as pointed out here my message should have said (a) not (c)
Roland
On Mar 30, 2007, at 11:41 AM, Paul Pinigis wrote:
I would suggest that you ask the AHJ for the section that you are
violating. Are you violating Table 8.3.2.5(a)?
Paul J. Pinigis, P.E.
Chief Life Safety Engineer
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Bill
Minkel
Sent: Friday, March 30, 2007 2:33 PM
To: [email protected]
Subject: RE:C urious
We have an AHJ saying our center-of-tile recessed 155F sprinkler is
too
close to the HVAC supply diffuser in an A.T.C. (less than 2') I am
curious
as to what section or paragraph in NFPA-13, 2002 references this
requirement? I can't find it, maybe one of y'all can hep me?