Sent: Wednesday, August 30, 2023 6:31 AM To: EMC-PSTC@LISTSERV.IEEE.ORG Subject: Re: [PSES] DFMEA Component

Re: [PSES] thoughts on ESD test lab problems

2023-08-13 Thread Ralph McDiarmid
I wonder why industry is spending so much on EMC compliance. Is it because the development teams are leaving this work to the final phase of the design, where changes are expensive and schedules slip ? Ralph From: doug emcesd.com Sent: Saturday, August 12, 2023 8:57 PM To:

Re: [PSES] Friday Question - Line Cords in China

2023-08-11 Thread Ralph McDiarmid
Manufacturers cannot side-step liability by claiming ignorance. The manufacture is solely responsible for any product they place on the market, with or without the correct power cord. From: Douglas Powell Sent: Friday, August 11, 2023 7:53 AM To: EMC-PSTC@LISTSERV.IEEE.ORG Subject: Re:

Re: [PSES] Friday Question - Line Cords in China

2023-08-11 Thread Ralph McDiarmid
How would the customs folks in those countries check appliance line cords ? Do they open boxes, pull contents, and inspect? If the USA plug is not rated for higher voltage, does it really present a hazard ? (compliance vs safety) The USA/Canadian plugs have a LOTS of creepage distance

Re: [PSES] Necessary Lab accreditations, class 2 permissible change

2023-08-10 Thread Ralph McDiarmid
Cord-connected equipment? From: Elliott Martinson Sent: Thursday, August 10, 2023 12:27 PM To: EMC-PSTC@LISTSERV.IEEE.ORG Subject: Re: [PSES] Necessary Lab accreditations, class 2 permissible change If it were to become a leakage current issue, I’d wonder whether the parasitic inductance

Re: [PSES] BBC news article re Li-ion batteries...

2023-08-06 Thread Ralph McDiarmid
UL1973 and UL1642 do a pretty through job of addressing functional safety of batteries and safety of the individual cells. Perhaps some LiON batteries are finding their way into the USA market without 3rd party certification. How to prevent uncertified or unlisted products from reaching the

Re: [PSES] Hazard warning labels on panel doors where COTS UPS installed?

2023-08-03 Thread Ralph McDiarmid
Doug, a quick search through NFPA70 (USA national electrical code) says in article 645 Information Technology Equipment: 645.16 Marking. Each unit of an information technology system supplied by a branch circuit shall be provided with a manufacturer's nameplate, which shall also include the

Re: [PSES] GFCI vs GFPE discussion

2018-01-31 Thread Ralph McDiarmid
to, as in shock versus electrocution protection. Is 6mA enough for strong muscle reaction or a startle reaction sufficient to cause someone to loose balance for instance? Still, some protection better than none at all. Ralph McDiarmid Product Compliance Specialist Solar Business Schneider

Re: [PSES] GFCI vs GFPE

2018-01-30 Thread Ralph McDiarmid
Agreed, and current carry-carrying of PE and bonding of internal parts must meet stringent UL/CSA requirements. (not mA!) It seems to me that 30mA is close to lethal, and the GFCI outlets Listed over here are 6mA trip. (still a painful shock) Ralph McDiarmid Product Compliance Specialist

Re: [PSES] Measurement dilemma

2018-01-29 Thread Ralph McDiarmid
put connector with just such a probe, modified to keep probe parasitic inductance to a minimum. At least that’s what I think is going on with Doug’s demonstration. Ralph McDiarmid Solar Business Schneider Electric From: Doug Smith [mailto:d...@emcesd.com] Sent: Friday, January 26, 2018 2:50 PM To:

Re: [PSES] CI Software Flicker/Harmonics

2017-12-31 Thread Ralph McDiarmid
That’s what we do here, when needed. Ralph McDiarmid Product Compliance Engineering Solar Business Schneider Electric From: Pat Lawler [mailto:plawl...@gmail.com] Sent: Thursday, December 21, 2017 6:18 PM To: EMC-PSTC@LISTSERV.IEEE.ORG Subject: Re: [PSES] CI Software Flicker/Harmonics Hi

Re: [PSES] CI Software Flicker/Harmonics

2017-12-20 Thread Ralph McDiarmid
A co-op computer science student on a work term would probably wrestle that to the ground in short order. Ralph McDiarmid Product Compliance Engineering Solar Business Schneider Electric From: John Woodgate [mailto:j...@woodjohn.uk] Sent: Wednesday, December 20, 2017 1:26 PM To: EMC-PSTC

Re: [PSES] CI Software Flicker/Harmonics

2017-12-20 Thread Ralph McDiarmid
oes not need 8G of ram nor does it need Windows 10, we're happy with it thanks and it only control this or that instrument and there is no network connectivity . . . so kindly buzz off" (or words to that effect) ;^)) Ralph McDiarmid Product Compliance Engineering Solar Busines

Re: [PSES] Temp rise measurement

2017-12-20 Thread Ralph McDiarmid
I agree it is a serious omission, but perhaps the technique is so rarely used the question doesn't arise? Thermocouples do a pretty good job IF they are carefully affixed and IF a few are placed, at various locations on the winding. Ralph McDiarmid Product Compliance Engineering Solar Business

Re: [PSES] Temp rise measurement

2017-12-19 Thread Ralph McDiarmid
is limited to 85C rise (in 25C ambient) using thermocouple method. The discrepancy accounts for hotspots inside the coil which may be much warmer than the coil surface measurement. See table 3 in that standard and read all its notes. Ralph McDiarmid Product Compliance Engineering Solar Business

Re: [PSES] Li-Fi

2017-12-11 Thread Ralph McDiarmid
Sure, but fiber optics are special purpose, dedicate circuits. Isn't this fella talking about using existing luminaire in the home for data transmission? Maybe I don't know enough about his concept. Ralph McDiarmid Product Compliance Engineering Solar Business Schneider Electric From

Re: [PSES] Li-Fi

2017-12-11 Thread Ralph McDiarmid
I haven't studied it, but seems to me that one would need to modulate the light very quickly to get any sort of usable BAUD rate, unless you settle for transmission of text only. (like the good old Bell 202 modems over voice band land lines) Ralph McDiarmid Product Compliance Engineering

Re: [PSES] Pilot rating

2017-12-11 Thread Ralph McDiarmid
for capacitive elements) Ralph McDiarmid Product Compliance Engineering Solar Business Schneider Electric From: Peter Tarver [mailto:ptar...@enphaseenergy.com] Sent: Friday, December 08, 2017 5:23 PM To: EMC-PSTC@LISTSERV.IEEE.ORG Subject: Re: [PSES] Pilot rating Hi, Jon. Switching

Re: [PSES] Pilot rating

2017-12-07 Thread Ralph McDiarmid
(dissipate) the energy stored in the coil during turn-off release. Could save your circuit cost of two zeners. Ralph McDiarmid Product Compliance Engineering Solar Business Schneider Electric From: Adam Dixon [mailto:lanterna.viri...@gmail.com] Sent: Thursday, December 07, 2017 2:42 PM To

Re: [PSES] Use of LED Spots in EMC Chambers [General Use]

2017-11-22 Thread Ralph McDiarmid
Series-pass regulator with a simple bridge rectifier is not zero emission, but negligible compared to a well-filtered switch-mode PSU. Ralph McDiarmid Product Compliance Engineering Solar Business Schneider Electric From: John Woodgate [mailto:j...@woodjohn.uk] Sent: Wednesday, November 22

Re: [PSES] Use of LED Spots in EMC Chambers [General Use]

2017-11-22 Thread Ralph McDiarmid
well. Ralph McDiarmid Product Compliance Engineering Solar Business Schneider Electric -Original Message- From: Ken Javor [mailto:ken.ja...@emccompliance.com] Sent: Wednesday, November 22, 2017 8:28 AM To: EMC-PSTC@LISTSERV.IEEE.ORG Subject: Re: [PSES] Use of LED Spots in EMC Chambers

Re: [PSES] Regulatory requirements for MOVs placed line-to-ground on AC mains ports?

2017-11-20 Thread Ralph McDiarmid
My assumption as well Perhaps, but keep in mind that the impedance specified by 60725 is a maximum value that 90% of household service would not exceed. It might be 1/2 that value on average. Ralph McDiarmid Product Compliance Engineering Solar Business Schneider Electric

Re: [PSES] Regulatory requirements for MOVs placed line-to-ground on AC mains ports?

2017-11-20 Thread Ralph McDiarmid
be twice that value or higher for some customers Ralph McDiarmid Product Compliance Engineering Solar Business Schneider Electric -Original Message- From: Brian O'Connell [mailto:oconne...@tamuracorp.com] Sent: Monday, November 20, 2017 10:26 AM To: EMC-PSTC@LISTSERV.IEEE.ORG Subject: Re

Re: [PSES] Regulatory requirements for MOVs placed line-to-ground on AC mains ports?

2017-11-17 Thread Ralph McDiarmid
0.5A without further increase in current. Ralph McDiarmid Product Compliance Engineering Solar Business Schneider Electric -Original Message- From: Joe Randolph [mailto:j...@randolph-telecom.com] Sent: Monday, November 13, 2017 7:56 PM To: EMC-PSTC@LISTSERV.IEEE.ORG Subject: Re: [PSES

Re: [PSES] Regulatory requirements for MOVs placed line-to-ground on AC mains ports?

2017-11-17 Thread Ralph McDiarmid
I've see MOVS flame after being hit repeatedly with 6kV combination wave surges too quickly (30s apart), during type testing to ANSI C62.45 Ralph McDiarmid Product Compliance Engineering Solar Business Schneider Electric -Original Message- From: Joe Randolph [mailto:j...@randolph

Re: [PSES] Clicks per CISPR 14-1

2017-11-14 Thread Ralph McDiarmid
Indeed, why not merely add a Peak limit or perhaps better, an Average limit? Doing that would avoid an effort to clarify the issue with words. Avg & QP limits have served well in CISPR11 and in CISPR22 for a long time. Ralph McDiarmid Product Compliance Engineering Solar Business Schne

Re: [PSES] "persons" in IEC 62368-1

2017-11-09 Thread Ralph McDiarmid
, since the principles of electric circuits can be taught just as effectively using magnitude 1 energy sources. Ralph McDiarmid Product Compliance Engineering Solar Business Schneider Electric -Original Message- From: Richard Nute [mailto:ri...@ieee.org] Sent: Thursday, November 09

Re: [PSES] Regulatory requirements for MOVs placed line-to-ground on AC mains ports?

2017-11-01 Thread Ralph McDiarmid
ccredited institute, not just on-the-job experience. I have fixed a few TVs in my time, but I wouldn't say I was qualified; skilled maybe. Ralph McDiarmid Product Compliance Engineering Solar Business Schneider Electric -Original Message- From: Joe Randolph [mailto:j...@randolp

[PSES] Regulatory requirements for MOVs placed line-to-ground on AC mains ports?

2017-11-01 Thread Ralph McDiarmid
some considerable resistance (no pun intended) Ralph McDiarmid Product Compliance Engineering Solar Business Schneider Electric From: Joe Randolph [mailto:j...@randolph-telecom.com] Sent: Tuesday, October 31, 2017 9:43 PM To: EMC-PSTC@LISTSERV.IEEE.ORG Subject: Re: [PSES] Regulatory requirements

Re: [PSES] EN 301 489-1 and RED

2017-10-30 Thread Ralph McDiarmid
I think Charlie’s final bullet point is key. The customs and surveillance authorities are looking for references to the latest harmonized standards in a DofC. The don’t understand or will not accept the concept of ‘presumption of conformity’; they want to see the EN standards listed. Ralph

Re: [PSES] IEC 61000-3-2 Confusion

2017-10-16 Thread Ralph McDiarmid
I thought it was 15% duty cycle. Ralph McDiarmid Product Compliance Engineering Solar Business Schneider Electric From: James Pawson (U3C) [mailto:ja...@unit3compliance.co.uk] Sent: Monday, October 16, 2017 7:31 AM To: EMC-PSTC@LISTSERV.IEEE.ORG Subject: Re: [PSES] IEC 61000-3-2 Confusion Hi

Re: [PSES] NEMA 5-20P with IEC 60320 C13

2017-10-11 Thread Ralph McDiarmid
plus 125 percent of the continuous load." It's easy for our equipment where it is always supplied by a dedicated "branch circuit" (often a dedicated transformer) and current is continuous by definition. (> 3hrs) Strictly speaking, it's a 125% rule, not an 80% rule Ralph McDia

Re: [PSES] NEMA 5-20P with IEC 60320 C13

2017-10-11 Thread Ralph McDiarmid
Since you're asking for an opinion and since IEC would allow it, I think it's reasonable to allow it in N.Am too. There is no apparent hazard; the 15A OCPD adequately protects both the connector and the cordage. Ralph McDiarmid Product Compliance Engineering Solar Business Schneider Electric

Re: [PSES] IEC 61000-3-2 Confusion

2017-10-11 Thread Ralph McDiarmid
That is an interesting technical point. Notice that EN61000-6-3 (generic residential) calls out 61000-3-2, -3, -11  and -12, but EN61000-6-4 (industrial) does not. Presumably, EN61000-6-4 makes full provision for the apparatus ? Ralph McDiarmid Product Compliance Engineering Solar Business

Re: [PSES] IEC 61000-3-2 Confusion

2017-10-11 Thread Ralph McDiarmid
I wonder if your customer's triac equipment falls under the EN61000-6-4 (EMC) Emission standard for industrial environments? I didn't see 61000-3-2 called out in that generic standard. Ralph McDiarmid Product Compliance Engineering Solar Business Schneider Electric From: James Pawson (U3C

Re: [PSES] NEMA 5-20P with IEC 60320 C13

2017-10-11 Thread Ralph McDiarmid
Sounds like an example of the 125% rule for continuous (>3hr) current. (20/16) Ralph McDiarmid Product Compliance Engineering Solar Business Schneider Electric From: Ted Eckert [mailto:07cf6ebeab9d-dmarc-requ...@ieee.org] Sent: Wednesday, October 11, 2017 5:50 AM To: EMC-P

Re: [PSES] NEMA 5-20P with IEC 60320 C13

2017-10-10 Thread Ralph McDiarmid
, and short circuit PV currents need a 1.25 multiplier. Ralph McDiarmid Product Compliance Engineering Solar Business Schneider Electric From: Ted Eckert [mailto:07cf6ebeab9d-dmarc-requ...@ieee.org] Sent: Tuesday, October 10, 2017 1:58 PM To: EMC-PSTC@LISTSERV.IEEE.ORG Subject: Re: [PSES

Re: [PSES] NEMA 5-20P with IEC 60320 C13

2017-10-10 Thread Ralph McDiarmid
The NEC (NFPA 70) talks about “continuous currents” and when to apply the all-too-familiar 125% rule. Canadian Electric Code (CSA part I) has same requirement. The IEC seems to have avoided it. Ralph McDiarmid Product Compliance Engineering Solar Business Schneider Electric D  604-422-2622

Re: [PSES] Authorized personnel only

2017-10-10 Thread Ralph McDiarmid
Maybe a padlock symbol, if there is no “standardized” symbol offered by ISO Restricted Access locations are commonly locked, and only the privileged few have the key Ralph McDiarmid Product Compliance Engineering Solar Business Schneider Electric From: Doug Powell [mailto:doug...@gmail.com

Re: [PSES] power strip details

2017-09-19 Thread Ralph McDiarmid
I trust all the good background information in C62.41.1 doesn't get lost when pull the standard in 2018. Hopefully it gets transferred (and perhaps revised) to a new IEEE std. I will hazard a guess that MSPD stands for Mains Surge Protection Device. Ralph McDiarmid Product Compliance

Re: [PSES] power strip details

2017-09-18 Thread Ralph McDiarmid
for those. The ANSI standard seems a very good summary of what is a complex topic. Ralph McDiarmid Product Compliance Engineering Solar Business Schneider Electric From: Richard Nute [mailto:ri...@ieee.org] Sent: Saturday, September 16, 2017 12:30 PM To: EMC-PSTC@LISTSERV.IEEE.ORG Subject: Re

Re: [PSES] power strip details

2017-09-18 Thread Ralph McDiarmid
Pardon me, the correct reference is ANSI C62.41.1 (finger trouble on keyboard) Ralph McDiarmid Product Compliance Engineering Solar Business Schneider Electric -Original Message- From: Ralph McDiarmid Sent: Monday, September 18, 2017 8:55 AM To: EMC-PSTC@LISTSERV.IEEE.ORG Subject: RE

Re: [PSES] power strip details

2017-09-15 Thread Ralph McDiarmid
I invite you to also read the Preface in the NEC 2014 Handbook. It provides an interesting history. Ralph McDiarmid Product Compliance Engineering Solar Business Schneider Electric -Original Message- From: Richard Nute [mailto:ri...@ieee.org] Sent: Friday, September 15, 2017 12:42

Re: [PSES] power strip details

2017-09-15 Thread Ralph McDiarmid
peculiar requirements we find in the NEC. Anyway, I've again drifted off topic and into a mini rant. Sorry about that. Ralph McDiarmid Product Compliance Engineering Solar Business Schneider Electric From: Scott Aldous [mailto:scottald...@google.com] Sent: Friday, September 15, 2017 11:00 AM

Re: [PSES] power strip details

2017-09-15 Thread Ralph McDiarmid
this, but the rule goes way back in the code. Anybody know where it came from? You won't find it in any part of IEC 60364-4-43. Apparently, the NEC 'code' was derived originally from the IEC. Ralph McDiarmid Product Compliance Engineering Solar Business Schneider Electric From: Pete Perkins

Re: [PSES] power strip details

2017-09-15 Thread Ralph McDiarmid
a justification. Someone must have written one. If UL Lists a circuit breaker at 15A, then there are no ‘conditions of acceptability’ like those for a Recognized component, and so 15A should be just fine for > 3hours, otherwise the marking is misleading at best. Ralph McDiarmid Product Complia

Re: [PSES] EN 62368-1:2014 DoW

2017-09-12 Thread Ralph McDiarmid
Gee, and I thought SDOs like UL and CSA were the only ones with issues. ;^)) Ralph McDiarmid Product Compliance Engineering Solar Business Schneider Electric From: John Woodgate [mailto:jmw1...@btinternet.com] Sent: Monday, September 11, 2017 2:34 AM To: EMC-PSTC@LISTSERV.IEEE.ORG Subject: Re

Re: [PSES] LISN Calibration Measurement Uncertainty

2017-09-11 Thread Ralph McDiarmid
in the lab and in the field before agreeing on the LISN as a standard transducer for the evaluation of conducted RF emission. If there were something fundamentally wrong with the method of measurement, I suspect it would have been uncovered long ago. Ralph McDiarmid Product Compliance Engineering

Re: [PSES] LISN Calibration Measurement Uncertainty

2017-09-11 Thread Ralph McDiarmid
the DUT. I think save to say that most DUTs will have a least two power poles, a "line" and a "neutral for connection to the a.c. mains. I think some manufactures provide a graph or two plotting something (perhaps insertion loss versus frequency) for that serial number. I hope t

Re: [PSES] LISN Calibration Measurement Uncertainty

2017-09-11 Thread Ralph McDiarmid
I agree that the AMN (LISN) is intended only to provide consistent (more or less) results, not to represent a real-world impedance at RF. I don't know how much that impedance changes from site to site; quite a lot I'll bet. Ralph McDiarmid Product Compliance Engineering Solar Business

Re: [PSES] LISN Calibration Measurement Uncertainty

2017-09-11 Thread Ralph McDiarmid
ce further away from the ideal 50 ohms. Ralph McDiarmid Product Compliance Engineering Solar Business Schneider Electric From: Ken Javor [mailto:ken.ja...@emccompliance.com] Sent: Monday, September 11, 2017 10:21 AM To: EMC-PSTC@LISTSERV.IEEE.ORG Subject: Re: [PSES] LISN Calibration Measurem

Re: [PSES] Surge Suppression - Dos, and Don'ts

2017-08-22 Thread Ralph McDiarmid
Hi Brian, An open-circuit of 15kV pk and short-circuit peak of 7500A, tells me an internal impedance of 2 ohms. If I recall correctly, 61000-4-5 specifies source impedance, depending on L-L or L-G coupling (2 ohms or 12 ohms) Ralph McDiarmid Product Compliance Engineering Solar Business

Re: [PSES] Inrush Current

2017-08-10 Thread Ralph McDiarmid
Just curious to why delete the highest and lowest values before taking the average? Ralph McDiarmid Product Compliance Engineering Solar Business Schneider Electric From: John Woodgate [mailto:jmw1...@btinternet.com] Sent: Thursday, August 10, 2017 5:00 AM To: EMC-PSTC@LISTSERV.IEEE.ORG

Re: [PSES] Quasipeak definition

2017-08-01 Thread Ralph McDiarmid
Yes, however, I haven't seen a slide rule in 40 years nor an analog meter in 20 years. Ralph McDiarmid Product Compliance Engineering Solar Business Schneider Electric -Original Message- From: Richard Nute [mailto:ri...@ieee.org] Sent: Tuesday, August 01, 2017 9:59 AM To: Ralph

Re: [PSES] Quasipeak definition

2017-08-01 Thread Ralph McDiarmid
Those topics used to be taught in engineer school. That should not be on-the-job learning. Ralph McDiarmid Product Compliance Engineering Solar Business Schneider Electric From: Brent DeWitt [mailto:bdew...@ix.netcom.com] Sent: Monday, July 31, 2017 8:09 PM To: EMC-PSTC@LISTSERV.IEEE.ORG

Re: [PSES] Quasipeak definition

2017-07-31 Thread Ralph McDiarmid
television receivers suffered similar susceptibility to impulsive noise because the video carrier was amplitude-modulated and had a much wider bandwidth compared to an AM receiver. Ralph McDiarmid Product Compliance Engineering Solar Business Schneider Electric From: John Woodgate [m

  1   2   3   >