sk me to name a brand, just study the
product you use…for everyones good.
Larry Crutcher
Starlight Solar Power Systems
On Apr 9, 2020, at 4:07 PM, Bruce Leininger wrote:
Hi. I was wondering if there are any known instances of fires from residential
or commercial storage systems. I'm spe
than you design for can be backed up with a generator.
Larry Crutcher
Starlight Solar Power Systems
On Mar 13, 2020, at 6:09 PM, Jeff Clearwater
wrote:
Thanks All,
Mick and Tump - I'll look into the Victron - good suggestion - Thanks!
Chris - I'm not sure a transformer will buffer
battery at 100%. Protect the PS
with the appropriate AC surge or LV protection. With this setup your AC power
is always on with no brownouts or loss of power.
Larry Crutcher
Starlight Solar Power Systems
On Mar 13, 2020, at 12:02 PM, Jeff Clearwater
wrote:
Good Day Esteemed Wrenchers,
So
-PowerBond-112-Inch-15-5-Inch/dp/B002MWDI44
Larry Crutcher
Starlight Solar Power Systems
On Mar 9, 2020, at 11:07 AM, Ray wrote:
I 2nd Larry's experience. I've never seen any flex modules that have held up
for more than a few years. Complete degradation in our high a
long as you don’t
expect the longevity of a framed, glass module. Customers using them
occasionally as a portable module are experiencing long life.
Larry Crutcher
Starlight Solar Power Systems
On Mar 8, 2020, at 4:02 PM, Jay wrote:
Hi all,
Especially those that do RV,
Any recommendations
%7C2510416%2F2301910&a7=In%20Stock%20Only&n8744=1%20Pole&n11096=50%20VDC%2C48%20VDC
3A example:
https://www.alliedelec.com/product/te-connectivity/w58-xb1a4a-3/70199433/
Larry Crutcher
Starlight Solar Power Systems
On Feb 28, 2020, at 12:35 PM, drake.chamber...@redwoodalliance.org w
transfer to use in off grid power
systems.
Please reply off list if you need more info.
Larry Crutcher
Starlight Solar Power Systems
(928) 342-9103
sa...@starlightsolar.com
On Feb 23, 2020, at 7:40 PM, Mac Lewis wrote:
Hey wrenches,
What are you using for Lithium in the 100 kWh-200 kWh range
We have used Gigavac in some of our Li-ion EMS systems for many years with
hundreds in the field and no failures. GX11 good to 800Vdc.
https://www.gigavac.com/catalog/power-products/gx-series
Larry Crutcher
Starlight Solar Power Systems
On Nov 22, 2019, at 8:47 PM, Chris Sparadeo wrote
to you Howie.
Larry Crutcher
Starlight Solar Power Systems
On Sep 26, 2019, at 3:58 PM, Dave Angelini Offgrid Solar
wrote:
My 2 cents are each client is different and if they have been fine on that one
set of batteries then do what is in their interest. An inverter is easily
replaced. I
above 125 Vac. Control boards are not to pricy and
very easy to replace. Hope that helps.
Larry Crutcher
Starlight Solar Power Systems
On Sep 24, 2019, at 9:39 AM, Starlight Solar Power Systems
wrote:
Hi Dave,
I’m curious, can you describe the problem you had with a Magnum inverter and
charge rate to about 50% or
less, they work flawlessly.
Larry Crutcher
Starlight Solar Power Systems
On Sep 24, 2019, at 8:30 AM, Dave Angelini Offgrid Solar
wrote:
We ended up usine a 50 foot #14 extension cord and the drop got the 2000i to
play nice with the magnum. Outback and
fully charge them, for offgrid use, the advantages are huge. For people
making growing weeds, buy the best. Contact me off the list if you would
like more understanding about Li battery storage.
Larry Crutcher
Starlight Solar Power Systems
la...@starlightsolar.com
On Sep 6, 2019, at 9:32
internal BMS.
You can build a box and add a silicone type heater with a temp controller. I’ve
bought items like that on eBay for about $25. See photo.
Larry Crutcher
Starlight Solar Power Systems
On May 16, 2019, at 4:41 PM, jay wrote:
HI All,
I”m wondering if anyone has suggestions about how to
revent charge current when below freezing.
Larry Crutcher
Starlight Solar Power Systems
On May 3, 2019, at 12:45 PM, Howie Michaelson
wrote:
Hi Folks,
About to spec my first Lithium battery backup job. The client is not a heavy
user, but wants things done right more than being totally cost ef
, Starlight Solar Power Systems <la...@starlightsolar.com> wrote:Sorry Drake, I should read better…you said Concorde.
Larry
On Apr 30, 2019, at 12:42 PM, Starlight Solar Power Systems <la...@starlightsolar.com> wrote:Hi Drake,The way I wire them is to place them side by side and flip
Sorry Drake, I should read better…you said Concorde.
Larry
On Apr 30, 2019, at 12:42 PM, Starlight Solar Power Systems
wrote:
Hi Drake,
The way I wire them is to place them side by side and flip every other battery
180°. Then you can use a interconnect cable without tight bends. I attached
Hi Drake,The way I wire them is to place them side by side and flip every other battery 180°. Then you can use a interconnect cable without tight bends. I attached a diagram as it is easier to see than to describe.Larry CrutcherStarlight Solar Power Systems
untitled.pdf
Description: Adobe PDF docu
higher loads or a greater percentage
of capacity loss. I was just trying to give a more accurate consumption total
to compare voltage.
Larry Crutcher
Starlight Solar Power Systems
On Apr 19, 2019, at 4:14 PM, Glenn Burt wrote:
Hi Larry,
I am curious why you would use the 100Hr rate for this
Starlight Solar Power Systems
On Apr 19, 2019, at 10:27 AM, Mac Lewis wrote:
Hello Wrenches,
We recently inherited an Outback system that I've been keeping an eye on via
Optics. Its a dual stack 3648 VFXR, with about 4kW of PV with a single string
of EnergyCell 1100RE battery
e low and high
voltage disconnect, it may be a dangerous battery without external control. Did
you get that release form yet?
Just FYI about us, since 2013 we have designed and sold Li battery power
systems now numbering hundreds of customers.
Larry Crutcher
Starlight Solar Power Systems
O
William,
It seems this question needs to be addressed: What is the intended meaning of
“installed in one system” in 2014? If you have separate “systems”, they should
not be governed by 705.12. So, at what point does a “system” begin and end? PV
modules to the disconnect? ...to the load panel? .
protection opens.
We mostly sell Midnite and Blue Sky Energy controllers with some Outback in the
mix. No failures have been reported to us.
Larry Crutcher
Starlight Solar Power Systems
On Jan 7, 2019, at 7:46 AM, d...@foxfire-energy.com wrote:
I've been asked to trouble shoot a problem
Howie,
We have many hundreds of Li battery systems sold and installed. Never had any
failure of PV controllers including Outback due to charging Li-ion.
Larry Crutcher
Starlight Solar Power Systems
On Jan 7, 2019, at 11:23 AM, Howie Michaelson
wrote:
Hey Dan,
Are you saying that OB is
.
Larry Crutcher
Starlight Solar Power Systems
On Dec 20, 2018, at 6:05 PM, Jay wrote:
Hi all,
I was doing some research on the Chevy bolt, and found that it’s battery cost
about $145 per kWh in 2015.
All the batteries I can find for sale for offgrid small systems ( 10-100 kWh)
are in the
Let me confirm what William has shared about Deka/MK 8D AGM batteries; they
have a very high failure rate. We saw over 40% fail within 2-3 years of
installation. Deka would not own up to the problem and offered no compensation.
Fullriver has been the finest AGM we have ever sold. All DC models a
Thank you Hilton and Darryl. That explains what I’m seeing here in Yuma: A 90kW
installation that went slowly, and is now entirely, off line.
These are the linear alternator design. Any chance your friend will have
technical documents?
Larry
On Nov 24, 2018, at 11:37 AM, Hilton Dier wrote:
been recombined, these areas are
targeted for recombination. Slowing the growth of irreversible sulfation
results in retaining higher capacity and thus longer cycle life. Just my
opinion developed over the years it took me to acquire a gray beard.
Larry Crutcher
Starlight Solar Power Systems
On N
discounts to wrenches.
Thank you,
Larry Crutcher
Starlight Solar Power Systems
On Aug 30, 2018, at 10:37 AM, Marco Mangelsdorf wrote:
Aloha all,
I’m on the hunt for three-phase storage @ 277/480V.
Yes, Tesla has its Powerpack. But availability is questionable.
I’m open to suggestions
myths. Careful what you read.
Larry Crutcher
Starlight Solar Power Systems
On Aug 21, 2018, at 12:26 PM, Sindelar Solar wrote:
Yes, I just did. Ralph retired last year and I spoke with the new owner. In
short, little change - use 2% of capacity for amp threshold and set CEF to 98%
from
Starlight Solar Power Systems
On Aug 17, 2018, at 12:09 PM, Lou Russo wrote:
Hello All,
Does anybody have any insight in getting the SOC to report accurately on the
Outback FNDC when using batteries that have a minimal voltage curve? I have
several systems with LFP batteries that have both a
ything is field serviceable
and if the EMS does turn off, there are simple ways to continue using the
battery until it is repaired. Much happier customer.
You can contact me off the list or call if you would like further advise.
Thank you,
Larry Crutcher
Starlight Solar Power Systems
(928) 34
are simple ways to continue
using the battery until it is repaired. Much happier customer.
You can contact me off the list or call if you would like further advise.
Thank you,
Larry Crutcher
Starlight Solar Power Systems
(928) 342-9103
On Aug 16, 2018, at 2:51 PM, Jason Szumlanski
wrote
http://www.lifebluebattery.com/rv-boat-lithium-ion-batteries/index.html
Bluetooth communications with the EMS built in.
On Jun 7, 2018, at 11:56 AM, cwarfel wrote:
I am trying to redesign a couple hundred watt load off-grid system by first
focusing on the battery technology. The Li based
Steve,
Here is another similar installation. There is air space on top of and some
between the battery. Many of our installations have the AGM batteries
completely sealed in a box. 17 years of installing battery systems like this
and not one single problem.
Larry Crutcher
Starlight Solar
Sorry…to fast on reply…I have received the messages I sent.
Larry Crutcher
On May 11, 2018, at 10:35 AM, Starlight Solar Power Systems
wrote:
I have sent 4 replies and none are showing.
Larry
On May 11, 2018, at 10:32 AM, Mark Frye wrote:
Could have sworn there was a thread here
I have sent 4 replies and none are showing.
Larry
On May 11, 2018, at 10:32 AM, Mark Frye wrote:
Could have sworn there was a thread here about melted batteries, but it not
showing in my email client anymore.
___
List sponsored by Redwood Alliance
Starlight Solar Power Systems
On May 10, 2018, at 1:59 PM, Steve Higgins wrote:
Larry,
Do you have any pic's of them installed?
That would help a lot in getting an idea of how/why these failed.
I do have two questions for you...
Were there tie down straps over the tops of the batt
I agree….that is something we have never done. These batteries are same date
and both new when installed.
Larry
On May 10, 2018, at 3:49 PM, Rick Brown
wrote:
I’m inclined to agree with Maverick. Mixing old and new batteries is not
recommended. Differing internal resistance coupled with po
used?
Was it a bus system?
Absorb with End Amps was turned on?
Sent from my iPhone
On May 10, 2018, at 4:41 PM, Michael Morningstar mailto:mjmornings...@gmail.com>> wrote:
>
> One year old. Well looked after system.
> On May 10, 2018, at 1:42 PM, Starlight Solar Power Syste
. Fullriver would not allow anything towards replacement do to
the reporting date being grater than 24 months.
I would like to know has anyone else had a similar failure with Rolls or
Fullriver AGM batteries, specifically L16 size.
Thank you,
Larry Crutcher
Starlight Solar Power Systems
mmend cheap instead.
Larry Crutcher
Starlight Solar Power Systems
On May 4, 2018, at 10:07 AM, Kristopher Schmid wrote:
Greetings wrenches,
I have a client that is looking to buy some salvaged modules off of a building
that was near a fire. What kind of potential issues can you antic
Starlight Solar Power Systems
On Apr 23, 2018, at 11:33 AM, RE Ellison wrote:
I have a customer with a 20-year-old modified sine wave inverter that has been
no issue at all until recently when he arrived from New York City with his
Chevy bolt
Obviously the Bolt will not tolerate the modified sine
Crutcher
Starlight Solar Power Systems
On Mar 7, 2018, at 12:42 PM, Mac Lewis wrote:
Hello wrenches,
I have a client with an older Whisper 200, 1 kW wind turbine. We didn't
install this but have taken over the site maintenance since the original
installer left town. The site rec
Hey Chris,
Might be a long-shot but check with Frank at BZ Products. Rings a bell but
can’t think why.
Larry Crutcher
Starlight Solar Power Systems
On Feb 28, 2018, at 1:22 PM, ch...@oasismontana.com wrote:
Dear people:
I have a fellow looking for a supplier of LCBs for their PV pumping
a
bit too much,…”
Quote “…best to just isolate the battery bank if below 32-35F..."
As I mentioned, these features are already built into the Li EMS system of 2
brands that we sell and likely other brands. No need to reinvent it.
Larry Crutcher
Starlight Solar Power Systems
On Feb
know our product and educate the
customer. Too often, this does not happen.
Larry Crutcher
Starlight Solar Power Systems
On Feb 27, 2018, at 7:11 AM, drake.chamber...@redwoodalliance.org wrote:
Snow on the array could be a very big problem with the heater load, inverter
idle current and
inhibit controls that prevent charge current when a cell is below
freezing.
Larry Crutcher
Starlight Solar Power Systems
On Feb 26, 2018, at 12:09 PM, Darryl Thayer wrote:
Hi Daniel and Larry,
I have a LI-FePO system, Simpliphy 10 kWh it is on its third winter, the
batteries are
ith-Sensor-D/112145401355?hash=item1a1c63060b:m:mpDAMY9SK0sPRVsidEQ682w
<https://www.ebay.com/itm/Digital-STC-1000-All-Purpose-Temperature-Controller-Thermostat-With-Sensor-D/112145401355?hash=item1a1c63060b:m:mpDAMY9SK0sPRVsidEQ682w>
Larry Crutcher
Starlight Solar Power Systems
On Feb 26, 2018, at 9:56 AM, Daniel Youn
will use a battery like that on the other.
Besides, in a decade or so, will Li-ion battery cost make lead batteries a
relic?
IMO, lead is dead…or at least dying…slowly.
Larry Crutcher
Starlight Solar Power Systems
On Feb 20, 2018, at 9:02 AM, Kirpal wrote:
Larryyes those are big
be a catch. Do you have any
information about testing or a copy of their warranty?
Larry Crutcher
Starlight Solar Power Systems
On Feb 19, 2018, at 4:10 PM, Kirpal wrote:
Blue Planet - Lithium Iron Phosphate batteries are a good option for off grid
and work very well with the Outback
done either as they were just
fantasies to begin with.
Larry Crutcher
Starlight Solar Power Systems
On Jan 23, 2018, at 11:48 AM, jay wrote:
HI All,
I’ve had a large company want to do a project and they want me to invoice it as
follows. They said it had to do with knowing the cost of
issues.
Thank you,
Larry Crutcher
Starlight Solar Power Systems
(928) 342-9103
On Jan 18, 2018, at 9:18 AM, Drake wrote:
A Concorde AGM PVX 3050T recently failed in a bank of 8. Larry mentioned a
couple of brands experiencing problems. These batteries are 4 years old and
have been kept
I too would like to know the make and model of batteries that are loosing
capacity. In the past 5 years we have experienced abnormally high failures from
2 brands.
Larry
On Jan 15, 2018, at 2:00 PM, Jay wrote:
Can you tell us:
Battery make,model and size?
Jay
Peltz power.
On Jan 15, 2018
Starlight Solar Power Systems
On Nov 6, 2017, at 4:05 AM, gary easton wrote:
Is anyone stocking up on modules before the 15th when the first tariff
gets signed?
___
List sponsored by Redwood Alliance
List Address: RE-wrenches@lists.re-wrenches.org
ure.
Am I correct about these?
Allan
On 10/20/2017 3:58 PM, Starlight Solar Power Systems wrote:
> Look at the JLD 404. 500Vdc, 10kA
> see http://www.evwest.com/catalog/product_info.php?products_id=162
>
> Larry Crutcher
> Starlight Solar Power Systems
>
> On Oct 20, 2017, at
charge or whatever. For under $90 it has its place and covers the voltage range
you need.
Thank you,
Larry Crutcher
Starlight Solar Power Systems
(928) 342-9103
On Oct 20, 2017, at 3:38 PM, Sindelar Solar wrote:
Larry,
Thank you for the referral to this item. Unless I'm missing some
Look at the JLD 404. 500Vdc, 10kA
see http://www.evwest.com/catalog/product_info.php?products_id=162
Larry Crutcher
Starlight Solar Power Systems
On Oct 20, 2017, at 2:48 PM, Sindelar Solar wrote:
Wrenches,
I have an upcoming remote residential off grid upgrade job that uses one of the
How many eBay sellers know this?
Re-purposing - yes, with good understanding and extreme caution in the
application.
Larry Crutcher
Starlight Solar Power Systems
On Oct 19, 2017, at 2:05 PM, Drake wrote:
Hello Wrenches,
Here is feedback on the second life batteries from Morgan Hager, m
e are involved with, I’m not
so sure the manufacturers have provided the same level of QC.
Larry Crutcher
Starlight Solar Power Systems
On Oct 7, 2017, at 8:05 PM, Darryl Thayer wrote:
I have only limited experience with Lithium batteries. But in that
experience, a module of small cylindrical
If you are going to play without knowledge, never have these battery cells near
anything you are not willing to loose to fire. Worst case is you burn something
that you did not intend to. Might be something cheap or your home and all your
possessions or your eyes and skin. If that happens, don’t
-destructive testing method. Study the formation of dendrites.
This subject is too vast to discuss in an email, so I recommend that you study
much before you proceed. Many others have been where you are now and have paid
a very high price for assumed understanding.
Larry Crutcher
Starlight Solar Power
to 62 Tesla battery modules. Itâs programmable and
> has output contacts for PV solar controllers and other devices.
> See http://store.evtv.me/proddetail.php?prod=modulecontroller
>
> Larry Crutcher
> Starlight Solar Power Systems
>
>
> On Aug 24, 2017, at 8:28 AM, ja
://store.evtv.me/proddetail.php?prod=modulecontroller
Larry Crutcher
Starlight Solar Power Systems
On Aug 24, 2017, at 8:28 AM, jay wrote:
Does anyone know anything about Elithion BMS systems?
Or had experience with them?
Would be used for control on tesla salvage batteries, to control upper
Crutcher
Starlight Solar Power Systems
On Aug 17, 2017, at 6:51 AM, Mick Abraham wrote:
Hi, Wrenchies~
My client has an AC coupled battery based setup. The batteries are good ol'
lead floodies in pretty good health, the battery based inverter is Magnum
MS4448PAE, & the string in
uot;we go where powerlines don't"
>>> http://members.sti.net/offgridsolar/
>>> e-mail offgridso...@sti.net
>>> text 209 813 0060
>>
>>
>
___
List sponsored by Redwood Alliance
List
does.
Larry Crutcher
Starlight Solar Power Systems
On Aug 10, 2017, at 9:41 AM, Glenn Burt wrote:
Has anyone experience with Battle Born lithium batteries? Their price point is
better than others we have looked at.
From: Dave Angelini Offgrid Solar <mailto:offgridso...@sti.net>
Sent:
Hi Jay and Dave,
LiFeBlue battery has a wireless Bluetooth monitor that is connected to the BMS
in each battery. SoC, current, cycle life, voltage, health, battery faults and
more is provided on the free IOS or Android App. Up to 62kWh at 48 volts
available today.
http://www.lifebluebattery.co
Hey Drake,
Because of the very low cost of producing power by PV solar, I always recommend
a standard, high efficiency refrigerator. It doesn’t makes sense to by
speciality refrigerators that cost 2-4 times times the price of ‘off the shelf”
brands. Many brands have models that use about 1 kWh
85°….I wish…it’s 114° here right now. Unshaded pools are unusable for many
summer months, even at night, without a refrigeration system. But, in the
winter, they need solar gain to reduce heating bills. Not a good plan for a
permanent cover.
Larry
On Jun 26, 2017, at 2:49 PM, Jason Szumlanski
Daunting, an excellent description. Means intimidating, formidable,
disconcerting, unnerving, unsettling, dismaying; discouraging, disheartening,
and so on. I had to become Hazmat Certified to ship lithium ion batteries….so,
yes to all the synonyms.
49 CFR 173 regulates shipment and transport o
. I want to know if anyone else is
having issues with these and is the problem really fixed before I quote another
one.
Thank you,
Larry Crutcher
Starlight Solar Power Systems
(928) 342-9103
___
List sponsored by Redwood Alliance
List Address: RE
Hi Drake,
We have been using Gigavac for high current DC switching a few years now. They
also switch high voltage DC. Very reliable. See
http://www.gigavac.com/catalog/power-products
Larry Crutcher
Starlight Solar Power Systems
On Apr 12, 2017, at 8:45 AM, Drake wrote:
Hello Wrenches
I want to 2nd David’s recommendation for Fullriver. 6 years and many pallet
loads sold, only one failure covered by warranty. 7 year warranty when used in
RE systems. Best AGM battery we have ever sold.
Larry Crutcher
Starlight Solar Power Systems
On Mar 27, 2017, at 6:33 AM, Dave Palumbo
y can't be used in the off grid environment. If you can't use it,
why do they rate it at 2.4kWh? BTW, the Voltage vs.Energy chart on the spec
sheet does not match the first chart I posted."
Thank you,
Larry Crutcher
Starlight Solar Power Systems
(928) 342-9103
On Mar 8, 201
inverter might
just sweep and invert.
August
From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org
<mailto:re-wrenches-boun...@lists.re-wrenches.org>] On Behalf Of Starlight
Solar Power Systems
Sent: Thursday, February 23, 2017 3:14 PM
To: RE-wrenches
Subject: Re: [RE-wr
in the 350 to 400 v range.
August
From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org
<mailto:re-wrenches-boun...@lists.re-wrenches.org>] On Behalf Of Starlight
Solar Power Systems
Sent: Wednesday, February 22, 2017 11:17 AM
To: RE-wrenches
Subject: [RE-wrenches] Dischar
sure bugs me.
My uneducated guess is the inverter will be immediately damaged. My thought is
how would it limit the input current? Or, is there such an inverter available
that can do the job?
Any input is appreciated.
Larry Crutcher
Starlight Solar Power Systems
looking for a switching arrangement to do this without arcing since it will
be used a few times each week. Any have a recommendation?
Thank you,
Larry Crutcher
Starlight Solar Power Systems
___
List sponsored by Redwood Alliance
List Address: RE
Solar Power Systems
On Oct 14, 2016, at 9:42 AM, Chris Mason mailto:cometenergysyst...@gmail.com>> wrote:
I'm curious to see if anyone is finding Lithium battery systems available that
will be suitable for an Outback Radian based system. Let me know what is out
there please.
--
One other advantage, recombination caps wear out. We have had Water Miser caps
returned (during upgrade to AGM’s) that are over 10 years old. By washing in
baking soda and water, thoroughly rinsing, they continue working. Should last
decades.
Larry Crutcher
Starlight Solar Power Systems
On
please contact the sender and delete or destroy this message
and all copies.
On Thu, Oct 13, 2016 at 3:33 PM, Starlight Solar Power Systems
wrote:
Battery Wrenches,
The problem with recombination style caps is they require using a low absorb
voltage, about 2.35 to 2.4 Vpc. I am a big fan of
.
Larry Crutcher
Starlight Solar Power Systems
On Oct 13, 2016, at 11:02 AM, jay wrote:
while we are on the subject of recombining caps has anyone used the following.
http://www.sbsbattery.com/PDFs/Battery-Recombination-Plug.pdf
<http://www.sbsbattery.com/PDFs/Battery-Recombination-Plug.
Hey Drake,
I’ve been using a 334 for many years. I recently looked at the 381 because of
the wireless removable display. There have been many situations where the wire
I’m clamped onto puts the display in a position that I can’t easily read it.
Having a wireless display would be SO handy. Readi
I’m curious. If a critical load center is powered from an alternative source
and the main panel is not energized, won’t all neutral conductors still be
energized from the sub panel back feeding the main? Or is that OK?
Larry
On Sep 8, 2016, at 6:43 PM, Ray Walters wrote:
Hi Chris;
Its the
Solar Power Systems
On Sep 2, 2016, at 10:40 AM, Tom Duffy wrote:
Gary
A number of years ago I designed the back-up system for the Washington DC Metro
System communications in conjunction with Apollo Solar. After extensive testing
of both the Concorde and Full River brand batteries. We chose
Hey Gary,
We have used those in about 10 systems. Our oldest bank of 2V is about 5 years.
As with all FullRiver batteries, no one has had any trouble.
Thank you,
Larry Crutcher
Starlight Solar Power Systems
On Sep 1, 2016, at 8:08 PM, Gary Willett wrote:
Larry:
What is your experience
you,
Larry Crutcher
Starlight Solar Power Systems
(928) 342-9103
On Sep 1, 2016, at 6:19 PM, jay wrote:
HI Ray,
I second your opinion.
jay
peltz power
> On Sep 1, 2016, at 4:43 PM, Ray Walters <mailto:r...@solarray.com>> wrote:
>
> Hi Gary;
>
> I think it wou
Wrenches,
Is anyone setup as a dealer with Exeltech? I need a 22kW MX bi-phase system but
they only offer me retail pricing. Please contact off the list:
la...@starlightsolar.com
Thank you,
Larry Crutcher
Starlight Solar Power Systems
(928) 342-9103
Perhaps I should rephrase my question: Has anyone else been selling the PT-100?
If so, how many? Any failures?
Early on a tech told me that I’m the only one experiencing the failures.
Larry
On Jul 28, 2016, at 4:27 PM, Starlight Solar Power Systems
wrote:
Hello Battery Wrenches,
I have
Have you been here: http://www.luminousrenewable.com/whisper100.php
Thank you,
Larry Crutcher
Starlight Solar Power Systems
On Jul 29, 2016, at 11:34 AM, Dan Fink wrote:
Wrenches;
I was contacted by an individual in remote Alaska who is heavily invested in
Whisper 100s (the best turbine
Hello Battery Wrenches,
I have installed about 35 of the Magnum PT-100 charge controllers since
November 2015. I have had about 10 fail, another one just today. The problem we
have is the same every time: network communications fail which causes other
problems until you remove the network cable
-watt-high-surge-pure-sine-wave-inverter
that works wonders with all kinds of complex loads. Extremely low failures and
their customer service is excellent.
Thank you,
Larry Crutcher
Starlight Solar Power Systems
On Jul 28, 2016, at 10:21 AM, frenergy wrote:
Off-gridders,
I'v
Is anyone interested in building an off grid system in Blythe, CA?
Contact me off the list la...@starlightsolar.com
Thank you,
Larry
___
List sponsored by Redwood Alliance
List Address: RE-wrenches@lists.re-wrenches.org
Change listserver email addr
Be nice William ;-)
Hi Gary,
DC can not be transformed without converting it to AC first then back to DC
again. Probably not feasible to do while tracking the MMP.
Larry Crutcher
Starlight Solar Power Systems
On Jul 22, 2016, at 12:50 PM, William Miller wrote:
Gary:
I want one of those
them with
remanufactured units.
Bill, the typical failure is Voc of about 10 volts. However, the failure can be
intermittent. For this reason, any modules in the date period should be
replaced even though they appear to test OK.
Larry Crutcher
Starlight Solar Power Systems
On Jul 2, 2016, at
How about another Whisper? http://luminousrenewable.com/whisper200.php
I don’t know of much else in that size and price range.
Thank you,
Larry Crutcher
On May 6, 2016, at 11:41 AM, Jeremy Rodriguez wrote:
Hello
Does anyone have a recommended replacement turbine for a Whisper 100 or whisper
Aurora generators can be used in all off grid applications with full warranty.
http://www.auroragenerators.com/generators
Larry Crutcher
Starlight Solar Power Systems
On May 5, 2016, at 8:11 AM, Luke Christy wrote:
Hi Wrenches,
I have been following this thread with interest ever since Lena
prolonged periods or just
poor care overall.
Thanks for a bit more insight.
Bill
Feather River Solar Electric
Bill Battagin, Owner
4291 Nelson St.
Taylorsville, CA 95983
530.284.7849
CA Lic 874049
www.frenergy.net <http://www.frenergy.net/>
On 5/1/2016 9:54 AM, Starlight Sol
long term non-use. You can simply discharge the battery to 50% then turn off
the battery and walk away. When you return in 6-7 months, you will find it at
the same SoC as when you left. For long term seasonal storage, that is all I
recommend anymore.
Larry Crutcher
Starlight Solar Power Systems
I agree with Todd and Bob, leave the PV solar on, EQ off.
I also instruct my customers to reduce the absorb timer to 0.1 hours. Since the
battery is staying full, there is no need to spend time above cell gassing
point which will increase water loss.
Larry
On Apr 30, 2016, at 10:28 AM, RE E
1 - 100 of 489 matches