Re: [RE-wrenches] Known residential/commercial fires from LI batteries

2020-04-13 Thread Starlight Solar Power Systems
me to name a brand, just study the product you use…for everyones good. Larry Crutcher Starlight Solar Power Systems On Apr 9, 2020, at 4:07 PM, Bruce Leininger wrote: Hi. I was wondering if there are any known instances of fires from residential or commercial storage systems. I'm specifically

Re: [RE-wrenches] Brown-Out Prone Opportunity Charging

2020-03-16 Thread Starlight Solar Power Systems
than you design for can be backed up with a generator. Larry Crutcher Starlight Solar Power Systems On Mar 13, 2020, at 6:09 PM, Jeff Clearwater wrote: Thanks All, Mick and Tump - I'll look into the Victron - good suggestion - Thanks! Chris - I'm not sure a transformer will buffer the spikes

Re: [RE-wrenches] Brown-Out Prone Opportunity Charging

2020-03-13 Thread Starlight Solar Power Systems
the battery at 100%. Protect the PS with the appropriate AC surge or LV protection. With this setup your AC power is always on with no brownouts or loss of power. Larry Crutcher Starlight Solar Power Systems On Mar 13, 2020, at 12:02 PM, Jeff Clearwater wrote: Good Day Esteemed Wrenchers, So

Re: [RE-wrenches] Semi flexible modules

2020-03-09 Thread Starlight Solar Power Systems
-PowerBond-112-Inch-15-5-Inch/dp/B002MWDI44 Larry Crutcher Starlight Solar Power Systems On Mar 9, 2020, at 11:07 AM, Ray wrote: I 2nd Larry's experience. I've never seen any flex modules that have held up for more than a few years. Complete degradation in our high altitude UV

Re: [RE-wrenches] Semi flexible modules

2020-03-09 Thread Starlight Solar Power Systems
as long as you don’t expect the longevity of a framed, glass module. Customers using them occasionally as a portable module are experiencing long life. Larry Crutcher Starlight Solar Power Systems On Mar 8, 2020, at 4:02 PM, Jay wrote: Hi all, Especially those that do RV, Any recommendations

Re: [RE-wrenches] 48 VDC Control fusing

2020-02-28 Thread Starlight Solar Power Systems
%7C2510416%2F2301910=In%20Stock%20Only=1%20Pole=50%20VDC%2C48%20VDC 3A example: https://www.alliedelec.com/product/te-connectivity/w58-xb1a4a-3/70199433/ Larry Crutcher Starlight Solar Power Systems On Feb 28, 2020, at 12:35 PM, drake.chamber...@redwoodalliance.org wrote: Hello Wrenches

Re: [RE-wrenches] Large Lithium 100 kWh-200kWh

2020-02-24 Thread Starlight Solar Power Systems
that will transfer to use in off grid power systems. Please reply off list if you need more info. Larry Crutcher Starlight Solar Power Systems (928) 342-9103 sa...@starlightsolar.com On Feb 23, 2020, at 7:40 PM, Mac Lewis wrote: Hey wrenches, What are you using for Lithium in the 100 kWh-200 kWh range

Re: [RE-wrenches] 600V DC contactor

2019-11-23 Thread Starlight Solar Power Systems
We have used Gigavac in some of our Li-ion EMS systems for many years with hundreds in the field and no failures. GX11 good to 800Vdc. https://www.gigavac.com/catalog/power-products/gx-series Larry Crutcher Starlight Solar Power Systems On Nov 22, 2019, at 8:47 PM, Chris Sparadeo wrote

Re: [RE-wrenches] 24 volt LiFePO4 Battery options

2019-09-27 Thread Starlight Solar Power Systems
to you Howie. Larry Crutcher Starlight Solar Power Systems On Sep 26, 2019, at 3:58 PM, Dave Angelini Offgrid Solar wrote: My 2 cents are each client is different and if they have been fine on that one set of batteries then do what is in their interest. An inverter is easily replaced. I

Re: [RE-wrenches] Honda EU2000i output V adjustment - Magnum Energy

2019-09-24 Thread Starlight Solar Power Systems
above 125 Vac. Control boards are not to pricy and very easy to replace. Hope that helps. Larry Crutcher Starlight Solar Power Systems On Sep 24, 2019, at 9:39 AM, Starlight Solar Power Systems wrote: Hi Dave, I’m curious, can you describe the problem you had with a Magnum inverter

Re: [RE-wrenches] Honda EU2000i output V adjustment - Magnum Energy

2019-09-24 Thread Starlight Solar Power Systems
the charge rate to about 50% or less, they work flawlessly. Larry Crutcher Starlight Solar Power Systems On Sep 24, 2019, at 8:30 AM, Dave Angelini Offgrid Solar wrote: We ended up usine a 50 foot #14 extension cord and the drop got the 2000i to play nice with the magnum. Outback

Re: [RE-wrenches] Large off-grid inverter/storage

2019-09-06 Thread Starlight Solar Power Systems
to fully charge them, for offgrid use, the advantages are huge. For people making growing weeds, buy the best. Contact me off the list if you would like more understanding about Li battery storage. Larry Crutcher Starlight Solar Power Systems la...@starlightsolar.com On Sep 6, 2019, at 9:32

Re: [RE-wrenches] heating lithium in cold weather

2019-05-17 Thread Starlight Solar Power Systems
by the internal BMS. You can build a box and add a silicone type heater with a temp controller. I’ve bought items like that on eBay for about $25. See photo. Larry Crutcher Starlight Solar Power Systems On May 16, 2019, at 4:41 PM, jay wrote: HI All, I”m wondering if anyone has suggestions about how

Re: [RE-wrenches] Lithium Batteries - Li-ion battery warning

2019-05-03 Thread Starlight Solar Power Systems
revent charge current when below freezing. Larry Crutcher Starlight Solar Power Systems On May 3, 2019, at 12:45 PM, Howie Michaelson wrote: Hi Folks, About to spec my first Lithium battery backup job. The client is not a heavy user, but wants things done right more than being totally cost ef

Re: [RE-wrenches] Bus bar battery jumpers

2019-04-30 Thread Starlight Solar Power Systems
, Starlight Solar Power Systems <la...@starlightsolar.com> wrote:Sorry Drake, I should read better…you said Concorde. Larry On Apr 30, 2019, at 12:42 PM, Starlight Solar Power Systems <la...@starlightsolar.com> wrote:Hi Drake,The way I wire them is to place them side by side and flip

Re: [RE-wrenches] Bus bar battery jumpers

2019-04-30 Thread Starlight Solar Power Systems
Sorry Drake, I should read better…you said Concorde. Larry On Apr 30, 2019, at 12:42 PM, Starlight Solar Power Systems wrote: Hi Drake, The way I wire them is to place them side by side and flip every other battery 180°. Then you can use a interconnect cable without tight bends. I attached

Re: [RE-wrenches] Bus bar battery jumpers

2019-04-30 Thread Starlight Solar Power Systems
Hi Drake,The way I wire them is to place them side by side and flip every other battery 180°. Then you can use a interconnect cable without tight bends. I attached a diagram as it is easier to see than to describe.Larry CrutcherStarlight Solar Power Systems untitled.pdf Description: Adobe PDF

Re: [RE-wrenches] Operating Voltages Outback RE High Capacity Battery

2019-04-22 Thread Starlight Solar Power Systems
higher loads or a greater percentage of capacity loss. I was just trying to give a more accurate consumption total to compare voltage. Larry Crutcher Starlight Solar Power Systems On Apr 19, 2019, at 4:14 PM, Glenn Burt wrote: Hi Larry, I am curious why you would use the 100Hr rate

Re: [RE-wrenches] Operating Voltages Outback RE High Capacity Battery

2019-04-19 Thread Starlight Solar Power Systems
Starlight Solar Power Systems On Apr 19, 2019, at 10:27 AM, Mac Lewis wrote: Hello Wrenches, We recently inherited an Outback system that I've been keeping an eye on via Optics. Its a dual stack 3648 VFXR, with about 4kW of PV with a single string of EnergyCell 1100RE battery bank

Re: [RE-wrenches] DKD Lithium Batteries

2019-03-04 Thread Starlight Solar Power Systems
and high voltage disconnect, it may be a dangerous battery without external control. Did you get that release form yet? Just FYI about us, since 2013 we have designed and sold Li battery power systems now numbering hundreds of customers. Larry Crutcher Starlight Solar Power Systems On Mar

Re: [RE-wrenches] Multiple inverters

2019-02-27 Thread Starlight Solar Power Systems
William, It seems this question needs to be addressed: What is the intended meaning of “installed in one system” in 2014? If you have separate “systems”, they should not be governed by 705.12. So, at what point does a “system” begin and end? PV modules to the disconnect? ...to the load panel?

Re: [RE-wrenches] LiFePo4 vs BOS

2019-01-08 Thread Starlight Solar Power Systems
protection opens. We mostly sell Midnite and Blue Sky Energy controllers with some Outback in the mix. No failures have been reported to us. Larry Crutcher Starlight Solar Power Systems On Jan 7, 2019, at 7:46 AM, d...@foxfire-energy.com wrote: I've been asked to trouble shoot a problem

Re: [RE-wrenches] LiFePo4 vs BOS

2019-01-07 Thread Starlight Solar Power Systems
Howie, We have many hundreds of Li battery systems sold and installed. Never had any failure of PV controllers including Outback due to charging Li-ion. Larry Crutcher Starlight Solar Power Systems On Jan 7, 2019, at 11:23 AM, Howie Michaelson wrote: Hey Dan, Are you saying that OB

Re: [RE-wrenches] Lithium battery cost

2018-12-21 Thread Starlight Solar Power Systems
. Larry Crutcher Starlight Solar Power Systems On Dec 20, 2018, at 6:05 PM, Jay wrote: Hi all, I was doing some research on the Chevy bolt, and found that it’s battery cost about $145 per kWh in 2015. All the batteries I can find for sale for offgrid small systems ( 10-100 kWh

Re: [RE-wrenches] FullRiver battery question

2018-11-29 Thread Starlight Solar Power Systems
Let me confirm what William has shared about Deka/MK 8D AGM batteries; they have a very high failure rate. We saw over 40% fail within 2-3 years of installation. Deka would not own up to the problem and offered no compensation. Fullriver has been the finest AGM we have ever sold. All DC models

Re: [RE-wrenches] Infinia Stirling linear alternators generators

2018-11-24 Thread Starlight Solar Power Systems
Thank you Hilton and Darryl. That explains what I’m seeing here in Yuma: A 90kW installation that went slowly, and is now entirely, off line. These are the linear alternator design. Any chance your friend will have technical documents? Larry On Nov 24, 2018, at 11:37 AM, Hilton Dier

Re: [RE-wrenches] Batt Cap AGM...equalizing AGM

2018-11-23 Thread Starlight Solar Power Systems
recombined, these areas are targeted for recombination. Slowing the growth of irreversible sulfation results in retaining higher capacity and thus longer cycle life. Just my opinion developed over the years it took me to acquire a gray beard. Larry Crutcher Starlight Solar Power Systems On Nov 22

Re: [RE-wrenches] SOC and LFP batteries and TriMetric

2018-08-21 Thread Starlight Solar Power Systems
myths. Careful what you read. Larry Crutcher Starlight Solar Power Systems On Aug 21, 2018, at 12:26 PM, Sindelar Solar wrote: Yes, I just did. Ralph retired last year and I spoke with the new owner. In short, little change - use 2% of capacity for amp threshold and set CEF to 98% from

Re: [RE-wrenches] SOC, FNDC, and LFP batteries

2018-08-18 Thread Starlight Solar Power Systems
Starlight Solar Power Systems On Aug 17, 2018, at 12:09 PM, Lou Russo wrote: Hello All, Does anybody have any insight in getting the SOC to report accurately on the Outback FNDC when using batteries that have a minimal voltage curve? I have several systems with LFP batteries that have both

Re: [RE-wrenches] Lithionics Batteries

2018-08-16 Thread Starlight Solar Power Systems
ything is field serviceable and if the EMS does turn off, there are simple ways to continue using the battery until it is repaired. Much happier customer. You can contact me off the list or call if you would like further advise. Thank you, Larry Crutcher Starlight Solar Power Systems (928) 34

Re: [RE-wrenches] Lithionics Batteries

2018-08-16 Thread Starlight Solar Power Systems
, there are simple ways to continue using the battery until it is repaired. Much happier customer. You can contact me off the list or call if you would like further advise. Thank you, Larry Crutcher Starlight Solar Power Systems (928) 342-9103 On Aug 16, 2018, at 2:51 PM, Jason Szumlanski wrote

Re: [RE-wrenches] Small system lithium or equivalent battery technology

2018-06-07 Thread Starlight Solar Power Systems
http://www.lifebluebattery.com/rv-boat-lithium-ion-batteries/index.html Bluetooth communications with the EMS built in. On Jun 7, 2018, at 11:56 AM, cwarfel wrote: I am trying to redesign a couple hundred watt load off-grid system by first focusing on the battery technology. The Li

Re: [RE-wrenches] Fullriver Battery meltdown

2018-05-11 Thread Starlight Solar Power Systems
Steve, Here is another similar installation. There is air space on top of and some between the battery. Many of our installations have the AGM batteries completely sealed in a box. 17 years of installing battery systems like this and not one single problem. Larry Crutcher Starlight Solar

Re: [RE-wrenches] Disappearing Thread

2018-05-11 Thread Starlight Solar Power Systems
Sorry…to fast on reply…I have received the messages I sent. Larry Crutcher On May 11, 2018, at 10:35 AM, Starlight Solar Power Systems <la...@starlightsolar.com> wrote: I have sent 4 replies and none are showing. Larry On May 11, 2018, at 10:32 AM, Mark Frye <ma...@berkeley

Re: [RE-wrenches] Disappearing Thread

2018-05-11 Thread Starlight Solar Power Systems
I have sent 4 replies and none are showing. Larry On May 11, 2018, at 10:32 AM, Mark Frye wrote: Could have sworn there was a thread here about melted batteries, but it not showing in my email client anymore. ___ List

Re: [RE-wrenches] Fullriver Battery meltdown

2018-05-11 Thread Starlight Solar Power Systems
Starlight Solar Power Systems On May 10, 2018, at 1:59 PM, Steve Higgins <st...@surrette.com> wrote: Larry, Do you have any pic's of them installed? That would help a lot in getting an idea of how/why these failed. I do have two questions for you... Were there tie down strap

Re: [RE-wrenches] Fullriver Battery meltdown

2018-05-11 Thread Starlight Solar Power Systems
I agree….that is something we have never done. These batteries are same date and both new when installed. Larry On May 10, 2018, at 3:49 PM, Rick Brown wrote: I’m inclined to agree with Maverick. Mixing old and new batteries is not recommended.

Re: [RE-wrenches] Fullriver Battery meltdown

2018-05-11 Thread Starlight Solar Power Systems
towards replacement >> do to the reporting date being grater than 24 months. >> >> I would like to know has anyone else had a similar failure with Rolls or >> Fullriver AGM batteries, specifically L16 size. >> >> Thank you, >> >> Larry Crutc

[RE-wrenches] Fullriver Battery meltdown

2018-05-10 Thread Starlight Solar Power Systems
. Fullriver would not allow anything towards replacement do to the reporting date being grater than 24 months. I would like to know has anyone else had a similar failure with Rolls or Fullriver AGM batteries, specifically L16 size. Thank you, Larry Crutcher Starlight Solar Power Systems

Re: [RE-wrenches] Fire damage

2018-05-04 Thread Starlight Solar Power Systems
mmend cheap instead. Larry Crutcher Starlight Solar Power Systems On May 4, 2018, at 10:07 AM, Kristopher Schmid <sol...@legacysolar.com> wrote: Greetings wrenches, I have a client that is looking to buy some salvaged modules off of a building that was near a fire. What kind of poten

Re: [RE-wrenches] Chevy Bolt

2018-04-23 Thread Starlight Solar Power Systems
Starlight Solar Power Systems On Apr 23, 2018, at 11:33 AM, RE Ellison <reelli...@gmail.com> wrote: I have a customer with a 20-year-old modified sine wave inverter that has been no issue at all until recently when he arrived from New York City with his Chevy bolt Obviously th

Re: [RE-wrenches] Stuck in a furl

2018-03-07 Thread Starlight Solar Power Systems
Crutcher Starlight Solar Power Systems On Mar 7, 2018, at 12:42 PM, Mac Lewis <maclew...@gmail.com> wrote: Hello wrenches, I have a client with an older Whisper 200, 1 kW wind turbine. We didn't install this but have taken over the site maintenance since the original installer lef

Re: [RE-wrenches] Pump LCBs

2018-02-28 Thread Starlight Solar Power Systems
Hey Chris, Might be a long-shot but check with Frank at BZ Products. Rings a bell but can’t think why. Larry Crutcher Starlight Solar Power Systems On Feb 28, 2018, at 1:22 PM, ch...@oasismontana.com wrote: Dear people: I have a fellow looking for a supplier of LCBs for their PV pumping

Re: [RE-wrenches] heating a lithium battery bank

2018-02-28 Thread Starlight Solar Power Systems
t too much,…” Quote “…best to just isolate the battery bank if below 32-35F..." As I mentioned, these features are already built into the Li EMS system of 2 brands that we sell and likely other brands. No need to reinvent it. Larry Crutcher Starlight Solar Power Systems On Feb 28, 2

Re: [RE-wrenches] heating a lithium battery bank

2018-02-27 Thread Starlight Solar Power Systems
to know our product and educate the customer. Too often, this does not happen. Larry Crutcher Starlight Solar Power Systems On Feb 27, 2018, at 7:11 AM, drake.chamber...@redwoodalliance.org wrote: Snow on the array could be a very big problem with the heater load, inverter idle current

Re: [RE-wrenches] heating a lithium battery bank; Danger of charging frozen

2018-02-26 Thread Starlight Solar Power Systems
inhibit controls that prevent charge current when a cell is below freezing. Larry Crutcher Starlight Solar Power Systems On Feb 26, 2018, at 12:09 PM, Darryl Thayer <darylsol...@gmail.com> wrote: Hi Daniel and Larry, I have a LI-FePO system, Simpliphy 10 kWh it is on its third

Re: [RE-wrenches] heating a lithium battery bank

2018-02-26 Thread Starlight Solar Power Systems
ith-Sensor-D/112145401355?hash=item1a1c63060b:m:mpDAMY9SK0sPRVsidEQ682w <https://www.ebay.com/itm/Digital-STC-1000-All-Purpose-Temperature-Controller-Thermostat-With-Sensor-D/112145401355?hash=item1a1c63060b:m:mpDAMY9SK0sPRVsidEQ682w> Larry Crutcher Starlight Solar Power Systems On Feb 26, 2018, at 9:56 AM, Daniel Yo

Re: [RE-wrenches] Li+ Systems Puerto Rico

2018-02-20 Thread Starlight Solar Power Systems
will use a battery like that on the other. Besides, in a decade or so, will Li-ion battery cost make lead batteries a relic? IMO, lead is dead…or at least dying…slowly. Larry Crutcher Starlight Solar Power Systems On Feb 20, 2018, at 9:02 AM, Kirpal <solarwo...@gmail.com> wrote:

Re: [RE-wrenches] Li+ Systems Puerto Rico

2018-02-19 Thread Starlight Solar Power Systems
be a catch. Do you have any information about testing or a copy of their warranty? Larry Crutcher Starlight Solar Power Systems On Feb 19, 2018, at 4:10 PM, Kirpal <solarwo...@gmail.com> wrote: Blue Planet - Lithium Iron Phosphate batteries are a good option for off grid and wor

Re: [RE-wrenches] has anyone ever had this happen?

2018-01-23 Thread Starlight Solar Power Systems
done either as they were just fantasies to begin with. Larry Crutcher Starlight Solar Power Systems On Jan 23, 2018, at 11:48 AM, jay <jay.pe...@gmail.com> wrote: HI All, I’ve had a large company want to do a project and they want me to invoice it as follows. They said it had

[RE-wrenches] Concorde Lifeline Battery failures

2018-01-19 Thread Starlight Solar Power Systems
issues. Thank you, Larry Crutcher Starlight Solar Power Systems (928) 342-9103 On Jan 18, 2018, at 9:18 AM, Drake <drake.chamber...@redwoodalliance.org> wrote: A Concorde AGM PVX 3050T recently failed in a bank of 8. Larry mentioned a couple of brands experiencing problems. These bat

Re: [RE-wrenches] Off grid DC Loads: DC Converter

2018-01-16 Thread Starlight Solar Power Systems
I too would like to know the make and model of batteries that are loosing capacity. In the past 5 years we have experienced abnormally high failures from 2 brands. Larry On Jan 15, 2018, at 2:00 PM, Jay wrote: Can you tell us: Battery make,model and size? Jay Peltz

Re: [RE-wrenches] Tariff

2017-11-06 Thread Starlight Solar Power Systems
Starlight Solar Power Systems On Nov 6, 2017, at 4:05 AM, gary easton <g...@arp-solar.com> wrote: Is anyone stocking up on modules before the 15th when the first tariff gets signed? ___ List sponsored by Redwood Alliance List Address: RE-wr

Re: [RE-wrenches] System Monitor for HV Off Grid System? JLD 404

2017-10-20 Thread Starlight Solar Power Systems
shunt, but I'm not sure. Am I correct about these? Allan On 10/20/2017 3:58 PM, Starlight Solar Power Systems wrote: > Look at the JLD 404. 500Vdc, 10kA > see http://www.evwest.com/catalog/product_info.php?products_id=162 > > Larry Crutcher > Starlight Solar Power Systems > >

Re: [RE-wrenches] System Monitor for HV Off Grid System?

2017-10-20 Thread Starlight Solar Power Systems
to charge or whatever. For under $90 it has its place and covers the voltage range you need. Thank you, Larry Crutcher Starlight Solar Power Systems (928) 342-9103 On Oct 20, 2017, at 3:38 PM, Sindelar Solar <al...@sindelarsolar.com> wrote: Larry, Thank you for the referral to this item.

Re: [RE-wrenches] System Monitor for HV Off Grid System?

2017-10-20 Thread Starlight Solar Power Systems
Look at the JLD 404. 500Vdc, 10kA see http://www.evwest.com/catalog/product_info.php?products_id=162 Larry Crutcher Starlight Solar Power Systems On Oct 20, 2017, at 2:48 PM, Sindelar Solar <al...@sindelarsolar.com> wrote: Wrenches, I have an upcoming remote residential off grid u

Re: [RE-wrenches] Second Life Batteries

2017-10-19 Thread Starlight Solar Power Systems
many eBay sellers know this? Re-purposing - yes, with good understanding and extreme caution in the application. Larry Crutcher Starlight Solar Power Systems On Oct 19, 2017, at 2:05 PM, Drake <drake.chamber...@redwoodalliance.org> wrote: Hello Wrenches, Here is feedback on the

Re: [RE-wrenches] lithium battereis

2017-10-12 Thread Starlight Solar Power Systems
et we are involved with, I’m not so sure the manufacturers have provided the same level of QC. Larry Crutcher Starlight Solar Power Systems On Oct 7, 2017, at 8:05 PM, Darryl Thayer <darylsol...@gmail.com> wrote: I have only limited experience with Lithium batteries. But in that experienc

Re: [RE-wrenches] Second Life Batteries

2017-10-05 Thread Starlight Solar Power Systems
If you are going to play without knowledge, never have these battery cells near anything you are not willing to loose to fire. Worst case is you burn something that you did not intend to. Might be something cheap or your home and all your possessions or your eyes and skin. If that happens,

Re: [RE-wrenches] Second Life Batteries

2017-10-05 Thread Starlight Solar Power Systems
-destructive testing method. Study the formation of dendrites. This subject is too vast to discuss in an email, so I recommend that you study much before you proceed. Many others have been where you are now and have paid a very high price for assumed understanding. Larry Crutcher Starlight Solar Power

Re: [RE-wrenches] Elithion BMS

2017-08-25 Thread Starlight Solar Power Systems
and can monitor up to 62 Tesla battery modules. It’s programmable and > has output contacts for PV solar controllers and other devices. > See http://store.evtv.me/proddetail.php?prod=modulecontroller > > Larry Crutcher > Starlight Solar Power Systems > > > On Aug 24, 2017,

Re: [RE-wrenches] Elithion BMS

2017-08-24 Thread Starlight Solar Power Systems
://store.evtv.me/proddetail.php?prod=modulecontroller Larry Crutcher Starlight Solar Power Systems On Aug 24, 2017, at 8:28 AM, jay <jay.pe...@gmail.com> wrote: Does anyone know anything about Elithion BMS systems? Or had experience with them? Would be used for control on tesla s

Re: [RE-wrenches] "DC current Injection": Whazzat?

2017-08-17 Thread Starlight Solar Power Systems
Crutcher Starlight Solar Power Systems On Aug 17, 2017, at 6:51 AM, Mick Abraham <m...@abrahamsolar.com> wrote: Hi, Wrenchies~ My client has an AC coupled battery based setup. The batteries are good ol' lead floodies in pretty good health, the battery based inverter is Magnum MS4

Re: [RE-wrenches] SimpliPhi Power PHI3.4 Smart -Tech Batteries

2017-08-10 Thread Starlight Solar Power Systems
> ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-arc

Re: [RE-wrenches] SimpliPhi Power PHI3.4 Smart -Tech Batteries and LifeBlue

2017-08-10 Thread Starlight Solar Power Systems
does. Larry Crutcher Starlight Solar Power Systems On Aug 10, 2017, at 9:41 AM, Glenn Burt <glenn.b...@glbcc.com> wrote: Has anyone experience with Battle Born lithium batteries? Their price point is better than others we have looked at. From: Dave Angelini Offgrid Solar <mailto:

Re: [RE-wrenches] SimpliPhi Power PHI3.4 Smart -Tech Batteries

2017-08-07 Thread Starlight Solar Power Systems
Hi Jay and Dave, LiFeBlue battery has a wireless Bluetooth monitor that is connected to the BMS in each battery. SoC, current, cycle life, voltage, health, battery faults and more is provided on the free IOS or Android App. Up to 62kWh at 48 volts available today.

Re: [RE-wrenches] Off Grid Refrigeration

2017-06-27 Thread Starlight Solar Power Systems
Hey Drake, Because of the very low cost of producing power by PV solar, I always recommend a standard, high efficiency refrigerator. It doesn’t makes sense to by speciality refrigerators that cost 2-4 times times the price of ‘off the shelf” brands. Many brands have models that use about 1 kWh

Re: [RE-wrenches] Solar over a Pool

2017-06-26 Thread Starlight Solar Power Systems
85°….I wish…it’s 114° here right now. Unshaded pools are unusable for many summer months, even at night, without a refrigeration system. But, in the winter, they need solar gain to reduce heating bills. Not a good plan for a permanent cover. Larry On Jun 26, 2017, at 2:49 PM, Jason

Re: [RE-wrenches] Battery Transport

2017-05-23 Thread Starlight Solar Power Systems
Daunting, an excellent description. Means intimidating, formidable, disconcerting, unnerving, unsettling, dismaying; discouraging, disheartening, and so on. I had to become Hazmat Certified to ship lithium ion batteries….so, yes to all the synonyms. 49 CFR 173 regulates shipment and transport

[RE-wrenches] Outback VFXR3648 failures

2017-05-03 Thread Starlight Solar Power Systems
with these. I want to know if anyone else is having issues with these and is the problem really fixed before I quote another one. Thank you, Larry Crutcher Starlight Solar Power Systems (928) 342-9103 ___ List sponsored by Redwood Alliance List Address: RE

Re: [RE-wrenches] DC Transfer switch

2017-04-12 Thread Starlight Solar Power Systems
Hi Drake, We have been using Gigavac for high current DC switching a few years now. They also switch high voltage DC. Very reliable. See http://www.gigavac.com/catalog/power-products Larry Crutcher Starlight Solar Power Systems On Apr 12, 2017, at 8:45 AM, Drake <drake.cham

Re: [RE-wrenches] High End battery

2017-03-27 Thread Starlight Solar Power Systems
I want to 2nd David’s recommendation for Fullriver. 6 years and many pallet loads sold, only one failure covered by warranty. 7 year warranty when used in RE systems. Best AGM battery we have ever sold. Larry Crutcher Starlight Solar Power Systems On Mar 27, 2017, at 6:33 AM, Dave Palumbo

Re: [RE-wrenches] Aquion Batteries

2017-03-08 Thread Starlight Solar Power Systems
used in the off grid environment. If you can't use it, why do they rate it at 2.4kWh? BTW, the Voltage vs.Energy chart on the spec sheet does not match the first chart I posted." Thank you, Larry Crutcher Starlight Solar Power Systems (928) 342-9103 On Mar 8, 2017, at 2:13 P

Re: [RE-wrenches] Discharging a high voltage battery

2017-02-23 Thread Starlight Solar Power Systems
though – the MPPT circuit on the inverter might just sweep and invert. August From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org <mailto:re-wrenches-boun...@lists.re-wrenches.org>] On Behalf Of Starlight Solar Power Systems Sent: Thursday, February 23, 2017 3:14 PM To:

Re: [RE-wrenches] Discharging a high voltage battery

2017-02-23 Thread Starlight Solar Power Systems
nd LG Chem RESU batteries in the 350 to 400 v range. August From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org <mailto:re-wrenches-boun...@lists.re-wrenches.org>] On Behalf Of Starlight Solar Power Systems Sent: Wednesday, February 22, 2017 11:17 AM To: RE-wrenches

[RE-wrenches] Discharging a high voltage battery

2017-02-22 Thread Starlight Solar Power Systems
but sure bugs me. My uneducated guess is the inverter will be immediately damaged. My thought is how would it limit the input current? Or, is there such an inverter available that can do the job? Any input is appreciated. Larry Crutcher Starlight Solar Power Systems

[RE-wrenches] Using same PV array for water pump, battery charging

2017-02-16 Thread Starlight Solar Power Systems
looking for a switching arrangement to do this without arcing since it will be used a few times each week. Any have a recommendation? Thank you, Larry Crutcher Starlight Solar Power Systems ___ List sponsored by Redwood Alliance List Address: RE

[RE-wrenches] Lithium battery systems

2016-10-14 Thread Starlight Solar Power Systems
Solar Power Systems On Oct 14, 2016, at 9:42 AM, Chris Mason <cometenergysyst...@gmail.com <mailto:cometenergysyst...@gmail.com>> wrote: I'm curious to see if anyone is finding Lithium battery systems available that will be suitable for an Outback Radian based system. Let me know

Re: [RE-wrenches] Rolls Surrette Re-combiner caps.

2016-10-13 Thread Starlight Solar Power Systems
One other advantage, recombination caps wear out. We have had Water Miser caps returned (during upgrade to AGM’s) that are over 10 years old. By washing in baking soda and water, thoroughly rinsing, they continue working. Should last decades. Larry Crutcher Starlight Solar Power Systems

Re: [RE-wrenches] Rolls Surrette Re-combiner caps.

2016-10-13 Thread Starlight Solar Power Systems
please contact the sender and delete or destroy this message and all copies. On Thu, Oct 13, 2016 at 3:33 PM, Starlight Solar Power Systems <la...@starlightsolar.com> wrote: Battery Wrenches, The problem with recombination style caps is they require using a low absorb voltage, about 2.35 to 2

Re: [RE-wrenches] Rolls Surrette Re-combiner caps.

2016-10-13 Thread Starlight Solar Power Systems
. Larry Crutcher Starlight Solar Power Systems On Oct 13, 2016, at 11:02 AM, jay <jay.pe...@gmail.com> wrote: while we are on the subject of recombining caps has anyone used the following. http://www.sbsbattery.com/PDFs/Battery-Recombination-Plug.pdf <http://www.sbsbattery.com/PDF

Re: [RE-wrenches] Fluke 337

2016-09-13 Thread Starlight Solar Power Systems
Hey Drake, I’ve been using a 334 for many years. I recently looked at the 381 because of the wireless removable display. There have been many situations where the wire I’m clamped onto puts the display in a position that I can’t easily read it. Having a wireless display would be SO handy.

Re: [RE-wrenches] Splices in service panel

2016-09-08 Thread Starlight Solar Power Systems
I’m curious. If a critical load center is powered from an alternative source and the main panel is not energized, won’t all neutral conductors still be energized from the sub panel back feeding the main? Or is that OK? Larry On Sep 8, 2016, at 6:43 PM, Ray Walters wrote:

Re: [RE-wrenches] Test procedure for Concorde batteries

2016-09-02 Thread Starlight Solar Power Systems
Solar Power Systems On Sep 2, 2016, at 10:40 AM, Tom Duffy <t...@solar-biz.com> wrote: Gary A number of years ago I designed the back-up system for the Washington DC Metro System communications in conjunction with Apollo Solar. After extensive testing of both the Concorde and Full River

Re: [RE-wrenches] Test procedure for Concorde batteries

2016-09-01 Thread Starlight Solar Power Systems
you, Larry Crutcher Starlight Solar Power Systems (928) 342-9103 On Sep 1, 2016, at 6:19 PM, jay <jay.pe...@gmail.com> wrote: HI Ray, I second your opinion. jay peltz power > On Sep 1, 2016, at 4:43 PM, Ray Walters <r...@solarray.com > <mailto:r...@solarray.com>

[RE-wrenches] Any Exeltech Dealers here?

2016-08-16 Thread Starlight Solar Power Systems
Wrenches, Is anyone setup as a dealer with Exeltech? I need a 22kW MX bi-phase system but they only offer me retail pricing. Please contact off the list: la...@starlightsolar.com Thank you, Larry Crutcher Starlight Solar Power Systems (928) 342-9103

Re: [RE-wrenches] Has anyone had Magnum Energy PT-100 controller failures

2016-07-30 Thread Starlight Solar Power Systems
Perhaps I should rephrase my question: Has anyone else been selling the PT-100? If so, how many? Any failures? Early on a tech told me that I’m the only one experiencing the failures. Larry On Jul 28, 2016, at 4:27 PM, Starlight Solar Power Systems <la...@starlightsolar.com> wrote:

Re: [RE-wrenches] Whisper 100 parts?

2016-07-29 Thread Starlight Solar Power Systems
Have you been here: http://www.luminousrenewable.com/whisper100.php Thank you, Larry Crutcher Starlight Solar Power Systems On Jul 29, 2016, at 11:34 AM, Dan Fink <danbo...@gmail.com> wrote: Wrenches; I was contacted by an individual in remote Alaska who is heavily invested in W

[RE-wrenches] Has anyone had Magnum Energy PT-100 controller failures

2016-07-28 Thread Starlight Solar Power Systems
Hello Battery Wrenches, I have installed about 35 of the Magnum PT-100 charge controllers since November 2015. I have had about 10 fail, another one just today. The problem we have is the same every time: network communications fail which causes other problems until you remove the network

Re: [RE-wrenches] Off grid

2016-07-28 Thread Starlight Solar Power Systems
-watt-high-surge-pure-sine-wave-inverter that works wonders with all kinds of complex loads. Extremely low failures and their customer service is excellent. Thank you, Larry Crutcher Starlight Solar Power Systems On Jul 28, 2016, at 10:21 AM, frenergy <frene...@psln.com> wrote: Off-gr

[RE-wrenches] Off grid in Blythe, AZ

2016-07-22 Thread Starlight Solar Power Systems
Is anyone interested in building an off grid system in Blythe, CA? Contact me off the list la...@starlightsolar.com Thank you, Larry ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email

Re: [RE-wrenches] Replacing grounded inverters

2016-07-22 Thread Starlight Solar Power Systems
Be nice William ;-) Hi Gary, DC can not be transformed without converting it to AC first then back to DC again. Probably not feasible to do while tracking the MMP. Larry Crutcher Starlight Solar Power Systems On Jul 22, 2016, at 12:50 PM, William Miller <will...@millersolar.com>

Re: [RE-wrenches] PV output but no power

2016-07-02 Thread Starlight Solar Power Systems
them with remanufactured units. Bill, the typical failure is Voc of about 10 volts. However, the failure can be intermittent. For this reason, any modules in the date period should be replaced even though they appear to test OK. Larry Crutcher Starlight Solar Power Systems On Jul 2, 2016

Re: [RE-wrenches] Whisper Turbine Replacement

2016-05-06 Thread Starlight Solar Power Systems
How about another Whisper? http://luminousrenewable.com/whisper200.php I don’t know of much else in that size and price range. Thank you, Larry Crutcher On May 6, 2016, at 11:41 AM, Jeremy Rodriguez wrote: Hello Does anyone have a recommended replacement turbine for

Re: [RE-wrenches] Off-grid generator update?

2016-05-05 Thread Starlight Solar Power Systems
Aurora generators can be used in all off grid applications with full warranty. http://www.auroragenerators.com/generators Larry Crutcher Starlight Solar Power Systems On May 5, 2016, at 8:11 AM, Luke Christy <sgsrenewab...@gmail.com> wrote: Hi Wrenches, I have been following this

Re: [RE-wrenches] Winter Battery Maintenance

2016-05-02 Thread Starlight Solar Power Systems
term seasonal storage, that is all I > recommend anymore. > > Larry Crutcher > Starlight Solar Power Systems > > > > On Apr 30, 2016, at 12:54 PM, Dana < > <mailto:d...@solarwork.com>d...@solarwork.com <mailto:d...@solarwork.com>> > wrot

Re: [RE-wrenches] Winter Battery Maintenance

2016-05-01 Thread Starlight Solar Power Systems
for long term non-use. You can simply discharge the battery to 50% then turn off the battery and walk away. When you return in 6-7 months, you will find it at the same SoC as when you left. For long term seasonal storage, that is all I recommend anymore. Larry Crutcher Starlight Solar Power Systems

Re: [RE-wrenches] Winter Battery Maintenance

2016-04-30 Thread Starlight Solar Power Systems
I agree with Todd and Bob, leave the PV solar on, EQ off. I also instruct my customers to reduce the absorb timer to 0.1 hours. Since the battery is staying full, there is no need to spend time above cell gassing point which will increase water loss. Larry On Apr 30, 2016, at 10:28 AM, RE

[RE-wrenches] time delay relay

2016-04-27 Thread Starlight Solar Power Systems
timer has finished. Does anyone know what this type is called or any other help? Thank you, Larry Crutcher Starlight Solar Power Systems ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email

Re: [RE-wrenches] Inverter/AC pump compatibility question

2016-04-26 Thread Starlight Solar Power Systems
You can tell the grey-beards from younger wrenches…..A square wave is generated and modified to act like a sine wave, thus, it is a modified square wave. As I see it, in order to deceive the consumer, the term "modified sine wave" was created. Larry On Apr 26, 2016, at 5:57 AM, Carl Hansen