Occupant load vs Square footage

2010-05-20 Thread Owen Evans
Here's the situation: A person wants to open up a martial arts studio in a strip mall. The middle unit has 2800 square feet of open floor space for matting. The building dept. comes up with an occupant load of greater than 50 people therefor, it is classed an assembly. The planning dept. gave

Re: Pipe and fitting cost data

2010-05-20 Thread Richard Lindner
Any reason you're not using Means?? If you're looking for ballpark, those books will provide that with ease. ___ Sprinklerforum mailing list Sprinklerforum@firesprinkler.org http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical

RE: Galv fittings?

2010-05-20 Thread George Church
That was in the spec and since our shop does welded outlets, I took it out. Chris, surely you have "insta-galv" spray in your shop, too? -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Chris Cahill Sent: Thurs

RE: Galv fittings?

2010-05-20 Thread Chris Cahill
So when you want galv pipe do you allow welded outlets? Noting the outlets and weld aren't exactly galv even with a coat of paint. Chris Cahill, P.E. Fire Protection Engineer Sentry Fire Protection, Inc. 763-658-4483 763-658-4921 fax Email: chr...@sentryfiremn.com Mail: P.O. Box 69

RE: Galv fittings?

2010-05-20 Thread George Church
LOL, Rahe, I seriously laughed out loud in my office. Thanks for the smile. I just had them taken out of a MasterSpec for a project we helped put out to bid, and didn't get any argument from the PE who was backpedaling from MasterSpec and its 60 pages of how to install a sprinkler system without e

Re: Galv fittings?

2010-05-20 Thread rahe . loftin
Chris, I understand your plight and even I don't require screwed galvanized fittings. We all know how difficult it is to thread pipe into them. However, why are they made? Is there really a market for them? Not to mention that newly threaded pipe has threads exposed that are not galvanized. The

RE: Galv fittings?

2010-05-20 Thread Matthew J. Willis
I use Galv. fitting with pipe in one place only. Bad environment. Everything else gets black. R/ Matt Matthew J. Willis, CET Automatic Fire Sprinklers Norred Fire Systems L.L.C. 318-387-1134 Voice 318-816-1087 Mobile 318-387-1163 Facsimile m...@norredfire.com > >-Original Message-

Galv fittings?

2010-05-20 Thread Chris Cahill
How often do you see galv fittings required on galv piping? Usually ductile or cast are permitted aren't they? Don't ask where just know your tax dollars are being put to good use - NOT! SIPA in a 20k office building with galv required on both. We're not talking some secret agency or historic wh

RE: Domestic Supply

2010-05-20 Thread Greg McGahan
What about water hoses? Greg -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Bobby Gillett Sent: Thursday, May 20, 2010 12:49 PM To: sprinklerforum@firesprinkler.org Subject: RE: Domestic Supply That sounds

2010 changes - was Ceiling Tiles or Lack thereof...

2010-05-20 Thread Chris Cahill
I was being tongue-in-cheek related to you can't prohibit something that doesn't exist. I shall make it a point to work on my emoticons :-J, :j, 8-;) On the topic of changes I saw some other odd language things the committee did. 0.003" cellophane or thin bags? Great specificity or what the he

RE: Ant-Freeze Systems

2010-05-20 Thread Matthew J. Willis
For clarification from the 2010 edition, Caps mine: 3.4.1 Antifreeze Sprinkler System. A wet pipe sprinkler system employing automatic sprinklers that are attached to a piping system that contains an antifreeze solution and that are connected to a water supply. The antifreeze solution is discharge

Re: Ant-Freeze Systems

2010-05-20 Thread Roland Huggins
Unless you find ANYTHING in NFPA 13 supporting such an arrangement and countering the definition (yes that is a weak place to rely on for not doing something but it is quite explicit), I'd go beyond calling it a bad idea and say you would be installing a non-conforming system. Roland On May

Re: Ceiling Tiles or Lack thereof...

2010-05-20 Thread Roland Huggins
Didn't realize you were from Texas since most don't consider 15' x 15' a SMALL item. Even such large sections with opening between them (often called floating clouds) are not an acceptable ceiling but just an obstruction. Roland On May 20, 2010, at 12:16 PM, Todd Williams wrote: > So we c

Re: Ceiling Tiles or Lack thereof...

2010-05-20 Thread Todd Williams
So we can't consider a ceiling a collection of interconnected 15'x 15' heat collectors? At 03:13 PM 5/20/2010, you wrote: >That reference does NOT support the existence of functional heat >collectors - even if you presume such a thing (I prefer to use assume >since we know what that means). It

Re: Ceiling Tiles or Lack thereof...

2010-05-20 Thread Roland Huggins
That reference does NOT support the existence of functional heat collectors - even if you presume such a thing (I prefer to use assume since we know what that means). It's to stop folks from sticking small items over the sprinkler then claiming they provide some value. As the Annex points

RE: [Bulk] RE: Pipe and fitting cost data

2010-05-20 Thread Cliff Whitfield
Craig, I would think that if you are simply looking for list prices any supplier or manufacturer would be happy to provide you with that. If you can't get that from anyone, contact me offline and I'll see what I can do to help. I haven't been in the contracting side of this for 8 or 9 years but

RE: Pipe and fitting cost data

2010-05-20 Thread Craig.Prahl
It doesn't matter. I don't need to know the discounted price ABC sprinkler gets versus XYZ Sprinkler. Just looking for list prices. If I get differing info I'll use the highest. These estimates are used for funding of the project so if they get more than what's needed they usually just spen

RE: Pipe and fitting cost data

2010-05-20 Thread Matthew J. Willis
That information is confidential for the most part. Different discounts are given to different contractors. I am sure the more you buy the better the break. So even if you got info from a couple on here, it could still be miles different. R/ Matt Matthew J. Willis, CET Automatic Fire Sprinkler

RE: Domestic Supply

2010-05-20 Thread Bobby Gillett
That sounds accurate, thank you. Bobby Gillett Sr. Project Manager Key Fire Protection, Inc. (731) 424-0130 office (731) 424-9285 fax (731) 267-4853 cell bobby.gill...@keyfireprotection.com -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-bou

RE: Ceiling Tiles or Lack thereof...

2010-05-20 Thread Craig.Prahl
I'd just list the issue as a Misc. Observation. Used to do that when I'd notice things like crates stacked too close to ceilings or items being stored in places they weren't intended to be stored. It's not a system deficiency but it's noted. Craig L. Prahl, CET Fire Protection Specialist M

RE: Pipe and fitting cost data

2010-05-20 Thread Craig.Prahl
The suppliers wouldn't send their info since I'm not a contractor and wouldn't be buying pipe from them. Local prices are irrelevant since majority of my projects are all over the place, not here locally. I've got Tyco's data, but that's just parts, no pipe. Craig L. Prahl, CET Fire Prote

RE: Ant-Freeze Systems

2010-05-20 Thread Brad
Sounds like if he was smart cheap he would buy min. 40 deg F for a few months a year, but the 54k and many blowout thing sounds like he is also into insurance on the side somehow -Original Message- From: Daniel Merkle [mailto:dlmcolon...@yahoo.com] Sent: Thursday, May 20, 2010 11:00 AM To

RE: Pipe and fitting cost data

2010-05-20 Thread Chris Cahill
If all he's checking is magnitude differences changing prices shouldn't have that much effect. Sprinkler pipe has gone up several times already this year. And yes expecting more. Pipe and the scrape steel it's made from is a world market and China didn't go into recession just dropped back to bi

Re: Pipe and fitting cost data

2010-05-20 Thread Todd Williams
Can't help you with that, but a friend of mine in the steel business told me there may be a big price increase in steel coming in June. Reason: dramatic increase in raw materials. That could make most current pricing info obsolete. At 12:23 PM 5/20/2010, you wrote: >Would anyone happen to hav

RE: Ceiling Tiles or Lack thereof...

2010-05-20 Thread Matthew J. Willis
Always do. Thanks for the heads up. Matt Matthew J. Willis, CET Automatic Fire Sprinklers Norred Fire Systems L.L.C. 318-387-1134 Voice 318-816-1087 Mobile 318-387-1163 Facsimile m...@norredfire.com > >-Original Message- > >From: sprinklerforum-boun...@firesprinkler.org [mailto:spr

RE: Ceiling Tiles or Lack thereof...

2010-05-20 Thread Thom McMahon
Read Roland's article in Sprinkler age NFPA 25 Upcoming 2011 Edition, especially the part about Hazard Evaluation. Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926 -Original Message- From: sprinklerfor

RE: Ceiling Tiles or Lack thereof...

2010-05-20 Thread Matthew J. Willis
Gotta love these computers and back up. Cheap and Very effective. R/ Matt Matthew J. Willis, CET Automatic Fire Sprinklers Norred Fire Systems L.L.C. 318-387-1134 Voice 318-816-1087 Mobile 318-387-1163 Facsimile m...@norredfire.com > >-Original Message- > >From: sprinklerforum-boun

RE: Ceiling Tiles or Lack thereof...

2010-05-20 Thread Thom McMahon
You can write and mail anything you want too. Just having that piece of paper in the file could save you and your insurance co. everything, including your kids college fund. Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 97

RE: Domestic Supply

2010-05-20 Thread Mike Cabral
Water flow switch must not operate before 4 GPM and not after 10 GPM most are in the 8 to 9 GPM range. Unless you have a big pan head shower or tub the switch wont operate if you set the retard to the max. Mike Cabral Bobby Gillett wrote: > Truly you think you would be able to since the

RE: Ceiling Tiles or Lack thereof...

2010-05-20 Thread Matthew J. Willis
Oh the notification happens. On the SEPARATE form from the report thingy. You know, the one that is thrown away. What I want is something I can hang a Yellow/Red tag on and get the state behind me. But if it is not in the adopted code/standard, then I cannot write it up. The lawyers can scream all

RE: Ceiling Tiles or Lack thereof...

2010-05-20 Thread Thom McMahon
I would say that unless you have an inspector that is totally ignorant on 13, 1, IBC or any applicable code or standard besides 25, some Lawyer will say that YOU KNEW!!! Of the deficiency, and did not make any attempt to report it either to the owner or the AHJ. "Therefore as a "Professional" Inspe

Pipe and fitting cost data

2010-05-20 Thread Craig.Prahl
Would anyone happen to have a distributor price list on pipe and ftgs? Looking for black and Galv. Standard sizes up to 8". This can be straight list prices. Just need to make sure the estimators are using the right values, so far they seem off. This is for rough order of magnitude estimati

RE: Ant-Freeze Systems

2010-05-20 Thread Matthew J. Willis
See 3.4.1 in the 02 edition. Handbook commentary is specific. Then look at 7.1.3 same edition. Finally 7.5.3.1 It is not allowed. R/ Matt Matthew J. Willis, CET Automatic Fire Sprinklers Norred Fire Systems L.L.C. 318-387-1134 Voice 318-816-1087 Mobile 318-387-1163 Facsimile m...@norredfire

RE: Domestic Supply

2010-05-20 Thread Bobby Gillett
Truly you think you would be able to since the tie in point for us is tee'd off just after the backflow, but I am trying to prevent going back and adding later. Bobby Gillett Sr. Project Manager Key Fire Protection, Inc. (731) 424-0130 office (731) 424-9285 fax (731) 267-4853 cell bobby.gill...@

RE: Domestic Supply

2010-05-20 Thread George Church
Could you set the WFS retard out to 90 sec and avoid the check? -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Bobby Gillett Sent: Thursday, May 20, 2010 11:47 AM To: sprinklerforum@firesprinkler.org Subject:

Re: Ant-Freeze Systems

2010-05-20 Thread Mike Cabral
At first blush this is not a good idea. You could develop a head pressure water column above the DPV which can slow or even prevent operation of the DPV. Newer DPV have a low differential. You still need expansion tank $$. How do you do a trip test AF then air then water. No No No! Sent on the S

Re: Ant-Freeze Systems

2010-05-20 Thread Daniel Merkle
The smaller attic area is well below 40 gallons. The total dry system is probably closer to 350. Daniel L. Merkle, CET NICET # 118915 Automatic Sprinkler System Layout, Level III "COLONIAL" Fire Protection Systems Inc. 937 Linden Ave. W. E. Rochester, N.Y. 14445 Office-(585) 381-7362 Fax-

RE: Ceiling Tiles or Lack thereof...

2010-05-20 Thread Matthew J. Willis
> > > >Tiles are part of the ceiling assembly and the protection design for a > >standard drop ceiling presumes the tiles are in place and yes, grid > >with no tiles is a design style, grids with some tiles is a design > >style, floating grid with an open perimeter is a design style, but > >th

RE: Ant-Freeze Systems

2010-05-20 Thread Matt Grise
How large is the complete dry system? (gallon capacity) Matt Grisé PE*, LEED AP Sales Engineer Alliance Fire Protection *Licensed in KS & MO 913.888.0647 ph 913.888.0618 f 913.927.0222 cell www. AFPsprink.com -Original Message- From: sprinklerforum-boun...@firesprinkler.org [ma

Re: Ant-Freeze Systems

2010-05-20 Thread Daniel Merkle
Well that is sort of the problem. He has had many blow outs over the years and is afraid of dry systems. He had another sprinkler company do about 20k worth of work to his system last year and I can't determine if they made the system better or worse. He had a blow-out on x-mas eave this past wi

Re: Ant-Freeze Systems

2010-05-20 Thread Daniel Merkle
I completely agree that it sounds like a bad idea and will do everything that I can to talk the owner out of it. However, I am just trying to figure out if this would even be allowed per code. If the owner persists, I will walk away. Daniel L. Merkle, CET NICET # 118915 Automatic Sprinkler Sy

RE: Ant-Freeze Systems

2010-05-20 Thread Matt Grise
Just wait until the dry system freezes and pops, and then have him compare the cleanup bill to the cost of retrofit. Matt Grisé PE*, LEED AP Sales Engineer Alliance Fire Protection *Licensed in KS & MO 913.888.0647 ph 913.888.0618 f 913.927.0222 cell www. AFPsprink.com -Original Me

Re: Ant-Freeze Systems

2010-05-20 Thread Daniel Merkle
$$$. Cheap owner. Daniel L. Merkle, CET NICET # 118915 Automatic Sprinkler System Layout, Level III "COLONIAL" Fire Protection Systems Inc. 937 Linden Ave. W. E. Rochester, N.Y. 14445 Office-(585) 381-7362 Fax-(585) 381-8263 E-mail - dlmcolon...@yahoo.com _

RE: Ant-Freeze Systems

2010-05-20 Thread Matt Grise
I agree. This sounds like trouble. I would not want to have to explain that design in court. Is there any reason why the entire dry system cannot be converted to anti-freeze? Or a wet line run to supply the anti-freeze branch? Matt Grisé PE*, LEED AP Sales Engineer Alliance Fire Protection *

Re: Ant-Freeze Systems

2010-05-20 Thread Todd Williams
The definition of anti-freeze systems in NFPA 13 specifically references it feeding from a wet system. Also, is a sprinkler activates, it dump anti-freeze, then air and finally water. I don't know haw antifreeze would impact water delivery time. Sounds like a bad idea. At 11:40 AM 5/20/2010,

Domestic Supply

2010-05-20 Thread Bobby Gillett
I have 4 sprinklers in room coming from domestic supply. In NFPA 13 D.4 (LSC101:7.7.1.2) says an indicating shutoff valve shall be installed in an accessible location between the sprinklers and the connection to the domestic water supply. IBC 2006 903.3.5.1.1 (1) Valves shall not be installed betw

RE: Ant-Freeze Systems

2010-05-20 Thread Vince Sabolik
So now I'm wondering why this is OK but the NFPA frowns on trapped water in a heated area in a dry system. At 11:42 AM 5/20/2010, you wrote: >So the idea would be that when the anti-freeze system activates, the >antifreeze solution would be blown out by the supervisory air, then >the dry valve

Re: Ant-Freeze Systems

2010-05-20 Thread Daniel Merkle
Correct. Daniel L. Merkle, CET NICET # 118915 Automatic Sprinkler System Layout, Level III "COLONIAL" Fire Protection Systems Inc. 937 Linden Ave. W. E. Rochester, N.Y. 14445 Office-(585) 381-7362 Fax-(585) 381-8263 E-mail - dlmcolon...@yahoo.com From:

RE: Ant-Freeze Systems

2010-05-20 Thread Matt Grise
So the idea would be that when the anti-freeze system activates, the antifreeze solution would be blown out by the supervisory air, then the dry valve would trip, then the water would fill the system and discharge? Matt Grisé PE*, LEED AP Sales Engineer Alliance Fire Protection *Licensed in K

Re: Ant-Freeze Systems

2010-05-20 Thread Daniel Merkle
He would like to a line off the dry system to feed the anti-freeze. Daniel L. Merkle, CET NICET # 118915 Automatic Sprinkler System Layout, Level III "COLONIAL" Fire Protection Systems Inc. 937 Linden Ave. W. E. Rochester, N.Y. 14445 Office-(585) 381-7362 Fax-(585) 381-8263 E-mail - dlmco

RE: Anti-Freeze Systems

2010-05-20 Thread Matt Grise
Is there a CPVC pipe that is listed for use in dry systems? Matt Grisé PE*, LEED AP Sales Engineer Alliance Fire Protection *Licensed in KS & MO 913.888.0647 ph 913.888.0618 f 913.927.0222 cell www. AFPsprink.com -Original Message- From: sprinklerforum-boun...@firesprinkler.org

RE: Anti-Freeze Systems

2010-05-20 Thread Art Tiroly
I have done this a few times. After the dry system piping had rusted out this was suggested to the owner to reduce the maintenance problems with dry sprinklers in attics. I have only know of one problem ie: when PG was refilled in a system with CPVC piping. Art Tiroly and Associates. -Origin

RE: Ant-Freeze Systems

2010-05-20 Thread Matt Grise
So he wants to remove the dry pipe valve and replace it with an anti-freeze bfp and expansion tank? Or does he want to take a line off of the dry system to feed the anti-freeze system (keeping the dry system in place)? Matt Grisé PE*, LEED AP Sales Engineer Alliance Fire Protection *Licensed

RE: SC sprinkler requirement delay

2010-05-20 Thread David Blackwell
It hasn't made it out of the Legislature yet. It was sent back to the House with amendments. It is listed on the House Calendar [http://www.scstatehouse.gov/hcal/20100520.htm] today under the heading "UNANIMOUS CONSENT REQUESTS SENATE AMENDMENTS" on page 26 as H. 4

Ant-Freeze Systems

2010-05-20 Thread Daniel Merkle
Based on the 2002 version of NFPA-13 is there anything that restricts an anti-freeze system from being piped off of a dry system? I have an owner of a building with a relatively small attic that has a dry system in place that was not installed properly and he would like to make this portion of h

RE: Ceiling Tiles or Lack thereof...

2010-05-20 Thread John Denhardt
I am not sure I agree with your approach. This is enforceable language that is NFPA 1. NFPA 1 is not adopted in many areas. A simple copy will make the enforcement of removed ceilings much easier. John John August Denhardt, P.E. Strickland Fire Protection Incorporated 5113 Berwyn Road College

RE: Ceiling Tiles or Lack thereof...

2010-05-20 Thread Thom McMahon
So using your theory, we should not encourage the adoption by the IRC of residential sprinklers, nor should we encourage the adoption of that code by states until they, in your opinion, adequately enforce existing codes. We should not incorp. CMSA into 13, or anything else "NEW" until all of existi

RE: Hospital curtains with mesh

2010-05-20 Thread Bobby Gillett
Thank you, Matthew Bobby Gillett Sr. Project Manager Key Fire Protection, Inc. (731) 424-0130 office (731) 424-9285 fax (731) 267-4853 cell bobby.gill...@keyfireprotection.com -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkl

Re: Hospital curtains with mesh

2010-05-20 Thread Matthew . Drewello
2007 section 8.6.5.2.2 Matthew Drewello, PE Fluor Corporation 100 Fluor Daniel Drive Greenville, SC 29681 864-517-1814 "Bobby Gillett" Sent by: sprinklerforum-boun...@firesprinkler.org 05/20/2010 09:49 AM Please respond to sprinklerforum To cc Subject Hospital curtains with mesh

Hospital curtains with mesh

2010-05-20 Thread Bobby Gillett
Can someone direct me to the allowances for the mesh opening in hospital curtains in NFPA 13? I know it used to be in there, but I cant seem to find it. Thank you, Bobby Gillett Sr. Project Manager Key Fire Protection, Inc. (731) 424-0130 office (731) 424-9285 fax (731) 267-4853 cell

Re: Ceiling Tiles or Lack thereof...

2010-05-20 Thread cherokeefire...@aol.com
It doesn't need carried over to 25 25 cannot be expected to incorporate all the building codes. Sprinkler inspection and maintenance should not turn into building code analysis. Besides, there are so many items NFPA has added to 25 that aren't being followed or enforced anyway. I don't thin

RE: Ceiling Tiles or Lack thereof...

2010-05-20 Thread Thomas Reinhardt
Matt, Depending on what codes they have adopted in their jurisdiction. I use the IFC (2003) Chapter seven Fire-Resistance-Rated Construction. Fire resistant rated construction must be maintained. Also with out ceiling tiles the heat would rise and cause a delay in sprinkler activation. I hope th

RE: Ceiling Tiles or Lack thereof...

2010-05-20 Thread Johnson, Duane (NIH/OD/ORS) [C]
NFPA 1 Chapter 13 Fire Protection Systems Section 13.3.3.3 Inspection, Testing and Maintenance... Where automatic sprinklers are installed, ceilings necessary for the proper actuation of the fire protection device in accordance with NFPA 13 shall be maintained. Sounds like someone should propos