You might want to look at the wording in 9.3.2.4 which deals with Flexible Coupling for Drops where it uses the term “drops to hose lines”. So a line coming off a sprinkler system serving a hose line is referred to as a “drop”, not a riser.
Also, for example, 9.3.5.5 speaking of lateral sway bracing uses the phrase “…and OTHER piping….”, therefore addressing piping in the system which does not fall within the definitions of Feed and Cross Mains and Branch lines which are the typical piping components of a sprinkler system. I would submit that a drop to a hose valve would fall under the “other piping” category. Craig L. Prahl Fire Protection Group Lead/SME CH2M 200 Verdae Blvd. Greenville, SC 29607 Direct - 864.920.7540 Fax - 864.920.7129 CH2MHILL Extension 77540 [email protected] From: Sprinklerforum [mailto:[email protected]] On Behalf Of rongreenman . Sent: Wednesday, September 21, 2016 12:40 PM To: [email protected] Subject: Re: small hose connections [EXTERNAL] You might also want to point out for the approximately 650 lurkers on the forum who may be confused that a riser is any vertical piping, regardless of the direction of water flow that isn't a drop, sprig up or arm over ending with a sprig or drop. On Wednesday, September 21, 2016, Parsley Consulting <[email protected]<mailto:[email protected]>> wrote: Cliff, You've pointed out a conclusion on my part that was not in what Rocci posted. He didn't say it was a part of a standpipe. That was a supposition on my part. If it were a part of a sprinkler system, such as a line feeding a hose valve in rack storage, the horizontal portions would not require bracing, in my perspective, as they simply aren't mains [longitudinal], and aren't branch lines [lateral]. Now, if they had an elevation change exceeding 3'-0", that pipe would be regarded as a "riser", by 3.5.9, it would require a 4-way brace at the top per 9.3.5.8.1. It also might fall into the need for flexible couplings per 9.3.2.3.1(1). Good call. And I suppose I should acknowledge Craig's question, and note that I made the conclusion that since Rocci is in California, where almost everything has to be protected from earthquake damage, AND he asked the question, that seismic protection was necessary on his system. sincerely, Ken Wagoner, SET Parsley Consulting 350 West 9th Avenue, Suite 206 Escondido, California 92025 Phone 760-745-6181 Visit our website<http://www.parsleyconsulting.com/> On 09/21/2016 9:10 AM, Cliff Whitfield wrote: Ken, If this is an 1½” hose line in an NFPA 13 condition (which Rocci didn’t actually state but I’m assuming it is), then the definition of ‘branch line’ in NFPA 14 would not apply. If that is the case, would this still be considered a ‘branch line’ or does it become a ‘feed main’? Cliff Whitfield From: Sprinklerforum [mailto:[email protected]<javascript:_e(%7B%7D,'cvml','[email protected]');>] On Behalf Of Parsley Consulting Sent: Wednesday, September 21, 2016 12:06 PM To: [email protected]<javascript:_e(%7B%7D,'cvml','[email protected]');> Subject: Re: small hose connections Rocci, Glad to see you made it back safely from Nashville, and it was great to meet there and put a face with the name. By the definition in section 3.3.2 of NFPA 14 [2013 ed], the pipe you describe is a "branch line." Section 6.1.2.5 of that document advises that you need to follow NFPA 13 to provide protection against damage from earthquakes. Lateral bracing for that line is not required per NFPA 13 [2013] 9.3.5.5.1, as it is not a branch line 2½" or larger. Longitudinal bracing for that line is not required per 9.5.6.1 as it is not a feed or cross main. My opinion only. Please see the disclaimer below. sincerely, Ken Wagoner, SET Parsley Consulting 350 West 9th Avenue, Suite 206 Escondido, California 92025 Phone 760-745-6181 Visit our website<http://www.parsleyconsulting.com/> IMPORTANT NOTICE: This correspondence is not a Formal Interpretation issued pursuant to NFPA Regulations. Any opinion expressed is the personal opinion of the author and does not necessarily represent the official position of the NFPA or its Technical Committees. In addition, this correspondence is neither intended, nor should it be relied upon, to provide professional consultation or services It should be noted that the above is my opinion as a member of the NFPA Automatic Sprinkler System Hanging and Bracing Committee in accordance with the NFPA Regulations Governing Committee Projects and should therefore not be considered, nor relied upon, as the official position of the NFPA or its Committees On 09/21/2016 8:17 AM, Rocci Cetani 3 wrote: Do I need to earthquake brace my 1½” feed for hose connections? Rocci Cetani III, CET Designer Water-Based Fire Protections Systems Layout, Nicet Level III Northern California Fire Protection Services Inc. 16840 Joleen Way Bldg. A Morgan Hill, CA 93037 P-(408) 776-1580 EXT.111 F-(408) 776-1590 [email protected]<javascript:_e(%7B%7D,'cvml','[email protected]');> www.norcalfire.com<http://www.norcalfire.com/> CONFIDENTIALITY NOTICE: This message and any document accompanying it may contain confidential information belonging to the sender. The information is intended only for the use of individual or entity named above. If you are not the intended recipient, or the employee or agent responsible to deliver this message to the intended recipient, you are hereby notified that any disclosure, copying or taking of any action in reliance on the contents of this information is strictly prohibited. If you have received this transmission in error, please immediately notify us by telephone to arrange for return of the documents. _______________________________________________ Sprinklerforum mailing list [email protected]<javascript:_e(%7B%7D,'cvml','[email protected]');> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org ________________________________ [Avast logo]<https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient> This email has been checked for viruses by Avast antivirus software. www.avast.com<https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient> _______________________________________________ Sprinklerforum mailing list [email protected]<javascript:_e(%7B%7D,'cvml','[email protected]');> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org -- Sent from Gmail Mobile
_______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org