You might also want to point out for the approximately 650 lurkers on the
forum who may be confused that a riser is any vertical piping, regardless
of the direction of water flow that isn't a drop, sprig up or arm over
ending with a sprig or drop.

On Wednesday, September 21, 2016, Parsley Consulting <
parsleyconsult...@cox.net> wrote:

> Cliff,
>     You've pointed out a conclusion on my part that was not in what Rocci
> posted.  He didn't say it was a part of a standpipe.  That was a
> supposition on my part.
>     If it were a part of a sprinkler system, such as a line feeding a hose
> valve in rack storage, the horizontal portions would not require bracing,
> in my perspective, as they simply aren't mains [longitudinal], and aren't
> branch lines [lateral].
>     Now, if they had an elevation change exceeding 3'-0", that pipe would
> be regarded as a "riser", by 3.5.9, it would require a 4-way brace at the
> top per 9.3.5.8.1.
>     It also might fall into the need for flexible couplings per
> 9.3.2.3.1(1).
>     Good call.  And I suppose I should acknowledge Craig's question, and
> note that I made the conclusion that since Rocci is in California, where
> almost everything has to be protected from earthquake damage, AND he asked
> the question, that seismic protection was necessary on his system.
> sincerely,
>
> *Ken Wagoner, SET Parsley Consulting*
>
>
>
> * 350 West 9th Avenue, Suite 206 Escondido, California 92025 Phone
> 760-745-6181 Visit our website <http://www.parsleyconsulting.com/> *
> On 09/21/2016 9:10 AM, Cliff Whitfield wrote:
>
> Ken,
>
>
>
> If this is an 1½” hose line in an NFPA 13 condition (which Rocci didn’t
> actually state but I’m assuming it is), then the definition of ‘branch
> line’ in NFPA 14 would not apply.  If that is the case, would this still be
> considered a ‘branch line’ or does it become a ‘feed main’?
>
>
>
> Cliff Whitfield
>
>
>
> *From:* Sprinklerforum [mailto:sprinklerforum-bounces@lists.firesprinkler.
> org
> <javascript:_e(%7B%7D,'cvml','sprinklerforum-boun...@lists.firesprinkler.org');>]
> *On Behalf Of *Parsley Consulting
> *Sent:* Wednesday, September 21, 2016 12:06 PM
> *To:* sprinklerforum@lists.firesprinkler.org
> <javascript:_e(%7B%7D,'cvml','sprinklerforum@lists.firesprinkler.org');>
> *Subject:* Re: small hose connections
>
>
>
> Rocci,
>     Glad to see you made it back safely from Nashville, and it was great
> to meet there and put a face with the name.
>     By the definition in section 3.3.2 of NFPA 14 [2013 ed], the pipe you
> describe is a "branch line."  Section 6.1.2.5 of that document advises that
> you need to follow NFPA 13 to provide protection against damage from
> earthquakes.
>     Lateral bracing for that line is not required per NFPA 13 [2013]
> 9.3.5.5.1, as it is not a branch line 2½" or larger.
>     Longitudinal bracing for that line is not required per 9.5.6.1 as it
> is not a feed or cross main.
>     My opinion only.  Please see the disclaimer below.
> sincerely,
>
>
> *Ken Wagoner, SET *
>
>
> *Parsley Consulting 350 West 9th Avenue, Suite 206 Escondido, California
> 92025 *
> *Phone 760-745-6181 **Visit our website
> <http://www.parsleyconsulting.com/> *
>
>
>
> *IMPORTANT NOTICE: This correspondence is not a Formal Interpretation
> issued pursuant to NFPA Regulations. Any opinion expressed is the personal
> opinion of the author and does not necessarily represent the official
> position of the NFPA or its Technical Committees. In addition, this
> correspondence is neither intended, nor should it be relied upon, to
> provide professional consultation or services It should be noted that the
> above is my opinion as a member of the NFPA Automatic Sprinkler System
> Hanging and Bracing Committee in accordance with the NFPA Regulations
> Governing Committee Projects and should therefore not be considered, nor
> relied upon, as the official position of the NFPA or its Committees*
>
>
> On 09/21/2016 8:17 AM, Rocci Cetani 3 wrote:
>
> Do I need to earthquake brace my 1½” feed for hose connections?
>
>
>
> *Rocci Cetani III, **CET*
>
> *Designer*
>
> *Water-Based Fire Protections Systems Layout, Nicet Level III*
>
>
>
> *Northern California Fire Protection Services Inc.*
>
> 16840 Joleen Way Bldg. A
>
> Morgan Hill, CA 93037
>
> P-(408) 776-1580 EXT.111
>
> F-(408) 776-1590
>
>
>
>
>
> roc...@norcalfire.com
> <javascript:_e(%7B%7D,'cvml','roc...@norcalfire.com');>
>
> www.norcalfire.com
>
>
>
> CONFIDENTIALITY NOTICE: This message and any document accompanying it may
> contain confidential information
>
> belonging to the sender. The information is intended only for the use of
> individual or entity named above. If you are not the intended recipient, or
> the employee or agent responsible to deliver this message to the intended
> recipient, you are hereby notified that any disclosure, copying or taking
> of any action in reliance on the contents of this information is strictly
> prohibited. If you have received this transmission in error, please
> immediately notify us by telephone to arrange for return of the documents.
>
>
>
>
>
>
> _______________________________________________
>
> Sprinklerforum mailing list
>
> Sprinklerforum@lists.firesprinkler.org 
> <javascript:_e(%7B%7D,'cvml','Sprinklerforum@lists.firesprinkler.org');>
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
>
>
>
> ------------------------------
> [image: Avast logo]
> <https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient>
>
> This email has been checked for viruses by Avast antivirus software.
> www.avast.com
> <https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient>
>
>
>
> _______________________________________________
> Sprinklerforum mailing listsprinklerfo...@lists.firesprinkler.org 
> <javascript:_e(%7B%7D,'cvml','Sprinklerforum@lists.firesprinkler.org');>http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
>
>

-- 
Sent from Gmail Mobile
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to