for
85kV? What it means if transformer is immersed in oil with regards of
calculation of required cl/crd distances?
Thank you for your support.
Best regards,
Bostjan
Boštjan Glavič
Vodja laboratorija, Laboratorij za elektroniko
Head of Laboratory, Laboratory of Electronic Engineering
Laborleiter
Dear Brian,
You cannot buy a prepared test report form with all national deviations. You
can only buy a basic IEC TRF on iec web page. TRFs are available free of charge
if your laboratory is a member of CB scheme. You can ask your certification
body for support.
Each certification body and
Hi Bill,
You can use MOV (VDR) primary to PE as long as you have reliable earth.
Reliable earth is considered for pluggable equipment type B or permanently
connected equipment. For pluggable equipment type A, you would need additional
earthing point, what is usually not acceptable for clients.
Dear experts,
What would be the limit of USB output? I know IEC 60950-1 requires only that
it complies with limited power source, but there might be some other
requirements to limit power from USB?
In particular, I am talking about power supply with USB connector. Can it go up
to 5Vd.c./3A?
Dear Julias,
I believe it is enough to measure pressure in one location only. So you can
save some money on calibration
We are using omega dataloger in every room. It can store data up to 1 month
without the problem and batteries are ok for 6 months.
See below link.
Best regards,
Bostjan
a fault when
connected to the USB port you propose.
Ted Eckert
Compliance Engineer
Microsoft Corporation
ted.eck...@microsoft.com
The opinions expressed are my own and do not necessarily reflect those of my
employer.
-Original Message-
From: Boštjan Glavič [mailto:bostjan.gla...@siq.si
Dear experts,
Does anyone know if it is required to use approved secondary cable on a direct
plug-in power supply, where output meets limited power source (also meets class
2 according to UL1310). Power supply is intended for US/CAN market and it
tested according to UL/CSA 60950-1.
There is
Dear safety experts,
During the abnormal tests in primary circuit, internal input fuse operates and
glass breaks. However, fuse is inside the tubing and broken glass does not
spread around.
Would you accept such construction?
Best regards,
Bostjan
SIQ
-
fuse. That's why I decided to
ask you experts for 2nd opinion.
UL has a PAG about this issue and does not allow it. However in the past many
such construction were acceptable also by UL.
Best regards,
Boštjan Glavič
Head of Laboratory, Laboratory of Electronic Engineering
www.siq.si
SIQ
Brian,
Are you sure? I have heard that CSA and UL are able to issue NRTL according to
3 rd Ed.
We are just in process for applying 2 projects according to 3rd Ed to CSA.
Best regards,
Bostjan
SIQ
On 12. avg. 2013, at 15:03, Kunde, Brian brian_ku...@lecotc.com wrote:
Regarding UL 61010-1 3rd
Dear Experts,
We are just approving one product for US/CAN market that comprises LED monitor.
Would you consider LED monitor as a critical component and ask for NRTL
approval? There is no back-light inverter inside and therefore no hazardous
voltages.
LED display panel itself is UL approved.
do you find approval of the panel useless?
Best regards,
Bostjan
From: Richard Nute [mailto:ri...@ieee.org]
Sent: Tuesday, August 13, 2013 6:57 PM
To: Boštjan Glavič
Cc: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Re: LED monitor
Hello Bostjan:
If the LED monitor runs on mains voltage
by; it is
not necessary to include other data.
Best regards,
Richard
On 8/13/2013 10:29 AM, Boštjan Glavič wrote:
Hello Richard,
Yes the unit is supplied by external power supply source with SELV, LPS output.
The complete unit will be NRTL certified. My question is whether we need to
consider
In addition to 5000m and 2000m we have also approved products up to 2500m,
3048m and 4000m.
Best regards,
Bostjan Glavic
SIQ
On 6. sep. 2013, at 03:12, IBM Ken
ibm...@gmail.commailto:ibm...@gmail.com wrote:
I've used a number of different altitudes beyond the 2000m default (scaling
based on
,Inc.Beijing Office
Tel:86-10-58203318
Cell:86-13810026747
-邮件原件-
发件人: Boštjan Glavič [mailto:bostjan.gla...@siq.si]
发送时间: 2013年9月6日 11:20
收件人: EMC-PSTC@LISTSERV.IEEE.ORG
主题: Re: [PSES] Safety and Altitude
In addition to 5000m and 2000m we have also approved products up to 2500m,
3048m and 4000m
considered as dead metal enclosure?
Best regards,
Bostjan
Boštjan Glavič
Safety and Electromagnetics
Laboratory of Electronic Engineering
Head of Laboratory
SIQ, Tržaška cesta 2
SI-1000 Ljubljana, Slovenia
T: + 386 (0)1 47 78 265
F: + 386 (0)1 47 78 444
E-Mail: bostjan.gla...@siq.simailto:bostjan.gla
Hi Brian,
Standard IEC 60950-1 only allows use of MOV or combination MOV + GDT in
primary circuit. No other surge protectors are allowed.
As you mentioned, manufacturers are mostly using T protection (2 MOVs and one
GDT).
Best regards,
Bostjan
On 9. sep. 2013, at 18:00, Cortland Richmond
Dear Zhang,
As fair as I know, there are many old twisted pair wirings around the world
without standardized cross-sectional are. Therefore they checked it and set
maximum limit from central office to 1.3A. However on the subscriber side you
will never get more than few 10mA (usually 20-40mA).
Dear experts,
I was yesterday speaking with one client who is quite desperate. They are
producing medical products which contain wifi modules. They have told me, that
FDA currently does not accept any such product if no additional testing on wifi
module inside the unit are performed. The
From IEC 62368-1 (FDIS):
Groups RG-1 and RG-2 according to IEC 62471 belong to exempt group-- no hazard
The different classes are defined in IEC 62471. Low power application of LEDs
are in the exempt group.
UV radiation from general purpose incandescent and fluorescent lamps, with
ordinary
Hi Kim,
What will be the PSU used for? Standard depends on the application. If the PSU
will be used to supply information technology equipment then standard EN
60950-1 is applicable. BS 1363 is used just to verify plug part.
I hope it helps.
Best regards,
Bostjan
On 27. jan. 2014, at 16:32,
our
metrology department made just circuits according to IEC 60990 which do pass
the calibration requirements. Output is directly attached to scope.
Easy and usable.
Best regards,
Bostjan
Boštjan Glavič
Vodja laboratorija, Laboratorij za elektroniko
Head of Laboratory, Laboratory of Electronic
Dear Experts,
Is anyone familiar if it is allowed to use a contactor instead of circuit
breaker in PV application to disconnect inverter from the grid?
NEC in Article 690 does not specify it precisely.
What standard needs to comply this contactor?
Best regards,
Boštjan Glavič
Safety
Dear experts,
Does anyone know if anti- islanding relay in power inverter also needs to
disconnect a neutral conductor of 3W system? I have looked in UL 1741 and
couldn't find any requirement.
Thank you for your support.
With best regards,
Bostjan
Boštjan Glavič
Vodja laboratorija
requirements from UL 1778?
Thank you for your support.
Boštjan Glavič
-
This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send your e-mail to
emc-p...@ieee.org
All
will be
generated from batteries.
Best regards,
Bostjan
Boštjan Glavič
Vodja laboratorija, Laboratorij za elektroniko
Head of Laboratory, Laboratory of Electronic Engineering
[SIQlogo60px]
www.siq.sihttp://www.siq.si/
SIQ Ljubljana, Trzaska c. 2, SI-1000 Ljubljana, Slovenia, VAT ID: SI23509678
t +386
Dear experts,
I am trying to figure out how to determine correct spacings for non-isolated
inverter. According UL1741 OVC IV needs to be considered for inverter. From
table 8.1 from UL840 I get a transients of 8,0kV for 450VDC input. Is that
correct?
Output of inverter is connected to AC grid
Dear Rich,
Thank you. DC input comes from solar cells therefore from outside. UL 1741
states that OVC IV needs to be used and for 120/240V it means 4000V. So what
transient should I use from DC side?
Why table 8.1 in UL840 also mentions dc input?
Best regards,
Bostjan
Boštjan Glavič
Vodja
Hello Mike,
There is a standard EN 50514 Audio, video and information technology equipment
- Routine electrical safety testing in Production in EU which describes
requirements for routine testing. This standard for example is used if your
product bears ENEC mark.
There are mention values of
projects and i think that some requirements are not really clear.
Best regards,
Bostjan
Boštjan Glavič
Vodja laboratorija, Laboratorij za elektroniko
Head of Laboratory, Laboratory of Electronic Engineering
[SIQlogo60px]
www.siq.sihttp://www.siq.si/
SIQ Ljubljana, Trzaska c. 2, SI-1000 Ljubljana
Doug,
I did, also many other documents like UL technical briefs. I have exact
technical questions. Maybe I prepare a new email and list some of them.
Best regards,
Bostjan
Boštjan Glavič
Vodja laboratorija, Laboratorij za elektroniko
Head of Laboratory, Laboratory of Electronic Engineering
Dear all,
Below are some tecnical questions about IEC 62368-1 I found during power supply
testing according to this standard. There are plenty of others, but let's
discuss these first.
Best regards,
Bostjan
1) Y2 capacitor across basic insulation.
According to the clause G.11 and tables G.8,
.
This is what I remember from my colleagues who used to test TVs. Unfortunately
we have no more audio devices to test, since they are mostly designed in far
east.
Best regards,
Bostjan
Best regards,
Bostjan
Boštjan Glavič
Vodja laboratorija, Laboratorij za elektroniko
Head of Laboratory
on a recording r.m.s.
ammeter, during a representativeperiod.
Boštjan Glavič
Vodja laboratorija, Laboratorij za elektroniko
Head of Laboratory, Laboratory of Electronic Engineering
[SIQlogo60px]
www.siq.sihttp://www.siq.si/
SIQ Ljubljana, Trzaska c. 2, SI-1000 Ljubljana, Slovenia, VAT ID: SI23509678
Dear experts,
We have an IT product intended for connection to OVC IV (6kV transients). Input
filter also comprises two IEC 61051-2 certified varistors (L to middle point, N
to middle point) and one GDT (middle point to PE).
Annex G of IEC 60950-1 is saying that we need to measure transient
Dear Sudhakar,
So what is the point being member of CB scheme if they do not accept results
from IECEE CB report? This is in contradiction to CB scheme idea which points
out one time testing. US national standard is also UL 60950-1 but they accept
IECEE report if national differences are
Dear experts,
Does anyone know where I can find spacing requirement for anti-islanding relay?
I need to know required distance when contact is open. UL1741 does not include
such requirement.
Do I need to simulate short accross the relay's contact during fault condition
testing?
Best regards,
Good point Brian. Also standard says portable cells and batteries. Does it
mean that no IEC 62133 approval is required if battery is installed in fixed
device, e.g. transmitter?
Best regards,
Bostjan
Boštjan Glavič
Vodja laboratorija, Laboratorij za elektroniko
Head of Laboratory, Laboratory
Dear Jim,
You probably mean near appliance inlet? I do not see a background for such
label. Special label is required for service engineer if you have more
connection to mains supply.
What kind of service activities are planed on the unit?
Best regards,
Bostjan
Boštjan Glavič
Vodja
Dear experts,
I have one question. One of our clients is generating high voltage DC bus out
of primary circuit without the insulation. This 800VDC circuit is therefore
considered as part of primary circuit. They are using Y2 capacitor between this
DC voltage and PE (accross basic insulation).
Dear Experts,
Does anyone know what standard should be followed for a power supply cord used
to supply outdoor IT equipment? I need requirements for EU, China and US.
I am not sure if normal cords approved to standard IEC 60227 and IEC 60245 can
be used.
Best regards,
Bostjan
Boštjan Glavič
Hi Ted,
Thank you. It will be permanently installed outdoor unit.
Best regards,
Bostjan
Boštjan Glavič
Vodja laboratorija, Laboratorij za elektroniko
Head of Laboratory, Laboratory of Electronic Engineering
[SIQlogo60px]
www.siq.sihttp://www.siq.si/
SIQ Ljubljana, Trzaska c. 2, SI-1000
on this subject.
Best regards,
Bostjan
Boštjan Glavič
Vodja laboratorija, Laboratorij za elektroniko
Head of Laboratory, Laboratory of Electronic Engineering
[SIQlogo60px]
www.siq.sihttp://www.siq.si/
SIQ Ljubljana, Trzaska c. 2, SI-1000 Ljubljana, Slovenia, VAT ID: SI23509678
t +386 (0)1 4778 265tel
,
Boštjan Glavič
On 21. jan. 2015, at 21:04, Richard Nute
ri...@ieee.orgmailto:ri...@ieee.org wrote:
Dear Boštjan:
Page 7 is mostly wrong. Comments in blue.
Best regards,
Rich
DC/DC converter isolation requirements
Functional insulation between the DC/DC converter’s
input
Dear Rich,
Thank you. So in reality no way to avoid abnormal testing, since on transformer
we always measure 42,4Vpk.
Best regards,
Bostjan
From: Richard Nute [mailto:ri...@ieee.org]
Sent: Thursday, January 15, 2015 1:52 AM
To: Boštjan Glavič; EMC-PSTC@LISTSERV.IEEE.ORG
Subject: RE: [PSES
conditions are required in
order to verify that output remains SELV.
http://archive.ericsson.net/service/internet/picov/get?DocNo=31/28701-FGB101378Lang=ENHighestFree=Y
Boštjan Glavič
On 20. jan. 2015, at 20:05, Scott Aldous
0220f70c299a-dmarc-requ...@ieee.orgmailto
Dear Brian,
I am afraid they are right. There are no requirements for VDR located after
bridge rectifier - same as for X capacitors.
Best regards,
Bostjan
-Original Message-
From: Brian Oconnell [mailto:oconne...@tamuracorp.com]
Sent: Monday, January 26, 2015 8:56 PM
To:
to avoid fault condition tests.
I am quite positive about scenario a) and c) but not sure about scenario b).
Thank you for your support.
Best regards,
Boštjan Glavič
-
This message is from the IEEE Product Safety Engineering Society
Yes, it has to be connected, add requirements in installation instructions.
Best regards,
Bostjan
Boštjan Glavič
Vodja laboratorija, Laboratorij za elektroniko
Head of Laboratory, Laboratory of Electronic Engineering
[SIQlogo60px]
www.siq.sihttp://www.siq.si/
SIQ Ljubljana, Trzaska c. 2, SI
Dear experts,
Is anyone familiar with construction of electronic backfeed protection in UPS?
When user or service engineer disconnects UPS terminal/connector from mains
supply, only electronic components / semiconductors are protecting the
user/service engineer from internal hazardous
Hi Chris,
For permanently connected equipment or pluggable equipment type B or pluggable
equipment type A with additional PE conductor for permanent connection you do
not need a GDT in series to varistor. You can directly connect varistor primary
to PE.
For pluggable equipment type A you
answered for China.
Do you know when hybrid TRF will be available?
Best regards,
Bostjan
From: Pete Perkins [mailto:peperkin...@cs.com]
Sent: Monday, April 20, 2015 2:08 AM
To: Boštjan Glavič; EMC-PSTC@LISTSERV.IEEE.ORG
Subject: RE: [PSES] IEC 62368-1
Bostjan, et al
Dear experts,
Does anyone know what is behind the requirement, that measured input current of
the unit can exceed the rated current by 10%? Where this 10% come from?
Best regards,
Bostjan
-
This message is from the IEEE
:24 AM
To: Boštjan Glavič
Cc: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Re: [PSES] input current rating
Hi Bostjan!
I had heard (and perhaps this is apocryphal) that the 10% was intended to allow
for manufacturing tolerances in the final product. I don't know how the number
was arrived at.
-Ken
On Sun
, Japan, Australia, Korea, Taiwan,
Argentina.
Thank you for your support.
Best regards,
Boštjan Glavič
Laboratory of Electronic Engineering
Head of Laboratory
SIQ Ljubljana, Tržaška cesta 2
SI-1000 Ljubljana, Slovenia
T: + 386 (0)1 47 78 265
F: + 386 (0)1 47 78 444
E-Mail: bostjan.gla
Glavič; EMC-PSTC@LISTSERV.IEEE.ORG
Subject: RE: IEC 62368-1
Dear Boštjan Glavič,
Chinese version of IEC 62368-1 is in draft, I guess the time to be a formal
Chinese standard is about one to two years.
Best Regards,
Tsing ZHANG
[tʃiːŋ ]
Chinese name : Zhang Guoqing
Product Safety Compliance
Dear Experts,
Do you know when this requirement will become mandatory in US/CAN? It is
intended to protect firemen.
Thank you for your support.
Best regards,
Boštjan Glavič
Laboratory of Electronic Engineering
Head of Laboratory
SIQ Ljubljana, Tržaška cesta 2
SI-1000 Ljubljana, Slovenia
T
560VDC
(marked on the label).
Thank you for your support.
Best regards,
Bostjan
Boštjan Glavič
Laboratory of Electronic Engineering
Head of Laboratory
SIQ Ljubljana, Tržaška cesta 2
SI-1000 Ljubljana, Slovenia
T: + 386 (0)1 47 78 265
F: + 386 (0)1 47 78 444
E-Mail: bostjan.gla...@siq.si
Hi Charlie,
I started this qestion on linked in some time ago. See below link. I hope you
can see it, otherwise you need to join linked-in.
Best regards,
Bostjan
https://www.linkedin.com/grp/post/1899348-195516492
From: Charlie Blackham [mailto:char...@sulisconsultants.com]
Sent: Friday,
Dear colleagues,
Is anyone familiar with 1,3ms surge test according to EN 61000-4-1. I am
looking for a test house in EU capable of performing this test. Peak voltage
is 735V (3phase unit).
Thank you for your support.
Best regards,
Bostjan
-
Hello Rich,
I understand your point.
Unit is DC/DC converter supplied from generator or windmill. There is a 3 phase
rectifier in front of the unit. Wind mild has rated phase voltage 230V
tolerances of -15%/+30% (e.g. 195,5-299V). For short period (at start) output
voltage can achieve 343V~
in place to ensure that this is reliably the case, etc. Again, the
requirements of the end product standard need to be taken into account and will
certainly influence your decision.
On Wed, Sep 9, 2015 at 4:03 AM, Boštjan Glavič
<bostjan.gla...@siq.si<mailto:bostjan.gla...@siq.
Dear all,
TC 69 is dealing with wireless charging for automotive use. See link below to
see an example how it works. There is also test for coins or other metal part
inserted between the receiver and transmitter.
https://www.youtube.com/watch?v=FBYEGhf3pbs
TC100 is dealing with
Ian,
I am afraid it is not so. I only know that IEC 62368-1 standard that will
replace IEC 60950-1 and IEC 60065 is accepting power supply certified to IEC
60065 or IEC 60950-1.
Maybe think if you are able to certify your product according to IEC 60950-1 or
maybe IEC 62368-1. Check IEC guide
know where the values from table 2D or 3B are comming from?
Thank you for your support.
Best regards,
Boštjan Glavič
Laboratory of Electronic Engineering
Head of Laboratory
SIQ Ljubljana
-
This message is from the IEEE Product
". What if the PCB
> trace cross-sectional area is greater than or equal to the cross-sectional
> area stated in table 31? Meeting Table 31 on PCB traces would result in very
> wide traces but it doesn't seem to be prohibited the way 62368 is worded.
>
> -Ken
>
>
>
Hi Scott,
Most of the manufacturers use one layer of thin sheet material between two
windings (one TIW and one normal enamel) just to avoid stress on insulation of
TIW. The problem is mechanical stress which could by some time damage the wire
insulation.
Two TIW in contact is not a problem.
ut the
need of additional protection?.
Thanks and regards,
Scott
On 22 Jan, 2016, at 2:24 am, Boštjan Glavič
<bostjan.gla...@siq.si<mailto:bostjan.gla...@siq.si>> wrote:
Hi Scott,
Most of the manufacturers use one layer of thin sheet material between two
windings (one TIW and
Dear experts,
Is anyone familiar with UL 1741? I am dealing with solar inverter for US
market. Solar inverter can operate in utility interactive mode (feeding the
grid) or in a standalone mode where only homeloads are supplied by inverter
(anti-islanding relays are open, due to problems with
16, 2016 9:28 AM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Re: [PSES] grounding of output of solar inverter
Reference articles 250 and 690 of the NEC (NFPA70). Canada and Mexico code
similar.
Brian
From: Boštjan Glavič [mailto:bostjan.gla...@siq.si]
Sent: Monday, February 15, 2016 9:05 PM
To: EMC
Dear experts,
I have a question with regard of requirements in UPS standard IEC 62040-1/A1
and UL 1778.
There are listed options how to waive short-time withstand current testing,
however these options in UL 1778 standard are different from one in IEC
62040-1. Client would like to fulfil
Dear Amund,
On short: You need to apply Table 2N on outer layers and in inner layers only
in case that temperature of the PCB exceeds 90°C and no thermal cycling test
performed.
If temperature of the PCB is <90°C, no thermal cycling test for cemented joints
required and you need apply only
Dear Experts,
I need your opinion about requirements of IEC 62368-1 standard. Standard
requires special limited short-circuit test on earthed accessible parts that
are earthed through PCB traces. However this test is only applicable if
protective current rating is below 25A according to clause
end-product."
>
> "NOTE This paragraph will be deleted in edition 3
> of this standard. It is added here to provide a
> smooth transition from the latest editions of IEC
> 60950-1 and IEC 60065 to this standard."
>
> Does this help?
>
>
> Rich
>
>
, 2016 9:12 PM
To: Boštjan Glavič <bostjan.gla...@siq.si>
Cc: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: RE: [PSES] earthing through PCB traces
Hi Boštjan:
> What is your view to this statement? How should
we fill
> the verdict in the test report in this case with
pass or
> N/A?
I would
Hi Ted,
It is not exactly true that if fire enclosure complies with IEC 60950-1 it will
also comply with IEC 62368-1, except if you use the statement from clause 4.1.1.
IEC 62368-1 has requirements also for top openings and side openings if fire
cone from PIS propagates through the opening,
What about IEC 62477-1: Safety requirements for power electronic converter
systems and equipment - Part 1: General
With kind regards,
Boštjan Glavič
Head of Laboratory
Safety and Electromagnetics
phone +386 1 4778 265
SIQ Ljubljana - Trzaska cesta 2 - 1000 Ljubljana - Slovenia - www.siq.si
Dear experts,
Can you help me with below item. I do not have experiences with NEC/CEC. Some
people told me that only ATMs are allowed to be connected to mains without the
plug, but i think this is strange requirement.
Customer has an IT equipment cabinet (IEC 60950-1) with built-in power
ITU L.1201, or ETSI 300 132-3-1, or ATIS-0600315.01.2015.
Best Regards,
ZHANG Guoqing
Huawei Technologies Duesseldorf GmbH
From: Boštjan Glavič [mailto:bostjan.gla...@siq.si]
Sent: 2016年9月21日 6:10
To: EMC-PSTC@LISTSERV.IEEE.ORG<mailto:EMC-PSTC@LISTSERV.IEEE.ORG>
Subject: [PSES] standard for
regards,
Bostjan
From: IBM Ken [mailto:ibm...@gmail.com]
Sent: Monday, September 5, 2016 6:52 PM
To: Boštjan Glavič <bostjan.gla...@siq.si>
Cc: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Re: [PSES] Connection to ac mains with split end line cord
Hi Bostjan!
NEC (NFPA 70) has an Article 645 which
The Other Brian
From: Boštjan Glavič [mailto:bostjan.gla...@siq.si]
Sent: Tuesday, September 20, 2016 12:29 AM
To: EMC-PSTC@LISTSERV.IEEE.ORG<mailto:EMC-PSTC@LISTSERV.IEEE.ORG>
Subject: Re: [PSES] Connection to ac mains with split end line cord
Hi Ken,
With short delay, Thank you.
So
Dear experts I again need your opinion on below issue.
Customer was asked for development of power supply which will be used to supply
a server in data centre. Input to power supply is defined as 750VDC.
Unfortunately no information is available how this DC supply voltage is
generated and
Hi Doug,
Thank you for your tip. I was already thinking of it, however I believe this is
allowed only if middle point of supply has reference to earth.
Best regards,
Bostjan
From: Doug Powell [mailto:doug...@gmail.com]
Sent: Wednesday, September 21, 2016 6:17 AM
To: Boštjan Glavič
: Wednesday, September 21, 2016 6:36 AM
To: Boštjan Glavič <bostjan.gla...@siq.si>
Cc: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Re: [PSES] standard for power suply for server room.
Hi Bostjan!
You might be able to use 60950 or (UL1012?) anyway; I know the scope says
"Mains or Battery powered
Measurement uncertainty depends on instruments used, method used etc. Each lab
has to do calculation of measurement uncertainty for particular method.
Measurement uncertainty becomes critical when results are close to the limit.
High uncertainty means you have more chance to be in »a grey area«
Dear Experts,
One customer is designing own connector for hot-plug application (power
supply). Question is how much longer shall be PE pin than supply pins. Which
standard shall be used for such connector?
For reference you can see similar connector on below link.
the stud arrangement provides at
least triple that contact area.
-Ken
On Wed, Nov 30, 2016 at 11:33 PM, Boštjan Glavič
<bostjan.gla...@siq.si<mailto:bostjan.gla...@siq.si>> wrote:
Hi Ken,
Thanks.
So on short, if table 3B brings requirement of 50mm2 conductor, you would
accept terminal
Dear experts
I hope there are some experts dealing with IEC 60950-1 standard. We have a
product that has rated input current 130A. Unit is intended for permanent
connection to mains and provide special terminals for 3 phases and bolt with
stud for PE connectio.
Question is how should we
Hi Ken,
Thanks.
So on short, if table 3B brings requirement of 50mm2 conductor, you would
accept terminal if it brings contact area of 150mm2?
Best regards,
Bostjan
From: IBM Ken [mailto:ibm...@gmail.com]
Sent: Thursday, December 1, 2016 5:24 AM
To: Boštjan Glavič <bostjan.gla...@siq.si&
Hi Doug,
I am familiar with expressions: operational voltage range and rated voltage
range. Operational voltage range is in fact rated voltage range with
tolerances. In your case 85-264V is operational voltage range, while unit is
rated 100-240V. tolerances on rated voltages in your case are
Hello Kannan,
As far as I know it was used in Russia, however they switch now to 48VDC. In
deed there are many different systems and somewhere they might still use 60VDC.
Maybe also in some other ex-Soviet Union countries.
Best regards,
Bostjan
From: Kannan Dhamodaran
Hi Chuck,
The answer could be found in Circular no. 2 from September and December 2016,
explaining power supplies used for servers or storage and all are covered
http://meity.gov.in/writereaddata/files/Circular%201of2016_Power%20Supplies.pdf
Hi John,
I believe IT system in Norway is still in use since they declared national
difference to new hazard based EN 62368-1 standard with below text:
Norway: After the 3rd paragraph the following is added: Due to the IT power
system used, capacitors are required to be rated for the
Hi Brian,
As far as I know in Norway they use IT system with phase-phase voltage 230V.
They have no Neutral.
Best regards
Bostjan
On 7. avg. 2017, at 21.08, Kunde, Brian
> wrote:
Greetings.
Sorry if this is a stupid question (I’ve asked
that majority of DIN rail
power supplies without PE connection bear class II symbol.
What is your view on this matter?
With kind regards,
Boštjan Glavič
Head of Laboratory
Safety and Electromagnetics
phone +386 1 4778 265
SIQ Ljubljana - Trzaska cesta 2 - 1000 Ljubljana - Slovenia -
www.siq.si
Dear experts,
Is anyone familiar if there exists laboratory with accreditation for hosedown
test according to UL 50E (type 4X)? The best would be in EU.
Thank you for your support.
Best regards
Bostjan
-
This message is from the
Dear experts
What is your understanding of requirement in IEC 62368-1 about insulation
system for transformer? On one part standard says that below 100°C no declared
insulation system is required and on other part is says that above class 100
EIS shall comply with IEC 60085.
So far it was very
, the last update to the LVD OJEU was to
add "take into account the new status of the 60335-2-9"
There are a number of updates in the pipeline and they are working with CENELEC.
Best Regards
Nick
From: Boštjan Glavič [mailto:bostjan.gla...@siq.si]
Sent: 11 September 2017 09:08
To: EMC-PS
Hello Ian,
EN 60065:2014 has a DoW 17.11.2017. This is in two months.
For this standard CENELEC and OJ show the same DoW.
Best regards,
Bostjan
From: McBurney, Ian [mailto:ian.mcbur...@allen-heath.com]
Sent: Monday, September 11, 2017 10:54 AM
To: Boštjan Glavič <bostjan.gla...@siq.si>
Dear all,
There was new EU official journey published on Sep 08 2017, however still DoW
20.06.2019 is mentioned for EN 62368-1. Is anyone familiar about it? It is very
important topic for customer who need to change certification for EN 60950-1
into EN 62368-1. Cenelec web page shows DoW as
1 - 100 of 152 matches
Mail list logo