RE: What I'm Hearing About Hydrostatic Testing

2007-03-09 Thread George Church
What is supposed to happen and what may happen can be two completely different things. And as Russ points out in his #25 Seminar, when you do a lot of work, it's not a matter of IF something will happen, but WHEN something does happen. We upgraded the supply for an ex industrial building for a

Aerosol spray activates sprinklers ???

2007-03-09 Thread Richard Mote
I came across this report this morning just shows how ignorant the general public is regarding sprinklers and how they work. http://www.kcentv.com/news/c-article.php?cid=1nid=12344 Richard L. Mote Layout Technician Rowe Sprinkler Systems, Inc ___

Pandora's Box

2007-03-09 Thread Chris Brown
Question to the forum: What effect does a 5/8 inch or 3/4 inch water meter have on fire sprinkler system installed in an NFPA 13D or NFPA 13R system. The issue is one of the maximum continuous flow thru the meter and its effect on the ability of the fire sprinkler system to operate as intended.

RE: Pandora's Box

2007-03-09 Thread Craig.Prahl
What, a thinking test on a FRIDAY? What's wrong with you dude?That's just so wrong. ;) Craig L. Prahl, CET Fire Protection Group Mechanical Department CH2MHILL Lockwood Greene 1500 International Drive PO Box 491, Spartanburg, SC 29304-0491 Direct - 864.599.4102 Fax - 864.599.8439

RE: Aerosol spray activates sprinklers ???

2007-03-09 Thread Don Lowry
I actually watched that on the morning news, and the report stated the aeresol was sprayed into smoke detectors. Probably the transcriber of the text inserted sprinkler instead of smoke detector. Don Lowry -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of

RE: Pandora's Box

2007-03-09 Thread art
A 3/4 water supply will probably not be capable of supplying two sprinklers. You need to have a friction loss graph for the meter. Do the hydraulic calcs to show what it will provide then show the required pipe size to allow the system to work. Art - ATCO Fire Protection Design -Original

RE: audible alarms

2007-03-09 Thread Thomas Reinhardt
Hi Greg, I know in our town we enforce installation of a full fire alarm, (horns, strobes etc...)based on the fact that we have adopted the Illinois Accessibility code.NFPA 72 just tells you how it shall be installed. I would check with your state ADA requirements. I hope this helps.

Re[2]: Aerosol spray activates sprinklers ???

2007-03-09 Thread Charles Thurston
Hello Don, I just watched it on line and she said Aimed at sprinklers Friday, March 9, 2007, 10:27:45 AM, you wrote: I actually watched that on the morning news, and the report stated the aeresol was sprayed into smoke detectors. Probably the transcriber of the text inserted sprinkler

RE: Pandora's Box

2007-03-09 Thread Pete Schwab
Viking has a listed head for Residential - 9 GPM each. Spacings are obviously not 20'x20'. However, you can have the system at the manufacturer's guidelines on the meter. Pete Schwab Wayne Automatic Fire -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of

Re: Aerosol spray activates sprinklers ???

2007-03-09 Thread Richard Mote
This link take you to a transcribed page, in the video link on that page the women specifically says sprinklers. Maybe they got it right later. - Original Message - From: Don Lowry [EMAIL PROTECTED] To: sprinklerforum@firesprinkler.org Sent: Friday, March 09, 2007 8:27 AM Subject: RE:

RE: What I'm Hearing About Hydrostatic Testing

2007-03-09 Thread Thomas Reinhardt
I think Roland Huggins is correct.Just test the system and if there is a problem fix it. -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Roland Huggins Sent: Thursday, March 08, 2007 2:22 PM To: sprinklerforum@firesprinkler.org Subject: Re: What I'm

RE: Pandora's Box

2007-03-09 Thread Bob Knight
The charts that I have show a 5/8 meter rated for 20 gpm and a 3/4 meter rated for 30 gpm. These charts are for NEPTUNE water meters which our local purveyor uses. This being the case, two RES sprinklers will create more flow than the 5/8 meter is rated for, and in most cases two sprinklers will

RE: Re[2]: Aerosol spray activates sprinklers ???

2007-03-09 Thread Don Lowry
The video online is apparently from yesterdays news at 6:00 PM. (That was the evening news anchor lady.) This morning they said and showed smoke detectors. They were called on it last night and got it correct this morning. -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL

Re: Pandora's Box

2007-03-09 Thread PCE
Chris, They would have the same effect that any valve or fitting would have on the ability of a sprinkler system to function properly. The loss in pressure due to friction at various flows through the meters is required to be accounted for in the hydraulic calculations. Interestingly

RE: What I'm Hearing About Hydrostatic Testing

2007-03-09 Thread Mike Brown (TECH- GVL)
Folks A water hammer can do nasty things to a sprinklers system but just pump pressure can cause problems if the sprinkler fitters have not done their work properly. Years ago at Phillips Plaza in Atlanta a grooved coupling was not properly tightened because the groove on the pipe was too

Re: Pandora's Box

2007-03-09 Thread Thom McMahon
Since this is a test: 1) The meter will have no effect on the operation of the 13D system if you install it per NFPA 13D, 2007 Figure A.6.2(a) or (b) or 2) There are no 5/8 meters that will not screw you over bad for pressure and flow.The only possible hope is you have no rooms with more

Re: Pandora's Box

2007-03-09 Thread Roland Huggins
I know the Dallas water dept will not allow small standard water meters (displacement types I think) to be used on a residential sprinkler system. They say these unit will not operate RELIABLY at the higher flow presented by the sprinkler system. I believe they require a minimum 1 -1/2

Another Sprinkler Success Story!

2007-03-09 Thread Ray Vance
There was a fire at one of the properties that Wayne Automatic FIre Sprinklers installed and currently services. Camden Sedgebrook located in the Huntersville area of NC had a fire break out around 2:30 am this morning and the sprinkler system was able to put the fire out. AND NOBODY

RE: Pandora's Box

2007-03-09 Thread Chris Brown
If you look at the Hersey Meter 400 Series IIS and 500 Series IIS the flow characteristics are shown and it becomes very clear that a 1 meter would be the minimum size for MOST Dwelling fire sprinkler systems (NOT ALL). Real life example: 2 low flow sprinklers requiring a minimum of 13 GPM

Re: Pandora's Box

2007-03-09 Thread Richard Matsuda
Okay, since Roland mentions Dallas water dept/utilities (DWU), I thought I'd contribute to this discussion. Contrary to what Roland has inferred, DWU actually is very understanding and has tried to address the reliability of the domestic meters during high flow (fire) conditions. Prior to

RE: Pandora's Box

2007-03-09 Thread Chris Brown
I totally agree with the statements made by Rick. The Heresy charts I have, confirm those numbers as Typical Operating Ranges. The issue I am trying to confirm is how does the Maximum Continuous Operation affect a dwelling or residential fire sprinkler system. Given the valves of the Hersey

RE: What I'm Hearing About Hydrostatic Testing

2007-03-09 Thread G. Tim Stone
All sprinkler systems should be able to with stand a 200 PSI hydro test at any time the owner's or AHJ's might request it during the life span of that sprinkler system. I don't think anyone would argue this point. The point I was trying to make in my earlier response was that the contractor

RE: Pandora's Box

2007-03-09 Thread Kathryn Tyler
This is the water meter we use here a lot. http://www.badgermeter.com/pdf/recdisk/tech/rd-t-34.pdf http://www.vikinggroupinc.com/databook/sprinklers/residential/103105.pdf is an example of a concealed head that could work with up to 16x16 spacing (flat ceilings only though - if on sloped clgs,

RE: Pandora's Box

2007-03-09 Thread Kathryn Tyler
No problem Chris just wanting to add my 'thinking' for Friday... I am now done, going home soon, short day every Friday!!! Yippee!!! Good Luck! -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Chris Brown Sent: Friday, March 09, 2007 10:50 AM To:

RE: Standpipe at Intermediate Landing

2007-03-09 Thread Bob Knight
This is a follow up for yesterday's postings. Thanks to each of you that provided input. I did speak with the AHJ this morning and he agreed with the arguments that were presented to me by you. So as Roland mentioned, I would think the intermediate connection at the first landing is for the

Re: Pandora's Box

2007-03-09 Thread PCE
Chris, Badger makes a meter, model M40, which is 3/4 x 3/4, and their chart shows that it can accept flows of up to 35 gpm. And, at that flow, it has a pressure loss of around 6.5 to 7.0 psi. I would think that would certainly be sufficient to not impact the design of a residential system

RE: Pandora's Box

2007-03-09 Thread Chris Brown
I agree again Ken. My experience with the water districts I have to contend with is that they will install the meter they like and not the one being used in other jurisdictions. It is all driven by the cost of a meter at the time they purchase them and the cheapest manufactured meter they can

Re: Pandora's Box

2007-03-09 Thread Roland Huggins
Cutsheets on all listed devices should be submitted BUT the wording in 13 is a tad obscure - Specially Listed Equipment must be submitted. Now that's clear as mud. Back in my days reviewing items, EVERYTHING was submitted. What is the norm today? I beat this would be a good item to be

Sway Bracing Fasteners

2007-03-09 Thread Bob Knight
When sizing the size of fasteners for the attachment of sway bracing to post-tension slabs, do I need to be concerned with tension load or shear load? The reason I ask is that we will be using HILTI HDI-P 3/8 concrete inserts. It has an allowable load under tension of 380 lbs and an allowable

Re: Sway Bracing Fasteners

2007-03-09 Thread Thom McMahon
If your using a fitting attachment similar to the TOLCO Fig. 909 or 910 and your brace angle is less than 60 deg. from horizontal the load is all shear. From 60 deg. on down to 90 (vertical) the load becomes increasingly Tension. You'll find it very beneficial to keep your hangers between 30

Re: Pandora's Box

2007-03-09 Thread Garth W. Warren
Does anyone know how much pressure would it take to push 35 gpm through a 3/4 meter? Thanks - Garth - Original Message - From: PCE [EMAIL PROTECTED] To: sprinklerforum@firesprinkler.org Sent: Friday, March 09, 2007 2:01 PM Subject: Re: Pandora's Box Chris, Badger makes a meter, model

Unsubscribe / [EMAIL PROTECTED] / chief303

2007-03-09 Thread Scott Adams
Unsubscribe / [EMAIL PROTECTED] / chief303 Scott W. Adams Assistant Fire Chief District Fire Marshal Park City Fire Service District Direct - (435) 940-2503 Fire Prev - (435) 940-2532 [EMAIL PROTECTED] -Original Message- From: [EMAIL PROTECTED] [mailto:sprinklerforum- [EMAIL PROTECTED]

Re: Pandora's Box

2007-03-09 Thread Todd Williams - work
Could be a lot. You'd have to get the information from the manufacturer. They can be stingy about giving it out, but they do have it. I recently went through this drill on a 1-1/2 meter. BTW, if there is someone living in South Florida out there, would you please e-mail me privately. Thanks.

Re: Pandora's Box

2007-03-09 Thread Thom McMahon
For a 3/4 Badger meter the maximum flow is only 25 Gpm At 5 Psi loss. You are off the chart with 35 Gpm, so it will probly break the meter, and then its anyone's guess how much pressure you'll lose. Thom McMahon Firetech, Inc. 2560 Copper Ridge Dr Steamboat Springs, CO 80488-2136 Tel:

Re: Pandora's Box

2007-03-09 Thread PCE
Thom, Are you sure on that? I have a Badger catalog sheet, showing the M40, 3/4 model, has a max flow of 35 gpm. Just asking, maybe my data is out of date. PARSLEY CONSULTING Ken Wagoner, SET 760.745.6181 voice 760.745.0537 fax [EMAIL PROTECTED] mailto:[EMAIL PROTECTED] e-mail

RE: Pandora's Box

2007-03-09 Thread John Drucker
Everything. Now that doesn't mean that the applicant drops the RAS, TYCO, etc catalog on table, just the cuts needed to validate the design for code compliance. I've stopped counting the number of times a sprinkler specified in the legend was standard response where the design clearly included a

RE: Pandora's Box

2007-03-09 Thread Tom Duross
Unless it's multipurpose, do we really have to meter the water? I mean for 20-30 gallons a year? Fortunately, up here in Beantown we're not metering YET but we can't even do a single family without a separate service. No questionable meter loss figures here yet. Just questionable bfp losses. TGIF

RE: (no subject)

2007-03-09 Thread Top Myers
I believe you are speaking about change in NFPA-25 which requires testing of all dry sprinklers after 10 years. Sample size is same as any other heads. Top Myers Myers Risk Services -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of [EMAIL PROTECTED] Sent: