[RE-wrenches] Xantrex MPPT 80 600 Not Showing Up in SCP

2020-04-16 Thread Jason Szumlanski
So the MPPT is in the middle and is passing through the XW signal just fine. The MPPT also has a red error light illuminated, but it is charging the battery (positive current measured via clamp meter). Any ideas? Thanks, Jason Szumlanski ___ List sponso

[RE-wrenches] SunPower Monitoring Setup

2020-03-16 Thread Jason Szumlanski
Any advice or direct help (contact me off-list) would be greatly appreciated. Jason Szumlanski Florida Solar Design Group ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & s

Re: [RE-wrenches] Disconnect spacing

2020-03-12 Thread Jason Szumlanski
s://mailtrack.io/trace/link/8f4b435fd24ee3593fa2399dacb78aa18022c8c1?url=http%3A%2F%2Fwww.frenergy.net&userId=1613865&signature=3b40f9d3d79780f0> > > On 3/11/2020 3:03 PM, Jason Szumlanski wrote: > > I'm meeting him tomorrow. He tells me it's too close but I can

Re: [RE-wrenches] Disconnect spacing

2020-03-11 Thread Jason Szumlanski
able to open, the handle needs to be accessible >> for operation, and NEC 110.26 working clearances need to be maintained. I >> suppose there may be manufacturer clearance requirements, but I haven't >> seen them for standard knife blade disconnects. >> >> Augus

Re: [RE-wrenches] Old & new Enphase communication issues

2020-03-10 Thread Jason Szumlanski
You can have both M series and IQ series in a "system" if you have an old Envoy and a new IQ Envoy. An Enlighten monitoring site can have multiple Envoys of different generations. As always, Envoys should be as electrically close as possible to the MIs. Jason Szumlanski Florida Solar De

[RE-wrenches] SunPower Invisimount Span Tables

2020-03-04 Thread Jason Szumlanski
h mount, 5 degree roof tilt (ASCE 7-10). Please contact me off-list if you able to help. Jason Szumlanski Florida Solar Design Group ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address

Re: [RE-wrenches] Solectria TL woes

2020-02-25 Thread Jason Szumlanski
-morning as a result. Usually the utilities here will resolve it if you demonstrate the voltage is high, even if it's not out of their acceptable range. Jason Szumlanski On Tue, Feb 25, 2020 at 3:16 PM Jerry Shafer wrote: > Andrew > What is the AC Voltage when this occurs, to much VA

Re: [RE-wrenches] High Power Split phase inverter/chargers

2020-02-23 Thread Jason Szumlanski
You should be able to go to 32kW with four Outback Radians. I agree, there are not enough 32-100kW split phase inverter system options. With LiPO batteries becoming popular, a high integrated charging capacity is desirable in larger battery capacity scenarios, especially if trying to maximize gener

Re: [RE-wrenches] Inverter Output Circuit OCPD Meltdown

2020-01-23 Thread Jason Szumlanski
v to go to a > 120 v circuit. Not good. > > August > > On Wed, Jan 22, 2020 at 2:58 PM Jason Szumlanski < > ja...@floridasolardesigngroup.com> wrote: > >> I discovered the issue I believe, so I thought I'd update all of you who >> gave me ideas on what to l

Re: [RE-wrenches] Inverter Output Circuit OCPD Meltdown

2020-01-22 Thread Jason Szumlanski
but once we started continuity testing and finding strange results, it became clear. Jason Szumlanski On Tue, Jan 21, 2020 at 12:10 PM Jason Szumlanski < ja...@floridasolardesigngroup.com> wrote: > (System installed by another contractor...) > > I have been tasked with assisting

Re: [RE-wrenches] Enphase Envoy - original version

2020-01-22 Thread Jason Szumlanski
rsion, but that is quite a bit more cost and work. Jason Szumlanski On Wed, Jan 22, 2020 at 10:47 AM Kirpal wrote: > Hi Wrenches. We have a customer whose Envoy stopped working. We are > looking for a used or new original envoy. Please contact me off list if > you have one that you

Re: [RE-wrenches] Inverter Output Circuit OCPD Meltdown

2020-01-21 Thread Jason Szumlanski
t; have no idea whether the breakers were faulty or what, but thought I'd just > mention it in case there is a pattern. > > Best, August > Luminalt > > > On Tue, Jan 21, 2020 at 9:10 AM Jason Szumlanski < > ja...@floridasolardesigngroup.com> wrote: > >> (S

Re: [RE-wrenches] Inverter Output Circuit OCPD Meltdown

2020-01-21 Thread Jason Szumlanski
ton breakers. I >> have no idea whether the breakers were faulty or what, but thought I'd just >> mention it in case there is a pattern. >> >> Best, August >> Luminalt >> >> >> On Tue, Jan 21, 2020 at 9:10 AM Jason Szumlanski < >> ja...@flor

Re: [RE-wrenches] NEC 2020 not available as a portable PDF?

2020-01-08 Thread Jason Szumlanski
We are going backwards in this world. Thanks for making us less productive, NFPA. #Greedy. On Wed, Jan 8, 2020 at 5:26 PM gary easton wrote: > It’s a subscription. The digital you pay for access each year. > > On Wed, Jan 8, 2020 at 5:20 PM Glenn Burt wrote: > >> It is true, I have both 2017 a

Re: [RE-wrenches] SMA connection box access

2019-12-04 Thread Jason Szumlanski
NTEX-1-x-3-4-PVC-Reducer-4FYK1 Regardless of the conduit type, you could also just pass through a j-box rather than splicing inside. The 3/4" KO should still be big enough for your #6 inverter output circuit. Jason Szumlanski On Tue, Dec 3, 2019 at 9:05 PM frenergy wrote: > Wrenchers, &

[RE-wrenches] Enphase Envoy and Ring Chime

2019-11-13 Thread Jason Szumlanski
Is anyone else aware of difficulties connecting an Envoy to a Wi-Fi network where there is a Chime extender installed? I have had repeated issues with the setup (trying to connect to the router, not the extender). Unplugging the chime results and success invariably. Jason Szumlanski

Re: [RE-wrenches] Maximum Devices on Combox

2019-11-01 Thread Jason Szumlanski
-mail offgridso...@sti.net > text 209 813 0060* > > On Fri, 1 Nov 2019 07:26:59 -0400, Jason Szumlanski < > ja...@floridasolardesigngroup.com> wrote: > > The Conext Combox manual states: > > Max. number of Xanbus > devices: Up to 20 (depending on the device type)

[RE-wrenches] Conext Inverter Grid Support Mode

2019-11-01 Thread Jason Szumlanski
power all the time rather than the generator power bypassing the inverters and powering the loads directly during battery charging. I told him it is not possible without using an external battery charger and eliminating the generator AC input to the inverter. I think I am correct on that, but

[RE-wrenches] Maximum Devices on Combox

2019-11-01 Thread Jason Szumlanski
The Conext Combox manual states: Max. number of Xanbus devices: Up to 20 (depending on the device type) Does anyone know what "(depending on the device type)" means? What are the actual limitations? Jason Szumlanski ___ List sponsored

Re: [RE-wrenches] Strategies for staged startup of appliances

2019-09-13 Thread Jason Szumlanski
Good Luck! > > *Dave Angelini Offgrid Solar > "we go where powerlines don't" > http://members.sti.net/offgridsolar/ <http://members.sti.net/offgridsolar/> > e-mail offgridso...@sti.net > text 209 813 0060* > > On Thu, 12 Sep 2019 17:39:13 -0400, Jason Szumlanski

Re: [RE-wrenches] Strategies for staged startup of appliances

2019-09-12 Thread Jason Szumlanski
ent it. The refrigerators and AC’s are on all > the time waiting for the thermostat to activate. And it’s not good to turn > a working fridge on/off especially is the compressor is running. > > Bigger loads, bigger inverters, bigger dollars. > > Jay > > > > On Sep 11, 2

Re: [RE-wrenches] Strategies for staged startup of appliances

2019-09-11 Thread Jason Szumlanski
all those motors (I forgot to mention well and pressure pumps also!) Jason On Wed, Sep 11, 2019 at 5:50 PM Michael Morningstar wrote: > Put the loads on contractors, control the contractors with adjustable time > delay relays. Stagger the timing. > > On Sep 11,

[RE-wrenches] Strategies for staged startup of appliances

2019-09-11 Thread Jason Szumlanski
It's going to be outdoors in Florida and they expect it to make 25-50 pounds of ice per day. I am finding it really hard to estimate energy use for this appliance. Any ideas (other than the obvious "don't do it" answer)? Jason Szumlan

[RE-wrenches] Supply Side Connections: Grounding

2019-09-07 Thread Jason Szumlanski
ctly to the existing grounding electrode, and do not run an EGC to the main service panel. - Some combination of the above. Can anyone point to a clear and concise 3-line diagram that explains the acceptable options? Hopefully something that and AHJ will consider, like an IAEI article or NEC Handb

Re: [RE-wrenches] Mission PVs

2019-08-21 Thread Jason Szumlanski
proven to be great panels for us, and we have 180 mph design wind speeds here. It's a solid product. *Jason Szumlanski* Principal Solar Designer | Florida Solar Design Group On Wed, Aug 21, 2019 at 1:33 PM Ryan Harkins wrote: > Bill, > > Sometimes we add some duct tape to the co

Re: [RE-wrenches] Enphase M-250 Source

2019-08-08 Thread Jason Szumlanski
os and spelling errors. > > -- Original message-- > *From: *Jason Szumlanski > *Date: *Thu, Aug 8, 2019 8:41 AM > *To: *RE-wrenches; > *Cc: * > *Subject:*[RE-wrenches] Enphase M-250 Source > > Does anyone have a source for discontinued M-series microinverters? I'm > start

[RE-wrenches] Enphase M-250 Source

2019-08-08 Thread Jason Szumlanski
odate add-ons to non-fully populated branch circuits to allow for cost effective add-ons. We're having a hard time fulfilling that promise due to lack of M250s out there. Jason Szumlanski Florida Solar Design Group ___ List sponsored by Redwood Alli

Re: [RE-wrenches] SolarEdge

2019-08-05 Thread Jason Szumlanski
ven the recent customer service and hardware issues I have heard about. Note: I own no ENPH stock. What am I thinking?!?! Jason Szumlanski Florida Solar Design Group On Mon, Aug 5, 2019 at 4:31 PM Kirpal wrote: > Hi FolksDoes anyone know how to reach SolarEdge support. We have >

Re: [RE-wrenches] To Bond or Not to Bond the Neutral to Ground

2019-07-25 Thread Jason Szumlanski
I think the answer is in 250.28(D)(2). A bonding jumper is required in each service disconnect (including the solar disconnect) bonding neutral to ground. Then you have to look to 250.64(D) for how to run your GEC. There are multiple ways to comply. Consider 250.64(D)(3): Think of a wiring enclos

Re: [RE-wrenches] Consolidating meters

2019-07-25 Thread Jason Szumlanski
In Florida the utility must offer a single point of service for a property or contiguous properties owned by a single entity, even if broken by a road or other easement. If the properties are not contiguous, the utility can require separate meters, but you'd have a hard time maintaining electrical

Re: [RE-wrenches] Large Off-Grid Residential System and ciculating currents

2019-07-25 Thread Jason Szumlanski
[mailto:re-wrenches-boun...@lists.re-wrenches.org] *On >> Behalf Of *Lou Russo >> *Sent:* Saturday, July 20, 2019 1:50 PM >> *To:* RE-wrenches >> *Subject:* Re: [RE-wrenches] Large Off-Grid Residential System >> >> >> >> Blue Ion 2.0 with Outback or SMA.

Re: [RE-wrenches] Enphase IQ combiner for M series microinverters

2019-07-22 Thread Jason Szumlanski
Envoy can just be plugged in nearby. I really like this approach but I don't want to run into a situation where I find out does not allow for this. On Thu, Jun 6, 2019, 2:34 PM Jason Szumlanski < ja...@floridasolardesigngroup.com> wrote: > Yes, correct. The M Series Envoy would be plu

[RE-wrenches] Large Off-Grid Residential System

2019-07-19 Thread Jason Szumlanski
loop, particularly on the battery side of things. Jason Szumlanski Florida Solar Design Group ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wre

Re: [RE-wrenches] Cutting rail

2019-06-18 Thread Jason Szumlanski
Milwaukee cordless deep cut band saw with lubricant wax, then use plastic end caps from the mfr to hide edges. It's not a cheap tool, but it doesn't take much abuse and it uses the same batts as our other tools. On Thu, Jun 13, 2019 at 11:20 PM frenergy wrote: > Fantastic response in part bec

Re: [RE-wrenches] Solar ready meter extension

2019-06-18 Thread Jason Szumlanski
Check with your utility. FPL, the biggest in our state, and the local Co-op both rejected this product (sadly). On Mon, Jun 17, 2019 at 2:54 PM Glenn Burt wrote: > The only one I am aware of is the ConnectDER. > > https://connectder.com/ >

Re: [RE-wrenches] Enphase IQ combiner for M series microinverters

2019-06-06 Thread Jason Szumlanski
like the M250’s. > > Chad Waits > President/Owner – Net Zero Solar > 101 W. 5th St., Tucson, AZ 85705 > Office: 520-207-4053 > Cell: 520-270-4873 > NABCEP Certified PV Installation Professional > > > > From: RE-wrenches on behalf > of Jason Szumlanski > Reply-

[RE-wrenches] Enphase IQ combiner for M series microinverters

2019-06-06 Thread Jason Szumlanski
listing or code reasons come to mind? Jason Szumlanski Florida Solar Design Group ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/

Re: [RE-wrenches] Schneider Configuration Tool

2019-05-23 Thread Jason Szumlanski
BMS manufacturer replaced them at no charge. Jason Szumlanski On Thu, May 23, 2019 at 5:55 PM Drake wrote: > Hello Wrenches, > > Does anyone know how to synchronize the DC voltage readings on Schneider > inverters using the configuration tool? I don't think that information

Re: [RE-wrenches] 225A Meter Main with Pass Through Lugs

2019-05-09 Thread Jason Szumlanski
I should note that if you are on NEC 2014 the 60 OCPD is not the correct figure to use in the 120% rule. It would be 125% of the Inverter Output Circuit rated current. It's probably a moot point in this case, but it is an important distinction. On Thu, May 9, 2019 at 3:06 PM Jason Szuml

Re: [RE-wrenches] 225A Meter Main with Pass Through Lugs

2019-05-09 Thread Jason Szumlanski
, which is becoming a pretty small system these days around here. I tell every home builder I see to avoid meter-main combos but they keep putting them in. Sadly our utility accepts NONE of the "solar ready" panels on the market. That's another snag we run into. Jason Szumlanski F

Re: [RE-wrenches] Enphase Envoy in PVC J-Box

2019-04-03 Thread Jason Szumlanski
age" is safe for them to do that. I hope I did not miss > your question. Chris > On 3/28/2019 12:55 PM, Jason Szumlanski wrote: > > When mounting an Envoy on the supplied DIN rail in a PVC box wired via PVC > conduit, is there any requirement to accompany the conductors with a groun

Re: [RE-wrenches] Enphase Envoy in PVC J-Box

2019-04-01 Thread Jason Szumlanski
nce is to use manufacturer's equipment instead of making > my own. I don't know if the AHJ would complain about non-listed equipment > in the case of making your own DAS center. The Envoy may need a button > pushed once in a while. I have asked customers to do this to save a trip. &g

Re: [RE-wrenches] Big AGM's and 24V Lithium batteries

2019-04-01 Thread Jason Szumlanski
I just replaced a 48V Lithionics battery with a 51V and I saw on their spec sheet that they do 12V and 24V as well. It seems like a very solid battery and BMS, but I have limited information on longevity.

Re: [RE-wrenches] Xantrex XW6048 (quad) blowing past setpoints

2019-04-01 Thread Jason Szumlanski
On Tue, Mar 26, 2019 at 9:00 AM Sandra Herrera > wrote: > > Jason, > > > > The Battery daily summary from the ComBox is information on one day at a > time, this is not part of the logs, and it should be available even if you > have 1 hour or charging. > > > &g

[RE-wrenches] Enphase Envoy in PVC J-Box

2019-03-28 Thread Jason Szumlanski
When mounting an Envoy on the supplied DIN rail in a PVC box wired via PVC conduit, is there any requirement to accompany the conductors with a ground wire? The envoy itself does not have a ground connection and the only exposed metallic part is the DIN rail. I'm thinking I need to mount a ground

Re: [RE-wrenches] Dc discos

2019-03-27 Thread Jason Szumlanski
I'm happy to see others are using that PVC j-box from Sceptre. No screws to rust out! We use that JBX### line of boxes extensively. Jason On Wed, Mar 27, 2019 at 11:59 AM Glenn Burt wrote: > Just a pic of our typical application of the IMO. > > -Glenn > > -Original Message- > From: R

Re: [RE-wrenches] Xantrex XW6048 (quad) blowing past setpoints

2019-03-27 Thread Jason Szumlanski
> resetting to factory defaults and then checking every setting. With the bad > firmware I was seeing the charge rate and voltage setpoints totally ignored > and saw battery go up to 67 volts! > > John Blittersdorf > > > On Mon, Mar 25, 2019 at 4:35 PM Jason Szumlanski <

Re: [RE-wrenches] Xantrex XW6048 (quad) blowing past setpoints

2019-03-27 Thread Jason Szumlanski
it should be available even if you > have 1 hour or charging. > > > > However, based on your discovery of different DC voltages from the > inverter, my recommendation is to calibrate them. > > > > Sandra > > > > > > *From:* RE-wrenches *On >

Re: [RE-wrenches] Xantrex XW6048 (quad) blowing past setpoints

2019-03-25 Thread Jason Szumlanski
e two > inverter battery voltage readings are the issue. Is there a way to > calibrate the XW battery voltage readings? I suppose I could disable the > chargers on these inverters, but that is not a permanent solution if that > is found to be the issue. > > Ja

Re: [RE-wrenches] Xantrex XW6048 (quad) blowing past setpoints

2019-03-25 Thread Jason Szumlanski
issue. Jason On Mon, Mar 25, 2019 at 5:05 PM Darryl Thayer wrote: > Is the chargingfrom the inverter orfrom a solar source? > > On Mon, Mar 25, 2019, 3:35 PM Jason Szumlanski < > ja...@floridasolardesigngroup.com> wrote: > >> I have four inverter/chargers (master and

Re: [RE-wrenches] Xantrex XW6048 (quad) blowing past setpoints

2019-03-25 Thread Jason Szumlanski
; > > > Sandra Herrera > > > > *From:* RE-wrenches *On > Behalf Of *Jason Szumlanski > *Sent:* Monday, March 25, 2019 1:36 PM > *To:* RE-wrenches > *Subject:* [RE-wrenches] Xantrex XW6048 (quad) blowing past setpoints > > > > [External email: Use ca

[RE-wrenches] Xantrex XW6048 (quad) blowing past setpoints

2019-03-25 Thread Jason Szumlanski
on individual units, so I know the settings are getting uploaded via the Combox. Jason Szumlanski ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://list

[RE-wrenches] Xantrex AGS wiring harness replacement

2019-03-25 Thread Jason Szumlanski
Does anyone know where I can get one? Jason ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Ar

Re: [RE-wrenches] Mystery racking-who knows what this is?

2019-03-12 Thread Jason Szumlanski
s a few similar items with hex drive screws. It looks awfully close to this: http://www.tripsolar.com/products_detail/productId=85.html You're probably looking at something that was imported as a complete kit, possibly with panels included. Are there any hints from the other equipment in the i

Re: [RE-wrenches] Crimper for Enphase field wireable connectors

2019-03-08 Thread Jason Szumlanski
ke we are being forced into a single source/brand tool. Jason Szumlanski On Fri, Mar 8, 2019 at 11:32 AM Nick Soleil wrote: > Hi Jason, > > > The Field Wireable Connectors Installation Guide specified the following > crimping tools for use with the connectors: Multi-Contact PV-

Re: [RE-wrenches] Crimper for Enphase field wireable connectors

2019-03-07 Thread Jason Szumlanski
isting to do so. Jason Szumlanski Principal Solar Designer Florida Solar Design Group On Wed, Mar 6, 2019, 9:16 PM Jay wrote: > Hi Jason > > Talk to Bryan at PV cables > > 707-923-3000 > > He’s got the Rennsteig tool for under $200 and the MFG tool for just under > $300

[RE-wrenches] Crimper for Enphase field wireable connectors

2019-03-06 Thread Jason Szumlanski
Is there a reasonably priced alternative to the Multi-Contact PV-CZM-##100 models? These are the only ones specified in the quick install guide. Obviously I don't want to violate the listing, but I also don't want to spend $500 for a tool for each truck. Jason Szumlanski Principal Sola

Re: [RE-wrenches] Corrugated Metal - Odd Seam Profile

2019-02-14 Thread Jason Szumlanski
Have you looked at the Proteabracket? Jason Szumlanski Principal Solar Designer Florida Solar Design Group On Thu, Feb 14, 2019, 12:05 PM Sam Haraldson Wrenches, > > I have encountered a corrugated metal seam profile that doesn't fit the > standard S-5! Corrubracket we typicall

Re: [RE-wrenches] Curved solar mounting

2019-02-09 Thread Jason Szumlanski
ic > > > On Thu, Feb 7, 2019 at 8:06 AM Jason Szumlanski < > ja...@floridasolardesigngroup.com> wrote: > >> Hi all, >> >> I'm looking for some ideas for attaching modules to a curved carport >> system. I attached a concept drawing. I'm pret

Re: [RE-wrenches] Curved solar mounting

2019-02-08 Thread Jason Szumlanski
lications. I'm not > certain that the shared rail can accommodate the slight different in angle > between module rows due to the curve, but it might be worth checking out if > you haven't already: > > https://unirac.com/sunframe/ > > August &

[RE-wrenches] Curved solar mounting

2019-02-07 Thread Jason Szumlanski
olution for the structure. Thanks! Jason Szumlanski Florida Solar Design Group ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-w

Re: [RE-wrenches] Equipment ideas for very large residential PV and battery backup

2019-01-09 Thread Jason Szumlanski
consumer demand for batteries is high... until they see the price and understand the limitations, that is. Jason Szumlanski Florida Solar Design Group On Tue, Jan 8, 2019 at 3:49 PM August Goers wrote: > Hi Wrenches, > > We have a new potential client who wants a 60 kW PV system and

Re: [RE-wrenches] Bi-Facial or transparent modules

2019-01-03 Thread Jason Szumlanski
I'm curious about this, too. I'm looking for something that accepts MLPE bolted to the frame and has a good wind rating. Jason Szumlanski Florida Solar Design Group On Thu, Jan 3, 2019 at 2:19 AM Wayne Irwin wrote: > Does anyone have a source for bi-facial or double glass

[RE-wrenches] Enphase IQ6PLUS

2018-12-10 Thread Jason Szumlanski
If you are aware of any suppliers with these in stock, please let me know privately. I need 27 of them. Jason Szumlanski ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & sett

[RE-wrenches] Fronius Warranty Policy

2018-09-21 Thread Jason Szumlanski
at the returned unit is a "no-fault replacement" and get charged for shipping and fees. I'm hoping that someone has been in this position and can help me decide what risk to take. Ultimately I can't keep going back over and over losing money on a system I didn't install in t

Re: [RE-wrenches] Raised up ground mounts

2018-09-20 Thread Jason Szumlanski
pricey. > > Good luck! > > > On Thu, Sep 20, 2018 at 4:55 AM, Jason Szumlanski < > ja...@floridasolardesigngroup.com> wrote: > >> Any suggestions for ground mount racks where panels need to have the >> leading edge 6-8 feet above grade (due to flood level requir

[RE-wrenches] Raised up ground mounts

2018-09-20 Thread Jason Szumlanski
reasonable since it won't have a dual function like a carport or shade structure. Jason Szumlanski Florida Solar Design Group ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address &

[RE-wrenches] Lithionics Batteries

2018-08-16 Thread Jason Szumlanski
hould I consider another option? It's about 110aH @ 51V x 8 batteries, total of about 44 kWh rated capacity. Jason Szumlanski ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address

Re: [RE-wrenches] Bi-Directional / Netmetering question

2018-08-16 Thread Jason Szumlanski
t;> >> >> Sunny Regards, >> Kirpal Khalsa >> Oregon LRT#25 >> NABCEP Certified PV Installation Professional >> Oregon Solarworks LLC >> www.oregonsolarworks.com >> 541-299-0402 >> >> On Wed, Aug 15, 2018 at 4:01 PM, Jason Szumlanski

[RE-wrenches] Bi-Directional / Netmetering question

2018-08-15 Thread Jason Szumlanski
oed to start and the initial billing period readings show DEL exceeded REC by 400 kWh, which matches what was billed (net usage of positive 400 kWh). Jason Szumlanski ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Cha

Re: [RE-wrenches] Microinverter Fault Trips Branch Circuit Breaker

2018-07-05 Thread Jason Szumlanski
lar.com > www.facebook.com/mdelectricandsolar > > > On Jul 3, 2018, at 12:45 PM, Jason Szumlanski < > ja...@floridasolardesigngroup.com> wrote: > > This is not a knock on microinverters, but information to potentially help > save the next guy a bunch of time... This is no

[RE-wrenches] Microinverter Fault Trips Branch Circuit Breaker

2018-07-03 Thread Jason Szumlanski
ther than a straight-up wiring fault. Jason Szumlanski ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.o

Re: [RE-wrenches] grounding on metal roofs

2018-07-03 Thread Jason Szumlanski
rage metal roofing manufacturers to get 2703 listing (haha - right). Side note: I don't see AHJ's worrying about overhead service conductors potentially energizing a metal roof. I've seen some pretty shaky rusted out weatherhead pipes and downed poles in storms with overhead conductors

Re: [RE-wrenches] Painting anodized rails?

2018-06-11 Thread Jason Szumlanski
We have been painting mill finish aluminum flashings for one large repeat customer, and I can tell you that it doesn't look great. I strongly question the long-term efficacy of this practice. But the customer is always right... so we do it despite our protests. I would refuse for a one-off job. I o

Re: [RE-wrenches] Looking for insulated #6 bare standoff

2018-04-21 Thread Jason Szumlanski
s reviewers and inspectors to approve our request! Jason Szumlanski Florida Solar Design Group On Sat, Apr 21, 2018 at 12:41 PM, Dana wrote: > Hey Ray, > > I completely agree with you. I had an inspector in CO that was know in the > early days of solar among the manufacturers as that SOB in C

[RE-wrenches] Alternative to Enphase Raw Q Cable

2018-01-25 Thread Jason Szumlanski
My supplier can't seem to get their hands on this bare cable, which I see as pretty essential/helpful to an efficient installation for Enphase's IQ system. The tech brief notes that the Type DG cable is based on the Type TC-ER construction. There is 12/2 flat TC-ER cable available out there, but it

Re: [RE-wrenches] MIXING ENPHASE M-2XX / IQ6 MICROS & ENVOY / IQ-ENVOY ON SAME AC COMBINER LOAD CENTER

2017-11-29 Thread Jason Szumlanski
t;https://mailtrack.io/trace/link/5fc48423e6c27d599cc32923131f73d02876a93c?url=http%3A%2F%2Fow.ly%2FHbVS3&userId=1613865&signature=02e06bbb7674409c> > > > > > NABCEP Certified Solar PV Installer #03262011-300 > > California C10 Licensed Electrician #986315 > > T

Re: [RE-wrenches] MIXING ENPHASE M-2XX / IQ6 MICROS & ENVOY / IQ-ENVOY ON SAME AC COMBINER LOAD CENTER

2017-11-28 Thread Jason Szumlanski
IQ systems are not showing any issues yet. Jason Szumlanski On Mon, Nov 27, 2017 at 8:27 PM, Gary Willett wrote: >ESTEEMED WRENCHES: >I'm in the process of engineering a project to add 16 new Enphase IQ6 >micros to an existing 48 Enphase M215-IG system that has be

Re: [RE-wrenches] Off grid in Florida

2017-11-03 Thread Jason Szumlanski
uld not let her live her life. Her problem was that she didn't make her house livable with a suitable alternative source of power and water. That's what is illegal in Florida. Jason Szumlanski Florida Solar Design Group <https://mailtrack.io/trace/link/491250ad7050a46fc3ae4e0974d

Re: [RE-wrenches] Array Mock-up Software (Jason Szumlanski)

2017-10-30 Thread Jason Szumlanski
DJI Phantom 4 Pro Drone Deploy Flight Data Recording and Processing Sketchup Post-Processing The Drone Deploy processing is expensive and time-consuming, so it's only suitable for larger projects with a healthy budget or opportunity. I don't think the technology is really there yet for our purpos

Re: [RE-wrenches] Array Mock-up Software

2017-10-28 Thread Jason Szumlanski
equipment go, and in many cases, fit before they arrive on site. > > -Glenn > > -Original Message- > From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On > Behalf Of Jason Szumlanski > Sent: Thursday, October 26, 2017 5:45 PM > To: RE-wrenches >

Re: [RE-wrenches] Array Mock-up Software

2017-10-26 Thread Jason Szumlanski
-up as part of the proposal. > > Glenn > > -Original Message- > From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On > Behalf Of Jason Szumlanski > Sent: Thursday, October 26, 2017 9:22 AM > To: RE-wrenches > Subject: Re: [RE-wrenches] Array Mock-u

Re: [RE-wrenches] Array Mock-up Software

2017-10-26 Thread Jason Szumlanski
have received this message in error, any use > or distribution is prohibited. Please notify me immediately by reply e-mail > and delete this message from your computer system. Thank you. > > > > From: RE-wrenches on behalf > of Jason Szumlanski > Sent: Thursday,

Re: [RE-wrenches] Array Mock-up Software

2017-10-26 Thread Jason Szumlanski
Glenn, How are you dealing with the new inferior imagery from Digital Globe now that Sketchup's contract with Google for imagery is dead? In my area, it's totally unusable. I'm having to pull in imagery from other sources and scale it, which is not as accurate as the Add Location feature in Sketch

Re: [RE-wrenches] Array Mock-up Software

2017-10-25 Thread Jason Szumlanski
here are too many nuances to sizing roofs, dealing with setbacks and obstructions, and dealing with skew in aerial imagery. A single person dedicated to this task seems much more plausible. Jason Szumlanski On Wed, Oct 25, 2017 at 1:32 PM, Chad Waits wrote: > Wrenches, > > Wondering

Re: [RE-wrenches] Enphase and Smart? phone

2017-10-16 Thread Jason Szumlanski
ilt-in Wi-Fi. So in short, the Installer Toolkit is light years better, but it isn't 100% necessary. If you want Wi-Fi you need the Installer Toolkit. Jason Szumlanski On Mon, Oct 16, 2017 at 2:38 PM, Nick Soleil wrote: > Hi Bill, > > > Give me a call and we can discuss. I

Re: [RE-wrenches] Hurricanes Forces

2017-09-17 Thread Jason Szumlanski
or turbulence created by the nearby trees or the structure > itself in very high winds. We like to model wind loading as a simple > vector force, when we all know the reality is extremely dynamic. > > Ray Walters > > Remote Solar > > On 9/16/17 8:15 AM, Jason Szumlanski wrote

Re: [RE-wrenches] Hurricane damage to solar arrays

2017-09-16 Thread Jason Szumlanski
rricane damage to solar arrays > > What was the pressure rating for the modules that got sucked off the > racks? Also, is it possible that flying debris caused some of the random > location module failures? > > Ray Walters > > Remote Solar > > On 9/14/17 1:53 P

Re: [RE-wrenches] Hurricanes Forces

2017-09-16 Thread Jason Szumlanski
I generally agree on all points. I'd love to use three rails on all systems, but there is an economic factor, and as Tom mentions, a third rail doesn't necessarily stop glass being sucked out or a tree landing on the array. At what point do we cease over-engineering the mounting structure and the m

Re: [RE-wrenches] Hurricane damage to solar arrays

2017-09-15 Thread Jason Szumlanski
that got sucked off the > racks? Also, is it possible that flying debris caused some of the random > location module failures? > > Ray Walters > > Remote Solar > > On 9/14/17 1:53 PM, Jason Szumlanski wrote: > > More early anecdotal data... > > We are finding N

Re: [RE-wrenches] Hurricane damage to solar arrays

2017-09-14 Thread Jason Szumlanski
. Maybe there are enough monitored systems with historical data > now to see the effects, if any. > > Brian Teitelbaum > AEE Solar > > On Wed, Sep 13, 2017 at 3:18 PM, Jason Szumlanski floridasolardesigngroup.com> wrote: > >> I'm based in Fort Myers and we cov

Re: [RE-wrenches] Hurricane damage to solar arrays

2017-09-13 Thread Jason Szumlanski
out values are pretty high. It looks like the attachment points into the roof are not going to be the failure point in the systems in Florida, but there is a LOT of work to be done still. It's going to be a very interesting few months ahead! ​Jason Szumlanski Florida Solar Design Group​ ​ On

Re: [RE-wrenches] TPO Roofing

2017-08-31 Thread Jason Szumlanski
August, While compatible, I mentioned in another recent thread that Geocel 4500 lacks testing to ASTM standards. If you have an AHJ that cares about that kind of stuff, you might want to pass it by them first. Geocel 2300 and 3300 do meet ASTM standards per the manufacturer. Jason Szumlanski

Re: [RE-wrenches] TPO Roofing

2017-08-31 Thread Jason Szumlanski
If you can identify the brand, maybe try Anchor Products. We use their hardware on TPO. We screw down the attachments (they also make a non-penetrating version) and the roofer comes in behind to seal the patch. It's a breeze. Jason Szumlanski Florida Solar Design Group On Thu, Aug 31, 20

Re: [RE-wrenches] AC Coupled Enphase

2017-08-29 Thread Jason Szumlanski
losed condition (shorted). This would preclude their use in a situation where opening the circuit is the preferred failure mode. Maybe someone with some more knowledge in this area can chime in on whether SSRs are a good idea in this scenario. Jason Szumlanski On Mon, Aug 28, 2017 at 10:19 PM, Nick S

[RE-wrenches] Enphase Installer Toolkit Broken on Android #Scanning #Bug

2017-08-11 Thread Jason Szumlanski
lkit on a Microsoft Surface Pro? ​Jason Szumlanski​ ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.o

Re: [RE-wrenches] Enphase installer compensation M-190's discontinued

2017-07-06 Thread Jason Szumlanski
Correction - I think it started at 15 years with labor included. I don't see how they can renege on that now. In fact, they had a power guarantee, too. They would reimburse people for lost energy as a result of warranty issues. Jason On Thu, Jul 6, 2017 at 3:02 PM, Jason Szumlanski

Re: [RE-wrenches] Enphase installer compensation M-190's discontinued

2017-07-06 Thread Jason Szumlanski
This seems odd. I thought they had a 25 year warranty originally with labor compensation, then went to 15 year at some point with no labor compensation. We have lots of M190s out there that were sold with labor coverage, so this would be important to know for certain. Jason On Thu, Jul 6, 2017

Re: [RE-wrenches] Solar over a Pool

2017-06-26 Thread Jason Szumlanski
idea. Jason Szumlanski ​​ FL State Certified Contractor License: CVC56956 On Sun, Jun 25, 2017 at 7:42 AM, Tom Lane wrote: > Solar over a pool of any type electric or solar pool collectors , IS A BAD > IDEA , as it will significantly drop the length of the swimming season as >

Re: [RE-wrenches] concrete roof tile install

2017-06-24 Thread Jason Szumlanski
. That's why we wanted to use Geocel 4500. Jason Szumlanski Florida Solar Design Group On Thu, Jun 22, 2017 at 5:11 PM, James Rudolph wrote: > Aloha Jay, > When the application fits the QuickMount product line is always the way to > go. We have also had success on curved tile with h