Mick,
Are you sure that the neutral is isolated from the frame on that "portable"
generator?
If so, it's a strange generator indeed.
Brian Teitelbaum
AEE Solar
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Mi
es I knew about.
Brian Teitelbaum
AEE Solar
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Mick Abraham
Sent: Thursday, August 19, 2010 5:20 PM
To: al...@positiveenergysolar.com; RE-wrenches
Subject: Re: [RE-wrenches] DR2424 inverters
Kent,
Thanks for that info.
Have you tested for voltage between the L1 and ground while the generator is
running, or just tested for continuity between neutral and ground when not
running?
I wonder how much Honda paid the City of LA for that sticker :)
Brian Teitelbaum
AEE Solar
From: re
Hi Mick,
To answer part of your post, the DPW Power Rail mid-clamps give you a 3/8" gap
between modules, and the SnapNrack mids give you a 1/2" gap.
I doubt if that will give you much of a walkway though....
Brian Teitelbaum
AEE Solar
From: re-wrenches-boun...@lists.re-wr
odule without worry of
electrocution if it were under 50VDC. See page 22 in this EPRI paper
http://www.narucmeetings.org/Presentations/Dorr-NARUC%20SV%20Panel%202009.pdf
Brian Teitelbaum
AEE Solar
-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches
number of hours needed each day to get to full charge.
Brian Teitelbaum
AEE Solar
-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of j...@asis.com
Sent: Thursday, September 09, 2010 5:23 PM
To: RE-wrenches
Subject
Hi Holt,
The S-460-AGM is too new for any meaningful feedback to be generated. I guess
we will know in 5 years or so. This is always a problem with new battery
designs.
It is interesting though that Rolls/Surrette does not list that battery in
their "Renewable Energy Products" line. Next time
Opps! Sorry guys. That was supposed to just go to Holt
Brian Teitelbaum
AEE Solar
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Brian Teitelbaum
Sent: Monday, September 20, 2010 10:59 AM
To: RE-wrenches
Subject: Re: [RE-wrenches
"tech publications", in the right sidebar
Google is our friend.
Brian Teitelbaum
AEE Solar
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Allan Sindelar
Sent: Tuesday, October 05, 2010 9:28 AM
To: RE-wrenches
Subject: [RE-
boB,
There is a chart in that white paper that graphs the losses on each module in
the string. No significant losses seem to occur until you get to 5 in series
I can send the whole paper to you, or anyone, off list if you are interested
Brian Teitelbaum
AEE Solar
bteitelb...@aeesolar.com
From
o a variety of
inverters, including an OutBack PS1, and even an old Beacon M5. I'm sure that
the SolarEdge stuff will provide more output...when we actually get the sun on
the array.
Brian Teitelbaum
AEE Solar
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-bou
rrent from the
main into a partial fault.
Brian Teitelbaum
AEE Solar
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Mark Frye
Sent: Wednesday, March 30, 2011 9:49 AM
To: 'RE-wrenches'
Subject: Re: [RE-wrenches] sizing a su
I don't see it there either. You may have to call them
Vaporware??
Brian T
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of jay peltz
Sent: Thursday, April 14, 2011 4:40 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] solar thermal/
Mark,
Are both buildings being fed from the same utility transformer?
I thank that may be a key question here
Brian Teitelbaum
AEE Solar
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Mark Frye
Sent: Monday, April 18, 2011 12:42
other, and this wouldn't be a problem.
I'm I off-base here? What think you, esteemed wrenches?
Brian Teitelbaum
AEE Solar
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Mark Frye
Sent: Monday, April 18, 2011 1:09 PM
T
Does anyone know of a manufacturer or supplier of fused battery buss bars or
battery string combiners (preferably using Class-T fuses) that are UL Listed
for use in residential or commercial applications?
Brian Teitelbaum
AEE Solar
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re
r to replace it.
We never cut it open to take a look, but I suspect that it was a micro-fracture
in one of the internal buss bars, with enough continuity to provide voltage but
not enough for current flow. We didn't measure the SG either, but I doubt that
it was anything other than normal.
uld have made more sense, and would have made it a more truly
solar-powered event.
Brian Teitelbaum
AEE Solar
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of benn kilburn
Sent: Wednesday, April 27, 2011 3:51 PM
To: Wrenches
Subjec
o get into the DC voltage range of the Enphase.
Brian Teitelbaum
AEE Solar
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Peter Talmage
Sent: Thursday, May 05, 2011 10:26 AM
To: RE-wrenches
Subject: [RE-wrenches] Interfacing an
ed
with a "safety factor of 3" (whatever that means, since I doubt that they would
handle 366 mph!).
Brian Teitelbaum
AEE Solar
-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of
penobscotso.
Wrenches,
Has anyone tried to do a grid-tie AC coupled system with a Trace/Xantrex SW4024
inverter and a GT inverter? Is the Trace's stepped waveform an issue for the GT
inverter?
Brian Teitelbaum
AEE Solar
___
List sponsored by Home Power mag
Oh my
This from their "news" tab:
"The time has never been better to make an intelligent investment that keeps
paying you forever."
Need I say anything to mock this?
Brian Teitelbaum
AEE Solar
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenc
, 500A, 1000A, and also
maybe able to be daisy-chained for really large systems, like up to 100kW at
48VDC
Hint..hint…
Brian Teitelbaum
AEE Solar
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of boB Gudgel
Sent: Thursday, June 02
suggestion to load test each battery
Brian Teitelbaum
AEE Solar
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of
m...@hurshtown.com
Sent: Tuesday, October 11, 2011 4:55 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] intermittent battery
Hi Kirk,
The Sunny Boy inverters also have a pair of lugs for a single conductor pair
coming in from the array. They are meant to be used if you have an external
combiner. No bus bars as you describe are needed.
Brian Teitelbaum
AEE Solar
From: re-wrenches-boun...@lists.re-wrenches.org
that
much clipping, unless it's in a cold climate. I doubt that the extra cost of
using two smaller inverters would be justified.
Brian Teitelbaum
AEE Solar
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of jay peltz
Sent: Sunda
at it automatically brought in the
location's temp specs when you add a city to the input field.
I'd like to see both of them available on the website.
Brian Teitelbaum
AEE Solar
-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-w
tribution Panel.
Also shown is the use of an external bypass switch to make up for the lack of
enough AC breaker spaces in a single Distribution Panel. It shows a
breaker/interlock panel, but a 2-pole manual transfer switch will also work.
Either way, it should be rated for at least 200A.
Brian
t should be rated for at least 200A.
Brian Teitelbaum
AEE Solar
___
List sponsored by Home Power magazine
List Address: RE-wrenches@lists.re-wrenches.org
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
Lis
Hi Jeff,
The Sunny Island 4248U has been discontinued by SMA, and replaced with the
SI5048U
If you use a transfer switch between the grid and a generator on the SI input,
make sure that you put in a relay that will prevent the Sunny Boy from
“selling” power to the generator
Brian Teitelbaum
.
Cheers!
Brian Teitelbaum
AEE Solar
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Jeff Yago
Sent: Thursday, May 28, 2009 6:55 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] AC Coupled (Again)
Although we have completed tons of
Well...there goes the neighborhood!
Congrats Ezra!
Good thing that "NA..." stands for North American...
Brian T
AEE Solar
-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Michael Welch
Sent: Tuesday, Ju
robably won't need the generator at
all. Then I can dump my 1942 Servel gas fridge, and go electric.
Brian Teitelbaum
AEE Solar
-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Travis Creswell
Hi Ezra,
I got out my Murphy's Law book, and found the relevant part in Chapter IV,
Section 3, Sub-section 21, Paragraph 12, lines 9-14
Brian Teitelbaum
AEE Solar
-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.or
t connected to that CU200. He
couldn't just run one pump. I never did talk to Grundfos about that.
Cheers!
Brian Teitelbaum
AEE Solar
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Mark Dickson
Sent: Thursday, June 11, 2009
LOL!
OK, now maybe I can take that long awaited vacation
Brian Teitelbaum
AEE Solar
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of William Miller
Sent: Tuesday, June 16, 2009 9:53 AM
To: RE-wrenches
Subject: [RE-wrenches
50" is still made by Xantrex, but only contains a main breaker, and no
boards, and has small-breaker knockouts on the sides. The door is not hinged
Brian Teitelbaum
AEE Solar
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of C
encapsulates, but I
used to keep a tube of 739 in my toolbox to seal damaged back skins, and seal
module's JB's. I do know that acetic acid can damage metallic parts, including
cell metallization and internal JB metal parts.
Brian Teitelbaum
AEE Solar
-Original Message-
Fr
these what they want in a
generator.
Maybe we can get a Kohler engineer to join this site as a manufacturer's rep,
although it's hard to call their product "renewable energy".
Brian Teitelbaum
AEE Solar
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun
Hey Darryl,
You said - " never allow a single wire to pass through a metal surface as this
will induce eddy currents and magnetic effects into the metal causing voltage
drop and heating"
Is that true even for non-ferrous metals, like aluminum, or say, gold?
Brian Teitelbaum
US made.
And, of course, the Satcon 30.
Enphase?
Too many choices!
Brian Teitelbaum
AEE Solar
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Peter Parrish
Sent: Tuesday, August 11, 2009 9:50 AM
To: 'RE-wrenches'
losses, would give a more
accurate reading of the Fridge's true running watts.
There are a number of plug-in products on the market that are supposed to
improve power factor, apparently through added capacitance. How would they work
here, or would they?
Brian Teitelbaum
AEE Solar
-
e the clearance. On top of that, the shunt ends up
only about 2-3" from the negative battery post, and is a hell of a hassle to
connect with 2/0 or 4/0 cable.
Brian Teitelbaum
AEE Solar
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org
inverter), but if you ever have the battery-inverter shut off,
you will likely have damage. It's really just safer to connect the hydro unit
to the DC system directly.
Brian Teitelbaum
AEE Solar
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrench
A "compact optical device" would still have to work with the sun's energy at
1000W/square.meter, and even if they could get 20% conversion efficiency
(highly unlikely), it would still need to cover an area of more than 5
sq.meters per kW output.
Not very "compact'
B
Active-High or
Active-Low configuration, and are SPDT switches rated at 30A at 12/24VDC, 15A
at 36VDC, and 3A at 48VDC. Voltage range is 10V-63V. Fully adjustable on and
off voltage setpoints. They consume 17mA when “off” and between 32 and 75mA
when “on” (depending on the voltage)
Brian
ejkf=PQ4y9C2vFEtL0I9NN25RaXTu7nvvtfQWhY2ly2ShYpg%3d
Or, you can also use a splicer right at the inverter terminals:
http://www.ilsco.com/ProductsDetail.aspx?kfjkff=uE1VYYLG5SoDpPlUKKAJeg%3d%3d&fjjfhjhj=H5Hi3ZmGXgnPYbyoSlyg192pVV62SE3BAZmhQMpx%2bq0%3d
Brian Teitelbaum
AEE Solar
From: re-wrenches-boun...@
Joel,
Contact me off-list
bteitelbaum at aeesolar dot com
Brian Teitelbaum
AEE Solar
-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Joel Davidson
Sent: Sunday, September 27, 2009 6:11 PM
To: RE
guarantee that the OutBacks will sync up.
Brian Teitelbaum
AEE Solar
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Orion Thornton
Sent: Monday, September 28, 2009 11:43 AM
To: 'RE-wrenches'
Subject: [RE-wrenches] Batte
Randy,
The charge voltages are not adjustable, but are set at 14.2V +/-0.2 for "charge
termination" and 12.8V +/-0.2 for "charge resumption".
I have a paper copy of the manual that I can scan for you. Let me know if you
want it.
Brian Teitelbaum
AEE Solar
Fr
nd Engineering makes nice
Windows-based PC software that works with the OutBack equipment to monitor and
display status, with data logging and system control:
http://www.righthandeng.com/hm_wvmob.htm
Brian Teitelbaum
AEE Solar
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenc
William,
The SW Parallel Stacking Interface (SWI/PAR) was much more than just a cable
(like the Series Stacking Cable -SWI). it was a separate box, like the Grid Tie
Interface (GTI) unit was. It retailed for about $345.00
Good luck finding one.
Brian Teitelbaum
AEE Solar
From: re-wrenches
8, so that was the
first year that they were available.
Those are 20-year-old inverters. Some of them are probably still out there
working.
If any of this is useful to you, contact me off-list and I'll scan it all into
pdf's and send it to you.
Brian Teitelbaum
AEE Solar
-Orig
lly close to
600VDC (595VDC) at 14⁰F. You might want to play it safe and drop one of the
modules. Unfortunately, none of the SMA inverters will operate with only 12
modules in a string (with two strings). However, a Fronius IG-3000 will, so you
might want to go with that, although it has a lowe
with bypass diodes installed, so if
you do use them in a system above 24V, be sure to add the diodes.
Brian Teitelbaum
AEE Solar
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Solar Plexus
Sent: Wednesday, November 18, 2009 9:33
Hi Jamie,
Have you seen any change in cycle life by having the three cells in the L16
connected in parallel instead of series? Just a question that has been on my
mind for a while.
Brian Teitelbaum
AEE Solar
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re
n the L16 connected in parallel instead of series? Just a
> question that has
> been on my mind for a while.
>
> Brian Teitelbaum
>
> AEE Solar
>
>
>
>
>
>
>
> From:
> re-wrenches-boun...@lists.re-wrenches.org<mailto:re-wrenches-boun...@lists.re-wren
that replaced a battery cap and would send a warning signal out if the
electrolyte level got low, at least in that cell. Sure would be nice if someone
picked up that ball and integrated it into their System Control Panel or MATE.
Brian Teitelbaum
AEE Solar
From: re-wrenches-boun...@lists.re
Hey Windy!
Congratulations to a proud Papa.
I'm thrilled, not only because these fine pumps will be back on the market, but
that a fine brand name was revived.
Three Cheers to Innovative Solar!
Brian Teitelbaum
AEE Solar
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wre
batteries can’t be brought up to a full state of
charge within a few days of a major discharge, you need to add more PV, reduce
loads, or run a genny.
Brian Teitelbaum
AEE Solar
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Allan
HI Ray,
Have you checked the grid voltage to see if there is variation during the day
which would be enough to kick the inverters out of connection?
Brian Teitelbaum
AEE Solar
-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re
erly, the genny should get minimal hours per year, and the manufacturer
should be able to warranty them. They need to be educated.
Brian Teitelbaum
AEE Solar
-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Beha
I see absolutely no Code compliance issues with this method.
The April Fool's Code that is...
Brian Teitelbaum
AEE Solar
-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Jason Szumlanski
Sent: Thu
Marco,
PV Powered makes a 16-circuit:
http://www.pvpowered.com/intellistring-commercial-monitoring.php
Brian Teitelbaum
AEE Solar
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Marco
Mangelsdorf
Sent: Wednesday, April 07
n or warranties with
respect to this product."
Brian Teitelbaum
AEE Solar
___
List sponsored by Home Power magazine
List Address: RE-wrenches@lists.re-wrenches.org
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wr
the winter, but that's still
easier than doing a separate inverter system, especially for customers who are
not Wrenches.
Brian Teitelbaum
AEE Solar
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Phil
Undercuffler
Sent: Tue
s 612 Whrs, or about 25AH
from the battery. This is quite a bit of power, and if you were in a sunnier
area, it would certainly make sense to just add PV. Where you are, it might be
more iffy, but I still think that you are better off just adding to the PV
array.
Brian Teitelbaum
AEE Solar
is if you use a DPDT transfer relay held closed by the grid, but defaulting
to PV direct if the grid goes down.
Unless you have some compelling reason, I just don't see having a PV array just
sit there most of the time not being used.
Brian Teitelbaum
AEE Solar
From: re-wrenches-boun
hen maybe I can get rid of my 1942 Servel fridge. But
you'll never pry me away from my late 30's six-burner, dual-oven Wedgewood gas
stove.
Brian Teitelbaum
AEE Solar
-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-w
would work. It would at least be an
interesting experiment, and not very expensive.
Brian Teitelbaum
AEE Solar
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Kirpal Khalsa
Sent: Tuesday, May 25, 2010 4:07 PM
To: RE-wrenches
Subjec
ich uses moisture present in the air as the
curing agent. I was told many years ago that this is the stuff that is used by
module manufacturers to attach and seal module junction boxes and the exit
point in the laminate where the tabs come out. It would be great if a module
rep could con
n business.
Brian Teitelbaum
ASE Solar
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Jeff Oldham
Sent: Thursday, June 17, 2010 9:14 AM
To: re-wrenches@lists.re-wrenches.org
Subject: [RE-wrenches] Supply side tap not allowed
I j
chronic undercharging. In a 5
peak sun-hour location, that's only 40Ah/day of charging capacity.
Brian Teitelbaum
AEE Solar
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of William Miller
Sent: Tuesday, July 23, 2013 1:13 PM
T
e charging day is limited to hours of sunlight, and as
long as you stay under the gassing voltage it should be fine. But as Eric
Benson noted, the battery manufacturer should have the final word.
Brian Teitelbaum
AEE Solar
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-
it could eventually wear through the copper.
But that is just a guess.
Brian Teitelbaum
AEE Solar
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Nik Ponzio,
Building Energy
Sent: Monday, September 16, 2013 2:10 PM
To: RE-w
Chris,
Is that the "inspector" saying that, or the LADWP rep?
Brian Teitelbaum
AEE Solar
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Chris Daum
Sent: Tuesday, September 24, 2013 12:41 PM
To: 'RE-wrenches'
S
reezing. I just have to use less cold-water mix during the winter.
Are you finding the new Bosch models to be this reliable?
Brian Teitelbaum
AEE Solar
-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Bill
son Lerner
Waldron Power and Light Co.
On Sep 30, 2013, at 9:39 AM, Brian Teitelbaum wrote:
> Hi Bill,
>
> I'm still running an Aquastar 125BS (original French model, before Bosch
> bought them) that I installed in 1990. I've had to rebuild the water valve
> once (aft
Alan and all,
FYI, Magnum makes a 24V version of the 120/240VAC inverter, the MS4024PAE.
Brian Teitelbaum
AEE Solar
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Allan Sindelar
Sent: Wednesday, October 30, 2013 12:25 PM
To
ave an amp-hour meter in the system, you should talk them into
letting you install one. Of course, if they get 28+ years out of a set of
flooded batteries, they must be doing it right, and maybe don't really need it.
Brian Teitelbaum
AEE Solar
From: re-wrenches-boun...@lists.re-wrenches.org
s not available
(or not known), at least not for flooded batteries.
Brian Teitelbaum
AEE Solar
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of
will...@millersolar.com
Sent: Friday, February 07, 2014 5:29 PM
To: 'RE-wre
anel, with a Main breaker, couldn't act as the
PV system disconnect, as long as it's Service-rated, a minimum of 60A, and the
utility does not require an external-handle disconnect, lockable in the off
position. Many utility companies still do.
Brian Teitelbaum
AEE Solar
From: re-wre
Nathan,
What is the distance between the buildings, and where are the utility meters
located?
What are the sizes of the Services? 200A?
Can both buildings be powered from a single Service? Why is the workshop
metered separately?
Brian Teitelbaum
AEE Solar
From: re-wrenches-boun...@lists.re
PM, Brian Teitelbaum
mailto:bteitelb...@aeesolar.com>> wrote:
Nathan,
What is the distance between the buildings, and where are the utility meters
located?
What are the sizes of the Services? 200A?
Can both buildings be powered from a single Service? Why is the workshop
metered separately?
you
have a lockable disco, good signage, and the house meter and shop disco are
close together. You should consult with your AHJ.
Brian Teitelbaum
AEE Solar
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Nathan Charles
Se
can power pumps up to 600HP. Here's their link:
http://www.worldwatersolar.com/capabilities/solar-projects/
I've have not personally dealt with WorldWater, but it looks like they will
only do a complete installation themselves, so it cuts you out of the project.
Maybe you can get a fin
t is the case.
If it's a well, what is the diameter of the well casing?
What are the peak sun-hours at the site during the darkest time of year that
the water is needed?
There are lots of other questions to ask, but these should help a lot.
Brian Teitelbaum
AEE Solar
-Original Messa
Roy has an excellent suggestion...if you have constant AC power available.
In fact, if you use the Grundfos SQE models, they come with a constant-pressure
controller so you don't need a large pressure tank, and it also has dry-run
protection features.
Brian Teitelbaum
AEE
y
flow control.
Brian Teitelbaum
AEE Solar
-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of All Solar, Inc.
Sent: Wednesday, May 07, 2014 2:28 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Low flow high head pum
Corey,
The wire ampacity has to be sized for the OCPD, as this is potentially a
bidirectional wire in a fault. While the inverter is current limited, the
grid it’s connected to is only limited by the Service Main, and that 50A
OCPD, which would exceed the ampacity of #10 wire.
Brian
the PV array on a 5kW Sunny
Boy, or adding a second Sunny Island and using two Sunny Boy 5000’s. Using
two Islands would eliminate the need for a transformer, and allow for full
array power during grid outages.
Brian Teitelbaum
AEE Solar
*From:* RE-wrenches [mailto:re-wrenches-boun
the UL listed E Panel from Midnite.
R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer,
Licensed Master Electrician
Solar Design Engineer
303 505-8760
On 7/3/2014 9:01 PM, Brian Teitelbaum wrote:
Mac,
Be careful with breaker sizing here. The transfer switch in the SMA SI5048
the Intersolar show
next week.
Brian Teitelbaum
AEE Solar
*From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On
Behalf Of *b...@midnitesolar.com
*Sent:* Friday, July 04, 2014 11:11 AM
*To:* RE-wrenches
*Subject:* Re: [RE-wrenches] Sunny Island retrofit
The Sunny
Thanks boB and Robin. Good explanation.
I wish that SMA would be more clear on this in the manuals. It shouldn’t be
that hard.
Do other inverters with built-in transfer relays also self-protect against
over-current? I’ve never wanted to try my luck.
Brian Teitelbaum
AEE Solar
*From
electrolyte too strong will shorten the battery life, although
maybe not enough to go through this ritual.
Brian Teitelbaum
AEE Solar
*From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On
Behalf Of *Mac Lewis
*Sent:* Tuesday, August 12, 2014 6:55 PM
*To:* RE-wrenches
use of
the fuse rating or the fuse holder rating though.
Brian Teitelbaum
AEE Solar
-Original Message-
From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On
Behalf Of Ray Walters
Sent: Friday, August 22, 2014 6:14 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Assembl
Chris,
What is the wattage rating of the wind turbine?
And is that 48-60 VDC directly out of the turbine, or is that what comes
out of the turbine’s “controller”? To put that another way, are there just
two wires coming out of the turbine, or three wires?
Brian Teitelbaum
AEE Solar
developing large
battery-based inverters. I haven't checked on their progress lately
though.
Brian Teitelbaum
AEE Solar
-Original Message-
From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On
Behalf Of Phil Theis
Sent: Thursday, October 02, 2014 11:52 AM
To: RE-wr
ing a PV-direct arrangement, there is
not much advantage in using the Flex pumps.
Brian Teitelbaum
AEE solar
-Original Message-
From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On
Behalf Of Ron @ earthRight Solar
Sent: Monday, October 20, 2014 6:21 PM
To: RE-wre
Hi Jay,
You are correct about the CU-200. It has an operating voltage range of
30-300 VDC and 90-240 VAC.
However, the IO-101 transfer switch is another story, and I think that is
what Ron meant. Up until recently Grundfos was only importing the 120 VAC
version of the IO-101, but now you can get