RE: NFPA 13D

2020-03-31 Thread bill.brooks brooksfpe.com via Sprinklerforum
Stites Subject: Re: NFPA 13D Gary, I have to disagree with your position. Reading from the '16 edition of NFPA 13D, §7.4.1 states that, "Listed pipe shall be supported in accordance with any listing limitations." What I've read from most of the manufacturer's of

RE: [EXTERNAL] Re: NFPA 13D

2020-03-30 Thread Kyle.Montgomery via Sprinklerforum
/location issue. -Kyle M From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Parsley Consulting via Sprinklerforum Sent: Monday, March 30, 2020 9:00 AM To: sprinklerforum@lists.firesprinkler.org Cc: Parsley Consulting ; Gary Stites Subject: [EXTERNAL] Re: NFPA

Re: NFPA 13D

2020-03-30 Thread Parsley Consulting via Sprinklerforum
Gary, I have to disagree with your position.  Reading from the '16 edition of NFPA 13D, §7.4.1 states that, /"Listed pipe shall be supported in accordance with any listing limitations./" What I've read from most of the manufacturer's of CPVC is that the support criteria they've developed are

Re: NFPA 13D

2020-03-30 Thread Gary Stites via Sprinklerforum
13D is silent on this as it says to install piping per the plumbing code. The plumbing code would determine if you can hang from the piping or not. On Sun, Mar 29, 2020 at 2:29 AM Bruce Verhei via Sprinklerforum < sprinklerforum@lists.firesprinkler.org> wrote: > Do hang the HVAC from the CPVC. No

Re: NFPA 13D

2020-03-28 Thread Bruce Verhei via Sprinklerforum
Do hang the HVAC from the CPVC. Not just taking it off. Ever wonder how codes get thicker and thicker. One way is more pre-approved design options. The other. Needing to write this kind of into code. Simple question. Will HVAC firm post photo on their homepage as example work their proud

Re: NFPA 13D

2020-03-28 Thread Tom Wellen via Sprinklerforum
>From the Lubrizol website: Fiberglass Duct insulation with aluminum, paper, metalized polyester, polypropylene and polyethylene facing may come into contact with CPVC. On Sat, Mar 28, 2020 at 9:09 PM Tom Noble via Sprinklerforum < sprinklerforum@lists.firesprinkler.org> wrote: > What about th

Re: NFPA 13D

2020-03-28 Thread Parsley Consulting via Sprinklerforum
Tom, I did not see this post until today, so I apologize for the delayed response.  I'll share my thoughts on what you've observed. No, there is nothing in NFPA 13D regarding hangers for sprinkler system piping not being allowed to be used for non-system components, as there is in -13.  As I

RE: NFPA 13D

2020-03-27 Thread Greg McGahan via Sprinklerforum
Farrington Road Milton, FL 32583 O- 850-637-8535 C- 850-712-9555 From: Tom Noble via Sprinklerforum Sent: Friday, March 27, 2020 4:21 PM To: sprinklerforum@lists.firesprinkler.org Cc: Tom Noble Subject: Re: NFPA 13D Tom, Correct, I cannot find anything in the standard that addresses you issue.  Tom

RE: NFPA 13D

2020-03-27 Thread Tim Stone via Sprinklerforum
: (802) 434-2968 tston...@comcast.net <mailto:tston...@comcast.net> From: Sprinklerforum On Behalf Of Greg McGahan via Sprinklerforum Sent: Friday, March 27, 2020 5:07 PM To: sprinklerforum@lists.firesprinkler.org Cc: Greg McGahan Subject: RE: NFPA 13D What abo

RE: NFPA 13D

2020-03-27 Thread Tim Stone via Sprinklerforum
Tom, Refer to NFPA 13, 9.1.1 Shared support between trades. Might help you. I believe the larger issue is the HVAC insulation resting against the CPVC pipe. Is there a compatibility issue? Regards, G. Tim Stone G. Tim Stone Consulting, LLC NICET Level III Engineering Technician

Re: NFPA 13D

2020-03-27 Thread Tom Noble via Sprinklerforum
Tom, Correct, I cannot find anything in the standard that addresses you issue. Tom Noble CET, CFPS, CWBSP Technical Programs Specialist American Fire Sprinkler Association p: 214-349-5965 ext125 w: firesprinkler.org — Learn fire sprink

Re: NFPA 13D

2020-03-27 Thread Tom Wellen via Sprinklerforum
Are all the respondents politicians? Politicians sidestep the original question, fail to answer, distract into another direction. Regarding NFPA 13D, it's silent on sprinkler piping or hangers shall not be used to support non-system components. I'm looking for a confirmation that is a true stateme

RE: NFPA 13D

2020-03-27 Thread Tom Duross via Sprinklerforum
Look here they drilled the joists. From: Sprinklerforum On Behalf Of Travis Mack via Sprinklerforum Sent: Friday, March 27, 2020 4:55 PM To: sprinklerforum@lists.firesprinkler.org Cc: Travis Mack ; cl...@fire-design.com Subject: Re: NFPA 13D I’d be more concerned that the straps are not

Re: NFPA 13D

2020-03-27 Thread Travis Mack via Sprinklerforum
I’d be more concerned that the straps are not compatible with the cpvc. I agree it was lazy on the part of the hvac installer. Travis Mack, CFPS, CWBSP, RME-G, SET 480-505-9271 x700 MFP Design, LLC www.mfpdesign,com Send large files to MFP Design via: https://www.hightail.com/u/MFPDesign Sent

Re: NFPA 13D

2020-03-27 Thread Tom Noble via Sprinklerforum
What about the potential compatibility issues with the duct touching the CPVC pipe? Could you hang your hat on there? Could one defer to the installation instructions as they take precedence? > On Mar 27, 2020, at 3:35 PM, Tom Wellen via Sprinklerforum > wrote: > > HVAC duct was found being s

RE: NFPA 13D

2020-03-27 Thread cliff--- via Sprinklerforum
Tom, How much weight do you think a piece of flex duct for residential is going to apply to the pipe? It looks like the bracket for the diffuser is only about a foot away and has 4 screws holding it. I don’t think that is the same as a piece of sheet metal duct being supported by sprinkler

RE: NFPA 13D

2020-03-27 Thread Eric Hendrix via Sprinklerforum
That is sheer laziness by HVAC sub. The extra weight is not calculated in the support formula in NFPA chapter 9 (2016 and earlier). Thanks, Eric Hendrix Design Manager [cid:image001.jpg@01D6044E.276503A0] 124 Enterprise Drive | Madison, MS 39110 O: 601.898.9385 | C: 601-826-9071 [Image result

RE: NFPA 13D (13ed) exposed basements

2019-06-12 Thread Dewayne Martinez
I should note that the basement compartment is larger than 600 sq ft and the span of the TJI’s are over 20ft. Dewayne Martinez Fire Protection Design Manager *TOTAL* *Mechanical* *Building* *Integrity* W234 N2830 Paul Rd. Pewaukee, WI 53072 dmarti...@total-mechanical.com Ph: 262-522-7

Re: NFPA 13D - Adding 5 gpm Domestic Flow in Calculations

2017-08-18 Thread kmick44426
Hi we flow switch and relay to isolate the sprinkler if there is a demand -Original Message- From: Travis Mack To: sprinklerforum Sent: Fri, Aug 18, 2017 11:16 am Subject: Re: NFPA 13D - Adding 5 gpm Domestic Flow in Calculations Yes. We do have some authorities that mandate it

Re: NFPA 13D - Adding 5 gpm Domestic Flow in Calculations

2017-08-18 Thread Travis Mack
Yes. We do have some authorities that mandate it. But it is still above the minimum requirements of 13D. I always thought it was odd. But there are many things some authorities require that I feel are odd. Ha ha. Travis Mack, SET MFP Design, LLC "Follow" us on Facebook: https://www.facebook.

Re: NFPA 13D - Adding 5 gpm Domestic Flow in Calculations

2017-08-18 Thread Parsley Consulting
I believe the mandate for a 5 gpm addition for domestic demand was added for single family homes by some jurisdictions as a rule of thumb quite some time back. And, to put a fine point on it, Owen, it's state law in California, so yes you certainly _*are*_ required to add 5 gpm flow for domest

Re: NFPA 13D - Adding 5 gpm Domestic Flow in Calculations

2017-08-17 Thread Travis Mack
Correct. That seems to be a fallacy that people locked on to long ago and never let go of. NFPA 13D is for one and two family dwellings. For a single family home it is not required. If you are doing a duplex (a two family dwelling) then you add the demand. Travis Mack, SET MFP Design, LLC "F

RE: NFPA 13D Water Supplies

2013-12-06 Thread Tom Duross
Dude, I believe every tank system has refill whether off another pump and tank, or traditional domestic. We do pumps and tanks all over Boston (13D up to 3 family but 20 minute supply per Maurice P.) mainly because the purveyors are so expensive with permits, bonds, tap fees and pipe rentals that

RE: NFPA 13D or 13? Full Circle?

2013-12-06 Thread Brad Casterline
That does sound good Tom, thanks for the info. -Original Message- From: Tom Duross [mailto:tduro...@comcast.net] Sent: Friday, December 06, 2013 4:38 PM To: sprinklerforum@lists.firesprinkler.org Subject: RE: NFPA 13D or 13? Full Circle? I actually did a 13D system with one of those

RE: NFPA 13D or 13? Full Circle?

2013-12-06 Thread Tom Duross
I actually did a 13D system with one of those tanks Potter used to make. Spun fiberglass, wasn't heavy, beautiful design. Nitrogen from a 2K# tank into the top and water out the bottom. Even the panel that came with it had built in 9V battery backup. Something happened with whomever was making the

RE: NFPA 13D or 13? Full Circle?

2013-12-06 Thread Brad Casterline
makes sense Todd ! , thanks. -Original Message- From: Todd Williams [mailto:t...@fpdc.com] Sent: Friday, December 06, 2013 9:14 AM To: sprinklerforum@lists.firesprinkler.org Subject: Re: NFPA 13D or 13? Full Circle? Brad, It is great in theory but not in practice. Pressure vessels tend

Re: NFPA 13D or 13?

2013-12-06 Thread rongreenman .
And the ignorant among us, myself included, learned something. Since IRC 2012 was just recently was adopted in Washington this is critical for me to know. Thanks. On Fri, Dec 6, 2013 at 5:30 AM, Richard Mote wrote: > My thanks to everyone for their input. Bottom line the AHJ was right. Per > 201

Re: NFPA 13D or 13? Full Circle?

2013-12-06 Thread Todd Williams
roved automatic water supply? > It seems like the project of this thread would be ideal. > > -Original Message- > From: Tom Duross [mailto:tduro...@comcast.net] > Sent: Thursday, December 05, 2013 7:36 PM > To: sprinklerforum@lists.firesprinkler.org > Subject: RE: NFPA 13D

RE: NFPA 13D or 13? Full Circle?

2013-12-06 Thread Brad Casterline
PM To: sprinklerforum@lists.firesprinkler.org Subject: RE: NFPA 13D or 13? Full Circle? For the few 13D systems I've done with pumps and tanks, I've always been leery of the Basement systems. Whether CPVC and QR pendents (for 'future' sheetrock) or standard exposed steel with S

RE: NFPA 13D or 13?

2013-12-06 Thread Richard Mote
My thanks to everyone for their input. Bottom line the AHJ was right. Per 2012 IRC if you use non dimensional joists in basements you put in sprinklers, fire proofing, or gyp board. I think when they see the price for 2, 300 gallon tanks, pump, piping and sprinklers they will opt for gyp board.

Re: NFPA 13D or 13? Full Circle?

2013-12-05 Thread rongreenman .
As I understand it the UL test protocol for 13D has three heads in a compartment. The walls are surrounded with Ikea furniture, so solidified gasoline and kindling, along with drapes and all the trimmings of a living room. The fire is started and heads have to pop within a certain time frame. Two

RE: NFPA 13D or 13? Full Circle?

2013-12-05 Thread Tom Duross
For the few 13D systems I've done with pumps and tanks, I've always been leery of the Basement systems. Whether CPVC and QR pendents (for 'future' sheetrock) or standard exposed steel with SR or QR uprights (or pendents), I've wondered how they get away with 2 head calcs. The basements are open

Re: NFPA 13D or 13? Full Circle?

2013-12-05 Thread rongreenman .
NG INT'L. Ltd. > Santa Fe, New Mexico USA > (800) 503.1961 nationwide > > > -Original Message- > From: Ben Young > To: sprinklerforum > Sent: Thu, Dec 5, 2013 3:09 pm > Subject: Re: NFPA 13D or 13? > > > Its in the PA UCC, which he's operating under. It w

Re: NFPA 13D or 13?

2013-12-05 Thread Ed Vining
Ask the AHJ, but ask him also where the requirement comes from. He may be thinking of his building code requirement for sprinklering basements. Unless the world has changed, single family residences were exempted from the requirement. On Thu, Dec 5, 2013 at 12:15 PM, Todd Letterman wrote: > Wow

Re: NFPA 13D or 13? Full Circle?

2013-12-05 Thread accentfire
Founder ACCENT FIRE ENGINEERING INT'L. Ltd. Santa Fe, New Mexico USA (800) 503.1961 nationwide -Original Message- From: Ben Young To: sprinklerforum Sent: Thu, Dec 5, 2013 3:09 pm Subject: Re: NFPA 13D or 13? Its in the PA UCC, which he's operating under. It was added to the

RE: NFPA 13D or 13?

2013-12-05 Thread Taylor, Galen
05, 2013 3:05 PM To: sprinklerforum@lists.firesprinkler.org Subject: RE: NFPA 13D or 13? This was forwarded to me by a colleague off forum. Looks like paragraph 1 is where it is required. And paragraph IV is where it exempts dimensional lumber greater than 2 x 10. Looks like it came in with the

Re: NFPA 13D or 13?

2013-12-05 Thread Roland Huggins
Concessions on light weight construction went along with required sprinkler protection. Now remove the required sprinkler protection but retain the light weight construction. It's not just having to go down through the upward moving heat/fire but the floors fail most rickety tick. Roland Rol

RE: NFPA 13D or 13?

2013-12-05 Thread Cahill, Christopher
100 Best Companies to Work For *Registered in: MN -Original Message- From: sprinklerforum-boun...@lists.firesprinkler.org [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of rongreenman . Sent: Thursday, December 05, 2013 4:50 PM To: sprinklerforum@lists.firesprinkler.org

RE: NFPA 13D or 13?

2013-12-05 Thread Richard Mote
...@lists.firesprinkler.org] On Behalf Of rongreenman . Sent: Thursday, December 05, 2013 5:50 PM To: sprinklerforum@lists.firesprinkler.org Subject: Re: NFPA 13D or 13? I think this guy's concern is to fighting fires and firefighter safety regarding floor collapse. On the one hand I can&#x

Re: NFPA 13D or 13?

2013-12-05 Thread rongreenman .
ent: Thursday, December 05, 2013 5:09 PM > To: sprinklerforum@lists.firesprinkler.org > Subject: Re: NFPA 13D or 13? > > Its in the PA UCC, which he's operating under. It was added to the 2009 > edition after they took out the residential sprinkler requirement. > > Its also now

RE: NFPA 13D or 13?

2013-12-05 Thread Richard Mote
-boun...@lists.firesprinkler.org [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Ben Young Sent: Thursday, December 05, 2013 5:09 PM To: sprinklerforum@lists.firesprinkler.org Subject: Re: NFPA 13D or 13? Its in the PA UCC, which he's operating under. It was added t

RE: NFPA 13D or 13?

2013-12-05 Thread Taylor, Galen
klerforum-boun...@lists.firesprinkler.org [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Richard Mote Sent: Thursday, December 05, 2013 1:41 PM To: sprinklerforum@lists.firesprinkler.org Subject: RE: NFPA 13D or 13? In re reading my earlier posts I may have missta

Re: NFPA 13D or 13?

2013-12-05 Thread Ben Young
Its in the PA UCC, which he's operating under. It was added to the 2009 edition after they took out the residential sprinkler requirement. Its also now included in the 2012 edition of the IRC. We prefer to not call it a sprinkler system, but as a fire rating equivalency. Richard, I remember Geo

RE: NFPA 13D or 13?

2013-12-05 Thread Richard Mote
2013 4:21 PM To: sprinklerforum@lists.firesprinkler.org Subject: RE: NFPA 13D or 13? Richard, As an AHJ I thought I understood what your AHJ was asking. I was even preparing a cogent explanation to help you understand; but then you posted this comment about how the AHJ is asking for sprinklers beca

RE: NFPA 13D or 13?

2013-12-05 Thread Taylor, Galen
13 12:40 PM To: sprinklerforum@lists.firesprinkler.org Subject: RE: NFPA 13D or 13? The AHJ is telling the builder that if they had used conventional framing IE, 2"x12" @ 16 oc there would not be an issue. He says that the TJI's will burn faster than conventional framing therefore he wants them protec

RE: NFPA 13D or 13?

2013-12-05 Thread Brad Casterline
How about a Pressure Tank instead of Tank and Pump? -Original Message- From: Richard Mote [mailto:rich...@rowesprinkler.com] Sent: Thursday, December 05, 2013 3:07 PM To: sprinklerforum@lists.firesprinkler.org Subject: RE: NFPA 13D or 13? I don't want to spend a lot of time on

RE: NFPA 13D or 13?

2013-12-05 Thread David Autry
...@mfp-inc.com -Original Message- From: sprinklerforum-boun...@lists.firesprinkler.org [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Cahill, Christopher Sent: Thursday, December 05, 2013 3:00 PM To: sprinklerforum@lists.firesprinkler.org Subject: RE: NFPA 13D or

RE: NFPA 13D or 13?

2013-12-05 Thread Richard Mote
inkler.org [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Ben Young Sent: Thursday, December 05, 2013 4:02 PM To: sprinklerforum@lists.firesprinkler.org Subject: RE: NFPA 13D or 13? You use residential pendants and cpvc if within the listing. You can use the pendants because the owner may one day

RE: NFPA 13D or 13?

2013-12-05 Thread Ben Young
570-837-7647 > F 570-837-6335 > > -Original Message- > From: sprinklerforum-boun...@lists.firesprinkler.org [mailto: > sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Ben Young > Sent: Thursday, December 05, 2013 3:41 PM > To: sprinklerforum@lists.firesprinkler.org &g

RE: NFPA 13D or 13?

2013-12-05 Thread Cahill, Christopher
---Original Message- From: sprinklerforum-boun...@lists.firesprinkler.org [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Richard Mote Sent: Thursday, December 05, 2013 2:40 PM To: sprinklerforum@lists.firesprinkler.org Subject: RE: NFPA 13D or 13? The AHJ is telling the

RE: NFPA 13D or 13?

2013-12-05 Thread Richard Mote
ssage- From: sprinklerforum-boun...@lists.firesprinkler.org [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Ben Young Sent: Thursday, December 05, 2013 3:41 PM To: sprinklerforum@lists.firesprinkler.org Subject: RE: NFPA 13D or 13? Yes, you do it per 13d. Also check out the 2012 ver

RE: NFPA 13D or 13?

2013-12-05 Thread Steve Leyton
: sprinklerforum@lists.firesprinkler.org Subject: RE: NFPA 13D or 13? In NFPA-1 Section 13.3.2.2 requires that Basements exceeding 2500 ft2 (232 m2) in new buildings shall be protected throughout by an approved automatic sprinkler system. Thanks Inspector Joe Triolo Hudson Fire Prevention -Original

RE: NFPA 13D or 13?

2013-12-05 Thread David Autry
...@lists.firesprinkler.org] On Behalf Of Richard Mote Sent: Thursday, December 05, 2013 2:40 PM To: sprinklerforum@lists.firesprinkler.org Subject: RE: NFPA 13D or 13? The AHJ is telling the builder that if they had used conventional framing IE, 2"x12" @ 16 oc there would not be an issue. He says that

Re: NFPA 13D or 13? RETORT

2013-12-05 Thread accentfire
Ladies/Gents: 'Site' unseen - I would look at it as 13'D'/two-sprinkler design...This would be predicated, however, on what the basement is likely to have in it - Normal residential setting OR storage of tires, combustible liquids, heavy fuel loading encroaching on OH-2?? With potential invest

RE: NFPA 13D or 13?

2013-12-05 Thread Ben Young
esprinkler.org [mailto: > sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Travis Mack > Sent: Thursday, December 05, 2013 3:33 PM > To: sprinklerforum@lists.firesprinkler.org > Subject: Re: NFPA 13D or 13? > > Does NFPA 1 apply to a single family residence? > &g

RE: NFPA 13D or 13?

2013-12-05 Thread Richard Mote
Sent: Thursday, December 05, 2013 3:35 PM To: sprinklerforum@lists.firesprinkler.org Subject: RE: NFPA 13D or 13? It seems like it would be massive overkill to design this per 13, so I'd do the design for 13D. It might be prudent to ask the AHJ for his opinion since he seems to modifying the rules

RE: NFPA 13D or 13?

2013-12-05 Thread Triolo, Joe
@lists.firesprinkler.org Subject: Re: NFPA 13D or 13? Does NFPA 1 apply to a single family residence? Travis Mack, SET MFP Design, LLC 2508 E Lodgepole Drive Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 email:tm...@mfpdesign.com On 12/5/2013 1:31 PM, Triolo, Joe wrote: > In NFPA-1 Sect

RE: NFPA 13D or 13?

2013-12-05 Thread Sprinkler Design Services
It seems like it would be massive overkill to design this per 13, so I'd do the design for 13D. It might be prudent to ask the AHJ for his opinion since he seems to modifying the rules at his fancy. Marc Walter, SET Sprinkler Design Services Seaside, OR 97138 (503) 956-4019 -Original Message-

Re: NFPA 13D or 13?

2013-12-05 Thread Travis Mack
Of Todd Letterman Sent: Thursday, December 05, 2013 3:15 PM To: sprinklerforum@lists.firesprinkler.org Cc: sprinklerforum@lists.firesprinkler.org Subject: Re: NFPA 13D or 13? Wow! So much for life safety? Does the AHJ have a reason for this? Sent from my iPad On Dec 5, 2013, at 12:11 PM

RE: NFPA 13D or 13?

2013-12-05 Thread Matsuda, Richard
to smaller sections. rick matsuda city of dallas -Original Message- From: sprinklerforum-boun...@lists.firesprinkler.org [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Richard Mote Sent: Thursday, December 05, 2013 2:24 PM To: sprinklerforum@lists.firesprinkler.org Su

RE: NFPA 13D or 13?

2013-12-05 Thread Triolo, Joe
...@lists.firesprinkler.org [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Todd Letterman Sent: Thursday, December 05, 2013 3:15 PM To: sprinklerforum@lists.firesprinkler.org Cc: sprinklerforum@lists.firesprinkler.org Subject: Re: NFPA 13D or 13? Wow! So much for life safety? Does the AHJ have

RE: NFPA 13D or 13?

2013-12-05 Thread Richard Mote
:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Todd Letterman Sent: Thursday, December 05, 2013 3:15 PM To: sprinklerforum@lists.firesprinkler.org Cc: sprinklerforum@lists.firesprinkler.org Subject: Re: NFPA 13D or 13? Wow! So much for life safety? Does the AHJ have a reason for this

Re: NFPA 13D or 13?

2013-12-05 Thread rongreenman .
And I suppose the requirement is based on limited egress for the small army of illegal immigrant workers toiling away in the potential basement sweatshop. As Chris said when they start making things up nothing we say has any more significance than their own magic does. On Thu, Dec 5, 2013 at 12:1

RE: NFPA 13D or 13?

2013-12-05 Thread Cahill, Christopher
Since the AHJ is seemingly making thing up any advice you get here would be worthless. This is a question for the AHJ. If it's a single family home 13D seems applicable. I'd say once have to do the basement seems like the investment is already there and do the whole house 13D for not much mor

Re: NFPA 13D or 13?

2013-12-05 Thread Todd Letterman
Wow! So much for life safety? Does the AHJ have a reason for this? Sent from my iPad > On Dec 5, 2013, at 12:11 PM, "Richard Mote" wrote: > > I guess I will have to show my ignorance, I can count on one hand the number > of 13D systems I have designed in the last 10 years. This project is a 13

Re: NFPA 13D - Irregular shaped closet

2011-05-20 Thread Todd Williams
Greg, I ran into this on a 13R system a couple of years ago. The closet was abut the same size. We ended up putting one in because we could not find an exception and didn't want to deal with any liability issues. Agreed that this is stupid and something the Committee should consider. (such as