Re: Joining black carbon steel with stainless steel piping

2022-02-28 Thread John Denhardt via Sprinklerforum
gt; > Henry Fontana > Operations Manager (NYC) > Johnson Controls Fire Protection > 100 Lighting Way Secaucus, NJ 07094 > Cell: 201-210-9873 > henry.font...@jci.com > > > -Original Message- > From: Sprinklerforum On > Behalf Of John Denhardt via Spri

Fwd: Joining black carbon steel with stainless steel piping

2022-02-28 Thread John Denhardt via Sprinklerforum
I am not an expert on this topic. However, I was told the key was corrosion mainly occurs when water flows on a regular basis. With water flowing on a regular basis, corrosion becomes a larger concern. John August Denhardt, P.E. Vice-President Engineering and Technical Services American Fire

Re: [EXTERNAL] RE: INDOOR SPORTS FACILITY FIELD HOUSE

2022-02-07 Thread John Denhardt via Sprinklerforum
A NFPA 13 owner's certificate with additional clarifications and statements will assist the design professional and sprinkler designer to ensure the owner receives what he needs for the specific installation and provide a basis of design. Insist on a signed owner's certificate for all projects.

Re: Older copy of FMG 8-3

2022-01-27 Thread John Denhardt via Sprinklerforum
You have to appreciate this group of people on the forum. It is great to be part of the AFSA association and specifically this group! John John August Denhardt, P.E. Vice-President Engineering and Technical Services American Fire Sprinkler Association 301-343-1457 > On Jan 27, 2022, at 10:22

Re: UNUSED ATTIC DEFINITION

2022-01-15 Thread John Denhardt via Sprinklerforum
Following up on Bob's post. NFPA 13, the 2025 edition is now open for public input. My staff has been very active in reviewing the 2022 edition of NFPA 13 and other documents which are open for inputs. If any member needs assistance on submitting or developing public inputs, please contact our

Re: [EXTERNAL] Re: Food trucks inside a building

2022-01-14 Thread John Denhardt via Sprinklerforum
An ordinary hazard group 1 classification for a parking garage is most likely not appropriate for any modern garage. The 2022 edition of NFPA 13 annex has changed "parking garages" to an ordinary hazard group II classification and the technical committee had discussion on changing to extra hazard

Re: Need some help - Poz-lock Data sheets

2022-01-12 Thread John Denhardt via Sprinklerforum
What a great group of people. I have the information I was looking for already! Thanks, John John August Denhardt, PE *Vice President, Engineering and Technical Services* *American Fire Sprinkler Association* m: p: 301-343-1457 214-349-5965 ext 121 w: firesprinkler.org

Need some help - Poz-lock Data sheets

2022-01-12 Thread John Denhardt via Sprinklerforum
We are looking for data sheets on Poz-lock pipe and fittings. If anyone has these, please forward them to me at jdenha...@firesprinkler.org. We appreciate the assistance. Thanks, John John August Denhardt, PE *Vice President, Engineering and Technical Services* *American Fire Sprinkler

Re: Using Flex Head Connection from CPVV

2022-01-06 Thread John Denhardt via Sprinklerforum
My top of the head guess is that this would be allowed. I have never heard of any concerns or restrictions with this approach. *The above is my opinion and has not been processed as a formal interpretation in accordance with the NFPA Regulations Governing Committee Projects. This is provided

Re: Group of Pipe Obstruction

2021-12-16 Thread John Denhardt via Sprinklerforum
standing > underneath the piping group. > > > On Dec 16, 2021, at 1:59 PM, John Denhardt via Sprinklerforum < > sprinklerforum@lists.firesprinkler.org> wrote: > > > > NFPA 13 - 2019 - The answer depends on the hazard and the sprinkler type. > > ESFR a

Re: Group of Pipe Obstruction

2021-12-16 Thread John Denhardt via Sprinklerforum
NFPA 13 - 2019 - The answer depends on the hazard and the sprinkler type. ESFR and CMSA do have requirements that address this issue. For light and ordinary hazards, as long as the individual widths are 4' or less with some separation to allow water to hit the floor,and the sprinkler deflector is

Re: Fire Pump Shutdown

2021-11-22 Thread John Denhardt via Sprinklerforum
ent: Thursday, November 18, 2021 3:27 PM > To: sprinklerforum@lists.firesprinkler.org > Cc: BF Blake > Subject: [EXTERNAL] Re: Fire Pump Shutdown > > Copy. Was installed/designed to 2013 Edition. Central station reporting > is not operational. Thanks for all. > > Byron

Re: Fire Pump Shutdown

2021-11-18 Thread John Denhardt via Sprinklerforum
324> to submit a question today! On Thu, Nov 18, 2021 at 3:13 PM BF Blake via Sprinklerforum < sprinklerforum@lists.firesprinkler.org> wrote: > Thanks John, 100% with you. > Byron, Poland. > > > ____ > From: Sprinklerforum on >

Re: Omit sprinklers

2021-11-18 Thread John Denhardt via Sprinklerforum
Agree with Tom - as long as the spray-in insulation is noncombustible, you should be good to go. *The above is my opinion and has not been processed as a formal interpretation in accordance with the NFPA Regulations Governing Committee Projects. This is provided with the understanding that the

Re: Fire Pump Shutdown

2021-11-18 Thread John Denhardt via Sprinklerforum
To me, the intent is to have the fire pump operating anytime a sprinkler is operating. We do not want to short cycle the fire pump. My suggestion is always for manual shut-down unless the site is unmanned and response to Technical he site would take considerable time.. A properly designed and

Re: Shoe store complications

2021-11-16 Thread John Denhardt via Sprinklerforum
Whatever the engineer of the record is requiring. See the SFPE position statement 20-1. This is not a simple answer. The AHJ and insurer should also approve the selection Thanks, John *The above is my opinion and has not been processed as a formal interpretation in accordance with the NFPA

Re: Mixing of K-Factors in self-storage facilities

2021-10-29 Thread John Denhardt via Sprinklerforum
What K factor sprinkler are you trying to use? John August Denhardt, P.E. Vice-President Engineering and Technical Services American Fire Sprinkler Association 301-343-1457 > On Oct 29, 2021, at 10:09 AM, Sean Lockyer via Sprinklerforum > wrote: > > NFPA 13 generally discourages the use of

Re: Gridded dry system

2021-10-26 Thread John Denhardt via Sprinklerforum
If it looks and acts as a grid, it’s gridded. Multiple ways to supply one sprinkler; a grid. Water delivery time will be longer. The above is my opinion and has not been processed as a formal interpretation in accordance with the NFPA Regulations Governing Committee Projects. This is provided

Re: Supervised Air Manual Dry Standpipe

2021-10-22 Thread John Denhardt via Sprinklerforum
Henry and all - From Kevin Hall's earlier post: That being said, the committee is currently working on language for the 2022 edition to clarify this requirement. This is the current language that can be found in the first draft of the 2022 edition (see nfpa.org/14next to look at it in TerraView)

Re: Transport to Marriott

2021-09-17 Thread John Denhardt via Sprinklerforum
Uber. Around $15 John August Denhardt, P.E. Vice-President Engineering and Technical Services American Fire Sprinkler Association 301-343-1457 > On Sep 17, 2021, at 10:18 AM, Steve Leyton via Sprinklerforum > wrote: > > Is there anyone who has already arrived at the convention who can

Re: Fire Pump Room Sprinkler Classification

2021-09-13 Thread John Denhardt via Sprinklerforum
ormation you need to know and never miss another issue. > > > On Mon, Sep 13, 2021 at 2:06 PM Matthew J Willis > wrote: > >> NFPA 37 (18edt), section 11.4.5.1 states .3/2500. >> >> R/ >> Matt >> >> -Original Message- >> From: Sprinkler

Re: Fire Pump Room Sprinkler Classification

2021-09-13 Thread John Denhardt via Sprinklerforum
to get the latest information you need to know and never miss another issue. On Mon, Sep 13, 2021 at 2:06 PM Matthew J Willis wrote: > NFPA 37 (18edt), section 11.4.5.1 states .3/2500. > > R/ > Matt > > -Original Message----- > From: Sprinklerforum On > Beh

Re: Fire Pump Room Sprinkler Classification

2021-09-13 Thread John Denhardt via Sprinklerforum
Language was added to NFPA 20 a few cycles ago - EH2 for a diesel driven fire pump system. NFPA 20 - 2019 edition 4.14.1.3 Fire Pump Building or Rooms with Diesel Engines. Fire pump buildings or rooms enclosing diesel engine pump drivers and day tanks shall be protected with an automatic

Re: [EXTERNAL] Transfer Switches

2021-08-30 Thread John Denhardt via Sprinklerforum
equired - FM found several years ago that > the failure rate of installed pumps was roughly equal comparing diesel to > electric drives. > > Okay, Monday morning caffeine shot expended - carry on. > > SL > > -----Original Message- > From: Sprinklerforum [mail

Re: [EXTERNAL] Transfer Switches

2021-08-30 Thread John Denhardt via Sprinklerforum
Slightly off topic - the determination of "reliable" normal power can change with time. Look at the Texas area after last winter. Look at New Orleans after the last 24 hours. Just because an area was served by reliable power in the psat, things do change. Have the engineer of record determine

Re: Transfer Switches

2021-08-27 Thread John Denhardt via Sprinklerforum
A point to be mentioned: a fire pump is only supplied by normal power and if desired or required, "standby" power. "Emergency" power is different. "Shedding" of power is fully allowed with standby power. Thanks, John John August Denhardt, PE *Vice President, Engineering and Technical Services*

Re: [EXTERNAL] Re: Stub-up Material

2021-08-19 Thread John Denhardt via Sprinklerforum
> craig.pr...@jacobs.com | > https://nam12.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.jacobs.com%2Fdata=04%7C01%7Crhinson%40burnsmcd.com%7C1a13bdae20c7483ae05408d9635e869c%7Cbfbb9a2b6d994e78b3c795005d555c8b%7C0%7C0%7C637650080495691594%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiL

Re: [EXTERNAL] Re: Stub-up Material

2021-07-06 Thread John Denhardt via Sprinklerforum
p Lead/SME – Fire Protection | > craig.pr...@jacobs.com | www.jacobs.com > 1041 East Butler Road Greenville, South Carolina 29606 > CONTACT BY: email or MS TEAMS > > -Original Message- > From: Sprinklerforum On > Behalf Of John Denhardt via Sprinklerforum > Sent: Tuesd

Re: [EXTERNAL] Re: Stub-up Material

2021-07-06 Thread John Denhardt via Sprinklerforum
Looking at Craig's comments directly, I want to provide some information. *(in blue bold)* 1. Go to the manufacturer's data and see if it is listed to be installed above grade per UL and/or FM as a fire riser. * I am not aware of many nonmetallic underground materials which are Listed for a fire

Re: Sprinkler drop sizing

2021-07-06 Thread John Denhardt via Sprinklerforum
I know the answer has been given correctly. However, an assumption was made - steel piping. Other materials may be smaller: (NFPA 13-2019 edition) 27.2.1.2 Pipe sizes shall be no less than 1 in. (25 mm) nominal for black or galvanized steel piping and 3∕4 in. (20 mm) nominal for copper

Re: "Calculating" a Pipe Scheduled system for Backflow Retro

2021-05-21 Thread John Denhardt via Sprinklerforum
I know this is an old post but Look at NFPA 13 -2019 edition: 19.3.2 Water Demand Requirements — Pipe Schedule Method. 19.3.2.6* Residual Pressure. 19.3.2.6.1 The residual pressure requirement of Table 19.3.2.1 shall be met at the elevation of the highest sprinkler. 19.3.2.6.2 Friction

Re: 13 / 13R IN SAME BUILDING?

2021-05-11 Thread John Denhardt via Sprinklerforum
Something to think about Keep in mind NFPA 13R has limited property protection compared to a NFPA 13 system. Can the community afford to lose the use of the firehouse due to a fire which was not contained by a NFPA 13R system. John John August Denhardt, P.E Vice President Engineering and

Re: Available Pressure from Fire Water Storage Tank

2021-05-07 Thread John Denhardt via Sprinklerforum
Lots of items to think about. I always recommend using the tank at the lowest available level. - What is the level of the tank before refilled? - Is the tank being utilized for any other purposes. Reminder - account for the friction loss between the tank and the suction side of the fire

Re: Location of hydrant valves in CA.

2021-05-07 Thread John Denhardt via Sprinklerforum
NFPA 24 - 2019 7.1.1.2.2 Valves required by 7.1.1.2 shall be installed within 20 ft (6.1 m) of the hydrant. 7.1.1.2.2.1 Valves shall be clearly identified and kept free of obstructions. 7.1.1.2.3 Where valves cannot be located in accordance with 7.1.1.2.2, valve locations shall be permitted

Re: Manual Dry Standpipe

2021-05-04 Thread John Denhardt via Sprinklerforum
Fully agree. Interconnection is required. A control valve is required at each stairway riser. Thanks, John > > The foregoing is my opinion only and does not represent NFPA or the NFPA 14 > Technical Committee, nor intended to serve as an interpretation of the > standard. > John August

Re: Dry System Couplings

2021-04-30 Thread John Denhardt via Sprinklerforum
As usual, Scott is 100% correct. NFPA 13 and the Listing are minimum standards. An owner, contractor, or an engineer can always ask for higher grade material or methods. I have seen schedule 40 black steel with cut grooves, "flush" type gaskets, 1/2" per 10' of pitch, with hangers every 10'

Re: Car Dealerships

2021-04-29 Thread John Denhardt via Sprinklerforum
No other option. 1,500 Sq.Ft. minimum remote area. Any chance adjusting K factors of the sprinklers? *The above is my opinion and has not been processed as a formal interpretation in accordance with the NFPA Regulations Governing Committee Projects. This is provided with the understanding that

Re: Grooved joints in pump suction main

2021-04-06 Thread John Denhardt via Sprinklerforum
I have completed hundreds of design, installations, and commissioning with grooved connections on the suction and discharge sides of fire pumps. I never have seen an issue. In fact, I use FxG adapters when I have flanged valves or fittings. I know it probably will not happen during my career,

Re: Type of sprinkler in a Gravity Waste Chute

2021-03-26 Thread John Denhardt via Sprinklerforum
Interesting questions. I just had this situation a few weeks ago. These are my thoughts. NFPA 13 - 2019 edition and NFPA 82 as referenced in section 26.15 of NFPA 13 does not specify a specific temperature classification for the sprinkler. I would install an intermediate temperature rated

Re: New coil actuators - New standard

2021-03-26 Thread John Denhardt via Sprinklerforum
Below is the exact language from NFPA 13 -2019 edition: 8.3.1.2.1 Actuator Supervision. Effective January 1, 2021, removal of an electric actuator from the preaction or deluge valve that it controls shall result in an audible and visual indication of system impairment at the system releasing

Re: NFPA 13 2016 25.2.1.4.2

2021-03-18 Thread John Denhardt via Sprinklerforum
Please forgive spelling errors, > typographical transgressions and grammatical gaffs. > > ------ > *From:* Sprinklerforum > on behalf of John Denhardt via Sprinklerforum < > sprinklerforum@lists.firesprinkler.org> > *Sent:* Thursday, Ma

Re: NFPA 13 2016 25.2.1.4.2

2021-03-18 Thread John Denhardt via Sprinklerforum
John - Let's talk tomorrow. I think we can prepare an informal interpretation for you describing the intent of this section. AFSA will be covering Acceptance Testing is some upcoming AHJ webinars. Thanks, John John August Denhardt, PE *Vice President, Engineering and Technical Services*

Re: leaving abandoned sprinkler piping in place

2021-03-17 Thread John Denhardt via Sprinklerforum
NFPA 13 - 2019 29.2.2 Where all or part of an inactive sprinkler system is abandoned in place, components including sprinklers, hose valves and hoses, and alarm devices shall be removed. 29.2.3 Control valves abandoned in place shall have the operating mechanisms removed. 29.2.4 Sprinkler

Re: [External] Re: Does a remote free standing FDC require a valve pit?

2021-03-16 Thread John Denhardt via Sprinklerforum
inlet for every 250 demand. Stuff went south, maybe > southwest. > > -Original Message- > From: Sprinklerforum On > Behalf Of John Denhardt via Sprinklerforum > Sent: Thursday, March 11, 2021 11:11 AM > To: sprinklerforum@lists.firesprinkler.org > Cc: John Denhardt

Re: Check Valve After Flow switch?

2021-03-15 Thread John Denhardt via Sprinklerforum
I would like to know why this is the "best way" for the installation. I am not stating it is not, just not sure why one way is better especially since we have done it a certain way for years. Thanks, John John August Denhardt, PE *Vice President, Engineering and Technical Services* *American

Re: [External] Re: Does a remote free standing FDC require a valve pit?

2021-03-11 Thread John Denhardt via Sprinklerforum
inimum and inspect the work (all visible) to make sure there are no leaks. > > Applying that approach to what you described - if the ball drip is the > only thing leaking and the test pressure was never allowed to go below the > minimum, I'd say it passed. > > My thoughts, Scott > > -----

Re: Does a remote free standing FDC require a valve pit?

2021-03-11 Thread John Denhardt via Sprinklerforum
I would like to know how contractors are passing the required initial and the periodic NFPA 25 hydrostatic test of the free standing FDC when an automatic ball drip is installed in the underground piping? Thanks, John John August Denhardt, PE *Vice President, Engineering and Technical Services*

Re: Group III Aircraft Hangar

2021-02-21 Thread John Denhardt via Sprinklerforum
I fully agree it is the EOR responsibility to identify the hazard (design) requirements. The SFPE's Position Paper 20-1 makes this clear. This position paper was published in December 2020. AFSA is an endorsing organization to this position paper. *4.2.1 Engineering Documents* The Engineer is

Re: [EXTERNAL] Re: Air Venting (2021)

2021-02-18 Thread John Denhardt via Sprinklerforum
The language in NFPA 13 section 16.7 is an attempt to provide a method to vent some of the trapped air out of the system. At this point, the technical committee did not adapt language to require multiple air vents. In fact, a single 1/2" manual vent is acceptable. The air vent is required to be

Re: Hotel or Condo

2021-02-17 Thread John Denhardt via Sprinklerforum
Absolutely - Closets which are 24 sq.ft. or less in motels and hotels are the exception. Transient occupancy usually means low storage in closets, thus no protection is required. Thanks, John John August Denhardt, PE *Vice President, Engineering and Technical Services* *American Fire Sprinkler

Re: Multiple System Calculation

2021-02-15 Thread John Denhardt via Sprinklerforum
All - For the 2022 edition of NFPA 13, some clarifications and changes are coming for the "Phantom Flow" calculation process. The diagram in the annex has been revised. These changes are still tentative since the NITIAM process is currently occurring. Hopefully, these changes will make it easier

Re: [EXTERNAL] Noncontinuous obstructions More than 18" down

2021-02-15 Thread John Denhardt via Sprinklerforum
>> nearly 90% of the floor area. I'm not saying that you definitely need >> sprinklers, but it would be cool to see some fire modeling or something to >> see the impact of these panels on activation time and/or sprinkler >> discharge. >> >> -Kyle M &g

Re: [EXTERNAL] Noncontinuous obstructions More than 18" down

2021-02-15 Thread John Denhardt via Sprinklerforum
gt; sprinklers, but it would be cool to see some fire modeling or something to > see the impact of these panels on activation time and/or sprinkler > discharge. > > -Kyle M > > -Original Message- > From: Sprinklerforum On > Behalf Of John Denhardt via Sprin

Re: [EXTERNAL] Noncontinuous obstructions More than 18" down

2021-02-15 Thread John Denhardt via Sprinklerforum
My understanding of the standard is no additional protection is needed as long as you have the 18" of clearance between the sprinkler and the top of the obstruction. As you stated, the pattern is developed sufficiently to allow adequate protection since water will be delivered on both sides of

Re: Slopes / Storage / UFC 3-600-01 change 5

2021-02-05 Thread John Denhardt via Sprinklerforum
The UFC 3-600-1 requires the storage areas to be designed in accordance with NFPA 13. If under NFPA 13, you qualify for low-pile/miscellaneous storage, the 30% for slope increase is applicable. If you do not qualify for low-pile/miscellaneous storage, a slope ceiling is not allowed. Thanks,

Re: NFPA 13R & NFPA 14

2021-02-04 Thread John Denhardt via Sprinklerforum
Agree - anything could be possible! But very hard indeed. Thanks, John John August Denhardt, PE *Vice President, Engineering and Technical Services* *American Fire Sprinkler Association* m: p: 301-343-1457 214-349-5965 ext 121 w: firesprinkler.org

Re: Tissue Paper Wrapped in Plastic

2021-02-02 Thread John Denhardt via Sprinklerforum
Following up - the 2019 edition of NFPA 13 has similar language: Table A.20.4(b) Tissue products plastic-wrapped: exposed - Group A nonexpanded Tissue products plastic-wrapped; cartoned - Class III Hope this helps. Thanks, John John August Denhardt, PE *Vice President, Engineering and

Re: Area Increases

2021-01-26 Thread John Denhardt via Sprinklerforum
ally disclaiming that there's no > consideration given to a particular condition in the standard doesn't mean > that such a condition can't or doesn't exist. > > Definitely my opinion only, > > Steve L. > > -Original Message- > From: Sprinklerforum [mailto: > sp

Re: Area Increases

2021-01-26 Thread John Denhardt via Sprinklerforum
As Travis stated, slope ceilings are not covered under the protection schemes of NFPA 13 for "Storage". Thus, the increase does not apply to "Storage" unless miscellaneous or low-piled storage applies. NFPA 13 - 2019: 20.6.1 Ceiling Slope. The sprinkler system criteria specified in Chapters 20

Re: schedule 7 pipe?

2021-01-20 Thread John Denhardt via Sprinklerforum
Matt - fully understand the position you have. To answer your initial question specifically, I have heard of *no* push to change NFPA 13 with regard to piping material. Thanks, John John August Denhardt, PE *Vice President, Engineering and Technical Services* *American Fire Sprinkler

Re: schedule 7 pipe?

2021-01-20 Thread John Denhardt via Sprinklerforum
. > > Matt > > -----Original Message- > From: Sprinklerforum On > Behalf Of John Denhardt via Sprinklerforum > Sent: Wednesday, January 20, 2021 1:30 PM > To: sprinklerforum@lists.firesprinkler.org > Cc: John Denhardt > Subject: Re: schedule 7 pipe? > &

Re: schedule 7 pipe?

2021-01-20 Thread John Denhardt via Sprinklerforum
Keep in mind, NFPA 13 states piping or tubing that meets Table 7.3.1.1 is acceptable. Listing is NOT required. *NFPA 13 - 2019: 7.3.1.1 Pipe or tube shall meet or exceed one of the standards in Table 7.3.1.1 or be in accordance with 7.3.3.* Thus, as long as any piping or tubing material

Re: RV Storage

2021-01-08 Thread John Denhardt via Sprinklerforum
My suggestions: - RV Storage Building* - Extra Hazard Group 2* - Boat Storage Building (just parked, not on racks) *- Extra Hazard Group 2* - Storage lockers with height less than 12 feet *- Depends on what is being stored. For example, Group A plastics might be more demanding.

Re: CPVC EQ Bracing - 2 hole straps and another question

2021-01-02 Thread John Denhardt via Sprinklerforum
Scott makes a great point. CPVC piping has to be free to move. Thanks, John John August Denhardt, PE *Vice President, Engineering and Technical Services* *American Fire Sprinkler Association* m: p: 301-343-1457 214-349-5965 ext 121 w: firesprinkler.org

Re: Open Grate Flooring - Calculations

2021-01-02 Thread John Denhardt via Sprinklerforum
Bill - I agree with Cecil; look at the system as levels. Calculate the system which is most demanding. Thanks, John John August Denhardt, PE *Vice President, Engineering and Technical Services* *American Fire Sprinkler Association* m: p: 301-343-1457 214-349-5965 ext 121 w: firesprinkler.org

Re: Merry Christmas,

2020-12-25 Thread John Denhardt via Sprinklerforum
Merry Christmas to all my friends. John John August Denhardt, P.E. Vice-President Engineering and Technical Services American Fire Sprinkler Association 301-343-1457 > On Dec 25, 2020, at 1:01 PM, Bob Caputo via Sprinklerforum > wrote: > > Thank youSame to you and yours > >> On Fri,

Re: potential freezing in ESFR system

2020-12-22 Thread John Denhardt via Sprinklerforum
what would be the point of doing a hydrostatic test and > then replacing all the sprinklers. In a 40,000 sq. ft. system at 100 sq. > ft. per, that a potential for 400 new leaks. > > > -----Original Message- > From: John Denhardt via Sprinklerforum < > spr

Re: potential freezing in ESFR system

2020-12-22 Thread John Denhardt via Sprinklerforum
Again personally, I would never knowingly put water in a wet piping system unless the "client" can ensure or take responsibility" for any damage due to freezing. Pulling the pendent sprinklers is not a viable option. As a contractor, in almost all cases, our client backed down. In the case when

Re: Standpipe signage

2020-11-25 Thread John Denhardt via Sprinklerforum
On a standpipe system, I always indicate the FDC sign requirements on the shop drawing. I usually just state “CHARGE FDC AT 150 PSIG” unless the system needs more. John August Denhardt, P.E. Vice-President Engineering and Technical Services American Fire Sprinkler Association 301-343-1457 >

Re: Domestic Demands 13R

2020-11-12 Thread John Denhardt via Sprinklerforum
That request is now our list of items to be considered or the 2025 edition of 13R. Thanks, John John August Denhardt, PE *Vice President, Engineering and Technical Services* *American Fire Sprinkler Association* m: p: 301-343-1457 214-349-5965 ext 121 w: firesprinkler.org

Re: Clearance around all pump equipment

2020-11-08 Thread John Denhardt via Sprinklerforum
Others have stated the requirements. I have seen many installations where there was room and the installer did not take advantage of it. Adequate and reasonable space must be maintained to properly inspect, service, repair, and replace all equipment. I always ask, how would I work on this

Announcement - AFSA President and our AFSA 39 General Session

2020-10-08 Thread John Denhardt via Sprinklerforum
I am very pleased with this announcement. Congratulations Bob! *The AFSA Board of Directors and AFSA are excited to announce the unanimous selection of Bob Caputo, CFPS, as the association’s President. Caputo’s will begin with AFSA on November 1, 2020. * A link to the announcement on our blog

Re: [EXTERNAL] Re: Submittal Packages

2020-10-08 Thread John Denhardt via Sprinklerforum
aGT7kLeKIbnZg4TvDPBxUoz195Nl4J%2BkvETIT7u%2F50%3Dreserved=0 > 1041 East Butler Road Greenville, South Carolina 29606 > > -Original Message- > From: Sprinklerforum On > Behalf Of John Denhardt via Sprinklerforum > Sent: Thursday, October 8, 2020 11:32 AM > To: s

Re: Submittal Packages

2020-10-08 Thread John Denhardt via Sprinklerforum
I have seen both. I prefer the entire package. However, I have worked with General Contractors that demand equipment data sheets with 2 weeks of contract award. Engineers - a suggestion: put the requirement in your specification to require a complete package if that is what you want. Thanks,

Re: ssu - concealed space - small room???

2020-10-07 Thread John Denhardt via Sprinklerforum
You got it. You must satisfy the definition of small room and my guess is you will not meet the requirements. Thanks, John John August Denhardt, PE *Vice President, Engineering and Technical Services* *American Fire Sprinkler Association* m: p: 301-343-1457 214-349-5965 ext 121 w:

Re: 8.17.5 Hose Connections

2020-10-02 Thread John Denhardt via Sprinklerforum
In a storage application, hose connections (without hose) are for the responding trained emergency personnel to utilize for "mop up" and if necessary final extinguishment. of the fire. They are not considered as part of a standpipe system. *The above is my personal opinion as a professional

Re: FM 8-9

2020-10-01 Thread John Denhardt via Sprinklerforum
AFSA is trying to schedule a Webinar on this topic. Keep an eye out for this. Thanks, John John August Denhardt, PE *Vice President, Engineering and Technical Services* *American Fire Sprinkler Association* m: p: 301-343-1457 214-349-5965 ext 121 w: firesprinkler.org

Re: Hangers for CPVC Pipe going through TGI Joists

2020-09-30 Thread John Denhardt via Sprinklerforum
Agree - the structure is the support. Restraints or chafing protectuion might be needed. Thanks, John John August Denhardt, PE *Vice President, Engineering and Technical Services* *American Fire Sprinkler Association* m: p: 301-343-1457 214-349-5965 ext 121 w: firesprinkler.org

Re: [EXTERNAL] RE: On/Off Switch in the Electric supply to a Dry Pipe System Air Compressor

2020-09-25 Thread John Denhardt via Sprinklerforum
Denhardt > > > > > > Subject: [EXTERNAL] RE: On/Off Switch in the Electric supply to a Dry > > > Pipe System Air Compressor > > > > > > IMHO, yes, it should be. Off the shelf, big box store compressors, > don't last very long costing

Re: On/Off Switch in the Electric supply to a Dry Pipe System Air Compressor

2020-09-24 Thread John Denhardt via Sprinklerforum
ter, film director, author, actor and opera director > (1942-) > > > On Thu, Sep 24, 2020 at 12:02 PM Mike Hairfield via Sprinklerforum < > sprinklerforum@lists.firesprinkler.org> wrote: > > > Like the one for a light switch, there is breaker in the electrical > > p

Re: On/Off Switch in the Electric supply to a Dry Pipe System Air Compressor

2020-09-24 Thread John Denhardt via Sprinklerforum
You are required to have a disconnect switch. What kind of “On/Off” switch are you seeing? John John August Denhardt, P.E. Vice-President Engineering and Technical Services American Fire Sprinkler Association 301-343-1457 > On Sep 24, 2020, at 2:50 PM, Mike Hairfield via Sprinklerforum >

Welcome to the AFSA Technical Service Team - Kevin Hall

2020-09-10 Thread John Denhardt via Sprinklerforum
I am excited to announce to the SprinklerForum the addition of Kevin Hall to our staff. He will be a great asset to the team. Official Press Release: The American Fire Sprinkler Association (AFSA) is pleased to welcome Coordinator of Technical Services Kevin Hall, P.E., MSFPE, to its Department

AFSA Membership

2020-09-03 Thread John Denhardt via Sprinklerforum
*I want to first off offer a Thank You for all the support I have received in my new position at AFSA.* I can not believe it has already been 8 months. Lots of great things have been happening at AFSA. I love my job! *To all of our current AFSA members -* I appreciate you being a member! AFSA

Re: [EXTERNAL] RE: Ethanol unloading exposure protection

2020-09-03 Thread John Denhardt via Sprinklerforum
Craig - Great summary! Bruce has a valid point. Ben make sure you are not overstepping your obligations and make sure you are being compensated fairly for this work and the associated liability. Thanks, John John August Denhardt, PE *Vice President, Engineering and Technical Services*

Re: C-Clamp Hangers

2020-08-26 Thread John Denhardt via Sprinklerforum
I think Ryan is onto the issue. If it is in the specification, request clarification from the engineer. A large percentage of time, the engineer is not clear enough when the specification is written. Thanks, John John August Denhardt, PE *Vice President, Engineering and Technical Services*

Re: C-Clamp Hangers

2020-08-26 Thread John Denhardt via Sprinklerforum
Possibly an outdated specification. I have not heard of any issues with properly installed listed C-clamps. Thanks, John John August Denhardt, PE *Vice President, Engineering and Technical Services* *American Fire Sprinkler Association* m: p: 301-343-1457 214-349-5965 ext 121 w:

Re: Window Sprinklers

2020-08-25 Thread John Denhardt via Sprinklerforum
Agree 100%. Follow the Listing - period. If an architect or an engineer wants to violate the Listing, let them provide direction and assume all liability. Thanks, John John August Denhardt, PE *Vice President, Engineering and Technical Services* *American Fire Sprinkler Association* m: p:

Re: Ambulatory Health Care protection

2020-06-26 Thread John Denhardt via Sprinklerforum
Since it is new construction, all light hazard areas must utilize quick response sprinklers. Thanks, John John August Denhardt, PE *Vice President, Engineering and Technical Services* *American Fire Sprinkler Association* m: p: 301-343-1457 214-349-5965 ext 121 w: firesprinkler.org

Re: Listed sprinkler guard for horizontal or vertical spray sidewalls

2020-06-24 Thread John Denhardt via Sprinklerforum
Agree. This forum is a valuable asset. Thanks to all for their contribution. John John August Denhardt, P.E. Vice-President Engineering and Technical Services American Fire Sprinkler Association 301-343-1457 > On Jun 24, 2020, at 7:03 PM, Mark Phillips via Sprinklerforum > wrote: > >  >

Re: [EXTERNAL] Edge of a platform

2020-06-15 Thread John Denhardt via Sprinklerforum
I am unaware of any allowances for this situation. However, I like Kyle's thoughts. I would want to see more details but I would consider that approach. Thanks, John John August Denhardt, PE *Vice President, Engineering and Technical Services* *American Fire Sprinkler Association* m: p:

Re: stairways & elevators when only the basement is sprinklered

2020-06-10 Thread John Denhardt via Sprinklerforum
In my opinion, you are looking for direction from NFPA 13 where NFPA 13 is not applicable in this case. Someone has decided to make a partial sprinklered building. That person needs to tell you what sections of NFPA 13 are to be followed or ignored. Otherwise, the liability falls on you. Do not

Re: [EXTERNAL] Re: mattress storage

2020-06-04 Thread John Denhardt via Sprinklerforum
As others have already stated, exposed expanded, Group A, Table A.20.4.5.1. Depending on the storage height, Table 4.3.1.7.1 might be applicable. References are to the 2019 edition of NFPA 13. Thanks, John John August Denhardt, PE *Vice President, Engineering and Technical Services* *American

Re: Structural Load

2020-06-03 Thread John Denhardt via Sprinklerforum
I agree with Ken. I have been down this road before. The structure needs to support the piping plus 250 pounds at the point of hanging. If the structure can handle this load, then the structure has an issue. Thanks, John John August Denhardt, PE *Vice President, Engineering and Technical

Re: Exemption for sprinklers

2020-06-02 Thread John Denhardt via Sprinklerforum
FWIW - Pete works for the Veterans Administration. So NFPA 101 most likely applies. John John August Denhardt, P.E. Vice-President Engineering and Technical Services American Fire Sprinkler Association 301-343-1457 > On Jun 2, 2020, at 4:02 PM, Prahl, Craig/GVL via Sprinklerforum > wrote:

Re: [EXTERNAL] Re: NFPA 13, 2013 ed - hangers and pressures above 100psi

2020-05-29 Thread John Denhardt via Sprinklerforum
gt; > > *TOTAL Mechanical* > > *Building* *Integrity* > > > W234 N2830 Paul Rd. > Pewaukee, WI 53072 > > dmarti...@total-mechanical.com > > Ph: 262-522-7110 > > Cell: 414-406-5208 > > http://www.total-mechanical.com/ > <https://urldefense.proofpoint.c

Re: NFPA 13, 2013 ed - hangers and pressures above 100psi

2020-05-29 Thread John Denhardt via Sprinklerforum
.@gmail.com > > 253.576.9700 > > The Universe is monstrously indifferent to the presence of man. -Werner > Herzog, screenwriter, film director, author, actor and opera > director (1942-) > > > On Fri, May 29, 2020 at 8:40 AM John Denhardt via Sprinklerforum < > sprin

Re: NFPA 13, 2013 ed - hangers and pressures above 100psi

2020-05-29 Thread John Denhardt via Sprinklerforum
In my opinion, no. The flexible drop assembly is anchored to the ceiling. The point of this requirement is to keep the pendent sprinkler from moving upwards during activation. The flexible drop assembly accomplishes this requirement. Thanks, John John August Denhardt, PE *Vice President,

Re: Dust Collection

2020-05-22 Thread John Denhardt via Sprinklerforum
Now that’s is just funny but unfortunately is sometimes typical for a technical committee. Happy Memorial Day weekend. John John August Denhardt, P.E. Vice-President Engineering and Technical Services American Fire Sprinkler Association 301-343-1457 > On May 22, 2020, at 3:49 PM,

RE: [External] Re: I-B construction - ABS plumbing piping

2020-05-21 Thread John Denhardt via Sprinklerforum
As Travis stated, it is in the works!  Thanks, John John August Denhardt, P.E. Strickland Fire Protection Incorporated 4011 Penn Belt Place Forestville, Maryland 20747-4737 301.474.1136 - Office 301.343.1457 - Mobile From: Sprinklerforum On Behalf Of Travis Mack via Sprinklerforum Sent:

Re: [EXTERNAL] Re: Help Finding Code Section

2020-05-20 Thread John Denhardt via Sprinklerforum
The 2019 edition of 13 has been changed to (*the red bold highlighted text has been deleted*): 9.3.14.3 - Where there is a noncombustible space above a noncombustible or limited-combustible drop ceiling that is sprinklered because it is open to an adjacent sprinklered space *on only one side *and

  1   2   >