Bill, I would start with Table 8.3.2.5(a) and go from there. Item 1(c) is for a diffuser. PARSLEY CONSULTING Ken Wagoner, SET 760.745.6181 voice 760.745.0537 fax [EMAIL PROTECTED] <mailto:[EMAIL PROTECTED]> e-mail www.ParsleyConsulting.com <http://www.ParsleyConsulting.com> website
Bill Minkel wrote:
We have an AHJ saying our center-of-tile recessed 155F sprinkler is too close to the HVAC supply diffuser in an A.T.C. (less than 2') I am curious as to what section or paragraph in NFPA-13, 2002 references this requirement? I can't find it, maybe one of y'all can hep me? _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)