Re: Response times to system deficiencies

2013-05-13 Thread John Drucker
The NJ Uniform Fire Code at NJAC 5:70-2.16(5) stipulates a time frame of 24 hours for inadequate fire protection system as an imminent hazard. However the fire official has the authority to take immediate measures such as evacuation. in two recent situations fire department pumpers were placed

RE: Back flush FDC

2013-05-13 Thread Ford, Charles
Thanks, Ron. That's the answer I was looking for. There did seem to be a great deal of silence from the forum. C. Burton Ford NICET Certified IV NFPA Certified Fire Protection Specialist Cintas Fire Protection Inc 1038 Conshohocken Rd Conshohocken, PA 19428 Tel 610-233-1400 Fax 610-233-1401

Re: Back flush FDC

2013-05-13 Thread Ron Greenman
Now that I'm with my stuff, a cursory check of every edition back to the first (1992) and nothing about a five year back flushing. I think we're into one of those things thought up at soem Fire Marshals' meeting and has become considered gospel. You always hear, It's in the Constitution, when it's

Re: Back flush FDC

2013-05-13 Thread Tom
Check the philadephia fire code, when I. used to Do inspections in phila. About 11 yrs ago it was Required on every annual. You had to backflush The fdc and open and operate the fdc check Sent from my Verizon Wireless 4G LTE smartphone Ron Greenman rongreen...@gmail.com wrote: Now that I'm

NFPA 13: 11.1.2 (separation between hazards)

2013-05-13 Thread Ralphy Henderson
(NFPA 13: 11.1.2 - 2013 ed) I have a situation where there is a 12 ft. opening leading from one hazard area to another but the opening has an 18 steel wide flange beam running along it. I'm wondering if this 18 beam would suffice to adequately contain the heat in the separate areas since NFPA

Sizing tanks with hydrants?

2013-05-13 Thread Bobby Gillett
When sizing a water storage tank feeding a fire pump for a new facility with multiple sprinkler systems and fire hydrants, do you have to include any type of allowance for the hydrants? The tank will be the sole source of supply for all (rural area). There will be no hose stations or standpipes,

RE: Sizing tanks with hydrants?

2013-05-13 Thread Steve Leyton
Omigosh, yes. Have you checked the fire code requirement for fire flow yet? Required flow x reduction factor for sprinklers x duration in hours = reserve volume. What size and construction type is the building and what reduction will the serving fire department offer for sprinklers? 50% is

Re: Sizing tanks with hydrants?

2013-05-13 Thread Travis Mack
Yeah, you are looking at possibly a 180,000 gallon tank or bigger if you are supposed to take care of site fire flow. Travis Mack, SET MFP Design, LLC 2508 E Lodgepole Drive Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 email:tm...@mfpdesign.com On 5/13/2013 10:23 AM, Steve Leyton wrote:

RE: Sizing tanks with hydrants?

2013-05-13 Thread Jack Carlson
Yes - Tank serves sprinklers and hydrants NFPA 13 2010 edition Figure 11.2.3.1.1 .20/1500 Table 11.2.3.1.2250 hose for 60 minutes min (assume remote supervision) Jack W. Carlson, SET Triple A Fire Protection Office - 251.649.2034 Fax - 251.649.2037 Cell - 706.247.5050

RE: Warehouse protection

2013-05-13 Thread Art Tiroly
I need some history on warehouse protection requirements. When was high piled storage protection with hydraulic calculations required? That was covered in NFPA 231 back then. The problem is a 22 ft high building with a 1975 - 130 SF pipe schedule system and a 45 psi water supply for class 3 and

Re: NFPA 13: 11.1.2 (separation between hazards)

2013-05-13 Thread Ron Greenman
I don't think so. If you have two separate hazard classes you'd need to extend the higher into the lower the requisite number of feet (I have 16 in my head but I'm not trusting memory) and to both sides. On Mon, May 13, 2013 at 9:06 AM, Ralphy Henderson ralphbuccan...@yahoo.comwrote: (NFPA 13:

RE: Sizing tanks with hydrants?

2013-05-13 Thread Steve Leyton
That's only part of it: you size the tank for the greater of (sprinklers + HSA) or the fire flow demand, whichever is greater when calculated as flow x duration. Steve L. -Original Message- From: sprinklerforum-boun...@lists.firesprinkler.org

Re: Sizing tanks with hydrants?

2013-05-13 Thread Ron Greenman
Jack, I don't think you need to allow hose stream for this, but as mentioned you have to add fire flow per IFC, with whatever reduction for sprinklers the Fire Marshal allows. On Mon, May 13, 2013 at 10:30 AM, Jack Carlson ja...@aaafp.com wrote: Yes - Tank serves sprinklers and hydrants

RE: Warehouse protection

2013-05-13 Thread David Autry
1980 231C has it. David Autry Meininger Fire Protection Inc. 2521 W L St. Suite No.4 Lincoln, Ne 68522 Voice (402) 466-2616 Fax (402) 466-2617 da...@mfp-inc.com -Original Message- From: sprinklerforum-boun...@lists.firesprinkler.org

Re: Sizing tanks with hydrants?

2013-05-13 Thread Ron Greenman
Won't fire flow always exceed sprinkies and hose allowance? On Mon, May 13, 2013 at 10:35 AM, Steve Leyton st...@protectiondesign.comwrote: That's only part of it: you size the tank for the greater of (sprinklers + HSA) or the fire flow demand, whichever is greater when calculated as flow x

RE: Warehouse protection

2013-05-13 Thread Scott A Futrell
231C goes back to 1971, but the real question is what did the building or fire code require? Scott   (763) 425-1001 Office (612) 759-5556 Cell -Original Message- From: sprinklerforum-boun...@lists.firesprinkler.org [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of

RE: Sizing tanks with hydrants?

2013-05-13 Thread Steve Leyton
Still not semantically correct. You don't have to proved fire flow and sprinkler demand concurrently. Sprinkler demand is calculated as (sprinkler design area + hose stream allowance) x duration. Fire flow is just fire flow. You determine the most demanding and the water supply volume has to

RE: Sizing tanks with hydrants?

2013-05-13 Thread Steve Leyton
Usually. The only real-world exception that comes to mind would be if you a relatively small building of fire resistive construction and a very demanding sprinkler system such as for H-occupancies or really demanding storage. I could see a situation where you had a 2,000gpm-or-less fire flow

RE: Warehouse protection

2013-05-13 Thread Art Tiroly
I think it dates back to mid 70's. Arthur Tiroly ATCO Fire Protection Design -Original Message- From: sprinklerforum-boun...@lists.firesprinkler.org [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of David Autry Sent: Monday, May 13, 2013 1:36 PM To:

RE: Sizing tanks with hydrants?

2013-05-13 Thread Craig.Prahl
One BIG thing that is often overlooked is the Code requirement for Fire Flow. The IFC talks about determining fire flow by an approved method. Jurisdictions vary in the approach they may or may not take in determining fire flow. Appendix B of the IFC is fairly common, however there are

RE: Sizing tanks with hydrants?

2013-05-13 Thread Art Tiroly
The building will never be used for high piled storage right? Arthur Tiroly ATCO Fire Protection Design Tiroly and Associates 24400 Highland Rd rm 25, CLE 44143 216-621-8899 216-570-7030 Cell WWW.ATCOfirepro.com -Original Message- From: sprinklerforum-boun...@lists.firesprinkler.org

RE: NFPA 13: 11.1.2 (separation between hazards)

2013-05-13 Thread Craig.Prahl
A barrier for separation is a wall, not just a beam. Craig L. Prahl, CET Fire Protection CH2MHILL Lockwood Greene 1500 International Drive Spartanburg, SC  29304-0491 Direct - 864.599.4102 Fax - 864.599.8439 CH2MHILL Extension 74102 craig.pr...@ch2m.com -Original Message- From:

Re: NFPA 13: 11.1.2 (separation between hazards)

2013-05-13 Thread Ralphy Henderson
It's 15 feet - but only if you don't have a barrier between areas able to contain the heat from one area into the other. The 18 beam is essentially a lintel between these areas. - Original Message - From: Ron Greenman rongreen...@gmail.com To: sprinklerforum@lists.firesprinkler.org

Extra Hazard storage

2013-05-13 Thread Craig Leadbetter
Can an extra hazard storage facility be protected by a gas system or dry chemical system? -- Craig Leadbetter Safeguard of Marquette PO Box 116 Marquette, MI 49855 (O) 906-475-9955 (F) 906-475-5474 (C) 906-362-5393 craigleadbet...@gmail.com ___

Re: NFPA 13: 11.1.2 (separation between hazards)

2013-05-13 Thread Ralphy Henderson
But it doesn't say a wall... it says a barrier or partition capable of delaying heat. Isn't the intent to basically have a compartment capable of containing the heat in one area and ensuring only the sprinklers in the compartment operate? In dealing w/ compartments it is acceptable to have

RE: Sizing tanks with hydrants?

2013-05-13 Thread Bobby Gillett
No. This is a tech school. Bobby Gillett Sr. Project Manager Key Fire Protection, Inc. (731) 424-0130 office (731) 424-9285 fax (731) 267-4853 cell www.keyfireprotection.com -Original Message- From: sprinklerforum-boun...@lists.firesprinkler.org

RE: Sizing tanks with hydrants?

2013-05-13 Thread Johnson, Duane (NIH/OD/ORS) [C]
NFPA 1:18.4.1* Scope. A.18.4.1 Section 18.4 and the associated tables are only applicable for determining minimum water supplies for manual fire suppression efforts. Water supplies for fire protection systems are not addressed by this section. It is not the intent to add the minimum fire

RE: Sizing tanks with hydrants?

2013-05-13 Thread Johnson, Duane (NIH/OD/ORS) [C]
Forgot this one: NFPA 1:18.4.5.2.1 Required fire flow shall be reduced by 75 percent when the building is protected throughout by an approved automatic sprinkler system. The resulting fire flow shall not be less than 1000 gpm (3785 L/min). Duane Johnson, PE Program Manager Division of the

RE: Sizing tanks with hydrants?

2013-05-13 Thread Steve Leyton
But the IFC says that fire flow MAY be reduced up to 75% as approved by the Fire Official. Most jurisdictions that accept a reduction - at least out here in CA - offer 50%, but not 75%. I have dealt with fire departments that only offer 25% when certain more hazardous conditions exist, such as

RE: Extra Hazard storage

2013-05-13 Thread Craig.Prahl
Is it bigger than a breadbox? Dry chem. Is typically reserved for protecting areas inside equipment. Not occupied or potentially occupied spaces. For large areas there are so many problems with keeping the area tight to contain gas such as FM-200 that it would be virtually impossible.

RE: Sizing tanks with hydrants?

2013-05-13 Thread Johnson, Duane (NIH/OD/ORS) [C]
You are correct, it all depends on the applicable code and approved ammendments. NFPA 1: 18.4.5.2.1 Required fire flow shall be reduced by 75 percent when the building is protected throughout by an approved automatic sprinkler system. The resulting fire flow shall not be less than 1000 gpm

Re: Extra Hazard storage

2013-05-13 Thread Ron Greenman
Gas is also a one shot and it's over scenario. Even where gas is the primary protection for a piece of equipment (what it's designed for, hence the Special Hazards monicker) there's a sprinkler system in case 1. the gas system fails to extinguisher the fire altogether, 2. can't provide long term

RE: NFPA 13: 11.1.2 (separation between hazards)

2013-05-13 Thread Craig.Prahl
Can the combustion gases accumulate and migrate below the 18 beam into the adjacent space? Depending on fuel loading, very good possibility. A barrier or partition from floor to ceiling creates a physical separation. Look at the specific wording in A.11.1.2 where is talks about a wall or

Re: Extra Hazard storage

2013-05-13 Thread Craig Leadbetter
The project is a Class IC storage facility storing lampricide in 5 gallon containers with rack storage that is 2400 sqft. With a required .45/3000 plus 500 PGM for two hours the cost of the water supply is going to outweigh the cost of the building. The site is remote and there is no municipal

RE: Sizing tanks with hydrants?

2013-05-13 Thread Bobby Gillett
Thank you everyone. I was asking for another designer in our office; he asked me and I didn't have the quick answer. Bobby Gillett Sr. Project Manager Key Fire Protection, Inc. (731) 424-0130 office (731) 424-9285 fax (731) 267-4853 cell www.keyfireprotection.com -Original Message-

RE: Extra Hazard storage

2013-05-13 Thread Craig.Prahl
Make a call to the guys at Victaulic and look at the Vortex system. You may be able to offer it as an alternative design to traditional sprinklers to the AHJ. It takes very little water, can suppress high challenge fuel fires in open environments, doesn't require the same closure restrictions

Re: Extra Hazard storage

2013-05-13 Thread Craig Leadbetter
I will give them a call. It might be an option I hadn't thought about this system. thanks On Mon, May 13, 2013 at 2:31 PM, craig.pr...@ch2m.com wrote: Make a call to the guys at Victaulic and look at the Vortex system. You may be able to offer it as an alternative design to traditional

RE: Extra Hazard storage

2013-05-13 Thread Art Tiroly
A foam/water system could reduce the water supply required. I had very good success with Compressed air foam. This greatly reduced water supply required. Arthur Tiroly ATCO Fire Protection Design Tiroly and Associates 24400 Highland Rd rm 25, CLE 44143 216-621-8899 216-570-7030 Cell

Re: Extra Hazard storage

2013-05-13 Thread Craig Leadbetter
Art, A foam system was acceptable per spec. Which manufacturer would I look at for the system that you have used. On Mon, May 13, 2013 at 2:39 PM, Art Tiroly atir...@atcofirepro.com wrote: A foam/water system could reduce the water supply required. I had very good success with Compressed

RE: Extra Hazard storage

2013-05-13 Thread Scott A Futrell
Hmmm...back to the fire code and building code first. Is it required to be sprinklered? Has the architect taken any advantages to area, height, separation, etc., based upon sprinklers? If so, gas or dry chem. don't substitute for required sprinklers... Scott   (763) 425-1001 Office (612)

Re: Extra Hazard storage

2013-05-13 Thread Craig Leadbetter
Scott, Unfortunately this is a design build project government project and the whole spec is about 60 pages and the fire protection spec is limited in the requirements except to meet code, although they did mention the classification of the storage and the 13 gpm well that is on site for our use

RE: Extra Hazard storage

2013-05-13 Thread Craig.Prahl
Craig, You said the building was storing a Lampricide. For exterminating/controlling Lamprey? Do you have an MSDS on the actual product being stored? Craig L. Prahl, CET Fire Protection CH2MHILL Lockwood Greene 1500 International Drive Spartanburg, SC  29304-0491 Direct - 864.599.4102 Fax

RE: Extra Hazard storage

2013-05-13 Thread Art Tiroly
Viking Fire Flex makes ICAF deluge systems. All open nozzles. You might use AFFF foam water closed head at a suitable density. Arthur Tiroly ATCO Fire Protection Design Tiroly and Associates 24400 Highland Rd rm 25, CLE 44143 216-621-8899 216-570-7030 Cell WWW.ATCOfirepro.com -Original

Forward Flow Testing of BFP's

2013-05-13 Thread Ralphy Henderson
I have an 8 riser with BFP with a system demand of 1500 gpm. I was going to provide a test header consisting of (6) 2 1/2 hose valves for the forward flow testing of the backflow preventor but then starting wondering if there were any other means or devices out there that could achieve the

RE: NFPA 13: 11.1.2 (separation between hazards)

2013-05-13 Thread Johnson, Duane (NIH/OD/ORS) [C]
NFPA 13:3.3.24 Thermal Barrier. A material that limits the average temperature rise of the unexposed surface to not more than 250°F (139°C) above ambient for a specified fire exposure duration using the standard time-temperature curve of ASTM E 119, Standard Test Methods for Fire Tests of

Exposed threads

2013-05-13 Thread Andy
I was told that bolts on a fire pump must have 3 threads showing on the bolt side I complied and then was told I must have 5 exposed threads because it will operate above 150 PSI I complied but I did ask were to find that. I love code trivia I was told its some were in the ASME codes that are

RE: Exposed threads

2013-05-13 Thread John O'Connor
Andy, I have never seen anything in writing about the number of exposed threads of a bolt thru the nut. However, I used to be an aircraft mechanic in the Navy, and we had a rule of two exposed threads. We lived by that rule, where it came from we never questioned. It worked in conditions of

Re: Exposed threads

2013-05-13 Thread Roland Huggins
Just like the velocity limit of 32ft/s rule. Never was valid but often enforced with great zeal. Roland Roland Huggins, PE - VP Engineering American Fire Sprinkler Assn. --- Fire Sprinklers Saves Lives Dallas, TX http://www.firesprinkler.org On May 13, 2013, at 1:34 PM, John

Re: Exposed threads

2013-05-13 Thread Andy
He is good natured FM I don't have a problem complying, but I did offer him 50 bucks for copy of the code. Thank you, Andy Johnston On May 13, 2013, at 4:34 PM, John O'Connor jocon...@nfspk.com wrote: Andy, I have never seen anything in writing about the number of exposed threads of a

RE: Exposed threads

2013-05-13 Thread Jamey Prentice
Never seen it applied to an NFPA document, but I have heard referenced a document called DIN 78 EN-Bolt end protrusions? Jamey -Original Message- From: sprinklerforum-boun...@lists.firesprinkler.org [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Andy Sent: Monday,

Re: Forward Flow Testing of BFP's

2013-05-13 Thread Roland Huggins
The latest issue of Sprinkler Age has an article addressing how to calculate the flow for exercising the BFP. You certainly don't need six 2-1/2 hose valves. Approximately what pressure do you have at the riser when flowing the system demand (without hose demand unless you have INSIDE hose

Re: NFPA 13: 11.1.2 (separation between hazards)

2013-05-13 Thread Roland Huggins
By definition, a lintel is a header above an opening in a wall. If a beam would suffice, a room with a beam is would be two compartments. We reasonable assume that a fuel package is not placed within a doorway (aka under the lintel). Roland Roland Huggins, PE - VP Engineering American Fire

RE: Forward Flow Testing of BFP's

2013-05-13 Thread Art Tiroly
A 4 pipe 40 long with a shutoff valve should flow 1500 gpm and provide a smooth flow to pitot. Arthur Tiroly ATCO Fire Protection Design Tiroly and Associates 24400 Highland Rd rm 25, CLE 44143 216-621-8899 216-570-7030 Cell WWW.ATCOfirepro.com -Original Message- From:

RE: NFPA 13: 11.1.2 (separation between hazards)

2013-05-13 Thread Steve Leyton
In traditional architectural terms a lintel is the piece between two vertical supports over a portal, so it could (and often is) used to describe the header span not only over doors but also windows. SML -Original Message- From: sprinklerforum-boun...@lists.firesprinkler.org

Re: Forward Flow Testing of BFP's

2013-05-13 Thread Ralphy Henderson
I have 68 psi at  1570 gpm... - Original Message - From: Roland Huggins rhugg...@firesprinkler.org To: sprinklerforum@lists.firesprinkler.org Cc: Sent: Monday, May 13, 2013 1:57 PM Subject: Re: Forward Flow Testing of BFP's The latest issue of Sprinkler Age has an article addressing

RE: Ah Yes.... Velocity....

2013-05-13 Thread Sprinkler Academy - C Bilbo
There was once a white paper that discussed Porches and Tractors when it came to Velocities... From: rhugg...@firesprinkler.org Subject: Re: Exposed threads Date: Mon, 13 May 2013 13:45:02 -0700 To: sprinklerforum@lists.firesprinkler.org Just like the velocity limit of 32ft/s rule.

Re: Ah Yes.... Velocity....

2013-05-13 Thread George Church
Written by one of those Terp FPEs, right? Sent from my iPhone On May 13, 2013, at 6:21 PM, Sprinkler Academy - C Bilbo prodesigngr...@msn.com wrote: There was once a white paper that discussed Porches and Tractors when it came to Velocities... From: rhugg...@firesprinkler.org

RE: Ah Yes.... Velocity....

2013-05-13 Thread MPhelps
Now that is a tease if I ever heard one. so spill it!! Mark at Aero -Original Message- From: sprinklerforum-boun...@lists.firesprinkler.org [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Sprinkler Academy - C Bilbo Sent: Monday, May 13, 2013 3:22 PM To:

RE: Forward Flow Testing of BFP's

2013-05-13 Thread John Drucker - Home
Forward Flow Testing of BFP's Flushing of FDC's Interesting how these two topics came up relatively in quick succession, and more interesting how you can achieve both (even though it's not in the constitution ;-) 1) Install Bypass Piping around the FDC Check 2) Install Storz Connections or

Re: Ah Yes.... Velocity....

2013-05-13 Thread Ron Greenman
My porch has no velocity. It just sits out front of the house. Sent from my iPhone On May 13, 2013, at 3:21 PM, Sprinkler Academy - C Bilbo prodesigngr...@msn.com wrote: There was once a white paper that discussed Porches and Tractors when it came to Velocities... From:

RE: Exposed threads

2013-05-13 Thread Phong - Indochine Engineering
One size of the nut thickness? Regards, Le Vu Phong Mobile:  +84 (0) 902 363 525   phong_indochineengineering -Original Message- From: sprinklerforum-boun...@lists.firesprinkler.org [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of John

RE: Ah Yes.... Velocity....

2013-05-13 Thread Sprinkler Academy - C Bilbo
I am guessing that somewhere on the AFSA website, there is a white paper that one Roland Huggins wrote some years ago about putting tractor tires on a PORSCHE (not front porch) it involved the idea of taking a design that was meant to do a very good job, and making it into something that

Re: Exposed threads

2013-05-13 Thread Andy
No just wants 3 threads showing if 150 PSI 5 threads if more. We normally use NBK that comes with the fittings. The are marked with the ANSI marks. Never had any work loose. Even on diesel pumps that do get run like the should. I have complied with his request. If it exist I would like to find

Re: Exposed threads

2013-05-13 Thread MPhelps
Try this one on for originality. The great City of Phoenix is set to amend the requirements of all the NFPA standards regarding FDC's. They will now require an industrial complex supplied by a fire pump taking suction from the city main, to have an FDC on the pump discharge and in addition, an

baffles

2013-05-13 Thread A.P.Silva
NFPA 13 requires baffles (between sprinklers) to be non-combustible or limited-combustible. The contractor has installed plexi-glass baffles, and claims that is what is normally used and has been approved on previous projects. Any comments? Tony ___